In a current thread, gfretw told a poster that one
way to indentify 3 phase service is if it's connected
to two or three transformers. That brought back a
question that has stumped me for a very long time.

I know that it's possible to get 3 phase service with
just two transformers. Apparently that is used for cost
savings on lighter 3 phase loads. But what I don't
understand is how you can get true 3 phase with only
TWO transformers. Coming down the road you
have 3 high voltage lines. Each of those has an AC
waveform and each is 120deg off in phase from the
other. If you have three step-down transformers,
then you have one transformer connected to each
high voltage line and obviously you get 3 waveforms
out that have the same 120deg phase relation as
those on the high voltage side.

But how do you get 3 waveforms at 120deg shift
relative to each other with only two transformers
connected to only two of the 3 high voltage lines?
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Three phase from 2 transformers?

On 1/14/2013 9:31 AM, wrote:
In a current thread, gfretw told a poster that one
way to indentify 3 phase service is if it's connected
to two or three transformers. That brought back a
question that has stumped me for a very long time.

I know that it's possible to get 3 phase service with
just two transformers. Apparently that is used for cost
savings on lighter 3 phase loads. But what I don't
understand is how you can get true 3 phase with only
TWO transformers. Coming down the road you
have 3 high voltage lines. Each of those has an AC
waveform and each is 120deg off in phase from the
other. If you have three step-down transformers,
then you have one transformer connected to each
high voltage line and obviously you get 3 waveforms
out that have the same 120deg phase relation as
those on the high voltage side.

But how do you get 3 waveforms at 120deg shift
relative to each other with only two transformers
connected to only two of the 3 high voltage lines?


Would be a lot easier to explain with a pencil and piece of paper.

The usual delta connection has a 120/240V transformer, and then adds
3-phase to that. A diagram is about halfway down
http://en.wikipedia.org/wiki/Three-phase_electric_power
where the transformers are connected in a triangle.

L1-N-L2 is a single phase 120/240V Edison circuit. Two transformers add
L3 - L1-L2-L3 is 3 phase 240V. The voltage from N-L3 is 208V and is
called the "high" leg (or several other names). This is "high-leg delta".

But it still works if the L1-L3 transformer is not used. It is then
called open delta and only uses 2 transformers. This used to be
moderately common and is still around. It is probably not used for
anything new. It is pretty easy to identify because of 2 utility
transformers, only one of which has a secondary neutral connection.

=======================================
For a wye connection, a Scott (or T) transformer connection can be used.
See the diagram about halfway down labeled "Scott T transformer 3ph to 3 ph"
http://en.wikipedia.org/wiki/Scott-T_transformer
X1-X2-X3 are 3-phase with X0 being the neutral. This gives a wye
3-phase. A rather common use would be 480V 3-phase connected to H1-H2-H3
and 277/120V coming out X1-X2-X3-X0.

This is used on some relatively small "dry" transformers in buildings
with a 480V service. The advantage is you have 3 phase with only 2
transformers. The disadvantage is you screw up the power factor on both
transformers and have to derate them to 87% (if I remember right). (And
if I remember right, the delta transformers above also have to be
derated for the 3-phase power.)

I don't think utilities ever use this connection.

The transformers actually run at real 2-phase at 90 degrees. You can use
a Scott connection to actually use the 2-phase.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Three phase from 2 transformers?

On Jan 14, 11:22*am, bud-- wrote:
On 1/14/2013 9:31 AM, wrote:





In a current thread, gfretw told a poster that one
way to indentify 3 phase service is if it's connected
to two or three transformers. * That brought back a
question that has stumped me for a very long time.


I know that it's possible to get 3 phase service with
just two transformers. *Apparently that is used for cost
savings on lighter 3 phase loads. *But what I don't
understand is how you can get true 3 phase with only
TWO transformers. *Coming down the road you
have 3 high voltage lines. *Each of those has an AC
waveform and each is 120deg off in phase from the
other. *If you have three step-down transformers,
then you have one transformer connected to each
high voltage line and obviously you get 3 waveforms
out that have the same 120deg phase relation as
those on the high voltage side.


But how do you get 3 waveforms at 120deg shift
relative to each other with only two transformers
connected to only two of the 3 high voltage lines?


Would be a lot easier to explain with a pencil and piece of paper.

The usual delta connection has a 120/240V transformer, and then adds
3-phase to that. A diagram is about halfway downhttp://en.wikipedia.org/wiki/Three-phase_electric_power
where the transformers are connected in a triangle.

L1-N-L2 is a single phase 120/240V Edison circuit. Two transformers add
L3 - L1-L2-L3 is 3 phase 240V. The voltage from N-L3 is 208V and is
called the "high" leg (or several other names). This is "high-leg delta".

But it still works if the L1-L3 transformer is not used. It is then
called open delta and only uses 2 transformers. This used to be
moderately common and is still around. It is probably not used for
anything new. It is pretty easy to identify because of 2 utility
transformers, only one of which has a secondary neutral connection.

=======================================
For a wye connection, a Scott (or T) transformer connection can be used.
See the diagram about halfway down labeled "Scott T transformer 3ph to 3 ph"http://en.wikipedia.org/wiki/Scott-T_transformer
X1-X2-X3 are 3-phase with X0 being the neutral. This gives a wye
3-phase. A rather common use would be 480V 3-phase connected to H1-H2-H3
and 277/120V coming out X1-X2-X3-X0.

This is *used on some relatively small "dry" transformers in buildings
with a 480V service. The advantage is you have 3 phase with only 2
transformers. The disadvantage is you screw up the power factor on both
transformers and have to derate them to 87% (if I remember right). (And
if I remember right, the delta transformers above also have to be
derated for the 3-phase power.)

I don't think utilities ever use this connection.

The transformers actually run at real 2-phase at 90 degrees. You can use
a Scott connection to actually use the 2-phase.- Hide quoted text -

- Show quoted text -


But the question is, when using only two transformers
tied into two of the 3 phases, what generates the missing third phase
that is 120deg away from the other two? Does a special transformer
give the phase shift? A typical
transformer that you would use in a 3 phase installation
using 3 transformers, tied to all 3 high voltage phases
gives outputs that are not phase shifted, or at least by
only a little, right?
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,907
Default Three phase from 2 transformers?

On 1/14/2013 11:22 AM, bud-- wrote:
On 1/14/2013 9:31 AM, wrote:
In a current thread, gfretw told a poster that one
way to indentify 3 phase service is if it's connected
to two or three transformers. That brought back a
question that has stumped me for a very long time.

I know that it's possible to get 3 phase service with
just two transformers. Apparently that is used for cost
savings on lighter 3 phase loads. But what I don't
understand is how you can get true 3 phase with only
TWO transformers. Coming down the road you
have 3 high voltage lines. Each of those has an AC
waveform and each is 120deg off in phase from the
other. If you have three step-down transformers,
then you have one transformer connected to each
high voltage line and obviously you get 3 waveforms
out that have the same 120deg phase relation as
those on the high voltage side.

But how do you get 3 waveforms at 120deg shift
relative to each other with only two transformers
connected to only two of the 3 high voltage lines?


Would be a lot easier to explain with a pencil and piece of paper.

The usual delta connection has a 120/240V transformer, and then adds
3-phase to that. A diagram is about halfway down
http://en.wikipedia.org/wiki/Three-phase_electric_power
where the transformers are connected in a triangle.

L1-N-L2 is a single phase 120/240V Edison circuit. Two transformers add
L3 - L1-L2-L3 is 3 phase 240V. The voltage from N-L3 is 208V and is
called the "high" leg (or several other names). This is "high-leg delta".

But it still works if the L1-L3 transformer is not used. It is then
called open delta and only uses 2 transformers. This used to be
moderately common and is still around. It is probably not used for
anything new. It is pretty easy to identify because of 2 utility
transformers, only one of which has a secondary neutral connection.



Open delta is our fairly large utilities standard implementation for
light commercial loads that need 3 phase.



=======================================
For a wye connection, a Scott (or T) transformer connection can be used.
See the diagram about halfway down labeled "Scott T transformer 3ph to 3
ph"
http://en.wikipedia.org/wiki/Scott-T_transformer
X1-X2-X3 are 3-phase with X0 being the neutral. This gives a wye
3-phase. A rather common use would be 480V 3-phase connected to H1-H2-H3
and 277/120V coming out X1-X2-X3-X0.

This is used on some relatively small "dry" transformers in buildings
with a 480V service. The advantage is you have 3 phase with only 2
transformers. The disadvantage is you screw up the power factor on both
transformers and have to derate them to 87% (if I remember right). (And
if I remember right, the delta transformers above also have to be
derated for the 3-phase power.)

I don't think utilities ever use this connection.

The transformers actually run at real 2-phase at 90 degrees. You can use
a Scott connection to actually use the 2-phase.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Three phase from 2 transformers?

On 1/15/2013 8:11 AM, wrote:
On Jan 14, 11:22 am, wrote:
On 1/14/2013 9:31 AM, wrote:





In a current thread, gfretw told a poster that one
way to indentify 3 phase service is if it's connected
to two or three transformers. That brought back a
question that has stumped me for a very long time.


I know that it's possible to get 3 phase service with
just two transformers. Apparently that is used for cost
savings on lighter 3 phase loads. But what I don't
understand is how you can get true 3 phase with only
TWO transformers. Coming down the road you
have 3 high voltage lines. Each of those has an AC
waveform and each is 120deg off in phase from the
other. If you have three step-down transformers,
then you have one transformer connected to each
high voltage line and obviously you get 3 waveforms
out that have the same 120deg phase relation as
those on the high voltage side.


But how do you get 3 waveforms at 120deg shift
relative to each other with only two transformers
connected to only two of the 3 high voltage lines?


Would be a lot easier to explain with a pencil and piece of paper.

The usual delta connection has a 120/240V transformer, and then adds
3-phase to that. A diagram is about halfway downhttp://en.wikipedia.org/wiki/Three-phase_electric_power
where the transformers are connected in a triangle.

L1-N-L2 is a single phase 120/240V Edison circuit. Two transformers add
L3 - L1-L2-L3 is 3 phase 240V. The voltage from N-L3 is 208V and is
called the "high" leg (or several other names). This is "high-leg delta".

But it still works if the L1-L3 transformer is not used. It is then
called open delta and only uses 2 transformers. This used to be
moderately common and is still around. It is probably not used for
anything new. It is pretty easy to identify because of 2 utility
transformers, only one of which has a secondary neutral connection.

=======================================
For a wye connection, a Scott (or T) transformer connection can be used.
See the diagram about halfway down labeled "Scott T transformer 3ph to 3 ph"http://en.wikipedia.org/wiki/Scott-T_transformer
X1-X2-X3 are 3-phase with X0 being the neutral. This gives a wye
3-phase. A rather common use would be 480V 3-phase connected to H1-H2-H3
and 277/120V coming out X1-X2-X3-X0.

This is used on some relatively small "dry" transformers in buildings
with a 480V service. The advantage is you have 3 phase with only 2
transformers. The disadvantage is you screw up the power factor on both
transformers and have to derate them to 87% (if I remember right). (And
if I remember right, the delta transformers above also have to be
derated for the 3-phase power.)

I don't think utilities ever use this connection.

The transformers actually run at real 2-phase at 90 degrees. You can use
a Scott connection to actually use the 2-phase.- Hide quoted text -

- Show quoted text -


But the question is, when using only two transformers
tied into two of the 3 phases, what generates the missing third phase
that is 120deg away from the other two? Does a special transformer
give the phase shift? A typical
transformer that you would use in a 3 phase installation
using 3 transformers, tied to all 3 high voltage phases
gives outputs that are not phase shifted, or at least by
only a little, right?


Crappy ASCII art (requires fixed width font):

B
\
\
\
\
\
A ___________C
N

This is a 240V open-delta secondary connection diagram (all diagrams are
show pseudo-phasor relationships). A center-tapped 240V transformer is
shown between A and C. A 240V transformer is shown between B and C.

Transformer connections on the primary are different voltage but connect
to the 3 phase supply the same way (with no neutral). *The primary
connections use all 3 phases*. The primary connections to the 3-phase
supply put transformer AC and transformer BC at a 120 degree phase
relationship. As a result you have 3-phase at secondary A-B-C just like
you have 3-phase where the transformer primaries are connected.

==============================================
Any modern 3-phase is likely to be 208/120V wye, or 480/277V wye for
larger buildings and industrial.

A
|
|
|
|
N
/ \
/ \
/ \
/ \
B C


There isn't a simple trick like open delta for wye (because you need to
create the neutral), but the Scott connection is about as simple.


B
|
|
|
|N
|
A____________C
Q


On the primary side one transformer connects between phases A and C. The
other transformer connects from phase B to the centertap (Q) of
transformer AC. As a result the transformers are electrically at 90
degrees.

The secondary connections are similar and convert the 2-phase from the
transformers back to 3-phase. The critical addition is a tap at N to
supply the neutral.

For a 208/120V secondary you have AB=BC=AC=208V. AN=BN=CN=120V (BQ=180V)


============================
For both open-delta and Scott the transformer primaries connect to all 3
phases, which determines the phase relationships between the 2
transformers, and the phase relationship of the transformers creates the
3-phase at the secondary connections.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Three phase from 2 transformers?

On Jan 15, 12:03*pm, wrote:
On Tue, 15 Jan 2013 06:11:52 -0800 (PST), "

wrote:
But the question is, when using only two transformers
tied into two of the 3 phases, what generates the missing third phase
that is 120deg away from the other two? *Does a special transformer
give the phase shift? *A typical
transformer that you would use in a 3 phase installation
using 3 transformers, tied to all 3 high voltage phases
gives outputs that are not phase shifted, or at least by
only a little, right?


With the open delta, usually the only time you have phase problems is
if you connect 240v line to line loads across the "missing"
transformer. Then you will see *voltage differences phase to phase.


But I'm not talking about phase problems. I'm talking
about what creates the missing third phase period. Coming
down the road we have 3 high voltage phases. One
is at 0deg, one is at 120deg, one is at 240deg. If
I hook up 3 seperate transformers to get 3 phase,
which I see a lot, then coming out of those 3
transformers are lower voltage waveforms that are
at 0deg, 120deg, 240deg, neglecting any unintentional
shift. So, you have 3 phase just like on the high voltage
side, just stepped down. It makes sense.

But now if they only use 2 transformers, I can see where
you directly get any two of those 3 waveforms. Let's say
I hook one of the two transformers to the 0 deg high
voltage line. I hood the other to the 120deg high voltage
line. I can see how out of that I get 0deg and 120deg
for the 3 phase service, just like I did before. The question is,
what generates the 240deg phase? Phase shift from one
of the transformers?





  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1
Default Three phase from 2 transformers?

Look up open delta transformer, you will get the answer you seek.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rotary phase converter versus trying to run a VMC straight from single phase Wes[_2_] Metalworking 0 February 19th 08 06:31 PM
Single Phase Backup Generator to Three Phase Mains Supply? [email protected] Home Repair 3 January 24th 08 02:30 AM
Single Phase Backup Generator to Three Phase Mains Supply? [email protected] UK diy 5 January 22nd 08 10:08 PM
profit-motive question: single phase adapter for 3-phase motor drives gwes Metalworking 8 October 5th 07 08:33 PM
3-phase used for 1-phase (split-phase) power SRK Home Repair 9 July 22nd 06 11:01 AM


All times are GMT +1. The time now is 07:59 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"