Sump pumps -- GFCI required?
I have a sump pump in an unfinished basement. It is on a dedicated 15-amp
120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? |
#2
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
"Jay-T" wrote in message ... I have a sump pump in an unfinished basement. It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? It's not done by the appliance, but the receptacle location. The NEC requires all outlets in unfinished parts of basements to be GFCI protected. I do a lot of work with pumps, and from my experience, about 1 in 10 sump pumps will trip a GFCI, when brand new, right out of the box. You have two choices: Cheat, and replace the GFCI with a standard outlet, or cut the plug off of the pump and hard wire it with a switch to shut it off, which wouldn't require GFCI protection |
#3
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
For whats its worth during selling home 2 seperate home inspectors
wqrote up my sump pump first for no GFCI.......... sale fell thru........ \but I installed GFCI, second home inspector wrote it up saying you should never GFCI a sump pump. second buyer bought home anyway...... I beleve a single non GFCI outlet is proper |
#4
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
wrote in message ... For whats its worth during selling home 2 seperate home inspectors wqrote up my sump pump first for no GFCI.......... sale fell thru........ \but I installed GFCI, second home inspector wrote it up saying you should never GFCI a sump pump. second buyer bought home anyway...... I beleve a single non GFCI outlet is proper Home inspectors are not by any stretch, electrical inspectors. If you had five different ones, you'd probably get five different opinions. Typically, electrical wiring is inspected and certified, when installed, and grandfathered until such a time when changes are made to it, otherwise, virtually all the wiring in a home that isn't 90 degree, would have to be replaced. If the outlet that you plug your pump into was installed before GFCI protection was required, there is most likely no legal reason why you should have to replace it. |
#5
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
"RBM" wrote in message
... "Jay-T" wrote in message ... I have a sump pump in an unfinished basement. It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? It's not done by the appliance, but the receptacle location. The NEC requires all outlets in unfinished parts of basements to be GFCI protected. I do a lot of work with pumps, and from my experience, about 1 in 10 sump pumps will trip a GFCI, when brand new, right out of the box. You have two choices: Cheat, and replace the GFCI with a standard outlet, or cut the plug off of the pump and hard wire it with a switch to shut it off, which wouldn't require GFCI protection Thanks. I may end up going with the first option, "Cheat, and replace the GFCI with a standard outlet", since having a sump pump that trips the GFCI when in use doesn't make sense. I guess I could do the second option of cutting the plug off and hard wiring it. But, I would have to figure out how to do that because the sump pump I have has a plug with two cords going into it -- I assume one is power to the pump and the other is from the float switch. If I did that approach, would I have to have a shut-off switch added to the circuit, or would the dedicated sump pump circuit breaker be sufficient to serve as the shut-off? |
#6
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
"Jay-T" wrote in message ... "RBM" wrote in message ... "Jay-T" wrote in message ... I have a sump pump in an unfinished basement. It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? It's not done by the appliance, but the receptacle location. The NEC requires all outlets in unfinished parts of basements to be GFCI protected. I do a lot of work with pumps, and from my experience, about 1 in 10 sump pumps will trip a GFCI, when brand new, right out of the box. You have two choices: Cheat, and replace the GFCI with a standard outlet, or cut the plug off of the pump and hard wire it with a switch to shut it off, which wouldn't require GFCI protection Thanks. I may end up going with the first option, "Cheat, and replace the GFCI with a standard outlet", since having a sump pump that trips the GFCI when in use doesn't make sense. I guess I could do the second option of cutting the plug off and hard wiring it. But, I would have to figure out how to do that because the sump pump I have has a plug with two cords going into it -- I assume one is power to the pump and the other is from the float switch. If I did that approach, would I have to have a shut-off switch added to the circuit, or would the dedicated sump pump circuit breaker be sufficient to serve as the shut-off? It would require a means of disconnect within 50 feet of the pump and within sight of it. You could also install a lock on the circuit breaker |
#7
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
On Dec 17, 12:51*am, "Jay-T" wrote:
"RBM" wrote in message ... "Jay-T" wrote in message ... I have a sump pump in an unfinished basement. *It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? It's not done by the appliance, but the receptacle location. The NEC requires all outlets in unfinished parts of basements to be GFCI protected. I do a lot of work with pumps, and from my experience, about 1 in 10 sump pumps will trip a GFCI, when brand new, right out of the box.. You have two choices: Cheat, and replace the GFCI with a standard outlet, or cut the plug off of the pump and hard wire it with a switch to shut it off, which wouldn't require GFCI protection Thanks. *I may end up going with the first option, "Cheat, and replace the GFCI with a standard outlet", since having a sump pump that trips the GFCI when in use doesn't make sense. I guess I could do the second option of cutting the plug off and hard wiring it. *But, I would have to figure out how to do that because the sump pump I have has a plug with two cords going into it -- I assume one is power to the pump and the other is from the float switch. *If I did that approach, would I have to have a shut-off switch added to the circuit, or would the dedicated sump pump circuit breaker be sufficient to serve as the shut-off?- Hide quoted text - - Show quoted text - Just make sure that the GFCI doesn't feed other outlets downstream. If it does and you eliminate it from the sump pump outlet, make sure to re-install it in the next downstream outlet. |
#8
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
I have a sump pump in an unfinished basement. It is on a dedicated 15-amp
120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? *The latest code edition now requires that all unfinished basement receptacles as well as all garage receptacles regardless of their location be GFI protected. This apparently was changed because people will plug things in no matter where the receptacle is and what it is for. I have seen plenty of extension cords hanging from garage ceilings to agree with the requirement that garage door opener receptacles be GFI protected. Unfortunately that does present a problem as you found out the hard way. I suggest that you write to the NFPA about your personal experience in this case. My thought is that there should be another type of receptacle for the sump pump such as a twist lock without GFI protection. That would make the receptacle unavailable for general use and keep it for sump pump use only and thus eliminate the potential damage from nuisance tripping. If GFI protection is required for the pump, an equipment GFI can be installed along with the twist lock receptacle. An equipment GFI does not have the same low threshold for tripping as the one used for people protection and consequently is less prone to nuisance tripping. |
#9
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
In article , "John Grabowski" wrote:
I have a sump pump in an unfinished basement. It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? 2008 NEC, yes -- which IMHO is completely insane. 2005 and earlier NEC, no. Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? Won't matter. *The latest code edition now requires that all unfinished basement receptacles as well as all garage receptacles regardless of their location be GFI protected. This apparently was changed because people will plug things in no matter where the receptacle is and what it is for. I have seen plenty of extension cords hanging from garage ceilings to agree with the requirement that garage door opener receptacles be GFI protected. Yes, but note that it also says "for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like." [2008 NEC, Article 210.8(A)(5)] So put a TV, easy chair, and your beer fridge within a yard or two of the sump pit, and you've turned that "portion or area of the basement" into a "habitable room" -- which means that "for purposes of this section" it's no longer "unfinished" and therefore *not* required to have a GFCI. There's another workaround: the GFCI requirement applies only to "125-volt, single-phase, 15- and 20-ampere receptacles." So install a 30-amp circuit and receptacle, and change the plug on the sump pump. Note also that the *2005* NEC contains the same language, and additionally two pertinent exceptions to the GFCI requirement that were removed in the 2008 Code: "Receptacles that are not readily accessible" and "Receptacles located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected..." So if the governing authority in the OP's jurisdiction is the 2005 (or earlier) Code and not 2008, he apparently has no worries. |
#10
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
The latest code edition now requires that all unfinished basement
receptacles as well as all garage receptacles regardless of their location be GFI protected. Not in Oregon. There are local amendments to this rule and a GFCI is not required on a sump pump (in Oregon). Check with your local electrical inspector. |
#11
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
To the O/P
does the pump trip the GFI whenever the pump is underwater, or only during the on/off surge? If it trips whenever the pump is underwater, then you may want to investigate the source of the leakage. And don't put your hand in the water when the pump is plugged in. Mark |
#12
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
Doug Miller wrote:
There's another workaround: the GFCI requirement applies only to "125-volt, single-phase, 15- and 20-ampere receptacles." So install a 30-amp circuit and receptacle, and change the plug on the sump pump. Then it is not UL listed - it was designed and tested on a 20A ckt. Note also that the *2005* NEC contains the same language, and additionally two pertinent exceptions to the GFCI requirement that were removed in the 2008 Code: "Receptacles that are not readily accessible" and "Receptacles located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected..." So if the governing authority in the OP's jurisdiction is the 2005 (or earlier) Code and not 2008, he apparently has no worries. I would replace the GFCI with a single (not duplex) 15A receptacle. If at some point in the future (like a home inspection) this is flagged it is not that hard to reinstall a GFCI. I would call 7 1/2 feet high not "readily accessible". If it was installed before the 2008 NEC and is a single receptacle it should be compliant now. (And who is to say if a single receptacle is not what was installed.) Or if you are having any electrical work inspected, ask the inspector if they would theoretically approve a single receptacle in that case. If they would, have it inspected. An inspector has discretion to modify what is required, and this is a reasonable modification. If passed, it IMHO is compliant in the future. -- bud-- |
#13
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
Mark wrote:
To the O/P does the pump trip the GFI whenever the pump is underwater, or only during the on/off surge? I am the OP. I do not know for sure when the sump pump trips the GFCI. I own the property but another family lives there, not me. When I checked the basement recently, there was water in the basement in the sump pump area, about 1-2 inches above the floor level. There was no power to the sump pump, and resetting the GFCI made the pump turn on and it pumped out all of the water without tripping the GFCI again. The sump pump is on a dedicated circuit that goes directly from the main panel (on its own 15-amp breaker) to the GFCI receptacle in the ceiling. Nothing else is on that circuit -- no switches, no receptacles, etc. The sump pump had been there for 3+ years and used to be plugged into a regular, non-GFCI, outlet elsewhere in the basement with an extension cord. During those 3 years, it never failed to work. The new dedicated sump pump circuit with the ceiling GFCI outlet above the sump pump was installed 6 months ago by a licensed electrician. I guess it is possible that the pump tripped the GFCI some time during the last 6 months and no one noticed it. The family that lives there rarely goes into the basement and may not have thought to check the basement for water after a rain. But, my guess is that the GFCI was tripped more recently. If it trips whenever the pump is underwater, then you may want to investigate the source of the leakage. And don't put your hand in the water when the pump is plugged in. Mark |
#14
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
RBM wrote:
"Jay-T" wrote in message I guess I could do the second option of cutting the plug off and hard wiring it. But, I would have to figure out how to do that because the sump pump I have has a plug with two cords going into it -- I assume one is power to the pump and the other is from the float switch. If I did that approach, would I have to have a shut-off switch added to the circuit, or would the dedicated sump pump circuit breaker be sufficient to serve as the shut-off? It would require a means of disconnect within 50 feet of the pump and within sight of it. You could also install a lock on the circuit breaker. Good, the main panel is less than 30 feet away and in direct sight of the sump pump. The dedicated sump pump circuit breaker is very clearly marked and is at the bottom of the panel away from the other circuit breakers. So, I assume that would serve as the disconnect. I would rather do that than have another switch somewhere that someone could accidentally turn off or turn off intentionally and forget to turn it back on. I would still have to figure out how the wiring in the sump pump plug is set up. It's a molded plug and two cords go into it -- one from the back and one from the side. I am guessing that the cord that ges into the side of the plug is a switch loop coming up from the float, but I don't know. I would have to figure that out if I decided to cut the plug off and hard wire the sump pump. |
#16
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
John Grabowski wrote:
I have a sump pump in an unfinished basement. It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? *The latest code edition now requires that all unfinished basement receptacles as well as all garage receptacles regardless of their location be GFI protected. This apparently was changed because people will plug things in no matter where the receptacle is and what it is for. I have seen plenty of extension cords hanging from garage ceilings to agree with the requirement that garage door opener receptacles be GFI protected. Unfortunately that does present a problem as you found out the hard way. I suggest that you write to the NFPA about your personal experience in this case. If I figure out who the NFPA is, and what their contact/mailing information is, I may just do that. My thought is that there should be another type of receptacle for the sump pump such as a twist lock without GFI protection. That would make the receptacle unavailable for general use and keep it for sump pump use only and thus eliminate the potential damage from nuisance tripping. If GFI protection is required for the pump, an equipment GFI can be installed along with the twist lock receptacle. An equipment GFI does not have the same low threshold for tripping as the one used for people protection and consequently is less prone to nuisance tripping. I think that is a good suggestion. It makes sense and it solves the problem that is intended to be solved by the new NEC. Maybe you could write to the NFPA too and submit your suggestion to them. In terms of safety, one problem with the latest code for sump pumps in unfinished basements is that the GFCI could cause the pump to fail and the basement to flood. Then, there would be the newly-created hazard of someone walking in the water and accidentally coming into contact with any electrical power source in the basement. |
#17
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
bud-- wrote:
I would replace the GFCI with a single (not duplex) 15A receptacle. If at some point in the future (like a home inspection) this is flagged it is not that hard to reinstall a GFCI. I am having a little trouble figuring out the "single (not duplex) 15A receptacle" option. When I do a search for single 15-amp receptacles, all I see are receptacles that have differently-shaped holes for the plug to go into -- there is a ground hole and then 2 flat slots that are in the same line, not parallel with each other. So, I would need a different style plug than the standard one that is now on the sump pump. Meanwhile, I can find a single 20-amp receptacle that has a slightly different configuration than a standard 15-amp plug, but it looks like a standard plug could go into it (I don't know if that's true). But, then I would have a receptacle that looks like it is for a 20-amp circuit, but the existing sump pump circuit is on a 15-amp circuit breaker. I would have to go to the property and check, but I suspect that since it is a dedicated 15-amp circuit that is only for, and only connected to, the sump pump, it probably is wired with 14/2 wire not 12/2 wire. |
#18
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
On Dec 17, 11:29*am, "Jay-T" wrote:
bud-- wrote: I would replace the GFCI with a single (not duplex) 15A receptacle. If at some point in the future (like a home inspection) this is flagged it is not that hard to reinstall a GFCI. I am having a little trouble figuring out the "single (not duplex) 15A receptacle" option. When I do a search for single 15-amp receptacles, all I see are receptacles that have differently-shaped holes for the plug to go into -- there is a ground hole and then 2 flat slots that are in the same line, not parallel with each other. *So, I would need a different style plug than the standard one that is now on the sump pump. Meanwhile, I can find a single 20-amp receptacle that has a slightly different configuration than a standard 15-amp plug, but it looks like a standard plug could go into it (I don't know if that's true). *But, then I would have a receptacle that looks like it is for a 20-amp circuit, but the existing sump pump circuit is on a 15-amp circuit breaker. *I would have to go to the property and check, but I suspect that since it is a dedicated 15-amp circuit that is only for, and only connected to, the sump pump, it probably is wired with 14/2 wire not 12/2 wire. If the area is an unfinished area/workshop, then the exception to the rule would seem to apply, if I read earlier posts correctly. |
#19
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
"Jay-T" wrote in message ... RBM wrote: "Jay-T" wrote in message I guess I could do the second option of cutting the plug off and hard wiring it. But, I would have to figure out how to do that because the sump pump I have has a plug with two cords going into it -- I assume one is power to the pump and the other is from the float switch. If I did that approach, would I have to have a shut-off switch added to the circuit, or would the dedicated sump pump circuit breaker be sufficient to serve as the shut-off? It would require a means of disconnect within 50 feet of the pump and within sight of it. You could also install a lock on the circuit breaker. Good, the main panel is less than 30 feet away and in direct sight of the sump pump. The dedicated sump pump circuit breaker is very clearly marked and is at the bottom of the panel away from the other circuit breakers. So, I assume that would serve as the disconnect. I would rather do that than have another switch somewhere that someone could accidentally turn off or turn off intentionally and forget to turn it back on. I would still have to figure out how the wiring in the sump pump plug is set up. It's a molded plug and two cords go into it -- one from the back and one from the side. I am guessing that the cord that ges into the side of the plug is a switch loop coming up from the float, but I don't know. I would have to figure that out if I decided to cut the plug off and hard wire the sump pump. If you cut the plugs off, you'll find a three wire cord to the motor, and as you suspected, a two wire cord going to the float, pretty self explanatory |
#20
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
"Doug Miller" wrote in message ... In article , "John Grabowski" wrote: I have a sump pump in an unfinished basement. It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? 2008 NEC, yes -- which IMHO is completely insane. 2005 and earlier NEC, no. Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? Won't matter. *The latest code edition now requires that all unfinished basement receptacles as well as all garage receptacles regardless of their location be GFI protected. This apparently was changed because people will plug things in no matter where the receptacle is and what it is for. I have seen plenty of extension cords hanging from garage ceilings to agree with the requirement that garage door opener receptacles be GFI protected. Yes, but note that it also says "for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like." [2008 NEC, Article 210.8(A)(5)] So put a TV, easy chair, and your beer fridge within a yard or two of the sump pit, and you've turned that "portion or area of the basement" into a "habitable room" -- which means that "for purposes of this section" it's no longer "unfinished" and therefore *not* required to have a GFCI. To be technically correct, he may then have to install additional outlets, as per habitable rooms rules There's another workaround: the GFCI requirement applies only to "125-volt, single-phase, 15- and 20-ampere receptacles." So install a 30-amp circuit and receptacle, and change the plug on the sump pump. Note also that the *2005* NEC contains the same language, and additionally two pertinent exceptions to the GFCI requirement that were removed in the 2008 Code: "Receptacles that are not readily accessible" and "Receptacles located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected..." So if the governing authority in the OP's jurisdiction is the 2005 (or earlier) Code and not 2008, he apparently has no worries. |
#21
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
In article , bud-- wrote:
Doug Miller wrote: There's another workaround: the GFCI requirement applies only to "125-volt, single-phase, 15- and 20-ampere receptacles." So install a 30-amp circuit and receptacle, and change the plug on the sump pump. Then it is not UL listed - it was designed and tested on a 20A ckt. So what? It's not a Code violation to plug unlisted equipment into a receptacle. I would call 7 1/2 feet high not "readily accessible". So would the Code -- the definition of "readily accessible" includes not needing portable ladders to reach it. |
#22
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
In article , "Jay-T" wrote:
John Grabowski wrote: Unfortunately that does present a problem as you found out the hard way. I suggest that you write to the NFPA about your personal experience in this case. If I figure out who the NFPA is, and what their contact/mailing information is, I may just do that. NFPA = National Fire Protection Agency. www.nfpa.org |
#23
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
On Dec 16, 2:25*pm, "Jay-T" wrote:
I have a sump pump in an unfinished basement. *It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? My new home passed without it in 1998, things may have changed. I personally would not want any critical piece of equipment like that on a GFCI. Mkes no sense, its in the hole anyway. |
#24
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
RickH wrote:
On Dec 16, 2:25 pm, "Jay-T" wrote: I have a sump pump in an unfinished basement. It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? My new home passed without it in 1998, things may have changed. I personally would not want any critical piece of equipment like that on a GFCI. Mkes no sense, its in the hole anyway. If the Sump Pump or Freezer have 3-wire grounded cords, the shouldn't need a GFCI anyway. My Sump Pump and all three refrigerator/freezers are on non-GFCI outlets. |
#25
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
Jay-T wrote:
It's not done by the appliance, but the receptacle location. The NEC requires all outlets in unfinished parts of basements to be GFCI protected. Unless it is a dedicated SINGLE outlet. Sump pumps CAN'T be on GFCI's. |
#26
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
On Dec 16, 2:25*pm, "Jay-T" wrote:
I have a sump pump in an unfinished basement. *It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? You already flooded so you know the answer. Dont use one on a frige or sump pump. |
#27
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
"Steve Barker" wrote in message ... Jay-T wrote: It's not done by the appliance, but the receptacle location. The NEC requires all outlets in unfinished parts of basements to be GFCI protected. Unless it is a dedicated SINGLE outlet. Sump pumps CAN'T be on GFCI's. The NEC no longer has any exceptions |
#28
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
I would replace the GFCI with a single (not duplex) 15A receptacle. If at some point in the future (like a home inspection) this is flagged it is not that hard to reinstall a GFCI. I am having a little trouble figuring out the "single (not duplex) 15A receptacle" option. When I do a search for single 15-amp receptacles, all I see are receptacles that have differently-shaped holes for the plug to go into -- there is a ground hole and then 2 flat slots that are in the same line, not parallel with each other. So, I would need a different style plug than the standard one that is now on the sump pump. Meanwhile, I can find a single 20-amp receptacle that has a slightly different configuration than a standard 15-amp plug, but it looks like a standard plug could go into it (I don't know if that's true). But, then I would have a receptacle that looks like it is for a 20-amp circuit, but the existing sump pump circuit is on a 15-amp circuit breaker. I would have to go to the property and check, but I suspect that since it is a dedicated 15-amp circuit that is only for, and only connected to, the sump pump, it probably is wired with 14/2 wire not 12/2 wire. *I had the same problem several months ago trying to find a 15 amp, 120 volt single receptacle. My usual supply house doesn't stock them anymore and apparently Home Depot does not or was out of stock at the time. I wound up going to another supply house that had them. They are available, but you may have to look more. The fifteen amp that you found is for 220 volts and you should not put a 20 amp single there. |
#29
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
"Jay-T" wrote in message ... John Grabowski wrote: I have a sump pump in an unfinished basement. It is on a dedicated 15-amp 120-volt circuit, the outlet/receptacle is on the ceiling, and it is a duplex GFCI receptacle. The sump pump failed because the GFCI receptacle tripped, and the basement flooded. Are sump pumps required to have a GFCI receptacle according the National Electrical Code (NEC) even if the receptacle is on the ceiling about 7 1/2 feet from the floor? Could I change the receptacle from a duplex GFCI receptacle to a single receptacle that is not GFCI, and still be in compliance with the NEC? *The latest code edition now requires that all unfinished basement receptacles as well as all garage receptacles regardless of their location be GFI protected. This apparently was changed because people will plug things in no matter where the receptacle is and what it is for. I have seen plenty of extension cords hanging from garage ceilings to agree with the requirement that garage door opener receptacles be GFI protected. Unfortunately that does present a problem as you found out the hard way. I suggest that you write to the NFPA about your personal experience in this case. If I figure out who the NFPA is, and what their contact/mailing information is, I may just do that. The pertinent article in NFPA 70 is 210.8 and you can submit your suggestion on the form below: http://www.nfpa.org/assets/files/PDF...oposalForm.doc My thought is that there should be another type of receptacle for the sump pump such as a twist lock without GFI protection. That would make the receptacle unavailable for general use and keep it for sump pump use only and thus eliminate the potential damage from nuisance tripping. If GFI protection is required for the pump, an equipment GFI can be installed along with the twist lock receptacle. An equipment GFI does not have the same low threshold for tripping as the one used for people protection and consequently is less prone to nuisance tripping. I think that is a good suggestion. It makes sense and it solves the problem that is intended to be solved by the new NEC. Maybe you could write to the NFPA too and submit your suggestion to them. In terms of safety, one problem with the latest code for sump pumps in unfinished basements is that the GFCI could cause the pump to fail and the basement to flood. Then, there would be the newly-created hazard of someone walking in the water and accidentally coming into contact with any electrical power source in the basement. |
#30
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
John Grabowski wrote:
I would replace the GFCI with a single (not duplex) 15A receptacle. If at some point in the future (like a home inspection) this is flagged it is not that hard to reinstall a GFCI. I am having a little trouble figuring out the "single (not duplex) 15A receptacle" option. When I do a search for single 15-amp receptacles, all I see are receptacles that have differently-shaped holes for the plug to go into -- there is a ground hole and then 2 flat slots that are in the same line, not parallel with each other. So, I would need a different style plug than the standard one that is now on the sump pump. Meanwhile, I can find a single 20-amp receptacle that has a slightly different configuration than a standard 15-amp plug, but it looks like a standard plug could go into it (I don't know if that's true). But, then I would have a receptacle that looks like it is for a 20-amp circuit, but the existing sump pump circuit is on a 15-amp circuit breaker. I would have to go to the property and check, but I suspect that since it is a dedicated 15-amp circuit that is only for, and only connected to, the sump pump, it probably is wired with 14/2 wire not 12/2 wire. *I had the same problem several months ago trying to find a 15 amp, 120 volt single receptacle. My usual supply house doesn't stock them anymore and apparently Home Depot does not or was out of stock at the time. I wound up going to another supply house that had them. They are available, but you may have to look more. Thanks. I'll keep looking around. The fifteen amp that you found is for 220 volts and you should not put a 20 amp single there. Oops. |
#31
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
John Grabowski wrote:
"Jay-T" wrote If I figure out who the NFPA is, and what their contact/mailing information is, I may just do that. The pertinent article in NFPA 70 is 210.8 and you can submit your suggestion on the form below: http://www.nfpa.org/assets/files/PDF...oposalForm.doc Thanks. I'll do the form and submit it. I'm not going to try to create the actual suggested wording. I'll just write something that explains what my suggestion is and why. |
#32
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
Doug Miller wrote:
In article , bud-- wrote: Doug Miller wrote: There's another workaround: the GFCI requirement applies only to "125-volt, single-phase, 15- and 20-ampere receptacles." So install a 30-amp circuit and receptacle, and change the plug on the sump pump. Then it is not UL listed - it was designed and tested on a 20A ckt. So what? It's not a Code violation to plug unlisted equipment into a receptacle. You usually have good advice. This one isn't. The pump, float switch or line cords designed for 20A may not fail safely when operated on a 30A circuit. In addition to higher current the trip time can be longer. I would particularly wonder about the line cords. A smart person uses UL listed equipment. -- bud-- |
#33
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
In article , bud-- wrote:
Doug Miller wrote: In article , bud-- wrote: Doug Miller wrote: There's another workaround: the GFCI requirement applies only to "125-volt, single-phase, 15- and 20-ampere receptacles." So install a 30-amp circuit and receptacle, and change the plug on the sump pump. Then it is not UL listed - it was designed and tested on a 20A ckt. So what? It's not a Code violation to plug unlisted equipment into a receptacle. You usually have good advice. This one isn't. The pump, float switch or line cords designed for 20A may not fail safely when operated on a 30A circuit. I've got news for you: the line cord on a sump pump isn't "designed for 20A". Go have a look at one. Tell me what gauge the conductors are. |
#34
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
|
#35
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
On Fri, 18 Dec 2009 16:58:42 -0500, gfretwell wrote:
The pertinent article in NFPA 70 is 210.8 and you can submit your suggestion on the form below: http://www.nfpa.org/assets/files/PDF...oposalForm.doc You will be writing for the 2014 code cycle. The 2011 is closed. .... and the world ends in 2012. Crap. ;-) |
#36
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
"Dan Lanciani" ddl@danlan.*com wrote in message ... In article , (RBM) writes: | | "Steve Barker" wrote in message | ... | Jay-T wrote: | | | It's not done by the appliance, but the receptacle location. The NEC | requires all outlets in unfinished parts of basements to be GFCI | protected. | | Unless it is a dedicated SINGLE outlet. Sump pumps CAN'T be on GFCI's. | | The NEC no longer has any exceptions Is GFCI protection required for 15A or 20A 220V outlets? Dan Lanciani ddl@danlan.*com No, just 125 volt. Not a bad idea. The OP can rewire the circuit for 240 volt, change the outlet, and pump, and he's off to the races |
#37
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
Doug Miller wrote:
In article , bud-- wrote: Doug Miller wrote: In article , bud-- wrote: Doug Miller wrote: There's another workaround: the GFCI requirement applies only to "125-volt, single-phase, 15- and 20-ampere receptacles." So install a 30-amp circuit and receptacle, and change the plug on the sump pump. Then it is not UL listed - it was designed and tested on a 20A ckt. So what? It's not a Code violation to plug unlisted equipment into a receptacle. You usually have good advice. This one isn't. The pump, float switch or line cords designed for 20A may not fail safely when operated on a 30A circuit. I've got news for you: the line cord on a sump pump isn't "designed for 20A". Go have a look at one. Tell me what gauge the conductors are. The line cords are designed to be safe to operate on a 20A ckt. That means, for instance, that the conductors will survive the available fault current for the time until a 20A breaker/fuse will open. That is why you can have 18ga extension cords on a 20A ckt. I wouldn't bet that is true on a 30A breaker, which may have a higher fault current or will take a lot longer to trip at the same fault current. A smart person uses UL listed equipment. -- bud-- |
#38
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
In article , bud-- wrote:
Doug Miller wrote: In article , bud-- wrote: Doug Miller wrote: In article , bud-- wrote: Doug Miller wrote: There's another workaround: the GFCI requirement applies only to "125-volt, single-phase, 15- and 20-ampere receptacles." So install a 30-amp circuit and receptacle, and change the plug on the sump pump. Then it is not UL listed - it was designed and tested on a 20A ckt. So what? It's not a Code violation to plug unlisted equipment into a receptacle. You usually have good advice. This one isn't. The pump, float switch or line cords designed for 20A may not fail safely when operated on a 30A circuit. I've got news for you: the line cord on a sump pump isn't "designed for 20A". Go have a look at one. Tell me what gauge the conductors are. The line cords are designed to be safe to operate on a 20A ckt. Go have a look at the line cord on a sump pump. Tell me what gauge the conductors are. |
#39
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
In article , bud-- wrote:
The line cords are designed to be safe to operate on a 20A ckt. That means, for instance, that the conductors will survive the available fault current for the time until a 20A breaker/fuse will open. That is why you can have 18ga extension cords on a 20A ckt. I wouldn't bet that is true on a 30A breaker, which may have a higher fault current or will take a lot longer to trip at the same fault current. You're obviously another one of those misguided souls who believes that breakers are there to protect the stuff that's plugged in to the receptacles. Repeat after me: Breakers are there to protect the branch circuit wiring. Breakers are there to protect the branch circuit wiring. Breakers are there to protect the branch circuit wiring. Breakers are there to protect the branch circuit wiring. |
#40
Posted to alt.home.repair
|
|||
|
|||
Sump pumps -- GFCI required?
Doug Miller wrote:
In article , bud-- wrote: The line cords are designed to be safe to operate on a 20A ckt. That means, for instance, that the conductors will survive the available fault current for the time until a 20A breaker/fuse will open. That is why you can have 18ga extension cords on a 20A ckt. I wouldn't bet that is true on a 30A breaker, which may have a higher fault current or will take a lot longer to trip at the same fault current. You're obviously another one of those misguided souls who believes that breakers are there to protect the stuff that's plugged in to the receptacles. Repeat after me: Breakers are there to protect the branch circuit wiring. Breakers are there to protect the branch circuit wiring. Breakers are there to protect the branch circuit wiring. Breakers are there to protect the branch circuit wiring. Hummm, is that true of GFCI and arc fault breakers too? I be scared 'O lectwisity. Dat's why I don't be messin wit nuttin over 13.8kv. TDD |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Dual sump pumps | Home Repair | |||
GFCI outlets required with a GFCI Breaker? | Home Repair | |||
Stacked sump pumps | Home Repair | |||
Battery Operated Sump Pumps | Home Repair | |||
Back up sump pumps ? | Home Ownership |