/I just replaced a drier circuit. My problem is that the drier is a
European model that requires 240 volt service only and has an regular
drier plug with the common (white) wire cut away. Now my question:
when I measure the voltages at the outlet with a digital volt meter, I
get 120 volts on each leg but between the two hots, I don't get any
reading. How can that be?

The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,228
Default Drier circuit - electrical question.

When you replaced the dryer circuit you ran two 'hot' wires from the same
side of the circuit breaker/fuse box. Go back to the breaker box and move
one of the wires to the other side of the 120/240 circuit.

"Jimbo" wrote in message
...
/I just replaced a drier circuit. My problem is that the drier is a
European model that requires 240 volt service only and has an regular
drier plug with the common (white) wire cut away. Now my question:
when I measure the voltages at the outlet with a digital volt meter, I
get 120 volts on each leg but between the two hots, I don't get any
reading. How can that be?

The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).



  #3   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Drier circuit - electrical question.

Ralph Mowery wrote:
When you replaced the dryer circuit you ran two 'hot' wires from the same
side of the circuit breaker/fuse box. Go back to the breaker box and move
one of the wires to the other side of the 120/240 circuit.

....

Specifically, use a double-pole breaker in the distribution box in a
location intended to house one -- they're designed for the purpose and
will pick up the two opposing phase legs automagically. Plus, you'll
have a single-lever breaker rather than two; much better (and
Code-compliant whereas the other way isn't unless the two are made to be
(and are) "ganged" together.

--
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 116
Default Drier circuit - electrical question.

On Jan 25, 2:41*pm, dpb wrote:
Ralph Mowery wrote:
When you replaced the dryer circuit you ran two 'hot' wires from the same
side of the circuit breaker/fuse box. *Go back to the breaker box and move
one of the wires to the other side of the 120/240 circuit.


...

Specifically, use a double-pole breaker in the distribution box in a
location intended to house one -- they're designed for the purpose and
will pick up the two opposing phase legs automagically. *Plus, you'll
have a single-lever breaker rather than two; much better (and
Code-compliant whereas the other way isn't unless the two are made to be
(and are) "ganged" together.

--


Thanks Ralph and dpb.
As soon as I read your reply I realized what I had done There was
one vacant position and I moved a few single and double breaks around
to tidy everything up and, well, you can guess what the result was.
Sometimes, things are so obvious to another pair of eyes. Thanks
again.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Drier circuit - electrical question.


"Jimbo" wrote in message
...
/I just replaced a drier circuit. My problem is that the drier is a
European model that requires 240 volt service only and has an regular
drier plug with the common (white) wire cut away. Now my question:
when I measure the voltages at the outlet with a digital volt meter, I
get 120 volts on each leg but between the two hots, I don't get any
reading. How can that be?

The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).


In addition to what has already been said, it is possible that you installed
a "twin" circuit breaker, and not a double pole. The twin breaker has two
locations for circuit conductors to attach, but only attaches to one buss on
the panel.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 116
Default Drier circuit - electrical question.

On Jan 25, 3:40*pm, "RBM" wrote:
"Jimbo" wrote in message

...

/I just replaced a drier circuit. *My problem is that the drier is a
European model that requires 240 volt service only and has an regular
drier plug with the common (white) wire cut away. *Now my question:
when I measure the voltages at the outlet with a digital volt meter, I
get 120 volts on each leg but between the two hots, I don't get any
reading. *How can that be?


The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).


In addition to what has already been said, it is possible that you installed
a "twin" circuit breaker, and not a double pole. The twin breaker has two
locations for circuit conductors to attach, but only attaches to one buss on
the panel.


Not sure if that applies to my StabLok panel but I will check it out.
I just reused the breaker that had previously been used for the
original drier circuit. The circuit was removed during some basement
renovations and we had been using a smaller 120V drier since.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Drier circuit - electrical question.

Jimbo wrote:
On Jan 25, 3:40 pm, "RBM" wrote:
"Jimbo" wrote in message

...

/I just replaced a drier circuit. My problem is that the drier is a
European model that requires 240 volt service only and has an regular
drier plug with the common (white) wire cut away. Now my question:
when I measure the voltages at the outlet with a digital volt meter, I
get 120 volts on each leg but between the two hots, I don't get any
reading. How can that be?
The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).

In addition to what has already been said, it is possible that you installed
a "twin" circuit breaker, and not a double pole. The twin breaker has two
locations for circuit conductors to attach, but only attaches to one buss on
the panel.


Not sure if that applies to my StabLok panel but I will check it out.
I just reused the breaker that had previously been used for the
original drier circuit. The circuit was removed during some basement
renovations and we had been using a smaller 120V drier since.


StabLok? Uh-oh...

http://www.inspect-ny.com/fpe/fpepanel.htm

Seriously, you may wish to consider a complete replacement of your load
center.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Drier circuit - electrical question.

On Jan 25, 5:05�pm, Nate Nagel wrote:
Jimbo wrote:
On Jan 25, 3:40 pm, "RBM" wrote:
"Jimbo" wrote in message


....


/I just replaced a drier circuit. �My problem is that the drier is a
European model that requires 240 volt service only and has an regular
drier plug with the common (white) wire cut away. �Now my question:
when I measure the voltages at the outlet with a digital volt meter, I
get 120 volts on each leg but between the two hots, I don't get any
reading. �How can that be?
The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).
In addition to what has already been said, it is possible that you installed
a "twin" circuit breaker, and not a double pole. The twin breaker has two
locations for circuit conductors to attach, but only attaches to one buss on
the panel.


Not sure if that applies to my StabLok panel but I will check it out.
I just reused the breaker that had previously been used for the
original drier circuit. �The circuit was removed during some basement
renovations and we had been using a smaller 120V drier since.


StabLok? �Uh-oh...

http://www.inspect-ny.com/fpe/fpepanel.htm

Seriously, you may wish to consider a complete replacement of your load
center.

nate

--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel- Hide quoted text -

- Show quoted text -


yeah I had a stab loc breaker not trip on a dead short, the wiring
melted and exploded before my eyes. splattered with hot metal.

replace entire panel immediately
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 116
Default Drier circuit - electrical question.

On Jan 25, 5:16*pm, " wrote:
On Jan 25, 5:05 pm, Nate Nagel wrote:



Jimbo wrote:
On Jan 25, 3:40 pm, "RBM" wrote:
"Jimbo" wrote in message


....


/I just replaced a drier circuit. My problem is that the drier is a
European model that requires 240 volt service only and has an regular
drier plug with the common (white) wire cut away. Now my question:
when I measure the voltages at the outlet with a digital volt meter, I
get 120 volts on each leg but between the two hots, I don't get any
reading. How can that be?
The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).
In addition to what has already been said, it is possible that you installed
a "twin" circuit breaker, and not a double pole. The twin breaker has two
locations for circuit conductors to attach, but only attaches to one buss on
the panel.


Not sure if that applies to my StabLok panel but I will check it out.
I just reused the breaker that had previously been used for the
original drier circuit. The circuit was removed during some basement
renovations and we had been using a smaller 120V drier since.


StabLok? Uh-oh...


http://www.inspect-ny.com/fpe/fpepanel.htm


Seriously, you may wish to consider a complete replacement of your load
center.


nate


--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel-Hide quoted text -


- Show quoted text -


yeah I had a stab loc breaker not trip on a dead short, the wiring
melted and exploded before my eyes. splattered with hot metal.

replace entire panel immediately


Wow ... now that is a scary report! My experience so far is that when
shorts have happened as work is being done around the house, etc. is
that the appropriate breakers have tripped. There is also one circuit
that is constantly being overloaded - don't ask - and that trips with
irritating regularity. However, there is another with the garage/
workshop on it that I've worried about: lights dim severely when power
tools are switched on etc. but it has never tripped. I'm in Canada
and my panel looks completely different to the ones pictured on the
website. I'm going to call the City fire office and the utility
company tomorrow to see if they have any information on this.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Drier circuit - electrical question.


"Jimbo" wrote in message
...
On Jan 25, 3:40 pm, "RBM" wrote:
"Jimbo" wrote in message

...

/I just replaced a drier circuit. My problem is that the drier is a
European model that requires 240 volt service only and has an regular
drier plug with the common (white) wire cut away. Now my question:
when I measure the voltages at the outlet with a digital volt meter, I
get 120 volts on each leg but between the two hots, I don't get any
reading. How can that be?


The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).


In addition to what has already been said, it is possible that you
installed
a "twin" circuit breaker, and not a double pole. The twin breaker has two
locations for circuit conductors to attach, but only attaches to one buss
on
the panel.


Not sure if that applies to my StabLok panel but I will check it out.
I just reused the breaker that had previously been used for the
original drier circuit. The circuit was removed during some basement
renovations and we had been using a smaller 120V drier since.

No, FPE made half sized single pole breakers and double pole breakers, but I
don't believe they ever made twins




  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 42
Default Drier circuit - electrical question.


"Jimbo" wrote in message
...
On Jan 25, 5:16 pm, " wrote:
On Jan 25, 5:05 pm, Nate Nagel wrote:



Jimbo wrote:
On Jan 25, 3:40 pm, "RBM" wrote:
"Jimbo" wrote in message


...


/I just replaced a drier circuit. My problem is that the drier is a
European model that requires 240 volt service only and has an
regular
drier plug with the common (white) wire cut away. Now my question:
when I measure the voltages at the outlet with a digital volt meter,
I
get 120 volts on each leg but between the two hots, I don't get any
reading. How can that be?
The corresponding washer is also 240 but runs on a straight 240 volt
circuit and uses standard 240 volt outlet and lug (horizontal rather
than vertical blades on plug).
In addition to what has already been said, it is possible that you
installed
a "twin" circuit breaker, and not a double pole. The twin breaker has
two
locations for circuit conductors to attach, but only attaches to one
buss on
the panel.


Not sure if that applies to my StabLok panel but I will check it out.
I just reused the breaker that had previously been used for the
original drier circuit. The circuit was removed during some basement
renovations and we had been using a smaller 120V drier since.


StabLok? Uh-oh...


http://www.inspect-ny.com/fpe/fpepanel.htm


Seriously, you may wish to consider a complete replacement of your load
center.


nate


--
replace "roosters" with "cox" to
reply.http://members.cox.net/njnagel-Hide quoted text -


- Show quoted text -


yeah I had a stab loc breaker not trip on a dead short, the wiring
melted and exploded before my eyes. splattered with hot metal.

replace entire panel immediately


Wow ... now that is a scary report! My experience so far is that when
shorts have happened as work is being done around the house, etc. is
that the appropriate breakers have tripped. There is also one circuit
that is constantly being overloaded - don't ask - and that trips with
irritating regularity. However, there is another with the garage/
workshop on it that I've worried about: lights dim severely when power
tools are switched on etc. but it has never tripped. I'm in Canada
and my panel looks completely different to the ones pictured on the
website. I'm going to call the City fire office and the utility
company tomorrow to see if they have any information on this.


You might look here too (Canadian Federal Pioneer Electrical Hazards):
http://www.inspect-ny.com/fpe/FederalPioneer.htm

http://www.inspect-ny.com/fpe/schneider.htm

Cheers,
Jim


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Washer and drier on same circuit Jimbo Home Repair 8 November 13th 07 09:25 PM
Generic electrical question Do volts drop when a load is on the circuit hombrewdude Home Repair 13 September 11th 07 09:31 PM
Electrical Question and request for circuit diagram Brian_SouthJersey Home Repair 7 February 27th 07 02:27 PM
Electrical Service Box Question & Half Thick Circuit Breakers ? Robert11 Home Repair 5 February 23rd 06 11:57 PM
Electrical question: a gfci AND a lighting circuit Home Repair 4 December 9th 05 08:17 PM


All times are GMT +1. The time now is 10:57 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"