Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? In doing the above, how specifically should it be done to meet NEC? If I understand, it will still need to be bonded to the water pipe. Should that be within 5 foot of water entrance point? And can you bond it to more than one place (i.e. to the 5 foot and also close to panel?). I'm still not up to speed on this bonding concept, hence the question. Is there a specific way of doing it so that it will ensure that it trips the breaker? Do the grounds go IN the panel or are they attached to ground rod (assuming ground rod is attached to panel). Does it matter? At what point (if any) can the ground wires be combined into one? I seem to remember something about you couldn't use a junction box-- everyone had to have a home run. I just don't understand enough about this to know where that home run ends? Not sure if this is relate to the above, but he did mention something about "looping" the grounds--but I am not sure where he meant that or what it means. Hopefully, that is a good enough description that you can not only answer questions, but raise any issues that you forsee (as you can tell, I am not too up on electrical). -- John |
#2
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? In doing the above, how specifically should it be done to meet NEC? If I understand, it will still need to be bonded to the water pipe. Should that be within 5 foot of water entrance point? And can you bond it to more than one place (i.e. to the 5 foot and also close to panel?). I'm still not up to speed on this bonding concept, hence the question. Is there a specific way of doing it so that it will ensure that it trips the breaker? Do the grounds go IN the panel or are they attached to ground rod (assuming ground rod is attached to panel). Does it matter? At what point (if any) can the ground wires be combined into one? I seem to remember something about you couldn't use a junction box-- everyone had to have a home run. I just don't understand enough about this to know where that home run ends? Not sure if this is relate to the above, but he did mention something about "looping" the grounds--but I am not sure where he meant that or what it means. Hopefully, that is a good enough description that you can not only answer questions, but raise any issues that you forsee (as you can tell, I am not too up on electrical). -- John Not getting into the NEC, but if you have access via a crawl space to drop new ground wires down from the receptacles in question and run them back to the panel, I'd simply run a complete new wire (romex 12/2 w/ground) and be done with it. The extra cost of the wire is piddly compared to the labor required to run it, which should be about the same whether it's running a single conductor or a full cable. If / when you sell the place in the future, an add-on ground along side old two conductor romex is likely to raise questions with any home inspectors / buyers even if it's to code, vs. clean new runs of modern grounded romex. |
#3
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
"John Ross" wrote in message ups.com... Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? Once the ground rod is driven and connected to the buss in the panel, it also becomes attached to the existing water pipe ground which also runs to the buss in the panel. The individual ground conductor can be attached to any point along the grounding electrode system. The most practical location is probably the panel. IMO running ground conductors to non grounded outlets looks Rube Goldberg, if it's not to dificult, I would run new cables to these outlets, gang a few together in a jbox then run a line back to the panel In doing the above, how specifically should it be done to meet NEC? If I understand, it will still need to be bonded to the water pipe. Should that be within 5 foot of water entrance point? And can you bond it to more than one place (i.e. to the 5 foot and also close to panel?). I'm still not up to speed on this bonding concept, hence the question. Is there a specific way of doing it so that it will ensure that it trips the breaker? Do the grounds go IN the panel or are they attached to ground rod (assuming ground rod is attached to panel). Does it matter? At what point (if any) can the ground wires be combined into one? I seem to remember something about you couldn't use a junction box-- everyone had to have a home run. I just don't understand enough about this to know where that home run ends? Not sure if this is relate to the above, but he did mention something about "looping" the grounds--but I am not sure where he meant that or what it means. Hopefully, that is a good enough description that you can not only answer questions, but raise any issues that you forsee (as you can tell, I am not too up on electrical). -- John |
#4
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
The approval for any electrical work is up to your local electrical
inspector. They usually have office hours and will answer questions. Take plenty of pictures so the inspector can see what is what. (pictures of house, outlets, electrical panels, existing grounding, etc.) In my case I was required to install two grounds rods 6 ft. apart and run a ground wire from these to the panel. And install a cold water pipe ground and run this via a separate ground wire to the panel. Also to connect a ground wire from the cold water pipe to the hot water pipe on the water heater. My ground system is good. If one ground wire gets broken or disconnected (quite common actually), there is another ground wire and ground. Also there is a "central point of ground", that being at the main electrical panel. Once you get a good grounding system, then run new romex wires with ground to outlets you want grounds on. Installing a separate 20 amp outlet on its own breaker for the computer is a good idea. "John Ross" wrote in message Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? In doing the above, how specifically should it be done to meet NEC? If I understand, it will still need to be bonded to the water pipe. Should that be within 5 foot of water entrance point? And can you bond it to more than one place (i.e. to the 5 foot and also close to panel?). I'm still not up to speed on this bonding concept, hence the question. Is there a specific way of doing it so that it will ensure that it trips the breaker? Do the grounds go IN the panel or are they attached to ground rod (assuming ground rod is attached to panel). Does it matter? At what point (if any) can the ground wires be combined into one? I seem to remember something about you couldn't use a junction box-- everyone had to have a home run. I just don't understand enough about this to know where that home run ends? Not sure if this is relate to the above, but he did mention something about "looping" the grounds--but I am not sure where he meant that or what it means. Hopefully, that is a good enough description that you can not only answer questions, but raise any issues that you forsee (as you can tell, I am not too up on electrical). -- John |
#5
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? In doing the above, how specifically should it be done to meet NEC? If I understand, it will still need to be bonded to the water pipe. Should that be within 5 foot of water entrance point? And can you bond it to more than one place (i.e. to the 5 foot and also close to panel?). I'm still not up to speed on this bonding concept, hence the question. Is there a specific way of doing it so that it will ensure that it trips the breaker? Do the grounds go IN the panel or are they attached to ground rod (assuming ground rod is attached to panel). Does it matter? At what point (if any) can the ground wires be combined into one? I seem to remember something about you couldn't use a junction box-- everyone had to have a home run. I just don't understand enough about this to know where that home run ends? Not sure if this is relate to the above, but he did mention something about "looping" the grounds--but I am not sure where he meant that or what it means. Hopefully, that is a good enough description that you can not only answer questions, but raise any issues that you forsee (as you can tell, I am not too up on electrical). Running a separate circuit (including ground) to a dedicated outlet with its own breaker is the best idea. Think of the water pipes as a potential source of power - that's why they are grounded. The water pipes are not the SOURCE of a ground for the electrical system - grounding pipes protects you when you come into contact with the plumbing. |
#6
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
"HeyBub" wrote in message ... John Ross wrote: Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? In doing the above, how specifically should it be done to meet NEC? If I understand, it will still need to be bonded to the water pipe. Should that be within 5 foot of water entrance point? And can you bond it to more than one place (i.e. to the 5 foot and also close to panel?). I'm still not up to speed on this bonding concept, hence the question. Is there a specific way of doing it so that it will ensure that it trips the breaker? Do the grounds go IN the panel or are they attached to ground rod (assuming ground rod is attached to panel). Does it matter? At what point (if any) can the ground wires be combined into one? I seem to remember something about you couldn't use a junction box-- everyone had to have a home run. I just don't understand enough about this to know where that home run ends? Not sure if this is relate to the above, but he did mention something about "looping" the grounds--but I am not sure where he meant that or what it means. Hopefully, that is a good enough description that you can not only answer questions, but raise any issues that you forsee (as you can tell, I am not too up on electrical). Running a separate circuit (including ground) to a dedicated outlet with its own breaker is the best idea. Think of the water pipes as a potential source of power - that's why they are grounded. The water pipes are not the SOURCE of a ground for the electrical system - grounding pipes protects you when you come into contact with the plumbing. This is incorrect. Ten foot of buried metal water pipe is the source of ground and is required to be bonded to other grounding electrodes and attached to the service disconnect panel |
#7
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Pete C. wrote: John Ross wrote: Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? In doing the above, how specifically should it be done to meet NEC? If I understand, it will still need to be bonded to the water pipe. Should that be within 5 foot of water entrance point? And can you bond it to more than one place (i.e. to the 5 foot and also close to panel?). I'm still not up to speed on this bonding concept, hence the question. Is there a specific way of doing it so that it will ensure that it trips the breaker? Do the grounds go IN the panel or are they attached to ground rod (assuming ground rod is attached to panel). Does it matter? At what point (if any) can the ground wires be combined into one? I seem to remember something about you couldn't use a junction box-- everyone had to have a home run. I just don't understand enough about this to know where that home run ends? Not sure if this is relate to the above, but he did mention something about "looping" the grounds--but I am not sure where he meant that or what it means. Hopefully, that is a good enough description that you can not only answer questions, but raise any issues that you forsee (as you can tell, I am not too up on electrical). -- John Not getting into the NEC, but if you have access via a crawl space to drop new ground wires down from the receptacles in question and run them back to the panel, I'd simply run a complete new wire (romex 12/2 w/ground) and be done with it. The extra cost of the wire is piddly compared to the labor required to run it, which should be about the same whether it's running a single conductor or a full cable. If / when you sell the place in the future, an add-on ground along side old two conductor romex is likely to raise questions with any home inspectors / buyers even if it's to code, vs. clean new runs of modern grounded romex. Clarifiation: The wiring does not run in the crawlspace, so you would not have a new ground running along side old 2 wire romex. Obviously, if it was like that I can see your point. The crawlspace is only being used so we don't have to tear up the walls and rewire the whole house. -- John |
#8
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
RBM remove this wrote: "John Ross" wrote in message ups.com... Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? Once the ground rod is driven and connected to the buss in the panel, it also becomes attached to the existing water pipe ground which also runs to the buss in the panel. The individual ground conductor can be attached to any point along the grounding electrode system. The most practical location is probably the panel. IMO running ground conductors to non grounded outlets looks Rube Goldberg, if it's not to dificult, I would run new cables to these outlets, gang a few together in a jbox then run a line back to the panel I may have not made this clear, but the original wiring is NOT run in the crawlspace. The idea is to drill a hole up through the floor and bring the ground from receptacle down to crawlspace and then over to panel. I assume in this situation you could not just run a new romex to each one unless it was dedicated? As far as being connected to the water pipe. My understanding is that back then they just connected it to the closest pipe to the panel. So what I was asking is if the pipe connection should be connected closer to the water entrance point of the house (which is the opposite side of the house)? Also, can you explain what he meant by "looping the grounds?" Any search on that term brings up very negative things so I am not sure if I have it in the right context. thanks, -- John |
#9
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
wrote: On Sat, 22 Sep 2007 06:24:38 -0700, John Ross wrote: At what point (if any) can the ground wires be combined into one? You can use a single equipment grounding conductor for several circuits as long as it is sized to the biggest one. I have seen people run one #8 solid as a bus and use split bolts to pick up grounding pigtails from the various circuits along the way. The code is really pretty ambiguous about wiring methods when you are adding an EGC to a circuit that doesn't have one. As long as you are getting back to the main bonding jumper with your ground (the bus in the panel) in a solidly connected way you should be OK. I was more concerned with the possibility of having the grounds run to to a junction box, then have a single ground come out of that and then have THAT connect to the panel. I saw someone say that the NEC for this type of retrofit implies that each ground has to make a home run? The other thing is that someone brought up something about creating a magnetic loop (not sure if that is correct term) and implied that could be a big problem in that it would raise resistance in the grounds wires. thanks -- John Ross |
#10
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
RBM wrote: "HeyBub" wrote in message ... Running a separate circuit (including ground) to a dedicated outlet with its own breaker is the best idea. Think of the water pipes as a potential source of power - that's why they are grounded. The water pipes are not the SOURCE of a ground for the electrical system - grounding pipes protects you when you come into contact with the plumbing. This is incorrect. Ten foot of buried metal water pipe is the source of ground and is required to be bonded to other grounding electrodes and attached to the service disconnect panel This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? -- John |
#11
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
RBM wrote: "HeyBub" wrote in message ... Running a separate circuit (including ground) to a dedicated outlet with its own breaker is the best idea. Think of the water pipes as a potential source of power - that's why they are grounded. The water pipes are not the SOURCE of a ground for the electrical system - grounding pipes protects you when you come into contact with the plumbing. This is incorrect. Ten foot of buried metal water pipe is the source of ground and is required to be bonded to other grounding electrodes and attached to the service disconnect panel This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? -- John |
#12
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 23, 9:21?am, John Ross wrote:
RBM wrote: "HeyBub" wrote in message ... Running a separate circuit (including ground) to a dedicated outlet with its own breaker is the best idea. Think of the water pipes as a potential source of power - that's why they are grounded. The water pipes are not the SOURCE of a ground for the electrical system - grounding pipes protects you when you come into contact with the plumbing. This is incorrect. Ten foot of buried metal water pipe is the source of ground and is required to be bonded to other grounding electrodes and attached to the service disconnect panel This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? -- John new bonded ground should be right where pipe leaves home. how many AMPS is the main panel? 60? I would start by replacing the main panel and service drop. Is your fuses? |
#13
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Bill wrote: The approval for any electrical work is up to your local electrical inspector. They usually have office hours and will answer questions. Take plenty of pictures so the inspector can see what is what. (pictures of house, outlets, electrical panels, existing grounding, etc.) In my case I was required to install two grounds rods 6 ft. apart and run a ground wire from these to the panel. And install a cold water pipe ground and run this via a separate ground wire to the panel. Also to connect a ground wire from the cold water pipe to the hot water pipe on the water heater. My ground system is good. If one ground wire gets broken or disconnected (quite common actually), there is another ground wire and ground. Also there is a "central point of ground", that being at the main electrical panel. Once you get a good grounding system, then run new romex wires with ground to outlets you want grounds on. Installing a separate 20 amp outlet on its own breaker for the computer is a good idea. What was your original system? The hot water heater connection is a good idea. I am going to do that no matter what else. -- John |
#14
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
|
#16
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
The only part of the water main pipe into your house that can be used as a
grounding electrode is the first five feet from the point of entrance. A ground conductor attaches to the pipe and runs to the ground buss in your main service panel. In addition to that electrode, essentially two driven ground rods are required. They get driven six feet apart and another conductor is connected to them and run back to the ground buss in the main service panel, effectively bonding these rods to the service equipment and the water pipe. Looping is probably someone's expression for bonding "John Ross" wrote in message oups.com... RBM remove this wrote: "John Ross" wrote in message ups.com... Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? Once the ground rod is driven and connected to the buss in the panel, it also becomes attached to the existing water pipe ground which also runs to the buss in the panel. The individual ground conductor can be attached to any point along the grounding electrode system. The most practical location is probably the panel. IMO running ground conductors to non grounded outlets looks Rube Goldberg, if it's not to dificult, I would run new cables to these outlets, gang a few together in a jbox then run a line back to the panel I may have not made this clear, but the original wiring is NOT run in the crawlspace. The idea is to drill a hole up through the floor and bring the ground from receptacle down to crawlspace and then over to panel. I assume in this situation you could not just run a new romex to each one unless it was dedicated? As far as being connected to the water pipe. My understanding is that back then they just connected it to the closest pipe to the panel. So what I was asking is if the pipe connection should be connected closer to the water entrance point of the house (which is the opposite side of the house)? Also, can you explain what he meant by "looping the grounds?" Any search on that term brings up very negative things so I am not sure if I have it in the right context. thanks, -- John |
#17
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Yes, move it and leave the existing connection alone
"John Ross" wrote in message oups.com... RBM wrote: "HeyBub" wrote in message ... Running a separate circuit (including ground) to a dedicated outlet with its own breaker is the best idea. Think of the water pipes as a potential source of power - that's why they are grounded. The water pipes are not the SOURCE of a ground for the electrical system - grounding pipes protects you when you come into contact with the plumbing. This is incorrect. Ten foot of buried metal water pipe is the source of ground and is required to be bonded to other grounding electrodes and attached to the service disconnect panel This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? -- John |
#18
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
"John Ross" wrote in message
Bill wrote: The approval for any electrical work is up to your local electrical inspector. They usually have office hours and will answer questions. Take plenty of pictures so the inspector can see what is what. (pictures of house, outlets, electrical panels, existing grounding, etc.) In my case I was required to install two grounds rods 6 ft. apart and run a ground wire from these to the panel. And install a cold water pipe ground and run this via a separate ground wire to the panel. Also to connect a ground wire from the cold water pipe to the hot water pipe on the water heater. My ground system is good. If one ground wire gets broken or disconnected (quite common actually), there is another ground wire and ground. Also there is a "central point of ground", that being at the main electrical panel. Once you get a good grounding system, then run new romex wires with ground to outlets you want grounds on. Installing a separate 20 amp outlet on its own breaker for the computer is a good idea. What was your original system? The hot water heater connection is a good idea. I am going to do that no matter what else. My original grounding system was no ground at all, an old rusted fuse box, and all sorts of other nasty stuff in an 80 year old house... |
#19
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
Pete C. wrote: John Ross wrote: Quick recap: 1960 house, crawlspace, 2 wire romex, grounds only run to baths and kitchen, galvanized water pipe to street was used for grounding (NO ground rod). I want to ground 2 or 3 outlets and discussed going to a water pipe method here. Everyone mentioned the "5 foot rule" per NEC. Some were concerned about the ground not tripping the breaker. I have had nothing but problems finding a good electrician in my town!!! I think I finally did and want input on his plan. Talking on the phone, he proposed the following and said it would pass code (local): 1. Drive 8 foot ground rod and connect to panel. 2. From desired ungrounded receptacle(s) go through floor to crawlspace with ground wire and run back to panel. 3. One receptacle is for pc, and he suggested doing same method, but use new wire and make it a dedicated circuit so there would be no interference or something with pc. Not sure if this is necessary? In doing the above, how specifically should it be done to meet NEC? If I understand, it will still need to be bonded to the water pipe. Should that be within 5 foot of water entrance point? And can you bond it to more than one place (i.e. to the 5 foot and also close to panel?). I'm still not up to speed on this bonding concept, hence the question. Is there a specific way of doing it so that it will ensure that it trips the breaker? Do the grounds go IN the panel or are they attached to ground rod (assuming ground rod is attached to panel). Does it matter? At what point (if any) can the ground wires be combined into one? I seem to remember something about you couldn't use a junction box-- everyone had to have a home run. I just don't understand enough about this to know where that home run ends? Not sure if this is relate to the above, but he did mention something about "looping" the grounds--but I am not sure where he meant that or what it means. Hopefully, that is a good enough description that you can not only answer questions, but raise any issues that you forsee (as you can tell, I am not too up on electrical). -- John Not getting into the NEC, but if you have access via a crawl space to drop new ground wires down from the receptacles in question and run them back to the panel, I'd simply run a complete new wire (romex 12/2 w/ground) and be done with it. The extra cost of the wire is piddly compared to the labor required to run it, which should be about the same whether it's running a single conductor or a full cable. If / when you sell the place in the future, an add-on ground along side old two conductor romex is likely to raise questions with any home inspectors / buyers even if it's to code, vs. clean new runs of modern grounded romex. Clarifiation: The wiring does not run in the crawlspace, so you would not have a new ground running along side old 2 wire romex. Obviously, if it was like that I can see your point. The crawlspace is only being used so we don't have to tear up the walls and rewire the whole house. -- John My point is that if you have access to the crawl space you can run new 12/2 w/ground romex to the receptacle locations and install new grounded receptacles. The existing ungrounded wiring can simply be cut back and abandoned in place in the walls (disconnected from power sources of course). I was looking at purchasing the house and found the separate ground addition, I would be factoring in my cost to strip it out and replace it "correctly" into any offer I made. Code compliance has no relevance in such buyer decisions and even if the additional ground installation is 100% code compliant, a potential buyer is under no obligation to accept it. I know not every home maintenance decision should be based on future sales worthiness, but the point here is that the material and labor difference between doing the job in a manner likely to put off future buyers, and doing the job in a more acceptable manner is relatively small. |
#20
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 23, 9:22 am, John Ross wrote:
This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? The purpose of a green safety ground wire is to connect fault electricity to the ground bus bar inside breaker box. Electric faults must connect back to breaker box to trip a circuit breaker - for human safety. Pipes must never be a carrier of electricity - an attitude change from many decades ago. That cold water pipe ground clamp is to remove electricity from water pipes; not to dump electricity into water pipes. Its primary function is human safety. Your earth ground is those rod electrodes that are nearby the breaker box and dedicated only for earthing. BTW, those rods should be separated eight feet or more (not six feet). They bond the breaker box, short, to earth ground. That safety ground wire to water pipe must be less than 5 feet from where pipe enters the building. This for numerous reasons including to pickup any stray currents that might enter from outside via city water. Some jurisdictions also want a steel bathtub bonded by a dedicated 6 AWG ground wire to breaker box safety ground. Again, a connection for same reason - to remove electricity from plumbing. Plumbing must not carry electricity. General concepts for safety grounding are summarized by volts500 in alt.home.repair entitled "Grounding Rod Info" on 12 July 2003 at http://tinyurl.com/hkjq Post includes good safety tips such as hot water heater and meter ground shunts. |
#21
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
"w_tom" wrote in message oups.com... On Sep 23, 9:22 am, John Ross wrote: This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? The purpose of a green safety ground wire is to connect fault electricity to the ground bus bar inside breaker box. Electric faults must connect back to breaker box to trip a circuit breaker - for human safety. Pipes must never be a carrier of electricity - an attitude change from many decades ago. That cold water pipe ground clamp is to remove electricity from water pipes; not to dump electricity into water pipes. Its primary function is human safety. Your earth ground is those rod electrodes that are nearby the breaker box and dedicated only for earthing. BTW, those rods should be separated eight feet or more (not six feet). They bond the breaker box, short, to earth ground. Your grounding electrode system is those driven rods, 10 feet or more buried metallic water pipe, well casing and any of a number of other types of electrodes NEC 250.53B Ground rod spacing minimum 6 feet apart, albeit 8 feet would probably be better That safety ground wire to water pipe must be less than 5 feet from where pipe enters the building. This for numerous reasons including to pickup any stray currents that might enter from outside via city water. Some jurisdictions also want a steel bathtub bonded by a dedicated 6 AWG ground wire to breaker box safety ground. Again, a connection for same reason - to remove electricity from plumbing. Plumbing must not carry electricity. General concepts for safety grounding are summarized by volts500 in alt.home.repair entitled "Grounding Rod Info" on 12 July 2003 at http://tinyurl.com/hkjq Post includes good safety tips such as hot water heater and meter ground shunts. |
#22
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
w_tom wrote:
On Sep 23, 9:22 am, John Ross wrote: This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? Pipes must never be a carrier of electricity - an attitude change from many decades ago. That cold water pipe ground clamp is to remove electricity from water pipes; not to dump electricity into water pipes. Its primary function is human safety. Its the village idiot back again with his nonsense about water pipes. Buried metal water service pipe at least 10 ft length has been *required* to be used as a grounding electrode since 1777. Grounding wires, that the OP is interested in, can connect in the first 5 feet of water pipe if the pipe is used as a grounding electrode. “Remove electricity from water pipes” is technical illiteracy. That safety ground wire to water pipe must be less than 5 feet from where pipe enters the building. If the pipe is only being ‘bonded’ (not used as an earthing electrode) the connection does not have to be within 5 feet of the entrance. It is not used as an earthing electrode only when less than 10 ft buried metal. This for numerous reasons including to pickup any stray currents that might enter from outside via city water. More technical illiteracy. Some jurisdictions also want a steel bathtub bonded by a dedicated 6 AWG ground wire to breaker box safety ground. Name one. -- bud-- |
#23
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
bud-- wrote: w_tom wrote: On Sep 23, 9:22 am, John Ross wrote: This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? Pipes must never be a carrier of electricity - an attitude change from many decades ago. That cold water pipe ground clamp is to remove electricity from water pipes; not to dump electricity into water pipes. Its primary function is human safety. Its the village idiot back again with his nonsense about water pipes. Buried metal water service pipe at least 10 ft length has been *required* to be used as a grounding electrode since 1777. Grounding wires, that the OP is interested in, can connect in the first 5 feet of water pipe if the pipe is used as a grounding electrode. "Remove electricity from water pipes" is technical illiteracy. That safety ground wire to water pipe must be less than 5 feet from where pipe enters the building. If the pipe is only being 'bonded' (not used as an earthing electrode) the connection does not have to be within 5 feet of the entrance. It is not used as an earthing electrode only when less than 10 ft buried metal. This for numerous reasons including to pickup any stray currents that might enter from outside via city water. More technical illiteracy. Some jurisdictions also want a steel bathtub bonded by a dedicated 6 AWG ground wire to breaker box safety ground. Name one. -- bud-- If it is connected at the first five feet and there is the all metal water pipe, would it serve as BOTH a bonding and and additional "ground"? In my case the house already uses the water pipe as the only ground. So if a ground rod was installed and then "bonded" to the pipe, wouldn't the pipe still act as sorta a second ground anyway (like having 2 ground rods, maybe)? As far as your comment about it would be ok to just attach the ground wire to the first five feet of the pipe to ground the outlet, doesn't that contradict what you previously have said about that would not trip the breaker and wanted me to make sure the wire went back to the panel? thanks, -- John |
#24
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John, the thing you're not getting is that it's a grounding electrode
system. Everything that is part of it is connected together and becomes one. If your outlet ground was connected to the panel or the water pipe (first 5 feet) or a ground rod, it's all the same, as they are interconnected "John Ross" wrote in message ups.com... bud-- wrote: w_tom wrote: On Sep 23, 9:22 am, John Ross wrote: This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? Pipes must never be a carrier of electricity - an attitude change from many decades ago. That cold water pipe ground clamp is to remove electricity from water pipes; not to dump electricity into water pipes. Its primary function is human safety. Its the village idiot back again with his nonsense about water pipes. Buried metal water service pipe at least 10 ft length has been *required* to be used as a grounding electrode since 1777. Grounding wires, that the OP is interested in, can connect in the first 5 feet of water pipe if the pipe is used as a grounding electrode. "Remove electricity from water pipes" is technical illiteracy. That safety ground wire to water pipe must be less than 5 feet from where pipe enters the building. If the pipe is only being 'bonded' (not used as an earthing electrode) the connection does not have to be within 5 feet of the entrance. It is not used as an earthing electrode only when less than 10 ft buried metal. This for numerous reasons including to pickup any stray currents that might enter from outside via city water. More technical illiteracy. Some jurisdictions also want a steel bathtub bonded by a dedicated 6 AWG ground wire to breaker box safety ground. Name one. -- bud-- If it is connected at the first five feet and there is the all metal water pipe, would it serve as BOTH a bonding and and additional "ground"? In my case the house already uses the water pipe as the only ground. So if a ground rod was installed and then "bonded" to the pipe, wouldn't the pipe still act as sorta a second ground anyway (like having 2 ground rods, maybe)? As far as your comment about it would be ok to just attach the ground wire to the first five feet of the pipe to ground the outlet, doesn't that contradict what you previously have said about that would not trip the breaker and wanted me to make sure the wire went back to the panel? thanks, -- John |
#25
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
bud-- wrote: w_tom wrote: On Sep 23, 9:22 am, John Ross wrote: This is what I was getting at. Should the connection to the water pipe be moved to within 5 feet of the entrance of the house (to be closer to that 10 foot of pipe you refer to).And also does it matter if the old connection is left (i.e. 2 places it is bonded at)? Pipes must never be a carrier of electricity - an attitude change from many decades ago. That cold water pipe ground clamp is to remove electricity from water pipes; not to dump electricity into water pipes. Its primary function is human safety. Its the village idiot back again with his nonsense about water pipes. Buried metal water service pipe at least 10 ft length has been *required* to be used as a grounding electrode since 1777. Grounding wires, that the OP is interested in, can connect in the first 5 feet of water pipe if the pipe is used as a grounding electrode. "Remove electricity from water pipes" is technical illiteracy. That safety ground wire to water pipe must be less than 5 feet from where pipe enters the building. If the pipe is only being 'bonded' (not used as an earthing electrode) the connection does not have to be within 5 feet of the entrance. It is not used as an earthing electrode only when less than 10 ft buried metal. This for numerous reasons including to pickup any stray currents that might enter from outside via city water. More technical illiteracy. Some jurisdictions also want a steel bathtub bonded by a dedicated 6 AWG ground wire to breaker box safety ground. Name one. If it is connected at the first five feet and there is the all metal water pipe, would it serve as BOTH a bonding and and additional "ground"? If a water pipe is used as a grounding electrode, it is "bonded" in the process. In my case the house already uses the water pipe as the only ground. So if a ground rod was installed and then "bonded" to the pipe, wouldn't the pipe still act as sorta a second ground anyway (like having 2 ground rods, maybe)? As RBM said, the grounding electrodes form a system. Your water pipe and the added ground rod are *both* grounding electrodes for your electrical service. You could have more electrodes. Your added ground wires to receptacles can be connected anywhere in that *system*. That includes the service panel ground bar, the first 5 feet of the water pipe and the heavy connecting wires to the water pipe and ground rod. An added ground rod can be connected anywhere in the present water pipe grounding electrode system (but there are rules). An added ground rod would probably not be connected to the first 5 feet of water pipe (but it could be) - there are usually better places to make the connection. I would usually make added connections to the heavy connecting wires using a split bolt (also known as a karnie). As far as your comment about it would be ok to just attach the ground wire to the first five feet of the pipe to ground the outlet, doesn't that contradict what you previously have said about that would not trip the breaker and wanted me to make sure the wire went back to the panel? I believe I said there has to be a *metal* path back to the panel. What is not allowed is using the earth as part of the path - like connecting your added ground wires only to a ground rod with no additional metal path to the electrical service. I questioned using a ground rod as "insurance" for a metal path because a ground rod (with earth path) provides very bad "insurance". -- bud-- |
#26
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 26, 9:04 am, John Ross wrote:
If it is connected at the first five feet and there is the all metal water pipe, would it serve as BOTH a bonding and and additional "ground"? In my case the house already uses the water pipe as the only ground. So if a ground rod was installed and then "bonded" to the pipe, wouldn't the pipe still act as sorta a second ground anyway (like having 2 ground rods, maybe)? The heart of a human safety ground system is a bus bar inside that breaker box. Everything it grounds (bonds to) must connect directly to that bus bar by approved materials. For example, you cannot connect a wall receptacle to an earth ground or water pipe. Neither earth nor pipe to is approved to make that connection. Code says there must be a direct wire connection from wall receptacle grounds to breaker box safety ground. Each ground for each circuit must connect directly back to the breaker box safety ground. Each wire that earths that bus bar also must connect directly back to the breaker box. Code even defines which conductors can only make that connection. Connecting a ground rod to breaker box via any pipes is not valid. The ground rod will better earth a water pipe. But from the perspective of a breaker box, that is still only a water pipe connection - no longer sufficient for earthing. Irrelevant is whether your water pipe does or does not create an earth ground. Your breaker box must be earthed by some other earthing electrode with its own dedicated connection - regardless of whether a water pipe ground does or does not exist. Code is quite blunt about it. The code lists electrodes that are sufficient for a breaker box earth ground. Cold water pipe is no longer on that list. The water pipe is only an earth ground that can be an 'also' earth ground. Water pipe earth ground is no longer sufficient. Code lists other electrodes that must make ant earth ground. List includes the dedicated ground rod, a large earthing plate, or an Ufer ground. Each must make a dedicated connection to breaker box safety ground using listed conductors. Pipes, which are installed for other (non-electrical) purposes, are no longer sufficient for earthing. Take everything Bud posts with a grain of salt. Truth is not a strong suite with salesmen - especially those who only learn from salesmen classes. What jurisdictions now required steel bathtubs bonded to breaker box safety ground? Many including mine. If Bud had any experience, he would know that. But the point of that example: pipes are not longer sufficient for bonding or earthing anything. Pipes bonding a steel bathtub, in some jurisdictions, are no longer considered sufficient for human safety. If a pipe is being used for earthing, one must still install another earthing electrode as if the pipe did not even exist. It does not matter if a metal connection exists. Conductor that connects an earthing electrode to that bus bar inside a breaker box must be 'listed' - approved for making a connection. Totally irrelevant is whether a connection is metal. It must be even better. It must be approved for making that connection. Even if bonding an earth ground rod to a water pipe, to the breaker box, that is only a water pipe earth ground. To meet post 1990 code requirements, that earth ground rod must be bonded directly to the breaker box via 6 AWG bare copper wire. Water pipes are no long acceptable as a connecting device. When bonding an earth ground rod via water pipes, then you are using pipes as a conductor. Water pipes are no longer sufficient for earthing AND are not approved for making that electrical connection. |
#27
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
I never saw such a pile of cockamamie nonsense in my life. Instead of
dreaming this stuff up, Please direct us to the locations in the NEC where we can find this "information" "w_tom" wrote in message ups.com... On Sep 26, 9:04 am, John Ross wrote: If it is connected at the first five feet and there is the all metal water pipe, would it serve as BOTH a bonding and and additional "ground"? In my case the house already uses the water pipe as the only ground. So if a ground rod was installed and then "bonded" to the pipe, wouldn't the pipe still act as sorta a second ground anyway (like having 2 ground rods, maybe)? The heart of a human safety ground system is a bus bar inside that breaker box. Everything it grounds (bonds to) must connect directly to that bus bar by approved materials. For example, you cannot connect a wall receptacle to an earth ground or water pipe. Neither earth nor pipe to is approved to make that connection. Code says there must be a direct wire connection from wall receptacle grounds to breaker box safety ground. Each ground for each circuit must connect directly back to the breaker box safety ground. Each wire that earths that bus bar also must connect directly back to the breaker box. Code even defines which conductors can only make that connection. Connecting a ground rod to breaker box via any pipes is not valid. The ground rod will better earth a water pipe. But from the perspective of a breaker box, that is still only a water pipe connection - no longer sufficient for earthing. Irrelevant is whether your water pipe does or does not create an earth ground. Your breaker box must be earthed by some other earthing electrode with its own dedicated connection - regardless of whether a water pipe ground does or does not exist. Code is quite blunt about it. The code lists electrodes that are sufficient for a breaker box earth ground. Cold water pipe is no longer on that list. The water pipe is only an earth ground that can be an 'also' earth ground. Water pipe earth ground is no longer sufficient. Code lists other electrodes that must make ant earth ground. List includes the dedicated ground rod, a large earthing plate, or an Ufer ground. Each must make a dedicated connection to breaker box safety ground using listed conductors. Pipes, which are installed for other (non-electrical) purposes, are no longer sufficient for earthing. Take everything Bud posts with a grain of salt. Truth is not a strong suite with salesmen - especially those who only learn from salesmen classes. What jurisdictions now required steel bathtubs bonded to breaker box safety ground? Many including mine. If Bud had any experience, he would know that. But the point of that example: pipes are not longer sufficient for bonding or earthing anything. Pipes bonding a steel bathtub, in some jurisdictions, are no longer considered sufficient for human safety. If a pipe is being used for earthing, one must still install another earthing electrode as if the pipe did not even exist. It does not matter if a metal connection exists. Conductor that connects an earthing electrode to that bus bar inside a breaker box must be 'listed' - approved for making a connection. Totally irrelevant is whether a connection is metal. It must be even better. It must be approved for making that connection. Even if bonding an earth ground rod to a water pipe, to the breaker box, that is only a water pipe earth ground. To meet post 1990 code requirements, that earth ground rod must be bonded directly to the breaker box via 6 AWG bare copper wire. Water pipes are no long acceptable as a connecting device. When bonding an earth ground rod via water pipes, then you are using pipes as a conductor. Water pipes are no longer sufficient for earthing AND are not approved for making that electrical connection. |
#28
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 26, 8:00 pm, "RBM" rbm2(remove wrote:
I never saw such a pile of cockamamie nonsense in my life. Instead of dreaming this stuff up, Please direct us to the locations in the NEC where we can find this "information" Instead of posting denials, instead, ask about the sentences you do not understand. Meanwhile, if you think pipes are acceptable as electrical conductors, then don't bother. If you don't even know that basic concept, then ignorance will not even be justified by a reply. |
#29
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Virtually everything you wrote is baseless incoherent gibberish, otherwise
you'd be able to produce some NEC documentation to back it up "w_tom" wrote in message ups.com... On Sep 26, 8:00 pm, "RBM" rbm2(remove wrote: I never saw such a pile of cockamamie nonsense in my life. Instead of dreaming this stuff up, Please direct us to the locations in the NEC where we can find this "information" Instead of posting denials, instead, ask about the sentences you do not understand. Meanwhile, if you think pipes are acceptable as electrical conductors, then don't bother. If you don't even know that basic concept, then ignorance will not even be justified by a reply. |
#30
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
w_tom wrote:
On Sep 26, 8:00 pm, "RBM" rbm2(remove wrote: I never saw such a pile of cockamamie nonsense in my life. Instead of dreaming this stuff up, Please direct us to the locations in the NEC where we can find this "information" Instead of posting denials, instead, ask about the sentences you do not understand. Meanwhile, if you think pipes are acceptable as electrical conductors, then don't bother. If you don't even know that basic concept, then ignorance will not even be justified by a reply. Gee. NEC seems to think that water pipes are permitted as Grounding electrodes. Section 250.52(A) Electrodes Permitted for Grounding. subsection (1) "Metal Underground Wter Pipe" Go read it if you can. |
#31
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
RBM remove this wrote: John, the thing you're not getting is that it's a grounding electrode system. Everything that is part of it is connected together and becomes one. If your outlet ground was connected to the panel or the water pipe (first 5 feet) or a ground rod, it's all the same, as they are interconnected I think one thing that throws me off is that when they built these houses, they just connected to the nearest water pipe to the panel (which is on the opposite side of house where water pipe enters). I had an electrician come out and told me he would drive a ground rod and just leave the pipe bond alone (since it is "already connected"). I asked about the 5 foot thing and as EVERY electrician in this town I have talked to, get a blank look or a "I never heard of that." You can see why I am going crazy. But back to your comment about the "grounding electrode system." I thought that 5 foot rule was because of people replacing pipes with plastic. OK, so that makes sense if you look at it as a ground to earth. In other words, if someone adds a plastic pipe past the 5 foot, you now have the earth ground, but I thought the idea of "bonding" pipes was to (also) protect the pipes from becoming energized if a hot wire touches one. So wouldn't you want a requirement to have it bonded to other parts beyond the 5 foot also? Another thing: Not one electrician has told me anything about 2 ground rods; they just say one. Is that a requirement, or just something you think is better? Thanks for the patience It seems my city doesn't have one competent electrician! -- John |
#32
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
bud-- wrote: John Ross said: As far as your comment about it would be ok to just attach the ground wire to the first five feet of the pipe to ground the outlet, doesn't that contradict what you previously have said about that would not trip the breaker and wanted me to make sure the wire went back to the panel? I believe I said there has to be a *metal* path back to the panel. What is not allowed is using the earth as part of the path - like connecting your added ground wires only to a ground rod with no additional metal path to the electrical service. I questioned using a ground rod as "insurance" for a metal path because a ground rod (with earth path) provides very bad "insurance". Yes, I remember that was the guy who wanted to just put a ground rod in and connect it to the water pipe. I think that is when you got into different resistances(?) and might not go back to the panel and thus not trip breaker. So if the new ground rod IS connected to the panel, and the water pipe still serves as a ground, then you are saying that is not a concern as far as tripping breaker if added ground wire is connected at any point? I guess I got mixed up, but I thought you were saying that the ground rod had more resistance than the water pipe. So am I correct in that you were just concerned about that if the ground rod was not connected to the panel? That would clear up some confusion, because I was thinking you were saying that adding the ground rod might actually give an inferior ground that what I already have. Thanks for your patience also I wish you or RBM could come out and do the job! -- John |
#33
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
M Q wrote:
w_tom wrote: On Sep 26, 8:00 pm, "RBM" rbm2(remove wrote: I never saw such a pile of cockamamie nonsense in my life. Instead of dreaming this stuff up, Please direct us to the locations in the NEC where we can find this "information" Instead of posting denials, instead, ask about the sentences you do not understand. Meanwhile, if you think pipes are acceptable as electrical conductors, then don't bother. If you don't even know that basic concept, then ignorance will not even be justified by a reply. Gee. NEC seems to think that water pipes are permitted as Grounding electrodes. Section 250.52(A) Electrodes Permitted for Grounding. subsection (1) "Metal Underground Wter Pipe" Go read it if you can. Not only permitted - they are *required* to be used as electrodes. w_ uses google-groups to find "grounding" so he can post his bullcrap. He gets corrected regularly on this newsgroup, but it doesn't matter. You can't argue with a Jehovah's witness. -- bud-- |
#34
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 27, 9:19 am, John Ross wrote:
Yes, I remember that was the guy who wanted to just put a ground rod in and connect it to the water pipe. I think that is when you got into different resistances(?) and might not go back to the panel and thus not trip breaker. Apparently, you are talking about connecting a ground rod to a 6 AWG wire that also connects to water pipe. But that is not what you posted. You posted bonding a ground rod directly to water pipe which is not acceptable. That '5 foot' requirement is for numerous reasons. One is due to currents existing outside the building. A water pipe entering the building must be bonded to the breaker box safety ground where those currents would enter the building. Those currents would only travel inside the builiding on less than 5 feet. Better ground means no wire splices. Although not require by code, you want that earthing rod to be connected by a continuous 6 AWG wire - no splices. One ground rod is sufficient if its resistance measures less than 25 ohms. Many electricians don't even know how to measure that resistance. Code does not even define how to measure it. But certain soils are know to be sufficiently conductive. Therefore some electricians assume one ground rod is less than 25 ohms. Other electricians don't even bother 'guessing'. Code says that if a second rod does not drop resistance below 25 ohms, then nothing more need be done. Therefore other electricians automatically install two rods, don't care what the earthing resistance is, and don't buy an expensive ground resistance measuring tool. I am appauled that you would have Bud do any electrical work. He is a salesman - all about presentation and severely short on electrical knowledge. His knowledge comes only from reading books and taking seminars. He is a promoter - a snake oil salesman - has been exposed lying. Not anything metal can be used as Bud posts. For example, not any split bolt can be used. Grounding must be only with a split bolt that is also listed (approved). Not any pipe or rod can be used. Those too must be listed. Of course, this is not a problem. Electrical supply houses only sell earth ground rods that are listed. The point is that everything in that connection from ground rod to breaker box safety ground must be approved for that function. Connecting a ground rod to the water pipe - using the water pipe as a connection from ground rod to breaker box - violates code requirements for earthing. Whatever makes that connection must be 'listed' as a conductor. Water pipe is not approved as an electrical conductor. Only connection to a pipe is to remove electricity. Using pipes as an electrical conductor - dumping electricity into water pipes - is no longer permitted. |
#35
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Folks:
w_tom is slipping. I keep throwing random refs to surge protectors into Usenet and private-forum posts, and he never comes in to reply. Such neglect. Correct me if I am wrong, but there was a time when the NEC allowed one to ground equipment to a nearby water pipe. Of course, there was also a time (look at the 1899 code, which is posted online somewhere) when they allowed one to use a gas pipe as a grounding electrode. The time for either of those is not today. Back when men were men and jackets were braided, one could safely assume that all pipes were metal. Metal pipes full of water from the ground to the might well provide a nice low-impedance path to ground. But we can't assume that now. My own house has all metal pipes. Were I to open up a 2nd floor wall, and install a ground clamp on a cold water pipe, and test the ground, it would probably be excellent. But then the wall is closed, the clamp forgotten. Down the road, somebody replaces sections of the copper cold water pipes with plastic. Now I have a ground connected to a pipe, connected to nothing, and unless somebody tests the ground before and after plumbing, nobody is going to know about it. One day there is a direct short to ground. Fixtures have been replumbed with plastic supply connectors, except one old sink with separate hot and cold faucets. The cold faucet is now hot. The hot faucet is still bonded to ground at the water heater. Somebody turns one on, and reaches for the other... In any case, a falsely advertised ground is bad enough; a ground that goes to unbonded metal is worse, and that's what grounding to a water pipe can get you. Sometimes I see washers or dryers that had been grounded to a nearby pipe. This isn't as bad in an unfinished basement; you can see all the pipe, but it's also the situation where putting in a run of grounded cable and a new receptacle is very easy. Besides, if you're going to pull a single conductor into a space, you might as well pull in a cable, as somebody up there pointed out. G P |
#36
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 27, 1:35 am, M Q wrote:
Gee. NEC seems to think that water pipes are permitted as Grounding electrodes. Section 250.52(A) Electrodes Permitted for Grounding. subsection (1) "Metal Underground Wter Pipe" Go read it if you can. To perform electrical work, you are required to understand everything in Article 250.52. If using water pipe for earth ground, then any other electrode in Article 250.52(A) paragraphs two through seven also must be installed. Why? Water pipes are no longer sufficient for earthing. If using any other earthing electrode, then a water pipe earthing electrode is not required. BUT if using the water pipe for earthing, then the building remains insufficiently earthed according to Article 250.52. Another electrode must be installed. "A metal underground water pipe shall be supplemented by an additional electrode .... " A building must also be earthed by structure frame, Ufer ground, ground ring (halo ground), or an earthing plate or rod. Water pipe is no longer sufficient for earthing. You are supposed to read everything; not read selectively. Keep reading. Article 205.52(D)(2). Article 250 then continues another 12 pages farther. |
#37
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
bud-- wrote: John Ross said: As far as your comment about it would be ok to just attach the ground wire to the first five feet of the pipe to ground the outlet, doesn't that contradict what you previously have said about that would not trip the breaker and wanted me to make sure the wire went back to the panel? I believe I said there has to be a *metal* path back to the panel. What is not allowed is using the earth as part of the path - like connecting your added ground wires only to a ground rod with no additional metal path to the electrical service. I questioned using a ground rod as "insurance" for a metal path because a ground rod (with earth path) provides very bad "insurance". Yes, I remember that was the guy who wanted to just put a ground rod in and connect it to the water pipe. I think that is when you got into different resistances(?) and might not go back to the panel and thus not trip breaker. So if the new ground rod IS connected to the panel, and the water pipe still serves as a ground, then you are saying that is not a concern as far as tripping breaker if added ground wire is connected at any point? Your added ground wires can be connected at any point on the grounding electrode system. At any point there will be low resistance back to the ground bar in the service panel. I guess I got mixed up, but I thought you were saying that the ground rod had more resistance than the water pipe. So am I correct in that you were just concerned about that if the ground rod was not connected to the panel? Yup. Contrary to what the village idiot says, the resistance to earth of a pipe connected to a municipal metal water supply will be much lower than the resistance to earth of a ground rod. Both are used to connect the *system* to earth so the system 'ground' is at about the same potential as the earth. That is not what the ground rod was being used for in the original scheme. That would clear up some confusion, because I was thinking you were saying that adding the ground rod might actually give an inferior ground that what I already have. Added to the existing system it improves the connection to earth. Your house could just use the water pipe when it was built (same with all the houses I have lived in). Because water service pipes in some locations were being replaced with plastic the code started requiring an additional electrode for new construction. Rods are the easiest to add. (The code now generally requires adding a "concrete encased electrode" for new construction.) I wish you or RBM could come out and do the job! We're both probably available. Travel & expenses might be a little high. -- bud-- |
#38
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article .com, w_tom wrote:
To perform electrical work, you are required to understand everything in Article 250.52. If using water pipe for earth ground, then any other electrode in Article 250.52(A) paragraphs two through seven also must be installed. Why? Water pipes are no longer sufficient for earthing. If using any other earthing electrode, then a water pipe earthing electrode is not required. False. If metal water pipe is present, it is *required* to use it as a grounding electrode in addition to the other electrodes. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#39
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 26, 10:04 pm, "RBM" rbm2(remove wrote:
Virtually everything you wrote is baseless incoherent gibberish, otherwise you'd be able to produce some NEC documentation to back it up An intelligent reply would have cited what you have problems with. But since you post insults, citing code numbers would not change your mind. Shame on RBM for not even knowing what can and cannot be conductors. Code is specific about what can be conductors. Pipes are no longer permitted. Those who are still living in 1970s would not know that pipes are not acceptable electrical conductors. If spending more time reading, then your responses would be devoid of insults. Profanity identifies one who typically finds reading difficult - who do not know. It explains why RBM knows pipes are acceptable as conductors. Profanity does not change the fact. Water pipes are no longer approved for electrical conductors. RBM should know that if posting recommendations here. Instead he posts profanity - will not even state which parts he has problems with. Note to self. Don't take RBM seriously. His intelligence is defined by his reasoning - insults rather than facts. |
#40
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 27, 11:26 am, wrote:
Correct me if I am wrong, but there was a time when the NEC allowed one to ground equipment to a nearby water pipe. Of course, there was also a time (look at the 1899 code, which is posted online somewhere) when they allowed one to use a gas pipe as a grounding electrode. The time for either of those is not today. ... Besides, if you're going to pull a single conductor into a space, you might as well pull in a cable, as somebody up there pointed out. Using water pipes as conductors is not acceptable. We bond both water pipes and gas pipes (some jurisdictions) for the same reason - to remove electricity from those pipes. A bond to the gas pipe would not be an earth ground since gas meters routinely have electric insulators. Some jurisdictions want the gas pipe bonded to breaker box safety ground; others do not. Consult the gas company for what they want. As w_tom repeatedly notes, the reason for pulling a cable is because that cable is approved as a conductor. Pipe that was acceptable as a condutor more than 30 years ago is no longer approved as a conductor today. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
I want to test C#code ,how Can i study ,? I want to get C# code What site.? | Home Repair | |||
electrical questions GFCIs, grounding, and code | Home Repair | |||
[Fwd: Self-grounding outlets vs. grounding wire] | Home Repair | |||
Self-grounding outlets vs. grounding wire | Home Repair | |||
Doulble Receptacle Grounding Question/ Switch Grounding | Home Repair |