Default York Heat Pump and furnace both run at the same time..is this normal?


I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.

The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.

Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?

thanks

Mark
  #2   Report Post  
Posted to alt.hvac,alt.home.repair
external usenet poster
 
Posts: 26
Default York Heat Pump and furnace both run at the same time..is this normal?


"Mark" wrote in message
...

I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.

The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.

Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?

thanks

Mark


It's wired wrong , they should NOT both run at the same time. Get the
installer back ASAP to correct the situation and shut off the HP until it's
fixed.Switch the T-stat to the Emerg.Heat position and leave the main power
on to the compressor


  #3   Report Post  
Posted to alt.hvac,alt.home.repair
external usenet poster
 
Posts: 35
Default York Heat Pump and furnace both run at the same time..is this normal?


"kool" wrote in message
news:Es0%i.212946$th2.45985@pd7urf3no...

"Mark" wrote in message
...

I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.

The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.

Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?

thanks

Mark


It's wired wrong , they should NOT both run at the same time. Get the
installer back ASAP to correct the situation and shut off the HP until

it's
fixed.Switch the T-stat to the Emerg.Heat position and leave the main

power
on to the compressor


Leave mains power to the compressor on ?

--


  #4   Report Post  
Posted to alt.hvac,alt.home.repair
external usenet poster
 
Posts: 190
Default York Heat Pump and furnace both run at the same time..is this normal?


"PrecisioNmachinisT" wrote in message
news:NN6dnRAHSfffO6HanZ2dnUVZ_tijnZ2d@scnresearch. com...

"kool" wrote in message
news:Es0%i.212946$th2.45985@pd7urf3no...

"Mark" wrote in message
...

I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.

The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.

Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?

thanks

Mark


It's wired wrong , they should NOT both run at the same time. Get the
installer back ASAP to correct the situation and shut off the HP until

it's
fixed.Switch the T-stat to the Emerg.Heat position and leave the main

power
on to the compressor


Leave mains power to the compressor on ?


yup.... compressor heater.


  #5   Report Post  
Posted to alt.hvac,alt.home.repair
external usenet poster
 
Posts: 35
Default York Heat Pump and furnace both run at the same time..is this normal?


"Noon-Air" wrote in message
. ..

"PrecisioNmachinisT" wrote in message
news:NN6dnRAHSfffO6HanZ2dnUVZ_tijnZ2d@scnresearch. com...

"kool" wrote in message
news:Es0%i.212946$th2.45985@pd7urf3no...

"Mark" wrote in message

...

I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.

The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.

Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the

controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?

thanks

Mark

It's wired wrong , they should NOT both run at the same time. Get the
installer back ASAP to correct the situation and shut off the HP until

it's
fixed.Switch the T-stat to the Emerg.Heat position and leave the main

power
on to the compressor


Leave mains power to the compressor on ?


yup.... compressor heater.


Okay thx threw me off there a sec..

--





  #6   Report Post  
Posted to alt.hvac, alt.home.repair
external usenet poster
 
Posts: 14,845
Default York Heat Pump and furnace both run at the same time..is thisnormal?

On Nov 15, 1:13 pm, Mark wrote:
I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.

The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.

Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?

thanks

Mark


Everything is working fine...

Based on the responses so far, perhaps that statement was a bit
premature. ;-)
  #7   Report Post  
Posted to alt.hvac, alt.home.repair
external usenet poster
 
Posts: 408
Default York Heat Pump and furnace both run at the same time..is thisnormal?

On Nov 15, 5:38 pm, DerbyDad03 wrote:
On Nov 15, 1:13 pm, Mark wrote:





I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.


The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.


Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?


thanks


Mark


Everything is working fine...

Based on the responses so far, perhaps that statement was a bit
premature. ;-)- Hide quoted text -

- Show quoted text -


well I've live din the house for 14 years and it has been fine..

I usually use the EM heat setting which is oil only, but with the
price of oil such as it is, I am starting to use the heat pump more
when it is above 30 deg F outside and I noticed this situation happens
occasionaly.

Mark

  #8   Report Post  
Posted to alt.hvac, alt.home.repair
external usenet poster
 
Posts: 408
Default York Heat Pump and furnace both run at the same time..is thisnormal?

On Nov 15, 10:36 pm, Mark wrote:
On Nov 15, 5:38 pm, DerbyDad03 wrote:





On Nov 15, 1:13 pm, Mark wrote:


I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.


The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.


Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?


thanks


Mark


Everything is working fine...


Based on the responses so far, perhaps that statement was a bit
premature. ;-)- Hide quoted text -


- Show quoted text -


well I've live din the house for 14 years and it has been fine..

I usually use the EM heat setting which is oil only, but with the
price of oil such as it is, I am starting to use the heat pump more
when it is above 30 deg F outside and I noticed this situation happens
occasionaly.

Mark- Hide quoted text -

- Show quoted text -


OK

I have traced the problem to the bonnet sensor. The compressor will
shut off when the bonnet sensor voltage gets below 3.75 Volts so the
controller works and is wired correctly. But the air temperature out
of the furnace and into the condensor gets well above 90 deg F and
the bonnet sensor voltage decreases only a little and is about 4.71
Volts when the air is 90 deg F. So I suspect the bonnet sensor is
bad. Does anybody know what the temperature vs resistance curve or
the voltage vs temperature for the bonnet sensor is supposed ot be so
that I can check it. It measures about 34 kOhms at room temperature.

thanks

Mark
  #9   Report Post  
Posted to alt.hvac, alt.home.repair
external usenet poster
 
Posts: 408
Default York Heat Pump and furnace both run at the same time..is thisnormal?

On Nov 16, 10:01 pm, Mark wrote:
On Nov 15, 10:36 pm, Mark wrote:





On Nov 15, 5:38 pm, DerbyDad03 wrote:


On Nov 15, 1:13 pm, Mark wrote:


I have a York combination system with an oil fired furnace and a heat
pump. Everything is working fine but I have a question about how the
heat pump and furnace work together.


The thermostat is a 2 stage, when the first stage calls for heat, the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is very
high at that point. I imagine I can hear the compressor straining to
pump heat into the already heated air and I'm thinking this can't be
good for the compressor.


Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the controls
be wired to turn the heat pump off immediately when the furnace comes
on for second stage?


thanks


Mark


Everything is working fine...


Based on the responses so far, perhaps that statement was a bit
premature. ;-)- Hide quoted text -


- Show quoted text -


well I've live din the house for 14 years and it has been fine..


I usually use the EM heat setting which is oil only, but with the
price of oil such as it is, I am starting to use the heat pump more
when it is above 30 deg F outside and I noticed this situation happens
occasionaly.


Mark- Hide quoted text -


- Show quoted text -


OK

I have traced the problem to the bonnet sensor. The compressor will
shut off when the bonnet sensor voltage gets below 3.75 Volts so the
controller works and is wired correctly. But the air temperature out
of the furnace and into the condensor gets well above 90 deg F and
the bonnet sensor voltage decreases only a little and is about 4.71
Volts when the air is 90 deg F. So I suspect the bonnet sensor is
bad. Does anybody know what the temperature vs resistance curve or
the voltage vs temperature for the bonnet sensor is supposed ot be so
that I can check it. It measures about 34 kOhms at room temperature.

thanks

Mark- Hide quoted text -

- Show quoted text -


Conclusion,,, it's fixed.

I replaceed the bonnet sensor with a 10 kOhm NTC thermistor. It works
perfectly now, when the second stage calls for heat, the furnace comes
on, when the bonnet temp reaches 91 deg F (and the senor voltage drpos
below 3.78Volts) the heat pump shuts off and the furnace continues to
run. When the second stage is satisfied, the furnace shuts off. When
the bonnet cools down to 89 deg F, (and the sensor voltge raises to
3.83 Volts) the heat pump comes back on. So with the correct bonnet
sensor in place, the heat pump never runs when the supply air is above
90. What I don't know is...if the sensor that was in there was the
wrong one from day one or if the sensor went bad. Either way...it's
fixed now. Thanks for the advice.
Mark

  #10   Report Post  
Posted to alt.hvac,alt.home.repair
external usenet poster
 
Posts: 190
Default York Heat Pump and furnace both run at the same time..is this normal?


"Mark" wrote in message
...
On Nov 16, 10:01 pm, Mark wrote:
On Nov 15, 10:36 pm, Mark wrote:





On Nov 15, 5:38 pm, DerbyDad03 wrote:


On Nov 15, 1:13 pm, Mark wrote:


I have a York combination system with an oil fired furnace and a
heat
pump. Everything is working fine but I have a question about how
the
heat pump and furnace work together.


The thermostat is a 2 stage, when the first stage calls for heat,
the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the
second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat
pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is
very
high at that point. I imagine I can hear the compressor straining
to
pump heat into the already heated air and I'm thinking this can't
be
good for the compressor.


Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the
controls
be wired to turn the heat pump off immediately when the furnace
comes
on for second stage?


thanks


Mark


Everything is working fine...


Based on the responses so far, perhaps that statement was a bit
premature. ;-)- Hide quoted text -


- Show quoted text -


well I've live din the house for 14 years and it has been fine..


I usually use the EM heat setting which is oil only, but with the
price of oil such as it is, I am starting to use the heat pump more
when it is above 30 deg F outside and I noticed this situation happens
occasionaly.


Mark- Hide quoted text -


- Show quoted text -


OK

I have traced the problem to the bonnet sensor. The compressor will
shut off when the bonnet sensor voltage gets below 3.75 Volts so the
controller works and is wired correctly. But the air temperature out
of the furnace and into the condensor gets well above 90 deg F and
the bonnet sensor voltage decreases only a little and is about 4.71
Volts when the air is 90 deg F. So I suspect the bonnet sensor is
bad. Does anybody know what the temperature vs resistance curve or
the voltage vs temperature for the bonnet sensor is supposed ot be so
that I can check it. It measures about 34 kOhms at room temperature.

thanks

Mark- Hide quoted text -

- Show quoted text -


Conclusion,,, it's fixed.

I replaceed the bonnet sensor with a 10 kOhm NTC thermistor. It works
perfectly now, when the second stage calls for heat, the furnace comes
on, when the bonnet temp reaches 91 deg F (and the senor voltage drpos
below 3.78Volts) the heat pump shuts off and the furnace continues to
run. When the second stage is satisfied, the furnace shuts off. When
the bonnet cools down to 89 deg F, (and the sensor voltge raises to
3.83 Volts) the heat pump comes back on. So with the correct bonnet
sensor in place, the heat pump never runs when the supply air is above
90. What I don't know is...if the sensor that was in there was the
wrong one from day one or if the sensor went bad. Either way...it's
fixed now. Thanks for the advice.
Mark


Now....if you actually had a clue......
The furnace heat and heat pump are not supposed to run at the same time.
when the heat pump runs, the furnace blower runs only to condition the air.
The *normal* air discharge temp for a heat pump is 95F - 105F.

The sensor that tells the system when to switch between the heat pump and
the furnace heat is the *OUTDOOR TEMP* sensor.

Here is some more food for thought.....
If the furnace heat runs at the same time as the heat pump, it will run the
refrigerant pressures through the roof and will eventually do terminal and
catastrophic damage to the compressor.

Still think you got it "fixed"??




  #11   Report Post  
Posted to alt.hvac, alt.home.repair
external usenet poster
 
Posts: 408
Default York Heat Pump and furnace both run at the same time..is thisnormal?

On Nov 25, 8:32 am, "Noon-Air" wrote:
"Mark" wrote in message

...





On Nov 16, 10:01 pm, Mark wrote:
On Nov 15, 10:36 pm, Mark wrote:


On Nov 15, 5:38 pm, DerbyDad03 wrote:


On Nov 15, 1:13 pm, Mark wrote:


I have a York combination system with an oil fired furnace and a
heat
pump. Everything is working fine but I have a question about how
the
heat pump and furnace work together.


The thermostat is a 2 stage, when the first stage calls for heat,
the
heat pump alone comes one. If the room temperature drops another
degree or so, the second stage calls for heat also and the furnace
then comes on. Here is where my question comes in. When the
second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat
pump
condenser input air is getting hotter and hotter. The heat pump is
trying to heat air that has already been heated by the furnace. At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due to a
high pressure safety or something and that the line pressure is
very
high at that point. I imagine I can hear the compressor straining
to
pump heat into the already heated air and I'm thinking this can't
be
good for the compressor.


Is it normal for a dual system to be designed so that the heat pump
and furnace both are operating at the same time or should the
controls
be wired to turn the heat pump off immediately when the furnace
comes
on for second stage?


thanks


Mark


Everything is working fine...


Based on the responses so far, perhaps that statement was a bit
premature. ;-)- Hide quoted text -


- Show quoted text -


well I've live din the house for 14 years and it has been fine..


I usually use the EM heat setting which is oil only, but with the
price of oil such as it is, I am starting to use the heat pump more
when it is above 30 deg F outside and I noticed this situation happens
occasionaly.


Mark- Hide quoted text -


- Show quoted text -


OK


I have traced the problem to the bonnet sensor. The compressor will
shut off when the bonnet sensor voltage gets below 3.75 Volts so the
controller works and is wired correctly. But the air temperature out
of the furnace and into the condensor gets well above 90 deg F and
the bonnet sensor voltage decreases only a little and is about 4.71
Volts when the air is 90 deg F. So I suspect the bonnet sensor is
bad. Does anybody know what the temperature vs resistance curve or
the voltage vs temperature for the bonnet sensor is supposed ot be so
that I can check it. It measures about 34 kOhms at room temperature.


thanks


Mark- Hide quoted text -


- Show quoted text -


Conclusion,,, it's fixed.


I replaceed the bonnet sensor with a 10 kOhm NTC thermistor. It works
perfectly now, when the second stage calls for heat, the furnace comes
on, when the bonnet temp reaches 91 deg F (and the senor voltage drpos
below 3.78Volts) the heat pump shuts off and the furnace continues to
run. When the second stage is satisfied, the furnace shuts off. When
the bonnet cools down to 89 deg F, (and the sensor voltge raises to
3.83 Volts) the heat pump comes back on. So with the correct bonnet
sensor in place, the heat pump never runs when the supply air is above
90. What I don't know is...if the sensor that was in there was the
wrong one from day one or if the sensor went bad. Either way...it's
fixed now. Thanks for the advice.
Mark


Now....if you actually had a clue......
The furnace heat and heat pump are not supposed to run at the same time.
when the heat pump runs, the furnace blower runs only to condition the air.
The *normal* air discharge temp for a heat pump is 95F - 105F.

The sensor that tells the system when to switch between the heat pump and
the furnace heat is the *OUTDOOR TEMP* sensor.

Here is some more food for thought.....
If the furnace heat runs at the same time as the heat pump, it will run the
refrigerant pressures through the roof and will eventually do terminal and
catastrophic damage to the compressor.

Still think you got it "fixed"??- Hide quoted text -

- Show quoted text -


the bonnet temp sensor is measuring the air coming out of the furnace
BEFORE it gets to the indoor coil.. it turns off the heat pump as soon
as the air out of the furnace and into the coil starts to get warm,
i.e. reaches about 90 deg F and yes it keeps the pressures from going
too high,,,

read this about how it is supposed to work:

http://johnsonsupply.com/york2001/PU...1/OUT/N10y.pdf

Mark
  #12   Report Post  
Posted to alt.hvac,alt.home.repair
external usenet poster
 
Posts: 14
Default York Heat Pump and furnace both run at the same time..is this normal?


"Mark" wrote in message
...
On Nov 25, 8:32 am, "Noon-Air" wrote:
"Mark" wrote in message

...





On Nov 16, 10:01 pm, Mark wrote:
On Nov 15, 10:36 pm, Mark wrote:


On Nov 15, 5:38 pm, DerbyDad03 wrote:


On Nov 15, 1:13 pm, Mark wrote:


I have a York combination system with an oil fired furnace and a
heat
pump. Everything is working fine but I have a question about
how
the
heat pump and furnace work together.


The thermostat is a 2 stage, when the first stage calls for
heat,
the
heat pump alone comes one. If the room temperature drops
another
degree or so, the second stage calls for heat also and the
furnace
then comes on. Here is where my question comes in. When the
second
stage calls for heat and the furnace comes on, the heat pump
compressor still remains on. As the furnace heats up, the heat
pump
condenser input air is getting hotter and hotter. The heat pump
is
trying to heat air that has already been heated by the furnace.
At
some point when the furnace warms up enough, the heat pump does
eventually shut off , but it seems that it is shutting off due
to a
high pressure safety or something and that the line pressure is
very
high at that point. I imagine I can hear the compressor
straining
to
pump heat into the already heated air and I'm thinking this
can't
be
good for the compressor.


Is it normal for a dual system to be designed so that the heat
pump
and furnace both are operating at the same time or should the
controls
be wired to turn the heat pump off immediately when the furnace
comes
on for second stage?


thanks


Mark


Everything is working fine...


Based on the responses so far, perhaps that statement was a bit
premature. ;-)- Hide quoted text -


- Show quoted text -


well I've live din the house for 14 years and it has been fine..


I usually use the EM heat setting which is oil only, but with the
price of oil such as it is, I am starting to use the heat pump more
when it is above 30 deg F outside and I noticed this situation
happens
occasionaly.


Mark- Hide quoted text -


- Show quoted text -


OK


I have traced the problem to the bonnet sensor. The compressor will
shut off when the bonnet sensor voltage gets below 3.75 Volts so the
controller works and is wired correctly. But the air temperature out
of the furnace and into the condensor gets well above 90 deg F and
the bonnet sensor voltage decreases only a little and is about 4.71
Volts when the air is 90 deg F. So I suspect the bonnet sensor is
bad. Does anybody know what the temperature vs resistance curve or
the voltage vs temperature for the bonnet sensor is supposed ot be so
that I can check it. It measures about 34 kOhms at room temperature.


thanks


Mark- Hide quoted text -


- Show quoted text -


Conclusion,,, it's fixed.


I replaceed the bonnet sensor with a 10 kOhm NTC thermistor. It works
perfectly now, when the second stage calls for heat, the furnace comes
on, when the bonnet temp reaches 91 deg F (and the senor voltage drpos
below 3.78Volts) the heat pump shuts off and the furnace continues to
run. When the second stage is satisfied, the furnace shuts off. When
the bonnet cools down to 89 deg F, (and the sensor voltge raises to
3.83 Volts) the heat pump comes back on. So with the correct bonnet
sensor in place, the heat pump never runs when the supply air is above
90. What I don't know is...if the sensor that was in there was the
wrong one from day one or if the sensor went bad. Either way...it's
fixed now. Thanks for the advice.
Mark


Now....if you actually had a clue......
The furnace heat and heat pump are not supposed to run at the same time.
when the heat pump runs, the furnace blower runs only to condition the
air.
The *normal* air discharge temp for a heat pump is 95F - 105F.

The sensor that tells the system when to switch between the heat pump and
the furnace heat is the *OUTDOOR TEMP* sensor.

Here is some more food for thought.....
If the furnace heat runs at the same time as the heat pump, it will run
the
refrigerant pressures through the roof and will eventually do terminal
and
catastrophic damage to the compressor.

Still think you got it "fixed"??- Hide quoted text -

- Show quoted text -


the bonnet temp sensor is measuring the air coming out of the furnace
BEFORE it gets to the indoor coil.. it turns off the heat pump as soon
as the air out of the furnace and into the coil starts to get warm,
i.e. reaches about 90 deg F and yes it keeps the pressures from going
too high,,,

read this about how it is supposed to work:

http://johnsonsupply.com/york2001/PU...1/OUT/N10y.pdf


Depending on the climate conditions, my Trane system, calls for the oil
burner
to run during the Defrost cycle to keep the air warm to the output plenum
because it is actually in the cooling mode.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
York Heat Pump PLS Help troubleshoot timO' Home Repair 1 May 20th 07 04:38 AM
York heat pump William Stacy Home Repair 0 December 11th 05 05:31 PM
York heat pump William Stacy Home Repair 3 December 9th 05 08:41 AM
York heat pump PrecisionMachinisT Home Repair 0 December 7th 05 06:33 AM
2 year old York heat pump [email protected] Home Ownership 0 June 15th 05 03:07 AM


All times are GMT +1. The time now is 07:41 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"