W.H.[_2_] October 28th 07 09:30 PM

Bryant Plus 90 furnace (gas heater) error code 33
 
Hi there, how are you doing?

We have a "Bryant Plus 90" which was purchased about 10-13 years ago.
It's been working great until about a year ago we had to "reset" it
and it went back to work. Recently the LED shows a error code (31,
three short blink and then one long blink) which according to the
manual meaning:

PRSSURE, DRAFT SAFGUARD, AUX-LIMIT SWITCH(WHEN USED)OR BLOCKED VENT
SWITCH(WHEN USED) DID NOT CLOSE OR REOPENED (DOWNFLOWONLY)
If open longer than five minutes, inducer shuts off for 15 minutes
before retry.
Check for:

* proper vent sizing
* defective inducer motor
* restricted vent
* excessive wind
* low inducer voltage(115VAC)
* defective blower motor or capacitor
* defective pressure switch
* inadequate combusstion air supply
* disconnected or obstructed pressure tubing

If it opens after trial for ignition period, blower will come on for
90 sec. recycle delay.
--

Just wondering if anyone knows anything about typically for such as
gas heater, if got this type of error code (33), what type of problem
it probably has? We would like to narrow it down so that we could
trouble shoot. Basically other than the LED code, the heater could
still be turned on but we don't know when it will stop working. Thanks!


Ken[_6_] October 28th 07 11:36 PM

Bryant Plus 90 furnace (gas heater) error code 33
 
W.H. wrote:
Hi there, how are you doing?

We have a "Bryant Plus 90" which was purchased about 10-13 years ago.
It's been working great until about a year ago we had to "reset" it
and it went back to work. Recently the LED shows a error code (31,
three short blink and then one long blink) which according to the
manual meaning:

PRSSURE, DRAFT SAFGUARD, AUX-LIMIT SWITCH(WHEN USED)OR BLOCKED VENT
SWITCH(WHEN USED) DID NOT CLOSE OR REOPENED (DOWNFLOWONLY)
If open longer than five minutes, inducer shuts off for 15 minutes
before retry.
Check for:

* proper vent sizing
* defective inducer motor
* restricted vent
* excessive wind
* low inducer voltage(115VAC)
* defective blower motor or capacitor
* defective pressure switch
* inadequate combusstion air supply
* disconnected or obstructed pressure tubing

If it opens after trial for ignition period, blower will come on for
90 sec. recycle delay.
--

Just wondering if anyone knows anything about typically for such as
gas heater, if got this type of error code (33), what type of problem
it probably has? We would like to narrow it down so that we could
trouble shoot. Basically other than the LED code, the heater could
still be turned on but we don't know when it will stop working. Thanks!

Is the inducer motor running? That is the motor that takes the exhaust
from the flame out the flu.

Joe October 29th 07 12:40 AM

Bryant Plus 90 furnace (gas heater) error code 33
 
On Oct 28, 4:30 pm, "W.H." wrote:
Hi there, how are you doing?

We have a "Bryant Plus 90" which was purchased about 10-13 years ago.
It's been working great until about a year ago we had to "reset" it
and it went back to work. Recently the LED shows a error code (31,
three short blink and then one long blink) which according to the
manual meaning:

PRSSURE, DRAFT SAFGUARD, AUX-LIMIT SWITCH(WHEN USED)OR BLOCKED VENT
SWITCH(WHEN USED) DID NOT CLOSE OR REOPENED (DOWNFLOWONLY)
If open longer than five minutes, inducer shuts off for 15 minutes
before retry.
Check for:

* proper vent sizing
* defective inducer motor
* restricted vent
* excessive wind
* low inducer voltage(115VAC)
* defective blower motor or capacitor
* defective pressure switch
* inadequate combusstion air supply
* disconnected or obstructed pressure tubing

If it opens after trial for ignition period, blower will come on for
90 sec. recycle delay.
--

Just wondering if anyone knows anything about typically for such as
gas heater, if got this type of error code (33), what type of problem
it probably has? We would like to narrow it down so that we could
trouble shoot. Basically other than the LED code, the heater could
still be turned on but we don't know when it will stop working. Thanks!


The pressure sensor or its connecting tubing are logical sources for
that symptom assuming the blower motor is still functional. A good
source for parts and advice is arnoldservice.com. Good luck.

Joe


No Name October 29th 07 03:37 AM

Bryant Plus 90 furnace (gas heater) error code 33
 

"W.H." wrote in message
oups.com...
Hi there, how are you doing?

We have a "Bryant Plus 90" which was purchased about 10-13 years ago.
It's been working great until about a year ago we had to "reset" it
and it went back to work. Recently the LED shows a error code (31,
three short blink and then one long blink) which according to the
manual meaning:

PRSSURE, DRAFT SAFGUARD, AUX-LIMIT SWITCH(WHEN USED)OR BLOCKED VENT
SWITCH(WHEN USED) DID NOT CLOSE OR REOPENED (DOWNFLOWONLY)
If open longer than five minutes, inducer shuts off for 15 minutes
before retry.
Check for:

* proper vent sizing
* defective inducer motor
* restricted vent
* excessive wind
* low inducer voltage(115VAC)
* defective blower motor or capacitor
* defective pressure switch
* inadequate combusstion air supply
* disconnected or obstructed pressure tubing

If it opens after trial for ignition period, blower will come on for
90 sec. recycle delay.
--

Just wondering if anyone knows anything about typically for such as
gas heater, if got this type of error code (33), what type of problem
it probably has? We would like to narrow it down so that we could
trouble shoot. Basically other than the LED code, the heater could
still be turned on but we don't know when it will stop working. Thanks!



The unit needs to be tested by a competent HVAC technician.
Everything else would be a guess, so why not call your HVAC guy and get it
repaired?




No Name October 29th 07 05:41 AM

Bryant Plus 90 furnace (gas heater) error code 33
 

"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:80c4a$47254794$9440c41e$20955
@STARBAND.NET:


"W.H." wrote in message
oups.com...
Hi there, how are you doing?

We have a "Bryant Plus 90" which was purchased about 10-13 years ago.
It's been working great until about a year ago we had to "reset" it
and it went back to work. Recently the LED shows a error code (31,
three short blink and then one long blink) which according to the
manual meaning:

PRSSURE, DRAFT SAFGUARD, AUX-LIMIT SWITCH(WHEN USED)OR BLOCKED VENT
SWITCH(WHEN USED) DID NOT CLOSE OR REOPENED (DOWNFLOWONLY)
If open longer than five minutes, inducer shuts off for 15 minutes
before retry.
Check for:

* proper vent sizing
* defective inducer motor
* restricted vent
* excessive wind
* low inducer voltage(115VAC)
* defective blower motor or capacitor
* defective pressure switch
* inadequate combusstion air supply
* disconnected or obstructed pressure tubing

If it opens after trial for ignition period, blower will come on for
90 sec. recycle delay.
--

Just wondering if anyone knows anything about typically for such as
gas heater, if got this type of error code (33), what type of problem
it probably has? We would like to narrow it down so that we could
trouble shoot. Basically other than the LED code, the heater could
still be turned on but we don't know when it will stop working. Thanks!



The unit needs to be tested by a competent HVAC technician.
Everything else would be a guess, so why not call your HVAC guy and get

it
repaired?

In other words you know nothing about the system and have nothing to

offer.


Yeah, I see you offered a whole lot of information.
What do you suggest he do, change the air filter? LOL