I was told that I couldn't convert my heating system to gas because
"my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce |
Oil to Gas Heat Conversion
"Bruce K." wrote in message
... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. This concerns fire safety. You can get specific information (usually without charge) from the municipal building permits office and/or the local fire brigade. -- Don Phillipson Carlsbad Springs (Ottawa, Canada) |
Oil to Gas Heat Conversion
I have no info for you, but I can guess that the first two questions
you're going to get here a What kind of heating do you have now? What sort of chimney do you have? |
Oil to Gas Heat Conversion
"Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Could be BS as many conversions have been done over the years. If you have an old heater, it may be a poor choice. If you get a new heater, it will be more efficient and no chimney needed. |
Oil to Gas Heat Conversion
On May 3, 8:26*am, Larry Fishel wrote:
I have no info for you, but I can guess that the first two questions you're going to get here a What kind of heating do you have now? What sort of chimney do you have? +1 to that. But in general it sounds like BS to me. Any heating system you buy today is going to be a lot more efficient than the one it replaces. And that should mean cooler exhaust temps, not higher ones. With a high efficiency condensing system, the exhaust gases are so cool that 1 1/2" or 3" PVC pipe is used to vent the unit directly outside without a chimney. Now it's entirely possible that he could have a crap chimney that is in such a sorry state that it won't pass inspection. That would prevent any new unit, oil or gas from being installed. |
Oil to Gas Heat Conversion
Sounds backwards. I'd call two more companies, for their opinions. Don't
mention what the first company said. Christopher A. Young Learn more about Jesus www.lds.org .. "Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce |
Oil to Gas Heat Conversion
"Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Gas runs cooler than oil. In the past gas required a double wall class-B metal chimney and oil required an insulated class-A chimney. A masonry chimney could be used if it was lined, water would condense out of the gas exhaust and damage unlined mortar joints until it leaked through to the outside. Now gas condensing furnaces/boilers need only a plastic pipe. Don't listen to the idiot who told you that, ask people who know the real answer, and can give you solutions. |
Oil to Gas Heat Conversion
On 5/3/2012 9:31 AM, EXT wrote:
"Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Gas runs cooler than oil. In the past gas required a double wall class-B metal chimney and oil required an insulated class-A chimney. A masonry chimney could be used if it was lined, water would condense out of the gas exhaust and damage unlined mortar joints until it leaked through to the outside. Now gas condensing furnaces/boilers need only a plastic pipe. Don't listen to the idiot who told you that, ask people who know the real answer, and can give you solutions. +1 Most brand new gas condensing furnaces exhaust out thru 4 " plastic pipe (636 it's called), rated for 65 C, not sure what that is in F. Chimneys are no longer required for high efficiency furnaces, and to honest, are they still allowed to sell furnaces under 92 AFUE where you are because they are not. My gas exhaust pipe just runs along some floor joists and out the wall for a total 20' run. These days gas furnace exhausts alot more steam than anything else. There may be government rebates in your area regarding furnace replacement. Research them. Sounds like you got to find some more guys in your area who can give you several options. |
Oil to Gas Heat Conversion
I hope you will reply back with some additional information regarding what
type of heating system you have now (such as steam, hot water, or hot air -- if steam, one-pipe or two-pipe radiator system), how many BTU's your heater and hot water heater are, what diameter connector pipes go into your present chimney, and what type of chimney you have now. Bruce K. wrote: I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce |
Oil to Gas Heat Conversion
On 5/3/2012 5:34 AM, Bruce K. wrote:
I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. So you switch to a high-efficiency gas furnace that vents out the wall and bypasses the chimney entirely. That's how high-efficiency gas furnaces work. Before I switched to a high-efficiency furnace, the installer for the prior gas furnace expressed some doubts about the heat integrity of my chimney. He installed a liner in it. Problem solved. There you go - two solutions that let you get what you want. |
Oil to Gas Heat Conversion
On 5/3/2012 5:34 AM, Bruce K. wrote:
I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce You can always have the installer put a liner in the chimney. -- Steve Barker remove the "not" from my address to email |
Oil to Gas Heat Conversion
On May 3, 8:26*am, Larry Fishel wrote:
I have no info for you, but I can guess that the first two questions you're going to get here a What kind of heating do you have now? What sort of chimney do you have? My bad. I failed to note the title of the thread... |
Oil to Gas Heat Conversion
EXT wrote:
"Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Gas runs cooler than oil. In the past gas required a double wall class-B metal chimney and oil required an insulated class-A chimney. A masonry chimney could be used if it was lined. . . . , Speaking of class B (or Type B) metal chimneys, I am in the middle of trying to get one figured out. I'll post a new thread about my situation and questions. Now gas condensing furnaces/boilers need only a plastic pipe. I my case, I couldn't change my boiler to a high efficiency direct-vent system without a huge expense because I have a one-pipe steam radiator heating system. They don't make high efficiency direct-vent steam boilers and changing over to a hot water system wouldn't work because I have one-pipe (not two-pipe) radiators now. |
Oil to Gas Heat Conversion
On Thu, 03 May 2012 06:34:16 -0400, Bruce K.
wrote: I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Two words - BEE ESS. You can ALWAYS go to a chimney-less condensing gas system that exhausts through the wall, just above ground level, with a 2 inch pipe that never gets hot enough to soften, or even be uncomfortably warm if touched. |
Oil to Gas Heat Conversion
On Thu, 3 May 2012 06:53:21 -0400, "Don Phillipson"
wrote: "Bruce K." wrote in message .. . I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. This concerns fire safety. You can get specific information (usually without charge) from the municipal building permits office and/or the local fire brigade. If it is good enough for an old oil furnace, adding a stainless steel liner pipe will definitely make it safe for gas, heat-wize. |
Oil to Gas Heat Conversion
On Thu, 3 May 2012 05:47:54 -0700 (PDT), "
wrote: On May 3, 8:26Â*am, Larry Fishel wrote: I have no info for you, but I can guess that the first two questions you're going to get here a What kind of heating do you have now? What sort of chimney do you have? +1 to that. But in general it sounds like BS to me. Any heating system you buy today is going to be a lot more efficient than the one it replaces. And that should mean cooler exhaust temps, not higher ones. With a high efficiency condensing system, the exhaust gases are so cool that 1 1/2" or 3" PVC pipe is used to vent the unit directly outside without a chimney. Now it's entirely possible that he could have a crap chimney that is in such a sorry state that it won't pass inspection. That would prevent any new unit, oil or gas from being installed. Unless it didn't need the chimney, as stated above. |
Oil to Gas Heat Conversion
On Thu, 3 May 2012 15:23:24 -0400, "TomR" wrote:
EXT wrote: "Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Gas runs cooler than oil. In the past gas required a double wall class-B metal chimney and oil required an insulated class-A chimney. A masonry chimney could be used if it was lined. . . . , Speaking of class B (or Type B) metal chimneys, I am in the middle of trying to get one figured out. I'll post a new thread about my situation and questions. Now gas condensing furnaces/boilers need only a plastic pipe. I my case, I couldn't change my boiler to a high efficiency direct-vent system without a huge expense because I have a one-pipe steam radiator heating system. They don't make high efficiency direct-vent steam boilers and changing over to a hot water system wouldn't work because I have one-pipe (not two-pipe) radiators now. OK - a totally different situation. You wanted to convert your BURNER from oil to gas. Chimney liner. |
Oil to Gas Heat Conversion
|
Oil to Gas Heat Conversion
"Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Most likely not from the heat but from the moisture Also modern high-efficiency gas furnaces will shove less heat up a chimney an old, less efficient, oil furnace. Why not look at a high performance gas furnace that does NOT need a chimney and has both vent and air intake to the side of the house ? |
Oil to Gas Heat Conversion
On Fri, 4 May 2012 12:05:22 -0500, "Attila.Iskander"
wrote: "Bruce K." wrote in message .. . I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Most likely not from the heat but from the moisture Right, particularly if the chimney is on an exterior wall. Also modern high-efficiency gas furnaces will shove less heat up a chimney an old, less efficient, oil furnace. Not even that. When I converted from oil to gas (same unit, different burner) they would have required a SS liner had the chimney not been in the center of the house. The idea is that if the chimney is not on an exterior wall it'll stay warm, so won't condense the excess water caused by burning gas. Why not look at a high performance gas furnace that does NOT need a chimney and has both vent and air intake to the side of the house ? Good plan, or just throw a liner in the chimney. It's not *that* expensive. A condensing unit is a better plan all around, IMO. |
Oil to Gas Heat Conversion
"TomR" wrote:
EXT wrote: "Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Gas runs cooler than oil. In the past gas required a double wall class-B metal chimney and oil required an insulated class-A chimney. A masonry chimney could be used if it was lined. . . . , Speaking of class B (or Type B) metal chimneys, I am in the middle of trying to get one figured out. I'll post a new thread about my situation and questions. Now gas condensing furnaces/boilers need only a plastic pipe. I my case, I couldn't change my boiler to a high efficiency direct-vent system without a huge expense because I have a one-pipe steam radiator heating system. They don't make high efficiency direct-vent steam boilers and changing over to a hot water system wouldn't work because I have one-pipe (not two-pipe) radiators now. Steam heat. Real boiler. There is a way to extract additional heat, just like the hot air furnace works, additional hot air heat extractor. You would need at least one complete air ducting. With steam the heat coming out of the chimney is going to be around 210 degrees or higher, if it's boiling. Greg |
Oil to Gas Heat Conversion
"gregz" wrote in message ... "TomR" wrote: EXT wrote: "Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Gas runs cooler than oil. In the past gas required a double wall class-B metal chimney and oil required an insulated class-A chimney. A masonry chimney could be used if it was lined. . . . , Speaking of class B (or Type B) metal chimneys, I am in the middle of trying to get one figured out. I'll post a new thread about my situation and questions. Now gas condensing furnaces/boilers need only a plastic pipe. I my case, I couldn't change my boiler to a high efficiency direct-vent system without a huge expense because I have a one-pipe steam radiator heating system. They don't make high efficiency direct-vent steam boilers and changing over to a hot water system wouldn't work because I have one-pipe (not two-pipe) radiators now. Steam heat. Real boiler. There is a way to extract additional heat, just like the hot air furnace works, additional hot air heat extractor. You would need at least one complete air ducting. With steam the heat coming out of the chimney is going to be around 210 degrees or higher, if it's boiling. On might want to pump that through a heat exchanger to a large water tank. There must be a way to save and use those calories being wasted up the chimney. |
Oil to Gas Heat Conversion
On Sat, 5 May 2012 18:35:02 -0500, "Attila.Iskander"
wrote: "gregz" wrote in message ... "TomR" wrote: EXT wrote: "Bruce K." wrote in message ... I was told that I couldn't convert my heating system to gas because "my chimney won't tolerate the exaust heat" I would appreciate any opinion on this. Thanks in advance. Bruce Gas runs cooler than oil. In the past gas required a double wall class-B metal chimney and oil required an insulated class-A chimney. A masonry chimney could be used if it was lined. . . . , Speaking of class B (or Type B) metal chimneys, I am in the middle of trying to get one figured out. I'll post a new thread about my situation and questions. Now gas condensing furnaces/boilers need only a plastic pipe. I my case, I couldn't change my boiler to a high efficiency direct-vent system without a huge expense because I have a one-pipe steam radiator heating system. They don't make high efficiency direct-vent steam boilers and changing over to a hot water system wouldn't work because I have one-pipe (not two-pipe) radiators now. Steam heat. Real boiler. There is a way to extract additional heat, just like the hot air furnace works, additional hot air heat extractor. You would need at least one complete air ducting. With steam the heat coming out of the chimney is going to be around 210 degrees or higher, if it's boiling. On might want to pump that through a heat exchanger to a large water tank. There must be a way to save and use those calories being wasted up the chimney. One of the reasons real "steam" heat is virtually extinct today. |
All times are GMT +1. The time now is 08:16 AM. |
Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter