Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,261
Default One circuit went out

At least I think that's what happened.

Several outlets stopped working. I flipped the relevant switch on the
breaker box
but it didn't help.

This is the first time I've confronted such a problem. Any
explanation of why
a given circuit would just poop out? Inquiring minds...

I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)

The dead circuit includes 4 outlets.

Any estimate what such a repair might cost, based on So. Calif prices?

TIA

Hypatia
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,341
Default One circuit went out

On Fri, 7 Aug 2009 21:54:11 -0700 (PDT), Higgs Boson
wrote:

At least I think that's what happened.

Several outlets stopped working. I flipped the relevant switch on the
breaker box
but it didn't help.

This is the first time I've confronted such a problem. Any
explanation of why
a given circuit would just poop out? Inquiring minds...

I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)

The dead circuit includes 4 outlets.

Any estimate what such a repair might cost, based on So. Calif prices?

TIA

Hypatia


Make sure you don't have any GFCIs tripped. They are usually located
outside or in the bathrooms.

If you want to avoid an electrician, you can use a voltage tester and
pull out the dead outlets and inspect them.

A loose connection on the outlets can be obvious if you take them out
and look at them.

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default One circuit went out


"Higgs Boson" wrote in message
...
At least I think that's what happened.

Several outlets stopped working. I flipped the relevant switch on the
breaker box
but it didn't help.

This is the first time I've confronted such a problem. Any
explanation of why
a given circuit would just poop out? Inquiring minds...

I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)

The dead circuit includes 4 outlets.

Any estimate what such a repair might cost, based on So. Calif prices?

TIA

Hypatia


More likely part of one circuit went out. The wiring is daisy chained
between the outlets and lights, so it's most likely a bad connection at one
of the devices. If you find which other outlets on that same circuit are
still live, then try to determine the wiring path, you will probably find
the problem at the last live outlet, or the first dead outlet. This should
be fairly easy for an electrician to find, and probably only cost whatever
they get for a service charge


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default One circuit went out

Options come to mind:

* Bad circuit breaker, not delivering power.
* Dirty contact between breaker, and the bar that supplies
power.
* Bad connection at one of the outlets, so the power goes as
far as a particular outlet, but no farther
* Broken wire, along the way
* Bad connection at the neutral bar

--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


"Higgs Boson" wrote in message
...
At least I think that's what happened.

Several outlets stopped working. I flipped the relevant
switch on the
breaker box
but it didn't help.

This is the first time I've confronted such a problem. Any
explanation of why
a given circuit would just poop out? Inquiring minds...

I haven't called an electrician yet, being very low in the
$$, so have
made
adjustments using other outlets (Yes, I'm being careful and
No, I'm
not overloading.)

The dead circuit includes 4 outlets.

Any estimate what such a repair might cost, based on So.
Calif prices?

TIA

Hypatia


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11,538
Default One circuit went out

Higgs Boson wrote:
At least I think that's what happened.

Several outlets stopped working. I flipped the relevant switch on the
breaker box
but it didn't help.

This is the first time I've confronted such a problem. Any
explanation of why
a given circuit would just poop out? Inquiring minds...

I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)

The dead circuit includes 4 outlets.

Any estimate what such a repair might cost, based on So. Calif prices?

TIA

Hypatia


This is a common situation and is easy to fix if your hand fits a
screwdriver.

In addition to the other observations, this is most often caused by
"push-in" or "stab" connectors on the outlets. These are the kind where a
stripped wire is pushed into a hole on the back of the outlet and is grabbed
by spring-type internal contacts. This type of connection is most often used
by installers who want to save time, but this type of connection is also
most troublesome (compared to screw-down connections).

Anyway, the bad stab-in connection most likely exists at the last good
outlet in the chain or the first bad outlet.

The fix is simple: Remove the wires from the push-in contact holes and move
them to the screw-down connections on the side.

Getting the wires OUT of the push-in holes requires an itty-bitty
screwdriver (or similar) to stick in a slot next to the hole. This action
loosen the internal wire-grabber thingy.

The whole thing is really pretty easy (a 3 on a 1-to-10 scale). If you need
any more help, don't hesitate to ask.

P.S.
My neighbor had exactly the same thing happen four years ago. ARS charged
her $80 for a service call and no parts.

P.P.S.
If you're uncomfortable fiddling with electricity, there should be a
handyman neighbor that would be glad to fix it in return for a plate of
cookies or a six-pack.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 307
Default One circuit went out

Double check gfi's. I found one on my front stoup that killed half bath
& dining room .Found out neighbor was plugging his mower in my out side
outlet. Drunk ******* ran his cord over and couldn't figure out why his
mower stopped ,dumb ass hole. Took me a week to find the problem. And I
also found a gfi in my basement that kills my garage. SO !!GOOD HUNTING

Jerry


http://community.webtv.net/awoodbutc...oodWorkingPage



http://community.webtv.net/awoodbutcher/1974RuppCentair

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,417
Default One circuit went out

On Aug 8, 1:14*am, Metspitzer wrote:
On Fri, 7 Aug 2009 21:54:11 -0700 (PDT), Higgs Boson





wrote:
At least I think that's what happened.


Several outlets stopped working. *I flipped the relevant switch on the
breaker box
but it didn't help.


This is the first time I've confronted such a problem. *Any
explanation of why
a given circuit would just poop out? *Inquiring minds...


I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)


The dead circuit includes 4 outlets.


Any estimate what such a repair might cost, based on So. Calif prices?


TIA


Hypatia


Make sure you don't have any GFCIs tripped. *They are usually located
outside or in the bathrooms.

If you want to avoid an electrician, you can use a voltage tester and
pull out the dead outlets and inspect them.

A loose connection on the outlets can be obvious if you take them out
and look at them.- Hide quoted text -

- Show quoted text -


Yeah I had an outdoor GFCI outlet that was wired into my bedroom and
part of my living room that caused me some grief. I rewired it so the
GFCI portion only effected the one outlet.

Jimmie
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default One circuit went out

Stealing electricity, too. Did you wire the socket for 220
VAC, and then act puzzled when his mower blew up in a cloud
of smoke?

--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


"Jerry - OHIO" wrote in message
...
Double check gfi's. I found one on my front stoup that
killed half bath
& dining room .Found out neighbor was plugging his mower in
my out side
outlet. Drunk ******* ran his cord over and couldn't figure
out why his
mower stopped ,dumb ass hole. Took me a week to find the
problem. And I
also found a gfi in my basement that kills my garage. SO
!!GOOD HUNTING

Jerry


http://community.webtv.net/awoodbutc...oodWorkingPage



http://community.webtv.net/awoodbutcher/1974RuppCentair


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,261
Default One circuit went out

On Aug 8, 3:53*am, "RBM" wrote:
"HiggsBoson" wrote in message

...



At least I think that's what happened.


Several outlets stopped working. *I flipped the relevant switch on the
breaker box
but it didn't help.


This is the first time I've confronted such a problem. *Any
explanation of why
a given circuit would just poop out? *Inquiring minds...


I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)


The dead circuit includes 4 outlets.


Any estimate what such a repair might cost, based on So. Calif prices?


TIA


Hypatia


More likely part of one circuit went out. The wiring is daisy chained
between the outlets and lights, so it's most likely a bad connection at one
of the devices. If you find which other outlets on that same circuit are
still live, then try to determine the wiring path, you will probably find
the problem at the last live outlet, or the first dead outlet. This should
be fairly easy for an electrician to find, and probably only cost whatever
they get for a service charge


NO outlets on that circuit are live. I tested them all.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,261
Default One circuit went out

On Aug 8, 5:06*am, "HeyBub" wrote:
HiggsBosonwrote:
At least I think that's what happened.


Several outlets stopped working. *I flipped the relevant switch on the
breaker box
but it didn't help.


This is the first time I've confronted such a problem. *Any
explanation of why
a given circuit would just poop out? *Inquiring minds...


I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)


The dead circuit includes 4 outlets.


Any estimate what such a repair might cost, based on So. Calif prices?


TIA


Hypatia


This is a common situation and is easy to fix if your hand fits a
screwdriver.

In addition to the other observations, this is most often caused by
"push-in" or "stab" connectors on the outlets. These are the kind where a
stripped wire is pushed into a hole on the back of the outlet and is grabbed
by spring-type internal contacts. This type of connection is most often used
by installers who want to save time, but this type of connection is also
most troublesome (compared to screw-down connections).

Anyway, the bad stab-in connection most likely exists at the last good
outlet in the chain or the first bad outlet.

The fix is simple: Remove the wires from the push-in contact holes and move
them to the screw-down connections on the side.

Getting the wires OUT of the push-in holes requires an itty-bitty
screwdriver (or similar) to stick in a slot next to the hole. This action
loosen the internal wire-grabber thingy.

The whole thing is really pretty easy (a 3 on a 1-to-10 scale). If you need
any more help, don't hesitate to ask.

P.S.
My neighbor had exactly the same thing happen four years ago. ARS charged
her $80 for a service call and no parts.

P.P.S.
If you're uncomfortable fiddling with electricity, there should be a
handyman neighbor that would be glad to fix it in return for a plate of
cookies or a six-pack.


Uncomfortable? Yeah...I am still embarrassed over an outlet
I thought I fixed properly (followed directions exactly on paper
enclosed),
but it gave trouble every time somebody pushed their bed against plug
in that outlet. Finally had to call electrician to fix it. He said I
made an unsafe
installation. Couldn't argue with him, though I repeated that I
followed directions exactly. So no, not eager to tackle what sounds
like a more complex problem, involving 4 outlets on same circuit.

I kinda doubt if the problem is a "push-in" outlet.
This circuit has been quietly operating for literally
decades, giving no trouble at all.



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,261
Default One circuit went out

On Aug 8, 5:05*am, "Stormin Mormon"
wrote:
Options come to mind:

* Bad circuit breaker, not delivering power.
* Dirty contact between breaker, and the bar that supplies
power.
* Bad connection at one of the outlets, so the power goes as
far as a particular outlet, but no farther
* Broken wire, along the way
* Bad connection at the neutral bar

OK, that's a hefty laundry list.

Just to push this a little; which is the most
likely candidate to go bad out of the blue
after decades of problem-free operation in
a mild environment?

TIA


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,261
Default One circuit went out

On Aug 8, 12:44*pm, JIMMIE wrote:
On Aug 8, 1:14*am, Metspitzer wrote:



On Fri, 7 Aug 2009 21:54:11 -0700 (PDT),HiggsBoson


wrote:
At least I think that's what happened.


Several outlets stopped working. *I flipped the relevant switch on the
breaker box
but it didn't help.


This is the first time I've confronted such a problem. *Any
explanation of why
a given circuit would just poop out? *Inquiring minds...


I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)


The dead circuit includes 4 outlets.


Any estimate what such a repair might cost, based on So. Calif prices?


TIA


Hypatia


Make sure you don't have any GFCIs tripped. *They are usually located
outside or in the bathrooms.


If you want to avoid an electrician, you can use a voltage tester and
pull out the dead outlets and inspect them.


A loose connection on the outlets can be obvious if you take them out
and look at them.- Hide quoted text -


- Show quoted text -


Yeah I had an outdoor GFCI outlet that was wired into my bedroom and
part of my living room that caused me some grief. *I rewired it so the
GFCI portion only effected the one outlet.

Jimmie


How do I know if I have a GFCI outlet on that circuit?
(You're talkin' to a greenie...g)

  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,444
Default One circuit went out

Higgs Boson wrote:
On Aug 8, 5:05 am, "Stormin Mormon"
wrote:
Options come to mind:

* Bad circuit breaker, not delivering power.
* Dirty contact between breaker, and the bar that supplies
power.
* Bad connection at one of the outlets, so the power goes as
far as a particular outlet, but no farther
* Broken wire, along the way
* Bad connection at the neutral bar

OK, that's a hefty laundry list.

Just to push this a little; which is the most
likely candidate to go bad out of the blue
after decades of problem-free operation in
a mild environment?


That would be:
"* Bad connection at one of the outlets, so the power goes as
far as a particular outlet, but no farther"

This is a classical symptom of a failed 'push on' connection
at the back of a 'daisy chained' outlet.
Obviously, please be extremely careful and work safely.

Set your multimeter to 'AC Volts'. If it does not autorange,
set it's range at 300V or more.

Open your breaker panel and confirm that each breaker is
supplying nominal voltage to it's connected wire.

Rig an extension cord from a 'known good' outlet over to
the location of your broken outlets.

Confirm that you see about 120V when measuring between 'hot'
and 'neutral' on the extension cord.

Measure between neutral on the extension cord and the hot side
of the broken outlets. You will see one of two things.

Low voltage. Like 3V - 40V or so. Open 'hot' side, probably.
Confirm this by measuring from the 'neutral' side of the
broken outlet to the 'hot' side of the extension cord.
If you now get nominal voltage, you probably have an open
'hot' on the broken outlets.

Nominal voltage. Like 120 V or so. Open 'neutral' side, probably.
Confirm this by measuring from the 'neutral' side of the broken
outlet and the 'hot' side of the extension cord. If you see
low voltage, you probably have an open 'neutral' in the
broken outlet string.

In either case, you get to find the first outlet in the chain
that connects to the circuit breaker.


Turn off the main breaker before opening the outlet boxes for
inspection. Any outlets that use the 'push on' connections
in the back should be replaced so that the wires wrap around
and are secured by the screws in the side of the outlet.
Wrap the wires so that they grip the screw threads as you
tighten the screw.

Plug in a known-good table lamp into the broken outlet and
turn on the main breaker. If the lamp goes on, you can
turn off the breaker and button things up. If the lamp does
not turn on, you can turn off the breaker and call an electrician.

Tell her the symptom and everything you've done. She will probably
turn off the main breaker and do resistance tests from outlet
to outlet and from outlet to breaker.

It'll be right either way, eventually!



--Winston
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default One circuit went out


"Higgs Boson" wrote in message
...
On Aug 8, 3:53 am, "RBM" wrote:
"HiggsBoson" wrote in message

...



At least I think that's what happened.


Several outlets stopped working. I flipped the relevant switch on the
breaker box
but it didn't help.


This is the first time I've confronted such a problem. Any
explanation of why
a given circuit would just poop out? Inquiring minds...


I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)


The dead circuit includes 4 outlets.


Any estimate what such a repair might cost, based on So. Calif prices?


TIA


Hypatia


More likely part of one circuit went out. The wiring is daisy chained
between the outlets and lights, so it's most likely a bad connection at
one
of the devices. If you find which other outlets on that same circuit are
still live, then try to determine the wiring path, you will probably find
the problem at the last live outlet, or the first dead outlet. This should
be fairly easy for an electrician to find, and probably only cost whatever
they get for a service charge


NO outlets on that circuit are live. I tested them all.

It is very unlikely that an entire circuit is feeding just four outlets.
There are undoubtedly other outlets on the same circuit that you are unaware
of.



  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11,538
Default One circuit went out

Higgs Boson wrote:

Yeah I had an outdoor GFCI outlet that was wired into my bedroom and
part of my living room that caused me some grief. I rewired it so the
GFCI portion only effected the one outlet.

Jimmie


How do I know if I have a GFCI outlet on that circuit?
(You're talkin' to a greenie...g)


Look for an outlet with a push button and (often) red/green lights. Like
this:

http://www.howstuffworks.com/question117.htm




  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11,538
Default One circuit went out

Higgs Boson wrote:

Anyway, the bad stab-in connection most likely exists at the last
good outlet in the chain or the first bad outlet.

The fix is simple: Remove the wires from the push-in contact holes
and move them to the screw-down connections on the side.

Getting the wires OUT of the push-in holes requires an itty-bitty
screwdriver (or similar) to stick in a slot next to the hole. This
action loosen the internal wire-grabber thingy.

The whole thing is really pretty easy (a 3 on a 1-to-10 scale). If
you need any more help, don't hesitate to ask.

P.S.
My neighbor had exactly the same thing happen four years ago. ARS
charged her $80 for a service call and no parts.

P.P.S.
If you're uncomfortable fiddling with electricity, there should be a
handyman neighbor that would be glad to fix it in return for a plate
of cookies or a six-pack.



I kinda doubt if the problem is a "push-in" outlet.
This circuit has been quietly operating for literally
decades, giving no trouble at all.


That's common with push-in connections.

Stab connections are not like wine, more like a tuna salad at the Fourth of
July softball picnic.


  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default One circuit went out

I don't think you ever said where the non-working outlets are located. For
example, are some or all of them located in or near a kitchen, bathroom, or
laundry room?

Did you look to see if any of them look like the picture that HeyBub
provided through the link at: http://www.howstuffworks.com/question117.htm ?

Did you check ALL of the other outlets and lights (other than the 4
non-working ones) with the circuit breaker off to see if anything else goes
off when the circuit breaker is off?

Since you are a "greenie" (in your words), and seem to be very unsure about
doing any electrical work on your own, it may not be a good idea for you to
open up the electrical panel box. But, if you know someone who is
comfortable doing that, maybe he/she could open the box, take out the
"Problem" breaker, and then replace it with one of the onther breakers in
the box. If that fixes the problem, you may just have a bad circuit
breaker.

Higgs Boson wrote:
At least I think that's what happened.

Several outlets stopped working. I flipped the relevant switch on the
breaker box
but it didn't help.

This is the first time I've confronted such a problem. Any
explanation of why
a given circuit would just poop out? Inquiring minds...

I haven't called an electrician yet, being very low in the $$, so have
made
adjustments using other outlets (Yes, I'm being careful and No, I'm
not overloading.)

The dead circuit includes 4 outlets.

Any estimate what such a repair might cost, based on So. Calif prices?

TIA

Hypatia



  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,444
Default One circuit went out

HeyBub wrote:

(...)

Stab connections are not like wine, more like a tuna salad at the Fourth of
July softball picnic.


Nicely put!

--Winston
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How do you know a new circuit breaker is protecting the circuit properly? BobH Home Repair 19 December 4th 06 05:16 PM
12-3 Double Circuit Run Length - Should I Split the Circuit? [email protected] Home Repair 18 May 19th 06 01:59 AM
Short in Circuit or Circuit breaker? Greg Home Repair 13 January 29th 06 06:45 PM
circuit is off, circuit breaker is on Massi Home Repair 1 July 4th 04 11:31 PM
Convert radial (cooker) circuit to socket circuit Chi UK diy 3 December 23rd 03 05:48 PM


All times are GMT +1. The time now is 12:32 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"