replying to intersoft4you, HVAC Man wrote:
intersoft4you wrote: Hi everybody, I have just installed new High Efficiency furnace (Keeprite). In the manual 2 pipes are depicted (Exhaust and intake) running outside of the house. However, the installer has left the intake pipe inside of the basement (the pipe is about 20 inches long above the furnace). He says it's OK to have an intake pipe to suck the air from within the basement. Is it? Thanks a lot! Viktor A high efficiency furnace should draw air from the same pressure zone ! Meaning the inlet air pipe and the exhaust air pipe should be in close proximity to one another allowing equal pressure changes. Both pipes should always be installed on the same side of the house as well. Whomever said you are allowed to to draw intake air from the basement is just looking to make some easy money on nuisance pressure sensor trips.... -- |
#2
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside.Is that OK?
HVAC Man wrote:
replying to intersoft4you, HVAC Man wrote: intersoft4you wrote: Hi everybody, I have just installed new High Efficiency furnace (Keeprite). In the manual 2 pipes are depicted (Exhaust and intake) running outside of the house. However, the installer has left the intake pipe inside of the basement (the pipe is about 20 inches long above the furnace). He says it's OK to have an intake pipe to suck the air from within the basement. Is it? Thanks a lot! Viktor A high efficiency furnace should draw air from the same pressure zone ! Meaning the inlet air pipe and the exhaust air pipe should be in close proximity to one another allowing equal pressure changes. Both pipes should always be installed on the same side of the house as well. Whomever said you are allowed to to draw intake air from the basement is just looking to make some easy money on nuisance pressure sensor trips.... Hi, Mod mid-efficiency furnace haad fresh air insulated dampered intake duct for combustion. In this case intake can be inside the basement. Our local code allows this. |
#3
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is that OK?
On Monday, February 16, 2015 at 11:44:06 PM UTC-5, HVAC Man wrote:
replying to intersoft4you, HVAC Man wrote: intersoft4you wrote: Hi everybody, I have just installed new High Efficiency furnace (Keeprite). In the manual 2 pipes are depicted (Exhaust and intake) running outside of the house. However, the installer has left the intake pipe inside of the basement (the pipe is about 20 inches long above the furnace). He says it's OK to have an intake pipe to suck the air from within the basement. Is it? Thanks a lot! Viktor A high efficiency furnace should draw air from the same pressure zone ! Meaning the inlet air pipe and the exhaust air pipe should be in close proximity to one another allowing equal pressure changes. Both pipes should always be installed on the same side of the house as well. Whomever said you are allowed to to draw intake air from the basement is just looking to make some easy money on nuisance pressure sensor trips.... Nonsense. Many furnaces can be installed using either outside combustion air or inside. It's permitted per the manufacturer's installation instructions. In most cases it makes more sense to use outside air, especially if the furnace is located in a heated space, because if inside air is used, the makeup cold air will be drawn in to the structure from outside through leakage. |
#4
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is thatOK?
On 2/17/2015 7:24 AM, trader_4 wrote:
On Monday, February 16, 2015 at 11:44:06 PM UTC-5, HVAC Man wrote: replying to intersoft4you, HVAC Man wrote: intersoft4you wrote: Hi everybody, I have just installed new High Efficiency furnace (Keeprite). In the manual 2 pipes are depicted (Exhaust and intake) running outside of the house. However, the installer has left the intake pipe inside of the basement (the pipe is about 20 inches long above the furnace). He says it's OK to have an intake pipe to suck the air from within the basement. Is it? Thanks a lot! Viktor A high efficiency furnace should draw air from the same pressure zone ! Meaning the inlet air pipe and the exhaust air pipe should be in close proximity to one another allowing equal pressure changes. Both pipes should always be installed on the same side of the house as well. Whomever said you are allowed to to draw intake air from the basement is just looking to make some easy money on nuisance pressure sensor trips.... Nonsense. Many furnaces can be installed using either outside combustion air or inside. It's permitted per the manufacturer's installation instructions. In most cases it makes more sense to use outside air, especially if the furnace is located in a heated space, because if inside air is used, the makeup cold air will be drawn in to the structure from outside through leakage. Yep. Not only that, but some of the earlier high efficiency furnaces didn't even have an air intake pipe. I had an Amana, probably from the 90s, that had a standard open burner arrangement just like the furnaces from the 70s. I just drew air from the room where it was installed. The exhaust on the Amana, was the standard PVC out the side wall of the house. |
#5
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is that OK?
On Tuesday, February 17, 2015 at 8:30:13 AM UTC-5, Art Todesco wrote:
On 2/17/2015 7:24 AM, trader_4 wrote: On Monday, February 16, 2015 at 11:44:06 PM UTC-5, HVAC Man wrote: replying to intersoft4you, HVAC Man wrote: intersoft4you wrote: Hi everybody, I have just installed new High Efficiency furnace (Keeprite). In the manual 2 pipes are depicted (Exhaust and intake) running outside of the house. However, the installer has left the intake pipe inside of the basement (the pipe is about 20 inches long above the furnace). He says it's OK to have an intake pipe to suck the air from within the basement. Is it? Thanks a lot! Viktor A high efficiency furnace should draw air from the same pressure zone ! Meaning the inlet air pipe and the exhaust air pipe should be in close proximity to one another allowing equal pressure changes. Both pipes should always be installed on the same side of the house as well. Whomever said you are allowed to to draw intake air from the basement is just looking to make some easy money on nuisance pressure sensor trips.... Nonsense. Many furnaces can be installed using either outside combustion air or inside. It's permitted per the manufacturer's installation instructions. In most cases it makes more sense to use outside air, especially if the furnace is located in a heated space, because if inside air is used, the makeup cold air will be drawn in to the structure from outside through leakage. Yep. Not only that, but some of the earlier high efficiency furnaces didn't even have an air intake pipe. I had an Amana, probably from the 90s, that had a standard open burner arrangement just like the furnaces from the 70s. I just drew air from the room where it was installed. The exhaust on the Amana, was the standard PVC out the side wall of the house. Not that it matters at this point, as this is a revival of an old post, but the install manual for the furnace would have the answer as to how it can be installed. My Rheem, it could installed either with outside air or using air from within. |
#6
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is that OK?
trader_4 wrote:
On Tuesday, February 17, 2015 at 8:30:13 AM UTC-5, Art Todesco wrote: On 2/17/2015 7:24 AM, trader_4 wrote: On Monday, February 16, 2015 at 11:44:06 PM UTC-5, HVAC Man wrote: replying to intersoft4you, HVAC Man wrote: intersoft4you wrote: Hi everybody, I have just installed new High Efficiency furnace (Keeprite). In the manual 2 pipes are depicted (Exhaust and intake) running outside of the house. However, the installer has left the intake pipe inside of the basement (the pipe is about 20 inches long above the furnace). He says it's OK to have an intake pipe to suck the air from within the basement. Is it? Thanks a lot! Viktor A high efficiency furnace should draw air from the same pressure zone ! Meaning the inlet air pipe and the exhaust air pipe should be in close proximity to one another allowing equal pressure changes. Both pipes should always be installed on the same side of the house as well. Whomever said you are allowed to to draw intake air from the basement is just looking to make some easy money on nuisance pressure sensor trips.... Nonsense. Many furnaces can be installed using either outside combustion air or inside. It's permitted per the manufacturer's installation instructions. In most cases it makes more sense to use outside air, especially if the furnace is located in a heated space, because if inside air is used, the makeup cold air will be drawn in to the structure from outside through leakage. Yep. Not only that, but some of the earlier high efficiency furnaces didn't even have an air intake pipe. I had an Amana, probably from the 90s, that had a standard open burner arrangement just like the furnaces from the 70s. I just drew air from the room where it was installed. The exhaust on the Amana, was the standard PVC out the side wall of the house. Not that it matters at this point, as this is a revival of an old post, but the install manual for the furnace would have the answer as to how it can be installed. My Rheem, it could installed either with outside air or using air from within. Same thing here. My two Heil furnaces never required outside air, the first running for 22 years, The current one running for 10 years. No nuisance trips or other issues. |
#7
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is thatOK?
On 2/17/2015 10:03 AM, Smarty wrote:
Same thing here. My two Heil furnaces never required outside air, the first running for 22 years, The current one running for 10 years. No nuisance trips or other issues. Luxaire, installed 1994. No nussiance trips. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#8
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is thatOK?
On 2/17/2015 1:13 AM, Tony Hwang wrote:
Hi, Mod mid-efficiency furnace haad fresh air insulated dampered intake duct for combustion. In this case intake can be inside the basement. Our local code allows this. CAN BE does not mean SHOULD BE. Using outside air for combustion is more efficient. You are using air that you paid to heat and sending it up the flue. Sounds to me the contractor for the OP is just lazy. |
#9
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is that OK?
On Tuesday, February 17, 2015 at 10:29:50 AM UTC-5, Ed Pawlowski wrote:
On 2/17/2015 1:13 AM, Tony Hwang wrote: Hi, Mod mid-efficiency furnace haad fresh air insulated dampered intake duct for combustion. In this case intake can be inside the basement. Our local code allows this. CAN BE does not mean SHOULD BE. Using outside air for combustion is more efficient. You are using air that you paid to heat and sending it up the flue. Sounds to me the contractor for the OP is just lazy. The difference in heat may not be that great. One factor is where the furnace is located, ie is it in the heated space, an unheated basement, garage, attic, etc. Even assuming worse case, it's not clear to me how much difference it makes. Yes heated air is used for combustion. But the alternative, bringing in cold outside air, just means less heat is generated in the furnace. You're getting more heat of a furnace with 60F air going into it than with 20F air. I know relatively new, circa 2007, expensive houses built here that have furnaces in unfinished basements that use the basement air. |
#10
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside.Is that OK?
Ed Pawlowski wrote:
On 2/17/2015 1:13 AM, Tony Hwang wrote: Hi, Mod mid-efficiency furnace haad fresh air insulated dampered intake duct for combustion. In this case intake can be inside the basement. Our local code allows this. CAN BE does not mean SHOULD BE. Using outside air for combustion is more efficient. You are using air that you paid to heat and sending it up the flue. Sounds to me the contractor for the OP is just lazy. Hi, Any how, today's new houses are so air tight we have to bring in controlled outside fresh air into the house. |
#11
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is that OK?
On Tuesday, February 17, 2015 at 11:05:14 AM UTC-5, Tony Hwang wrote:
Ed Pawlowski wrote: On 2/17/2015 1:13 AM, Tony Hwang wrote: Hi, Mod mid-efficiency furnace haad fresh air insulated dampered intake duct for combustion. In this case intake can be inside the basement. Our local code allows this. CAN BE does not mean SHOULD BE. Using outside air for combustion is more efficient. You are using air that you paid to heat and sending it up the flue. Sounds to me the contractor for the OP is just lazy. Hi, Any how, today's new houses are so air tight we have to bring in controlled outside fresh air into the house. Maybe so, somewhere. But I've yet to see a new house that was so airtight that it needed it around here, NJ. |
#12
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside.Is that OK?
trader_4 wrote:
On Tuesday, February 17, 2015 at 11:05:14 AM UTC-5, Tony Hwang wrote: Ed Pawlowski wrote: On 2/17/2015 1:13 AM, Tony Hwang wrote: Hi, Mod mid-efficiency furnace haad fresh air insulated dampered intake duct for combustion. In this case intake can be inside the basement. Our local code allows this. CAN BE does not mean SHOULD BE. Using outside air for combustion is more efficient. You are using air that you paid to heat and sending it up the flue. Sounds to me the contractor for the OP is just lazy. Hi, Any how, today's new houses are so air tight we have to bring in controlled outside fresh air into the house. Maybe so, somewhere. But I've yet to see a new house that was so airtight that it needed it around here, NJ. Hi, In cold climate up here every new house going up has provision for fresh air intake. My house was built in 1994 per R2000 specs. If it doesn't bring in fresh air, it may cause indoor CO problem. Summer or winter, we seldom open windows. |
#13
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside.Is that OK?
Smarty wrote:
trader_4 wrote: On Tuesday, February 17, 2015 at 8:30:13 AM UTC-5, Art Todesco wrote: On 2/17/2015 7:24 AM, trader_4 wrote: On Monday, February 16, 2015 at 11:44:06 PM UTC-5, HVAC Man wrote: replying to intersoft4you, HVAC Man wrote: intersoft4you wrote: Hi everybody, I have just installed new High Efficiency furnace (Keeprite). In the manual 2 pipes are depicted (Exhaust and intake) running outside of the house. However, the installer has left the intake pipe inside of the basement (the pipe is about 20 inches long above the furnace). He says it's OK to have an intake pipe to suck the air from within the basement. Is it? Thanks a lot! Viktor A high efficiency furnace should draw air from the same pressure zone ! Meaning the inlet air pipe and the exhaust air pipe should be in close proximity to one another allowing equal pressure changes. Both pipes should always be installed on the same side of the house as well. Whomever said you are allowed to to draw intake air from the basement is just looking to make some easy money on nuisance pressure sensor trips.... Nonsense. Many furnaces can be installed using either outside combustion air or inside. It's permitted per the manufacturer's installation instructions. In most cases it makes more sense to use outside air, especially if the furnace is located in a heated space, because if inside air is used, the makeup cold air will be drawn in to the structure from outside through leakage. Yep. Not only that, but some of the earlier high efficiency furnaces didn't even have an air intake pipe. I had an Amana, probably from the 90s, that had a standard open burner arrangement just like the furnaces from the 70s. I just drew air from the room where it was installed. The exhaust on the Amana, was the standard PVC out the side wall of the house. Not that it matters at this point, as this is a revival of an old post, but the install manual for the furnace would have the answer as to how it can be installed. My Rheem, it could installed either with outside air or using air from within. Same thing here. My two Heil furnaces never required outside air, the first running for 22 years, The current one running for 10 years. No nuisance trips or other issues. Hi, Ever done an energy audit to see how air tight your house is? |
#14
Posted to alt.home.repair
|
|||
|
|||
High Efficiency Furnace intake pipe does not go outside. Is that OK?
On Tuesday, February 17, 2015 at 12:53:12 PM UTC-5, Tony Hwang wrote:
trader_4 wrote: On Tuesday, February 17, 2015 at 11:05:14 AM UTC-5, Tony Hwang wrote: Ed Pawlowski wrote: On 2/17/2015 1:13 AM, Tony Hwang wrote: Hi, Mod mid-efficiency furnace haad fresh air insulated dampered intake duct for combustion. In this case intake can be inside the basement. Our local code allows this. CAN BE does not mean SHOULD BE. Using outside air for combustion is more efficient. You are using air that you paid to heat and sending it up the flue. Sounds to me the contractor for the OP is just lazy. Hi, Any how, today's new houses are so air tight we have to bring in controlled outside fresh air into the house. Maybe so, somewhere. But I've yet to see a new house that was so airtight that it needed it around here, NJ. Hi, In cold climate up here every new house going up has provision for fresh air intake. My house was built in 1994 per R2000 specs. If it doesn't bring in fresh air, it may cause indoor CO problem. Summer or winter, we seldom open windows. Where is this CO problem supposed to come from? |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
How to avoid ice-clogged furnace air intake pipe? | Home Ownership | |||
High Efficiency Furnace | Home Repair | |||
High Efficiency gas furnace - return air temperature | Home Repair | |||
high efficiency gas furnace advice please | Home Repair | |||
High efficiency furnace - water out of outside pipe | Home Repair |