Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
A co-worker, who should *not* be doing his own wiring attempted to add
a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. His simple mind told him that if S1 controls LF1 via the black and white from LF1, then all he had to do was run a length of romex from LF2 and attach black to black and white to white at S1. Here's the reported result of his ignorance: He says that if S1 is on, LF1 is on and LF2 is off. That makes sense to me. However, he says that if he turns S1 off, LF1 goes off and LF2 comes on. If this is wired the way I think it is, then shouldn't *both* LF1 and LF2 come on when S1 is off? LF2 is in parallel with an open S1 and LF1 is now in series with LF2? Wouldn't that create a complete circuit through both fixtures? Does the fact that LF2 holds a compact fluorescent enter into this? |
#2
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 10:26 am, DerbyDad03 wrote:
A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. If there is only one romex coming into the box, that is out of the ordinary. You should have at least 2 romex, with one being the feed, other going to LF1. Could also be other romex that tap off feed at that point, etc. His simple mind told him that if S1 controls LF1 via the black and white from LF1, then all he had to do was run a length of romex from LF2 and attach black to black and white to white at S1. That is exactly correct. IF wired that way, it would work. The other choice would have been to run a romex from the switcht to then new fixture, if it were easier. Either way they wind up in parallel and have to go on and off together. Here's the reported result of his ignorance: He says that if S1 is on, LF1 is on and LF2 is off. That makes sense to me. However, he says that if he turns S1 off, LF1 goes off and LF2 comes on. If this is wired the way I think it is, then shouldn't *both* LF1 and LF2 come on when S1 is off? No, they should both come on when S1 is on. LF2 is in parallel with an open S1 and LF1 is now in series with LF2? Wouldn't that create a complete circuit through both fixtures? It can't be wired the way he's telling you, or both would go on and off together, simple as that. Does the fact that LF2 holds a compact fluorescent enter into this? No. |
#3
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 10:26 am, DerbyDad03 wrote:
A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. His simple mind told him that if S1 controls LF1 via the black and white from LF1, then all he had to do was run a length of romex from LF2 and attach black to black and white to white at S1. Here's the reported result of his ignorance: He says that if S1 is on, LF1 is on and LF2 is off. That makes sense to me. However, he says that if he turns S1 off, LF1 goes off and LF2 comes on. If this is wired the way I think it is, then shouldn't *both* LF1 and LF2 come on when S1 is off? LF2 is in parallel with an open S1 and LF1 is now in series with LF2? Wouldn't that create a complete circuit through both fixtures? Does the fact that LF2 holds a compact fluorescent enter into this? Sounds strange to me as well. Possibly LF2 is completing the circuit back through the ground and bypassing LF1 by following the path of least resistance. |
#4
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 10:26 am, DerbyDad03 wrote:
A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. His simple mind told him that if S1 controls LF1 via the black and white from LF1, then all he had to do was run a length of romex from LF2 and attach black to black and white to white at S1. Here's the reported result of his ignorance: He says that if S1 is on, LF1 is on and LF2 is off. That makes sense to me. However, he says that if he turns S1 off, LF1 goes off and LF2 comes on. If this is wired the way I think it is, then shouldn't *both* LF1 and LF2 come on when S1 is off? LF2 is in parallel with an open S1 and LF1 is now in series with LF2? Wouldn't that create a complete circuit through both fixtures? Does the fact that LF2 holds a compact fluorescent enter into this? This is a stretch, but a possibility. If he put white wire 2 (w2) and b2 onto different screws in the switch (because they were sitting there not doing anything) instead of onto the same screw as the existing wires, AND that the switch happened to be a double-throw switch; then you would get the situation that you described. |
#6
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 12:54 pm, wrote:
On Nov 6, 10:26 am, DerbyDad03 wrote: A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. If there is only one romex coming into the box, that is out of the ordinary. You should have at least 2 romex, with one being the feed, other going to LF1. Could also be other romex that tap off feed at that point, etc. His simple mind told him that if S1 controls LF1 via the black and white from LF1, then all he had to do was run a length of romex from LF2 and attach black to black and white to white at S1. That is exactly correct. IF wired that way, it would work. The other choice would have been to run a romex from the switch to then new fixture, if it were easier. Either way they wind up in parallel and have to go on and off together. Here's the reported result of his ignorance: He says that if S1 is on, LF1 is on and LF2 is off. That makes sense to me. However, he says that if he turns S1 off, LF1 goes off and LF2 comes on. If this is wired the way I think it is, then shouldn't *both* LF1 and LF2 come on when S1 is off? No, they should both come on when S1 is on. LF2 is in parallel with an open S1 and LF1 is now in series with LF2? Wouldn't that create a complete circuit through both fixtures? It can't be wired the way he's telling you, or both would go on and off together, simple as that. Does the fact that LF2 holds a compact fluorescent enter into this? No.- Hide quoted text - - Show quoted text - Without getting into black connected to black and white to white etc. it sounds as though his new wiring to LF2 is connected 'across' the switch? So when the switch is 'off' electricity then is flowing through LF2 and then on its way to LF1. In other words the two lights are 'in series' and electricity is flowing through both of them? In other words electricity is now never off. It's on all the time? The reason for LF2 lighting is probably because with LF2 and LF 1 in series the compact fluorescent which takes much less electricity gets enough voltage to light. One way to check this assumption is to exchange the two lamps (the regular bulb and the CFL) and it should be found that then LF1 (the CFL) will light with the switch off? Gee it takes longer to write this up than to do it! But should that individual really be doing any wiring at all????? Has the proper wire been used? Items grounded as required? Is the LF2 lamp socket wired with correct polarity? Wires clamped properly? Etc. etc. |
#7
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
wrote in message ups.com... On Nov 6, 10:26 am, DerbyDad03 wrote: A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. If there is only one romex coming into the box, that is out of the ordinary. You should have at least 2 romex, with one being the feed, other going to LF1. Could also be other romex that tap off feed at that point, etc. That's actually quite common. Power for LF1 is fed directly to LF1. The black wire in the LF1 box connects to one of the wires heading to S1. The other wire from S1 connect to the hot side of LF1. This circuit is controlled by the position of S1. S1 ---------------------Hot---LF1---Ground ----------------------------- Power Source W \-------------------------------------------------------------------------- Power Source B |
#8
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 11:09 am, (Doug Miller) wrote:
In article . com, wrote: If there is only one romex coming into the box, that is out of the ordinary. You should have at least 2 romex, with one being the feed, other going to LF1. Could also be other romex that tap off feed at that point, etc. No, that's perfectly normal -- it's called a switch leg. Power feed comes into the box at the light fixture, and is tied to the white wire of the switch leg, which goes to one side of the switch. The black wire of the switch leg goes to the other side of the switch, and to the black fixture wire. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. Agreed...I have no problem with the way the LF1 is switched. But, Doug...of all people ;-) you didn't comment on why only LF2 is on with the switch off. Any thoughts? |
#9
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
According to DerbyDad03 :
A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. It's the hot and switched hot. _No_ neutral. This is a switch leg, you can't get "proper" power from the switch end of this circuit. When S1 is on, LF1 will be on, but the leads to LF2 are shorted by the switch. When S1 is off, LF1 and LF2 are in series. Since LF2 is a CF, it's current draw is very low, and it lights up, but the current is insufficient to visibly light LF1. If LF1 and LF2 were identical incandescent bulbs, they'd both light dimly. If they were both CFs, can't predict precisely what they do without knowing what the CFs do with 60V. Might not do anything. He needs to take the wire from LF2 off S1, and move it to be across the leads on LF1 (inside the LF1 junction box). Eg: LF2's black wire wirenutted to the wire going to the center pin on LF1's bulb base, and white wire wirenutted to the wire going to LF2's base shell. Then the voltage seen on both bulb bases will be identical. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#10
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 11:10 am, terry wrote:
On Nov 6, 12:54 pm, wrote: On Nov 6, 10:26 am, DerbyDad03 wrote: A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. If there is only one romex coming into the box, that is out of the ordinary. You should have at least 2 romex, with one being the feed, other going to LF1. Could also be other romex that tap off feed at that point, etc. His simple mind told him that if S1 controls LF1 via the black and white from LF1, then all he had to do was run a length of romex from LF2 and attach black to black and white to white at S1. That is exactly correct. IF wired that way, it would work. The other choice would have been to run a romex from the switch to then new fixture, if it were easier. Either way they wind up in parallel and have to go on and off together. Here's the reported result of his ignorance: He says that if S1 is on, LF1 is on and LF2 is off. That makes sense to me. However, he says that if he turns S1 off, LF1 goes off and LF2 comes on. If this is wired the way I think it is, then shouldn't *both* LF1 and LF2 come on when S1 is off? No, they should both come on when S1 is on. LF2 is in parallel with an open S1 and LF1 is now in series with LF2? Wouldn't that create a complete circuit through both fixtures? It can't be wired the way he's telling you, or both would go on and off together, simple as that. Does the fact that LF2 holds a compact fluorescent enter into this? No.- Hide quoted text - - Show quoted text - Without getting into black connected to black and white to white etc. it sounds as though his new wiring to LF2 is connected 'across' the switch? So when the switch is 'off' electricity then is flowing through LF2 and then on its way to LF1. In other words the two lights are 'in series' and electricity is flowing through both of them? In other words electricity is now never off. It's on all the time? The reason for LF2 lighting is probably because with LF2 and LF 1 in series the compact fluorescent which takes much less electricity gets enough voltage to light. One way to check this assumption is to exchange the two lamps (the regular bulb and the CFL) and it should be found that then LF1 (the CFL) will light with the switch off? Gee it takes longer to write this up than to do it! But should that individual really be doing any wiring at all????? Has the proper wire been used? Items grounded as required? Is the LF2 lamp socket wired with correct polarity? Wires clamped properly? Etc. etc.- Hide quoted text - - Show quoted text - But should that individual really be doing any wiring at all? That's why I started my post with: "A co-worker, who should *not* be doing his own wiring..." This is the second time he's come to me with questions *after* what he's attempted has not worked, always adding "electrical wiring is not my strong suit." The scary part is that he's never questioned anything that's he's done that *did* work. |
#11
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
According to DerbyDad03 :
But, Doug...of all people ;-) you didn't comment on why only LF2 is on with the switch off. See my other posting. When you put a 100W incandescent in series with a, say, 13W CF, the CF is passing so little current that the IC bulb may not visibly light up at all, or only have a faint red glow. If they were both ICs of the same wattage, they'd both light up (dimly). -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#12
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
In article om, DerbyDad03 wrote:
On Nov 6, 11:09 am, (Doug Miller) wrote: In article . com, wrote: If there is only one romex coming into the box, that is out of the ordinary. You should have at least 2 romex, with one being the feed, other going to LF1. Could also be other romex that tap off feed at that point, etc. No, that's perfectly normal -- it's called a switch leg. Power feed comes into the box at the light fixture, and is tied to the white wire of the switch leg, which goes to one side of the switch. The black wire of the switch leg goes to the other side of the switch, and to the black fixture wire. Agreed...I have no problem with the way the LF1 is switched. But, Doug...of all people ;-) you didn't comment on why only LF2 is on with the switch off. That's because I'm still trying to figure it out!! Any thoughts? My first thought is that something there is *not* as it was described to you. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#13
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 11:33 am, (Chris Lewis) wrote:
According to DerbyDad03 : A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. It's the hot and switched hot. _No_ neutral. This is a switch leg, you can't get "proper" power from the switch end of this circuit. I knew that ;-) but he sure didn't. He always comes to me *after* he's screwed something up. When S1 is on, LF1 will be on, but the leads to LF2 are shorted by the switch. When S1 is off, LF1 and LF2 are in series. Since LF2 is a CF, it's current draw is very low, and it lights up, but the current is insufficient to visibly light LF1. If LF1 and LF2 were identical incandescent bulbs, they'd both light dimly. If they were both CFs, can't predict precisely what they do without knowing what the CFs do with 60V. Might not do anything. He needs to take the wire from LF2 off S1, and move it to be across the leads on LF1 (inside the LF1 junction box). Eg: LF2's black wire wirenutted to the wire going to the center pin on LF1's bulb base, and white wire wirenutted to the wire going to LF2's base shell. Then the voltage seen on both bulb bases will be identical. Yep ,that's exactly how I told him it should be wired, but I wasn't sure why only the CF lit. It makes sense that's it's a current issue. Now he has another problem...He opened LF1 and found that it is being used as a junction box (not his doing) to supply power to an outlet in the mudroom and an outside light with it's own switch. The key point being there are already at least 4 pieces of Romex coming into LF1 (source in, outlet out, S1 in/out, S2 in/out) therefore, I'm sure the box is way too crowded for another length of Romex from LF2. |
#14
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
|
#16
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
In article . com, DerbyDad03 wrote:
Now he has another problem...He opened LF1 and found that it is being used as a junction box (not his doing) to supply power to an outlet in the mudroom and an outside light with it's own switch. The key point being there are already at least 4 pieces of Romex coming into LF1 (source in, outlet out, S1 in/out, S2 in/out) therefore, I'm sure the box is way too crowded for another length of Romex from LF2. That's what they make extension rings for: you double the capacity of the box at the cost of two or three dollars and five minutes of work. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#17
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Tue, 06 Nov 2007 07:26:23 -0800, DerbyDad03
wrote: A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. His simple mind told him that if S1 controls LF1 via the black and white from LF1, then all he had to do was run a length of romex from LF2 and attach black to black and white to white at S1. Here's the reported result of his ignorance: He says that if S1 is on, LF1 is on and LF2 is off. That makes sense to me. However, he says that if he turns S1 off, LF1 goes off and LF2 comes on. If this is wired the way I think it is, then shouldn't *both* LF1 and LF2 come on when S1 is off? LF2 is in parallel with an open S1 and LF1 is now in series with LF2? Wouldn't that create a complete circuit through both fixtures? If could be that LF2 is drawing insufficient current to light LF1. In this case, unscrewing the bulb in LF1 will make LF2 go out. Does the fact that LF2 holds a compact fluorescent enter into this? I don't remember ever knowing as little about electricity as some people. BTW, this should be fixable by wiring LF2 across LF1 rather than the switch. -- 49 days until the winter solstice celebration Mark Lloyd http://notstupid.laughingsquid.com "Unlike biological evolution. 'intelligent design' is not a genuine scientific theory and, therefore, has no place in the curriculum of our nation's public school classes." -- Ted Kennedy |
#18
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
|
#20
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Tue, 06 Nov 2007 07:26:23 -0800, DerbyDad03
wrote: A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Light Fixture 1 (LF1) is an existing ceiling fixture in the mud room. An existing Switch (S1) controls LF1. He added LF2, a second ceiling fixture in the mud room, and wants to control it with S1. LF1 holds an incandescent bulb and LF2 holds a compact fluorescent. He took the cover off of S1 and found a black and white from length of Romex attached to S1. That's all that was in the box. So far, nothing out of the ordinary, as far as I can tell. I'm assuming this length of Romex is the switched hot from LF1. His simple mind told him that if S1 controls LF1 via the black and white from LF1, then all he had to do was run a length of romex from LF2 and attach black to black and white to white at S1. Here's the reported result of his ignorance: He says that if S1 is on, LF1 is on and LF2 is off. That makes sense to me. However, he says that if he turns S1 off, LF1 goes off and LF2 comes on. If this is wired the way I think it is, then shouldn't *both* LF1 and LF2 come on when S1 is off? LF2 is in parallel with an open S1 and LF1 is now in series with LF2? Wouldn't that create a complete circuit through both fixtures? Does the fact that LF2 holds a compact fluorescent enter into this? Sounds like S1 is a 3-way switch, then the above makes sense. Typically 3-way switch will not have "ON" nor "OFF" printed on the switch. It doesn't matter if LF2 is fluorescent or incandescent. |
#21
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
Terry wrote: On Tue, 06 Nov 2007 16:38:35 GMT, (Doug Miller) wrote: In article om, DerbyDad03 wrote: On Nov 6, 11:09 am, (Doug Miller) wrote: In article . com, wrote: If there is only one romex coming into the box, that is out of the ordinary. You should have at least 2 romex, with one being the feed, other going to LF1. Could also be other romex that tap off feed at that point, etc. No, that's perfectly normal -- it's called a switch leg. Power feed comes into the box at the light fixture, and is tied to the white wire of the switch leg, which goes to one side of the switch. The black wire of the switch leg goes to the other side of the switch, and to the black fixture wire. Agreed...I have no problem with the way the LF1 is switched. But, Doug...of all people ;-) you didn't comment on why only LF2 is on with the switch off. That's because I'm still trying to figure it out!! Any thoughts? My first thought is that something there is *not* as it was described to you. With the swtich open the two lights are in series. With the switch closed L2 is shorted. And to add to that, the CFL lamp is a lower wattage than the incandescent. As they are in series, most of the voltage will be across the CFL, so it will light. Also, there are peculiarities of both lamps, i.e. the incandescent lamp has a very low resistance when not lit and the CFL, having electronics in it, can do weird things. But, this seems perfectly normal for the abnormal wiring. |
#22
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 11:51 am, (Doug Miller) wrote:
In article . com, DerbyDad03 wrote: Now he has another problem...He opened LF1 and found that it is being used as a junction box (not his doing) to supply power to an outlet in the mudroom and an outside light with it's own switch. The key point being there are already at least 4 pieces of Romex coming into LF1 (source in, outlet out, S1 in/out, S2 in/out) therefore, I'm sure the box is way too crowded for another length of Romex from LF2. That's what they make extension rings for: you double the capacity of the box at the cost of two or three dollars and five minutes of work. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. Thanks to all for the replies, both the correct ones and the incorrect ones. :-) As I suspected, the CF was the culprit. When he described the symptoms, it didn't make sense which is why I asked him if the fixtures were the same. At first he said "Yes...I bought a matching fixture." Then I took it to the next level: OK, what about the bulbs? That's when I learned of the CFL. As far as using an extension ring...well... it's a finished ceiling which means he's going to have to remove all the existing wires to replace the box/add a ring and then put it all back together. Based on past experiences, I'm afraid to even suggest that to him. Thanks to all again. |
#23
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
According to Doug Miller :
We have a winner, ladies and gentlemen! Give that man a cigar! I'll be expecting it ;-) Just one quibble: you meant the *voltage* is insufficient to light LF1. In a series circuit, the current is the same everywhere. Assuming a single 60W lamp in LF1, and a 15W CF lamp in LF2, at 120V the voltage drop across the CF lamp in LF2 is 96V, and incandescent lamp in LF1 is seeing only 24V. Neither "voltage" or "current" are technically quite right in that sentence, but the correct way takes longer to explain ;-) CF's can't really be considered resistive devices, and IC bulbs when cold have much lower resistance than in continuous normal operation, so, the only real way to know what the voltage across them is to set up the circuit and measure it ... ;-) I prefer to think of LF1 (when not visibly showing any light) as being close to a dead short (very low resistance) when in series with another device with considerably higher effective resistance. I'd expect the voltage across LF2 to be a lot more than 96V as a simple-minded series "hot" resistance calculation would imply. You'd be better off measuring the cold resistance of LF1, and using that instead of the hot resistance at 60W output (~240ohms). -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#24
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
According to Terry :
The op said there was only two wires at the switch. That's correct. What makes you think that I implied otherwise? That's what a switch leg is. The way to make the light burn is to take it out of the switch and wire it in parallel to the existing light. Dat's what I said. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#25
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
According to DerbyDad03 :
As far as using an extension ring...well... it's a finished ceiling which means he's going to have to remove all the existing wires to replace the box/add a ring and then put it all back together. Based on past experiences, I'm afraid to even suggest that to him. Check the ceiling box depth. It may be deep enough for the 5 cables. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#26
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 1:16 pm, (Chris Lewis) wrote:
According to DerbyDad03 : As far as using an extension ring...well... it's a finished ceiling which means he's going to have to remove all the existing wires to replace the box/add a ring and then put it all back together. Based on past experiences, I'm afraid to even suggest that to him. Check the ceiling box depth. It may be deep enough for the 5 cables. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. Please save me (and him) the research...what would be the minimum depth for 5 cables? Isn't there also an issue with how many wires can be nutted together in given box? I'm not sure if LF1 has screws or pigtails. Pigtails would, obviously, mean more wires to be nutted. |
#27
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
DerbyDad03 wrote:
A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Sounds cool. When the main light is off, he has a night-light. |
#28
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On 2007-11-06, DerbyDad03 wrote:
Please save me (and him) the research...what would be the minimum depth for 5 cables? Isn't there also an issue with how many wires can be nutted together in given box? Box fill summary: minimum required box volume is a sum of terms, each of which depends on the wire size, in particular 2.00 in^3 for a #14 wire and 2.25 in^3 for a #12 wire. You individually count all current carrying conductors entering the box (hot and neutral), you count all the EGCs as only one wire, you count any internal wire clamps, and you count each device (yoke) in the box as two allowances. Cheers, Wayne |
#29
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Wed, 07 Nov 2007 00:13:54 GMT, Wayne Whitney
wrote: On 2007-11-06, DerbyDad03 wrote: Please save me (and him) the research...what would be the minimum depth for 5 cables? Isn't there also an issue with how many wires can be nutted together in given box? Box fill summary: minimum required box volume is a sum of terms, each of which depends on the wire size, in particular 2.00 in^3 for a #14 wire and 2.25 in^3 for a #12 wire. You individually count all current carrying conductors entering the box (hot and neutral), you count all the EGCs as only one wire, you count any internal wire clamps, and you count each device (yoke) in the box as two allowances. Cheers, Wayne How many #12s can you fit in a handy box? What is the record? |
#30
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 11:16 am, (Chris Lewis) wrote:
According to DerbyDad03 : Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. Several have had it right: Try to clear up the argeument with a diagram: Present wireing: ~--------S1-----------LF1-----------Return \---LF2--/ Should have been wired: ~-------S1----------LF1-----------Return \----LF2---/ |
#31
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Tue, 6 Nov 2007 15:54:00 -0600, "HeyBub"
wrote: DerbyDad03 wrote: A co-worker, who should *not* be doing his own wiring attempted to add a 2nd light fixture in his mudroom this weekend. Here is the situation he presented to me this morning. Sounds cool. When the main light is off, he has a night-light. Although that CFL will be operating on a lower voltage than usual. Is that OK? -- 48 days until the winter solstice celebration Mark Lloyd http://notstupid.laughingsquid.com "Unlike biological evolution. 'intelligent design' is not a genuine scientific theory and, therefore, has no place in the curriculum of our nation's public school classes." -- Ted Kennedy |
#32
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 6, 7:13 pm, Wayne Whitney wrote:
On 2007-11-06, DerbyDad03 wrote: Please save me (and him) the research...what would be the minimum depth for 5 cables? Isn't there also an issue with how many wires can be nutted together in given box? Box fill summary: minimum required box volume is a sum of terms, each of which depends on the wire size, in particular 2.00 in^3 for a #14 wire and 2.25 in^3 for a #12 wire. You individually count all current carrying conductors entering the box (hot and neutral), you count all the EGCs as only one wire, you count any internal wire clamps, and you count each device (yoke) in the box as two allowances. Cheers, Wayne I need some clarification... count all current carrying conductors entering the box (hot and neutral), you count all the EGCs as only one wire So, is a piece of 14/2 with ground counted as 3 "terms" or 2? i.e. requireing 6 in^3 or 4 in^3? you count any internal wire clamps Is an internal wire clamp the same as a wire nut or do you mean the clamp that secures the romex in the hole? What is the X in^3 for either item? If it's the wire nut, wouldn't it depend on the size of the wire nut which is dependent on the number of conductors it secures? count each device (yoke) in the box as two allowances What's a yoke? In the case of this "light fixture ceiling box" how does it (device/yoke) enter into the equation? It's not *in* the box, per se. Thanks |
#33
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
In article . com, DerbyDad03 wrote:
I need some clarification... count all current carrying conductors entering the box (hot and neutral), you count all the EGCs as only one wire So, is a piece of 14/2 with ground counted as 3 "terms" or 2? i.e. requireing 6 in^3 or 4 in^3? Depends on how many *other* cables are present. All the equipment grounding conductors together count as only one. So if you have only one 14/2 WG cable, that counts as three conductors. Two such cables counts as five conductors (two black, two white, plus one for the two EGCs). Three cables counts as seven (3 black, 3 white, plus one for the 3 EGCs). And so on. If the cables have conductors of different sizes, count the all EGCs as one conductor of the largest size. For example, if the box contains two 14/2 WG cables and two 12/2 WG, you count (4) 14ga and (5) 12ga to determine the required capacity. Note also that conductors that don't leave the box (e.g. pigtails) are not counted at all. Neither are up to 4 fixture wires 14ga and smaller. you count any internal wire clamps Is an internal wire clamp the same as a wire nut No or do you mean the clamp that secures the romex in the hole? Yes -- if the clamp is inside the box. The standard Romex connectors that mount through a knockout and are secured with a locknut inside the box have the clamp *outside* the box, and are not counted. What is the X in^3 for either item? Same as that for the largest conductor present. For example, if the box contains both 12ga and 14ga wires, you count the clamp as a 12ga. count each device (yoke) in the box as two allowances What's a yoke? A strap that holds wiring devices such as switches or receptacles -- or fixture nipples. In the case of this "light fixture ceiling box" how does it (device/yoke) enter into the equation? It's not *in* the box, per se. If the fixture mounts directly to the box, it doesn't. If the fixture mounts to a strap that mounts to the box, that's your yoke. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#34
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
On Nov 7, 11:40 am, (Doug Miller) wrote:
In article . com, DerbyDad03 wrote: I need some clarification... count all current carrying conductors entering the box (hot and neutral), you count all the EGCs as only one wire So, is a piece of 14/2 with ground counted as 3 "terms" or 2? i.e. requireing 6 in^3 or 4 in^3? Depends on how many *other* cables are present. All the equipment grounding conductors together count as only one. So if you have only one 14/2 WG cable, that counts as three conductors. Two such cables counts as five conductors (two black, two white, plus one for the two EGCs). Three cables counts as seven (3 black, 3 white, plus one for the 3 EGCs). And so on. If the cables have conductors of different sizes, count the all EGCs as one conductor of the largest size. For example, if the box contains two 14/2 WG cables and two 12/2 WG, you count (4) 14ga and (5) 12ga to determine the required capacity. Note also that conductors that don't leave the box (e.g. pigtails) are not counted at all. Neither are up to 4 fixture wires 14ga and smaller. you count any internal wire clamps Is an internal wire clamp the same as a wire nut No or do you mean the clamp that secures the romex in the hole? Yes -- if the clamp is inside the box. The standard Romex connectors that mount through a knockout and are secured with a locknut inside the box have the clamp *outside* the box, and are not counted. What is the X in^3 for either item? Same as that for the largest conductor present. For example, if the box contains both 12ga and 14ga wires, you count the clamp as a 12ga. count each device (yoke) in the box as two allowances What's a yoke? A strap that holds wiring devices such as switches or receptacles -- or fixture nipples. In the case of this "light fixture ceiling box" how does it (device/yoke) enter into the equation? It's not *in* the box, per se. If the fixture mounts directly to the box, it doesn't. If the fixture mounts to a strap that mounts to the box, that's your yoke. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. Jeez, could you have been *any* clearer in your explanation? ;-) That's a keeper! Thanks! |
#35
Posted to alt.home.repair
|
|||
|
|||
How Is This Switch Wired?
In article om, DerbyDad03 wrote:
Jeez, could you have been *any* clearer in your explanation? ;-) Actually, I probably could have -- failed to specify a couple things: A device yoke counts as *two* of the largest conductor connected to that device. And a support fitting (such as a fixture is attached to) counts as one of the largest conductor present in the box. That's a keeper! Thanks! You're welcome. Glad I could help. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
what is better 110 or 220 if the appliance can be wired for both. | Home Repair | |||
Incorrectly wired a three way switch? | Home Repair | |||
receptacle wired from switch? | Electronics Repair | |||
"Back Wired" Switch Question | Home Repair | |||
Getting wired for the U.S. and Italy!!! | Electronics Repair |