14 and 12 gauge wiring problem
I know that you cannot use 14 gauge wire in a 20amp circuit because 14
gauge can only handle 15 amps, but I ran into a problem with my bathroom remodel. I have a huge mirror on one wall that also has a vanity bar light on it that was stuck on the mirror with adhesive. The idiot who put the mirror on did not cut out the box opening, but rather just cut out a 1" hole. The wire feeding behind the mirror is a 14 gauge wire. There is no way I can get a 12 gauge wire inside the box because of the small opening in the mirror. And I can't even use the 14 gauge as a drag line to pull because its clamped in the box, and plus it's fed from the bottom. So my question is being that since the vanity light is the only load that the 14 gauge wire is feeding, any problem with tapping off the new 20A circuit that I ran? I figure the thin wiring inside the vanity would fry first anyway before the 14 gauge would if there was a problem. Otherwise I would have to tear down the mirrored wall to get to the box. |
#2
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
Mike,
Why did you run a new 20 amp circuit to power one light bar? I'm not sure if that's what you are saying but I can't figure ir out. Replace the 20 amp breaker with a 15 amp breaker and you will be ok. If you need 20 amps on that circuit for some reason then you can not use the 14 gauge wire. If a short circuit happens in the light bar the wire may overheat before the breaker blows. Can you go through this wall from the other side to acess this electrical box, then patch the hole and repaint? Might be easier than attacking the mirror. Dave M. |
#3
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
On Sep 16, 7:22*pm, "David L. Martel" wrote:
Mike, * *Why did you run a new 20 amp circuit to power one light bar? I'm not sure if that's what you are saying but I can't figure ir out. Replace the 20 amp breaker with a 15 amp breaker and you will be ok. * *If you need 20 amps on that circuit for some reason then you can not use the 14 gauge wire. If a short circuit happens in the light bar the wire may overheat before the breaker blows. * *Can you go through this wall from the other side to acess this electrical box, then patch the hole and repaint? Might be easier than attacking the mirror. Dave M. Before the remodel, the bathroom was fed by a 15A circuit, which was also shared by the outlets and lights in the adjac ent den. So I ran a new 20A circuit to feed the GFI outlet, bath fan and shower light. But the vanity light is the only box I can't access. It's on an outside wall so I can't get it on the other side. |
#4
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
"Mikepier" wrote in message ... I know that you cannot use 14 gauge wire in a 20amp circuit because 14 gauge can only handle 15 amps, but I ran into a problem with my bathroom remodel. I have a huge mirror on one wall that also has a vanity bar light on it that was stuck on the mirror with adhesive. The idiot who put the mirror on did not cut out the box opening, but rather just cut out a 1" hole. The wire feeding behind the mirror is a 14 gauge wire. There is no way I can get a 12 gauge wire inside the box because of the small opening in the mirror. And I can't even use the 14 gauge as a drag line to pull because its clamped in the box, and plus it's fed from the bottom. So my question is being that since the vanity light is the only load that the 14 gauge wire is feeding, any problem with tapping off the new 20A circuit that I ran? I figure the thin wiring inside the vanity would fry first anyway before the 14 gauge would if there was a problem. Otherwise I would have to tear down the mirrored wall to get to the box. Holy cow, I've run into that same mirror guy... several times. I doubt you'd fry the #14, but why not just connect it to the existing 15 amp circuit that is feeding the bathroom now. Only the outlets are required to be 20 amp |
#5
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
"Mikepier" wrote in message ... I know that you cannot use 14 gauge wire in a 20amp circuit because 14 gauge can only handle 15 amps, but I ran into a problem with my bathroom remodel. I have a huge mirror on one wall that also has a vanity bar light on it that was stuck on the mirror with adhesive. The idiot who put the mirror on did not cut out the box opening, but rather just cut out a 1" hole. The wire feeding behind the mirror is a 14 gauge wire. There is no way I can get a 12 gauge wire inside the box because of the small opening in the mirror. And I can't even use the 14 gauge as a drag line to pull because its clamped in the box, and plus it's fed from the bottom. So my question is being that since the vanity light is the only load that the 14 gauge wire is feeding, any problem with tapping off the new 20A circuit that I ran? I figure the thin wiring inside the vanity would fry first anyway before the 14 gauge would if there was a problem. Otherwise I would have to tear down the mirrored wall to get to the box. If it matters to you, you should know that what you have is not code compliant. All junction and outlet boxes are supposed to be accesssible, and this one obviously isn't. A mirror or other non-removable covering over a box should be cut out to the edges of the boxes and the fixture should cover the opening. Of course, lots of people figure codes are just to make more money for the electricians! Don Young |
#6
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
|
#7
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
On Sep 17, 1:29*am, Kevin Ricks wrote:
wrote: On Tue, 16 Sep 2008 19:40:01 -0400, "RBM" wrote: "Mikepier" wrote in message .... I know that you cannot use 14 gauge wire in a 20amp circuit because 14 gauge can only handle 15 amps, but I ran into a problem with my bathroom remodel. I have a huge mirror on one wall that also has a vanity bar *light on it that was stuck on the mirror with adhesive. The idiot who put the mirror on did not cut out the box opening, but rather just cut out a 1" hole. The wire feeding behind the mirror is a 14 gauge wire. There is no way I can get a 12 gauge wire inside the box because of the small opening in the mirror. And I can't even use the 14 gauge as a drag line to pull because its clamped in the box, and plus it's fed from the bottom. So *my question is being that since the vanity light is the only load that the 14 gauge wire is feeding, any problem with tapping off the new 20A circuit that I ran? I figure the thin wiring inside the vanity would fry first anyway before the 14 gauge would if there was a problem. Otherwise I would have to tear down the mirrored wall to get to the box. Holy cow, I've run into that same mirror guy... several times. I doubt you'd fry the #14, but why not just connect it to the existing 15 amp circuit that is feeding the bathroom now. Only the outlets are required to be 20 amp Good advice, the real answer. And if the GFCI trips he will still have lights powered on which is a plus. Kevin- Hide quoted text - - Show quoted text - The way this thread reads is that the previous wiring for the light is still there. The one inch hole is not code compliant; but anyway, why not just leave the light hooked up as before! Separate circuit. If that is not possible, hook up the 14AWG wiring to the mirror light fixture to the 20 amp circuit wired with 12 AWG and change the circuit breaker for the bathroom circuit to 15 amps. Surely 15 amp at 115 volts, a total of 1700 to 1800 watts is sufficient for whole bathroom? Even a hair dryer (plugged into the GFCI of course) will take say a maximum of 1300 watts leaving at least 400 watts for everything else! Everything in our bathroom uses no more than 500 watts at most, even if all the lights are on including one over the shower and one is electric shaving at the same time. |
#8
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
what if a person has a 1500, 1800, or 2000 watt hair dryer? Then i guess
your calcs would not work eh? s http://www.amazon.com/BaByliss-BAB20.../dp/B000ASDGK8 "terry" wrote in message ... The way this thread reads is that the previous wiring for the light is still there. The one inch hole is not code compliant; but anyway, why not just leave the light hooked up as before! Separate circuit. If that is not possible, hook up the 14AWG wiring to the mirror light fixture to the 20 amp circuit wired with 12 AWG and change the circuit breaker for the bathroom circuit to 15 amps. Surely 15 amp at 115 volts, a total of 1700 to 1800 watts is sufficient for whole bathroom? Even a hair dryer (plugged into the GFCI of course) will take say a maximum of 1300 watts leaving at least 400 watts for everything else! Everything in our bathroom uses no more than 500 watts at most, even if all the lights are on including one over the shower and one is electric shaving at the same time. |
#9
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
Complicating things more is that the vanity light, and the rest of old
bath circuit was buried in a junction box in the ceiling I found after taking down the sheetrock. So I only have a 3 foot tail out of the vanity, which means I need a junction box if I was to reuse it again. I'm going to give it another shot tonight. Maybe if I'm persistent, I can get the new wire in the box. |
#10
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
On Sep 17, 11:55*am, "Steve Barker DLT"
wrote: what if a person has a 1500, 1800, or 2000 watt hair dryer? *Then i guess your calcs would not work eh? shttp://www.amazon.com/BaByliss-BAB2000-Professional-Ceramix-Xtreme/dp... "terry" wrote in message ... The way this thread reads is that the previous wiring for the light is still there. The one inch hole is not code compliant; but anyway, why not just leave the light hooked up as before! Separate circuit. If that is not possible, hook up the 14AWG wiring to the mirror light fixture to the 20 amp circuit wired with 12 AWG and change the circuit breaker for the bathroom circuit to 15 amps. Surely 15 amp at 115 volts, a total of 1700 to 1800 watts is sufficient for whole bathroom? Even a hair dryer (plugged into the GFCI of course) will take say a maximum of 1300 watts leaving at least 400 watts for everything else! Everything in our bathroom uses no more than 500 watts at most, even if all the lights are on including one over the shower and one is electric shaving at the same time. Ok. Valid point about maximum wattage calculations. But didn't know that North American 115 volt hair dryers come in such high power versions! The only ones have seen here (Canada) have been around 1300 watts IIRC. Maybe am out of date here? Although some Canadian electrical codes occasionally seems to be a bit tougher than USA and UL etc. Only the hair dryers and other appliances I have seen in 230 volt countries seemed to be more powerful and would possibly not North American UL etc. code compliant anyway? You should see how fast a 2 kilowatt kettle, with a few litres of water in it, boils!!!!! Especially when the 230 volts is a bit on the high side! Perhaps 10% or so high; thus instead of wattage proportional to 'Voltage squared'; 230 x 230 = 52,900/R one gets 253 x 253 = 64,009. 64/52.9 = some 21% higher!!!! And yes; 2000 watts is 17.39 amps (2000/115 = 17.39 amps). Since it is a heater with a little fan motor that's mainly resistive. That is a little more than the recommended 80% of the rated 20 amp capacity of a 12 AWG circuit though. i.e. 0.8 x 20 = 16 amps. So 17.39/16.0 = 1.08. That's about 8% over recommended normal load capacity. Although it shouldn't cause any problems provided everything is in good condition and not much else, maybe a couple of light bulbs, is plugged in/switched on on same circuit. Thanks for the comment. Still feel that 115v x 15a = 1725 watts should be plenty for most entire bathrooms! |
#11
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
On Tue, 16 Sep 2008 16:00:37 -0700 (PDT), Mikepier
wrote: I know that you cannot use 14 gauge wire in a 20amp circuit because 14 gauge can only handle 15 amps, but I ran into a problem with my bathroom remodel. I have a huge mirror on one wall that also has a vanity bar light on it that was stuck on the mirror with adhesive. The idiot who put the mirror on did not cut out the box opening, but rather just cut out a 1" hole. The wire feeding behind the mirror is a 14 gauge wire. There is no way I can get a 12 gauge wire inside the box because of the small opening in the mirror. And I can't even use the 14 gauge as a drag line to pull because its clamped in the box, and plus it's fed from the bottom. So my question is being that since the vanity light is the only load that the 14 gauge wire is feeding, any problem with tapping off the new 20A circuit that I ran? I figure the thin wiring inside the vanity would fry first anyway before the 14 gauge would if there was a problem. Otherwise I would have to tear down the mirrored wall to get to the box. If your lighting fixture exceeds 1500 watts, replace the 14g with 12g or select a lower wattage fixture. It is best to have separate outlet and lighting circuits. |
#12
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
just a short comment about your 80% comment. That would only apply if you
use a hair dryer for over 3 hours at a time. The 80% rule is for 'continuous' duty, which is defined as anything over 3 hours at at time. s "terry" wrote in message ... And yes; 2000 watts is 17.39 amps (2000/115 = 17.39 amps). Since it is a heater with a little fan motor that's mainly resistive. That is a little more than the recommended 80% of the rated 20 amp capacity of a 12 AWG circuit though. i.e. 0.8 x 20 = 16 amps. So 17.39/16.0 = 1.08. That's about 8% over recommended normal load capacity. Although it shouldn't cause any problems provided everything is in good condition and not much else, maybe a couple of light bulbs, is plugged in/switched on on same circuit. Thanks for the comment. Still feel that 115v x 15a = 1725 watts should be plenty for most entire bathrooms! |
#13
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
In article , "Steve Barker DLT" wrote:
just a short comment about your 80% comment. That would only apply if you use a hair dryer for over 3 hours at a time. The 80% rule is for 'continuous' duty, which is defined as anything over 3 hours at at time. Close, but no cigar. The Code applies the 80% rule to "continuous load" which it explicitly defines as a load expected to operate _at_maximum_current_ for 3+ hours. |
#14
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
http://www.google.com/products?q=hai...&hl=en&show=dd
Yes, plenty of them. -- Christopher A. Young Learn more about Jesus www.lds.org .. "terry" wrote in message ... But didn't know that North American 115 volt hair dryers come in such high power versions! The only ones have seen here (Canada) have been around 1300 watts IIRC. |
#15
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
Well _THANK YOU_ for splitting that hair.
s "Doug Miller" wrote in message ... In article , "Steve Barker DLT" wrote: just a short comment about your 80% comment. That would only apply if you use a hair dryer for over 3 hours at a time. The 80% rule is for 'continuous' duty, which is defined as anything over 3 hours at at time. Close, but no cigar. The Code applies the 80% rule to "continuous load" which it explicitly defines as a load expected to operate _at_maximum_current_ for 3+ hours. |
#16
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
Well _THANK YOU_ for splitting that hair.
No pun intended? (hair dryer) |
#17
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
In article , "Steve Barker DLT" wrote:
Well _THANK YOU_ for splitting that hair. The point is, that it takes more than just a three-hour duration to invoke the 80% rule. |
#19
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
On Sep 16, 9:57 pm, "Don Young" wrote:
"Mikepier" wrote in message ... I know that you cannot use 14 gauge wire in a 20amp circuit because 14 gauge can only handle 15 amps, but I ran into a problem with my bathroom remodel. I have a huge mirror on one wall that also has a vanity bar light on it that was stuck on the mirror with adhesive. The idiot who put the mirror on did not cut out the box opening, but rather just cut out a 1" hole. The wire feeding behind the mirror is a 14 gauge wire. There is no way I can get a 12 gauge wire inside the box because of the small opening in the mirror. And I can't even use the 14 gauge as a drag line to pull because its clamped in the box, and plus it's fed from the bottom. So my question is being that since the vanity light is the only load that the 14 gauge wire is feeding, any problem with tapping off the new 20A circuit that I ran? I figure the thin wiring inside the vanity would fry first anyway before the 14 gauge would if there was a problem. Otherwise I would have to tear down the mirrored wall to get to the box. If it matters to you, you should know that what you have is not code compliant. All junction and outlet boxes are supposed to be accesssible, and this one obviously isn't. A mirror or other non-removable covering over a box should be cut out to the edges of the boxes and the fixture should cover the opening. Of course, lots of people figure codes are just to make more money for the electricians! Don Young If the light fixture itself is rated as a junction box, then no box is needed in the wall. This usually is the case with fluorescent fixtures into which the cable is led via a small hole; such fixtures have no mounting provision for an octagon box. If the fixture has been made to mount on an octagon box, then of course it ought to have been mounted on one, which would require a much larger hole in the mirror. Assuming the OP is in the US, he might find a solution using the 12/2/2 cable that I hear is available there; use one pair to feed the receptacle on a 20A breaker and the other pair would junction onto the old 14/2 to go to the light on a 15A breaker. A huge waste of copper and he's already pulled 12/2 to the outlet, so this is not an appealing solution, but it might be a consideration for someone else who's facing a similar spot. (If the OP happens to be in Canada, he needs to remember that Canadian code mandates 15A breakers on any circuit containing a lighting fixture, even if it's all wired 12-ga.) To my mind the worst of it is the junction box in the ceiling. That's going to require a cover plate, a monument to the original bad work. Chip C Toronto |
#20
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
On Sep 18, 11:27*am, Kevin Ricks wrote:
wrote: On Wed, 17 Sep 2008 09:02:46 -0700 (PDT), terry wrote: But didn't know that *North American 115 volt hair dryers come in such high power versions! The only ones have seen here (Canada) have been around 1300 watts IIRC. Maybe am out of date here? Although some Canadian electrical codes occasionally seems to be a bit tougher than USA and UL etc. They don't. This is the same creative rating method they use to make 6HP compressors that plug into a 14a receptacle. http://esteroriverheights.com/electr...hair_dryer.jpg Is the meter a true RMS type or averaging (cheap) type? The marketing people will use whichever gives the higher reading. Kevin For the 3 hour explanation. I learnt something. Thanks. Fortunately leaving a low wattage curling iron plugged in plus the short term use of the hair dryer should be fine. Also to my mind there is always difference between something one does temporarily which is 'right at the limit' and something that is not in accordance with code for the long term for use by those who do not understand. For example using a welder intermittently on a too small or too long an extension cord and getting away with it because you have someone else watching. The extension wire is outside in free air and if it did catch fire you immediately disconnect and since you are welding have a fire extinguisher at hand!. Compare that to someone who incompetently hooks up their clothes dryer with wrong AWG and puts pennies in place of blown fuses! Yup seen that! Also seen every appliance in a rural kitchen plugged into the ceiling light socket using a Christmas tree light extension cord! And wondered how with the extension cord getting hot the fridge ever got enough voltage to start! "Yes ma'am that's why the TV goes to about half width each time the well water pump starts". But it's amazing what WILL work at times; just! Was at a home construction area yesterday; three 115 volt extensions across the street, we just drove over them, plugged into one extension box from a completed home! At a glance all thee looked to be the usual 18 or 16 AWG all plugged into another that at best was #12; maybe #14? "Hey boss this skilsaw don't cut too good"! :-) |
#21
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
If the light fixture itself is rated as a junction box, then no box is needed in the wall. This usually is the case with fluorescent fixtures into which the cable is led via a small hole; such fixtures have no mounting provision for an octagon box. If the fixture has been made to mount on an octagon box, then of course it ought to have been mounted on one, which would require a much larger hole in the mirror. The 8 light vanity bar light was adhered to the mirror with mastic or glue. The existing wire comes out of the box, through the hole in the mirror, then out through the fixture hole, which has a grommet. Are you saying I can drill through fixture and mirror opening and into the electrical box to make a hole, then just snake the wire down through this new hole and just let it come out of the fixture the way the existing one is doing now? That might be do-able. |
#22
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
On Sep 18, 11:52 am, Mikepier wrote:
If the light fixture itself is rated as a junction box, then no box is needed in the wall. This usually is the case with fluorescent fixtures into which the cable is led via a small hole; such fixtures have no mounting provision for an octagon box. If the fixture has been made to mount on an octagon box, then of course it ought to have been mounted on one, which would require a much larger hole in the mirror. The 8 light vanity bar light was adhered to the mirror with mastic or glue. The existing wire comes out of the box, through the hole in the mirror, then out through the fixture hole, which has a grommet. Are you saying I can drill through fixture and mirror opening and into the electrical box to make a hole, then just snake the wire down through this new hole and just let it come out of the fixture the way the existing one is doing now? That might be do-able. Well, I don't know about making your own hole in the bar. I'd be more comfortable using it as the manufacturer had it certified. But yeah, as I understand it, if the fixture bar is a totally enclosed box, with a grommeted hole for entry of the romex, then there normally isn't a junction box at all. The cable can run within the wall, out through a hole in the wall (ie, wallboard+mirror), and in through the grommeted hole, which obviously needs to be exactly aligned with the hole in the wall. Then you make the connections to the fixture's internal wiring within the bar, which must be accessible from the front somehow. I've only seen this with fluorescent fixtures but I've never installed a bathroom light bar. Here's a blog from someone who is replacing such a fixture with one that needs a junction box: http://www.hammerzone.com/archives/e...iling4/pvc.htm. In the first picture you can see the cabling emerging from a small hole in the ceiling. This is, I believe, correct, for an appropriate fixture. In this case, there ought not to be (or does not need to be) any junction box in the ceiling at all. CERTAINLY if there is a box there must be no splice made in it, the cable should be continuous all the way back to the prior accessible junction (switch, other fixture, etc.) My guess is that there is a junction box behind the mirror dating from some original over-mirror fixture; and when the new big mirror went up, they spliced a short pigtail within that box and led it through the hole in the new mirror. See if you can push a long nail through the hole and figure out whether there's a box there or not. Chip C Toronto |
#23
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
Mikepier wrote:
.... The 8 light vanity bar light was adhered to the mirror with mastic or glue. The existing wire comes out of the box, through the hole in the mirror, then out through the fixture hole, which has a grommet. Are you saying I can drill through fixture and mirror opening and into the electrical box to make a hole, then just snake the wire down through this new hole and just let it come out of the fixture the way the existing one is doing now? That might be do-able. Too many "the hole"'s...I have no clue what the arrangement is or what the objective is any more from this. But, if the new hole includes a cable clamp that part would be ok. There's no real provision against adding a hole in an existing box, but it'll be a pita to do it by drilling thru some other small hole and highly prone to damaging whatever else is already in there so that part I'd not recommend. IIRC this is an outside wall? What's the siding material? If you're adamant you're not going to take this fixture down and access it that way, if it's simply siding of some sort, going in that way isn't necessarily much worse than drywall. Again, I can't envision what you're trying to do from the above -- a picture somewhere could be worth more than the thousands of words already expended... -- |
#24
Posted to alt.home.repair
|
|||
|
|||
14 and 12 gauge wiring problem
etc.)
My guess is that there is a junction box behind the mirror dating from some original over-mirror fixture; and when the new big mirror went up, they spliced a short pigtail within that box and led it through the hole in the new mirror. See if you can push a long nail through the hole and figure out whether there's a box there or not. Chip C There is a box behind the mirror, I can see it. I wanted to try and push the existing wires inside out of the way, then drill through the grommet hole/fixture/mirror/wallboard and through the box. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
How can I tell if the wires are 14 gauge or 12 gauge? | Home Repair | |||
Can I stick two 4 gauge and one 6 gauge wire into a 3/4" conduit | Home Repair | |||
Peugeot 306 TD fuel gauge and speedo problem | UK diy | |||
Wiring problem | UK diy | |||
wiring problem wioth loop in wiring and two way switching | UK diy |