Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Carrier Weathermaker (58MXA) code 31

Hi! I have a problem w/my Carrier Weathermaker 9000? (it's a 58MXA)
not heating.

Though the "component test" checks out OK, this is the ONLY time that
I see that I see the HSI energized (the ignitor). Also, the test of
the pressure switch in the op's manual (i.e., disconnect the inducer
motor, call for heat, and make sure that the HSI is NOT glowing after
about a minute) was fine.

I see a steady ~26VAC signal to the pressure switch.

Other checks:

- air intake/exhaust not clogged (good flow when inducer runs)
- inducer motor supply voltage fine (120VAC)
- inducer cap fine (3.0 uF and resistance huge @ DC)
- install was years ago so PVC sizing must be right
- no backup of water in the drain system
- no clogging of the other rubber/plastic tubing (from the pressure
switch to the burner box)

So am I at a point where the board is in question or might it still be
the pressure switch?

I've tried shorting across the terminals, but an HVAC tech has
informed me that not doing it at the proper time or with the
connections previously ok (i.e., apparently you can't just disconnect
the leads and short the terminals) won't show the proper behavior.

???
HELP!

Thanks

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Carrier Weathermaker (58MXA) code 31

On Tue, 30 Oct 2007 10:32:23 -0700, wrote:

Hi! I have a problem w/my Carrier Weathermaker 9000? (it's a 58MXA)
not heating.

Though the "component test" checks out OK, this is the ONLY time that
I see that I see the HSI energized (the ignitor). Also, the test of
the pressure switch in the op's manual (i.e., disconnect the inducer
motor, call for heat, and make sure that the HSI is NOT glowing after
about a minute) was fine.

I see a steady ~26VAC signal to the pressure switch.

Other checks:

- air intake/exhaust not clogged (good flow when inducer runs)
- inducer motor supply voltage fine (120VAC)
- inducer cap fine (3.0 uF and resistance huge @ DC)
- install was years ago so PVC sizing must be right
- no backup of water in the drain system
- no clogging of the other rubber/plastic tubing (from the pressure
switch to the burner box)

So am I at a point where the board is in question or might it still be
the pressure switch?

I've tried shorting across the terminals, but an HVAC tech has
informed me that not doing it at the proper time or with the
connections previously ok (i.e., apparently you can't just disconnect
the leads and short the terminals) won't show the proper behavior.

???
HELP!

Thanks



Code 31 is for the pressure switch not making. Check the following: is
the inducer motor running, are you getting 24v on both sides of the
switch, is the flue pipe obstructed, is the rubber hose that connects
to the pressure switch plugged?
  #3   Report Post  
Posted to alt.home.repair
Zyp Zyp is offline
external usenet poster
 
Posts: 140
Default Carrier Weathermaker (58MXA) code 31

http://www.thehvacmedic.com/cgi-bin/forum/Blah.pl wrote:
On Tue, 30 Oct 2007 10:32:23 -0700, wrote:

Hi! I have a problem w/my Carrier Weathermaker 9000? (it's a 58MXA)
not heating.

Though the "component test" checks out OK, this is the ONLY time that
I see that I see the HSI energized (the ignitor). Also, the test of
the pressure switch in the op's manual (i.e., disconnect the inducer
motor, call for heat, and make sure that the HSI is NOT glowing after
about a minute) was fine.

I see a steady ~26VAC signal to the pressure switch.

Other checks:

- air intake/exhaust not clogged (good flow when inducer runs)
- inducer motor supply voltage fine (120VAC)
- inducer cap fine (3.0 uF and resistance huge @ DC)
- install was years ago so PVC sizing must be right
- no backup of water in the drain system
- no clogging of the other rubber/plastic tubing (from the pressure
switch to the burner box)

So am I at a point where the board is in question or might it still
be the pressure switch?

I've tried shorting across the terminals, but an HVAC tech has
informed me that not doing it at the proper time or with the
connections previously ok (i.e., apparently you can't just disconnect
the leads and short the terminals) won't show the proper behavior.

???
HELP!

Thanks



Code 31 is for the pressure switch not making. Check the following: is
the inducer motor running, are you getting 24v on both sides of the
switch, is the flue pipe obstructed, is the rubber hose that connects
to the pressure switch plugged?


Sometimes the inducer isn't up to speed and cause's nusiance tripping of the
pressure switch. On this model, it must prove to the control board that
it's in a open, then closed position upon inducer induction. If checking
the flu pipe doesn't prove out, then measure the inducer performance by
connecting a incline manometer to the pressure switch [BTW: it's actually a
vacuum switch] and take a reading. If the reading isn't what's marked on
the switch, suspect the inducer or a clogged hose. [Sometimes spiders crawl
into the hose and plug it.]

--
Zyp


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Carrier Weathermaker - no heat [email protected] Home Repair 5 February 20th 07 04:09 AM
I want to test C#code ,how Can i study ,? I want to get C# code What site.? [email protected] Home Repair 6 June 13th 06 05:33 AM
Carrier Weathermaker 8000 furnace Tony Hwang Home Repair 2 August 30th 05 11:46 AM
Carrier Weathermatic 8000 error code Tony Hwang Home Repair 1 August 19th 05 02:33 AM
New Furnace - Trane XV80 vs Carrier Weathermaker 8000 VS arturo bandini Home Repair 3 April 3rd 04 02:35 AM


All times are GMT +1. The time now is 03:17 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"