Default Using #14 wire on a 20A if plugged in

Here's a puzzler......

I put a permanent wall fan in my barn at the eaves. This is a small
motor fan, probably 1/10 to 1/4hp.at most. It's just there to vent
out the heat in the summer and/or manure odor. It makes the barn
better for animals. There is a control on the fan to turn it on at a
specified temperature (such as over 75deg). The outlet in the
adjoining feed room was the closest outlet, and is on a 20A breaker.
I needed to get this fan running this last summer when the outdoor
temp went above 90 deg. and I had a sick horse in there. I was out of
#12 romex, so I ran some #14 that I had. To speed up the job even
more, (and knowing it would have to be replaced), I did not hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet. As in all farm operations, nothing ever
gets done before some other job or chore comes along, so I have left
it the way it was. In some sense, I almost wonder if I should just
leave it, and I can unplug it during the cooler weather since it's not
needed.

My question is whether using #14 wires is up to code, when it's not
hard wired? For example, many lamps, radios, and other small
appliances have #18 or #16 cords, and they are plugged into 15 or 20 A
circuits. I'm just curious. One of these days I might find the time
to wire this properly and will have to add a switch so I can turn it
off when I want. But for now, it works and is safe at least according
to common sense, if not the code.

Alvin
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Using #14 wire on a 20A if plugged in

On Oct 1, 6:47?am, (Doug Miller) wrote:
In article , wrote:
Here's a puzzler......


I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?


Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


the fire hazard is the same,,,,,,,,,,, bard fires are nasty..

really all extension cords and plugs should be fused for safety at the
maximum current capacity of the wire and device. I am amazed that
hasnt been made a law

if you like your current setup why not add a dedicated fuse or breaker
just for this item?

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Using #14 wire on a 20A if plugged in

In article . com, " wrote:
On Oct 1, 6:47?am, (Doug Miller) wrote:
In article ,

wrote:
Here's a puzzler......


I put a permanent wall fan in my barn at the eaves. [...] I did not hard

wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?


Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


the fire hazard is the same,,,,,,,,,,, bard fires are nasty..


WHAT fire hazard?

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 17
Default Using #14 wire on a 20A if plugged in

Or just change that 20 amp breaker to a 15

--

Mike S.

wrote in message
ups.com...

if you like your current setup why not add a dedicated fuse or breaker
just for this item?





  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Using #14 wire on a 20A if plugged in

On Oct 1, 8:10?am, (Doug Miller) wrote:
In article . com, " wrote:





On Oct 1, 6:47?am, (Doug Miller) wrote:
In article ,

wrote:
Here's a puzzler......


I put a permanent wall fan in my barn at the eaves. [...] I did not hard

wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?


Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


the fire hazard is the same,,,,,,,,,,, bard fires are nasty..


WHAT fire hazard?

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.- Hide quoted text -

- Show quoted text -


any time anyone plugs a device into a circuit capable of carrying
enough current to cause overheating thats a fire hazard.

ultimately whats the difference between a 14 gauge wire on a 20 amp
breaker and a 16 gauge wire on a 15 amp breaker?

guess what no difference, both can overheat and start a fire, fact is
the 16 gauge extension cord is more likely to be a source. given their
tough life.

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,743
Default Using #14 wire on a 20A if plugged in

Doug Miller wrote:

the fire hazard is the same,,,,,,,,,,, bard fires are nasty..


WHAT fire hazard?


Ever lit a poet?


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Using #14 wire on a 20A if plugged in

In article om, " wrote:
On Oct 1, 8:10?am, (Doug Miller) wrote:
In article . com,

" wrote:

On Oct 1, 6:47?am, (Doug Miller) wrote:
In article ,
wrote:
Here's a puzzler......


I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?


Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


the fire hazard is the same,,,,,,,,,,, bard fires are nasty..


WHAT fire hazard?


any time anyone plugs a device into a circuit capable of carrying
enough current to cause overheating thats a fire hazard.


And where exactly did you get the idea that the OP's fan is going to draw that
much current?

You realize, don't you, that all over your house you have appliances with
18-ga power cords plugged into outlets on 15A and 20A circuits?

What's the difference?

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Using #14 wire on a 20A if plugged in

On Oct 1, 8:55?am, (Doug Miller) wrote:
In article om, " wrote:





On Oct 1, 8:10?am, (Doug Miller) wrote:
In article . com,

" wrote:


On Oct 1, 6:47?am, (Doug Miller) wrote:
In article ,
wrote:
Here's a puzzler......


I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?


Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


the fire hazard is the same,,,,,,,,,,, bard fires are nasty..


WHAT fire hazard?


any time anyone plugs a device into a circuit capable of carrying
enough current to cause overheating thats a fire hazard.


And where exactly did you get the idea that the OP's fan is going to draw that
much current?

You realize, don't you, that all over your house you have appliances with
18-ga power cords plugged into outlets on 15A and 20A circuits?

What's the difference?

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.- Hide quoted text -

- Show quoted text -


thats my point, every home is filled with fire hazards,,,,,,,,

About 10 years ago I nearly lost our home to a fire after a cieling
lamp shorted and sparked to its base showeing the bed with sparks in
the middle of the nite, I had gotten up to go to the bathroom. All
those fixtures went to the trash.

while the code rules that no conductor should be smaller than its
breaker those rules end at the receptable.........

I see nice but err dump folks plug too much stuff in extension cords
constantly. shouldnt extension cordes be fused to their max carrying
capacity somehow?

whats more likely to cause a fire?

a 14 gauge romex carrying 20 amps

or a 16 gauge extension cord beat up by use carrying 15 amps laying on
carpet?

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Using #14 wire on a 20A if plugged in

In article . com, " wrote:
On Oct 1, 8:55?am, (Doug Miller) wrote:
In article om,

" wrote:


On Oct 1, 8:10?am, (Doug Miller) wrote:
In article . com,
" wrote:


On Oct 1, 6:47?am, (Doug Miller) wrote:
In article ,
wrote:
Here's a puzzler......


I put a permanent wall fan in my barn at the eaves. [...] I did not

hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?


Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


the fire hazard is the same,,,,,,,,,,, bard fires are nasty..


WHAT fire hazard?


any time anyone plugs a device into a circuit capable of carrying
enough current to cause overheating thats a fire hazard.


And where exactly did you get the idea that the OP's fan is going to draw that
much current?

You realize, don't you, that all over your house you have appliances with
18-ga power cords plugged into outlets on 15A and 20A circuits?

What's the difference?


thats my point, every home is filled with fire hazards,,,,,,,,


Speak for yourself. Some of us know how to avoid creating them -- either in
reality or in our imaginations.

[snip irrelevant anecdote]
whats more likely to cause a fire?

a 14 gauge romex carrying 20 amps

or a 16 gauge extension cord beat up by use carrying 15 amps laying on
carpet?


Obviously the latter -- but so what? *Neither* has *anything* to do with the
question the OP asked.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,300
Default Using #14 wire on a 20A if plugged in

wrote:
On Oct 1, 6:47?am, (Doug Miller) wrote:

In article , wrote:

Here's a puzzler......


I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?


Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.



the fire hazard is the same,,,,,,,,,,, bard fires are nasty..

really all extension cords and plugs should be fused for safety at the
maximum current capacity of the wire and device. I am amazed that
hasnt been made a law

if you like your current setup why not add a dedicated fuse or breaker
just for this item?



Mybe that's why the Brits have (had) a pair of small sized replaceable
cartridge fuses built into the plugs on the end of every appliance's
cord, sized to suit the load?

Or at least they did the last time I looked, maybe 20 years ago. Do they
still use that system?

IIRC they ran quite heavy conductors from the power source to groups of
chained outlets and relied on the fuses built into the plugs to keep
things safe. I think they called that a "ring main" system?

Jeff

--
Jeffry Wisnia
(W1BSV + Brass Rat '57 EE)
The speed of light is 1.98*10^14 fathoms per fortnight.
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default Using #14 wire on a 20A if plugged in


wrote in message
...
Here's a puzzler......

I put a permanent wall fan in my barn at the eaves. This is a small
motor fan, probably 1/10 to 1/4hp.at most. It's just there to vent
out the heat in the summer and/or manure odor. It makes the barn
better for animals. There is a control on the fan to turn it on at a
specified temperature (such as over 75deg). The outlet in the
adjoining feed room was the closest outlet, and is on a 20A breaker.
I needed to get this fan running this last summer when the outdoor
temp went above 90 deg. and I had a sick horse in there. I was out of
#12 romex, so I ran some #14 that I had. To speed up the job even
more, (and knowing it would have to be replaced), I did not hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet. As in all farm operations, nothing ever
gets done before some other job or chore comes along, so I have left
it the way it was. In some sense, I almost wonder if I should just
leave it, and I can unplug it during the cooler weather since it's not
needed.

My question is whether using #14 wires is up to code, when it's not
hard wired? For example, many lamps, radios, and other small
appliances have #18 or #16 cords, and they are plugged into 15 or 20 A
circuits. I'm just curious. One of these days I might find the time
to wire this properly and will have to add a switch so I can turn it
off when I want. But for now, it works and is safe at least according
to common sense, if not the code.

I don't think you can put a plug on romex; it isn't approved for that use.
As a practical matter though, what is going to happen?
To be dangerous you would have to have a overload on the 14 that isn't
enough to trip the breaker; yet is enough to start a fire.
While not impossible, it is most unlikely; especially if the the circuit is
dedicated to your little fan.
Its a judgement call.

The one time I was in a similar situation I changed the breaker, since there
was no need for 20a.


  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,185
Default Using #14 wire on a 20A if plugged in

Doug Miller wrote:

My question is whether using #14 wires is up to code, when it's not
hard wired?



Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


Isn't it a violation to use romex as an extension cord?

Chris
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Using #14 wire on a 20A if plugged in

In article , Chris Friesen wrote:
Doug Miller wrote:

My question is whether using #14 wires is up to code, when it's not
hard wired?



Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


Isn't it a violation to use romex as an extension cord?


Where does the Code address extension cords?

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 161
Default Using #14 wire on a 20A if plugged in

so i guess that 350' of 12/2 i have laying on the ground to my barn is not
quite kopasetic?

s


"Chris Friesen" wrote in message
...
Doug Miller wrote:

My question is whether using #14 wires is up to code, when it's not
hard wired?



Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


Isn't it a violation to use romex as an extension cord?

Chris





  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8,803
Default Using #14 wire on a 20A if plugged in

Ask the fire department.

Bob

"Steve Barker LT" wrote in message
...
so i guess that 350' of 12/2 i have laying on the ground to my barn is not
quite kopasetic?

s


"Chris Friesen" wrote in message
...
Doug Miller wrote:

My question is whether using #14 wires is up to code, when it's not
hard wired?


Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)


Isn't it a violation to use romex as an extension cord?

Chris





  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 248
Default Using #14 wire on a 20A if plugged in

On Mon, 01 Oct 2007 13:18:05 GMT, (Doug Miller)
wrote:

In article . com, " wrote:
On Oct 1, 8:55?am, (Doug Miller) wrote:
In article om,

" wrote:


On Oct 1, 8:10?am, (Doug Miller) wrote:
In article . com,
" wrote:

On Oct 1, 6:47?am, (Doug Miller) wrote:
In article ,
wrote:
Here's a puzzler......

I put a permanent wall fan in my barn at the eaves. [...] I did not

hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?

Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)

the fire hazard is the same,,,,,,,,,,, bard fires are nasty..

WHAT fire hazard?

any time anyone plugs a device into a circuit capable of carrying
enough current to cause overheating thats a fire hazard.

And where exactly did you get the idea that the OP's fan is going to draw that
much current?

You realize, don't you, that all over your house you have appliances with
18-ga power cords plugged into outlets on 15A and 20A circuits?

What's the difference?


thats my point, every home is filled with fire hazards,,,,,,,,


Speak for yourself. Some of us know how to avoid creating them -- either in
reality or in our imaginations.

[snip irrelevant anecdote]
whats more likely to cause a fire?

a 14 gauge romex carrying 20 amps

or a 16 gauge extension cord beat up by use carrying 15 amps laying on
carpet?


Obviously the latter -- but so what? *Neither* has *anything* to do with the
question the OP asked.


I'm just reading all the replies to my question. Thanks for all the
help.

I wanted to mention that those of us who know and understand
electricity are much better off than the average homeowner or
apartment dweller who only knows enough to plug something into an
outlet and how to flip a light switch. The scarey thing are people
who dont know enough, and use a #16 or #18 extension cord for
something like a refrigerator. That's where the real fire hazzards
exist. It's too bad they even sell those small cords, but then what
would we use for table lamps, xmas decorations, etc.....
Maybe our elementary and high schools should spend more time teaching
EVERYONE about household things such as electrical uses, rather than
some of the useless junk they teach. Heck, it's 35 years since I left
H.S. but I still wonder why I had to take calculus..... Bettering
"homeowners" education would save lives.

I DO NOT consider my #14 romex plug-in to be a fire hazzard, or I
would not have done it. My animals are my best friends, so I surely
wont risk their lives. I just wanted to know the code regulations.
Actually, that small motor fan could be safely plugged into a #16 or
#18 extension cord, but I would not use that in a barn.

Alvin
  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 248
Default Using #14 wire on a 20A if plugged in

On Mon, 01 Oct 2007 10:19:17 -0400, Jeff Wisnia
wrote:

wrote:
On Oct 1, 6:47?am, (Doug Miller) wrote:

In article , wrote:

Here's a puzzler......

I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire
to the outlet, I just put a grounded plug on the end of the romex and
plugged it in to the outlet.[...]
My question is whether using #14 wires is up to code, when it's not
hard wired?

Yes. The Code basically stops at the receptacle. (This is an
oversimplification, but it gets the point across.)

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.



the fire hazard is the same,,,,,,,,,,, bard fires are nasty..

really all extension cords and plugs should be fused for safety at the
maximum current capacity of the wire and device. I am amazed that
hasnt been made a law

if you like your current setup why not add a dedicated fuse or breaker
just for this item?



Mybe that's why the Brits have (had) a pair of small sized replaceable
cartridge fuses built into the plugs on the end of every appliance's
cord, sized to suit the load?

Or at least they did the last time I looked, maybe 20 years ago. Do they
still use that system?

IIRC they ran quite heavy conductors from the power source to groups of
chained outlets and relied on the fuses built into the plugs to keep
things safe. I think they called that a "ring main" system?

Jeff


Kind of like those xmas light sets, huh?
  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 161
Default Using #14 wire on a 20A if plugged in

The fire dept would prefer we don't use ANY extension cord for any reason,
made of any material.

s


"Bob F" wrote in message
...
Ask the fire department.

Bob



  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,185
Default Using #14 wire on a 20A if plugged in

Doug Miller wrote:
In article , Chris Friesen wrote:


Isn't it a violation to use romex as an extension cord?


Where does the Code address extension cords?


According to the index of the online version, 240.5 and 590.6.

I suspect that section 400 (flexible cords) would apply as well (since
extension cords are not fixed in place), which would lead me to conclude
that that romex is not suitable for use as an extension cord.

Chris



  #21   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Using #14 wire on a 20A if plugged in

Jeff Wisnia wrote:


Maybe that's why the Brits have (had) a pair of small sized replaceable
cartridge fuses built into the plugs on the end of every appliance's
cord, sized to suit the load?

Or at least they did the last time I looked, maybe 20 years ago. Do they
still use that system?

IIRC they ran quite heavy conductors from the power source to groups of
chained outlets and relied on the fuses built into the plugs to keep
things safe. I think they called that a "ring main" system?


Sometimes hard to imagine we speak the same language (more or less).

The UK does have "ring" circuits with both ends connected to the same
breaker. The rating is 32A (230V) and plugs do have fuses in them (at
32A, a good idea). The wire is not rated for 32A but each outlet is
supplied from 2 directions.

--------------------
I agree that UL and the NEC would not be happy with putting a plug on
Romex and calling it a power cord.


--
bud--
  #22   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 408
Default Using #14 wire on a 20A if plugged in


I DO NOT consider my #14 romex plug-in to be a fire hazzard, or I
would not have done it. My animals are my best friends, so I surely
wont risk their lives. I just wanted to know the code regulations.
Actually, that small motor fan could be safely plugged into a #16 or
#18 extension cord, but I would not use that in a barn.



I would however check that the fan motor itself has some thermal
protection so that it fails in a safe way should the blades get jammed
or the bearings seize up etc..., or you may want to wire in a smaller
3 Amp fuse just for that purpose...

Mark

  #23   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 361
Default Using #14 wire on a 20A if plugged in

Jeff Wisnia writes:

Mybe that's why the Brits have (had) a pair of small sized replaceable
cartridge fuses built into the plugs on the end of every appliance's
cord, sized to suit the load?


Or at least they did the last time I looked, maybe 20 years ago. Do they
still use that system?


Last time I visited there, every plug seemed to have one (not two)
fuses. It's single phase, with one side grounded (neutral), so only one
side needs to be fused. The fuse or circuit breaker in the panel
protects the wire in the wall and the outlet, while the fuse in the plug
protects the appliance and its cord. It allows nice thin cords on
appliances that don't draw a lot of current, while plenty of power is
available for appliances that need it. (The largest normal plug fuse is
13 A, which can deliver 3 kW).

In addition, modern outlets seem to have built-in shutters that block
access to the hot and neutral openings until the (longer) ground pin is
inserted. It all makes North American cords and plugs and outlets look
like cheap junk.

IIRC they ran quite heavy conductors from the power source to groups of
chained outlets and relied on the fuses built into the plugs to keep
things safe. I think they called that a "ring main" system?


The "ring main" system apparently runs the wires for a circuit in a
ring: from the panel, around the outlets on one floor (typically) in
sequence, and back to the panel - where the other end of the wires are
connected to the same breaker or fuse. So there are two current paths
from the panel to any outlet, going around the ring CW and CCW. This
design was apparently used to reduce copper requirements (compared to a
bunch of home run circuits of lower capacity).

Each ring circuit is normally fused for 30 A, so you can have a couple
of 13 A loads operating simultaneously on the same circuit with some
capacity left over.

Dave
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plugged sink followup comcastss news groups Home Repair 3 January 31st 07 07:12 PM
sediment plugged facet mike Home Repair 3 July 11th 05 03:54 AM
Plugged aerator? [email protected] Home Repair 2 December 15th 04 05:39 PM
holes plugged... Silvan Woodworking 2 November 5th 04 03:32 AM
Plugged Tub Drain Bob P. Home Repair 6 November 18th 03 11:52 PM


All times are GMT +1. The time now is 02:49 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"