All

I recently installed an on-demand hot water heater and use it for both
domestic and space heating. Details are in the document at
www.consol.ca/downloads/Dual_heating_system.pdf

I would appreciate your comments on this article.
Please send your comments via email as I do not subscribe to this
newsgroup.

Thanks!
Roy Jensen

  #2   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default On-demand hot water heater for domestic and space heating...

On Mon, 18 Jun 2007 23:14:19 -0700, wrote:

All

I recently installed an on-demand hot water heater and use it for both
domestic and space heating. Details are in the document at
www.consol.ca/downloads/Dual_heating_system.pdf

I would appreciate your comments on this article.


For what purpose?

Please send your comments via email as I do not subscribe to this
newsgroup.

Thanks!


Don't thank us too soon. It's hard enough to get people to read a pdf
file, and then all you want are comments? Don't you have any
questions? What are you trying to do and what problems do you need to
solve in order to do it?

And then you want people to email you. No one will do that but me,
but I don't like pdf's and I'm not going to read it.

Subscribing to a newsgroup is not as difficult as hanging from a rope
and rescuing a woman from an active volcano. If Indiana Jones can do
that, you can subscribe to a newsgroup.

P&M

Roy Jensen


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default On-demand hot water heater for domestic and space heating...

I wonder why a guy installs a heating system, writes a whole goddamm
analysis about it, and then crows about not being remunerated.
Sheeit, iffin I'm gonna write a whole big shpiel about sumpn, I'd wanna be
remunerated....

Inyway, after all his analysis/crowing, his own table shows efficiencies no
greater than many other systems.
His claim of 100% efficiency in the text is 1. impossible and 2.
inconsistent with his own table, of 84-96%.
Personally, I don't think any gas-fired system can come anywhere near 90%,
but I could be wrong.

In addition, the btu/hr of 200,000 is fairly whopping. My near-5,000 sq ft
hovel is heated by a 70,000 btu gas forced-air system, and cooled by a 5 ton
(60,000 btu) system. Sep. Sears HWT, gas fired.
I wonder how efficient how such a 200K system can be so efficient, esp. when
the very premise of "on-demand" requires fairly high "instantaneous" energy
input.

I gather that what is nice about this On-demand stuff is that you never have
to worry about running out of HW, which, if you got a showering SIL like I
got, can come in handy. I'm thinking of making her shower coin-operated.


Anyway, not saying on-demand is not efficient or a good idea, just wonder...

If I had my druthers, I'd get rid of forced air, and do a nice hot
water/chilled water heating/A/C system, like what you see in some high-rise
condos. Quiet, easily zoned, no big-assed noisy fan motors/duct work, etc.
You then have various choices of how to heat/chill the water for the system.

Anyway, semi-inneresting read, if a little dense and hard to follow.

Mr. Jensen is obviously perty pleased with hisself.
If he deigns to come back here, he should post to alt.hvac. Hope he's got
thick skin.
--
------
Mr. P.V.'d (formerly Droll Troll), Yonkers, NY

Stop Corruption in Congress & Send the Ultimate Message:
Absolutely Vote, but NOT for a Democrat or a Republican.
Ending Corruption in Congress is the *Single Best Way*
to Materially Improve Your Family's Life.
The Solution is so simple--and inexpensive!

entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie,
all d'numbuhs

wrote in message
oups.com...
All

I recently installed an on-demand hot water heater and use it for both
domestic and space heating. Details are in the document at
www.consol.ca/downloads/Dual_heating_system.pdf

I would appreciate your comments on this article.
Please send your comments via email as I do not subscribe to this
newsgroup.

Thanks!
Roy Jensen



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8,803
Default On-demand hot water heater for domestic and space heating...


wrote in message
oups.com...
All

I recently installed an on-demand hot water heater and use it for
both
domestic and space heating. Details are in the document at
www.consol.ca/downloads/Dual_heating_system.pdf

I would appreciate your comments on this article.
Please send your comments via email as I do not subscribe to this
newsgroup.


I would wonder about the life expectation of a heater spec'ed for
occasional use being used where it will operated a significant
percentage of the time. I'm sure it won't last as long as spec'ed.

Are these unit really up to 96% efficient? When heating already warm
water?

Newsgroups are for questions and answers. Not wanting to subscribe is
insufficient reason to expect e-mail response.

Bob


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default On-demand hot water heater for domestic and space heating...

Yeah, I have thick skin. To answer your questions:

...then crows about not being remunerated.

Because I want to emphasize that it is not a biased evaluation.

His claim of 100% efficiency in the text is 1. impossible and 2.
inconsistent with his own table, of 84-96%.

The fan-coil is not listed in Table 1. The fan-coil IS 100 % efficient
because there is no heat loss. Any residual heat is simply heats the
room with the fan-coil.

Personally, I don't think any gas-fired system can come anywhere near 90%,
but I could be wrong.

Yep, you're wrong.


In addition, the btu/hr of 200,000 is fairly whopping. My near-5,000 sq ft
hovel is heated by a 70,000 btu gas forced-air system, and cooled by a 5 ton
(60,000 btu) system. Sep. Sears HWT, gas fired.

WOW, an EXECELLENT observation. Which, btw, is what got me thinking
about using the on-demand unit to heat the house.


I wonder how efficient how such a 200K system can be so efficient, esp. when
the very premise of "on-demand" requires fairly high "instantaneous" energy
input.

Up to 96 % efficient, according to the manufacturers.

Anyway, semi-inneresting read, if a little dense and hard to follow.

Thanks. Where is it hard to follow?

Mr.Jensen is obviously perty pleased with hisself.


Not particularly. Thought others might like the idea.
And btw, it is DR. JENSEN. (PhD in physical chemistry, that I am
pleased about!)


If he deigns to come back here, he should post to alt.hvac. Hope he's got
thick skin.



Roy Jensen



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8,803
Default On-demand hot water heater for domestic and space heating...


wrote in message
ups.com...
Yeah, I have thick skin. To answer your questions:

...then crows about not being remunerated.

Because I want to emphasize that it is not a biased evaluation.

His claim of 100% efficiency in the text is 1. impossible and 2.
inconsistent with his own table, of 84-96%.

The fan-coil is not listed in Table 1. The fan-coil IS 100 %
efficient
because there is no heat loss. Any residual heat is simply heats the
room with the fan-coil.


But as the water temp of the returning water increases, the efficiency
of the water heater decreases. More heat goes out the stack because
the differential is less.


Bob


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default On-demand hot water heater for domestic and space heating...

Well.....

As a phys chemist, you know about Carnot efficiency, reversible processes,
and alladat, and from virtually all thermodynamic considerations, the less
quasi-static a process is, *necessarily* the less efficient it must be.

Now, you can do thermodynamic damage control, of course, but all other
things being equal, you have *hurt your efficiency* merely by dint of the
higher instantaneous energy input req'd for on-demand!
Probably equal to the insulation losses of stored hot water.

Now, Carnot does not really apply here, as this is simple heat transfer and
not a heat engine, but the same principles of quasi-staticness apply, in the
form of transfer time.
Thus, it is possible, in a simple heat transfer process, to get 100% heat
transfer.
But that requires a flue gas whose temperature is *ambient*.

How does one do that?
Well, with *small* flames, low combustion gas velocity, long-assed transfer
times, etc. *All inconsistent with On-demand.*

And, with one *long-assed chiminey*, jack (and yes, chiminey *is* a
3-syllable word), and one *long-assed* coil of copper tubing around sed
long-assed chiminey, for heat reclamation.
Which then creates draft problems, S02 problems (depending on the fuel), and
just overall complexity.

However, for on-demand situations, ELECTRIC energy would in fact be
near-100%, as there are no flue losses.
You just have to factor in the generally higher cost of electricity.
The only thermodynamic consideration for electric on-demand might be the
additional IR drop from high current surges.
And likely shorter filament life, etc.

Note that your system here is sort of the *inverse* of the more traditional
system where a hot-water tank (or coils), are driven by a hot-water or steam
boiler.
Here, your "furnace" is driven by the hot water heater.
Which means you might have a considerably larger water mass in your HW
heater than necessary for HW itself--didn't check the details.

Imo, if you are going to pump HW to a heat-transfer coil, those coils might
as well be baseboard units in a room!
Forced air is a pita, AND the losses from those big-assed blower fans are
*considerable*. Noisy, too.
Mine is 10 effing amps, running all the goddamm time. Convert DAT to btus,
bro, and calc THOSE losses!!

Yes, you can argue that that energy becomes a part of the heat sent to the
house, but it is "low-quality" heat, in the literal entropic sense, but
moreso in the "sensible" sense, where you need heat beyond a certain
temperature to create a comfort range--esp. in a low-mass/low specific
medium such as effing air.
So the current draw of a blow is not a total loss, just not the best use of
the intended energy. imo.

Virtually the same itty bitty circulating pump feeding the fan coil in your
system could feed the whole house!
Wonderfully quiet, efficient, elegant.
Indeed, you got more initial plumbing, but the overall efficiency, from
zoning as well, proly more than makes up for it.

And, you seem willing to take the manufacturers' word on their numbers.
Manufacturers are lying sacks of ****. This is like thermodynamic law.
Just look at mfr's EPA claims for mpg's, and Consumer Reports' numbers.
20-30% difference, across the board.

You in particular could probably well envision the experimental setups
required to test all the explicit/implicit assertions in this system. Do
you really think these effing mfr's go thru the trouble?
Of course they don't. They fukn wing it, at your/our expense.
It's called marketing.
Marketing don't give a flying **** about facts or experiments.

Not saying this system is not worthwhile, but I think it overlooks more
important HVAC/thermodynamic fundamentals than simple insulation losses of a
HW tanks.
It's selling point, is, I think, that it is a little different.
With the nice feature that theoretically you can never run out of HW.

But, sheeeit, Jethro, take shorter showers!

Baseboard hot water heating can also double as chilled water-A/C, with a
drain system built in to collect all the condensate and perhaps recycle
that. A 5-ton A/C can easily produce 50 gallons/day of near-pure
condensate, on a humid day.
Large housing complexes indeed use this system.
Super quiet, efficient, infinitely zonable.

Previous snippy comments aside, actually a very good and interesting post,
altho a little hard to follow, as, first of all, you mixed too entirely
different concepts, that of On Demand, and that of using the HW supply as
the domestic heat source.
Second, imo, I think with anything related to thermo/HVAC, you need to more
clearly state the various premises, how they differ from tradition, and move
along in more bite-sized conceptual increments.

DR. Violated.
--
------
Mr. P.V.'d (formerly Droll Troll), Yonkers, NY

Stop Corruption in Congress & Send the Ultimate Message:
Absolutely Vote, but NOT for a Democrat or a Republican.
Ending Corruption in Congress is the *Single Best Way*
to Materially Improve Your Family's Life.
The Solution is so simple--and inexpensive!

entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie,
all d'numbuhs

wrote in message
ups.com...
Yeah, I have thick skin. To answer your questions:

...then crows about not being remunerated.

Because I want to emphasize that it is not a biased evaluation.

His claim of 100% efficiency in the text is 1. impossible and 2.
inconsistent with his own table, of 84-96%.

The fan-coil is not listed in Table 1. The fan-coil IS 100 % efficient
because there is no heat loss. Any residual heat is simply heats the
room with the fan-coil.

Personally, I don't think any gas-fired system can come anywhere near
90%,
but I could be wrong.

Yep, you're wrong.


In addition, the btu/hr of 200,000 is fairly whopping. My near-5,000 sq
ft
hovel is heated by a 70,000 btu gas forced-air system, and cooled by a 5
ton
(60,000 btu) system. Sep. Sears HWT, gas fired.

WOW, an EXECELLENT observation. Which, btw, is what got me thinking
about using the on-demand unit to heat the house.


I wonder how efficient how such a 200K system can be so efficient, esp.
when
the very premise of "on-demand" requires fairly high "instantaneous"
energy
input.

Up to 96 % efficient, according to the manufacturers.

Anyway, semi-inneresting read, if a little dense and hard to follow.

Thanks. Where is it hard to follow?

Mr.Jensen is obviously perty pleased with hisself.


Not particularly. Thought others might like the idea.
And btw, it is DR. JENSEN. (PhD in physical chemistry, that I am
pleased about!)


If he deigns to come back here, he should post to alt.hvac. Hope he's
got
thick skin.



Roy Jensen



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default On-demand hot water heater for domestic and space heating...

wrote in message
ups.com...
***Responding to things that I believe warrant a response.***


Now, you can do thermodynamic damage control, of course, but all other
things being equal, you have *hurt your efficiency* merely by dint of the
higher instantaneous energy input req'd for on-demand!
Probably equal to the insulation losses of stored hot water.


As long as the combustion mixture is ideal, it doesn't matter what the
flame size is.


From a chemical reaction/combustion pov, correct.
From a *heat transfer* pov, absolutely incorrect. Flame size is directly
proportional to gas velocity, which is inversely proportional to transfer
time, and therefore inversely proportional to heat transfer per unit fuel.
Thus, a system capable of pumping out 200,000 btu, to keep the same heat
transfer efficiency, would have to be substantially larger in dimension than
my 70,000 btu system, to accommodate 3x the combustion rate.

Thermodynamically, on-demand is *necessarily* less efficient than
quasi-static (small flame) systems.
Unless the system is made really large.
Then, you are back to square one, cuz you now have so much volume of boiler
HW, that you wind up with the same insulation losses you were trying to cure
in yer HW heater!!


As you comment below, this is nothing more than a fancy heat
exchanger. Good engineering (can't believe I just said that) using a
counterflow heat-exchanger does a good job of extracting energy into
the water.


Well, with *small* flames, low combustion gas velocity, long-assed
transfer
times, etc. *All inconsistent with On-demand.*

And, with one *long-assed chiminey*, jack (and yes, chiminey *is* a
3-syllable word), and one *long-assed* coil of copper tubing around sed
long-assed chiminey, for heat reclamation.


Whoa! think about this Heat rises, copper coils surrounding a vertical
chimney do diddly!
The chimney is warm with continuous use. Horizontal mounting allows
some of that heat to warm the chimney and escape into the room.

The only device I claim to be 100 % efficient is the fan coil.


Yeah, but this is a trivial 100%, one step removed from where the relevant
heat transfer problems exist, that is, between the combustion gas/water
interface. You still have that inefficiency (shared with all heating
plants), and then put the coil in hot water--really no different than steam
boilers with an immersed HW coil--which in fact is an "on demand" system,
around for ages, in virtually all apartment buildings.



Imo, if you are going to pump HW to a heat-transfer coil, those coils
might
as well be baseboard units in a room!
Forced air is a pita, AND the losses from those big-assed blower fans are
*considerable*.
Virtually the same itty bitty circulating pump feeding the fan coil in
your
system could feed the whole house!


The article was to emphasize a system that could easily integrate into
what most homes have: forced air.


But with questionable benefits. See above. The coil is just one step
removed from the same heat transfer vicissitudes of all gas/oil fired
systems.

I whole-heartedly agree that the same pump could be used for infloor
heating, which is mentioned in the article.


And, you seem willing to take the manufacturers' word on their numbers.
Manufacturers are lying sacks of ****. This is like thermodynamic law.
Just look at mfr's EPA claims for mpg's, and Consumer Reports' numbers.
20-30% difference, across the board.


All manufacturers lie. But that lie has to be based on something --
ideal conditions, most likely.
Consider that some lie and quote 95 % efficiency but others can only
quote 80 % efficiency for their systems. If they all exagerate by 20
%, the ODHW is still on top.
Price doesn't change; the ODHW is still half the price.


I don't see why it would be that much cheaper.
I got my sears 50 gal HW gas heater for $180.
On sale, of course.


You in particular could probably well envision the experimental setups
required to test all the explicit/implicit assertions in this system.


As I write this sentence, I have developed a procedure to test the
efficiency with a few thermometers and flow meters. It even includes
several redundancy factors and checks. Now, who has money to fund it?


Not that hard. I did it, way back when.
Not with air, tho, but the same principle.
E = m c delta T


But, sheeeit, Jethro, take shorter showers!


You don't have teen-agers, do you?


Well, not post-pubescent boys, who spend 20-30 minutes masturbating, on my
HW dime. Thank gawd....
Must cost a fortune....



A 5-ton A/C can easily produce 50 gallons/day of near-pure
condensate, on a humid day.


It picks up what is in the air, in a mechanical room being blown over
the coils. Wouldn't call that near-pure.
And near-pure water is GREAT for bacterial growth. Just ask any
chemistry lab with a deionizer.


Well, purer than lake/well water, fergodsake.



Previous snippy comments aside, actually a very good and interesting
post,
altho a little hard to follow, as, first of all, you mixed too entirely
different concepts, that of OnDemand, and that of using the HW supply as
the domestic heat source.
Second, imo, I think with anything related to thermo/HVAC, you need to
more
clearly state the various premises, how they differ from tradition, and
move
along in more bite-sized conceptual increments.


THANKS! This is exactly what I was looking for. Will post an updated
version shortly.


Looking forward to it. Suggest crossposting to alt.hvac.
Some smart experienced guys over there, but none too flush with manners.
But I'm sure this would generate an, uh, energetic thread.
--
------
Mr. P.V.'d (formerly Droll Troll), Yonkers, NY

Stop Corruption in Congress & Send the Ultimate Message:
Absolutely Vote, but NOT for a Democrat or a Republican.
Ending Corruption in Congress is the *Single Best Way*
to Materially Improve Your Family's Life.
The Solution is so simple--and inexpensive!

entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie,
all d'numbuhs




Roy Jensen



  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default On-demand hot water heater for domestic and space heating...

Looking forward to it. Suggest crossposting to alt.hvac.
Some smart experienced guys over there, but none too flush with manners.
But I'm sure this would generate an, uh, energetic thread.


Did that last week. Absolutely ZERO responses.

Roy Jensen

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default On-demand hot water heater for domestic and space heating...

I am absolutely shocked and amazed--it usually takes very little for those
guys to lite into someone's ass, whether or not they understand the
proposition(s). Just for the helluvit.

I'm impressed!

Was it just what you posted here, or a revision?

Could also be that it's A/C season, the ones that wouuld respond are really
busy.
Here in the metro NYC area, it can be very very difficult to get *anyone* to
come over (the whole Yellow Pages list!) during peak season.
--
------
Mr. P.V.'d (formerly Droll Troll), Yonkers, NY

Stop Corruption in Congress & Send the Ultimate Message:
Absolutely Vote, but NOT for a Democrat or a Republican.
Ending Corruption in Congress is the *Single Best Way*
to Materially Improve Your Family's Life.
The Solution is so simple--and inexpensive!

entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie,
all d'numbuhs

wrote in message
oups.com...
Looking forward to it. Suggest crossposting to alt.hvac.
Some smart experienced guys over there, but none too flush with manners.
But I'm sure this would generate an, uh, energetic thread.


Did that last week. Absolutely ZERO responses.

Roy Jensen



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Demand (Tankless) Water Heater with Thermostatic Shower Control [email protected] Home Repair 16 March 21st 07 09:47 PM
On-demand water heater [email protected] Home Repair 12 February 1st 07 03:54 PM
Noritz N-069M-OD question (on demand water heater) Dan_Musicant Home Repair 2 June 10th 06 02:55 AM
Help with On Demand Water Heaters and Minisplit heater-coolers pjbphd Home Ownership 0 April 3rd 06 01:38 AM
on demand electric water heater gcroix Home Repair 3 February 2nd 05 02:44 PM


All times are GMT +1. The time now is 10:32 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"