Default GFCI outlets required with a GFCI Breaker?

Redoing my bathroom and I purchased GFCI outlets for the walls. But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. Does standard practice or the NEC require both? Or is that
overdoing it?

-Theodore
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 25
Default GFCI outlets required with a GFCI Breaker?

On Jul 15, 3:10*pm, wrote:
Redoing my bathroom and I purchased GFCI outlets for the walls. *But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. *Does standard practice or the NEC require both? Or is that
overdoing it?

-Theodore


Per NEC 2005, 550.13 (B) - a GFCI outlet is not required in a bathroom
if the feeder supplying the branch circuit is protected by a ground-
fault circuit-interrupter.

I like put the stickers on the outlet that say "GFCI Protected" when
my protection is at the feeder.

BRW
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default GFCI outlets required with a GFCI Breaker?


"metspitzer" wrote in message
...
On Tue, 15 Jul 2008 22:09:19 -0400, "RBM" wrote:


"mm" wrote in message
. ..
On Tue, 15 Jul 2008 18:26:56 -0400, "RBM" wrote:


"mm" wrote in message
m...
On Tue, 15 Jul 2008 12:10:06 -0700 (PDT), wrote:

Redoing my bathroom and I purchased GFCI outlets for the walls. But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. Does standard practice or the NEC require both? Or is that
overdoing it?

Not needed. My house was built with one GFI breaker for the bathroom
outlets, the kitchen sink outlets, and the outdoor outlets.

-Theodore

All those outlets are on one GF breaker?

Yeah. I think the kitchen sink would be on it, at least. There is
no other GFI in the house, or the other 108 houses like mine.

I never use any of the outlets though, except the one in the kitchen,
which I really only use for a radio, and sometimes two light bulbs
under the cabinet.

Lately I've been using one in the bathroom for an electric toothbrush
which takes almost no current, and a 12" tv, which uses some.


I question that because there was never a time in NEC history, when
Kitchen counter outlets and bathroom outlets or outside outlets could
legally be protected by the same GF breaker



The restriction you are talking about is that kitchen outlets can
serve no other parts of the house. Correct?

Anything else in and around the house can share GFCI protection.


Correct, circuits for kitchen outlets can serve dining room outlets but no
others. Today, bathroom circuits can't serve any other outlets, but other
bathrooms


  #10   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default GFCI outlets required with a GFCI Breaker?

On Tue, 15 Jul 2008 22:09:19 -0400, "RBM" wrote:


"mm" wrote in message
.. .
On Tue, 15 Jul 2008 18:26:56 -0400, "RBM" wrote:


"mm" wrote in message
...
On Tue, 15 Jul 2008 12:10:06 -0700 (PDT), wrote:

Redoing my bathroom and I purchased GFCI outlets for the walls. But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. Does standard practice or the NEC require both? Or is that
overdoing it?

Not needed. My house was built with one GFI breaker for the bathroom
outlets, the kitchen sink outlets, and the outdoor outlets.

-Theodore

All those outlets are on one GF breaker?


Yeah. I think the kitchen sink would be on it, at least. There is
no other GFI in the house, or the other 108 houses like mine.

I never use any of the outlets though, except the one in the kitchen,
which I really only use for a radio, and sometimes two light bulbs
under the cabinet.

Lately I've been using one in the bathroom for an electric toothbrush
which takes almost no current, and a 12" tv, which uses some.


I question that because there was never a time in NEC history, when
Kitchen counter outlets and bathroom outlets or outside outlets could
legally be protected by the same GF breaker


I had trouble finding your reply because it had in front of it.
How did that happen!!!


Maybe I'm wrong about the kitchen outlets. I may never have confirmed
it.

But since I only have one GFI anything, and I thought the outlet in
the kitchen nearest the sink had to be GFI'd, even in 1979, (Don't
they?) I figured it was on the same GFI.

I know for sure that the front outdoor outlet is on the GFI breaker,
and I know for sure that the outlet in the bathroom with the bathtub
is on the same breaker. Is that against code?

I haven't checked the outlets in the other bathrooms or the powder
room, because I guess, I almost never use them, and they've always
worked.

I haven't checked the one close to the basement sink, into which is
plugged the washing machine.

That's not readily accessible, because I do have a washing machine and
it's in front of the outlet, but is that supposed to be GFIed. (It's
always worked.)


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,341
Default GFCI outlets required with a GFCI Breaker?

On Tue, 15 Jul 2008 22:09:19 -0400, "RBM" wrote:


"mm" wrote in message
.. .
On Tue, 15 Jul 2008 18:26:56 -0400, "RBM" wrote:


"mm" wrote in message
...
On Tue, 15 Jul 2008 12:10:06 -0700 (PDT), wrote:

Redoing my bathroom and I purchased GFCI outlets for the walls. But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. Does standard practice or the NEC require both? Or is that
overdoing it?

Not needed. My house was built with one GFI breaker for the bathroom
outlets, the kitchen sink outlets, and the outdoor outlets.

-Theodore

All those outlets are on one GF breaker?


Yeah. I think the kitchen sink would be on it, at least. There is
no other GFI in the house, or the other 108 houses like mine.

I never use any of the outlets though, except the one in the kitchen,
which I really only use for a radio, and sometimes two light bulbs
under the cabinet.

Lately I've been using one in the bathroom for an electric toothbrush
which takes almost no current, and a 12" tv, which uses some.


I question that because there was never a time in NEC history, when
Kitchen counter outlets and bathroom outlets or outside outlets could
legally be protected by the same GF breaker



The restriction you are talking about is that kitchen outlets can
serve no other parts of the house. Correct?

Anything else in and around the house can share GFCI protection.
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default GFCI outlets required with a GFCI Breaker?


"mm" wrote in message
...
On Tue, 15 Jul 2008 22:09:19 -0400, "RBM" wrote:


"mm" wrote in message
. ..
On Tue, 15 Jul 2008 18:26:56 -0400, "RBM" wrote:


"mm" wrote in message
m...
On Tue, 15 Jul 2008 12:10:06 -0700 (PDT), wrote:

Redoing my bathroom and I purchased GFCI outlets for the walls. But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. Does standard practice or the NEC require both? Or is that
overdoing it?

Not needed. My house was built with one GFI breaker for the bathroom
outlets, the kitchen sink outlets, and the outdoor outlets.

-Theodore

All those outlets are on one GF breaker?

Yeah. I think the kitchen sink would be on it, at least. There is
no other GFI in the house, or the other 108 houses like mine.

I never use any of the outlets though, except the one in the kitchen,
which I really only use for a radio, and sometimes two light bulbs
under the cabinet.

Lately I've been using one in the bathroom for an electric toothbrush
which takes almost no current, and a 12" tv, which uses some.


I question that because there was never a time in NEC history, when
Kitchen counter outlets and bathroom outlets or outside outlets could
legally be protected by the same GF breaker


I had trouble finding your reply because it had in front of it.
How did that happen!!!


Maybe I'm wrong about the kitchen outlets. I may never have confirmed
it.

But since I only have one GFI anything, and I thought the outlet in
the kitchen nearest the sink had to be GFI'd, even in 1979, (Don't
they?) I figured it was on the same GFI.

I know for sure that the front outdoor outlet is on the GFI breaker,
and I know for sure that the outlet in the bathroom with the bathtub
is on the same breaker. Is that against code?

I haven't checked the outlets in the other bathrooms or the powder
room, because I guess, I almost never use them, and they've always
worked.

I haven't checked the one close to the basement sink, into which is
plugged the washing machine.

That's not readily accessible, because I do have a washing machine and
it's in front of the outlet, but is that supposed to be GFIed. (It's
always worked.)


I believe in 1979 outlets on either side of kitchen sink , within six feet
of the sink were required to be GF protected, but they would be 20 amp
circuits. It was typical to have bathroom outlets, outside outlets, and
possibly garage outlets, on one circuit, protected by either a GF breaker,
or the first outlet in the string, usually nearest the panel, would be a
GFCI


  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 199
Default GFCI outlets required with a GFCI Breaker?

On Tue, 15 Jul 2008 12:10:06 -0700, millinghill wrote:

Redoing my bathroom and I purchased GFCI outlets for the walls. But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. Does standard practice or the NEC require both? Or is that
overdoing it?

-Theodore


I did a remodel once and the building inspector approved a GFCI breaker
instead of outlets. It was the easiest way at the time to deal with
multiple GFCI requirements.



--

=================================================
Franz Fripplfrappl
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14
Default GFCI outlets required with a GFCI Breaker?

wrote:
Redoing my bathroom and I purchased GFCI outlets for the walls. But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. Does standard practice or the NEC require both? Or is that
overdoing it?

-Theodore


Use one or the other. It does no particular harm to have both, but if
one trips, it is much more trouble to figure out which and reset it.

It has been common practice until recently to use a single CGI breaker,
or even a single GFI outlet to protect all the kitchen, bathroom,
garage, and outdoor outlets. This is no longer allowed.

If you are remodeling the bathroom, the right way to do it is to run a
new 20a feed from the panel for the bathroom alone. You can put the GFI
in the panel or at the outlets, but I would put it at the outlet for
convenience. One GFI can protect other outlets downstream, or each
outlet can have its own GFI, as you prefer, for convenience. Read the
instructions and follow the diagram that comes with each GFI for more
information on how to wire it.

Each "ordinary" outlet that is protected by a GFI located elsewhere,
whether at another outlet or in the panel should be labeled "GFCI
protected". Most GFIs come with these labels packed in the box.

If you are not doing a remodel, but just replacing the outlets, you can
keep the existing GFI breaker and use appropriately-labeled regular
outlets. You can also replace the GFI breaker with a non-GFI breaker and
protect the bathroom outlets with one GFI at the "first" outlet. If you
replace the GFI breaker with a non-GFI breaker, make sure it is not also
protecting other outlets that require GFI protection, such as another
bathroom, basement, kitchen, garage, or outdoors.
** Posted from
http://www.teranews.com **


  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default GFCI outlets required with a GFCI Breaker?

On Aug 3, 3:14*am, Tony wrote:
wrote:
Redoing my bathroom and I purchased GFCI outlets for the walls. *But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. *Does standard practice or the NEC require both? Or is that
overdoing it?


-Theodore


Use one or the other. It does no particular harm to have both, but if
one trips, it is much more trouble to figure out which and reset it.

It has been common practice until recently to use a single CGI breaker,
or even a single GFI outlet to protect all the kitchen, bathroom,
garage, and outdoor outlets. This is no longer allowed.


I don't know what your definition of "recently" is, but around here it
would be hard to find a house with all of the above wired onto a
single circuit of any kind.





If you are remodeling the bathroom, the right way to do it is to run a
new 20a feed from the panel for the bathroom alone. You can put the GFI
in the panel or at the outlets, but I would put it at the outlet for
convenience. One GFI can protect other outlets downstream, or each
outlet can have its own GFI, as you prefer, for convenience. Read the
instructions and follow the diagram that comes with each GFI for more
information on how to wire it.

Each "ordinary" outlet that is protected by a GFI located elsewhere,
whether at another outlet or in the panel should be labeled "GFCI
protected". Most GFIs come with these labels packed in the box.

If you are not doing a remodel, but just replacing the outlets, you can
keep the existing GFI breaker and use appropriately-labeled regular
outlets. You can also replace the GFI breaker with a non-GFI breaker and
protect the bathroom outlets with one GFI at the "first" outlet. If you
replace the GFI breaker with a non-GFI breaker, make sure it is not also
protecting other outlets that require GFI protection, such as another
bathroom, basement, kitchen, garage, or outdoors.
** Posted fromhttp://www.teranews.com**


  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14
Default GFCI outlets required with a GFCI Breaker?

wrote:
On Aug 3, 3:14 am, Tony wrote:
wrote:
Redoing my bathroom and I purchased GFCI outlets for the walls. But I
just realized that the bathroom, as a whole, is on a GFCI circuit
breaker. Does standard practice or the NEC require both? Or is that
overdoing it?
-Theodore

Use one or the other. It does no particular harm to have both, but if
one trips, it is much more trouble to figure out which and reset it.

It has been common practice until recently to use a single CGI breaker,
or even a single GFI outlet to protect all the kitchen, bathroom,
garage, and outdoor outlets. This is no longer allowed.


I don't know what your definition of "recently" is, but around here it
would be hard to find a house with all of the above wired onto a
single circuit of any kind.


I can't tell you which edition of the NEC started to change those rules.
It didn't happen all at once. It has probably been at least 10 years,
but probably not more than 20. I have seen plenty of this kind of thing.

The phone call goes like this: "All the circuits are dead in my
bathrooms." "How about the garage and outdoor outlets." "Oh my goodness,
yes, those are broken, too." "Go see if you have a GFI outlet in your
garage." "What's that?" "It looks like an outlet, except it has two
buttons on the front." "OK, I found one -- what's it for?" "I can
explain, but first why not go push the reset button." "I have to go get
my other glasses, I can't read the label. -- Oh! My bathroom outlet is
working! What is going on!" Etc, for half an hour.

It was either that, or charge her $70 to drive over there and reset that
GFI. I can tell you that after working up numerous quotes to run new
feeders to the kitchen, bathroom, and garage, I never made a sale from
fixing that problem.
** Posted from
http://www.teranews.com **
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI outlets - how many test/reset cycles are too many? DA Home Repair 12 February 4th 08 07:22 AM
Undermounting GFCI outlets from Kitchen Cabinets [email protected] Home Repair 4 December 24th 07 10:48 PM
Outdoor outlets and GFCI Percival P. Cassidy Home Repair 10 November 28th 06 08:16 AM
GFCI outlets in kitchen chester Home Repair 10 March 4th 05 09:48 PM
GFCI outlets vs. GFCI breakers? Alan Beagley Home Repair 10 October 30th 03 05:44 PM


All times are GMT +1. The time now is 02:13 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"