On 2008-03-31, Guy Noir wrote:

Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?

Cheers, Wayne
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11
Default Main Panel and Sub Panel questions and the NEC

On Mar 31, 1:34*pm, Wayne Whitney wrote:
On 2008-03-31, Guy Noir wrote:

Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. *Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?

Cheers, Wayne


Sure enough Wayne.


-----Line from pole-----meter------Main Panel Lugs only------55 Amp
Breaker in Main Panel---------Sub Panel 1 Lugs only

|

|

--------55 Amp Breaker in Main Panel---------Sub Panel 2 Lugs only

Another question, I guess, is what is the max sub panel feed I can
have and not need a Main Breaker installed in the main panel. Or, is
there a cummulative load that would require the addition of a Main
Breaker; like if I add a 3rd panel on a 3rd 55amp breaker.

TIA!
-A


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11
Default Main Panel and Sub Panel questions and the NEC

On Mar 31, 2:02*pm, Guy Noir wrote:
On Mar 31, 1:34*pm, Wayne Whitney wrote:

On 2008-03-31, Guy Noir wrote:


Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. *Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?


Cheers, Wayne


Sure enough Wayne.

-----Line from pole-----meter------Main Panel Lugs only------55 Amp
Breaker in Main Panel---------Sub Panel 1 Lugs only

|

|

--------55 Amp Breaker in Main Panel---------Sub Panel 2 Lugs only

Another question, I guess, is what is the max sub panel feed I can
have and not need a Main Breaker installed in the main panel. Or, is
there a cummulative load that would require the addition of a Main
Breaker; like if I add a 3rd panel on a 3rd 55amp breaker.

TIA!
-A


Further reading indicates that if the Main Panel exceeeds 6 circuits/
Breakers, a main disconnect will be needed. Does a 220 (2 spaces)
count as 1 circuit/breaker?
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Main Panel and Sub Panel questions and the NEC


"Guy Noir" wrote in message
...
On Mar 31, 1:34 pm, Wayne Whitney wrote:
On 2008-03-31, Guy Noir wrote:

Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?

Cheers, Wayne


Sure enough Wayne.


-----Line from pole-----meter------Main Panel Lugs only------55 Amp
Breaker in Main Panel---------Sub Panel 1 Lugs only

|

|

--------55 Amp Breaker in Main Panel---------Sub Panel 2 Lugs only

Another question, I guess, is what is the max sub panel feed I can
have and not need a Main Breaker installed in the main panel. Or, is
there a cummulative load that would require the addition of a Main
Breaker; like if I add a 3rd panel on a 3rd 55amp breaker.

TIA!
-A

If there is not a 200 amp disconnect at the meter equipment, you are limited
to six disconnects in or at the main panel. The sub panels do not need
disconnects in them unless they are in separate buildings, garages, out
buildings, etc, but if the main panel is larger than what will hold 6-
double pole breakers, you need a main disconnect to use those spaces


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Main Panel and Sub Panel questions and the NEC


"Guy Noir" wrote in message
...
On Mar 31, 2:02 pm, Guy Noir wrote:
On Mar 31, 1:34 pm, Wayne Whitney wrote:

On 2008-03-31, Guy Noir wrote:


Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?


Cheers, Wayne


Sure enough Wayne.

-----Line from pole-----meter------Main Panel Lugs only------55 Amp
Breaker in Main Panel---------Sub Panel 1 Lugs only

|

|

--------55 Amp Breaker in Main Panel---------Sub Panel 2 Lugs only

Another question, I guess, is what is the max sub panel feed I can
have and not need a Main Breaker installed in the main panel. Or, is
there a cummulative load that would require the addition of a Main
Breaker; like if I add a 3rd panel on a 3rd 55amp breaker.

TIA!
-A


Further reading indicates that if the Main Panel exceeeds 6 circuits/
Breakers, a main disconnect will be needed. Does a 220 (2 spaces)
count as 1 circuit/breaker?

One handle, regardless if single or double, is one disconnect


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Panel and Sub Panel questions and the NEC Guy Noir Home Repair 6 April 1st 08 08:48 PM
Main panel to main panel wiring in converting multi-family to single family dwelling [email protected] Home Repair 6 November 10th 06 03:18 AM
OT security system main panel Karl Townsend Metalworking 4 September 11th 05 10:48 PM
Main Panel alive with breakers off? Walter R. Home Repair 3 August 6th 05 02:09 AM
Breaker panel with main fuses? zxcvbob Home Repair 8 December 18th 04 05:33 AM


All times are GMT +1. The time now is 09:38 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"