[email protected] December 6th 07 01:02 AM

30A duplex receptacles possible?
 
I've got about 60A of 120v equipment to run in one room (at times, all
of it simultaneously). Currently there's only one 20A circuit feeding
the entire floor. So I was thinking of installing two 30A circuits
and one 20A. I would have three ganged boxes, each holding two duplex
receptacles, and each circuit would feed two of those receptacles (in
adjacent boxes).

However, when reading my books on wiring, I see no mention of any 30A
duplex receptacles...only the single receptacles you might see for an
A/C. I could use all 20A circuits I suppose but would probably need
four. Are 30A 120v duplex receptacles something that exists? Is it
strange to do things this way?

thanks!

RBM December 6th 07 01:29 AM

30A duplex receptacles possible?
 
If you were going to use 30 amp outlets, you'd need to use 30 amp plugs as
well. It would be less expensive to use 15 or 20 amp plugs on the cords, and
use more 20 amp receptacles


wrote in message
...
I've got about 60A of 120v equipment to run in one room (at times, all
of it simultaneously). Currently there's only one 20A circuit feeding
the entire floor. So I was thinking of installing two 30A circuits
and one 20A. I would have three ganged boxes, each holding two duplex
receptacles, and each circuit would feed two of those receptacles (in
adjacent boxes).

However, when reading my books on wiring, I see no mention of any 30A
duplex receptacles...only the single receptacles you might see for an
A/C. I could use all 20A circuits I suppose but would probably need
four. Are 30A 120v duplex receptacles something that exists? Is it
strange to do things this way?

thanks!




Bob F December 6th 07 01:41 AM

30A duplex receptacles possible?
 

wrote in message
...
I've got about 60A of 120v equipment to run in one room (at times, all
of it simultaneously). Currently there's only one 20A circuit feeding
the entire floor. So I was thinking of installing two 30A circuits
and one 20A. I would have three ganged boxes, each holding two duplex
receptacles, and each circuit would feed two of those receptacles (in
adjacent boxes).

However, when reading my books on wiring, I see no mention of any 30A
duplex receptacles...only the single receptacles you might see for an
A/C. I could use all 20A circuits I suppose but would probably need
four. Are 30A 120v duplex receptacles something that exists? Is it
strange to do things this way?


Run a larger cable to the room, and add a subpanel there, with 20 amp breakers
as needed.

Bob



S. Barker December 6th 07 01:47 AM

30A duplex receptacles possible?
 
what in the world are you running? 60 amps is a lot of heat.

s


wrote in message
...
I've got about 60A of 120v equipment to run in one room (at times, all
of it simultaneously). Currently there's only one 20A circuit feeding
the entire floor. So I was thinking of installing two 30A circuits
and one 20A. I would have three ganged boxes, each holding two duplex
receptacles, and each circuit would feed two of those receptacles (in
adjacent boxes).

However, when reading my books on wiring, I see no mention of any 30A
duplex receptacles...only the single receptacles you might see for an
A/C. I could use all 20A circuits I suppose but would probably need
four. Are 30A 120v duplex receptacles something that exists? Is it
strange to do things this way?

thanks!




[email protected] December 6th 07 01:50 AM

30A duplex receptacles possible?
 
On Dec 5, 7:29 pm, "RBM" rbm2(remove wrote:
If you were going to use 30 amp outlets, you'd need to use 30 amp plugs as
well. It would be less expensive to use 15 or 20 amp plugs on the cords, and
use more 20 amp receptacles


Do you mean I can hook multiple 20A outlets to a 30A circuit and as
long as I don't draw more than 20A from any single outlet (and don't
go over 30A cumulative) I'm ok? Wouldn't that have a danger of
drawing more than the outlet can handle w/o the breaker tripping? Or
perhaps nothing that draws more than 20A would ever be able to plug
into a 20A receptacle?

[email protected] December 6th 07 01:54 AM

30A duplex receptacles possible?
 

Run a larger cable to the room, and add a subpanel there, with 20 amp breakers
as needed.


This did occur to me. I have one subpanel off the main now. It uses
a breaker that spreads across both sides of the box. Another subpanel
would make things simpler in some ways. I guess I can add up to more
than 200A total in breakers as long as I don't draw more than 200 at
once?


[email protected] December 6th 07 01:57 AM

30A duplex receptacles possible?
 
On Dec 5, 7:47 pm, "S. Barker" wrote:
what in the world are you running? 60 amps is a lot of heat.


no doubt. this is for my art studio. here's a partial list:

electric griddle 12A
electric griddle 12A
heat stripping gun 12A
1 or 2 space heaters 12A each
A/C in summer 8A
computers 4A or more
tools 15A

this wouldn't all be on at the same time, but the griddles, stripping
gun, computers, and an A/C or heater would be on any time i want to do
encaustic (wax-based) painting

RBM December 6th 07 02:02 AM

30A duplex receptacles possible?
 
No, you can connect multiple 20 amp receptacles to multiple 20 amp circuits




wrote in message
...
On Dec 5, 7:29 pm, "RBM" rbm2(remove wrote:
If you were going to use 30 amp outlets, you'd need to use 30 amp plugs
as
well. It would be less expensive to use 15 or 20 amp plugs on the cords,
and
use more 20 amp receptacles


Do you mean I can hook multiple 20A outlets to a 30A circuit and as
long as I don't draw more than 20A from any single outlet (and don't
go over 30A cumulative) I'm ok? Wouldn't that have a danger of
drawing more than the outlet can handle w/o the breaker tripping? Or
perhaps nothing that draws more than 20A would ever be able to plug
into a 20A receptacle?




RBM December 6th 07 02:05 AM

30A duplex receptacles possible?
 
That was my point. None of the things you plan to use have 30 amp plugs on
them, so why would you want to use 30 amp receptacles?




wrote in message
...
On Dec 5, 7:47 pm, "S. Barker" wrote:
what in the world are you running? 60 amps is a lot of heat.


no doubt. this is for my art studio. here's a partial list:

electric griddle 12A
electric griddle 12A
heat stripping gun 12A
1 or 2 space heaters 12A each
A/C in summer 8A
computers 4A or more
tools 15A

this wouldn't all be on at the same time, but the griddles, stripping
gun, computers, and an A/C or heater would be on any time i want to do
encaustic (wax-based) painting




ransley December 6th 07 02:10 AM

30A duplex receptacles possible?
 
On Dec 5, 7:57 pm, wrote:
On Dec 5, 7:47 pm, "S. Barker" wrote:

what in the world are you running? 60 amps is a lot of heat.


no doubt. this is for my art studio. here's a partial list:

electric griddle 12A
electric griddle 12A
heat stripping gun 12A
1 or 2 space heaters 12A each
A/C in summer 8A
computers 4A or more
tools 15A

this wouldn't all be on at the same time, but the griddles, stripping
gun, computers, and an A/C or heater would be on any time i want to do
encaustic (wax-based) painting


You need alot of lumens to grow alot of Mariguana in ONE ROOM, so 60a
might do it., Yea Art studio. The Art of pottery................

M Q December 6th 07 02:21 AM

30A duplex receptacles possible?
 
wrote:

On Dec 5, 7:47 pm, "S. Barker" wrote:

what in the world are you running? 60 amps is a lot of heat.



no doubt. this is for my art studio. here's a partial list:

electric griddle 12A
electric griddle 12A
heat stripping gun 12A
1 or 2 space heaters 12A each
A/C in summer 8A
computers 4A or more
tools 15A

this wouldn't all be on at the same time, but the griddles, stripping
gun, computers, and an A/C or heater would be on any time i want to do
encaustic (wax-based) painting


You may not put 15 or 20 amp outlets ("receptacles") on a 30 amp circuit.
You may put 15 or 20 amp outlets on a 20 amp circuit
(however if there is only outlet, it must be 20 amp)( NEC 210.21(B)(3) ).

I count at least 6 loads that you cannot put 2 of them at the same time
on a 20 amp circuit. You are going to need at least 6 circuits.


Doug Miller December 6th 07 12:55 PM

30A duplex receptacles possible?
 
In article , wrote:
On Dec 5, 7:29 pm, "RBM" rbm2(remove wrote:
If you were going to use 30 amp outlets, you'd need to use 30 amp plugs as
well. It would be less expensive to use 15 or 20 amp plugs on the cords, and
use more 20 amp receptacles


Do you mean I can hook multiple 20A outlets to a 30A circuit


No. That's a Code violation. 30A circuits require 30A receptacles.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

HerHusband December 6th 07 03:45 PM

30A duplex receptacles possible?
 
I've got about 60A of 120v equipment to run in one room (at times, all
of it simultaneously). Currently there's only one 20A circuit feeding
the entire floor. So I was thinking of installing two 30A circuits
and one 20A.
this is for my art studio. here's a partial list:
electric griddle 12A
electric griddle 12A
heat stripping gun 12A
1 or 2 space heaters 12A each
A/C in summer 8A
computers 4A or more
tools 15A


It sounds like you have a lot of high current appliances. I personally
would run a separate circuit for each of those.

Based on your list, I would install eight 20A circuits, using 12/2 cable,
and regular 20A recepticles. Your computers could share the lighting
circuit if you wish.

Depending on your usage patterns, you may be able to combine the stripping
gun and "tools" on a single circuit too. For example, you probably wouldn't
be using the stripping gun, a drill, and a dremel tool all at the same
time. Those could share a circuit if you wish.

Basically, if you use an appliance that draws 10A or more and is on
continously (i.e. the griddles), you should have a separate circuit for it.
You could probably get by with 15A circuits for most of your appliances,
but it wouldn't cost much more to run 20A and would give you greater
capacity.

If you have balanced loads (i.e. two matching griddles), you could combine
a couple of circuits with a single 12/3 cable, sharing the neutral line.
Just make sure the two hot wires are on opposite legs of the incoming 240V
supply. This would reduce your cable runs somewhat, and is frequently done
for similar situations like kitchen wiring.

If your breaker panel is a long distance from your studio, it may make more
sense to install a subpanel in the studio, then run each circuit from the
subpanel. This would ease later additions too.

Anthony

[email protected] December 6th 07 05:18 PM

30A duplex receptacles possible?
 
Thanks all for the advice---I really appreciate it. I'm now leaning
towards a subpanel in the studio, as running 6-8 circuits from the
basement to the 2nd floor attic is going to be difficult. I have a
passage that will work for 2 or 3 cables, but 6-8 will require a lot
more fishing.

I appreciate the 12/3 cable idea...I'll consider that. This would
also be easier to accomplish with a subpanel (so I wouldnt' have to
move current breakers to get on both sides of the incoming).

Just to clarify--when I originally proposed 30A outlets I was hoping
that 30A outlets were available in the 'normal' blade style (e.g. it
would look just like a 20A plug but would allow up to 30A to be drawn
through it, say for two griddles). Clearly that's not the case.

thanks again



Chris Friesen December 6th 07 05:47 PM

30A duplex receptacles possible?
 
wrote:

Just to clarify--when I originally proposed 30A outlets I was hoping
that 30A outlets were available in the 'normal' blade style (e.g. it
would look just like a 20A plug but would allow up to 30A to be drawn
through it, say for two griddles). Clearly that's not the case.


You could run 14/3 to an outlet and break off the tab on a duplex
receptacle. This would give you 15A to each plug. The loads on the two
plugs do not need to be equal.

With 3 14/3 cables this would give you a minimum of three duplex
receptacles with a total of 90A of potential current draw. You could
also add more outlets on each circuit for convenience.

You could run #12 but it's going to be bigger and more expensive cable,
and somewhat harder to work with. I did it in the garage, but I have
some tools that draw 15A so they needed it.

One other thing to consider is that once you start bundling cables
together you need to account for the heat. This starts to reduce the
allowed cable ampacity.

Chris

Jeepwolf December 6th 07 06:05 PM

30A duplex receptacles possible?
 
On Wed, 5 Dec 2007 17:50:47 -0800 (PST), wrote:

On Dec 5, 7:29 pm, "RBM" rbm2(remove wrote:
If you were going to use 30 amp outlets, you'd need to use 30 amp plugs as
well. It would be less expensive to use 15 or 20 amp plugs on the cords, and
use more 20 amp receptacles


Do you mean I can hook multiple 20A outlets to a 30A circuit and as
long as I don't draw more than 20A from any single outlet (and don't
go over 30A cumulative) I'm ok? Wouldn't that have a danger of
drawing more than the outlet can handle w/o the breaker tripping? Or
perhaps nothing that draws more than 20A would ever be able to plug
into a 20A receptacle?


Since you want to put Two duplex outlets into a box, put one on one
20A breaker and the other on another 20A breaker. Put several of
these in the room on separate breakers. I'd run at least 6 breakers
for that room. If your panel lacks spaces. run a sub panel in that
room, off a 60A main from the house panel. You can easily buy 6 or 8
breaker sub boxes. I'd go for the 8 or even a 10 for expansion, and
maybe put a 100A sub in the main panel. Of course you need thicker
wire to feed the thing and you need enough power coming into the house
to start with.

Jeepwolf December 6th 07 06:15 PM

30A duplex receptacles possible?
 
On Wed, 5 Dec 2007 17:57:00 -0800 (PST), wrote:

On Dec 5, 7:47 pm, "S. Barker" wrote:
what in the world are you running? 60 amps is a lot of heat.


no doubt. this is for my art studio. here's a partial list:

electric griddle 12A


1 - 20A breaker

electric griddle 12A


1 - 20A breaker

heat stripping gun 12A


1 - 20A breaker

1 or 2 space heaters 12A each


2 - 20A breakers on 2 separate duplex outlets

A/C in summer 8A


1 - 20A breaker

computers 4A or more


1 - 15A breaker (and you want this separated from other stuff except
maybe room lights)

tools 15A


1 - 20A breaker w/ two duplex outs so you dont have to keep unplugging
them.

this wouldn't all be on at the same time, but the griddles, stripping
gun, computers, and an A/C or heater would be on any time i want to do
encaustic (wax-based) painting


Total 7 - 20A breakers and 1 - 15A breaker.
I'd add one more breaker w/ an outlet for a spare.

This isn't rocket science, just a lot of wiring.

You can always plug a small hand tool like a drill into the same
outlet as the griddles. Like I said, keep the computer on it's own
breaker other than some lights. Power tools can cause issues with a
computer.

Bob F December 6th 07 07:48 PM

30A duplex receptacles possible?
 

wrote in message
...

Run a larger cable to the room, and add a subpanel there, with 20 amp
breakers
as needed.


This did occur to me. I have one subpanel off the main now. It uses
a breaker that spreads across both sides of the box. Another subpanel
would make things simpler in some ways. I guess I can add up to more
than 200A total in breakers as long as I don't draw more than 200 at
once?


Indeed you can.



franz frippl December 7th 07 11:28 AM

30A duplex receptacles possible?
 
On Wed, 05 Dec 2007 17:02:08 -0800, benjunk wrote:

I've got about 60A of 120v equipment to run in one room (at times, all
of it simultaneously). Currently there's only one 20A circuit feeding
the entire floor. So I was thinking of installing two 30A circuits and
one 20A. I would have three ganged boxes, each holding two duplex
receptacles, and each circuit would feed two of those receptacles (in
adjacent boxes).

However, when reading my books on wiring, I see no mention of any 30A
duplex receptacles...only the single receptacles you might see for an
A/C. I could use all 20A circuits I suppose but would probably need
four. Are 30A 120v duplex receptacles something that exists? Is it
strange to do things this way?

thanks!


Go with 20 amp circuits. Wiring is easier, cheaper and less explaining
to do if and when you ever sell your property. Besides, if you split the
loads over several circuits, if one circuit fails or blows, the others
are still working.


franz frippl December 7th 07 11:31 AM

30A duplex receptacles possible?
 
On Wed, 05 Dec 2007 17:57:00 -0800, benjunk wrote:

On Dec 5, 7:47 pm, "S. Barker" wrote:
what in the world are you running? 60 amps is a lot of heat.


no doubt. this is for my art studio. here's a partial list:

electric griddle 12A
electric griddle 12A
heat stripping gun 12A
1 or 2 space heaters 12A each
A/C in summer 8A
computers 4A or more
tools 15A

this wouldn't all be on at the same time, but the griddles, stripping
gun, computers, and an A/C or heater would be on any time i want to do
encaustic (wax-based) painting


Isolate your computers on their own circuit to protect them.

Are you going to have all the things running at once? Probably not.

John Cochran December 7th 07 01:20 PM

30A duplex receptacles possible?
 
In article ,
HerHusband wrote:

If you have balanced loads (i.e. two matching griddles), you could combine
a couple of circuits with a single 12/3 cable, sharing the neutral line.
Just make sure the two hot wires are on opposite legs of the incoming 240V
supply. This would reduce your cable runs somewhat, and is frequently done
for similar situations like kitchen wiring.

Actually, he wouldn't even need balanced loads. Using an Edison circuit
like that and breaking the brass tab on the duplex outlets would give
him some nice duplexes where he could draw 20 amps from both the top and
bottom outlets of a duplex.