Default simple electrical question

Hi folks,
In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...

we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.

when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...

Thanks in advance!

- Jay
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default simple electrical question


"RedDwarf" wrote in message
...
Hi folks,
In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...

we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.

when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...

Thanks in advance!

- Jay


If you got 208 volts between hot and ground, you'd have really big problems.
It should read roughly 208 between the two hot legs, and roughly 120 volts
between either hot leg and ground


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default simple electrical question

On Fri, 7 Mar 2008 13:20:03 -0800 (PST), RedDwarf
wrote:

Hi folks,
In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...

we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.

when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...

Thanks in advance!

- Jay


Where are you getting large 3 prong electricians?

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default simple electrical question


"RBM" wrote in message
...

"RedDwarf" wrote in message
...
Hi folks,
In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...

we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.

when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...

Thanks in advance!

- Jay


If you got 208 volts between hot and ground, you'd have really big
problems. It should read roughly 208 between the two hot legs, and roughly
120 volts between either hot leg and ground


There is also the possibility that you need three phase 208 volt. It would
help if you post the actual electrical requirements of the equipment you're
trying to operate




  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default simple electrical question

On Mar 7, 5:29�pm, "RBM" wrote:
"RBM" wrote in message

...







"RedDwarf" wrote in message
...
Hi folks,
In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...


we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.


when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...


Thanks in advance!


- Jay


If you got 208 volts between hot and ground, you'd have really big
problems. It should read roughly 208 between the two hot legs, and roughly
120 volts between either hot leg and ground


There is also the possibility that you need three phase 208 volt. It would
help if you post the actual electrical requirements of the equipment you're
trying to operate



- Hide quoted text -

- Show quoted text -- Hide quoted text -

- Show quoted text -


i have been thru this in malls, check the volatge at different times
of the day, i found it swung wide, and caused great machine troubles.
floating neutrals and a idiot electrician.

i finally gave up and dumped the customer, the hassle just wasnt worth
it.

commervcial buildings have wierd wiring troubles


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default simple electrical question


Where are you getting large 3 prong electricians?

Dang - too slow!


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,447
Default simple electrical question

On Mar 8, 3:36*am, "Mamba" wrote:
Where are you getting large 3 prong electricians?


Dang - too slow!


OK. This from a 3 prong electrician. Presently in Middle East where
all domestic electricity tend to be 3 phase and 230 volts phase to
neutral!
Forgetting all that, but boy those plug in 230 volt appliances often
heat up fast! Would you believe a 2200 watt 2 litre kettle!

We are without all the info to go on from the OP and
presuming this is in North America or somewhere similar?

But as mentioned what is it for? What is the equipment to be plugged
in? Does it require a 3 phase supply? The 208 volt number sounds
suspiciously like the voltage between two phases of 3 phase supply!

Howerver if the electrical supply in the environmernt mentioned
requires to be similar to that in a typical North American domestic
sitaution. (But not Europe or elsewhere), what you have installed
'may' be OK.
.
To the OP. Domestically and in many 'light' buildings there are
typically a three wire supply. (And a ground wire; ignore the ground
wire although it is essential for safety, for a moment).

Between each of the 'outer' wires or legs and a centre point
(neutral), which if present but may not be required in this case, is
usually a white wire which is at approx. zero volts; there should be
about 110 to 125 volts.

One way (although not completely correct) to think of this is to
imagine a red wire leg being at plus approx 115 volts and a black
wire leg being at minus 115 volts. So between the two there is approx
115 + 115 = 230 volts.

If between the two outer wires there is approximately 210 to 230
volts. This could be very similar to what an electrical home clothes
dryer connects.

If you have a 3 wire socket, installed correctly and it is correct for
the equipment to be plugged into it requiring 230 volts 'single phase'
the third pin should be the safety ground and your measurement of
approx 210 to 240 volts between the two live pins may indicate all is
OK.

A few other questions! Is this a dedicated circuit, for a special
purpose machine? Does it have a separate circuit breaker of the
correct rating to match the gauge and type of wiring used (not the
machine itself)? Or ist a circuit shared with other outlets/sockets?

Just telling someone to install a 230 or 208 volt outlet without other
specifications may not have been sufficient info!

Rather like telling someone they need a new battery without specifying
if it is
for a boat, a heavy truck, motorcycle, garden tractor or flashlight!

Sorry for the length of this comment but the original post raises
questions.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 856
Default simple electrical question

According to RedDwarf :
In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...


we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.


when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...


There is _no_ neutral in a 208V circuit. Just two hots and a ground.
It's the same arrangement as a pure 240V circuit (no 120V loads) - two
hots and a ground.

A 208V circuit is derived from a 3 phase (of the right type) circuit.
It's just two of the three hots and a ground.

So, 120V between either current carrying conductor and the ground,
and 208 between the two current carrying conductors is EXACTLY what you
SHOULD be seeing.

I assume that one of the conductors is white - that's what's fooling
you. It's not a neutral. (It should be marked or taped to black or
red).
--
Chris Lewis,

Age and Treachery will Triumph over Youth and Skill
It's not just anyone who gets a Starship Cruiser class named after them.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 102
Default simple electrical question

On Mar 7, 5:20 pm, RedDwarf wrote:
Hi folks,
In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...

we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.

when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...

Thanks in advance!

- Jay


As others have assured you, this is normal, just as the same outlet in
your home would show 240 and 120, respectively.

It's because North American commercial properties are generally fed
with scheme called "three-phase wye" (or "Y"), about which Wikipedia
or a bit of Googling can tell you lots.

The two hots were 208V apart, and each was also 208V from ground,
well, that just wouldn't add up. (Though if the hots were transformer-
isolated from ground, then...well, no, not even then.)

Is there some *reason* you needed to test the outlet after
installation? Did your new computers just not work?

Chip C
Toronto
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 37
Default simple electrical question

On Mar 10, 9:54*am, (Chris Lewis) wrote:
According :

In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...
we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.
when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...


There is _no_ neutral in a 208V circuit. *Just two hots and a ground.
It's the same arrangement as a pure 240V circuit (no 120V loads) - two
hots and a ground.

A 208V circuit is derived from a 3 phase (of the right type) circuit.
It's just two of the three hots and a ground.

So, 120V between either current carrying conductor and the ground,
and 208 between the two current carrying conductors is EXACTLY what you
SHOULD be seeing.

I assume that one of the conductors is white - that's what's fooling
you. *It's not a neutral. *(It should be marked or taped to black or
red).
--
Chris Lewis,

Age and Treachery will Triumph over Youth and Skill
It's not just anyone who gets a Starship Cruiser class named after them.


thanks so much. this makes perfect sense.


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 37
Default simple electrical question

On Mar 10, 11:17*am, Chip C wrote:
On Mar 7, 5:20 wrote:

Hi folks,
In our office - we have an electrical outlet (large 3 prong
electricians just installed). It is supposed to be 208 Volts...


we were having some problems with our equipment, so I ran a multimeter
on it - and when I hook up the hot and neutral to the meter (analog
type), I get the correct reading of 210volts +/-.


when I connect to the hot and the GROUND I get 120 volts... is that
correct, or does the electrician need to come back out? I thought hot
and ground should also produce the 210 volt reading...


Thanks in advance!


- Jay


As others have assured you, this is normal, just as the same outlet in
your home would show 240 and 120, respectively.

It's because North American commercial properties are generally fed
with scheme called "three-phase wye" (or "Y"), about which Wikipedia
or a bit of Googling can tell you lots.

The two hots were 208V apart, and each was also 208V from ground,
well, that just wouldn't add up. (Though if the hots were transformer-
isolated from ground, then...well, no, not even then.)

Is there some *reason* you needed to test the outlet after
installation? Did your new computers just not work?

Chip C
Toronto


we had a problem with the UPS (battery backup). it turns out it was
the UPS. Thanks for the reply... I understand how it works now.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Simple electrical question ** Frank ** Home Repair 18 July 18th 07 05:18 PM
Simple Variac Question Matthew Rossiter Electronics Repair 17 March 17th 07 01:20 AM
help - simple electrical question Mr_Bill Home Repair 9 November 26th 06 10:42 PM
Simple question on design of electrical subpanels Wayne Whitney Home Repair 14 July 16th 06 06:49 PM
Simple electrical question? ng_reader Home Repair 1 August 9th 05 08:25 PM


All times are GMT +1. The time now is 07:22 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"