  #1   Report Post  
Posted to alt.home.repair
JB JB is offline
external usenet poster
 
Posts: 63
Default Wiring All Kitchen Lights on One Circuit?

As part of a kitchen remodeling job, I am replacing a single overhead
fluorescent fixture with ~7 recessed cans and then a bunch of undercab
lights (either halogens or small fluor. boxes). Since the existing
fixture is part of a circuit that goes elsewhere in the house, I
calculated that all of those recessed lights would be too much for the
line. So I'm planning on running a new, dedicated 15A or 20A line.

Assuming the loads are within the capacity of the line (which I think
it is), the question is whether there is anything wrong with having
ALL of the lights -- overhead and undercab -- on this single circuit.
It seems OK to me but just checking.

--Jeff

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Wiring All Kitchen Lights on One Circuit?

On Nov 12, 9:52?am, JB wrote:
As part of a kitchen remodeling job, I am replacing a single overhead
fluorescent fixture with ~7 recessed cans and then a bunch of undercab
lights (either halogens or small fluor. boxes). Since the existing
fixture is part of a circuit that goes elsewhere in the house, I
calculated that all of those recessed lights would be too much for the
line. So I'm planning on running a new, dedicated 15A or 20A line.

Assuming the loads are within the capacity of the line (which I think
it is), the question is whether there is anything wrong with having
ALL of the lights -- overhead and undercab -- on this single circuit.
It seems OK to me but just checking.

--Jeff


oinstall at least 2 switches one for undercabinet, and one for general
overhead, perhaps one for task lighting at sink.

at night the undercabinet ones are nifty.

its CRITICAL you install at least 2 20 amp GFCI counter outlet groups,
give fridge its own circuit, dishwasher its own circuit better if
disposer is on its own, perhaps shared with gas stove if you use gas.

you will need 6 or 7 seperate breakers will your main panel accomdate
it?

kitchens are power hungry areas with many appliances

  #3   Report Post  
Posted to alt.home.repair
JB JB is offline
external usenet poster
 
Posts: 63
Default Wiring All Kitchen Lights on One Circuit?

On Nov 12, 10:04 am, " wrote:
On Nov 12, 9:52?am, JB wrote:

As part of a kitchen remodeling job, I am replacing a single overhead
fluorescent fixture with ~7 recessed cans and then a bunch of undercab
lights (either halogens or small fluor. boxes). Since the existing
fixture is part of a circuit that goes elsewhere in the house, I
calculated that all of those recessed lights would be too much for the
line. So I'm planning on running a new, dedicated 15A or 20A line.


Assuming the loads are within the capacity of the line (which I think
it is), the question is whether there is anything wrong with having
ALL of the lights -- overhead and undercab -- on this single circuit.
It seems OK to me but just checking.


--Jeff


oinstall at least 2 switches one for undercabinet, and one for general
overhead, perhaps one for task lighting at sink.

at night the undercabinet ones are nifty.

its CRITICAL you install at least 2 20 amp GFCI counter outlet groups,
give fridge its own circuit, dishwasher its own circuit better if
disposer is on its own, perhaps shared with gas stove if you use gas.

you will need 6 or 7 seperate breakers will your main panel accomdate
it?

kitchens are power hungry areas with many appliances


Everything you describe (except for the undercab lighting) is already
there.

--Jeff

  #4   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Wiring All Kitchen Lights on One Circuit?

JB wrote:
As part of a kitchen remodeling job, I am replacing a single overhead
fluorescent fixture with ~7 recessed cans and then a bunch of undercab
lights (either halogens or small fluor. boxes). Since the existing
fixture is part of a circuit that goes elsewhere in the house, I
calculated that all of those recessed lights would be too much for the
line. So I'm planning on running a new, dedicated 15A or 20A line.

Assuming the loads are within the capacity of the line (which I think
it is), the question is whether there is anything wrong with having
ALL of the lights -- overhead and undercab -- on this single circuit.
It seems OK to me but just checking.


It's fine by code -- the only thing is convenience. If you were to trip
a breaker on this lighting circuit at night is there sufficient light in
the area to cope well enough without a second lighting circuit? Same
reason it's best to not have all lights in any area on a single circuit.

--
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 627
Default Wiring All Kitchen Lights on One Circuit?

Good idea to place lighting on a separate circuit. Then if outlet trips
breaker, you still have lighting.

"JB" wrote in message
As part of a kitchen remodeling job, I am replacing a single overhead
fluorescent fixture with ~7 recessed cans and then a bunch of undercab
lights (either halogens or small fluor. boxes). Since the existing
fixture is part of a circuit that goes elsewhere in the house, I
calculated that all of those recessed lights would be too much for the
line. So I'm planning on running a new, dedicated 15A or 20A line.

Assuming the loads are within the capacity of the line (which I think
it is), the question is whether there is anything wrong with having
ALL of the lights -- overhead and undercab -- on this single circuit.
It seems OK to me but just checking.

--Jeff





  #6   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Wiring All Kitchen Lights on One Circuit?

dpb wrote:
JB wrote:
As part of a kitchen remodeling job, I am replacing a single overhead
fluorescent fixture with ~7 recessed cans and then a bunch of undercab
lights (either halogens or small fluor. boxes). Since the existing
fixture is part of a circuit that goes elsewhere in the house, I
calculated that all of those recessed lights would be too much for the
line. So I'm planning on running a new, dedicated 15A or 20A line.

Assuming the loads are within the capacity of the line (which I think
it is), the question is whether there is anything wrong with having
ALL of the lights -- overhead and undercab -- on this single circuit.
It seems OK to me but just checking.


It's fine by code -- the only thing is convenience. If you were to trip
a breaker on this lighting circuit at night is there sufficient light in
the area to cope well enough without a second lighting circuit? Same
reason it's best to not have all lights in any area on a single circuit.


That is more specifically, I'd recommend leaving at least a couple on
the existing circuit and add the new one as well...

--
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Wiring All Kitchen Lights on One Circuit?

On Nov 12, 10:26 am, dpb wrote:
JB wrote:
As part of a kitchen remodeling job, I am replacing a single overhead
fluorescent fixture with ~7 recessed cans and then a bunch of undercab
lights (either halogens or small fluor. boxes). Since the existing
fixture is part of a circuit that goes elsewhere in the house, I
calculated that all of those recessed lights would be too much for the
line. So I'm planning on running a new, dedicated 15A or 20A line.


Assuming the loads are within the capacity of the line (which I think
it is), the question is whether there is anything wrong with having
ALL of the lights -- overhead and undercab -- on this single circuit.
It seems OK to me but just checking.


It's fine by code -- the only thing is convenience. If you were to trip
a breaker on this lighting circuit at night is there sufficient light in
the area to cope well enough without a second lighting circuit? Same
reason it's best to not have all lights in any area on a single circuit.

--


I'd definitely put the under-counter lights on a seperate switch.
There could be times you want them on seperately from the ceiling
lights or vis-versa. And it's the more customary way to do it.

I went through same thing with my family room remodel. I was thinking
of having the lights above the fireplace tied to the recessed general
lighting. Glad now that I didn't. I don't put the lights above the
fireplace on that much and it would just be a waste of energy most of
the time.

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Wiring All Kitchen Lights on One Circuit?

On Nov 12, 10:37 am, dpb wrote:
wrote:
On Nov 12, 10:26 am, dpb wrote:
JB wrote:
As part of a kitchen remodeling job, I am replacing a single overhead
fluorescent fixture with ~7 recessed cans and then a bunch of undercab
lights (either halogens or small fluor. boxes). Since the existing
fixture is part of a circuit that goes elsewhere in the house, I
calculated that all of those recessed lights would be too much for the
line. So I'm planning on running a new, dedicated 15A or 20A line.
Assuming the loads are within the capacity of the line (which I think
it is), the question is whether there is anything wrong with having
ALL of the lights -- overhead and undercab -- on this single circuit.
It seems OK to me but just checking.
It's fine by code -- the only thing is convenience. If you were to trip
a breaker on this lighting circuit at night is there sufficient light in
the area to cope well enough without a second lighting circuit? Same
reason it's best to not have all lights in any area on a single circuit.


--


I'd definitely put the under-counter lights on a seperate switch.


...

That's a different question than which circuit powers them...


Yes, point well taken. I misread the question.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 129
Default Wiring All Kitchen Lights on One Circuit?

I think the main question here is how would you trip the breaker, if only
lights were on it?

and there's always a flashlight.


steve


"dpb" wrote in message ...

It's fine by code -- the only thing is convenience. If you were to trip a
breaker on this lighting circuit at night is there sufficient light in the
area to cope well enough without a second lighting circuit? Same reason
it's best to not have all lights in any area on a single circuit.

--





  #11   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Wiring All Kitchen Lights on One Circuit?

Steve Barker wrote:
I think the main question here is how would you trip the breaker, if only
lights were on it?


"Stuff" happens...

and there's always a flashlight.

,,,

And in a dark kitchen w/ hot stuff on a stove or similar, fumbling
around in the dark to find it can be sorta' risky when it's easy enough
to ensure the situation is protected against...

--
  #12   Report Post  
Posted to alt.home.repair
JB JB is offline
external usenet poster
 
Posts: 63
Default Wiring All Kitchen Lights on One Circuit?

On Nov 12, 12:26 pm, dpb wrote:
Steve Barker wrote:
I think the main question here is how would you trip the breaker, if only
lights were on it?


"Stuff" happens...

and there's always a flashlight.


,,,

And in a dark kitchen w/ hot stuff on a stove or similar, fumbling
around in the dark to find it can be sorta' risky when it's easy enough
to ensure the situation is protected against...

--


Folks...thanks for the tips and feedback. In my case, the chandelier
in the connected dining room in one direction and hall lights in the
other would give plenty of light during a circuit trip. They are on a
different line.

--Jeff

  #13   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Wiring All Kitchen Lights on One Circuit?

JB wrote:
On Nov 12, 12:26 pm, dpb wrote:
Steve Barker wrote:
I think the main question here is how would you trip the breaker, if only
lights were on it?

"Stuff" happens...

and there's always a flashlight.

,,,

And in a dark kitchen w/ hot stuff on a stove or similar, fumbling
around in the dark to find it can be sorta' risky when it's easy enough
to ensure the situation is protected against...

--


Folks...thanks for the tips and feedback. In my case, the chandelier
in the connected dining room in one direction and hall lights in the
other would give plenty of light during a circuit trip. They are on a
different line.


That sounds adequate, then I'd not worry about it...

--
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Wiring All Kitchen Lights on One Circuit?

Usually there is a light in the range hood as well, if it comes to that.
What hasn't been mentioned yet is there is a maximum number of drops
permitted on a circuit. I believe it is 12 but I'll be quickly corrected if
I'm wrong. So provided that your ~7 cans and bunch of cabinet lights = 12 or
less, you're fine with the one line.



"JB" wrote in message
ups.com...
On Nov 12, 12:26 pm, dpb wrote:
Steve Barker wrote:
I think the main question here is how would you trip the breaker, if
only
lights were on it?


"Stuff" happens...

and there's always a flashlight.


,,,

And in a dark kitchen w/ hot stuff on a stove or similar, fumbling
around in the dark to find it can be sorta' risky when it's easy enough
to ensure the situation is protected against...

--


Folks...thanks for the tips and feedback. In my case, the chandelier
in the connected dining room in one direction and hall lights in the
other would give plenty of light during a circuit trip. They are on a
different line.

--Jeff



  #15   Report Post  
Posted to alt.home.repair
JB JB is offline
external usenet poster
 
Posts: 63
Default Wiring All Kitchen Lights on One Circuit?

On Nov 13, 9:19 am, "Jeff" wrote:
What hasn't been mentioned yet is there is a maximum number of drops

permitted on a circuit. I believe it is 12 but I'll be quickly corrected if
I'm wrong. So provided that your ~7 cans and bunch of cabinet lights = 12 or
less, you're fine with the one line.


Sorry, I don't see that in the code. 210.11 (A) talks about the
MINUMUM number of circuits based on load, but I don't see a MAXIMUM
number off of a breaker mentioned anywhere. Am I missing something??

--Jeff



  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Wiring All Kitchen Lights on One Circuit?

Sorry about that, I hadn't realized this was specific to Canadian code. A
quick Google search confirms a 12 drop limit in Canada, no specific limit
USA.


wrote in message
...
On Tue, 13 Nov 2007 11:11:55 -0800, JB wrote:

On Nov 13, 9:19 am, "Jeff" wrote:
What hasn't been mentioned yet is there is a maximum number of drops
permitted on a circuit. I believe it is 12 but I'll be quickly corrected
if
I'm wrong. So provided that your ~7 cans and bunch of cabinet lights =
12 or
less, you're fine with the one line.


Sorry, I don't see that in the code. 210.11 (A) talks about the
MINUMUM number of circuits based on load, but I don't see a MAXIMUM
number off of a breaker mentioned anywhere. Am I missing something??

--Jeff


He has a Canada address, they have different rules



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
wiring 4 pot lights in a circuit [email protected] Home Repair 4 August 18th 07 02:54 AM
Lights on the wrong circuit? Dave[_2_] UK diy 3 July 21st 07 04:38 PM
Lights keep going out, without Circuit Tripping [email protected] Home Repair 19 August 25th 06 03:25 AM
Kitchen lights on ring circuit antgel UK diy 6 June 13th 05 09:40 AM
how many recessed lights to a circuit? SaM Home Repair 3 August 29th 04 04:28 PM


All times are GMT +1. The time now is 07:08 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"