Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
Here's a puzzler......
I put a permanent wall fan in my barn at the eaves. This is a small motor fan, probably 1/10 to 1/4hp.at most. It's just there to vent out the heat in the summer and/or manure odor. It makes the barn better for animals. There is a control on the fan to turn it on at a specified temperature (such as over 75deg). The outlet in the adjoining feed room was the closest outlet, and is on a 20A breaker. I needed to get this fan running this last summer when the outdoor temp went above 90 deg. and I had a sick horse in there. I was out of #12 romex, so I ran some #14 that I had. To speed up the job even more, (and knowing it would have to be replaced), I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet. As in all farm operations, nothing ever gets done before some other job or chore comes along, so I have left it the way it was. In some sense, I almost wonder if I should just leave it, and I can unplug it during the cooler weather since it's not needed. My question is whether using #14 wires is up to code, when it's not hard wired? For example, many lamps, radios, and other small appliances have #18 or #16 cords, and they are plugged into 15 or 20 A circuits. I'm just curious. One of these days I might find the time to wire this properly and will have to add a switch so I can turn it off when I want. But for now, it works and is safe at least according to common sense, if not the code. Alvin |
#2
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
|
#3
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
On Oct 1, 6:47?am, (Doug Miller) wrote:
In article , wrote: Here's a puzzler...... I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet.[...] My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. the fire hazard is the same,,,,,,,,,,, bard fires are nasty.. really all extension cords and plugs should be fused for safety at the maximum current capacity of the wire and device. I am amazed that hasnt been made a law if you like your current setup why not add a dedicated fuse or breaker just for this item? |
#4
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
In article . com, " wrote:
On Oct 1, 6:47?am, (Doug Miller) wrote: In article , wrote: Here's a puzzler...... I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet.[...] My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) the fire hazard is the same,,,,,,,,,,, bard fires are nasty.. WHAT fire hazard? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#5
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
Or just change that 20 amp breaker to a 15
-- Mike S. wrote in message ups.com... if you like your current setup why not add a dedicated fuse or breaker just for this item? |
#6
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
On Oct 1, 8:10?am, (Doug Miller) wrote:
In article . com, " wrote: On Oct 1, 6:47?am, (Doug Miller) wrote: In article , wrote: Here's a puzzler...... I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet.[...] My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) the fire hazard is the same,,,,,,,,,,, bard fires are nasty.. WHAT fire hazard? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again.- Hide quoted text - - Show quoted text - any time anyone plugs a device into a circuit capable of carrying enough current to cause overheating thats a fire hazard. ultimately whats the difference between a 14 gauge wire on a 20 amp breaker and a 16 gauge wire on a 15 amp breaker? guess what no difference, both can overheat and start a fire, fact is the 16 gauge extension cord is more likely to be a source. given their tough life. |
#7
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
Doug Miller wrote:
the fire hazard is the same,,,,,,,,,,, bard fires are nasty.. WHAT fire hazard? Ever lit a poet? |
#8
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
In article om, " wrote:
On Oct 1, 8:10?am, (Doug Miller) wrote: In article . com, " wrote: On Oct 1, 6:47?am, (Doug Miller) wrote: In article , wrote: Here's a puzzler...... I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet.[...] My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) the fire hazard is the same,,,,,,,,,,, bard fires are nasty.. WHAT fire hazard? any time anyone plugs a device into a circuit capable of carrying enough current to cause overheating thats a fire hazard. And where exactly did you get the idea that the OP's fan is going to draw that much current? You realize, don't you, that all over your house you have appliances with 18-ga power cords plugged into outlets on 15A and 20A circuits? What's the difference? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#9
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
On Oct 1, 8:55?am, (Doug Miller) wrote:
In article om, " wrote: On Oct 1, 8:10?am, (Doug Miller) wrote: In article . com, " wrote: On Oct 1, 6:47?am, (Doug Miller) wrote: In article , wrote: Here's a puzzler...... I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet.[...] My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) the fire hazard is the same,,,,,,,,,,, bard fires are nasty.. WHAT fire hazard? any time anyone plugs a device into a circuit capable of carrying enough current to cause overheating thats a fire hazard. And where exactly did you get the idea that the OP's fan is going to draw that much current? You realize, don't you, that all over your house you have appliances with 18-ga power cords plugged into outlets on 15A and 20A circuits? What's the difference? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again.- Hide quoted text - - Show quoted text - thats my point, every home is filled with fire hazards,,,,,,,, About 10 years ago I nearly lost our home to a fire after a cieling lamp shorted and sparked to its base showeing the bed with sparks in the middle of the nite, I had gotten up to go to the bathroom. All those fixtures went to the trash. while the code rules that no conductor should be smaller than its breaker those rules end at the receptable......... I see nice but err dump folks plug too much stuff in extension cords constantly. shouldnt extension cordes be fused to their max carrying capacity somehow? whats more likely to cause a fire? a 14 gauge romex carrying 20 amps or a 16 gauge extension cord beat up by use carrying 15 amps laying on carpet? |
#10
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
In article . com, " wrote:
On Oct 1, 8:55?am, (Doug Miller) wrote: In article om, " wrote: On Oct 1, 8:10?am, (Doug Miller) wrote: In article . com, " wrote: On Oct 1, 6:47?am, (Doug Miller) wrote: In article , wrote: Here's a puzzler...... I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet.[...] My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) the fire hazard is the same,,,,,,,,,,, bard fires are nasty.. WHAT fire hazard? any time anyone plugs a device into a circuit capable of carrying enough current to cause overheating thats a fire hazard. And where exactly did you get the idea that the OP's fan is going to draw that much current? You realize, don't you, that all over your house you have appliances with 18-ga power cords plugged into outlets on 15A and 20A circuits? What's the difference? thats my point, every home is filled with fire hazards,,,,,,,, Speak for yourself. Some of us know how to avoid creating them -- either in reality or in our imaginations. [snip irrelevant anecdote] whats more likely to cause a fire? a 14 gauge romex carrying 20 amps or a 16 gauge extension cord beat up by use carrying 15 amps laying on carpet? Obviously the latter -- but so what? *Neither* has *anything* to do with the question the OP asked. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#11
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
|
#12
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
wrote in message ... Here's a puzzler...... I put a permanent wall fan in my barn at the eaves. This is a small motor fan, probably 1/10 to 1/4hp.at most. It's just there to vent out the heat in the summer and/or manure odor. It makes the barn better for animals. There is a control on the fan to turn it on at a specified temperature (such as over 75deg). The outlet in the adjoining feed room was the closest outlet, and is on a 20A breaker. I needed to get this fan running this last summer when the outdoor temp went above 90 deg. and I had a sick horse in there. I was out of #12 romex, so I ran some #14 that I had. To speed up the job even more, (and knowing it would have to be replaced), I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet. As in all farm operations, nothing ever gets done before some other job or chore comes along, so I have left it the way it was. In some sense, I almost wonder if I should just leave it, and I can unplug it during the cooler weather since it's not needed. My question is whether using #14 wires is up to code, when it's not hard wired? For example, many lamps, radios, and other small appliances have #18 or #16 cords, and they are plugged into 15 or 20 A circuits. I'm just curious. One of these days I might find the time to wire this properly and will have to add a switch so I can turn it off when I want. But for now, it works and is safe at least according to common sense, if not the code. I don't think you can put a plug on romex; it isn't approved for that use. As a practical matter though, what is going to happen? To be dangerous you would have to have a overload on the 14 that isn't enough to trip the breaker; yet is enough to start a fire. While not impossible, it is most unlikely; especially if the the circuit is dedicated to your little fan. Its a judgement call. The one time I was in a similar situation I changed the breaker, since there was no need for 20a. |
#13
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
Doug Miller wrote:
My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) Isn't it a violation to use romex as an extension cord? Chris |
#14
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
In article , Chris Friesen wrote:
Doug Miller wrote: My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) Isn't it a violation to use romex as an extension cord? Where does the Code address extension cords? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#15
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
so i guess that 350' of 12/2 i have laying on the ground to my barn is not
quite kopasetic? s "Chris Friesen" wrote in message ... Doug Miller wrote: My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) Isn't it a violation to use romex as an extension cord? Chris |
#16
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
Ask the fire department.
Bob "Steve Barker LT" wrote in message ... so i guess that 350' of 12/2 i have laying on the ground to my barn is not quite kopasetic? s "Chris Friesen" wrote in message ... Doug Miller wrote: My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) Isn't it a violation to use romex as an extension cord? Chris |
#17
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
|
#18
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
On Mon, 01 Oct 2007 10:19:17 -0400, Jeff Wisnia
wrote: wrote: On Oct 1, 6:47?am, (Doug Miller) wrote: In article , wrote: Here's a puzzler...... I put a permanent wall fan in my barn at the eaves. [...] I did not hard wire to the outlet, I just put a grounded plug on the end of the romex and plugged it in to the outlet.[...] My question is whether using #14 wires is up to code, when it's not hard wired? Yes. The Code basically stops at the receptacle. (This is an oversimplification, but it gets the point across.) -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. the fire hazard is the same,,,,,,,,,,, bard fires are nasty.. really all extension cords and plugs should be fused for safety at the maximum current capacity of the wire and device. I am amazed that hasnt been made a law if you like your current setup why not add a dedicated fuse or breaker just for this item? Mybe that's why the Brits have (had) a pair of small sized replaceable cartridge fuses built into the plugs on the end of every appliance's cord, sized to suit the load? Or at least they did the last time I looked, maybe 20 years ago. Do they still use that system? IIRC they ran quite heavy conductors from the power source to groups of chained outlets and relied on the fuses built into the plugs to keep things safe. I think they called that a "ring main" system? Jeff Kind of like those xmas light sets, huh? |
#19
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
The fire dept would prefer we don't use ANY extension cord for any reason,
made of any material. s "Bob F" wrote in message ... Ask the fire department. Bob |
#20
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
Doug Miller wrote:
In article , Chris Friesen wrote: Isn't it a violation to use romex as an extension cord? Where does the Code address extension cords? According to the index of the online version, 240.5 and 590.6. I suspect that section 400 (flexible cords) would apply as well (since extension cords are not fixed in place), which would lead me to conclude that that romex is not suitable for use as an extension cord. Chris |
#21
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
Jeff Wisnia wrote:
Maybe that's why the Brits have (had) a pair of small sized replaceable cartridge fuses built into the plugs on the end of every appliance's cord, sized to suit the load? Or at least they did the last time I looked, maybe 20 years ago. Do they still use that system? IIRC they ran quite heavy conductors from the power source to groups of chained outlets and relied on the fuses built into the plugs to keep things safe. I think they called that a "ring main" system? Sometimes hard to imagine we speak the same language (more or less). The UK does have "ring" circuits with both ends connected to the same breaker. The rating is 32A (230V) and plugs do have fuses in them (at 32A, a good idea). The wire is not rated for 32A but each outlet is supplied from 2 directions. -------------------- I agree that UL and the NEC would not be happy with putting a plug on Romex and calling it a power cord. -- bud-- |
#22
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
I DO NOT consider my #14 romex plug-in to be a fire hazzard, or I would not have done it. My animals are my best friends, so I surely wont risk their lives. I just wanted to know the code regulations. Actually, that small motor fan could be safely plugged into a #16 or #18 extension cord, but I would not use that in a barn. I would however check that the fan motor itself has some thermal protection so that it fails in a safe way should the blades get jammed or the bearings seize up etc..., or you may want to wire in a smaller 3 Amp fuse just for that purpose... Mark |
#23
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire on a 20A if plugged in
Jeff Wisnia writes:
Mybe that's why the Brits have (had) a pair of small sized replaceable cartridge fuses built into the plugs on the end of every appliance's cord, sized to suit the load? Or at least they did the last time I looked, maybe 20 years ago. Do they still use that system? Last time I visited there, every plug seemed to have one (not two) fuses. It's single phase, with one side grounded (neutral), so only one side needs to be fused. The fuse or circuit breaker in the panel protects the wire in the wall and the outlet, while the fuse in the plug protects the appliance and its cord. It allows nice thin cords on appliances that don't draw a lot of current, while plenty of power is available for appliances that need it. (The largest normal plug fuse is 13 A, which can deliver 3 kW). In addition, modern outlets seem to have built-in shutters that block access to the hot and neutral openings until the (longer) ground pin is inserted. It all makes North American cords and plugs and outlets look like cheap junk. IIRC they ran quite heavy conductors from the power source to groups of chained outlets and relied on the fuses built into the plugs to keep things safe. I think they called that a "ring main" system? The "ring main" system apparently runs the wires for a circuit in a ring: from the panel, around the outlets on one floor (typically) in sequence, and back to the panel - where the other end of the wires are connected to the same breaker or fuse. So there are two current paths from the panel to any outlet, going around the ring CW and CCW. This design was apparently used to reduce copper requirements (compared to a bunch of home run circuits of lower capacity). Each ring circuit is normally fused for 30 A, so you can have a couple of 13 A loads operating simultaneously on the same circuit with some capacity left over. Dave |