On Jun 23, 8:19*pm, The Daring Dufas
wrote:
jamesgangnc wrote:
I've done a fair bit of my own hvac work. *I replaced a couple of gas
furnaces and one split ac. *I'm building a new garage with living
space above it out at my lake house. *I picked up a "slightly" used
goodman 1 1/2 ton heat pump compressor off craig's list. *It was
installed as part of an attic conversion that was never completed.
While the seller was moving out of the house the low side line was
damaged and it lost charge. *Fast according to the seller.


The guy didn't know enough to shut the valves. *Instead he hacksawed
off the lines. *Folded the small one over and stuffed a piece of foam
in the big one. *I cut them off with a pipe cutter, closed the valves,
and blew them out with compressed air. *I was worried that I probably
did not get all the copper filings from the hacksaw so I opened the
valves and blew the lines out again via the third tap. (The one that
is used to check pressure during heat mode.) *I didn't get a lot of
air to move through it though that way so I doubt I blew out any more
filings.


So I'm worried that there still may be some copper filings in the
lines. *What else can I do?


I'm also a little worried that it may have lost some oil when the low
side was broken. *There doesn't seem to be any easy way to drain and
refill the oil though.


I won't be installing it from a few months. *I'd like to go ahead and
vaccum it down. *Can I do that via the third tap? *I'll fill it with
some r22 after I vacuum it.


Blowing compressed air into the unit was a little bit
of a bad move. People in the HVAC and refrigeration
trades use dry nitrogen for internal clean out along
with a suitable solvent for coils detached from the
compressor. Compressed air can carry moisture into a
system when blown through it. R11 isn't used as freely
as it once was because it kills the poor defenseless
little ozones. I use a product called CF-20 Internal
Coil Cleaner available at many HVAC supply houses and
it's available without any special permit:

http://tinyurl.com/lk2uq3

You would have been better off leaving the valves closed
and flushing out the pipe stubs with freeze spray which
is basically a freon mix of some sort or even dust blaster
which will blow the stuff out and leave no residue. The
low side line being pierced would not cause an appreciable
oil loss from an un-powered unit. Because of the compressed
air introduced to the system you will need to pull a deep
vacuum on the system. The warmer it is when you do it, the
better it will pull out the moisture. Of course a good sized
liquid line dryer like a C-163 Sporlan which is a 3/8 flare
dryer which makes for easy replacement. I always add a sight
glass with a moisture indicator to all the systems I install.
You can get one that will screw right on to the C-163 and
and attach to the tubing with a flare fitting. Heck, HVAC
work isn't rocket surgery, Storman Norman does it. *snicker*

TDD- Hide quoted text -

- Show quoted text -


The valves weren't closed when I got it so I figured the compressed
air was not going to make much difference at this point. I don't have
a nitrogen tank. My supplies are a vacuum pump, set of gauges, a can
of r22. My brazing skills are sketchy so I try to minimize that. I'd
like to have a nitrogen tank but so far I've gotten away without.

I'll go ahead and pump it down and fill it with r22. I'm guessing
it's ok to do that using that middle tap?

It has a filter/dryer on the high side. I can add one to the low
side. The guy moved it from one house to the another and kept it in a
shed. So it got moved around a bit. I'm afraid that there may be
some copper filings further down the low side line inside the unit
that I can't really get to. What happens when they go into the
compressor? Will they just end up sitting in the bottom in the oil?
Or the switching valve? Are these things engineered anticipating that
occasional small solid might get in? This is my biggest worry. The
moisture I can get out with my vacuum pump.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default Heat Pump ?s

Since the system was opened for a period of time (longer
than a few minutes), it's a good idea to install a BIG
liquid line filter dryer.

--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


"jamesgangnc" wrote in message
...

The valves weren't closed when I got it so I figured the
compressed
air was not going to make much difference at this point. I
don't have
a nitrogen tank. My supplies are a vacuum pump, set of
gauges, a can
of r22. My brazing skills are sketchy so I try to minimize
that. I'd
like to have a nitrogen tank but so far I've gotten away
without.

I'll go ahead and pump it down and fill it with r22. I'm
guessing
it's ok to do that using that middle tap?

It has a filter/dryer on the high side. I can add one to
the low
side. The guy moved it from one house to the another and
kept it in a
shed. So it got moved around a bit. I'm afraid that there
may be
some copper filings further down the low side line inside
the unit
that I can't really get to. What happens when they go into
the
compressor? Will they just end up sitting in the bottom in
the oil?
Or the switching valve? Are these things engineered
anticipating that
occasional small solid might get in? This is my biggest
worry. The
moisture I can get out with my vacuum pump.


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,761
Default Heat Pump ?s

jamesgangnc wrote:
On Jun 23, 8:19 pm, The Daring Dufas
wrote:
jamesgangnc wrote:
I've done a fair bit of my own hvac work. I replaced a couple of gas
furnaces and one split ac. I'm building a new garage with living
space above it out at my lake house. I picked up a "slightly" used
goodman 1 1/2 ton heat pump compressor off craig's list. It was
installed as part of an attic conversion that was never completed.
While the seller was moving out of the house the low side line was
damaged and it lost charge. Fast according to the seller.
The guy didn't know enough to shut the valves. Instead he hacksawed
off the lines. Folded the small one over and stuffed a piece of foam
in the big one. I cut them off with a pipe cutter, closed the valves,
and blew them out with compressed air. I was worried that I probably
did not get all the copper filings from the hacksaw so I opened the
valves and blew the lines out again via the third tap. (The one that
is used to check pressure during heat mode.) I didn't get a lot of
air to move through it though that way so I doubt I blew out any more
filings.
So I'm worried that there still may be some copper filings in the
lines. What else can I do?
I'm also a little worried that it may have lost some oil when the low
side was broken. There doesn't seem to be any easy way to drain and
refill the oil though.
I won't be installing it from a few months. I'd like to go ahead and
vaccum it down. Can I do that via the third tap? I'll fill it with
some r22 after I vacuum it.

Blowing compressed air into the unit was a little bit
of a bad move. People in the HVAC and refrigeration
trades use dry nitrogen for internal clean out along
with a suitable solvent for coils detached from the
compressor. Compressed air can carry moisture into a
system when blown through it. R11 isn't used as freely
as it once was because it kills the poor defenseless
little ozones. I use a product called CF-20 Internal
Coil Cleaner available at many HVAC supply houses and
it's available without any special permit:

http://tinyurl.com/lk2uq3

You would have been better off leaving the valves closed
and flushing out the pipe stubs with freeze spray which
is basically a freon mix of some sort or even dust blaster
which will blow the stuff out and leave no residue. The
low side line being pierced would not cause an appreciable
oil loss from an un-powered unit. Because of the compressed
air introduced to the system you will need to pull a deep
vacuum on the system. The warmer it is when you do it, the
better it will pull out the moisture. Of course a good sized
liquid line dryer like a C-163 Sporlan which is a 3/8 flare
dryer which makes for easy replacement. I always add a sight
glass with a moisture indicator to all the systems I install.
You can get one that will screw right on to the C-163 and
and attach to the tubing with a flare fitting. Heck, HVAC
work isn't rocket surgery, Storman Norman does it. *snicker*

TDD- Hide quoted text -

- Show quoted text -


The valves weren't closed when I got it so I figured the compressed
air was not going to make much difference at this point. I don't have
a nitrogen tank. My supplies are a vacuum pump, set of gauges, a can
of r22. My brazing skills are sketchy so I try to minimize that. I'd
like to have a nitrogen tank but so far I've gotten away without.

I'll go ahead and pump it down and fill it with r22. I'm guessing
it's ok to do that using that middle tap?

It has a filter/dryer on the high side. I can add one to the low
side. The guy moved it from one house to the another and kept it in a
shed. So it got moved around a bit. I'm afraid that there may be
some copper filings further down the low side line inside the unit
that I can't really get to. What happens when they go into the
compressor? Will they just end up sitting in the bottom in the oil?
Or the switching valve? Are these things engineered anticipating that
occasional small solid might get in? This is my biggest worry. The
moisture I can get out with my vacuum pump.


Around here it's dirt daubers/mud daubers and other flying
or crawling critters you have to worry about when a pipe is
left open. The little bit of copper filings isn't a big concern.
The vacuum needs to be drawn from both high and low service
fittings through the gauge set. If you're worried about moisture,
why on earth are you not replacing the liquid line dryer?
The dryer is the first thing to replace, just don't leave it
open to the air for any longer than it takes to install it.
Since it's a heat pump, it requires biflow or bidirectional
dryers because the refrigerant flow is reversed when changing
from heat to cool. If you're worried about trash getting into
the reversing valve, the best thing to do would be to remove
the section of large diameter tubing and clean it out. Make
sure you wrap a wet rag around the reversing valve when using
your torch near it. You can always cut the tubing a distance
away from the reversing valve and braze it back together with
a coupling. A lot of service techs are using a low temperature
silver solder on HVAC equipment which doesn't require the use
of oxygen-acetylene torches.

TDD

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,567
Default Heat Pump ?s

On Jun 24, 2:48*pm, The Daring Dufas
wrote:
jamesgangnc wrote:
On Jun 23, 8:19 pm, The Daring Dufas
wrote:
jamesgangnc wrote:
I've done a fair bit of my own hvac work. *I replaced a couple of gas
furnaces and one split ac. *I'm building a new garage with living
space above it out at my lake house. *I picked up a "slightly" used
goodman 1 1/2 ton heat pump compressor off craig's list. *It was
installed as part of an attic conversion that was never completed.
While the seller was moving out of the house the low side line was
damaged and it lost charge. *Fast according to the seller.
The guy didn't know enough to shut the valves. *Instead he hacksawed
off the lines. *Folded the small one over and stuffed a piece of foam
in the big one. *I cut them off with a pipe cutter, closed the valves,
and blew them out with compressed air. *I was worried that I probably
did not get all the copper filings from the hacksaw so I opened the
valves and blew the lines out again via the third tap. (The one that
is used to check pressure during heat mode.) *I didn't get a lot of
air to move through it though that way so I doubt I blew out any more
filings.
So I'm worried that there still may be some copper filings in the
lines. *What else can I do?
I'm also a little worried that it may have lost some oil when the low
side was broken. *There doesn't seem to be any easy way to drain and
refill the oil though.
I won't be installing it from a few months. *I'd like to go ahead and
vaccum it down. *Can I do that via the third tap? *I'll fill it with
some r22 after I vacuum it.
Blowing compressed air into the unit was a little bit
of a bad move. People in the HVAC and refrigeration
trades use dry nitrogen for internal clean out along
with a suitable solvent for coils detached from the
compressor. Compressed air can carry moisture into a
system when blown through it. R11 isn't used as freely
as it once was because it kills the poor defenseless
little ozones. I use a product called CF-20 Internal
Coil Cleaner available at many HVAC supply houses and
it's available without any special permit:


http://tinyurl.com/lk2uq3


You would have been better off leaving the valves closed
and flushing out the pipe stubs with freeze spray which
is basically a freon mix of some sort or even dust blaster
which will blow the stuff out and leave no residue. The
low side line being pierced would not cause an appreciable
oil loss from an un-powered unit. Because of the compressed
air introduced to the system you will need to pull a deep
vacuum on the system. The warmer it is when you do it, the
better it will pull out the moisture. Of course a good sized
liquid line dryer like a C-163 Sporlan which is a 3/8 flare
dryer which makes for easy replacement. I always add a sight
glass with a moisture indicator to all the systems I install.
You can get one that will screw right on to the C-163 and
and attach to the tubing with a flare fitting. Heck, HVAC
work isn't rocket surgery, Storman Norman does it. *snicker*


TDD- Hide quoted text -


- Show quoted text -


The valves weren't closed when I got it so I figured the compressed
air was not going to make much difference at this point. *I don't have
a nitrogen tank. *My supplies are a vacuum pump, set of gauges, a can
of r22. *My brazing skills are sketchy so I try to minimize that. *I'd
like to have a nitrogen tank but so far I've gotten away without.


I'll go ahead and pump it down and fill it with r22. *I'm guessing
it's ok to do that using that middle tap?


It has a filter/dryer on the high side. *I can add one to the low
side. *The guy moved it from one house to the another and kept it in a
shed. *So it got moved around a bit. * I'm afraid that there may be
some copper filings further down the low side line inside the unit
that I can't really get to. *What happens when they go into the
compressor? *Will they just end up sitting in the bottom in the oil?
Or the switching valve? *Are these things engineered anticipating that
occasional small solid might get in? *This is my biggest worry. *The
moisture I can get out with my vacuum pump.


Around here it's dirt daubers/mud daubers and other flying
or crawling critters you have to worry about when a pipe is
left open. The little bit of copper filings isn't a big concern.
The vacuum needs to be drawn from both high and low service
fittings through the gauge set. If you're worried about moisture,
why on earth are you not replacing the liquid line dryer?
The dryer is the first thing to replace, just don't leave it
open to the air for any longer than it takes to install it.
Since it's a heat pump, it requires biflow or bidirectional
dryers because the refrigerant flow is reversed when changing
from heat to cool. If you're worried about trash getting into
the reversing valve, the best thing to do would be to remove
the section of large diameter tubing and clean it out. Make
sure you wrap a wet rag around the reversing valve when using
your torch near it. You can always cut the tubing a distance
away from the reversing valve and braze it back together with
a coupling. A lot of service techs are using a low temperature
silver solder on HVAC equipment which doesn't require the use
of oxygen-acetylene torches.

TDD- Hide quoted text -

- Show quoted text -


Sorry if I seem stupid here, but I can't pull a vacuum through the
service valves without capping the lines can I?

Yes, I used silver solder on my regular hvac install at my primary
residence.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,567
Default Heat Pump ?s

On Jun 24, 3:27*pm, jamesgangnc wrote:
On Jun 24, 2:48*pm, The Daring Dufas
wrote:





jamesgangnc wrote:
On Jun 23, 8:19 pm, The Daring Dufas
wrote:
jamesgangnc wrote:
I've done a fair bit of my own hvac work. *I replaced a couple of gas
furnaces and one split ac. *I'm building a new garage with living
space above it out at my lake house. *I picked up a "slightly" used
goodman 1 1/2 ton heat pump compressor off craig's list. *It was
installed as part of an attic conversion that was never completed.
While the seller was moving out of the house the low side line was
damaged and it lost charge. *Fast according to the seller.
The guy didn't know enough to shut the valves. *Instead he hacksawed
off the lines. *Folded the small one over and stuffed a piece of foam
in the big one. *I cut them off with a pipe cutter, closed the valves,
and blew them out with compressed air. *I was worried that I probably
did not get all the copper filings from the hacksaw so I opened the
valves and blew the lines out again via the third tap. (The one that
is used to check pressure during heat mode.) *I didn't get a lot of
air to move through it though that way so I doubt I blew out any more
filings.
So I'm worried that there still may be some copper filings in the
lines. *What else can I do?
I'm also a little worried that it may have lost some oil when the low
side was broken. *There doesn't seem to be any easy way to drain and
refill the oil though.
I won't be installing it from a few months. *I'd like to go ahead and
vaccum it down. *Can I do that via the third tap? *I'll fill it with
some r22 after I vacuum it.
Blowing compressed air into the unit was a little bit
of a bad move. People in the HVAC and refrigeration
trades use dry nitrogen for internal clean out along
with a suitable solvent for coils detached from the
compressor. Compressed air can carry moisture into a
system when blown through it. R11 isn't used as freely
as it once was because it kills the poor defenseless
little ozones. I use a product called CF-20 Internal
Coil Cleaner available at many HVAC supply houses and
it's available without any special permit:


http://tinyurl.com/lk2uq3


You would have been better off leaving the valves closed
and flushing out the pipe stubs with freeze spray which
is basically a freon mix of some sort or even dust blaster
which will blow the stuff out and leave no residue. The
low side line being pierced would not cause an appreciable
oil loss from an un-powered unit. Because of the compressed
air introduced to the system you will need to pull a deep
vacuum on the system. The warmer it is when you do it, the
better it will pull out the moisture. Of course a good sized
liquid line dryer like a C-163 Sporlan which is a 3/8 flare
dryer which makes for easy replacement. I always add a sight
glass with a moisture indicator to all the systems I install.
You can get one that will screw right on to the C-163 and
and attach to the tubing with a flare fitting. Heck, HVAC
work isn't rocket surgery, Storman Norman does it. *snicker*


TDD- Hide quoted text -


- Show quoted text -


The valves weren't closed when I got it so I figured the compressed
air was not going to make much difference at this point. *I don't have
a nitrogen tank. *My supplies are a vacuum pump, set of gauges, a can
of r22. *My brazing skills are sketchy so I try to minimize that. *I'd
like to have a nitrogen tank but so far I've gotten away without.


I'll go ahead and pump it down and fill it with r22. *I'm guessing
it's ok to do that using that middle tap?


It has a filter/dryer on the high side. *I can add one to the low
side. *The guy moved it from one house to the another and kept it in a
shed. *So it got moved around a bit. * I'm afraid that there may be
some copper filings further down the low side line inside the unit
that I can't really get to. *What happens when they go into the
compressor? *Will they just end up sitting in the bottom in the oil?
Or the switching valve? *Are these things engineered anticipating that
occasional small solid might get in? *This is my biggest worry. *The
moisture I can get out with my vacuum pump.


Around here it's dirt daubers/mud daubers and other flying
or crawling critters you have to worry about when a pipe is
left open. The little bit of copper filings isn't a big concern.
The vacuum needs to be drawn from both high and low service
fittings through the gauge set. If you're worried about moisture,
why on earth are you not replacing the liquid line dryer?
The dryer is the first thing to replace, just don't leave it
open to the air for any longer than it takes to install it.
Since it's a heat pump, it requires biflow or bidirectional
dryers because the refrigerant flow is reversed when changing
from heat to cool. If you're worried about trash getting into
the reversing valve, the best thing to do would be to remove
the section of large diameter tubing and clean it out. Make
sure you wrap a wet rag around the reversing valve when using
your torch near it. You can always cut the tubing a distance
away from the reversing valve and braze it back together with
a coupling. A lot of service techs are using a low temperature
silver solder on HVAC equipment which doesn't require the use
of oxygen-acetylene torches.


TDD- Hide quoted text -


- Show quoted text -


Sorry if I seem stupid here, but I can't pull a vacuum through the
service valves without capping the lines can I?

Yes, I used silver solder on my regular hvac install at my primary
residence.- Hide quoted text -

- Show quoted text -


Guess I should add it's not been so open that bugs could get in. It's
just that the service valves were never closed. The high side line
was folded over. A piece of the low side foam was stuck in the low
side pipe.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,761
Default Heat Pump ?s

jamesgangnc wrote:
On Jun 24, 3:27 pm, jamesgangnc wrote:
On Jun 24, 2:48 pm, The Daring Dufas
wrote:





jamesgangnc wrote:
On Jun 23, 8:19 pm, The Daring Dufas
wrote:
jamesgangnc wrote:
I've done a fair bit of my own hvac work. I replaced a couple of gas
furnaces and one split ac. I'm building a new garage with living
space above it out at my lake house. I picked up a "slightly" used
goodman 1 1/2 ton heat pump compressor off craig's list. It was
installed as part of an attic conversion that was never completed.
While the seller was moving out of the house the low side line was
damaged and it lost charge. Fast according to the seller.
The guy didn't know enough to shut the valves. Instead he hacksawed
off the lines. Folded the small one over and stuffed a piece of foam
in the big one. I cut them off with a pipe cutter, closed the valves,
and blew them out with compressed air. I was worried that I probably
did not get all the copper filings from the hacksaw so I opened the
valves and blew the lines out again via the third tap. (The one that
is used to check pressure during heat mode.) I didn't get a lot of
air to move through it though that way so I doubt I blew out any more
filings.
So I'm worried that there still may be some copper filings in the
lines. What else can I do?
I'm also a little worried that it may have lost some oil when the low
side was broken. There doesn't seem to be any easy way to drain and
refill the oil though.
I won't be installing it from a few months. I'd like to go ahead and
vaccum it down. Can I do that via the third tap? I'll fill it with
some r22 after I vacuum it.
Blowing compressed air into the unit was a little bit
of a bad move. People in the HVAC and refrigeration
trades use dry nitrogen for internal clean out along
with a suitable solvent for coils detached from the
compressor. Compressed air can carry moisture into a
system when blown through it. R11 isn't used as freely
as it once was because it kills the poor defenseless
little ozones. I use a product called CF-20 Internal
Coil Cleaner available at many HVAC supply houses and
it's available without any special permit:
http://tinyurl.com/lk2uq3
You would have been better off leaving the valves closed
and flushing out the pipe stubs with freeze spray which
is basically a freon mix of some sort or even dust blaster
which will blow the stuff out and leave no residue. The
low side line being pierced would not cause an appreciable
oil loss from an un-powered unit. Because of the compressed
air introduced to the system you will need to pull a deep
vacuum on the system. The warmer it is when you do it, the
better it will pull out the moisture. Of course a good sized
liquid line dryer like a C-163 Sporlan which is a 3/8 flare
dryer which makes for easy replacement. I always add a sight
glass with a moisture indicator to all the systems I install.
You can get one that will screw right on to the C-163 and
and attach to the tubing with a flare fitting. Heck, HVAC
work isn't rocket surgery, Storman Norman does it. *snicker*
TDD- Hide quoted text -
- Show quoted text -
The valves weren't closed when I got it so I figured the compressed
air was not going to make much difference at this point. I don't have
a nitrogen tank. My supplies are a vacuum pump, set of gauges, a can
of r22. My brazing skills are sketchy so I try to minimize that. I'd
like to have a nitrogen tank but so far I've gotten away without.
I'll go ahead and pump it down and fill it with r22. I'm guessing
it's ok to do that using that middle tap?
It has a filter/dryer on the high side. I can add one to the low
side. The guy moved it from one house to the another and kept it in a
shed. So it got moved around a bit. I'm afraid that there may be
some copper filings further down the low side line inside the unit
that I can't really get to. What happens when they go into the
compressor? Will they just end up sitting in the bottom in the oil?
Or the switching valve? Are these things engineered anticipating that
occasional small solid might get in? This is my biggest worry. The
moisture I can get out with my vacuum pump.
Around here it's dirt daubers/mud daubers and other flying
or crawling critters you have to worry about when a pipe is
left open. The little bit of copper filings isn't a big concern.
The vacuum needs to be drawn from both high and low service
fittings through the gauge set. If you're worried about moisture,
why on earth are you not replacing the liquid line dryer?
The dryer is the first thing to replace, just don't leave it
open to the air for any longer than it takes to install it.
Since it's a heat pump, it requires biflow or bidirectional
dryers because the refrigerant flow is reversed when changing
from heat to cool. If you're worried about trash getting into
the reversing valve, the best thing to do would be to remove
the section of large diameter tubing and clean it out. Make
sure you wrap a wet rag around the reversing valve when using
your torch near it. You can always cut the tubing a distance
away from the reversing valve and braze it back together with
a coupling. A lot of service techs are using a low temperature
silver solder on HVAC equipment which doesn't require the use
of oxygen-acetylene torches.
TDD- Hide quoted text -
- Show quoted text -

Sorry if I seem stupid here, but I can't pull a vacuum through the
service valves without capping the lines can I?

Yes, I used silver solder on my regular hvac install at my primary
residence.- Hide quoted text -

- Show quoted text -


Guess I should add it's not been so open that bugs could get in. It's
just that the service valves were never closed. The high side line
was folded over. A piece of the low side foam was stuck in the low
side pipe.


I assumed you were referring to pulling a vacuum after installation,
not for storage purposes. If the pipes were plugged up in any fashion,
there shouldn't be much moisture infiltration since there would still
be mostly freon in the system. The dryer should still be replaced when
it is finally installed. Since you have no nitrogen, R22 would be fine
for putting a slight pressure on the unit for storage but when
installed, it will still need a deep vacuum drawn on it. When me and
my friends install a new system in the field, we pressurize it with
nitrogen and leave it that way before ever pulling a vacuum and opening
the valves for startup. If we don't leave the condenser because of
the theft problem with new construction, we cap the line set and
pressurize it with nitrogen until it's time for occupation. That way
we have no surprise leaks such as those caused by other tradesmen
putting a nail or screw through a pipe. The thing about dry nitrogen
is that the static pressure is not going to change perceptively with
a change in temperature. If you pressurize for a leak test and come
back a week later when the weather has changed, the test pressure
will be the same if there are no leaks.

TDD
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default Heat Pump ?s

Yes, you'd have to cap the lines.

--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


"jamesgangnc" wrote in message
...

Sorry if I seem stupid here, but I can't pull a vacuum
through the
service valves without capping the lines can I?

Yes, I used silver solder on my regular hvac install at my
primary
residence.


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,567
Default Heat Pump ?s

On Jun 24, 6:23*pm, The Daring Dufas
wrote:
jamesgangnc wrote:
On Jun 24, 3:27 pm, jamesgangnc wrote:
On Jun 24, 2:48 pm, The Daring Dufas
wrote:


jamesgangnc wrote:
On Jun 23, 8:19 pm, The Daring Dufas
wrote:
jamesgangnc wrote:
I've done a fair bit of my own hvac work. *I replaced a couple of gas
furnaces and one split ac. *I'm building a new garage with living
space above it out at my lake house. *I picked up a "slightly" used
goodman 1 1/2 ton heat pump compressor off craig's list. *It was
installed as part of an attic conversion that was never completed.
While the seller was moving out of the house the low side line was
damaged and it lost charge. *Fast according to the seller.
The guy didn't know enough to shut the valves. *Instead he hacksawed
off the lines. *Folded the small one over and stuffed a piece of foam
in the big one. *I cut them off with a pipe cutter, closed the valves,
and blew them out with compressed air. *I was worried that I probably
did not get all the copper filings from the hacksaw so I opened the
valves and blew the lines out again via the third tap. (The one that
is used to check pressure during heat mode.) *I didn't get a lot of
air to move through it though that way so I doubt I blew out any more
filings.
So I'm worried that there still may be some copper filings in the
lines. *What else can I do?
I'm also a little worried that it may have lost some oil when the low
side was broken. *There doesn't seem to be any easy way to drain and
refill the oil though.
I won't be installing it from a few months. *I'd like to go ahead and
vaccum it down. *Can I do that via the third tap? *I'll fill it with
some r22 after I vacuum it.
Blowing compressed air into the unit was a little bit
of a bad move. People in the HVAC and refrigeration
trades use dry nitrogen for internal clean out along
with a suitable solvent for coils detached from the
compressor. Compressed air can carry moisture into a
system when blown through it. R11 isn't used as freely
as it once was because it kills the poor defenseless
little ozones. I use a product called CF-20 Internal
Coil Cleaner available at many HVAC supply houses and
it's available without any special permit:
http://tinyurl.com/lk2uq3
You would have been better off leaving the valves closed
and flushing out the pipe stubs with freeze spray which
is basically a freon mix of some sort or even dust blaster
which will blow the stuff out and leave no residue. The
low side line being pierced would not cause an appreciable
oil loss from an un-powered unit. Because of the compressed
air introduced to the system you will need to pull a deep
vacuum on the system. The warmer it is when you do it, the
better it will pull out the moisture. Of course a good sized
liquid line dryer like a C-163 Sporlan which is a 3/8 flare
dryer which makes for easy replacement. I always add a sight
glass with a moisture indicator to all the systems I install.
You can get one that will screw right on to the C-163 and
and attach to the tubing with a flare fitting. Heck, HVAC
work isn't rocket surgery, Storman Norman does it. *snicker*
TDD- Hide quoted text -
- Show quoted text -
The valves weren't closed when I got it so I figured the compressed
air was not going to make much difference at this point. *I don't have
a nitrogen tank. *My supplies are a vacuum pump, set of gauges, a can
of r22. *My brazing skills are sketchy so I try to minimize that. *I'd
like to have a nitrogen tank but so far I've gotten away without.
I'll go ahead and pump it down and fill it with r22. *I'm guessing
it's ok to do that using that middle tap?
It has a filter/dryer on the high side. *I can add one to the low
side. *The guy moved it from one house to the another and kept it in a
shed. *So it got moved around a bit. * I'm afraid that there may be
some copper filings further down the low side line inside the unit
that I can't really get to. *What happens when they go into the
compressor? *Will they just end up sitting in the bottom in the oil?
Or the switching valve? *Are these things engineered anticipating that
occasional small solid might get in? *This is my biggest worry. *The
moisture I can get out with my vacuum pump.
Around here it's dirt daubers/mud daubers and other flying
or crawling critters you have to worry about when a pipe is
left open. The little bit of copper filings isn't a big concern.
The vacuum needs to be drawn from both high and low service
fittings through the gauge set. If you're worried about moisture,
why on earth are you not replacing the liquid line dryer?
The dryer is the first thing to replace, just don't leave it
open to the air for any longer than it takes to install it.
Since it's a heat pump, it requires biflow or bidirectional
dryers because the refrigerant flow is reversed when changing
from heat to cool. If you're worried about trash getting into
the reversing valve, the best thing to do would be to remove
the section of large diameter tubing and clean it out. Make
sure you wrap a wet rag around the reversing valve when using
your torch near it. You can always cut the tubing a distance
away from the reversing valve and braze it back together with
a coupling. A lot of service techs are using a low temperature
silver solder on HVAC equipment which doesn't require the use
of oxygen-acetylene torches.
TDD- Hide quoted text -
- Show quoted text -
Sorry if I seem stupid here, but I can't pull a vacuum through the
service valves without capping the lines can I?


Yes, I used silver solder on my regular hvac install at my primary
residence.- Hide quoted text -


- Show quoted text -


Guess I should add it's not been so open that bugs could get in. *It's
just that the service valves were never closed. *The high side line
was folded over. *A piece of the low side foam was stuck in the low
side pipe.


I assumed you were referring to pulling a vacuum after installation,
not for storage purposes. If the pipes were plugged up in any fashion,
there shouldn't be much moisture infiltration since there would still
be mostly freon in the system. The dryer should still be replaced when
it is finally installed. Since you have no nitrogen, R22 would be fine
for putting a slight pressure on the unit for storage but when
installed, it will still need a deep vacuum drawn on it. When me and
my friends install a new system in the field, we pressurize it with
nitrogen and leave it that way before ever pulling a vacuum and opening
the valves for startup. If we don't leave the condenser because of
the theft problem with new construction, we cap the line set and
pressurize it with nitrogen until it's time for occupation. That way
we have no surprise leaks such as those caused by other tradesmen
putting a nail or screw through a pipe. The thing about dry nitrogen
is that the static pressure is not going to change perceptively with
a change in temperature. If you pressurize for a leak test and come
back a week later when the weather has changed, the test pressure
will be the same if there are no leaks.

TDD- Hide quoted text -

- Show quoted text -


I gotta store it for a while. The garage/rec room is under
construction at the moment. It's about done with the framing/
exterior. My back is shot so I had to hire a local guy to do most of
that. I'm going to do the plumbing/electrical/hvac after he's
finished. Then I'll get someone back in to do the drywall, my back's
too bad for that as well. I picked this unit up because I've been
collecting stuff off craig's list local materials for a few months
now. If you know what you need and are not in a hurry it's a good way
to get supplies cheap. Lots of new items where someone changed their
mind or bought too many. This was $250 and johnstons wants $899 for
it. Some risk on my part but hey that's life.

I'll pull a vacuum via the third service port and follow up with a
little r22 into it.

I wouldn't mind having a nitrogen tank but a bargain hasn't come along
yet :-)
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,761
Default Heat Pump ?s

jamesgangnc wrote:
On Jun 24, 6:23 pm, The Daring Dufas
wrote:
jamesgangnc wrote:
On Jun 24, 3:27 pm, jamesgangnc wrote:
On Jun 24, 2:48 pm, The Daring Dufas
wrote:
jamesgangnc wrote:
On Jun 23, 8:19 pm, The Daring Dufas
wrote:
jamesgangnc wrote:
I've done a fair bit of my own hvac work. I replaced a couple of gas
furnaces and one split ac. I'm building a new garage with living
space above it out at my lake house. I picked up a "slightly" used
goodman 1 1/2 ton heat pump compressor off craig's list. It was
installed as part of an attic conversion that was never completed.
While the seller was moving out of the house the low side line was
damaged and it lost charge. Fast according to the seller.
The guy didn't know enough to shut the valves. Instead he hacksawed
off the lines. Folded the small one over and stuffed a piece of foam
in the big one. I cut them off with a pipe cutter, closed the valves,
and blew them out with compressed air. I was worried that I probably
did not get all the copper filings from the hacksaw so I opened the
valves and blew the lines out again via the third tap. (The one that
is used to check pressure during heat mode.) I didn't get a lot of
air to move through it though that way so I doubt I blew out any more
filings.
So I'm worried that there still may be some copper filings in the
lines. What else can I do?
I'm also a little worried that it may have lost some oil when the low
side was broken. There doesn't seem to be any easy way to drain and
refill the oil though.
I won't be installing it from a few months. I'd like to go ahead and
vaccum it down. Can I do that via the third tap? I'll fill it with
some r22 after I vacuum it.
Blowing compressed air into the unit was a little bit
of a bad move. People in the HVAC and refrigeration
trades use dry nitrogen for internal clean out along
with a suitable solvent for coils detached from the
compressor. Compressed air can carry moisture into a
system when blown through it. R11 isn't used as freely
as it once was because it kills the poor defenseless
little ozones. I use a product called CF-20 Internal
Coil Cleaner available at many HVAC supply houses and
it's available without any special permit:
http://tinyurl.com/lk2uq3
You would have been better off leaving the valves closed
and flushing out the pipe stubs with freeze spray which
is basically a freon mix of some sort or even dust blaster
which will blow the stuff out and leave no residue. The
low side line being pierced would not cause an appreciable
oil loss from an un-powered unit. Because of the compressed
air introduced to the system you will need to pull a deep
vacuum on the system. The warmer it is when you do it, the
better it will pull out the moisture. Of course a good sized
liquid line dryer like a C-163 Sporlan which is a 3/8 flare
dryer which makes for easy replacement. I always add a sight
glass with a moisture indicator to all the systems I install.
You can get one that will screw right on to the C-163 and
and attach to the tubing with a flare fitting. Heck, HVAC
work isn't rocket surgery, Storman Norman does it. *snicker*
TDD- Hide quoted text -
- Show quoted text -
The valves weren't closed when I got it so I figured the compressed
air was not going to make much difference at this point. I don't have
a nitrogen tank. My supplies are a vacuum pump, set of gauges, a can
of r22. My brazing skills are sketchy so I try to minimize that. I'd
like to have a nitrogen tank but so far I've gotten away without.
I'll go ahead and pump it down and fill it with r22. I'm guessing
it's ok to do that using that middle tap?
It has a filter/dryer on the high side. I can add one to the low
side. The guy moved it from one house to the another and kept it in a
shed. So it got moved around a bit. I'm afraid that there may be
some copper filings further down the low side line inside the unit
that I can't really get to. What happens when they go into the
compressor? Will they just end up sitting in the bottom in the oil?
Or the switching valve? Are these things engineered anticipating that
occasional small solid might get in? This is my biggest worry. The
moisture I can get out with my vacuum pump.
Around here it's dirt daubers/mud daubers and other flying
or crawling critters you have to worry about when a pipe is
left open. The little bit of copper filings isn't a big concern.
The vacuum needs to be drawn from both high and low service
fittings through the gauge set. If you're worried about moisture,
why on earth are you not replacing the liquid line dryer?
The dryer is the first thing to replace, just don't leave it
open to the air for any longer than it takes to install it.
Since it's a heat pump, it requires biflow or bidirectional
dryers because the refrigerant flow is reversed when changing
from heat to cool. If you're worried about trash getting into
the reversing valve, the best thing to do would be to remove
the section of large diameter tubing and clean it out. Make
sure you wrap a wet rag around the reversing valve when using
your torch near it. You can always cut the tubing a distance
away from the reversing valve and braze it back together with
a coupling. A lot of service techs are using a low temperature
silver solder on HVAC equipment which doesn't require the use
of oxygen-acetylene torches.
TDD- Hide quoted text -
- Show quoted text -
Sorry if I seem stupid here, but I can't pull a vacuum through the
service valves without capping the lines can I?
Yes, I used silver solder on my regular hvac install at my primary
residence.- Hide quoted text -
- Show quoted text -
Guess I should add it's not been so open that bugs could get in. It's
just that the service valves were never closed. The high side line
was folded over. A piece of the low side foam was stuck in the low
side pipe.

I assumed you were referring to pulling a vacuum after installation,
not for storage purposes. If the pipes were plugged up in any fashion,
there shouldn't be much moisture infiltration since there would still
be mostly freon in the system. The dryer should still be replaced when
it is finally installed. Since you have no nitrogen, R22 would be fine
for putting a slight pressure on the unit for storage but when
installed, it will still need a deep vacuum drawn on it. When me and
my friends install a new system in the field, we pressurize it with
nitrogen and leave it that way before ever pulling a vacuum and opening
the valves for startup. If we don't leave the condenser because of
the theft problem with new construction, we cap the line set and
pressurize it with nitrogen until it's time for occupation. That way
we have no surprise leaks such as those caused by other tradesmen
putting a nail or screw through a pipe. The thing about dry nitrogen
is that the static pressure is not going to change perceptively with
a change in temperature. If you pressurize for a leak test and come
back a week later when the weather has changed, the test pressure
will be the same if there are no leaks.

TDD- Hide quoted text -

- Show quoted text -


I gotta store it for a while. The garage/rec room is under
construction at the moment. It's about done with the framing/
exterior. My back is shot so I had to hire a local guy to do most of
that. I'm going to do the plumbing/electrical/hvac after he's
finished. Then I'll get someone back in to do the drywall, my back's
too bad for that as well. I picked this unit up because I've been
collecting stuff off craig's list local materials for a few months
now. If you know what you need and are not in a hurry it's a good way
to get supplies cheap. Lots of new items where someone changed their
mind or bought too many. This was $250 and johnstons wants $899 for
it. Some risk on my part but hey that's life.

I'll pull a vacuum via the third service port and follow up with a
little r22 into it.

I wouldn't mind having a nitrogen tank but a bargain hasn't come along
yet :-)


Keep looking, I found both of mine abandoned. Of course
over the years I've exchanged them numerous times but I
didn't have to pay that initial $135.00 or whatever it
is now. I have two "Q" sized cylinders and I bought a
good regulator which has the same fitting as an oxygen
regulator but is for inert gas. Dry nitrogen is some
very handy stuff to have around. I also have a gaggle
of 20lb CO2 cylinders that are for soft drink fountains.
Those are extremely useful when used with a high flow
regulator for blowing out condensers, clearing drains,
running air tools or inflating tires. I've found all
manner of tanks in dumpsters and as door props. Darn,
I have a bunch of propane tanks too. I'd make good
terrorist.

TDD

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
I want to switch from propane heat to a heat pump, any concerns? Mac Cool Home Repair 25 September 2nd 08 11:05 PM
Heat Pump vs. 2-Stage Heat Pump Susan Home Repair 3 December 25th 05 08:43 PM
Buddy tells me if I have elec heat and a heat pump, I can get a deal with PSE&G... dean Home Repair 3 September 26th 05 04:31 AM
HVAC - Oil or electric backup for new heat pump? Or oil heat only? anne in pa Home Repair 3 August 18th 05 01:55 PM
Zoned heat-pump and backup heat strip question Abe Home Repair 2 April 26th 05 01:54 AM


All times are GMT +1. The time now is 09:12 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"