Wayne Whitney March 31st 08 07:34 PM

Main Panel and Sub Panel questions and the NEC
 
On 2008-03-31, Guy Noir wrote:

Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?

Cheers, Wayne

Guy Noir March 31st 08 08:02 PM

Main Panel and Sub Panel questions and the NEC
 
On Mar 31, 1:34*pm, Wayne Whitney wrote:
On 2008-03-31, Guy Noir wrote:

Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. *Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?

Cheers, Wayne


Sure enough Wayne.


-----Line from pole-----meter------Main Panel Lugs only------55 Amp
Breaker in Main Panel---------Sub Panel 1 Lugs only

|

|

--------55 Amp Breaker in Main Panel---------Sub Panel 2 Lugs only

Another question, I guess, is what is the max sub panel feed I can
have and not need a Main Breaker installed in the main panel. Or, is
there a cummulative load that would require the addition of a Main
Breaker; like if I add a 3rd panel on a 3rd 55amp breaker.

TIA!
-A



Guy Noir March 31st 08 09:46 PM

Main Panel and Sub Panel questions and the NEC
 
On Mar 31, 2:02*pm, Guy Noir wrote:
On Mar 31, 1:34*pm, Wayne Whitney wrote:

On 2008-03-31, Guy Noir wrote:


Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. *Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?


Cheers, Wayne


Sure enough Wayne.

-----Line from pole-----meter------Main Panel Lugs only------55 Amp
Breaker in Main Panel---------Sub Panel 1 Lugs only

|

|

--------55 Amp Breaker in Main Panel---------Sub Panel 2 Lugs only

Another question, I guess, is what is the max sub panel feed I can
have and not need a Main Breaker installed in the main panel. Or, is
there a cummulative load that would require the addition of a Main
Breaker; like if I add a 3rd panel on a 3rd 55amp breaker.

TIA!
-A


Further reading indicates that if the Main Panel exceeeds 6 circuits/
Breakers, a main disconnect will be needed. Does a 220 (2 spaces)
count as 1 circuit/breaker?

RBM[_2_] March 31st 08 09:56 PM

Main Panel and Sub Panel questions and the NEC
 

"Guy Noir" wrote in message
...
On Mar 31, 1:34 pm, Wayne Whitney wrote:
On 2008-03-31, Guy Noir wrote:

Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?

Cheers, Wayne


Sure enough Wayne.


-----Line from pole-----meter------Main Panel Lugs only------55 Amp
Breaker in Main Panel---------Sub Panel 1 Lugs only

|

|

--------55 Amp Breaker in Main Panel---------Sub Panel 2 Lugs only

Another question, I guess, is what is the max sub panel feed I can
have and not need a Main Breaker installed in the main panel. Or, is
there a cummulative load that would require the addition of a Main
Breaker; like if I add a 3rd panel on a 3rd 55amp breaker.

TIA!
-A

If there is not a 200 amp disconnect at the meter equipment, you are limited
to six disconnects in or at the main panel. The sub panels do not need
disconnects in them unless they are in separate buildings, garages, out
buildings, etc, but if the main panel is larger than what will hold 6-
double pole breakers, you need a main disconnect to use those spaces



RBM[_2_] March 31st 08 10:04 PM

Main Panel and Sub Panel questions and the NEC
 

"Guy Noir" wrote in message
...
On Mar 31, 2:02 pm, Guy Noir wrote:
On Mar 31, 1:34 pm, Wayne Whitney wrote:

On 2008-03-31, Guy Noir wrote:


Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are
fine as a replacement....


Main lugs are fine at the subpanel as long as the feeder is protected
at its source by a circuit breaker sized to its wire size. Perhaps
you could provide a small diagram of the service conductors, the
meter, the disconnect, the breakers, and the feeders?


Cheers, Wayne


Sure enough Wayne.

-----Line from pole-----meter------Main Panel Lugs only------55 Amp
Breaker in Main Panel---------Sub Panel 1 Lugs only

|

|

--------55 Amp Breaker in Main Panel---------Sub Panel 2 Lugs only

Another question, I guess, is what is the max sub panel feed I can
have and not need a Main Breaker installed in the main panel. Or, is
there a cummulative load that would require the addition of a Main
Breaker; like if I add a 3rd panel on a 3rd 55amp breaker.

TIA!
-A


Further reading indicates that if the Main Panel exceeeds 6 circuits/
Breakers, a main disconnect will be needed. Does a 220 (2 spaces)
count as 1 circuit/breaker?

One handle, regardless if single or double, is one disconnect