How do you tell if you have 60 amp or 100 amp service?

The wiring in the service cable is aluminum. What sizes
would be 60 amp and what would be 100 amp?

I have an old size fusebox, with main on the left
side and range on the right side. While right now
there are 4 of the long 60 amp fuses in the fuse box,
am I correct that probably the correct numbers should
be 60 amp in the main and 40 amp in the range for a total
of 100 amps--and that this is probably a 100 amp service?

--
Jonathan Grobe Books
Browse our inventory of thousands of used books at:
http://www.grobebooks.com

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 254
Default How do you tell if you have 60 amp or 100 amp service?

On May 29, 12:59 am, Jonathan Grobe wrote:
How do you tell if you have 60 amp or 100 amp service?

The wiring in the service cable is aluminum. What sizes
would be 60 amp and what would be 100 amp?

I have an old size fusebox, with main on the left
side and range on the right side. While right now
there are 4 of the long 60 amp fuses in the fuse box,
am I correct that probably the correct numbers should
be 60 amp in the main and 40 amp in the range for a total
of 100 amps--and that this is probably a 100 amp service?

--
Jonathan Grobe Books
Browse our inventory of thousands of used books at:http://www.grobebooks.com


My guess (non professional) is 60A.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default How do you tell if you have 60 amp or 100 amp service?


"Jonathan Grobe" wrote in message
...
How do you tell if you have 60 amp or 100 amp service?

The wiring in the service cable is aluminum. What sizes
would be 60 amp and what would be 100 amp?

I have an old size fusebox, with main on the left
side and range on the right side. While right now
there are 4 of the long 60 amp fuses in the fuse box,
am I correct that probably the correct numbers should
be 60 amp in the main and 40 amp in the range for a total
of 100 amps--and that this is probably a 100 amp service?

--
Jonathan Grobe Books
Browse our inventory of thousands of used books at:
http://www.grobebooks.com


You are correct. The service entrance cable will determine the service size.
If it is aluminum, it should be #2, if it's copper #4. Anything smaller
would be a 60 amp service



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 26
Default How do you tell if you have 60 amp or 100 amp service?

On 2008-05-29, RBM wrote:

You are correct. The service entrance cable will determine the service size.
If it is aluminum, it should be #2, if it's copper #4. Anything smaller
would be a 60 amp service

What is the diameter of #2 aluminum?

--
Jonathan Grobe Books
Browse our inventory of thousands of used books at:
http://www.grobebooks.com

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default How do you tell if you have 60 amp or 100 amp service?

On May 29, 12:12�pm, Jonathan Grobe wrote:
On 2008-05-29, RBM wrote:

You are correct. The service entrance cable will determine the service size.
If it is aluminum, it should be #2, if it's copper #4. Anything smaller
would be a 60 amp service


What is the diameter of #2 aluminum?

--
Jonathan Grobe Books �
Browse our inventory of thousands of used books at:http://www.grobebooks.com


theres a chance of a miss match, like a undersized meter socket.......

my bet 60 amps....

might as well upgrade once to 200 amps........


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default How do you tell if you have 60 amp or 100 amp service?

On May 29, 1:59*am, Jonathan Grobe wrote:
How do you tell if you have 60 amp or 100 amp service?

The wiring in the service cable is aluminum. What sizes
would be 60 amp and what would be 100 amp?

I have an old size fusebox, with main on the left
side and range on the right side. While right now
there are 4 of the long 60 amp fuses in the fuse box,
am I correct that probably the correct numbers should
be 60 amp in the main and 40 amp in the range for a total
of 100 amps--and that this is probably a 100 amp service?

--
Jonathan Grobe Books *
Browse our inventory of thousands of used books at:http://www.grobebooks.com


I'm not too familiar with fuse boxes, but in a typical breaker box,
the main breaker is sized to match the size of the service. If my main
breaker (the one at the top of the box that would kill the entire
house if thrown) is labeled as 150A, then I have a 150A service.

I don't think you'd have a service wire size that was rated higher by
any great extent than the main breaker (or fuse in your case) and
you'd better not have a service wire size that was rated lower.

Do fuse boxes not have a "main fuse" for the entire system?
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default How do you tell if you have 60 amp or 100 amp service?

Jonathan Grobe wrote:
On 2008-05-29, RBM wrote:


You are correct. The service entrance cable will determine the service size.
If it is aluminum, it should be #2, if it's copper #4. Anything smaller
would be a 60 amp service


What is the diameter of #2 aluminum?


#2 wire is about 0.097" diameter.

Sounds like a "main and range" panel with both "main" and "range" being
service disconnects (the range circuit will still be hot if you pull out
the "main" fuses). I believe these all had a rating of 100A. You can
use 60A fuses in both the "main" and "range" (but you may want to limit
the range to 40). (If a calculation of the proper size of the service
for the house is 100A the fuses can all be 60A.)

--
bud--
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 26
Default How do you tell if you have 60 amp or 100 amp service?

Do electric companies always know what service you have?

--
Jonathan Grobe Books
Browse our inventory of thousands of used books at:
http://www.grobebooks.com

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default How do you tell if you have 60 amp or 100 amp service?


"Jonathan Grobe" wrote in message
...
Do electric companies always know what service you have?

--
Jonathan Grobe Books
Browse our inventory of thousands of used books at:
http://www.grobebooks.com


No, they don't. They only know how much you use. They may have a record of
the size meter you have, but any newer installation would use a 4 or 5 jaw
meter good for 200 amps. I don't know, offhand the circular mils of a #2
aluminum conductor, but even if you had that info, it probably won't help.
The cable should have the numbers written on it's sheath. It would say
something like 2-2-4 al




  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default How do you tell if you have 60 amp or 100 amp service?


"DerbyDad03" wrote in message
...
On May 29, 1:59 am, Jonathan Grobe wrote:
How do you tell if you have 60 amp or 100 amp service?

The wiring in the service cable is aluminum. What sizes
would be 60 amp and what would be 100 amp?

I have an old size fusebox, with main on the left
side and range on the right side. While right now
there are 4 of the long 60 amp fuses in the fuse box,
am I correct that probably the correct numbers should
be 60 amp in the main and 40 amp in the range for a total
of 100 amps--and that this is probably a 100 amp service?

--
Jonathan Grobe Books
Browse our inventory of thousands of used books
at:http://www.grobebooks.com


I'm not too familiar with fuse boxes, but in a typical breaker box,
the main breaker is sized to match the size of the service. If my main
breaker (the one at the top of the box that would kill the entire
house if thrown) is labeled as 150A, then I have a 150A service.

I don't think you'd have a service wire size that was rated higher by
any great extent than the main breaker (or fuse in your case) and
you'd better not have a service wire size that was rated lower.

Do fuse boxes not have a "main fuse" for the entire system?

His particular fuse box has two main disconnects, and it was common for
split buss breaker panels to have up to six main disconnects. The common
misconception is that the total amperage of the main disconnects cannot
exceed the rating of the service entrance cables. Theoretically you can have
a 200 amp service with six 100 amp main disconnects.


  #12   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default How do you tell if you have 60 amp or 100 amp service?

Jonathan Grobe wrote:
On 2008-05-29, RBM wrote:
You are correct. The service entrance cable will determine the service size.
If it is aluminum, it should be #2, if it's copper #4. Anything smaller
would be a 60 amp service

What is the diameter of #2 aluminum?


#2 is #2, whether it's Al or Cu -- it's the wire gauge and the gauge is
independent of material. Only the conductivity of Cu is better than Al
so can use smaller gauge wire compared to Cu for the same ampacity.

That said, #2 is roughly 0.25" diameter. See following link for table
of AWG dimensions.

http://www.rbeelectronics.com/wtable.htm

--




  #13   Report Post  
Posted to alt.home.repair
CJT CJT is offline
external usenet poster
 
Posts: 1,155
Default How do you tell if you have 60 amp or 100 amp service?

bud-- wrote:
Jonathan Grobe wrote:

On 2008-05-29, RBM wrote:



You are correct. The service entrance cable will determine the
service size. If it is aluminum, it should be #2, if it's copper #4.
Anything smaller would be a 60 amp service



What is the diameter of #2 aluminum?


#2 wire is about 0.097" diameter.


Huh?

Sounds like a "main and range" panel with both "main" and "range" being
service disconnects (the range circuit will still be hot if you pull out
the "main" fuses). I believe these all had a rating of 100A. You can
use 60A fuses in both the "main" and "range" (but you may want to limit
the range to 40). (If a calculation of the proper size of the service
for the house is 100A the fuses can all be 60A.)


You'd better at least consider the size of the wire downstream of the
breaker before making such claims.


--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default How do you tell if you have 60 amp or 100 amp service?

bud-- wrote:
Jonathan Grobe wrote:
On 2008-05-29, RBM wrote:


You are correct. The service entrance cable will determine the
service size. If it is aluminum, it should be #2, if it's copper #4.
Anything smaller would be a 60 amp service


What is the diameter of #2 aluminum?


#2 wire is about 0.097" diameter.



Oops, read the wrong column. #2 wire (conductor - stranded) is about
0.292" diameter. This is reasonable compared to dpb's value of "roughly
0.25" which may be solid wire.

--
bud--
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
ATTN: Renaud your HP 8116A service manual - "HP8116A Service.pdf" (19/33) 9.5 MBytes yEnc JW Electronic Schematics 0 January 2nd 08 10:57 AM
ATTN: Renaud your HP 8116A service manual - "HP8116A Service.pdf" (18/33) 9.5 MBytes yEnc JW Electronic Schematics 0 January 2nd 08 10:57 AM
ATTN: Renaud your HP 8116A service manual - "HP8116A Service.pdf" (17/33) 9.5 MBytes yEnc JW Electronic Schematics 0 January 2nd 08 10:57 AM
ATTN: Renaud your HP 8116A service manual - "HP8116A Service.pdf" (11/33) 9.5 MBytes yEnc JW Electronic Schematics 0 January 2nd 08 10:57 AM
Olympus V-90 Digital Voice Recorder. Service manual or advice to enter its service mode Peter Electronics Repair 0 February 9th 05 06:07 PM


All times are GMT +1. The time now is 02:33 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"