In the main service panel there are 2 bus bars ( neutral and ground ). I
don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. Can I: 1. Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or 2. Replace the entire full bus bar with a new longer one, or 3. Neither of the above 2 can be done at all???? If this is so, what can I do to solve this problem? In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that? |
#2
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
On Feb 13, 3:34*pm, "Al D" wrote:
In the main service panel there are 2 bus bars ( neutral and ground ). *I don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. *Can I: * * * * * * * * * * * * * * * * 1. *Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or * * * * * * * * * * * * * * * * 2. *Replace the entire full bus bar with a new longer one, or * * * * * * * * * * * * * * * * 3. *Neither of the above 2 can be done at all???? *If this is so, what can I do to solve this problem? In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? *I think it's the ground bar because it IS separate from the rest ( not bonded ). *Is this the right thinking on that? You should hire a qualified electrician. |
#3
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
"Al D" wrote in message . .. In the main service panel there are 2 bus bars ( neutral and ground ). I don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. Can I: 1. Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or 2. Replace the entire full bus bar with a new longer one, or 3. Neither of the above 2 can be done at all???? If this is so, what can I do to solve this problem? In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that? In the main service panel, your ground bar and neutral bar are tied together. Buy a new ground bar and bolt it to the panel with a substantial sized conductor to the existing ground bar. In the sub panel, the added bar is for grounds only. Do not connect a bonding screw or jumper to the neutral bar |
#4
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
In article , "Al D" wrote:
In the main service panel there are 2 bus bars ( neutral and ground ). I don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. Can I: 1. Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or Yes. Connect it mechanically to the panel chassis, then add a bonding jumper (#6 or #8 copper) to one of the existing bars. Move a ground wire from the existing bar to the new bar to make room for the jumper. 2. Replace the entire full bus bar with a new longer one, or You can, but it's an awful lot of work for no benefit. 3. Neither of the above 2 can be done at all???? If this is so, what can I do to solve this problem? See above. In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that? No. That's the neutral bar, because it's separate from the rest and not bonded. Ground and neutral are required to be bonded together in the main panel. They are *prohibited* from being bonded together anywhere else. Hence, in your subpanel, the bar that is bonded to the panel is the ground bar, and the one that is not bonded is the neutral bar. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#5
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
"Doug Miller" wrote in message ... In article , "Al D" wrote: In the main service panel there are 2 bus bars ( neutral and ground ). I don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. Can I: 1. Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or Yes. Connect it mechanically to the panel chassis, then add a bonding jumper (#6 or #8 copper) to one of the existing bars. Move a ground wire from the existing bar to the new bar to make room for the jumper. 2. Replace the entire full bus bar with a new longer one, or You can, but it's an awful lot of work for no benefit. 3. Neither of the above 2 can be done at all???? If this is so, what can I do to solve this problem? See above. In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that? No. That's the neutral bar, because it's separate from the rest and not bonded. I think you're misinterpreting him, because he's not clear in what he means. If he's talking about a bar that he added, it's a ground bar. The neutral bar is always integral to the panel Ground and neutral are required to be bonded together in the main panel. They are *prohibited* from being bonded together anywhere else. Hence, in your subpanel, the bar that is bonded to the panel is the ground bar, and the one that is not bonded is the neutral bar. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#6
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
Thanks Doug. I appreciate your advice.
"Doug Miller" wrote in message ... In article , "Al D" wrote: In the main service panel there are 2 bus bars ( neutral and ground ). I don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. Can I: 1. Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or Yes. Connect it mechanically to the panel chassis, then add a bonding jumper (#6 or #8 copper) to one of the existing bars. Move a ground wire from the existing bar to the new bar to make room for the jumper. 2. Replace the entire full bus bar with a new longer one, or You can, but it's an awful lot of work for no benefit. 3. Neither of the above 2 can be done at all???? If this is so, what can I do to solve this problem? See above. In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that? No. That's the neutral bar, because it's separate from the rest and not bonded. Ground and neutral are required to be bonded together in the main panel. They are *prohibited* from being bonded together anywhere else. Hence, in your subpanel, the bar that is bonded to the panel is the ground bar, and the one that is not bonded is the neutral bar. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#7
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
On Wed, 13 Feb 2008 22:12:04 -0500, RBM wrote:
If he's talking about a bar that he added, it's a ground bar. The neutral bar is always integral to the panel That's not true. Some panels have add-on neutral bars to be used when the panel is installed as a sub-panel (no ground-neutral bond). The add-on bars come with insulating (plastic) standoffs and usually a flexible plastic shield under and around one side of the bus. I think Siemens is one brand which does this, but I don't remember for certain which. sdb -- What's seen on your screen? http://PcScreenWatch.com sdbuse1 on mailhost bigfoot.com |
#8
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
"sylvan butler" wrote in message rnal... On Wed, 13 Feb 2008 22:12:04 -0500, RBM wrote: If he's talking about a bar that he added, it's a ground bar. The neutral bar is always integral to the panel That's not true. Some panels have add-on neutral bars to be used when the panel is installed as a sub-panel (no ground-neutral bond). The add-on bars come with insulating (plastic) standoffs and usually a flexible plastic shield under and around one side of the bus. I think Siemens is one brand which does this, but I don't remember for certain which. sdb I have never seen that. Every single phase main lug only panel I've ever seen, comes with the neutral buss installed and a ground detail loose or in a bag. Please give me the make and model number of one that comes with a neutral not installed -- What's seen on your screen? http://PcScreenWatch.com sdbuse1 on mailhost bigfoot.com |
#9
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
On Thu, 14 Feb 2008 00:59:46 GMT, Doug Miller wrote:
In article , "Al D" wrote: In the main service panel there are 2 bus bars ( neutral and ground ). I don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. Can I: 1. Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or Yes. Connect it mechanically to the panel chassis, then add a bonding jumper (#6 or #8 copper) to one of the existing bars. Move a ground wire from the existing bar to the new bar to make room for the jumper. 2. Replace the entire full bus bar with a new longer one, or You can, but it's an awful lot of work for no benefit. 3. Neither of the above 2 can be done at all???? If this is so, what can I do to solve this problem? See above. In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that? No. That's the neutral bar, because it's separate from the rest and not bonded. Ground and neutral are required to be bonded together in the main panel. They are *prohibited* from being bonded together anywhere else. Hence, in your subpanel, the bar that is bonded to the panel is the ground bar, and the one that is not bonded is the neutral bar. Error! Ground and neutral are required to be UNbonded. I just new service put in and the inspector required that the ground and neutral bars be isolated with the ground bar bonced to the box. The electrician had to cut the bonding bar. Mike D. |
#10
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
"Mike Dobony" wrote in message .. . On Thu, 14 Feb 2008 00:59:46 GMT, Doug Miller wrote: In article , "Al D" wrote: In the main service panel there are 2 bus bars ( neutral and ground ). I don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. Can I: 1. Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or Yes. Connect it mechanically to the panel chassis, then add a bonding jumper (#6 or #8 copper) to one of the existing bars. Move a ground wire from the existing bar to the new bar to make room for the jumper. 2. Replace the entire full bus bar with a new longer one, or You can, but it's an awful lot of work for no benefit. 3. Neither of the above 2 can be done at all???? If this is so, what can I do to solve this problem? See above. In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that? No. That's the neutral bar, because it's separate from the rest and not bonded. Ground and neutral are required to be bonded together in the main panel. They are *prohibited* from being bonded together anywhere else. Hence, in your subpanel, the bar that is bonded to the panel is the ground bar, and the one that is not bonded is the neutral bar. Error! Ground and neutral are required to be UNbonded. I just new service put in and the inspector required that the ground and neutral bars be isolated with the ground bar bonced to the box. The electrician had to cut the bonding bar. Mike D. The only way that would be correct, is if the main disconnect wasn't in the service panel. Do you have a main disconnect in a meter panel? |
#11
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
|
#13
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
"Al D" wrote in message . .. In the main service panel there are 2 bus bars ( neutral and ground ). I don't have any screw holes left to add an additional branch circuit to a detached subpanel located 60' away from the main. Can I: 1. Add an additional bus bar to the main panel and if so, how do I connect it to the old bus bar(s)? or 2. Replace the entire full bus bar with a new longer one, or 3. Neither of the above 2 can be done at all???? If this is so, what can I do to solve this problem? In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that? Al, humor me and describe this bus bar that you are installing as a "neutral bar". I am concerned that you may be doing something wrong and dangerous |
#14
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
On Thu, 14 Feb 2008 17:39:25 -0500, RBM wrote:
"sylvan butler" wrote in message rnal... On Wed, 13 Feb 2008 22:12:04 -0500, RBM wrote: If he's talking about a bar that he added, it's a ground bar. The neutral bar is always integral to the panel That's not true. Some panels have add-on neutral bars to be used when the panel is installed as a sub-panel (no ground-neutral bond). The add-on bars come with insulating (plastic) standoffs and usually a flexible plastic shield under and around one side of the bus. I think Siemens is one brand which does this, but I don't remember for certain which. I have never seen that. Every single phase main lug only panel I've ever You were talking about add-on bars. And so was my response. Read it again until you understand. sdb -- What's seen on your screen? http://PcScreenWatch.com sdbuse1 on mailhost bigfoot.com |
#15
Posted to alt.home.repair
|
|||
|
|||
Bus Bars (electrical)
"sylvan butler" wrote in message rnal... On Thu, 14 Feb 2008 17:39:25 -0500, RBM wrote: "sylvan butler" wrote in message rnal... On Wed, 13 Feb 2008 22:12:04 -0500, RBM wrote: If he's talking about a bar that he added, it's a ground bar. The neutral bar is always integral to the panel That's not true. Some panels have add-on neutral bars to be used when the panel is installed as a sub-panel (no ground-neutral bond). The add-on bars come with insulating (plastic) standoffs and usually a flexible plastic shield under and around one side of the bus. I think Siemens is one brand which does this, but I don't remember for certain which. I have never seen that. Every single phase main lug only panel I've ever You were talking about add-on bars. And so was my response. Read it again until you understand. sdb -- What's seen on your screen? http://PcScreenWatch.com sdbuse1 on mailhost bigfoot.com I do understand, your response was incorrect. You need to read what the OP wrote: "In the subpanel, the bus bar that is away from the breaker panel itself that I added to the subpanel box, does that bus bar become the ground bar or the neutral bar? I think it's the ground bar because it IS separate from the rest ( not bonded ). Is this the right thinking on that?" He's questioning the bus bar that did NOT come installed in the sub panel, The one that HE installed. Neutral bars come installed in MLO panels. They provide a bonding jumper, which you install if using the panel as a main service panel. Some panels include a GROUND detail for use when the panel is being used as a sub. Often this ground detail is loose or in a bag and gets installed by the electrician. The confusion is what the OP means by (not bonded), as the neutral bar is the one that wouldn't be bonded. You can purchase additional neutral bars and ground bars for any panel, but that's not what the OP was referring to |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Tie bars, brickwork | UK diy | |||
Horizontal Bars on New LCD and Plasma TVs - HELP! | Electronics Repair | |||
Panic bars | Home Repair | |||
Removing burglar bars | Home Ownership | |||
Sony strange vertical bars (not the dreaded scrolling bars!)? | Electronics Repair |