Attic Scuttle
Can I add a second attic access scuttle in my garage ceiling? Present
scuttle is in the MBR closet for mechanical access. 1758 sq ft, single story home. Attic with plumbing for NG furnace, electrical, etc. Two ridge vents, plus soffit vents. Split garages, single and double - attached. I would like to add an attic scuttle in the two car garage. This garage has the breaker panel, gas water heater, softener, tools, etc.... Thanks. The County Web site gets me this far* * R807.1 Attic Access Section R807.1 is amended to read: R807.1 Attic Access. In buildings with combustible ceiling or roof construction which have electrical, plumbing or mechanical fixtures or equipment installed within the attic space, an attic access opening shall be provided to attic areas that exceed 30 square feet (2.8 m2) and have a vertical height of 30 inches (762 mm) or greater The rough- framed opening shall not be less than 22 inches by 30 inches (559 mm by 762 mm) and shall be located in a hallway or other readily accessible location. A 30-inch (762 mm) minimum unobstructed headroom in the attic space shall be provided at some point above the access opening. See Uniform Mechanical Code for access requirements where mechanical equipment is located in attics. Oren -- |
#2
Posted to alt.home.repair
|
|||
|
|||
Attic Scuttle
On Wed, 30 Jan 2008 13:17:08 -0800, Oren wrote:
Can I add a second attic access scuttle in my garage ceiling? Present scuttle is in the MBR closet for mechanical access. 1758 sq ft, single story home. Attic with plumbing for NG furnace, electrical, etc. Two ridge vents, plus soffit vents. Should read gable vents, oops. Split garages, single and double - attached. I would like to add an attic scuttle in the two car garage. This garage has the breaker panel, gas water heater, softener, tools, etc.... Thanks. The County Web site gets me this far* * R807.1 Attic Access Section R807.1 is amended to read: R807.1 Attic Access. In buildings with combustible ceiling or roof construction which have electrical, plumbing or mechanical fixtures or equipment installed within the attic space, an attic access opening shall be provided to attic areas that exceed 30 square feet (2.8 m2) and have a vertical height of 30 inches (762 mm) or greater The rough- framed opening shall not be less than 22 inches by 30 inches (559 mm by 762 mm) and shall be located in a hallway or other readily accessible location. A 30-inch (762 mm) minimum unobstructed headroom in the attic space shall be provided at some point above the access opening. See Uniform Mechanical Code for access requirements where mechanical equipment is located in attics. Oren Oren -- |
#3
Posted to alt.home.repair
|
|||
|
|||
Attic Scuttle
Oren wrote:
Can I add a second attic access scuttle in my garage ceiling? Present scuttle is in the MBR closet for mechanical access. 1758 sq ft, single story home. Attic with plumbing for NG furnace, electrical, etc. Two ridge vents, plus soffit vents. Split garages, single and double - attached. I would like to add an attic scuttle in the two car garage. This garage has the breaker panel, gas water heater, softener, tools, etc.... Thanks. The County Web site gets me this far* * R807.1 Attic Access Section R807.1 is amended to read: R807.1 Attic Access. In buildings with combustible ceiling or roof construction which have electrical, plumbing or mechanical fixtures or equipment installed within the attic space, an attic access opening shall be provided to attic areas that exceed 30 square feet (2.8 m2) and have a vertical height of 30 inches (762 mm) or greater The rough- framed opening shall not be less than 22 inches by 30 inches (559 mm by 762 mm) and shall be located in a hallway or other readily accessible location. A 30-inch (762 mm) minimum unobstructed headroom in the attic space shall be provided at some point above the access opening. See Uniform Mechanical Code for access requirements where mechanical equipment is located in attics. Oren -- Yes. You can have as many as you want. The code requires access and sets the minimum number that you must have and for what. There is no code against having more. -- Robert Allison Rimshot, Inc. Georgetown, TX |
#4
Posted to alt.home.repair
|
|||
|
|||
Attic Scuttle
International Residential Code 2006 (2003 version has similar
language) says: R309.2: The garage shall be separated from the residence and its attic area by not less than 1/2 inch gypsum board applied to the garage side. R309.1.1 duct penetrations. Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum 26 gage sheet steel or other approved material and shall have no openings into the garage. R309.1.2 Other Penetrations. Penetrations through the separation required in 309.2 shall be protected by filling the openings around the penetrating item with approved material to resist the free passage of flame and products of combustion. I think the intent is to separate the garage from the residence. Therefore, if you put a hatch in the ceiling of the garage, a partition continuous from slab to roof has to be placed between garage and dwelling and any penetrations need to be treated in accordance with the code. T Oren wrote: Can I add a second attic access scuttle in my garage ceiling? Present scuttle is in the MBR closet for mechanical access. 1758 sq ft, single story home. Attic with plumbing for NG furnace, electrical, etc. Two ridge vents, plus soffit vents. Split garages, single and double - attached. I would like to add an attic scuttle in the two car garage. This garage has the breaker panel, gas water heater, softener, tools, etc.... Thanks. The County Web site gets me this far* * R807.1 Attic Access Section R807.1 is amended to read: R807.1 Attic Access. In buildings with combustible ceiling or roof construction which have electrical, plumbing or mechanical fixtures or equipment installed within the attic space, an attic access opening shall be provided to attic areas that exceed 30 square feet (2.8 m2) and have a vertical height of 30 inches (762 mm) or greater The rough- framed opening shall not be less than 22 inches by 30 inches (559 mm by 762 mm) and shall be located in a hallway or other readily accessible location. A 30-inch (762 mm) minimum unobstructed headroom in the attic space shall be provided at some point above the access opening. See Uniform Mechanical Code for access requirements where mechanical equipment is located in attics. Oren -- |
#6
Posted to alt.home.repair
|
|||
|
|||
Attic Scuttle
On Wed, 30 Jan 2008 13:17:08 -0800, Oren wrote:
Can I add a second attic access scuttle in my garage ceiling? Present scuttle is in the MBR closet for mechanical access. 1758 sq ft, single story home. Attic with plumbing for NG furnace, electrical, etc. Two ridge vents, plus soffit vents. Split garages, single and double - attached. I would like to add an attic scuttle in the two car garage. This garage has the breaker panel, gas water heater, softener, tools, etc.... Just cut the whole and be done with it. -- Click here every day to feed an animal that needs you today !!! http://www.theanimalrescuesite.com/ Paul ( pjm @ pobox . com ) - remove spaces to email me 'Some days, it's just not worth chewing through the restraints.' 'With sufficient thrust, pigs fly just fine.' HVAC/R program for Palm PDA's Free demo now available online http://pmilligan.net/palm/ |
#7
Posted to alt.home.repair
|
|||
|
|||
Attic Scuttle
On Thu, 31 Jan 2008 02:03:25 GMT, Robert Allison
wrote: wrote: International Residential Code 2006 (2003 version has similar language) says: R309.2: The garage shall be separated from the residence and its attic area by not less than 1/2 inch gypsum board applied to the garage side. R309.1.1 duct penetrations. Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum 26 gage sheet steel or other approved material and shall have no openings into the garage. R309.1.2 Other Penetrations. Penetrations through the separation required in 309.2 shall be protected by filling the openings around the penetrating item with approved material to resist the free passage of flame and products of combustion. I think the intent is to separate the garage from the residence. Therefore, if you put a hatch in the ceiling of the garage, a partition continuous from slab to roof has to be placed between garage and dwelling and any penetrations need to be treated in accordance with the code. T Not exactly. A scuttle hole in the garage will not require a fire rated wall between the garage and the house. Use a piece of drywall for the scuttle hole cover and you are fine. I have never had a problem even with pull down stairs (which are not fire rated). The attic access is usually in the garage, and is usually a pull down stair. Provides access to the entire attic. This is true for all of central Texas. YMMV. I was in my attic recently troubleshooting the furnace, before I called the service guy and had it fixed. (found original furnace documents in plastic sleeve ) Looked towards the garage area; where I want the next scuttle, I observed two things: - there was what I considered a fire block extending from the ceiling top plate to the roof. Not certain of full extent and how it was/is built. - through this apparent fire block, there was a hole large enough for any person. In fact an electrician had mentioned this to me a few years ago. That hole through the ply (3/4"?) would seem it would allow fire into the rest of the attic. It *appears* to be centered over the hallway and not a bedroom. I will put in the scuttle in. My garage is finished with 5/8" sheetrock on both ceiling and walls. Off to misplace the honey doo list... Thanks!! Oren -- |
#8
Posted to alt.home.repair
|
|||
|
|||
Attic Scuttle
Oren wrote:
On Thu, 31 Jan 2008 02:03:25 GMT, Robert Allison wrote: wrote: International Residential Code 2006 (2003 version has similar language) says: R309.2: The garage shall be separated from the residence and its attic area by not less than 1/2 inch gypsum board applied to the garage side. R309.1.1 duct penetrations. Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum 26 gage sheet steel or other approved material and shall have no openings into the garage. R309.1.2 Other Penetrations. Penetrations through the separation required in 309.2 shall be protected by filling the openings around the penetrating item with approved material to resist the free passage of flame and products of combustion. I think the intent is to separate the garage from the residence. Therefore, if you put a hatch in the ceiling of the garage, a partition continuous from slab to roof has to be placed between garage and dwelling and any penetrations need to be treated in accordance with the code. T Not exactly. A scuttle hole in the garage will not require a fire rated wall between the garage and the house. Use a piece of drywall for the scuttle hole cover and you are fine. I have never had a problem even with pull down stairs (which are not fire rated). The attic access is usually in the garage, and is usually a pull down stair. Provides access to the entire attic. This is true for all of central Texas. YMMV. I was in my attic recently troubleshooting the furnace, before I called the service guy and had it fixed. (found original furnace documents in plastic sleeve ) Looked towards the garage area; where I want the next scuttle, I observed two things: - there was what I considered a fire block extending from the ceiling top plate to the roof. Not certain of full extent and how it was/is built. - through this apparent fire block, there was a hole large enough for any person. In fact an electrician had mentioned this to me a few years ago. That hole through the ply (3/4"?) would seem it would allow fire into the rest of the attic. It *appears* to be centered over the hallway and not a bedroom. I will put in the scuttle in. My garage is finished with 5/8" sheetrock on both ceiling and walls. Off to misplace the honey doo list... Thanks!! Oren -- If the "firewall" is plywood, then it is not a fire wall. Sounds more like a shear wall or shear truss. Although a fire wall may have plywood on it, it must be a non combustible material (drywall) on the surface to qualify as a firewall. According to code, a fire wall must be two layers of 5/8" drywall, firetaped and firecaulked. A draft stop must be one layer of drywall, firetaped and caulked. -- Robert Allison Rimshot, Inc. Georgetown, TX |
#9
Posted to alt.home.repair
|
|||
|
|||
Attic Scuttle
On Thu, 31 Jan 2008 23:39:29 GMT, Robert Allison
wrote: Oren wrote: On Thu, 31 Jan 2008 02:03:25 GMT, Robert Allison wrote: wrote: International Residential Code 2006 (2003 version has similar language) says: R309.2: The garage shall be separated from the residence and its attic area by not less than 1/2 inch gypsum board applied to the garage side. R309.1.1 duct penetrations. Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum 26 gage sheet steel or other approved material and shall have no openings into the garage. R309.1.2 Other Penetrations. Penetrations through the separation required in 309.2 shall be protected by filling the openings around the penetrating item with approved material to resist the free passage of flame and products of combustion. I think the intent is to separate the garage from the residence. Therefore, if you put a hatch in the ceiling of the garage, a partition continuous from slab to roof has to be placed between garage and dwelling and any penetrations need to be treated in accordance with the code. T Not exactly. A scuttle hole in the garage will not require a fire rated wall between the garage and the house. Use a piece of drywall for the scuttle hole cover and you are fine. I have never had a problem even with pull down stairs (which are not fire rated). The attic access is usually in the garage, and is usually a pull down stair. Provides access to the entire attic. This is true for all of central Texas. YMMV. I was in my attic recently troubleshooting the furnace, before I called the service guy and had it fixed. (found original furnace documents in plastic sleeve ) Looked towards the garage area; where I want the next scuttle, I observed two things: - there was what I considered a fire block extending from the ceiling top plate to the roof. Not certain of full extent and how it was/is built. - through this apparent fire block, there was a hole large enough for any person. In fact an electrician had mentioned this to me a few years ago. That hole through the ply (3/4"?) would seem it would allow fire into the rest of the attic. It *appears* to be centered over the hallway and not a bedroom. I will put in the scuttle in. My garage is finished with 5/8" sheetrock on both ceiling and walls. Off to misplace the honey doo list... Thanks!! Oren -- If the "firewall" is plywood, then it is not a fire wall. Sounds more like a shear wall or shear truss. Although a fire wall may have plywood on it, it must be a non combustible material (drywall) on the surface to qualify as a firewall. According to code, a fire wall must be two layers of 5/8" drywall, firetaped and firecaulked. A draft stop must be one layer of drywall, firetaped and caulked. Thanks. Given my observations: it is not really a fire wall. I will look further when I cut the second scuttle in the garage. Oren -- |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Attic Fan, Whole House Fan, Pressurizing Attic? | Home Repair | |||
owl in our attic | Home Repair | |||
attic? | Home Repair | |||
Attic mold issue revisited - 105 degree attic temperature today | Home Repair | |||
Attic mold issue revisited - 105 degree attic temperature today | Home Ownership |