I am re-wiring my well house. The previous owner had run 12/2 wire (no
ground wire) from a 100 amp breaker on the service panel to a 30 amp
breaker in the yard on a metal stake, then on to the pump house. Along
this run were 2 splices covered with electrical tape. At the well
house he then ran a wire off one leg of the pressure switch and one
wire off the well casing to run a light bulb and heat tape. It looked
like an accident waiting to happen.

The pump motor is: 3450rpm, 3/4HP; Franklin Electric Motor, model
#2445070117, 3/4HP, 1ohm, 230V, 3450rmp, 6.0amp, 2 wire
I plan to use a 60 watt bulb for freeze protection.
The distance to the well from the service entrance is ~65 feet. I plan
to use 12/2 w/gound in conduit (I already have this wire and want to
avoid buying more wire)

Questions:
1. Will a two pole 20amp breaker be sufficient at the service
entrance?
2. If I pull a single 12 gauge wire to the well house, along with the
12/2, can I wire in a 110 circuit for a light?
3. How do I wire the circuit at the well house. Do I need a sub-panel
at the well house with a 20 amp, two pole breaker and a single pole 15
amp breaker?

Wiring to the pump seems straightforward but wiring for a simple light
bulb seems to be adding quite a bit of cost.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 460
Default Wiring for a well house

You need to run a minimum of a 12/3 wire. And technically, you should set a
panel at the well house and treat it as a subpanel with the ground and
neutral isolated from one another.

s


wrote in message
...
I am re-wiring my well house. The previous owner had run 12/2 wire (no
ground wire) from a 100 amp breaker on the service panel to a 30 amp
breaker in the yard on a metal stake, then on to the pump house. Along
this run were 2 splices covered with electrical tape. At the well
house he then ran a wire off one leg of the pressure switch and one
wire off the well casing to run a light bulb and heat tape. It looked
like an accident waiting to happen.

The pump motor is: 3450rpm, 3/4HP; Franklin Electric Motor, model
#2445070117, 3/4HP, 1ohm, 230V, 3450rmp, 6.0amp, 2 wire
I plan to use a 60 watt bulb for freeze protection.
The distance to the well from the service entrance is ~65 feet. I plan
to use 12/2 w/gound in conduit (I already have this wire and want to
avoid buying more wire)

Questions:
1. Will a two pole 20amp breaker be sufficient at the service
entrance?
2. If I pull a single 12 gauge wire to the well house, along with the
12/2, can I wire in a 110 circuit for a light?
3. How do I wire the circuit at the well house. Do I need a sub-panel
at the well house with a 20 amp, two pole breaker and a single pole 15
amp breaker?

Wiring to the pump seems straightforward but wiring for a simple light
bulb seems to be adding quite a bit of cost.



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 233
Default Wiring for a well house

On Sep 10, 10:57 am, wrote:

Wiring to the pump seems straightforward but wiring for a simple light
bulb seems to be adding quite a bit of cost.


Use a 240v light bulb


Or two 120v bulbs in series?

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default Wiring for a well house


wrote in message
...
I am re-wiring my well house. The previous owner had run 12/2 wire (no
ground wire) from a 100 amp breaker on the service panel to a 30 amp
breaker in the yard on a metal stake, then on to the pump house. Along
this run were 2 splices covered with electrical tape. At the well
house he then ran a wire off one leg of the pressure switch and one
wire off the well casing to run a light bulb and heat tape. It looked
like an accident waiting to happen.

The pump motor is: 3450rpm, 3/4HP; Franklin Electric Motor, model
#2445070117, 3/4HP, 1ohm, 230V, 3450rmp, 6.0amp, 2 wire
I plan to use a 60 watt bulb for freeze protection.
The distance to the well from the service entrance is ~65 feet. I plan
to use 12/2 w/gound in conduit (I already have this wire and want to
avoid buying more wire)



*If pulling wire underground it must be rated for a wet location. Ordinary
type NM (Romex) is not. You would need to use type UF or individual
conductors such as THWN. It is easier to pull individual conductors into a
conduit.


Questions:
1. Will a two pole 20amp breaker be sufficient at the service
entrance?


*Yes

2. If I pull a single 12 gauge wire to the well house, along with the
12/2, can I wire in a 110 circuit for a light?



*No. All of the conductors should be in the same cable.


3. How do I wire the circuit at the well house. Do I need a sub-panel
at the well house with a 20 amp, two pole breaker and a single pole 15
amp breaker?



*I Think that you will be better off pulling in four #10's and putting a
sub-panel at the well house. That way you can have power for your pump with
less voltage drop and power for lighting and a 120 volt GFI receptacle for
servicing purposes.


Wiring to the pump seems straightforward but wiring for a simple light
bulb seems to be adding quite a bit of cost.



*Labor will be your biggest expense. That wire needs to be at least 18"
deep in the ground.

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default Wiring for a well house

I am re-wiring my well house. The previous owner had run 12/2 wire (no
ground wire) from a 100 amp breaker on the service panel to a 30 amp
breaker in the yard on a metal stake, then on to the pump house. Along
this run were 2 splices covered with electrical tape.

SM: 100 amp breaker feeding 12 gage wire is a bit over capacity. 12 ga is
rated for 20 amps.

At the well
house he then ran a wire off one leg of the pressure switch and one
wire off the well casing to run a light bulb and heat tape. It looked
like an accident waiting to happen.

SM: I'm with you. Though, it probably worked fine for many years.

The pump motor is: 3450rpm, 3/4HP; Franklin Electric Motor, model
#2445070117, 3/4HP, 1ohm, 230V, 3450rmp, 6.0amp, 2 wire
I plan to use a 60 watt bulb for freeze protection.
The distance to the well from the service entrance is ~65 feet. I plan
to use 12/2 w/gound in conduit (I already have this wire and want to
avoid buying more wire)

SM: Yep, wire is expensive. Your 12-2 should feed your 6 amp pump just fine.

Questions:
1. Will a two pole 20amp breaker be sufficient at the service
entrance?

SM: Yes, that should drive your 6 amp motor just fine.

2. If I pull a single 12 gauge wire to the well house, along with the
12/2, can I wire in a 110 circuit for a light?

SM: A black colored stranded wire sounds good. Make the two blacks hot, and
the white a neutral.

3. How do I wire the circuit at the well house. Do I need a sub-panel
at the well house with a 20 amp, two pole breaker and a single pole 15
amp breaker?

SM: I'd want a disconnect switch for when you or someone else is working on
the equipment.

Wiring to the pump seems straightforward but wiring for a simple light
bulb seems to be adding quite a bit of cost.

SM: Do some net search, see if you can find 220 volt light bulbs. Skip the
110 volt sub circuit.
http://www.google.com/products?hl=en...-8&sa=N&tab=wf


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
whole house fan wiring lilo Home Repair 6 July 9th 08 05:22 PM
House wiring question. Ook Home Repair 26 December 28th 06 08:49 PM
New house wiring Jungle Jim Home Ownership 11 August 9th 05 12:19 AM
connecting ceiling fan to older house- 70 year old house. need help with wiring colors KOS Home Repair 8 July 18th 05 03:47 PM
Is it legal to DIY house wiring? PG UK diy 38 January 22nd 05 05:46 PM


All times are GMT +1. The time now is 11:54 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"