"Open rollout switch circuit" error message in furnace.
"Open rollout switch circuit" error message in furnace.
A friend called me and said his gas furnace keeps shutting off. It's fairly new and a high effencincy type, which vents out thru PVC. It has a digital readout which says "Open rollout switch circuit". I googled that, and found a simple drawing which shows it as a sort of sensor, and found a picture of one. Not much more. I emailed him the pictures and told him to shut off the power and set his meter to OHMS and check that switch. He said there are two of them and they are both turned to the ON or CLOSED position (Not open). The outside temperature is well below zero, and he has kids, so I told him he better just call a furnace repair company. If it was an older furnace I could probably fix it, (assuming I could get parts), but I dont know anything about these "computerized" furnaces. He called a furnace company, the guy is swamped with calls, but said he will come as soon as he can, but that could be several hours. The guy told him to use space heaters till he gets there. Even if I thought I could help, I doubt my truck will start in this cold, so it dont make any sense to try, knowing nothing about these kind of furnaces. All I know is that it's a Lennox and it's giving that error code. While I'm sure the furnace repair guy will get there before I even get a reply on here, I thought I'd post this to see if any of you know anything about it... I always like to learn new home repair stuff. What's the purpose of these switches and what could be wrong? I did tell the guy to make sure his intake and output pipes were not clogged outdoors. He said they are fine! He also tried another thermostat, since he had saved the old standard one when he replaced it with a programmable one last fall. That did not change anything, so we know the t-stat is not the cause. Anyone? |
#2
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Monday, January 11, 2016 at 12:53:09 AM UTC-6, wrote:
"Open rollout switch circuit" error message in furnace. A friend called me and said his gas furnace keeps shutting off. It's fairly new and a high effencincy type, which vents out thru PVC. It has a digital readout which says "Open rollout switch circuit". I googled that, and found a simple drawing which shows it as a sort of sensor, and found a picture of one. Not much more. I emailed him the pictures and told him to shut off the power and set his meter to OHMS and check that switch. He said there are two of them and they are both turned to the ON or CLOSED position (Not open). The outside temperature is well below zero, and he has kids, so I told him he better just call a furnace repair company. If it was an older furnace I could probably fix it, (assuming I could get parts), but I dont know anything about these "computerized" furnaces. He called a furnace company, the guy is swamped with calls, but said he will come as soon as he can, but that could be several hours. The guy told him to use space heaters till he gets there. Even if I thought I could help, I doubt my truck will start in this cold, so it dont make any sense to try, knowing nothing about these kind of furnaces. All I know is that it's a Lennox and it's giving that error code. While I'm sure the furnace repair guy will get there before I even get a reply on here, I thought I'd post this to see if any of you know anything about it... I always like to learn new home repair stuff. What's the purpose of these switches and what could be wrong? I did tell the guy to make sure his intake and output pipes were not clogged outdoors. He said they are fine! He also tried another thermostat, since he had saved the old standard one when he replaced it with a programmable one last fall. That did not change anything, so we know the t-stat is not the cause. Anyone? He should make sure nothing is blocking the flue. If the flames are backing up from the burners(roll out) like something is blocking the exhaust, it could cause a fire. The rollout switch/sensor is such an important safety device that the furnace control will not allow the furnace to operate if the switch is not working. If the flue is blocked, flames could have hit the rollout sensor or wiring multiple times causing a failure. I'd check the rollout switch and wiring, repair it or the connections and see if the furnace will startup. If it's a simple Klixon thermostat switch, it can be jumped out for testing purposes only. It will look like one of the thermostat switches on the manufacturer's website. ^_^ http://www.sensata.com/klixon/thermo...ision-7bt2.htm [8~{} Uncle Rollout Monster |
#3
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
|
#4
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
|
#6
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On 1/11/2016 1:47 AM, ir wrote:
"Open rollout switch circuit" error message in furnace. A friend called me and said his gas furnace keeps shutting off. It's fairly new and a high effencincy type, which vents out thru PVC. It has a digital readout which says "Open rollout switch circuit". I googled that, and found a simple drawing which shows it as a sort of sensor, and found a picture of one. Not much more. I emailed him the pictures and told him to shut off the power and set his meter to OHMS and check that switch. He said there are two of them and they are both turned to the ON or CLOSED position (Not open). The outside temperature is well below zero, and he has kids, so I told him he better just call a furnace repair company. If it was an older furnace I could probably fix it, (assuming I could get parts), but I dont know anything about these "computerized" furnaces. He called a furnace company, the guy is swamped with calls, but said he will come as soon as he can, but that could be several hours. The guy told him to use space heaters till he gets there. Even if I thought I could help, I doubt my truck will start in this cold, so it dont make any sense to try, knowing nothing about these kind of furnaces. All I know is that it's a Lennox and it's giving that error code. While I'm sure the furnace repair guy will get there before I even get a reply on here, I thought I'd post this to see if any of you know anything about it... I always like to learn new home repair stuff. What's the purpose of these switches and what could be wrong? I did tell the guy to make sure his intake and output pipes were not clogged outdoors. He said they are fine! He also tried another thermostat, since he had saved the old standard one when he replaced it with a programmable one last fall. That did not change anything, so we know the t-stat is not the cause. Anyone? Rollout safety switch senses when the flue gasses fail to go up the chimney. Very often when it is windy, the wind pushes "down" the chimney, and prevents the flue gas from going up and out. If the wind has changed, it may be fine to reset the switch (if it has manual reset button) and he's good to go. If it trips again, might be a birds nest or some other thing blocking the chimney. I'd not want to reset it more than once, there is a real risk of killing your family with carbon monoxide. -- .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#7
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On 1/11/2016 3:26 AM, Don Y wrote:
All I know is that it's a Lennox and it's giving that error code. While I'm sure the furnace repair guy will get there before I even get a reply on here, I thought I'd post this to see if any of you know anything about it... I always like to learn new home repair stuff. What's the purpose of these switches and what could be wrong? The switches verify the presence of flame where it SHOULD be and the absence of flame where it SHOULDN'T be! You (he) could have a blocked heat exchanger which is preventing the flames from flowing up through it and, instead, backing up into the blower compartment (*outside* the heat exchanger). Likewise, a blocked flue or something blocking the combustion relief (not enough air to support combustion). The switches can usually be reset, manually. But, this is A Bad Idea and really should only be done by a qualified technician - just to run the furnace long enough to understand why it/they are tripping. They function similar to a fuse: they should NEVER trip -- doing so means something is likely very wrong. You (he) may be able to get the furnace to run by reseting them, but run the risk of CO poisoning, fire, etc. as the reason for their initial trip probably hasn;t been fixed! Sometimes it's wind across or down the chimney that causes the problem. There is a good chance it's a rare thing, and the furnace is okay, now. In western NYS, it was very extremely windy last night. -- .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#8
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
wrote in message ... "Open rollout switch circuit" error message in furnace. A friend called me and said his gas furnace keeps shutting off. It's fairly new and a high effencincy type, which vents out thru PVC. It has a digital readout which says "Open rollout switch circuit". I googled that, and found a simple drawing which shows it as a sort of sensor, and found a picture of one. Not much more. I emailed him the pictures and told him to shut off the power and set his meter to OHMS and check that switch. He said there are two of them and they are both turned to the ON or CLOSED position (Not open). The outside temperature is well below zero, and he has kids, so I told him he better just call a furnace repair company. If it was an older furnace I could probably fix it, (assuming I could get parts), but I dont know anything about these "computerized" furnaces. He called a furnace company, the guy is swamped with calls, but said he will come as soon as he can, but that could be several hours. The guy told him to use space heaters till he gets there. Even if I thought I could help, I doubt my truck will start in this cold, so it dont make any sense to try, knowing nothing about these kind of furnaces. All I know is that it's a Lennox and it's giving that error code. While I'm sure the furnace repair guy will get there before I even get a reply on here, I thought I'd post this to see if any of you know anything about it... I always like to learn new home repair stuff. What's the purpose of these switches and what could be wrong? I did tell the guy to make sure his intake and output pipes were not clogged outdoors. He said they are fine! He also tried another thermostat, since he had saved the old standard one when he replaced it with a programmable one last fall. That did not change anything, so we know the t-stat is not the cause. Anyone? I have a high efficiency water heater that is very sensitive to atmospheric conditions. I have found that the intake fan creates such suction on the intake pipe that it can cause the temperature of the intake air to drop below the outside air, and when the wind blows the "fog" from the exhaust discharge across the intake line, it sucks some of the "fog" into the intake pipe and freezes it just inside the intake pipe. This builds up over time when the outside air is really cold and slowly blocks the intake pipe until the appliance cannot get enough air. At this point the switches detect a vacuum in the intake line and shut the heater off. The moral of this story is go outside and check the intake and exhaust lines to be sure that there is no blockage such as snow or ice over or inside the lines (an animal may have tried to get in and got stuck or killed by the exhaust fumes) and clear out anything you find. Put some mesh over both lines to keep animals out. Also look up the make, model and type of furnace and then go on line to get all the manuals from the manufacturer. The installer may have not left anything hoping for service calls. There is often a trouble-shooting repair manual that is available if you look. |
#9
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Mon, 11 Jan 2016 04:36:13 -0500, Eureka wrote:
On 01/11/2016 01:47 AM, ir wrote: Open rollout switch circuit" error message in furnace. A friend called me and said his gas furnace keeps shutting off. It's fairly new and a high effencincy type, which vents out thru PVC. It has a digital readout which says "Open rollout switch circuit". I googled that, and found a simple drawing which shows it as a sort of sensor, and found a picture of one. Not much more. I always do the simple stuff like checking to make sure the intake and exhaust vent pipes are clear, making sure some ****ing little mouse hasn't built a home in there. Then I'd check that the draft inducer is actually creating the proper air flow. I also check all electrical connections to make sure they're tight. Failing all that, then it's time to call the pros. Make sure there is no water in the draft inducer or any of the vacuum hoses due to condensation accumulatig where it shouldn't |
#10
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
|
#11
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
|
#12
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Monday, January 11, 2016 at 2:04:49 PM UTC-6, wrote:
Make sure there is no water in the draft inducer or any of the vacuum hoses due to condensation accumulatig where it shouldn't +1 The collection of condensate lines usually go to a box, which might have a mess of crud clogging it. |
#13
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
bob_villain wrote:
On Monday, January 11, 2016 at 2:04:49 PM UTC-6, wrote: Make sure there is no water in the draft inducer or any of the vacuum hoses due to condensation accumulatig where it shouldn't +1 The collection of condensate lines usually go to a box, which might have a mess of crud clogging it. |
#14
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
bob_villain wrote:
On Monday, January 11, 2016 at 2:04:49 PM UTC-6, wrote: Make sure there is no water in the draft inducer or any of the vacuum hoses due to condensation accumulatig where it shouldn't +1 The collection of condensate lines usually go to a box, which might have a mess of crud clogging it. My understanding of roll out switch is over heating by some cause. The switch usually has a tiny button(usually red in color) which will pop when triggered. First thing to try is try again after resetting the switch by pushing the button in. To get out of lock out state, turn the power off, wait a few seconds and turn back on. |
#15
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On 01/11/2016 2:51 PM, Tony Hwang wrote:
.... My understanding of roll out switch is over heating by some cause. Possibly, but mostly it's a _location_ indication that indicates the flame isn't in the normal geometry afaik. If that's so and it triggers more than once it's a dangerous-enough situation if can't uncover the cause to get the pro in first rather than later, cost or no cost. -- |
#16
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
dpb wrote:
On 01/11/2016 2:51 PM, Tony Hwang wrote: ... My understanding of roll out switch is over heating by some cause. Possibly, but mostly it's a _location_ indication that indicates the flame isn't in the normal geometry afaik. If that's so and it triggers more than once it's a dangerous-enough situation if can't uncover the cause to get the pro in first rather than later, cost or no cost. -- If inducer is in trouble, operations sequence will never reach ignition. It will fault out with inducer pressure switch problem.... Different diagnostic code. |
#17
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
Important basic info
Rollout means the fire has "rolled out" from where it belongs and a part of the heat exchanger that is not supposed to get hot, is getting too hot. So obviously this could be dangerous. If you reset the swicth, I would watch the the burner operation carefully for a while to make sure the fire stays here it belongs. That can be difficult if there are lockout safteys on the cabinet. Mark |
#18
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On 1/11/2016 3:06 PM, wrote:
On Mon, 11 Jan 2016 07:26:12 -0500, Stormin Mormon wrote: On 1/11/2016 1:47 AM, ir wrote: "Open rollout switch circuit" error message in furnace. A friend called me and said his gas furnace keeps shutting off. It's fairly new and a high effencincy type, which vents out thru PVC. It he's good to go. If it trips again, might be a birds nest or some other thing blocking the chimney. I'd not want to reset it more than once, there is a real risk of killing your family with carbon monoxide. If you read the OP, theer is no chimney. It is a high efficiency condensing furnace with pvc exhaust going throgh the wall. I'm sorry that you can't figure out what part of the system behaves like a chimney. -- .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#19
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
|
#20
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
|
#21
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Monday, January 11, 2016 at 9:33:25 PM UTC-6, wrote:
On Mon, 11 Jan 2016 14:01:13 -0800 (PST), wrote: Important basic info Rollout means the fire has "rolled out" from where it belongs and a part of the heat exchanger that is not supposed to get hot, is getting too hot. So obviously this could be dangerous. If you reset the swicth, I would watch the the burner operation carefully for a while to make sure the fire stays here it belongs. That can be difficult if there are lockout safteys on the cabinet. Mark Overfueling due to gas pressure set too high will cause roll-out - particularly on light-off. If you hear a big "whoomph" on startupget the pressure checked. The gas control valve will lock out if it's supplied with more than around 13 inches water column. The pressures will be listed on the label. There is an internal adjustable regulator for setting the output pressure to the burner manifold which is usually 3.5 inches water column. In The U.S. the normal gas pressure supplied by the regulator at the gas meter to natural gas appliances is approximately 8 inches water column. (€¢€¿€¢) [8~{} Uncle Pressured Monster |
#22
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Mon, 11 Jan 2016 20:16:57 -0800 (PST), Uncle Monster
wrote: On Monday, January 11, 2016 at 9:33:25 PM UTC-6, wrote: On Mon, 11 Jan 2016 14:01:13 -0800 (PST), wrote: Important basic info Rollout means the fire has "rolled out" from where it belongs and a part of the heat exchanger that is not supposed to get hot, is getting too hot. So obviously this could be dangerous. If you reset the swicth, I would watch the the burner operation carefully for a while to make sure the fire stays here it belongs. That can be difficult if there are lockout safteys on the cabinet. Mark Overfueling due to gas pressure set too high will cause roll-out - particularly on light-off. If you hear a big "whoomph" on startupget the pressure checked. The gas control valve will lock out if it's supplied with more than around 13 inches water column. The pressures will be listed on the label. There is an internal adjustable regulator for setting the output pressure to the burner manifold which is usually 3.5 inches water column. In The U.S. the normal gas pressure supplied by the regulator at the gas meter to natural gas appliances is approximately 8 inches water column. (•?•) [8~{} Uncle Pressured Monster It is the adjustment of that "internal regulator" I'm talking about. Changing from 3.5 to 4.2 inches can cause flame roll-out and also cause high CO emissions. Some "quacks" will adjust the pressure up trying to get more heat out of a furnace. It needs to be set properly. |
#23
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Monday, January 11, 2016 at 10:33:00 PM UTC-6, wrote:
On Mon, 11 Jan 2016 20:16:57 -0800 (PST), Uncle Monster wrote: On Monday, January 11, 2016 at 9:33:25 PM UTC-6, wrote: On Mon, 11 Jan 2016 14:01:13 -0800 (PST), wrote: Important basic info Rollout means the fire has "rolled out" from where it belongs and a part of the heat exchanger that is not supposed to get hot, is getting too hot. So obviously this could be dangerous. If you reset the swicth, I would watch the the burner operation carefully for a while to make sure the fire stays here it belongs. That can be difficult if there are lockout safteys on the cabinet. Mark Overfueling due to gas pressure set too high will cause roll-out - particularly on light-off. If you hear a big "whoomph" on startupget the pressure checked. The gas control valve will lock out if it's supplied with more than around 13 inches water column. The pressures will be listed on the label. There is an internal adjustable regulator for setting the output pressure to the burner manifold which is usually 3.5 inches water column. In The U.S. the normal gas pressure supplied by the regulator at the gas meter to natural gas appliances is approximately 8 inches water column. (*?*) [8~{} Uncle Pressured Monster It is the adjustment of that "internal regulator" I'm talking about. Changing from 3.5 to 4.2 inches can cause flame roll-out and also cause high CO emissions. Some "quacks" will adjust the pressure up trying to get more heat out of a furnace. It needs to be set properly. Oh yea, you mean the idiots who think a yellow flame puts out more heat? O_o [8~{} Uncle Flaming Monster |
#24
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On 1/12/2016 1:09 AM, Uncle Monster wrote:
On Monday, January 11, 2016 at 10:33:00 PM UTC-6, wrote: It is the adjustment of that "internal regulator" I'm talking about. Changing from 3.5 to 4.2 inches can cause flame roll-out and also cause high CO emissions. Some "quacks" will adjust the pressure up trying to get more heat out of a furnace. It needs to be set properly. Oh yea, you mean the idiots who think a yellow flame puts out more heat? O_o [8~{} Uncle Flaming Monster Only a yellow idiot would think that a blue flame puts out more heat! Your an idiot!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! (Usenet flame provided by a yellow belly coward who will deny having flamed you.) - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#25
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Mon, 11 Jan 2016 22:09:05 -0800 (PST), Uncle Monster
wrote: On Monday, January 11, 2016 at 10:33:00 PM UTC-6, wrote: On Mon, 11 Jan 2016 20:16:57 -0800 (PST), Uncle Monster wrote: On Monday, January 11, 2016 at 9:33:25 PM UTC-6, wrote: On Mon, 11 Jan 2016 14:01:13 -0800 (PST), wrote: Important basic info Rollout means the fire has "rolled out" from where it belongs and a part of the heat exchanger that is not supposed to get hot, is getting too hot. So obviously this could be dangerous. If you reset the swicth, I would watch the the burner operation carefully for a while to make sure the fire stays here it belongs. That can be difficult if there are lockout safteys on the cabinet. Mark Overfueling due to gas pressure set too high will cause roll-out - particularly on light-off. If you hear a big "whoomph" on startupget the pressure checked. The gas control valve will lock out if it's supplied with more than around 13 inches water column. The pressures will be listed on the label. There is an internal adjustable regulator for setting the output pressure to the burner manifold which is usually 3.5 inches water column. In The U.S. the normal gas pressure supplied by the regulator at the gas meter to natural gas appliances is approximately 8 inches water column. (*?*) [8~{} Uncle Pressured Monster It is the adjustment of that "internal regulator" I'm talking about. Changing from 3.5 to 4.2 inches can cause flame roll-out and also cause high CO emissions. Some "quacks" will adjust the pressure up trying to get more heat out of a furnace. It needs to be set properly. Oh yea, you mean the idiots who think a yellow flame puts out more heat? O_o [8~{} Uncle Flaming Monster You can have an overfueled burner in today's tube burners with no (or extremely little) yellow in the flame, and still get roll-out (and a noisy flame) |
#26
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Tuesday, January 12, 2016 at 7:20:54 PM UTC-6, wrote:
On Mon, 11 Jan 2016 22:09:05 -0800 (PST), Uncle Monster wrote: On Monday, January 11, 2016 at 10:33:00 PM UTC-6, wrote: On Mon, 11 Jan 2016 20:16:57 -0800 (PST), Uncle Monster wrote: On Monday, January 11, 2016 at 9:33:25 PM UTC-6, wrote: On Mon, 11 Jan 2016 14:01:13 -0800 (PST), wrote: Important basic info Rollout means the fire has "rolled out" from where it belongs and a part of the heat exchanger that is not supposed to get hot, is getting too hot. So obviously this could be dangerous. If you reset the swicth, I would watch the the burner operation carefully for a while to make sure the fire stays here it belongs. That can be difficult if there are lockout safteys on the cabinet. Mark Overfueling due to gas pressure set too high will cause roll-out - particularly on light-off. If you hear a big "whoomph" on startupget the pressure checked. The gas control valve will lock out if it's supplied with more than around 13 inches water column. The pressures will be listed on the label. There is an internal adjustable regulator for setting the output pressure to the burner manifold which is usually 3.5 inches water column. In The U.S. the normal gas pressure supplied by the regulator at the gas meter to natural gas appliances is approximately 8 inches water column. (*?*) [8~{} Uncle Pressured Monster It is the adjustment of that "internal regulator" I'm talking about. Changing from 3.5 to 4.2 inches can cause flame roll-out and also cause high CO emissions. Some "quacks" will adjust the pressure up trying to get more heat out of a furnace. It needs to be set properly. Oh yea, you mean the idiots who think a yellow flame puts out more heat? O_o [8~{} Uncle Flaming Monster You can have an overfueled burner in today's tube burners with no (or extremely little) yellow in the flame, and still get roll-out (and a noisy flame) I've seen it before when someone screws around with the regulator and/or air mixture. Or if the roof or side vent is improperly installed or in some odd spot where there are a lot of wind gusts. Of course there is also vegetation and critter invasion of the flue to consider. I've rarely seen rollout when there is a properly installed and operating draft inducer equipped furnace. I have seen all kinds of weird crap happen to equipment over the years. ^__^ [8~{} Uncle Furnace Monster |
#27
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On 1/11/2016 1:47 AM, ir wrote:
"Open rollout switch circuit" error message in furnace. A friend called me and said his gas furnace keeps shutting off. It's fairly new and a high effencincy type, which vents out thru PVC. It has a digital readout which says "Open rollout switch circuit". I googled that, and found a simple drawing which shows it as a sort of sensor, and found a picture of one. Not much more. I emailed him the pictures and told him to shut off the power and set his meter to OHMS and check that switch. He said there are two of them and they are both turned to the ON or CLOSED position (Not open). The outside temperature is well below zero, and he has kids, so I told him he better just call a furnace repair company. If it was an older furnace I could probably fix it, (assuming I could get parts), but I dont know anything about these "computerized" furnaces. He called a furnace company, the guy is swamped with calls, but said he will come as soon as he can, but that could be several hours. The guy told him to use space heaters till he gets there. Even if I thought I could help, I doubt my truck will start in this cold, so it dont make any sense to try, knowing nothing about these kind of furnaces. All I know is that it's a Lennox and it's giving that error code. While I'm sure the furnace repair guy will get there before I even get a reply on here, I thought I'd post this to see if any of you know anything about it... I always like to learn new home repair stuff. What's the purpose of these switches and what could be wrong? I did tell the guy to make sure his intake and output pipes were not clogged outdoors. He said they are fine! He also tried another thermostat, since he had saved the old standard one when he replaced it with a programmable one last fall. That did not change anything, so we know the t-stat is not the cause. Anyone? Is it just me? I don't believe we heard from the OP. Perhaps the furnace burned down and killed them all with monoxide? -- .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#28
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
I had the same error and you wouldn't believe what it was. The people that installed my lenox there were 2 wires that were connected opposite where they should have been. It was another furnace guy that fixed it not the people who installed it
|
#29
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Sunday, October 28, 2018 at 10:23:25 AM UTC-4, wrote:
I had the same error and you wouldn't believe what it was. The people that installed my lenox there were 2 wires that were connected opposite where they should have been. It was another furnace guy that fixed it not the people who installed it That seems a bit weird. You had a furnace installed where you got a flame rollout error and someone other than the installer fixed it? How does that happen? Presumably with that error, the furnace won't fire, so what did the installers do, just run away? Also installers shouldn't have to fiddle with any wires like that, those sensors are already wired, so if they were wired wrong, it would have had to have left the factory like that or the installers would have had to screw with them. |
#30
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On 10/28/18 10:03 AM, trader_4 wrote:
On Sunday, October 28, 2018 at 10:23:25 AM UTC-4, wrote: I had the same error and you wouldn't believe what it was. The people that installed my lenox there were 2 wires that were connected opposite where they should have been. It was another furnace guy that fixed it not the people who installed it That seems a bit weird. You had a furnace installed where you got a flame rollout error and someone other than the installer fixed it? How does that happen? Presumably with that error, the furnace won't fire, so what did the installers do, just run away? Also installers shouldn't have to fiddle with any wires like that, those sensors are already wired, so if they were wired wrong, it would have had to have left the factory like that or the installers would have had to screw with them. Sloppy work from the installers. I install and fix electrical stuff. Standard procedure is to try things to see if I got everything right. |
#31
Posted to alt.home.repair
|
|||
|
|||
"Open rollout switch circuit" error message in furnace.
On Sun, 28 Oct 2018 08:03:39 -0700 (PDT), trader_4
wrote: On Sunday, October 28, 2018 at 10:23:25 AM UTC-4, wrote: I had the same error and you wouldn't believe what it was. The people that installed my lenox there were 2 wires that were connected opposite where they should have been. It was another furnace guy that fixed it not the people who installed it That seems a bit weird. You had a furnace installed where you got a flame rollout error and someone other than the installer fixed it? How does that happen? Presumably with that error, the furnace won't fire, so what did the installers do, just run away? Also installers shouldn't have to fiddle with any wires like that, those sensors are already wired, so if they were wired wrong, it would have had to have left the factory like that or the installers would have had to screw with them. I wonder if the guy who "fixed it" really did fix it .. ? or did he actually disable it ? .. thereby creating a dangerous condition. John T. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
What is simplest possible circuit for letterbox flap "open" detector? | UK diy | |||
"Plgn Motor Error" on "TI Microlaser Plus" printer | Electronics Repair | |||
Sharp AL-1655CS "Replace the drum cartridge" error message | Electronics Repair |