Home |
Search |
Today's Posts |
![]() |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
I've got some wild temp swings between an office, machine
room, and production room (and the bathroom is almost always too cold 9 months out of 12). This part of the building has its own separate 1.5 ton heatpump for these areas, but it's on one thermostat in the office. Active zoning should take care of those temp issues, and the air-handler/heat exchanger is down below in a nice, easy-access crawl space. All the ducting is simple to get to as well. The folks who do the retrofit bladder system for zoning want a MINIMUM of $7K. It appears I can get a computer good for four zones, four stats, and the various dampers for probably around $700-800. Seems simple enough, but I always approach such things with caution. Has anyone done this? Any overlooked "gotchas"? Any suppliers/brands better than others? Given that the tiny machine room will probably call for cooling when nobody else does, there might be too much back pressure on the fan, as the duct in that room probably represents less than 5% of total system airflow capacity. (I might put in a larger duct and vent.) I still might also need a bypass damper. Are those "passive" (too much pressure opens a spring- or weight- loaded damper); or are there active ones controlled by the computer? I thought perhaps a variable speed blower might be the way to go, but that means a new fan, and still a likely chance for a coil freeze or overheat, unless the computer has the added smarts to run the blower longer and the compressor less. It'd be nice if the system was smart enough to use (recirculate) the waste heat from the machine room first, before calling for heat from the heatpump. A central computer where I could add functions or modify standard heating/cooling "events" would good. For example, I'd like to start the blower for a while first to redistribute the air before switching on a compressor, or perhaps periodically run the blower for all zones just to recirculate the air. (I do that now manually. This alone helps quite a bit.) And, a central computer with a heatpump "anti-slump" timeout would be good too. If anyone's done their own zoning on a forced-air system, I'd be interested in hearing your experiences, suggestions, and recommended DIY-friendly HVAC suppliers. Thanks in advance, Frank -- |
#2
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Bubba writes:
self-snips If anyone's done their own zoning on a forced-air system, I'd be interested in hearing your experiences, suggestions, and recommended DIY-friendly HVAC suppliers. Thanks in advance, Frank Not to get all over you but it works this way: If it sounds to good to be true ($700-$800)..... it probably is ($7k) Maybe you missed a few items... - That's PARTS ONLY that I obtain (CPU, stats, dampers), I do the 2-3 days labor and dialing in... (And oh yes, I know the building well -- I designed it, had it built, but did all the electrical and was on site everyday. Short-sighted at the time, I declined a 6 zone system and settled for two, one of which handles the rooms in questions. Live and learn.g) - I don't have a massive regional radio ad and marketing campaign to pay for in that parts budget, nor is there a home office and staff to fund. I don't at all begrudge their asking $7K, it's just that I'm willing to investigate this further on my own, given that I have some appitude for this stuff. After you replace a few compressors, fan motors and blower wheels, along with a multitude of other problems with the system never working right, refrigerant leaks and ridiculous energy bills, you might begin to understand that "Zoning" aint for the average joe. Well, not exactlty an average joe... extensive background with several kinds of engineering, and a lot of practical DIY experience across many areas (including being a multi-unit landlord for many years) -- enough overall experience to know that each trade has its interesting twists and that it's good to get as many data points as possible. So why a compressor failure? Blower & fan failures? Would that be due to no anti slump? Coil freeze? Too much back pressure? I hope I addressed those concerns by getting a smart enough CPU that will either "baby" the compressor or could have "events" added to its program so that the system would be treated gently. Not sure why the energy bill would be higher... Can you give me more background on that one? Thanks for your reply, and any added advice you might have. Frank -- |
#3
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Bubba writes:
On Mon, 03 Mar 2008 22:19:43 -0000, Frank Stearns wrote: Bubba writes: self-snips more snips Maybe you missed a few items... - That's PARTS ONLY that I obtain (CPU, stats, dampers), I do the 2-3 days labor and dialing in... (And oh yes, I know the building well -- I designed it, had it built, but did all the electrical and was on site everyday. Short-sighted at the time, I declined a 6 zone system and settled for two, one of which handles the rooms in questions. Live and learn.g) - I don't have a massive regional radio ad and marketing campaign to pay for in that parts budget, nor is there a home office and staff to fund. I don't at all begrudge their asking $7K, it's just that I'm willing to investigate this further on my own, given that I have some appitude for this stuff. After you replace a few compressors, fan motors and blower wheels, along with a multitude of other problems with the system never working right, refrigerant leaks and ridiculous energy bills, you might begin to understand that "Zoning" aint for the average joe. Well, not exactlty an average joe... extensive background with several kinds of engineering, and a lot of practical DIY experience across many areas (including being a multi-unit landlord for many years) -- enough overall experience to know that each trade has its interesting twists and that it's good to get as many data points as possible. So why a compressor failure? Blower & fan failures? Would that be due to no anti slump? Coil freeze? Too much back pressure? I hope I addressed those concerns by getting a smart enough CPU that will either "baby" the compressor or could have "events" added to its program so that the system would be treated gently. Not sure why the energy bill would be higher... Can you give me more background on that one? Thanks for your reply, and any added advice you might have. Frank Nope, actually I didnt miss any items. There is no "dialing in" on the system. It has many settings. They get Sure there is. In the various kinds of engineering I do, we routinely test; generally at very conservative settings until we know something is going to work. And I do appreciate the dangers of modifying a system to do a job is was not designed to do. What I'd probably do, especially if I'm adding programming to the CPU (or perhaps getting my own 6x6 industrial controller and programming the whole thing myself), is run the zoning controls (dampers, stats, CPU) NOT CONNECTED to the ductwork, but out in the shop. Emulate conditions; see how the added programming is working. Next move the stats into the spaces, dampers still not connected, and see if everything still looks good. set properly. No guessing. It doesnt matter how well you know the Seems that many of the systems done by "professionals" relies on a lot of guessing -- I've observed much HVAC nonsense, both in residential and commercial settings: noise (wrong duct and/or blower size or bad layout or wrong diffusers), hot/cold spots, short or long cycles because the thing wasn't sized correctly. and so on. building or that you "built it" etc. That has nothing to do with Maybe, maybe not; I do have the advantage of having been in this space for 15 years. I know its thermal (and other) quirks; I know that at one time the coil froze way too often (didn't blow the comp, though, knock on wood; but it did trip the overpressure limit a few times). I mitigated that -- all on my own. Two HVAC pros couldn't figure out what was going on (only that I should replace nearly new hardware for no good reason... well, $$$ for them). I finally figured out the problems by looking (the pros wouldn't even go down in the crawl space and look!). Freezing is now a far more rare occurrence. installing a zoned system properly. Your EE'ing counts for nothing either....sorry. Only that I'm generally conversant in new areas and understand much of the common design logic. But you don't know me, so that's a fair statement -- and I know what you mean. I've rolled my eyes at amateurs in my fields as well. The fact that you have no idea why an improperly installed zone system will fail a compressor, blower or blower wheel tells me you need to leave it to someone that does. Gee, I thought I covered that: back pressure, insuffient air flow over the coil such that it freezes (or return air that's "overly conditioned" due to poor return locations), etc, etc. If you'd like, provide a high-level overview of the more esoteric aspects that I missed. Improper static pressure in ductwork can make a blower wheel look like someone has bashed it with a sledghammer. Ive seen it many times. Improper air flow through a coil will also destroy a compressor. Ive seen that many times over too. Certainly makes sense. There is NO cpu that will "baby" your compressor. Try telling your cpu manufacturer that you want a free new compressor because their cpu Agreed. Not their responsibility. didnt take care of your compressor. There also are not "events" you can put in to "treat your system gently". Specifically, I was considering a longer fan runtime after the set temps had been reached, and also a longer antislump interval, given that such a system will tend to short-cycle because through zoning we're changing the entire design load "on the fly". And that's hard on everything. I was also considering a longer minimum run interval, and dumping the "extra" conditioning into the other spaces. I do know, for example, that the production room will tend to heat nearly as much as the machine room. So "extra" time on the machine room could go into the production room. Also, programmatically, it'd seem that increasing the fuzziness of some of the zones would be useful. A +/- 5 or even 10 degrees in the machine room would be fine. Doesn't need to be +/- 1 degree. Production room could be +/- 3; the office would nice a little tigher, but it doesn't matter all that much either, if it's better for the system. Programmatically, I'd also be looking at a logical weighting of using the blower before calling for conditioning. (In fact, programming the blower on/off in an of itself might get me 80% of what I'm looking for -- I do that manually now, but it's a pain to remember to do it right.) I've noticed in a lot of "modern" HVAC design thinking wants to hold things very tight, perhaps too tight, unless the system is sized *exactly right* and takes into account thermal loads from windows and other sources. Hell, around here, those calcs are routinely blown out of the water given the number of southern windows coupled with the wide variance of sun and cloudy days. Its called Proper Technique, Proper Installation and a whole lot of knowledge. Ive seen companies that do this regularly that can screw them up. Ive seen companies that only do a few of them that screw them up even worse. Could not agree more. I've seen the same. The difference is that because I own the joint I realllly want to be careful with this. Even if I were willing to spend the $7K, I'm not entirely sure I'd find pros that would care as much as I do, and would be willing to follow through as carefully. If you have the "money to burn" then have a stab at it and watch the sparks fly. Have Fun, Let me guess... you're an HVAC guy and hate it when consumers do their own stuff. That's fine. Do what I do in my fields and (a) offer to eval for a consult fee (but you'll need to provide your credentials and a reference list); (b) smile and clean up their mess afterwards -- on an open-ended cost-plus basis. In the meantime, as long as your responding to the posts, perhaps you could take a stab at the original questions, if so inclined? Thanks in advance, Frank -- |
#4
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Frank Stearns wrote:
I hope I addressed those concerns by getting a smart enough CPU... You might use a $100 Norhtec 2.5-watt mcjrxs 486 clone with Ubuntu linux (free) on a $10 1 GB compact flash ram, with a DS9490R USB-1-wire adapter and some $2 Dallas DS18B20 12-bit 1-wire temp sensors and a $48 Systronics 8-1 output board with OWFS, and program it in bwbasic. You can calculate dewpoints and economize with a humidity sensor like Aagelectronica's $48 TAI8540D and a foamboard damper made with a $10 used windshield wiper motor, and ventilate as needed with a $300 GE 8002 CO2 sensor. ... as long as your responding to the posts, perhaps you could take a stab at the original questions, if so inclined? Don't hold your breath, waiting for Bubba's constructive help :-) Nick |
#5
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Frank,
You designed this building and nmade a serious error when designing the heating and cooling. You now wish to correct this error. You claim to have an engineering background. Ok, it doesn't work, you do not seem to have much knowledge about heating and cooling, and you want it fixed. Your options are to hire someone knowledgeable (a civil engineer) or head to the library. If you hire an engineer, expect him to visit the building. You will not get good advice without such a visit so internet advice won't be much help. Dave M. " |
#6
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "Frank Stearns" wrote in message - I don't have a massive regional radio ad and marketing campaign to pay for in that parts budget, nor is there a home office and staff to fund. Frank, I'm with you on this one. Got three estimates to replace an old heat pump along with an eclectic furnace. Prices from highly advertised companies were, $ 8,500, $ 9,700 and $ 10,200. Got hooked up with a 'friend of a friend' who would do the same installation (all Carrier equipment). Total bill came to $ 2,400 and the installer made about $ 150 per hour for his on site labor. Lots of overhead and profit in this business. Ivan Vegvary |
#7
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
"David L. Martel" writes:
Frank, You designed this building and nmade a serious error when designing the The pro hired by the general to do the HVAC did the HVAC design and made some errors. Better than some, worse than others -- all around, a C+ (he did install two very quiet systems -- high marks for that). My mistake was not getting way more technical knowledge about such systems, but most consumers would balk at involvement at that level. I don't mind, but was out of time at that point. The later freezing problems never were identified by two other pros -- had to figure out that one out myself. (The original guy had gone out of business.) So far, I'm not exactly smitten with the pros in this field. There must be good ones... heating and cooling. You now wish to correct this error. You claim to have an engineering background. Pays the bills with long-time repeat customers. ![]() Ok, it doesn't work, you do not seem to have much knowledge about heating and cooling, and you want it fixed. Your options are to hire someone It's not really broken, but some things have become inconvenient and it'd be better to optimize them. knowledgeable (a civil engineer) or head to the library. If you hire an engineer, expect him to visit the building. You will not get good advice without such a visit so internet advice won't be much help. Will all respect, this isn't rocket science (though large building HVAC may be close) -- it is a highly-skilled trade with its own particular language and practices; I'm looking at visiting a subset of the trade for a while, if I can. And cookbook advice I'd not take from a Netnews group in any case, at least not without second-sourcing that advice. Such postings can, however, lead to previously unknown vendors, along with keywords and phrases that suggest additional lines of research. But thanks to all the (apparently) turf-guarding HVAC guys for their replies; while not exactly the info I was looking for that in itself has been useful. Frank -- |
#8
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
"Ivan Vegvary" writes:
"Frank Stearns" wrote in message - I don't have a massive regional radio ad and marketing campaign to pay for in that parts budget, nor is there a home office and staff to fund. Frank, I'm with you on this one. Got three estimates to replace an old heat pump along with an eclectic furnace. Prices from highly advertised companies were, $ 8,500, $ 9,700 and $ 10,200. Got hooked up with a 'friend of a friend' who would do the same installation (all Carrier equipment). Total bill came to $ 2,400 and the installer made about $ 150 per hour for his on site labor. Lots of overhead and profit in this business. Hi Ivan - Good story, and that's my "casual read" on the business side of HVAC. Nothing wrong with high profit, if that's what the market suggests. But if one has another workable route, as you did and as I might, that should be okay too. How's that Carrier system working? They had the variable speed system I *should* have gotten originally to better support zoning. Got talked into using another sub for HVAC who carried York. My mistake, and I accept that responsibility. Mostly the two systems are fine, but some of the usage patterns have changed. Thanks for the anecdote, Frank -- |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
zoning questions | Home Repair | |||
Zoning in bathrooms | UK diy | |||
Quick C/H Zoning Question. | UK diy | |||
Arzel Zoning Comments | Home Repair |