Default GFCI breaks on tiny load

[this has been tackled elsewhere, but not answered!]

Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.

Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.

Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).

The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.

Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.

When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.

- Rick


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,417
Default GFCI breaks on tiny load

On Jun 1, 11:53*am, RickMerrill
wrote:
[this has been tackled elsewhere, but not answered!]

Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.

Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.

Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).

The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.

Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.

When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). *Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.

- Rick


I have seen this happen too. The GFCI circuit only takes about 5ma of
ground current to trip it. I think you could get this due to
capacitance between conductor in a long extension cord.. I had my
trouble tryin to use an electric weed whacker. It doesnt even have a
ground connection. I megged the extension cord thinking it may be bad
but there was no leakage at 1000 volts. Another extension cord worked
fine.

Jimmie
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,040
Default GFCI breaks on tiny load

In article
,
JIMMIE wrote:

On Jun 1, 11:53*am, RickMerrill
wrote:
[this has been tackled elsewhere, but not answered!]

Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.

Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.

Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).

The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.

Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.

When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). *Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.

- Rick


I have seen this happen too. The GFCI circuit only takes about 5ma of
ground current to trip it. I think you could get this due to
capacitance between conductor in a long extension cord.. I had my
trouble tryin to use an electric weed whacker. It doesnt even have a
ground connection. I megged the extension cord thinking it may be bad
but there was no leakage at 1000 volts. Another extension cord worked
fine.

Jimmie


I smell a market for a "GFCI rated" line if extension cords.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 33
Default GFCI breaks on tiny load

Smitty Two wrote:
In article
,
JIMMIE wrote:

On Jun 1, 11:53 am, RickMerrill
wrote:
[this has been tackled elsewhere, but not answered!]

Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.

Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.

Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).

The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.

Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.

When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.

- Rick

I have seen this happen too. The GFCI circuit only takes about 5ma of
ground current to trip it. I think you could get this due to
capacitance between conductor in a long extension cord.. I had my
trouble tryin to use an electric weed whacker. It doesnt even have a
ground connection. I megged the extension cord thinking it may be bad
but there was no leakage at 1000 volts. Another extension cord worked
fine.

Jimmie


I smell a market for a "GFCI rated" line if extension cords.


b'gosh, you're right!


http://www.rewci.com/25grfaciinex.html
25' Ground Fault Circuit Interrupter Extension Cord - GFCI Line Cords &
Adapters

Howsomeever, I suspect that the GFCI here is at the END of the cord, not
at the BEGINNING!-)

Plus, at $2 per FOOT, I'm thinking DIY!
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 33
Default GFCI breaks on tiny load

RickMerrill wrote:
Smitty Two wrote:
In article
,
JIMMIE wrote:

On Jun 1, 11:53 am, RickMerrill
wrote:
[this has been tackled elsewhere, but not answered!]

Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.

Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.

Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).

The resistance of the extension cord only looks like a bigger drop
light
bulb. So resistance is not the problem.

Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.

When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.

- Rick
I have seen this happen too. The GFCI circuit only takes about 5ma of
ground current to trip it. I think you could get this due to
capacitance between conductor in a long extension cord.. I had my
trouble tryin to use an electric weed whacker. It doesnt even have a
ground connection. I megged the extension cord thinking it may be bad
but there was no leakage at 1000 volts. Another extension cord worked
fine.

Jimmie


I smell a market for a "GFCI rated" line if extension cords.


b'gosh, you're right!


http://www.rewci.com/25grfaciinex.html
25' Ground Fault Circuit Interrupter Extension Cord - GFCI Line Cords &
Adapters

Howsomeever, I suspect that the GFCI here is at the END of the cord, not
at the BEGINNING!-)

Plus, at $2 per FOOT, I'm thinking DIY!


On closer examination i see i'm wrong (again) and that the
GFCI is placed at the Plug-in beginning of the cord.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,907
Default GFCI breaks on tiny load

RickMerrill wrote:
[this has been tackled elsewhere, but not answered!]

Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.

Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.

Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).

The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.

Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.

When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.

- Rick


My guess is it is either a crappy extension cord or an flakey extra
sensitive GFCI that is the problem.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 33
Default GFCI breaks on tiny load

wrote:
On Mon, 01 Jun 2009 11:53:32 -0400, RickMerrill
wrote:

[this has been tackled elsewhere, but not answered!]

Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.

Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.

Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).

The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.

Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.

When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.

- Rick



There is a concern with capacitance in the wiring tripping GFCIs but
you need a very long circuit to see it.
I suspect you have a lot of leakage in that circuit and the cord
pushes it over the edge.


There is no leakage in the circuit because a perfectly parallel outlet
behaves properly - the problem is entirely due to the cord, but why that
is I am not sure. It could be that the cord is an "el cheapo" and has
all kinds of leakage problems that don't show up until a real load is
put in it. I'm chopping it down from 25' to 6' and see what happens!


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 33
Default GFCI breaks on tiny load

wrote:
On Mon, 01 Jun 2009 14:36:46 -0400, RickMerrill
wrote:

wrote:
On Mon, 01 Jun 2009 11:53:32 -0400, RickMerrill
wrote:

[this has been tackled elsewhere, but not answered!]

Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.

Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.

Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).

The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.

Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.

When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.

- Rick


There is a concern with capacitance in the wiring tripping GFCIs but
you need a very long circuit to see it.
I suspect you have a lot of leakage in that circuit and the cord
pushes it over the edge.

There is no leakage in the circuit because a perfectly parallel outlet
behaves properly - the problem is entirely due to the cord, but why that
is I am not sure. It could be that the cord is an "el cheapo" and has
all kinds of leakage problems that don't show up until a real load is
put in it. I'm chopping it down from 25' to 6' and see what happens!



I bet the cord has a neutral to ground short in it.
or the neutral and ground are swapped
Try it with the cheater on the GFCI end but be careful of the ground
tab on the cheater. If the light doesn't work there will be 120v on
the ground tab..


There is no short in the cable. It is fine until a (small)load
is added (other than the polarity tester).

Using just 6 feet of the same cable - Blat!

Cheater has NO ground tab ;-)

Polarity tester says the wiring is correct!

Note: the wires in this cord are in parallel; the insulation is yellow.
the wires are #16.

???

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default GFCI breaks on tiny load

On Jun 1, 6:52*pm, wrote:
On Mon, 01 Jun 2009 17:36:57 -0400, RickMerrill





wrote:
wrote:
On Mon, 01 Jun 2009 14:36:46 -0400, RickMerrill
wrote:


wrote:
On Mon, 01 Jun 2009 11:53:32 -0400, RickMerrill
wrote:


[this has been tackled elsewhere, but not answered!]


Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.


Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.


Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).


The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.


Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.


When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). *Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.


- Rick


There is a concern with capacitance in the wiring tripping GFCIs but
you need a very long circuit to see it.
I suspect you have a lot of leakage in that circuit and the cord
pushes it over the edge.
There is no leakage in the circuit because a perfectly parallel outlet
behaves properly - the problem is entirely due to the cord, but why that
is I am not sure. It could be that the cord is an "el cheapo" and has
all kinds of leakage problems that don't show up until a real load is
put in it. I'm chopping it down from 25' to 6' and see what happens!


I bet the cord has a neutral to ground short in it.
or the neutral and ground are swapped
Try it with the cheater on the GFCI end but be careful of the ground
tab on the cheater. If the light doesn't work there will be 120v on
the ground tab..


There is no short in the cable. It is fine until a (small)load
is added (other than the polarity tester).


Using just 6 feet of the same cable - Blat!


Cheater has NO ground tab ;-)


Polarity tester says the wiring is correct!


Note: the wires in this cord are in parallel; the insulation is yellow.
the wires are #16.


???


If the neutral and ground are shorted you will never know until you
plug it into a GFCI and put a load on it.


That was my first thought too. And it doesn't have to be anywhere
near a complete short, just enough to amount to the milliamps needed
to trip the GFCI.

On the other hand, I vaguely remember that maybe GFCI's actually try
to put a tiny current on the downstream load line all the time to be
able to detect this type of fault without any actual load being
connected at the far end?





What happened when the 2 pin adapter was plugged into the GFCI and the
cord plugged into it?- Hide quoted text -

- Show quoted text -


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default GFCI breaks on tiny load

wrote:
On Jun 1, 6:52 pm, wrote:
On Mon, 01 Jun 2009 17:36:57 -0400, RickMerrill
wrote:
wrote:
On Mon, 01 Jun 2009 14:36:46 -0400, RickMerrill
wrote:
wrote:
On Mon, 01 Jun 2009 11:53:32 -0400, RickMerrill
wrote:
[this has been tackled elsewhere, but not answered!]
Plug a drop light into GFCI - the light lights up!
Plug drop light into house AC - the light lights up.
Plug an extension cord into GFCI and test with
polarity tester - all is well with gnd, hot and neutral.
Plug (same) drop light into above extension cord and
the GFCI "blows" (i.e. cuts the circuit breaker).
The resistance of the extension cord only looks like a bigger drop light
bulb. So resistance is not the problem.
Plug a "cheater" into extension cord (above) and plug drop light into
the cheater (i.e. ground wire is not connected) making sure that there
are no possible ground contact points - GFCI "blows" [see above] !
So the grounding is not a problem.
When the GFCI compares the AC current in with the AV current out it is
obviously comparing similar phases (a.k.a. cycles). Clearly any phase
shift due to capacitance in the extension cord COULD cause what we see.
- Rick


There is a concern with capacitance in the wiring tripping GFCIs but
you need a very long circuit to see it.
I suspect you have a lot of leakage in that circuit and the cord
pushes it over the edge.


There is no leakage in the circuit because a perfectly parallel outlet
behaves properly - the problem is entirely due to the cord, but why that
is I am not sure. It could be that the cord is an "el cheapo" and has
all kinds of leakage problems that don't show up until a real load is
put in it. I'm chopping it down from 25' to 6' and see what happens!


I bet the cord has a neutral to ground short in it.
or the neutral and ground are swapped
Try it with the cheater on the GFCI end but be careful of the ground
tab on the cheater. If the light doesn't work there will be 120v on
the ground tab..


There is no short in the cable. It is fine until a (small)load
is added (other than the polarity tester).
Using just 6 feet of the same cable - Blat!
Cheater has NO ground tab ;-)
Polarity tester says the wiring is correct!
Note: the wires in this cord are in parallel; the insulation is yellow.
the wires are #16.
???


If the neutral and ground are shorted you will never know until you
plug it into a GFCI and put a load on it.


That was my first thought too. And it doesn't have to be anywhere
near a complete short, just enough to amount to the milliamps needed
to trip the GFCI.

On the other hand, I vaguely remember that maybe GFCI's actually try
to put a tiny current on the downstream load line all the time to be
able to detect this type of fault without any actual load being
connected at the far end?


Yes they do. There is info for a GFCI IC at:
http://www.national.com/ds/LM/LM1851.pdf
To detect a downstream crossed N-G only a second current transformer and
a capacitor are added. If the GFCI is wired H-N reversed it will still
detect a downstream "N"-G short.

A *really* old GFCI may not have this feature - don't know when it was
added to the UL standard.



N-G reverse on the cord as suggested above? (A receptacle tester won't
find a N-G reverse.)

If 6 ft of the cord trips the GFCI does the other length of cord trip it?

Do either of the lengths of cord trip other GFCIs?

Sounds like the GFCI is a breaker. That means the cord adds to the
capacitance of the rest of the circuit and could push it "over the edge"
- also suggested by gfretwell above.

What happened when the 2 pin adapter was plugged into the GFCI and the
cord plugged into it?



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI outlets required with a GFCI Breaker? [email protected] Home Repair 17 August 3rd 08 07:06 PM
Tiny, tiny metalwork - chip re-soldering Tom Gardner[_2_] Metalworking 20 June 24th 08 04:21 PM
(Q:) Switched light on load side of GFCI outlet [email protected] Home Repair 1 August 7th 07 04:48 PM
(Q:) Switched light on load side of GFCI outlet [email protected] Home Ownership 3 August 7th 07 03:08 PM
Two circuts on load side of GFCI? kevins_news Home Repair 5 October 26th 05 10:06 PM


All times are GMT +1. The time now is 06:25 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"