DIYbanter

DIYbanter (https://www.diybanter.com/)
-   Home Repair (https://www.diybanter.com/home-repair/)
-   -   GFCI's work, Chinese light fixtures don't (https://www.diybanter.com/home-repair/352695-gfcis-work-chinese-light-fixtures-dont.html)

DerbyDad03 February 4th 13 09:49 PM

GFCI's work, Chinese light fixtures don't
 
A couple of years ago I built a shed and ran power to it through some
underground PVC conduit. Power to the shed is sourced from a GFCI
receptacle under my deck. The shed has an interior light fixture, an
external receptacle and an external motion sensor light fixture.

Last week I noticed that the motion sensor fixture was not turning on
so I went out to the shed and found that the GFCI receptacle had
tripped. I reset the GFCI, both lights came on and seconds later the
GFCI tripped again. I turned off the disconnect switch in the shed,
reset the GFCI and it stayed on. Flipped on the disconnect and the
GFCI tripped.

Satisfied that (thankfully) it did not appear to be my underground
wiring, I opened the junction box for the motion sensor fixture and
disconnected it. When I reset the GFCI it stayed on. OK, problem
found.

I took the Made In China light fixture - which was clearly marked "For
External Use" - off of the shed and into the workshop. I opened the
bulb housing and saw water around the wires that went to the bulb
socket. I guess it's "For External Use" in dry locations only. The
best I can tell is that the water got in through the ball and socket
joint that allows you to aim the light.

I let the unit dry out and then filled the tube from the ball and
socket joint to the light socket with silicone so the water can't
reach the socket. I remounted it, aimed the light and then put some
more silicon around the exterior of the ball and socket joint to
hopefully prevent water from entering the fixture in the first place.

Piece of crap Chinese fixture. Maybe the GFCI was made in China also,
but at least it works the way it is supposed to.


Oren[_2_] February 4th 13 10:43 PM

GFCI's work, Chinese light fixtures don't
 
On Mon, 4 Feb 2013 13:49:40 -0800 (PST), DerbyDad03
wrote:

A couple of years ago I built a shed and ran power to it through some
underground PVC conduit. Power to the shed is sourced from a GFCI
receptacle under my deck. The shed has an interior light fixture, an
external receptacle and an external motion sensor light fixture.

Last week I noticed that the motion sensor fixture was not turning on
so I went out to the shed and found that the GFCI receptacle had
tripped. I reset the GFCI, both lights came on and seconds later the
GFCI tripped again. I turned off the disconnect switch in the shed,
reset the GFCI and it stayed on. Flipped on the disconnect and the
GFCI tripped.

Satisfied that (thankfully) it did not appear to be my underground
wiring, I opened the junction box for the motion sensor fixture and
disconnected it. When I reset the GFCI it stayed on. OK, problem
found.

I took the Made In China light fixture - which was clearly marked "For
External Use" - off of the shed and into the workshop. I opened the
bulb housing and saw water around the wires that went to the bulb
socket. I guess it's "For External Use" in dry locations only. The
best I can tell is that the water got in through the ball and socket
joint that allows you to aim the light.

I let the unit dry out and then filled the tube from the ball and
socket joint to the light socket with silicone so the water can't
reach the socket. I remounted it, aimed the light and then put some
more silicon around the exterior of the ball and socket joint to
hopefully prevent water from entering the fixture in the first place.

Piece of crap Chinese fixture. Maybe the GFCI was made in China also,
but at least it works the way it is supposed to.


I've believed that GFCI's work or don't work. I think two
(pool/garage) act funny during a reset.

The garage trips occasionally as it is also a bathroom circuit. It
trips if a hairdryer is used when I have something plugged in with a
higher amp draw? Lately, it tripped a few times. When I try to reset
it would not, but a little force on the reset button it did. The
thing "chattered" as I reset it.

I'll be replacing both the garage and the one for the pool light -
real soon (next trip to the Borg).

(something tripped at the Super Bowl G)

DerbyDad03[_2_] February 5th 13 01:03 AM

GFCI's work, Chinese light fixtures don't
 
On 02/04/13 5:43 PM, Oren wrote:
On Mon, 4 Feb 2013 13:49:40 -0800 (PST), DerbyDad03
wrote:

A couple of years ago I built a shed and ran power to it through some
underground PVC conduit. Power to the shed is sourced from a GFCI
receptacle under my deck. The shed has an interior light fixture, an
external receptacle and an external motion sensor light fixture.

Last week I noticed that the motion sensor fixture was not turning on
so I went out to the shed and found that the GFCI receptacle had
tripped. I reset the GFCI, both lights came on and seconds later the
GFCI tripped again. I turned off the disconnect switch in the shed,
reset the GFCI and it stayed on. Flipped on the disconnect and the
GFCI tripped.

Satisfied that (thankfully) it did not appear to be my underground
wiring, I opened the junction box for the motion sensor fixture and
disconnected it. When I reset the GFCI it stayed on. OK, problem
found.

I took the Made In China light fixture - which was clearly marked "For
External Use" - off of the shed and into the workshop. I opened the
bulb housing and saw water around the wires that went to the bulb
socket. I guess it's "For External Use" in dry locations only. The
best I can tell is that the water got in through the ball and socket
joint that allows you to aim the light.

I let the unit dry out and then filled the tube from the ball and
socket joint to the light socket with silicone so the water can't
reach the socket. I remounted it, aimed the light and then put some
more silicon around the exterior of the ball and socket joint to
hopefully prevent water from entering the fixture in the first place.

Piece of crap Chinese fixture. Maybe the GFCI was made in China also,
but at least it works the way it is supposed to.


I've believed that GFCI's work or don't work. I think two
(pool/garage) act funny during a reset.


Well, in this case, the one protecting the shed did exactly what it was
supposed to do, so I'm pretty satisfied. I've had the one in the garage
trip when the receptacles on the extension cords for the Halloween
decorations get wet. I try to wrap the ones that are going to be lying
on the lawn in plastic and/or to position them under a chair (or
tombstone) to keep them as dry as possible, but it's not always possible.


The garage trips occasionally as it is also a bathroom circuit. It
trips if a hairdryer is used when I have something plugged in with a
higher amp draw? Lately, it tripped a few times. When I try to reset
it would not, but a little force on the reset button it did. The
thing "chattered" as I reset it.


I had one near the kitchen sink that was used all the time for juicers,
coffee grinders, etc. It was there for years and never tripped except
when I tested it. It was looking kind of grimy so instead of trying to
clean it, I figured I'd just grab a spare from the shop and replace it.
Now when we use the juicer or coffee grinder, it will trip maybe 25% of
the time.

These devices do not trip any other GFCI's nor did they trip the
original one, so I have to assume that the new one is faulty. I keep
thinking about replacing it but I never remember...until it trips.


I'll be replacing both the garage and the one for the pool light -
real soon (next trip to the Borg).

(something tripped at the Super Bowl G)


I think all the computer generated animations during Beyonce's
performance sucked the power out of the grid.

[email protected] February 5th 13 01:27 AM

GFCI's work, Chinese light fixtures don't
 
On Mon, 04 Feb 2013 20:05:49 -0500, DerbyDad03
wrote:

On 02/04/13 6:03 PM, wrote:
On Mon, 04 Feb 2013 14:43:49 -0800, Oren wrote:

On Mon, 4 Feb 2013 13:49:40 -0800 (PST), DerbyDad03
wrote:

A couple of years ago I built a shed and ran power to it through some
underground PVC conduit. Power to the shed is sourced from a GFCI
receptacle under my deck. The shed has an interior light fixture, an
external receptacle and an external motion sensor light fixture.

Last week I noticed that the motion sensor fixture was not turning on
so I went out to the shed and found that the GFCI receptacle had
tripped. I reset the GFCI, both lights came on and seconds later the
GFCI tripped again. I turned off the disconnect switch in the shed,
reset the GFCI and it stayed on. Flipped on the disconnect and the
GFCI tripped.

Satisfied that (thankfully) it did not appear to be my underground
wiring, I opened the junction box for the motion sensor fixture and
disconnected it. When I reset the GFCI it stayed on. OK, problem
found.

I took the Made In China light fixture - which was clearly marked "For
External Use" - off of the shed and into the workshop. I opened the
bulb housing and saw water around the wires that went to the bulb
socket. I guess it's "For External Use" in dry locations only. The
best I can tell is that the water got in through the ball and socket
joint that allows you to aim the light.

I let the unit dry out and then filled the tube from the ball and
socket joint to the light socket with silicone so the water can't
reach the socket. I remounted it, aimed the light and then put some
more silicon around the exterior of the ball and socket joint to
hopefully prevent water from entering the fixture in the first place.

Piece of crap Chinese fixture. Maybe the GFCI was made in China also,
but at least it works the way it is supposed to.

I've believed that GFCI's work or don't work. I think two
(pool/garage) act funny during a reset.

The garage trips occasionally as it is also a bathroom circuit. It
trips if a hairdryer is used when I have something plugged in with a
higher amp draw? Lately, it tripped a few times. When I try to reset
it would not, but a little force on the reset button it did. The
thing "chattered" as I reset it.


A heavy load *shouldn't* trip a GFCI. It's more likely that it's
trying its best to save your life.


As I mentioned in response to Oren...

I had a GFCI near the kitchen sink that was used all the time for
juicers, coffee grinders, etc. It was there for years and never tripped
except when I tested it. It was looking kind of grimy so instead of
trying to clean it, I figured I'd just grab a spare from the shop and
replace it. Now when we use the juicer or coffee grinder, it will trip
maybe 25% of the time.

These devices do not trip any other GFCI's nor did they trip the
original one, so I have to assume that the new one is faulty. I keep
thinking about replacing it but I never remember...until it trips.

I don't know if it simply more sensitive to motors than the old one or
if it's faulty.

Long ago, motors would trip GFCIs (the reason for the exclusion of
freezers from GFCIs). Newer ones are much better. Perhaps your
"spare" is that old? Or perhaps the one you replaced was bad. It
*shouldn't* happen.


[email protected] February 5th 13 01:28 AM

GFCI's work, Chinese light fixtures don't
 
On Mon, 04 Feb 2013 20:03:52 -0500, DerbyDad03
wrote:

On 02/04/13 5:43 PM, Oren wrote:
On Mon, 4 Feb 2013 13:49:40 -0800 (PST), DerbyDad03
wrote:

A couple of years ago I built a shed and ran power to it through some
underground PVC conduit. Power to the shed is sourced from a GFCI
receptacle under my deck. The shed has an interior light fixture, an
external receptacle and an external motion sensor light fixture.

Last week I noticed that the motion sensor fixture was not turning on
so I went out to the shed and found that the GFCI receptacle had
tripped. I reset the GFCI, both lights came on and seconds later the
GFCI tripped again. I turned off the disconnect switch in the shed,
reset the GFCI and it stayed on. Flipped on the disconnect and the
GFCI tripped.

Satisfied that (thankfully) it did not appear to be my underground
wiring, I opened the junction box for the motion sensor fixture and
disconnected it. When I reset the GFCI it stayed on. OK, problem
found.

I took the Made In China light fixture - which was clearly marked "For
External Use" - off of the shed and into the workshop. I opened the
bulb housing and saw water around the wires that went to the bulb
socket. I guess it's "For External Use" in dry locations only. The
best I can tell is that the water got in through the ball and socket
joint that allows you to aim the light.

I let the unit dry out and then filled the tube from the ball and
socket joint to the light socket with silicone so the water can't
reach the socket. I remounted it, aimed the light and then put some
more silicon around the exterior of the ball and socket joint to
hopefully prevent water from entering the fixture in the first place.

Piece of crap Chinese fixture. Maybe the GFCI was made in China also,
but at least it works the way it is supposed to.


I've believed that GFCI's work or don't work. I think two
(pool/garage) act funny during a reset.


Well, in this case, the one protecting the shed did exactly what it was
supposed to do, so I'm pretty satisfied. I've had the one in the garage
trip when the receptacles on the extension cords for the Halloween
decorations get wet. I try to wrap the ones that are going to be lying
on the lawn in plastic and/or to position them under a chair (or
tombstone) to keep them as dry as possible, but it's not always possible.


The garage trips occasionally as it is also a bathroom circuit. It
trips if a hairdryer is used when I have something plugged in with a
higher amp draw? Lately, it tripped a few times. When I try to reset
it would not, but a little force on the reset button it did. The
thing "chattered" as I reset it.


I had one near the kitchen sink that was used all the time for juicers,
coffee grinders, etc. It was there for years and never tripped except
when I tested it. It was looking kind of grimy so instead of trying to
clean it, I figured I'd just grab a spare from the shop and replace it.
Now when we use the juicer or coffee grinder, it will trip maybe 25% of
the time.

These devices do not trip any other GFCI's nor did they trip the
original one, so I have to assume that the new one is faulty. I keep
thinking about replacing it but I never remember...until it trips.


I'll be replacing both the garage and the one for the pool light -
real soon (next trip to the Borg).

(something tripped at the Super Bowl G)


I think all the computer generated animations during Beyonce's
performance sucked the power out of the grid.


Or perhaps it was Flacco's F-Bomb.

DerbyDad03[_2_] February 5th 13 01:51 AM

GFCI's work, Chinese light fixtures don't
 
On 02/04/13 8:28 PM, wrote:
On Mon, 04 Feb 2013 20:03:52 -0500, DerbyDad03
wrote:

On 02/04/13 5:43 PM, Oren wrote:
On Mon, 4 Feb 2013 13:49:40 -0800 (PST), DerbyDad03
wrote:



Piece of crap Chinese fixture. Maybe the GFCI was made in China also,
but at least it works the way it is supposed to.

I've believed that GFCI's work or don't work. I think two
(pool/garage) act funny during a reset.


Well, in this case, the one protecting the shed did exactly what it was
supposed to do, so I'm pretty satisfied. I've had the one in the garage
trip when the receptacles on the extension cords for the Halloween
decorations get wet. I try to wrap the ones that are going to be lying
on the lawn in plastic and/or to position them under a chair (or
tombstone) to keep them as dry as possible, but it's not always possible.


The garage trips occasionally as it is also a bathroom circuit. It
trips if a hairdryer is used when I have something plugged in with a
higher amp draw? Lately, it tripped a few times. When I try to reset
it would not, but a little force on the reset button it did. The
thing "chattered" as I reset it.


I had one near the kitchen sink that was used all the time for juicers,
coffee grinders, etc. It was there for years and never tripped except
when I tested it. It was looking kind of grimy so instead of trying to
clean it, I figured I'd just grab a spare from the shop and replace it.
Now when we use the juicer or coffee grinder, it will trip maybe 25% of
the time.

These devices do not trip any other GFCI's nor did they trip the
original one, so I have to assume that the new one is faulty. I keep
thinking about replacing it but I never remember...until it trips.


I'll be replacing both the garage and the one for the pool light -
real soon (next trip to the Borg).

(something tripped at the Super Bowl G)


I think all the computer generated animations during Beyonce's
performance sucked the power out of the grid.


Or perhaps it was Flacco's F-Bomb.


The F-bomb was at the end of the game, long after the power came back
on. "Holy S---! F------ awesome."

http://mashable.com/2013/02/04/joe-flacco-f-bomb/



Erik[_5_] February 5th 13 03:30 AM

GFCI's work, Chinese light fixtures don't
 

(something tripped at the Super Bowl G)


As I'm not a football or commercial fan, I didn't watch the Super Bowl.
I did however take advantage of the few hours of light traffic it
provided... a rarity in my parts.

Having said that, a friend postulates the blackout might have been
intentional... conveniently 'inserted' to run bonus rations of
multimillion dollar ad's to a frenzied near global audience.

Wouldn't doubt it...

Erik

BillyBobT February 5th 13 10:40 AM

GFCI's work, Chinese light fixtures don't
 
DerbyDad03 wrote in news:ebf33553-5156-4842-88d5-
:

I let the unit dry out and then filled the tube from the ball and
socket joint to the light socket with silicone so the water can't
reach the socket. I remounted it, aimed the light and then put some
more silicon around the exterior of the ball and socket joint to
hopefully prevent water from entering the fixture in the first place.


Wow! You have a lot of time on your hands.

DerbyDad03 February 5th 13 11:16 AM

GFCI's work, Chinese light fixtures don't
 
BillyBobT wrote:
DerbyDad03 wrote in news:ebf33553-5156-4842-88d5-
:

I let the unit dry out and then filled the tube from the ball and
socket joint to the light socket with silicone so the water can't
reach the socket. I remounted it, aimed the light and then put some
more silicon around the exterior of the ball and socket joint to
hopefully prevent water from entering the fixture in the first place.


Wow! You have a lot of time on your hands.


It took less time to add some silicon to the old fixture than it would have
taken me to go to the store and buy a new one.

Removal and installation was required in both cases, so that's a wash.

Stormin Mormon[_7_] February 5th 13 12:24 PM

GFCI's work, Chinese light fixtures don't
 
The adult generation repairs things.
The kid generation throws it out and replaces.

Christopher A. Young
Learn more about Jesus
www.lds.org
..

"DerbyDad03" wrote in message
...
I let the unit dry out and then filled the tube from the ball and
socket joint to the light socket with silicone so the water can't
reach the socket. I remounted it, aimed the light and then put some
more silicon around the exterior of the ball and socket joint to
hopefully prevent water from entering the fixture in the first place.


Wow! You have a lot of time on your hands.


It took less time to add some silicon to the old fixture than it would have
taken me to go to the store and buy a new one.

Removal and installation was required in both cases, so that's a wash.




All times are GMT +1. The time now is 01:05 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter