Default Receptacles wired backwards..

I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.

Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT). Also, 120v from the small slot to the cold water pipe.

The two prong showed 101v from the large slot to the radiator pipe,
and 0v from the small slot to the radiator pipe (wrapped a piece of
copper wire around the corroded valve stem).

Now, the large slot is supposed to be neutral and 0 volts to the
ground/waterpipes/etc. and the small slot is suppsed to be hot.

Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?

and 2) what's the best way to run the ground wire? I think it's tacky
to run a 12ga (black insulated) from the green screw on the new outlet
outside the outlet cover, along the baseboard to the radiator. How is
this *supposed* to be done?

THanks, JB

  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Receptacles wired backwards..

You're getting strange readings because you don't have a ground. The proper
way to retrofit a ground conductor is to run it from the metal outlet box or
receptacle to your service panel ground bar, or any other part of the
grounding electrode system, which doesn't include radiators



wrote in message
ups.com...
I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.

Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT). Also, 120v from the small slot to the cold water pipe.

The two prong showed 101v from the large slot to the radiator pipe,
and 0v from the small slot to the radiator pipe (wrapped a piece of
copper wire around the corroded valve stem).

Now, the large slot is supposed to be neutral and 0 volts to the
ground/waterpipes/etc. and the small slot is suppsed to be hot.

Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?

and 2) what's the best way to run the ground wire? I think it's tacky
to run a 12ga (black insulated) from the green screw on the new outlet
outside the outlet cover, along the baseboard to the radiator. How is
this *supposed* to be done?

THanks, JB



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default Receptacles wired backwards..


wrote in message
ups.com...
I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.

Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT).


There is no way you can get these reading legitamately. My guess is that
ground screw is not grounded and the 60v is phantom voltage.

Also, 120v from the small slot to the cold water pipe.

The two prong showed 101v from the large slot to the radiator pipe,
and 0v from the small slot to the radiator pipe (wrapped a piece of
copper wire around the corroded valve stem).

Now, the large slot is supposed to be neutral and 0 volts to the
ground/waterpipes/etc. and the small slot is suppsed to be hot.

Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?

Yes, once you make certain you know what you are doing you should reverse
them.
I just don't have much confidence in what you are finding.

and 2) what's the best way to run the ground wire? I think it's tacky
to run a 12ga (black insulated) from the green screw on the new outlet
outside the outlet cover, along the baseboard to the radiator. How is
this *supposed* to be done?

To meet code you have to run a wire back to the circuit box, going through
all the same holes as the other wires. Even that might not be enough, but I
can't see your wiring.
It is debatable if a wire to the radiator is more or less safe than nothing.


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Receptacles wired backwards..

On 15 Sep, 16:27, "RBM" rbm2(remove wrote:
You're getting strange readings because you don't have a ground. The proper
way to retrofit a ground conductor is to run it from the metal outlet box or
receptacle to your service panel ground bar, or any other part of the
grounding electrode system, which doesn't include radiators

wrote in message

ups.com...



I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.


Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT). Also, 120v from the small slot to the cold water pipe.


The two prong showed 101v from the large slot to the radiator pipe,
and 0v from the small slot to the radiator pipe (wrapped a piece of
copper wire around the corroded valve stem).


Now, the large slot is supposed to be neutral and 0 volts to the
ground/waterpipes/etc. and the small slot is suppsed to be hot.


Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?


and 2) what's the best way to run the ground wire? I think it's tacky
to run a 12ga (black insulated) from the green screw on the new outlet
outside the outlet cover, along the baseboard to the radiator. How is
this *supposed* to be done?


THanks, JB- Hide quoted text -


- Show quoted text -



Two comments that trouble me:

"I'm in an old apartment and I'm rewiring my receptacles"

Are you sure you want to mess with the wires in a dwelling you don't
own? This should be handled by the landlord/management company. You
could be liable for any damage/injury you cause during/after the
rewiring project.

"...run a 12ga (black insulated) from the green screw..."

A ground wire is typically bare or green in residential wiring. Black
might be ground (negative) in a DC circuit, but never in a residential
120VAC circuit.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Receptacles wired backwards..

On Sep 15, 4:50 pm, "Toller" wrote:
wrote in message

ups.com...

I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.


Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT).


There is no way you can get these reading legitamately. My guess is that
ground screw is not grounded and the 60v is phantom voltage.

....

Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?


Yes, once you make certain you know what you are doing you should reverse
them.
I just don't have much confidence in what you are finding.

....

To meet code you have to run a wire back to the circuit box, going through
all the same holes as the other wires. Even that might not be enough, but I
can't see your wiring.
It is debatable if a wire to the radiator is more or less safe than nothing.


Thanks for the detailed reply. Holyheck, that's a lot of lath and
plaster walls to rip out - 2nd floor to the basement. The landlord
downstairs probably won't be interested in having his walls
disturbed. Nothing can be easy can it.. Wonder if anyone else has
suggestions. I'll see if I can get a lightbulb tester over those
voltages..




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Receptacles wired backwards..

On Sep 15, 4:52 pm, DerbyDad03 wrote:
On 15 Sep, 16:27, "RBM" rbm2(remove wrote:





You're getting strange readings because you don't have a ground. The proper
way to retrofit a ground conductor is to run it from the metal outlet box or
receptacle to your service panel ground bar, or any other part of the
grounding electrode system, which doesn't include radiators


wrote in message


oups.com...


I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.


Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT). Also, 120v from the small slot to the cold water pipe.


The two prong showed 101v from the large slot to the radiator pipe,
and 0v from the small slot to the radiator pipe (wrapped a piece of
copper wire around the corroded valve stem).


Now, the large slot is supposed to be neutral and 0 volts to the
ground/waterpipes/etc. and the small slot is suppsed to be hot.


Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?


and 2) what's the best way to run the ground wire? I think it's tacky
to run a 12ga (black insulated) from the green screw on the new outlet
outside the outlet cover, along the baseboard to the radiator. How is
this *supposed* to be done?


THanks, JB- Hide quoted text -


- Show quoted text -


Two comments that trouble me:

"I'm in an old apartment and I'm rewiring my receptacles"

Are you sure you want to mess with the wires in a dwelling you don't
own? This should be handled by the landlord/management company. You
could be liable for any damage/injury you cause during/after the
rewiring project.

Point taken, the landlord is a friend of mine and I'm just looking
into it for now.. looks like more than I want to do.


"...run a 12ga (black insulated) from the green screw..."

A ground wire is typically bare or green in residential wiring. Black
might be ground (negative) in a DC circuit, but never in a residential
120VAC circuit.- Hide quoted text -

- Show quoted text -


Yeh, I was pretty sure I didn't want to use black except that's what I
have laying around. Looks like it's not such a good idea anyways.
Seems like everyone says 'eh, just ground it to the cold water
pipe'..


Thanks.

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18
Default Receptacles wired backwards..


wrote in message
ups.com...
I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.

Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT). Also, 120v from the small slot to the cold water pipe.


man O man are system F----- up good luck you needed


The two prong showed 101v from the large slot to the radiator pipe,
and 0v from the small slot to the radiator pipe (wrapped a piece of
copper wire around the corroded valve stem).

Now, the large slot is supposed to be neutral and 0 volts to the
ground/waterpipes/etc. and the small slot is suppsed to be hot.

Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?

and 2) what's the best way to run the ground wire? I think it's tacky
to run a 12ga (black insulated) from the green screw on the new outlet
outside the outlet cover, along the baseboard to the radiator. How is
this *supposed* to be done?

THanks, JB



  #8   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Receptacles wired backwards..

What code requires you to run the conductor through the same holes?



"Toller" wrote in message
...

wrote in message
ups.com...
I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.

Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT).


There is no way you can get these reading legitamately. My guess is that
ground screw is not grounded and the 60v is phantom voltage.

Also, 120v from the small slot to the cold water pipe.

The two prong showed 101v from the large slot to the radiator pipe,
and 0v from the small slot to the radiator pipe (wrapped a piece of
copper wire around the corroded valve stem).

Now, the large slot is supposed to be neutral and 0 volts to the
ground/waterpipes/etc. and the small slot is suppsed to be hot.

Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?

Yes, once you make certain you know what you are doing you should reverse
them.
I just don't have much confidence in what you are finding.

and 2) what's the best way to run the ground wire? I think it's tacky
to run a 12ga (black insulated) from the green screw on the new outlet
outside the outlet cover, along the baseboard to the radiator. How is
this *supposed* to be done?

To meet code you have to run a wire back to the circuit box, going through
all the same holes as the other wires. Even that might not be enough, but
I can't see your wiring.
It is debatable if a wire to the radiator is more or less safe than
nothing.



  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 201
Default Receptacles wired backwards..

Meth,

Thanks for the detailed reply. Holyheck, that's a lot of lath and
plaster walls to rip out - 2nd floor to the basement. The landlord
downstairs probably won't be interested in having his walls
disturbed. Nothing can be easy can it.. Wonder if anyone else has
suggestions. I'll see if I can get a lightbulb tester over those
voltages..



Sorry but it really sounds as if you are in over your head. An
electrician could "fish" a ground wire from the junction box without doing
too much damage to the walls. You don't seem to know what a ground is and
are not getting good readings from a voltmeter.
The landlord would be crazy to allow you to work on his house.

Dave M.


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Receptacles wired backwards..

On Sep 15, 7:19 pm, "David Martel" wrote:
Meth,

Thanks for the detailed reply. Holyheck, that's a lot of lath and
plaster walls to rip out - 2nd floor to the basement. The landlord
downstairs probably won't be interested in having his walls
disturbed. Nothing can be easy can it.. Wonder if anyone else has
suggestions. I'll see if I can get a lightbulb tester over those
voltages..


Sorry but it really sounds as if you are in over your head. An
electrician could "fish" a ground wire from the junction box without doing
too much damage to the walls. You don't seem to know what a ground is and
are not getting good readings from a voltmeter.
The landlord would be crazy to allow you to work on his house.

Dave M.


Perhaps take some lessons in tact from derbydad03; he essentially said
the same thing that you did without the assumptions and inflamatory
verbage. Also, read the part where I said "looks like it's not such a
good idea anyways" and then stroke your ego with your insincere
'sorry' somewhere else. If at least your insults, however true, were
value added with a scrap of useful information, then by all means,
honesty is great. For example: "You don't seem to know what a ground
is. It's (short description of *your* definition)" Yes I know, it's
not your job and you're not being paid to instruct or teach... Nope,
you're just here to berate ppl and make yourself feel important.
Futher, "not getting good readings from a voltmeter" is completely
baseless. Those are the readings period. It could be phantom, it
could be real - but voltage is voltage, - you know, as long as we're
being pedants. Perhaps you meant "You're not coming to the right
conclusions with the voltmeter alone." Probably true... funny, I
mentioned that I planned to use a lightbulb tester on it too.. Perhaps
you missed that in your zeal to shoot at an easy target.



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Receptacles wired backwards..

In article .com, wrote:
On Sep 15, 7:19 pm, "David Martel" wrote:
Meth,

Thanks for the detailed reply. Holyheck, that's a lot of lath and
plaster walls to rip out - 2nd floor to the basement. The landlord
downstairs probably won't be interested in having his walls
disturbed. Nothing can be easy can it.. Wonder if anyone else has
suggestions. I'll see if I can get a lightbulb tester over those
voltages..


Sorry but it really sounds as if you are in over your head. An
electrician could "fish" a ground wire from the junction box without doing
too much damage to the walls. You don't seem to know what a ground is and
are not getting good readings from a voltmeter.
The landlord would be crazy to allow you to work on his house.

Dave M.


Perhaps take some lessons in tact from derbydad03; he essentially said
the same thing that you did without the assumptions and inflamatory
verbage. Also, read the part where I said "looks like it's not such a
good idea anyways" and then stroke your ego with your insincere
'sorry' somewhere else. If at least your insults, however true, were
value added with a scrap of useful information, then by all means,
honesty is great. For example: "You don't seem to know what a ground
is. It's (short description of *your* definition)" Yes I know, it's
not your job and you're not being paid to instruct or teach... Nope,
you're just here to berate ppl and make yourself feel important.


Sure, he could have phrased it a bit nicer... but you *are* in over your head.

Among other things, it's completely unnecessary to "rip out a lot of lath and
plaster" to run wires from one floor to another; a couple of small holes is
enough for someone who knows what he's doing -- hell, that's enough for
someone who *doesn't* know what he's doing, but is able to combine knowledge
of building construction with a little imagination.

Futher, "not getting good readings from a voltmeter" is completely
baseless. Those are the readings period. It could be phantom, it
could be real - but voltage is voltage, - you know, as long as we're
being pedants.


If you don't understand why this is the second indication that you're in over
your head... that's the third indication.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 38
Default Receptacles wired backwards..

Point taken, the landlord is a friend of mine and I'm just looking
into it for now.. looks like more than I want to do.


I gotta go with the original poster. Keep the landlord as a friend and let
an outside professional do it. That way, if ANYTHING happens, it can't
possibly be traced back to you, no matter what.

As a f'rinstance: as a ham radio operator, I've read old ham radio books
from the '60s and '70s when ham radios were often sources of television
interference. This wasn't because the ham rigs were operating outside of
their bands, it was because TV sets back then didn' t have adequate
filtering to prevent ham signals from getting in. If a neighbor sees your
antennas and complains, he doesn't want to hear "You've gotta buy a filter
for your antenna." As a sign of goodwill, you can give him a cheap antenna
filter, but here's the kicker -- and what the books scream in
"sky-is-falling" type: Don't touch the neighbor's TV set. Let him install
the filter; don't install it for him. If you so much as look hard at his
set, he's got you nailed for all time. "It worked all right until you
fooled with it!" And he'll expect free TV repair out of you forever.

So let's assume that this old electrical wiring in this old apartment soon
causes a fire. If you ever touched a screwdriver to any of it, guess what.

CYA,

Matt J. McCullar
Arlington, TX



  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 78
Default Receptacles wired backwards..

LMFAO!

Idiot!

wrote:
I'm in an old apartment and I'm rewiring my receptacles because they


  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 161
Default Receptacles wired backwards..

On Sat, 15 Sep 2007 20:14:45 +0000, methochias wrote:

I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.

Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT). Also, 120v from the small slot to the cold water pipe.

The two prong showed 101v from the large slot to the radiator pipe,
and 0v from the small slot to the radiator pipe (wrapped a piece of
copper wire around the corroded valve stem).

Now, the large slot is supposed to be neutral and 0 volts to the
ground/waterpipes/etc. and the small slot is suppsed to be hot.

Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?

and 2) what's the best way to run the ground wire? I think it's tacky
to run a 12ga (black insulated) from the green screw on the new outlet
outside the outlet cover, along the baseboard to the radiator. How is
this *supposed* to be done?

THanks, JB



As I read your post, I think the best recommendation to give you would be
to hire an electrician so the work gets done correctly.

Electricity is nothing to play with, especially if you are in doubt.

Besides personal safety, there's also the issue of fire.

This may be one time when hiring the right person is the best (and
cheapest) thing you could do.

Hope this helps.
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 161
Default Receptacles wired backwards..

On Sat, 15 Sep 2007 21:08:55 +0000, methochias wrote:

On Sep 15, 4:50 pm, "Toller" wrote:
wrote in message

ups.com...

I'm in an old apartment and I'm rewiring my receptacles because they
have no ground. I have some odd situations.


Most are two prong receptacles, but some are 3 prong. I tested the
voltage on them. The 3 prong I tested showed about 60v from ground
screw to the small slot-HOT and60v from the ground screw to the large
slot(NEUT).


There is no way you can get these reading legitamately. My guess is that
ground screw is not grounded and the 60v is phantom voltage.

...

Question is 1) Would it hurt to rewire the recepticles to large-
neutral, small-hot. I'm imagining a situation where one day I plug
something in with the ground and hot shorted... What should I check
and look out for?


Yes, once you make certain you know what you are doing you should reverse
them.
I just don't have much confidence in what you are finding.

...

To meet code you have to run a wire back to the circuit box, going through
all the same holes as the other wires. Even that might not be enough, but I
can't see your wiring.
It is debatable if a wire to the radiator is more or less safe than nothing.


Thanks for the detailed reply. Holyheck, that's a lot of lath and
plaster walls to rip out - 2nd floor to the basement. The landlord
downstairs probably won't be interested in having his walls
disturbed. Nothing can be easy can it.. Wonder if anyone else has
suggestions. I'll see if I can get a lightbulb tester over those
voltages..




Your comment here about the landlord is a red flag.

Let your landlord take care of the electrical problem, not you. If he
does not and you think there is a safety issue, take this up with the
building inspector.

The last thing you need to do is mess with a landlord's property. Even if
he/she were to give an OK, you certainly don't want to be in a position
where the responsibility could come back to haunt you.

If this were your own building, then that's another scenario. For now,
it's the landlord's problem to resolve.

By the way, if you don't have his OK and something goes wrong, you may
find yourself in hot water.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fan motor runs backwards Bobo Home Repair 23 July 18th 07 10:20 PM
putting on insulation backwards Eigenvector Home Repair 7 February 25th 07 10:03 AM
Sharpening a roundnose scraper backwards Walter H. Klaus Woodturning 10 May 6th 06 08:31 AM
Dremel runs backwards! Henry Home Repair 6 October 1st 05 08:21 PM
BSI - backwards and a total rippoff Mr Fizzion UK diy 21 August 12th 05 12:33 AM


All times are GMT +1. The time now is 08:10 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"