Posted to alt.home.repair
|
|||
|
|||
![]()
A customer called with an intermittent electrical problem: The electric
range and refrigerator on occasion stop working, then start working for no apparent reason. It's obvious that one of the hot legs is opening, as that would be the only common denominator between a 120 volt refrigerator circuit, and a 240 volt range circuit. The customer was also unaware of a multitude of other circuits that were also dead. Usually when I get these calls, I start with the connections in the most hostile environment, 1) The overhead service connections, 2) The outdoor meter socket, then check the main circuit breaker. In this case the culprit was the main circuit breaker, which by all outward appearance, looks fine. There was antiox paste on the conductor connections, no hissing or crackling sounds, and the breaker was cool to the touch. Upon removing the breaker, the problem became clear. A bad connection (factory) between one pole of the breaker and the panel buss, over time caused overheating and annealing of both the panel buss and the copper contact of the breaker. Pictures to follow: http://i17.photobucket.com/albums/b9...ldamage006.jpg http://i17.photobucket.com/albums/b9...ldamage008.jpg http://i17.photobucket.com/albums/b9...ldamage003.jpg http://i17.photobucket.com/albums/b9...ldamage005.jpg |
#2
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "RBM" wrote in message ... A customer called with an intermittent electrical problem: The electric range and refrigerator on occasion stop working, then start working for no apparent reason. It's obvious that one of the hot legs is opening, as that would be the only common denominator between a 120 volt refrigerator circuit, and a 240 volt range circuit. The customer was also unaware of a multitude of other circuits that were also dead. Usually when I get these calls, I start with the connections in the most hostile environment, 1) The overhead service connections, 2) The outdoor meter socket, then check the main circuit breaker. In this case the culprit was the main circuit breaker, which by all outward appearance, looks fine. There was antiox paste on the conductor connections, no hissing or crackling sounds, and the breaker was cool to the touch. Upon removing the breaker, the problem became clear. A bad connection (factory) between one pole of the breaker and the panel buss, over time caused overheating and annealing of both the panel buss and the copper contact of the breaker. Pictures to follow: http://i17.photobucket.com/albums/b9...ldamage006.jpg http://i17.photobucket.com/albums/b9...ldamage008.jpg http://i17.photobucket.com/albums/b9...ldamage003.jpg http://i17.photobucket.com/albums/b9...ldamage005.jpg Thanks for posting Roy. Did you have to change the load center? |
#3
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "John Grabowski" wrote in message ... "RBM" wrote in message ... A customer called with an intermittent electrical problem: The electric range and refrigerator on occasion stop working, then start working for no apparent reason. It's obvious that one of the hot legs is opening, as that would be the only common denominator between a 120 volt refrigerator circuit, and a 240 volt range circuit. The customer was also unaware of a multitude of other circuits that were also dead. Usually when I get these calls, I start with the connections in the most hostile environment, 1) The overhead service connections, 2) The outdoor meter socket, then check the main circuit breaker. In this case the culprit was the main circuit breaker, which by all outward appearance, looks fine. There was antiox paste on the conductor connections, no hissing or crackling sounds, and the breaker was cool to the touch. Upon removing the breaker, the problem became clear. A bad connection (factory) between one pole of the breaker and the panel buss, over time caused overheating and annealing of both the panel buss and the copper contact of the breaker. Pictures to follow: http://i17.photobucket.com/albums/b9...ldamage006.jpg http://i17.photobucket.com/albums/b9...ldamage008.jpg http://i17.photobucket.com/albums/b9...ldamage003.jpg http://i17.photobucket.com/albums/b9...ldamage005.jpg Thanks for posting Roy. Did you have to change the load center? Yes, that one section of buss was shot. My picture doesn't show how discolored it is was where the breaker connected to it. This is the 3rd Murray main breaker go bad this way that I've seen in this past year. The other two showed up in time to save the buss. |
#4
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() RBM wrote: A customer called with an intermittent electrical problem: The electric range and refrigerator on occasion stop working, then start working for no apparent reason. It's obvious that one of the hot legs is opening, as that would be the only common denominator between a 120 volt refrigerator circuit, and a 240 volt range circuit. The customer was also unaware of a multitude of other circuits that were also dead. Usually when I get these calls, I start with the connections in the most hostile environment, 1) The overhead service connections, 2) The outdoor meter socket, then check the main circuit breaker. In this case the culprit was the main circuit breaker, which by all outward appearance, looks fine. There was antiox paste on the conductor connections, no hissing or crackling sounds, and the breaker was cool to the touch. Upon removing the breaker, the problem became clear. A bad connection (factory) between one pole of the breaker and the panel buss, over time caused overheating and annealing of both the panel buss and the copper contact of the breaker. Pictures to follow: http://i17.photobucket.com/albums/b9...ldamage006.jpg http://i17.photobucket.com/albums/b9...ldamage008.jpg http://i17.photobucket.com/albums/b9...ldamage003.jpg http://i17.photobucket.com/albums/b9...ldamage005.jpg Eeew! This is why I stick with Square D QO equipment. Even then I do inspect items as I'm assembling and installing them. |
#5
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Dec 1, 4:27*pm, "RBM" wrote:
A customer called with an intermittent electrical problem: The electric range and refrigerator on occasion stop working, then start working for no apparent reason. It's obvious that one of the hot legs is opening, as that would be the only common denominator between a 120 volt refrigerator circuit, and a 240 volt range circuit. The customer was also unaware of a multitude of other circuits that were also dead. Usually when I get these calls, I start with the connections in the most hostile environment, 1) The overhead service connections, 2) The outdoor meter socket, then check the main circuit breaker. In this case the culprit was the main circuit breaker, which by all outward appearance, looks fine. There was antiox paste on the conductor connections, no hissing or crackling sounds, and the breaker was cool to the touch. Upon removing the breaker, the problem became clear. A bad connection (factory) between one pole of the breaker and the panel buss, over time caused overheating and annealing of both the panel buss and the copper contact of the breaker. Pictures to follow:http://i17.photobucket.com/albums/b9...%20Breaker%20p... http://i17.photobucket.com/albums/b9...%20Breaker%20p... http://i17.photobucket.com/albums/b9...%20Breaker%20p... http://i17.photobucket.com/albums/b9...%20Breaker%20p... Well that's one for the books. Nice pics, too. Joe |
#6
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
A couple friends of mine were having power problems in their home. Their
panel box was modern, can't remember what brand. Anyhow, the mains power came in through a double 100 breaker. There was a lot of white oxidation where the breaker connected to the panel. Myself, and the resident used strap on head lamps, to see. Turn off the main breaker, and unsnap it from the panel. Tough to do, it was plenty corroded on. Clean the distribution bars with sand screen. Pump a bunch of anti oxidant into the open slot end of the breaker, and put it all back together. No further problems. Those are very good picture. Thanks for posting. The repair I did, was before I got my digicam. -- Christopher A. Young Learn more about Jesus www.lds.org .. "RBM" wrote in message ... A customer called with an intermittent electrical problem: The electric range and refrigerator on occasion stop working, then start working for no apparent reason. It's obvious that one of the hot legs is opening, as that would be the only common denominator between a 120 volt refrigerator circuit, and a 240 volt range circuit. The customer was also unaware of a multitude of other circuits that were also dead. Usually when I get these calls, I start with the connections in the most hostile environment, 1) The overhead service connections, 2) The outdoor meter socket, then check the main circuit breaker. In this case the culprit was the main circuit breaker, which by all outward appearance, looks fine. There was antiox paste on the conductor connections, no hissing or crackling sounds, and the breaker was cool to the touch. Upon removing the breaker, the problem became clear. A bad connection (factory) between one pole of the breaker and the panel buss, over time caused overheating and annealing of both the panel buss and the copper contact of the breaker. Pictures to follow: http://i17.photobucket.com/albums/b9...ldamage006.jpg http://i17.photobucket.com/albums/b9...ldamage008.jpg http://i17.photobucket.com/albums/b9...ldamage003.jpg http://i17.photobucket.com/albums/b9...ldamage005.jpg |
#7
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
That does look like an older design.
-- Christopher A. Young Learn more about Jesus www.lds.org .. "John Grabowski" wrote in message ... Thanks for posting Roy. Did you have to change the load center? |
#8
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Third this year? You are an electrician?
-- Christopher A. Young Learn more about Jesus www.lds.org .. "RBM" wrote in message ... Thanks for posting Roy. Did you have to change the load center? Yes, that one section of buss was shot. My picture doesn't show how discolored it is was where the breaker connected to it. This is the 3rd Murray main breaker go bad this way that I've seen in this past year. The other two showed up in time to save the buss. |
#9
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "Stormin Mormon" wrote in message ... A couple friends of mine were having power problems in their home. Their panel box was modern, can't remember what brand. Anyhow, the mains power came in through a double 100 breaker. There was a lot of white oxidation where the breaker connected to the panel. Myself, and the resident used strap on head lamps, to see. Turn off the main breaker, and unsnap it from the panel. Tough to do, it was plenty corroded on. Clean the distribution bars with sand screen. Pump a bunch of anti oxidant into the open slot end of the breaker, and put it all back together. No further problems. As long as you catch it before the buss metal is destroyed from overheating that'll work. These Murray panels have bolt on main breakers, installed at the factory. There was some antiox on the connection, so my guess is that it's just a poor design. Murray no longer uses this type of main breaker. Those are very good picture. Thanks for posting. The repair I did, was before I got my digicam. -- Christopher A. Young Learn more about Jesus www.lds.org . "RBM" wrote in message ... A customer called with an intermittent electrical problem: The electric range and refrigerator on occasion stop working, then start working for no apparent reason. It's obvious that one of the hot legs is opening, as that would be the only common denominator between a 120 volt refrigerator circuit, and a 240 volt range circuit. The customer was also unaware of a multitude of other circuits that were also dead. Usually when I get these calls, I start with the connections in the most hostile environment, 1) The overhead service connections, 2) The outdoor meter socket, then check the main circuit breaker. In this case the culprit was the main circuit breaker, which by all outward appearance, looks fine. There was antiox paste on the conductor connections, no hissing or crackling sounds, and the breaker was cool to the touch. Upon removing the breaker, the problem became clear. A bad connection (factory) between one pole of the breaker and the panel buss, over time caused overheating and annealing of both the panel buss and the copper contact of the breaker. Pictures to follow: http://i17.photobucket.com/albums/b9...ldamage006.jpg http://i17.photobucket.com/albums/b9...ldamage008.jpg http://i17.photobucket.com/albums/b9...ldamage003.jpg http://i17.photobucket.com/albums/b9...ldamage005.jpg |
#10
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Must have caught this one, in time. Worked till they day they moved. Which
was a couple months later. Did you shut off the mains, by pulling the meter or something? -- Christopher A. Young Learn more about Jesus www.lds.org .. "RBM" wrote in message ... "Stormin Mormon" wrote in message ... the panel. Tough to do, it was plenty corroded on. Clean the distribution bars with sand screen. Pump a bunch of anti oxidant into the open slot end of the breaker, and put it all back together. No further problems. As long as you catch it before the buss metal is destroyed from overheating that'll work. These Murray panels have bolt on main breakers, installed at the factory. There was some antiox on the connection, so my guess is that it's just a poor design. Murray no longer uses this type of main breaker. |
#11
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "Stormin Mormon" wrote in message ... Must have caught this one, in time. Worked till they day they moved. Which was a couple months later. Did you shut off the mains, by pulling the meter or something? I have two electric companies in my area. One installs case hardened locks on the meter boxes, the other just uses a wire tag. With the locks, I have to cut the overhead conductors, then rebug them when I'm finished. This one was a tag type, so I just pulled the meter -- Christopher A. Young Learn more about Jesus www.lds.org . "RBM" wrote in message ... "Stormin Mormon" wrote in message ... the panel. Tough to do, it was plenty corroded on. Clean the distribution bars with sand screen. Pump a bunch of anti oxidant into the open slot end of the breaker, and put it all back together. No further problems. As long as you catch it before the buss metal is destroyed from overheating that'll work. These Murray panels have bolt on main breakers, installed at the factory. There was some antiox on the connection, so my guess is that it's just a poor design. Murray no longer uses this type of main breaker. |
#12
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Yes, that does sound safer than working on live circuit box. The power co in
my area uses Highfield barrel locks. Some of the meters have the metal tag with the serial number on it. They are pretty good about coming out to pull meters as needed, if an electrician is working. Cut the overhead feed wires sounds do-able if you have the right insulated cutters, and have whatever butt connector crimps are needed to put the wires together. I'm not sure I've got the courage or confidence to be cutting high amp wires like that. -- Christopher A. Young Learn more about Jesus www.lds.org .. "RBM" wrote in message ... "Stormin Mormon" wrote in message ... Must have caught this one, in time. Worked till they day they moved. Which was a couple months later. Did you shut off the mains, by pulling the meter or something? I have two electric companies in my area. One installs case hardened locks on the meter boxes, the other just uses a wire tag. With the locks, I have to cut the overhead conductors, then rebug them when I'm finished. This one was a tag type, so I just pulled the meter |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
HP/Agilent E3632A programmable power supply has power up failure (solution) | Electronics Repair | |||
Home Electrical Circuit (partial) Failure | Home Repair | |||
Partial power outage? | Home Repair | |||
Partial power loss | Home Ownership | |||
Transistor partial failure possible? | Electronics Repair |