Default Bathroom exhaust fan sizing

I am trying to size my bathroom exhaust fan. Most sizing chart says to use
the SQFT size and multiply by 1.1 to get the CFM if ceiling is standard 8'.
So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the fan on
and the bathroom door open right? So it's drawing the air in the bath PLUS
the air from outside the bath. Would it be a good rule of thumb to
overshoot the 1.1 multiplier? or that already have a safety factor
built-in?

Thanks,

MC


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8
Default Bathroom exhaust fan sizing

However when you use finish using your bath typically you have the fan on
and the bathroom door open right? *So it's drawing the air in the bath PLUS
the air from outside the bath. *Would it be a good rule of thumb to


Be careful if there is also a connection to a chimney in the rooms
from which it draws air! It works against the pressure pushing smoke
up and sucks CO2, CO, dust, and whatever is produced by your heating
into your living room.

I recommend to ask a chimney sweep. In my apartment there is a small
fan blowing air into the chimney. Our chimney sweep told us not to
enlarge it since it might blow smoke and poisonous gas into the other
apartments.

virtuPIC
--
Airspace V - international hangar flying!
http://www.airspace-v.com/ggadgets for tools & toys
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default Bathroom exhaust fan sizing

On May 6, 1:26*am, "MiamiCuse" wrote:
I am trying to size my bathroom exhaust fan. *Most sizing chart says to use
the SQFT size and multiply by 1.1 to get the CFM if ceiling is standard 8'..
So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the fan on
and the bathroom door open right? *So it's drawing the air in the bath PLUS
the air from outside the bath. *Would it be a good rule of thumb to
overshoot the 1.1 multiplier? *or that already have a safety factor
built-in?

Thanks,

MC


Most manufacturers assume that you'll be drawing air from room or a
window anyaway, so its built in to the calculations.
It also depends how you duct it, and how far away the fan has to push
the air to the outside. Rigid duct is a little better than flex duct,
but don't go out of your way if the run is short.
For a 10X10 room, 100CFM is fine, but like others said noise is a
factor, so look into quiet fans like Panasonic
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,489
Default Bathroom exhaust fan sizing

On Tue, 6 May 2008 01:26:14 -0400, "MiamiCuse"
wrote:

I am trying to size my bathroom exhaust fan. Most sizing chart says to use
the SQFT size and multiply by 1.1 to get the CFM if ceiling is standard 8'.
So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the fan on
and the bathroom door open right? So it's drawing the air in the bath PLUS
the air from outside the bath. Would it be a good rule of thumb to
overshoot the 1.1 multiplier? or that already have a safety factor
built-in?

Thanks,

MC



There's nothing wrong with a more powerful fan, other than the noise.
The faster you can dry your shower, the less chance of mold/mildew.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 343
Default Bathroom exhaust fan sizing

Joseph Meehan wrote:
"MiamiCuse" wrote in message
...
I am trying to size my bathroom exhaust fan. Most sizing chart says
to use the SQFT size and multiply by 1.1 to get the CFM if ceiling is
standard 8'. So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the fan
on and the bathroom door open right? So it's drawing the air in the
bath PLUS the air from outside the bath. Would it be a good rule of
thumb to overshoot the 1.1 multiplier? or that already have a safety
factor built-in?

Thanks,

MC


No additional factoring needed. They are measuring room air changes
per time. The make up air will come from somewhere like the heat vent,
open door or window etc.

Basically physics says you can't draw air out of the room with out
air coming into the room at the same time, even with the door closed air
has to come in from somewhere (like around the door or cold air return).



Many bathroom doors are cut a little short on the bottom to let air into
the room just because of exhaust fans.

Lou


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11,538
Default Bathroom exhaust fan sizing

MiamiCuse wrote:
I am trying to size my bathroom exhaust fan. Most sizing chart says
to use the SQFT size and multiply by 1.1 to get the CFM if ceiling is
standard 8'. So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the
fan on and the bathroom door open right? So it's drawing the air in
the bath PLUS the air from outside the bath. Would it be a good rule
of thumb to overshoot the 1.1 multiplier? or that already have a
safety factor built-in?


Good thinking. If I were you, I'd also consider the humidity of the existing
air modified by the presumably less-humid replacement air. Then, too,
there's the temperature of the air to consider. Of course this gets
complicated inasmuch as the relative humidity of the bathroom's air goes
down quite dramatically (usually). That's for a bath.

On the other hand, if trying to remove offensive odors, there's a table
somewhere of bean consumption vs time vs CFM necessary to purge the space
down to the undetectable levels.

Plus, individual levels of acceptable humidity, odors, noise, and cost have
to be factored in.


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default Bathroom exhaust fan sizing


Phisherman wrote:

On Tue, 6 May 2008 01:26:14 -0400, "MiamiCuse"
wrote:

I am trying to size my bathroom exhaust fan. Most sizing chart says to use
the SQFT size and multiply by 1.1 to get the CFM if ceiling is standard 8'.
So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the fan on
and the bathroom door open right? So it's drawing the air in the bath PLUS
the air from outside the bath. Would it be a good rule of thumb to
overshoot the 1.1 multiplier? or that already have a safety factor
built-in?

Thanks,

MC


There's nothing wrong with a more powerful fan, other than the noise.
The faster you can dry your shower, the less chance of mold/mildew.


Along the same lines, and avoiding the noise issue, you can install a
larger central ventilator fan that installs in the attic and has flex
ducts running from it to multiple bathrooms, kitchen, laundry, etc.
Since the fan is remote from the room there is less noise.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 89
Default Bathroom exhaust fan sizing


"Pete C." wrote in message
...

Phisherman wrote:

On Tue, 6 May 2008 01:26:14 -0400, "MiamiCuse"
wrote:

I am trying to size my bathroom exhaust fan. Most sizing chart says to
use
the SQFT size and multiply by 1.1 to get the CFM if ceiling is standard
8'.
So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the fan
on
and the bathroom door open right? So it's drawing the air in the bath
PLUS
the air from outside the bath. Would it be a good rule of thumb to
overshoot the 1.1 multiplier? or that already have a safety factor
built-in?

Thanks,

MC


There's nothing wrong with a more powerful fan, other than the noise.
The faster you can dry your shower, the less chance of mold/mildew.


Along the same lines, and avoiding the noise issue, you can install a
larger central ventilator fan that installs in the attic and has flex
ducts running from it to multiple bathrooms, kitchen, laundry, etc.
Since the fan is remote from the room there is less noise.



I'm wanting to do this too but I am concerned about ejecting too much of the
air I payed to heat or cool. A simple central fan will draw lots of air
from several ducts (depending on how many baths you have) and that could
eject several hundred CFM of heated air which you will just need to heat
again. Might as well leave a window open as far as the heater is concerned.

Sizing a fan close to what you need and having each fan controlled for a
single bath is more energy efficient depending on your climate and time of
year. Use a timer switch to operate the fan for convenience. Variable
speed would be nice as would automatic baffels to select which rooms are
ventilated. A well designed central ventilator can be efficient, you just
need to buy all the accessories.


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default Bathroom exhaust fan sizing


pipedown wrote:

"Pete C." wrote in message
...

Phisherman wrote:

On Tue, 6 May 2008 01:26:14 -0400, "MiamiCuse"
wrote:

I am trying to size my bathroom exhaust fan. Most sizing chart says to
use
the SQFT size and multiply by 1.1 to get the CFM if ceiling is standard
8'.
So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the fan
on
and the bathroom door open right? So it's drawing the air in the bath
PLUS
the air from outside the bath. Would it be a good rule of thumb to
overshoot the 1.1 multiplier? or that already have a safety factor
built-in?

Thanks,

MC


There's nothing wrong with a more powerful fan, other than the noise.
The faster you can dry your shower, the less chance of mold/mildew.


Along the same lines, and avoiding the noise issue, you can install a
larger central ventilator fan that installs in the attic and has flex
ducts running from it to multiple bathrooms, kitchen, laundry, etc.
Since the fan is remote from the room there is less noise.


I'm wanting to do this too but I am concerned about ejecting too much of the
air I payed to heat or cool. A simple central fan will draw lots of air
from several ducts (depending on how many baths you have) and that could
eject several hundred CFM of heated air which you will just need to heat
again. Might as well leave a window open as far as the heater is concerned.

Sizing a fan close to what you need and having each fan controlled for a
single bath is more energy efficient depending on your climate and time of
year. Use a timer switch to operate the fan for convenience. Variable
speed would be nice as would automatic baffels to select which rooms are
ventilated. A well designed central ventilator can be efficient, you just
need to buy all the accessories.


Variable speed heat recovery central ventilator zoned with humidistats
in each served room...
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,946
Default Bathroom exhaust fan sizing

LouB wrote in :

Joseph Meehan wrote:
"MiamiCuse" wrote in message
...
I am trying to size my bathroom exhaust fan. Most sizing chart says
to use the SQFT size and multiply by 1.1 to get the CFM if ceiling
is standard 8'. So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the
fan on and the bathroom door open right? So it's drawing the air in
the bath PLUS the air from outside the bath. Would it be a good
rule of thumb to overshoot the 1.1 multiplier? or that already have
a safety factor built-in?

Thanks,

MC


No additional factoring needed. They are measuring room air
changes
per time. The make up air will come from somewhere like the heat
vent, open door or window etc.

Basically physics says you can't draw air out of the room with out
air coming into the room at the same time, even with the door closed
air has to come in from somewhere (like around the door or cold air
return).



Many bathroom doors are cut a little short on the bottom to let air
into the room just because of exhaust fans.

Lou


As far as I know, all interior doors should have a 1/2-3/4" gap on the
bottom for air circulation if you have forced air HVAC.


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 43
Default Bathroom exhaust fan sizing

On May 6, 6:26 am, "MiamiCuse" wrote:
I am trying to size my bathroom exhaust fan. Most sizing chart says to use
the SQFT size and multiply by 1.1 to get the CFM if ceiling is standard 8'.
So for a 10x10 bath = 100 SF it would be 110 CFM.

However when you use finish using your bath typically you have the fan on
and the bathroom door open right? So it's drawing the air in the bath PLUS
the air from outside the bath. Would it be a good rule of thumb to
overshoot the 1.1 multiplier? or that already have a safety factor
built-in?

Thanks,

MC


The idea of having a bathroom fan is to exhaust the water vapour
outside into the garden where it will do no harm. While the fan is
running it pulls air into the room through cracks round the door and
holes in the walls and ceiling. Helping to ventilate your home.
When you leave the bathroom door open you negate the whole idea.
Most of that water vapour promptly makes its way into your home,
soaking into your bed and other soft furnishings, thats why your bed
feels cold. Where it can, it goes inside your walls and roof, leading
to wood rot, and starts green and black mould that will lead to
health problems. It makes a visible presence during the winter
condensing on your windows and any other cold surface.
Best to keep that door closed for at least 20 minutes, better still
all the time, as damp towels etc drying on the radiators produce the
same effect.
Interestingly there are millions of homes suffering from mould due to
this habit.
Perry
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,946
Default Bathroom exhaust fan sizing

"Joseph Meehan" wrote in news:48219dab$0$4100
:

"Red Green" wrote in message
...
LouB wrote in :



Many bathroom doors are cut a little short on the bottom to let air
into the room just because of exhaust fans.

Lou


As far as I know, all interior doors should have a 1/2-3/4" gap on the
bottom for air circulation if you have forced air HVAC.


No need if you have an air return in that room.



True, but the most places I've seen they don't exactly load all the BR's
with returns.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bathroom exhaust fan Q [email protected] Home Repair 3 October 11th 07 05:45 PM
Exhaust Fan in the Bathroom? SteveC Home Repair 3 March 1st 06 01:53 AM
Bathroom Exhaust Fan James Repetski Home Repair 6 November 1st 05 02:35 AM
Bathroom Exhaust Fan al Home Repair 8 June 8th 05 10:53 PM
Bathroom Exhaust fan twfsa Home Repair 1 December 31st 04 11:45 PM


All times are GMT +1. The time now is 06:21 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"