  #1   Report Post  
Barb Grajewski
 
Posts: n/a
Default high GFA plenum temps?


30+ year old GFA furnace, hoping to have it squeak through one more
winter. New to this home, old owner wasn't very good about routine
maintenance. Replaced the furnace filter right away; it was clogged
with dog hair and dust...

At the pre-sale home inspection, the inspector noted that the
temperature in the plenum was running high. I don't have the exact
figure, but the registers in the room directly above the furnace get
REALLY hot to the touch, way too hot to me. My impression is that the
blower isn't really blowing all that well, either.

Questions:
1) could there be dirt and crap further up in the system (A-coil??)
causing air flow restriction and the high temps at the plenum and near
registers? How to check? How to clean?

2) Calling in the HVAC guy is on the to-do list, but they're really
booked up right now. What minor stuff can we do (cleaning, examining)
until the HVAC guy comes to do the winter inspection/tune-up??

3) Is it dangerous to have such high plenum temp? Furnace is not short
cycling, or acting wacky in any other ways..

  #2   Report Post  
John Gilmer
 
Posts: n/a
Default high GFA plenum temps?


"Barb Grajewski" wrote in message
...

30+ year old GFA furnace, hoping to have it squeak through one more
winter. New to this home, old owner wasn't very good about routine
maintenance. Replaced the furnace filter right away; it was clogged
with dog hair and dust...

At the pre-sale home inspection, the inspector noted that the
temperature in the plenum was running high. I don't have the exact
figure, but the registers in the room directly above the furnace get
REALLY hot to the touch, way too hot to me. My impression is that the
blower isn't really blowing all that well, either.

Questions:
1) could there be dirt and crap further up in the system (A-coil??)


Yes!

If you even suspect that the furnace was operated without an air filter for
a time, you should try to gain access to the upstream side of the "A" coil.
Often, this requires you to party removing the coil (the line set has some
flexibility.)

BUT another cause of over heating in the ducts is a leak in the heat
exchanger.

IF you have a leak you call in the HVAC guys for replacement estimates. If
you just have a very dirty A-coil and don't want to move the line set to
clean it be prepared to pay $100 to $200 for a pro to come in and do it for
you.

IF you have such a leak a digital CO detector on an outlet MIGHT detect a
problem (you should have a digital CO detector whenever you have gas burning
in your house.

Frankly, if you have already planned to change out the unit, you might as
well do it before the start of the heating season.

How hot is too hot?

Some 30 years ago, the fan control was set to not turn on until the
temperature reached 130 or more and shut off when the temperature went down
to about 110. If you have a thermometer (digital) you can insert in the
duct (drill a hole and cover it with alluminum duct take afterward) take an
accurate measurement.


  #3   Report Post  
John Gilmer
 
Posts: n/a
Default high GFA plenum temps?


"Barb Grajewski" wrote in message
...

30+ year old GFA furnace, hoping to have it squeak through one more
winter. New to this home, old owner wasn't very good about routine
maintenance. Replaced the furnace filter right away; it was clogged
with dog hair and dust...

At the pre-sale home inspection, the inspector noted that the
temperature in the plenum was running high. I don't have the exact
figure, but the registers in the room directly above the furnace get
REALLY hot to the touch, way too hot to me. My impression is that the
blower isn't really blowing all that well, either.

Questions:
1) could there be dirt and crap further up in the system (A-coil??)


Yes!

If you even suspect that the furnace was operated without an air filter for
a time, you should try to gain access to the upstream side of the "A" coil.
Often, this requires you to party removing the coil (the line set has some
flexibility.)

BUT another cause of over heating in the ducts is a leak in the heat
exchanger.

IF you have a leak you call in the HVAC guys for replacement estimates. If
you just have a very dirty A-coil and don't want to move the line set to
clean it be prepared to pay $100 to $200 for a pro to come in and do it for
you.

IF you have such a leak a digital CO detector on an outlet MIGHT detect a
problem (you should have a digital CO detector whenever you have gas burning
in your house.

Frankly, if you have already planned to change out the unit, you might as
well do it before the start of the heating season.

How hot is too hot?

Some 30 years ago, the fan control was set to not turn on until the
temperature reached 130 or more and shut off when the temperature went down
to about 110. If you have a thermometer (digital) you can insert in the
duct (drill a hole and cover it with alluminum duct take afterward) take an
accurate measurement.


  #4   Report Post  
Darrell
 
Posts: n/a
Default high GFA plenum temps?

John Gilmer wrote:
"Barb Grajewski" wrote in message
...

30+ year old GFA furnace, hoping to have it squeak through one more
winter. New to this home, old owner wasn't very good about routine
maintenance. Replaced the furnace filter right away; it was clogged
with dog hair and dust...

At the pre-sale home inspection, the inspector noted that the
temperature in the plenum was running high. I don't have the exact
figure, but the registers in the room directly above the furnace get
REALLY hot to the touch, way too hot to me. My impression is that the
blower isn't really blowing all that well, either.

Questions:
1) could there be dirt and crap further up in the system (A-coil??)

Yes! If you even suspect that the furnace was operated without an air filter for
a time, you should try to gain access to the upstream side of the "A" coil.
Often, this requires you to partly remove the coil (the line set has some
flexibility.)

BUT another cause of over heating in the ducts is a leak in the heat
exchanger.

IF you have a leak you call in the HVAC guys for replacement estimates. If
you just have a very dirty A-coil and don't want to move the line set to
clean it be prepared to pay $100 to $200 for a pro to come in and do it for
you.

IF you have such a leak a digital CO detector on an outlet MIGHT detect a
problem (you should have a digital CO detector whenever you have gas burning
in your house.

Frankly, if you have already planned to change out the unit, you might as
well do it before the start of the heating season.

How hot is too hot?

Some 30 years ago, the fan control was set to not turn on until the
temperature reached 130 or more and shut off when the temperature went down
to about 110. If you have a thermometer (digital) you can insert in the
duct (drill a hole and cover it with alluminum duct take afterward) take an
accurate measurement.


Excellent advice, John.

When filters get too loaded they begin bypassing dirt and lint,
therefore the blower wheel and the E-Coil are both due for a thorough
cleaning. I doubt you will find a tech that will do it for 200.

http://www.udarrell.com/air-conditioning-seer.html

Thirty years is long enough, I would have a new unit installed asap.
Also, have the duct system and airflow cfm checked, and if it were me, I
would install a new 12 SEER high efficiency matched AC system.
Darrell - udarrell

--
Get the Cooling Capacity and Efficiency you Paid for -
http://www.udarrell.com/air-conditio...city-seer.html

  #5   Report Post  
Darrell
 
Posts: n/a
Default high GFA plenum temps?

John Gilmer wrote:
"Barb Grajewski" wrote in message
...

30+ year old GFA furnace, hoping to have it squeak through one more
winter. New to this home, old owner wasn't very good about routine
maintenance. Replaced the furnace filter right away; it was clogged
with dog hair and dust...

At the pre-sale home inspection, the inspector noted that the
temperature in the plenum was running high. I don't have the exact
figure, but the registers in the room directly above the furnace get
REALLY hot to the touch, way too hot to me. My impression is that the
blower isn't really blowing all that well, either.

Questions:
1) could there be dirt and crap further up in the system (A-coil??)

Yes! If you even suspect that the furnace was operated without an air filter for
a time, you should try to gain access to the upstream side of the "A" coil.
Often, this requires you to partly remove the coil (the line set has some
flexibility.)

BUT another cause of over heating in the ducts is a leak in the heat
exchanger.

IF you have a leak you call in the HVAC guys for replacement estimates. If
you just have a very dirty A-coil and don't want to move the line set to
clean it be prepared to pay $100 to $200 for a pro to come in and do it for
you.

IF you have such a leak a digital CO detector on an outlet MIGHT detect a
problem (you should have a digital CO detector whenever you have gas burning
in your house.

Frankly, if you have already planned to change out the unit, you might as
well do it before the start of the heating season.

How hot is too hot?

Some 30 years ago, the fan control was set to not turn on until the
temperature reached 130 or more and shut off when the temperature went down
to about 110. If you have a thermometer (digital) you can insert in the
duct (drill a hole and cover it with alluminum duct take afterward) take an
accurate measurement.


Excellent advice, John.

When filters get too loaded they begin bypassing dirt and lint,
therefore the blower wheel and the E-Coil are both due for a thorough
cleaning. I doubt you will find a tech that will do it for 200.

http://www.udarrell.com/air-conditioning-seer.html

Thirty years is long enough, I would have a new unit installed asap.
Also, have the duct system and airflow cfm checked, and if it were me, I
would install a new 12 SEER high efficiency matched AC system.
Darrell - udarrell

--
Get the Cooling Capacity and Efficiency you Paid for -
http://www.udarrell.com/air-conditio...city-seer.html



  #6   Report Post  
CBHvac
 
Posts: n/a
Default high GFA plenum temps?


"Darrell" wrote in message
...
John Gilmer wrote:
"Barb Grajewski" wrote in message
...

30+ year old GFA furnace, hoping to have it squeak through one more
winter. New to this home, old owner wasn't very good about routine
maintenance. Replaced the furnace filter right away; it was clogged
with dog hair and dust...

At the pre-sale home inspection, the inspector noted that the
temperature in the plenum was running high. I don't have the exact
figure, but the registers in the room directly above the furnace get
REALLY hot to the touch, way too hot to me. My impression is that the
blower isn't really blowing all that well, either.

Questions:
1) could there be dirt and crap further up in the system (A-coil??)

Yes! If you even suspect that the furnace was operated without an air

filter for
a time, you should try to gain access to the upstream side of the "A"

coil.
Often, this requires you to partly remove the coil (the line set has

some
flexibility.)

BUT another cause of over heating in the ducts is a leak in the heat
exchanger.

IF you have a leak you call in the HVAC guys for replacement estimates.

If
you just have a very dirty A-coil and don't want to move the line set to
clean it be prepared to pay $100 to $200 for a pro to come in and do it

for
you.

IF you have such a leak a digital CO detector on an outlet MIGHT detect

a
problem (you should have a digital CO detector whenever you have gas

burning
in your house.

Frankly, if you have already planned to change out the unit, you might

as
well do it before the start of the heating season.

How hot is too hot?

Some 30 years ago, the fan control was set to not turn on until the
temperature reached 130 or more and shut off when the temperature went

down
to about 110. If you have a thermometer (digital) you can insert in

the
duct (drill a hole and cover it with alluminum duct take afterward) take

an
accurate measurement.


Excellent advice, John.

When filters get too loaded they begin bypassing dirt and lint,
therefore the blower wheel and the E-Coil are both due for a thorough
cleaning. I doubt you will find a tech that will do it for 200.


Actually....

When a filter is brand new, dirt will tend to pass right through
it....filters do not start to filter at capacity until they load up a bit...
That old of a furnce I am sure cant take the added static that a 3M or
AirBear filter would add, but pleated paper, as all of us in the trade know
is the way to go...and I am sure that the A coil, or slab is clogged, and
the blowers prob toast as well in regards to being full of crap.

A proper filter fit, wont bypass a thing...much less air....unless the
blower is strong enough to allow for sucking the filter from its
mounts...and thats more rare than it is common.

BTW...I have done an evap coil, blower, AND HE clean for under
$200..recently...all shes got to do is shop around...it depends on more
factors than we need to get into here, and her area, but in some parts of
the country, $200 might be considered high, while I know in others it wont
get the tech to the door.


http://www.udarrell.com/air-conditioning-seer.html

Thirty years is long enough, I would have a new unit installed asap.
Also, have the duct system and airflow cfm checked, and if it were me, I
would install a new 12 SEER high efficiency matched AC system.
Darrell - udarrell


Only 12SEER? We stopped offering 10SEER a while back..stopped selling 80%
units as well. Now, a savy shopper can find that the 14SEER units are
running what a 12 was a couple of years ago....but higher SEER, in SOME
parts of the country, will not always equal a savings.


--
Get the Cooling Capacity and Efficiency you Paid for -
http://www.udarrell.com/air-conditio...city-seer.html



  #7   Report Post  
CBHvac
 
Posts: n/a
Default high GFA plenum temps?


"Darrell" wrote in message
...
John Gilmer wrote:
"Barb Grajewski" wrote in message
...

30+ year old GFA furnace, hoping to have it squeak through one more
winter. New to this home, old owner wasn't very good about routine
maintenance. Replaced the furnace filter right away; it was clogged
with dog hair and dust...

At the pre-sale home inspection, the inspector noted that the
temperature in the plenum was running high. I don't have the exact
figure, but the registers in the room directly above the furnace get
REALLY hot to the touch, way too hot to me. My impression is that the
blower isn't really blowing all that well, either.

Questions:
1) could there be dirt and crap further up in the system (A-coil??)

Yes! If you even suspect that the furnace was operated without an air

filter for
a time, you should try to gain access to the upstream side of the "A"

coil.
Often, this requires you to partly remove the coil (the line set has

some
flexibility.)

BUT another cause of over heating in the ducts is a leak in the heat
exchanger.

IF you have a leak you call in the HVAC guys for replacement estimates.

If
you just have a very dirty A-coil and don't want to move the line set to
clean it be prepared to pay $100 to $200 for a pro to come in and do it

for
you.

IF you have such a leak a digital CO detector on an outlet MIGHT detect

a
problem (you should have a digital CO detector whenever you have gas

burning
in your house.

Frankly, if you have already planned to change out the unit, you might

as
well do it before the start of the heating season.

How hot is too hot?

Some 30 years ago, the fan control was set to not turn on until the
temperature reached 130 or more and shut off when the temperature went

down
to about 110. If you have a thermometer (digital) you can insert in

the
duct (drill a hole and cover it with alluminum duct take afterward) take

an
accurate measurement.


Excellent advice, John.

When filters get too loaded they begin bypassing dirt and lint,
therefore the blower wheel and the E-Coil are both due for a thorough
cleaning. I doubt you will find a tech that will do it for 200.


Actually....

When a filter is brand new, dirt will tend to pass right through
it....filters do not start to filter at capacity until they load up a bit...
That old of a furnce I am sure cant take the added static that a 3M or
AirBear filter would add, but pleated paper, as all of us in the trade know
is the way to go...and I am sure that the A coil, or slab is clogged, and
the blowers prob toast as well in regards to being full of crap.

A proper filter fit, wont bypass a thing...much less air....unless the
blower is strong enough to allow for sucking the filter from its
mounts...and thats more rare than it is common.

BTW...I have done an evap coil, blower, AND HE clean for under
$200..recently...all shes got to do is shop around...it depends on more
factors than we need to get into here, and her area, but in some parts of
the country, $200 might be considered high, while I know in others it wont
get the tech to the door.


http://www.udarrell.com/air-conditioning-seer.html

Thirty years is long enough, I would have a new unit installed asap.
Also, have the duct system and airflow cfm checked, and if it were me, I
would install a new 12 SEER high efficiency matched AC system.
Darrell - udarrell


Only 12SEER? We stopped offering 10SEER a while back..stopped selling 80%
units as well. Now, a savy shopper can find that the 14SEER units are
running what a 12 was a couple of years ago....but higher SEER, in SOME
parts of the country, will not always equal a savings.


--
Get the Cooling Capacity and Efficiency you Paid for -
http://www.udarrell.com/air-conditio...city-seer.html



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got zapped by T.V. high voltage Arnold stewart Electronics Repair 7 May 15th 04 12:27 AM
Need High Meg Resistor Source Kim Roland Electronics 2 March 12th 04 09:11 PM
high voltage regulation in monitor Reinhard Electronics Repair 2 November 28th 03 02:52 PM
High voltage problem with JVC AV27BP4 TV James Peverill Electronics Repair 0 October 15th 03 04:28 AM
JVC colorTV AV-25F1EG high voltage problem? blabla Electronics Repair 4 August 31st 03 03:41 PM


All times are GMT +1. The time now is 12:27 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"