  #1   Report Post  
rchtravel
 
Posts: n/a
Default Installing a sub panel from a sub panel

Yeah I know, the title is interesting huh? Let me explain...I bought
a 26 year old house and gutted it replacing just about all the wiring
except for some of the ceiling light runs. The original main panel is
100 amp and because of an addition that was built, another 100 amp
sub-panel was installed 18" away and next to the "main" panel. This
was done by a professional electrician with the proper permits pulled
and final inspection was approved about 2 years ago (the state is MI
by-the-way). Oh, and he also replaced and installed new wire from the
transformer on the pole to the original 100 amp house panel.

NOW MY QUESTION:

I have a barn that needs power and requires a wire run of about 75-80
feet (actual run length from box to box, not just the distance from
house to barn). What I would like to do is run direct bury, #2
aluminum (4 wire) from a 100 amp breaker in the house sub-panel,
underground to another 100 amp sub-panel in the barn. The electrician
I hired 2 years ago said that doing so would not be a problem as long
as the 2nd sub panel in the barn was properly grounded. I would like
other opinions or advice on this please.

Why 100 amp instead of 60 amp in the barn you ask? Why not, besides I
already have a Square D 100 amp panel I bought that was much cheaper
than 60 amp panels I looked at, not to mention the expandability 100
amps offers. In the barn I plan to run lights, 20 amp power outlets,
an air compressor (220), small arch welder (220), gas furnace, and
typical power tools such as a table saw, drill press, etc...

Of course, if my "plans" aren't safe, than I would certainly change
whatever was needed to be considered safe. That's why I'm asking for
feedback from this group. In hind-sight, I really wish I would have
bought a new 200 amp panel when I remodeled the house. Ah...if only I
knew everything....lol

Thank you in advance, it's appreciated!

RC
  #2   Report Post  
Bill
 
Posts: n/a
Default Installing a sub panel from a sub panel

I would connect the new subpanel to your main electrical panel. The reason
for this is if you have overloading problems in the future. Then you would
only need to upgrade your main panel/service to 200 amps and not mess with
either subpanel.


"rchtravel" wrote in message
Yeah I know, the title is interesting huh? Let me explain...I bought
a 26 year old house and gutted it replacing just about all the wiring
except for some of the ceiling light runs. The original main panel is
100 amp and because of an addition that was built, another 100 amp
sub-panel was installed 18" away and next to the "main" panel. This
was done by a professional electrician with the proper permits pulled
and final inspection was approved about 2 years ago (the state is MI
by-the-way). Oh, and he also replaced and installed new wire from the
transformer on the pole to the original 100 amp house panel.

NOW MY QUESTION:

I have a barn that needs power and requires a wire run of about 75-80
feet (actual run length from box to box, not just the distance from
house to barn). What I would like to do is run direct bury, #2
aluminum (4 wire) from a 100 amp breaker in the house sub-panel,
underground to another 100 amp sub-panel in the barn. The electrician
I hired 2 years ago said that doing so would not be a problem as long
as the 2nd sub panel in the barn was properly grounded. I would like
other opinions or advice on this please.

Why 100 amp instead of 60 amp in the barn you ask? Why not, besides I
already have a Square D 100 amp panel I bought that was much cheaper
than 60 amp panels I looked at, not to mention the expandability 100
amps offers. In the barn I plan to run lights, 20 amp power outlets,
an air compressor (220), small arch welder (220), gas furnace, and
typical power tools such as a table saw, drill press, etc...

Of course, if my "plans" aren't safe, than I would certainly change
whatever was needed to be considered safe. That's why I'm asking for
feedback from this group. In hind-sight, I really wish I would have
bought a new 200 amp panel when I remodeled the house. Ah...if only I
knew everything....lol

Thank you in advance, it's appreciated!

RC



  #3   Report Post  
SQLit
 
Posts: n/a
Default Installing a sub panel from a sub panel


"Bill" wrote in message
...
I would connect the new subpanel to your main electrical panel. The reason
for this is if you have overloading problems in the future. Then you would
only need to upgrade your main panel/service to 200 amps and not mess with
either subpanel.


Snipped


Why 100 amp instead of 60 amp in the barn you ask? Why not, besides I
already have a Square D 100 amp panel I bought that was much cheaper
than 60 amp panels I looked at, not to mention the expandability 100
amps offers. In the barn I plan to run lights, 20 amp power outlets,
an air compressor (220), small arch welder (220), gas furnace, and
typical power tools such as a table saw, drill press, etc...

Of course, if my "plans" aren't safe, than I would certainly change
whatever was needed to be considered safe. That's why I'm asking for
feedback from this group. In hind-sight, I really wish I would have
bought a new 200 amp panel when I remodeled the house. Ah...if only I
knew everything....lol

Thank you in advance, it's appreciated!

RC

I agree completely. Install the new barn breaker in the main panel. Glad
to hear you going 4 wire.
If your careful you will not have a problem. Unless your trying to build an
project and your house is all electric. Which with an 100 amp service I will
bet you have some gas appliances.

Years ago I fed a residence (reasons are way to hard to explain) from a 60
amp 2 pole breaker. Unless the washer, dryer, oven were on every thing
worked fine until I changed it over to the utility some 2 years later. They
did trip 4-5 times those years but that is not bad. I owned a home in
Phoenix, 2 a/c's electric water heater, stove, and 3 swamp coolers. I
measured the conductors at the roof, pulling about 50 amps with everything
on.



  #4   Report Post  
Takoma Park Volunteer Fire Department Postmaster
 
Posts: n/a
Default Installing a sub panel from a sub panel

rchtravel wrote:
Yeah I know, the title is interesting huh? Let me explain...I bought
a 26 year old house and gutted it replacing just about all the wiring
except for some of the ceiling light runs. The original main panel is
100 amp and because of an addition that was built, another 100 amp
sub-panel was installed 18" away and next to the "main" panel. This
was done by a professional electrician with the proper permits pulled
and final inspection was approved about 2 years ago (the state is MI
by-the-way). Oh, and he also replaced and installed new wire from the
transformer on the pole to the original 100 amp house panel.

NOW MY QUESTION:

I have a barn that needs power and requires a wire run of about 75-80
feet (actual run length from box to box, not just the distance from
house to barn). What I would like to do is run direct bury, #2
aluminum (4 wire) from a 100 amp breaker in the house sub-panel,
underground to another 100 amp sub-panel in the barn. The electrician
I hired 2 years ago said that doing so would not be a problem as long
as the 2nd sub panel in the barn was properly grounded. I would like
other opinions or advice on this please.

Why 100 amp instead of 60 amp in the barn you ask? Why not, besides I
already have a Square D 100 amp panel I bought that was much cheaper
than 60 amp panels I looked at, not to mention the expandability 100
amps offers. In the barn I plan to run lights, 20 amp power outlets,
an air compressor (220), small arch welder (220), gas furnace, and
typical power tools such as a table saw, drill press, etc...

Of course, if my "plans" aren't safe, than I would certainly change
whatever was needed to be considered safe. That's why I'm asking for
feedback from this group. In hind-sight, I really wish I would have
bought a new 200 amp panel when I remodeled the house. Ah...if only I
knew everything....lol

Thank you in advance, it's appreciated!

RC


If your service load calculations indicate that your total load,
including the barn, will not exceed 100 amps then you can proceed as you
outlined. You do, however, have some alternatives you might want to
consider.

If you are in the US you can install a large NEMA 3R box at the meter in
which you can tap off a new service lateral to your barn. Those
conductors must remain entirely outside of your house. That lateral
would be three wire and you would wire the barn exactly as you would a
new service.

If the load exceeds the ampacity of the present service you can do a
heavy up by using a new service equipment panel to supply feeders to
both of your existing house panels and the new panel in the barn. Then
you can supply four wire feeders to each of the three panels. This
eliminates the cost of rewiring the existing circuits but you will have
to separate the Equipment Grounding Conductors, if any, from the
neutrals in the panels that are supplied by feeders. It may not be
practical to do that if the panels are of the older type that are only
suitable for use as service equipment.
--
Tom H

  #5   Report Post  
zxcvbob
 
Posts: n/a
Default Installing a sub panel from a sub panel

rchtravel wrote:

Yeah I know, the title is interesting huh? Let me explain...I bought
a 26 year old house and gutted it replacing just about all the wiring
except for some of the ceiling light runs. The original main panel is
100 amp and because of an addition that was built, another 100 amp
sub-panel was installed 18" away and next to the "main" panel. This
was done by a professional electrician with the proper permits pulled
and final inspection was approved about 2 years ago (the state is MI
by-the-way). Oh, and he also replaced and installed new wire from the
transformer on the pole to the original 100 amp house panel.

NOW MY QUESTION:

I have a barn that needs power and requires a wire run of about 75-80
feet (actual run length from box to box, not just the distance from
house to barn). What I would like to do is run direct bury, #2
aluminum (4 wire) from a 100 amp breaker in the house sub-panel,
underground to another 100 amp sub-panel in the barn. The electrician
I hired 2 years ago said that doing so would not be a problem as long
as the 2nd sub panel in the barn was properly grounded. I would like
other opinions or advice on this please.

Why 100 amp instead of 60 amp in the barn you ask? Why not, besides I
already have a Square D 100 amp panel I bought that was much cheaper
than 60 amp panels I looked at, not to mention the expandability 100
amps offers. In the barn I plan to run lights, 20 amp power outlets,
an air compressor (220), small arch welder (220), gas furnace, and
typical power tools such as a table saw, drill press, etc...

Of course, if my "plans" aren't safe, than I would certainly change
whatever was needed to be considered safe. That's why I'm asking for
feedback from this group. In hind-sight, I really wish I would have
bought a new 200 amp panel when I remodeled the house. Ah...if only I
knew everything....lol

Thank you in advance, it's appreciated!

RC




Run the 100A subpanel feeder off a 60A or 70A breaker; it will be plenty of
capacity for what you are doing, the breaker will be a lot cheaper, and the
feeder conductors can be a lot smaller and cheaper.

-bob


  #6   Report Post  
SueMarkP
 
Posts: n/a
Default Installing a sub panel from a sub panel

"zxcvbob" wrote in message
...
rchtravel wrote:
I have a barn that needs power and requires a wire run of about 75-80
feet (actual run length from box to box, not just the distance from
house to barn). What I would like to do is run direct bury, #2
aluminum (4 wire) from a 100 amp breaker in the house sub-panel,
underground to another 100 amp sub-panel in the barn. The electrician
I hired 2 years ago said that doing so would not be a problem as long
as the 2nd sub panel in the barn was properly grounded. I would like
other opinions or advice on this please.

Why 100 amp instead of 60 amp in the barn you ask? Why not, besides I
already have a Square D 100 amp panel I bought that was much cheaper
than 60 amp panels I looked at, not to mention the expandability 100
amps offers. In the barn I plan to run lights, 20 amp power outlets,
an air compressor (220), small arch welder (220), gas furnace, and
typical power tools such as a table saw, drill press, etc...

Of course, if my "plans" aren't safe, than I would certainly change
whatever was needed to be considered safe. That's why I'm asking for
feedback from this group. In hind-sight, I really wish I would have
bought a new 200 amp panel when I remodeled the house. Ah...if only I
knew everything....lol


Run the 100A subpanel feeder off a 60A or 70A breaker; it will be plenty

of
capacity for what you are doing, the breaker will be a lot cheaper, and

the
feeder conductors can be a lot smaller and cheaper.

-bob


I agree with this and would recommend taking it off the first panel or
whichever panel makes the wires long enough to reach either panel should you
upgrade one of them to 200A. Main reason being do you have any more neutral
lugs that can take a #2 wire? Do you have proper bending space for a #2
wire? Those big neutral lugs tend to disappear quickly. If you only have #4
holes, then a 60A feeder would be good with aluminum wire.

Its OK to feed a 100A panel with a 60A feeder.

--
Mark
Kent, WA


  #7   Report Post  
John Grabowski
 
Posts: n/a
Default Installing a sub panel from a sub panel

In addition to what the other posters have said, I would add this: Avoid
direct burial of aluminum wire. Even though aluminum is approved for the
purpose, if it is not installed carefully under optimum conditions the
failure of the wire can be premature. If you want to use aluminum wire, use
single conductors pulled into conduit such as PVC.


John Grabowski
http://www.mrelectrician.tv




"rchtravel" wrote in message
om...
Yeah I know, the title is interesting huh? Let me explain...I bought
a 26 year old house and gutted it replacing just about all the wiring
except for some of the ceiling light runs. The original main panel is
100 amp and because of an addition that was built, another 100 amp
sub-panel was installed 18" away and next to the "main" panel. This
was done by a professional electrician with the proper permits pulled
and final inspection was approved about 2 years ago (the state is MI
by-the-way). Oh, and he also replaced and installed new wire from the
transformer on the pole to the original 100 amp house panel.

NOW MY QUESTION:

I have a barn that needs power and requires a wire run of about 75-80
feet (actual run length from box to box, not just the distance from
house to barn). What I would like to do is run direct bury, #2
aluminum (4 wire) from a 100 amp breaker in the house sub-panel,
underground to another 100 amp sub-panel in the barn. The electrician
I hired 2 years ago said that doing so would not be a problem as long
as the 2nd sub panel in the barn was properly grounded. I would like
other opinions or advice on this please.

Why 100 amp instead of 60 amp in the barn you ask? Why not, besides I
already have a Square D 100 amp panel I bought that was much cheaper
than 60 amp panels I looked at, not to mention the expandability 100
amps offers. In the barn I plan to run lights, 20 amp power outlets,
an air compressor (220), small arch welder (220), gas furnace, and
typical power tools such as a table saw, drill press, etc...

Of course, if my "plans" aren't safe, than I would certainly change
whatever was needed to be considered safe. That's why I'm asking for
feedback from this group. In hind-sight, I really wish I would have
bought a new 200 amp panel when I remodeled the house. Ah...if only I
knew everything....lol

Thank you in advance, it's appreciated!

RC



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service panel upgrade question Speedy Jim Home Repair 5 December 14th 03 06:17 AM
Help upgrading Service panel from 60A to 125A, please. DaveG Home Repair 33 December 3rd 03 04:57 AM
Since I don't have any plans...whatsa best way to secure desk's back panel to side panels? (and other questions) Leon Woodworking 5 August 27th 03 05:08 AM


All times are GMT +1. The time now is 09:27 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"