GFI question
I have a dedicated 20 amp line for my pool. I have a GFI outlet by the deck
for the filter. I want to install a single pole switch in the house to turn the filter on and off from inside. If I install a switch, will the GFI trip everytime you turn the power off to the GFI? |
#2
Posted to alt.home.repair
|
|||
|
|||
GFI question
On Wed, 09 May 2007 01:49:56 GMT, "gntry" wrote:
I have a dedicated 20 amp line for my pool. I have a GFI outlet by the deck for the filter. I want to install a single pole switch in the house to turn the filter on and off from inside. If I install a switch, will the GFI trip everytime you turn the power off to the GFI? Why should switching power to a GFI trip it? A GFI works on difference on current flowing in 2 parts of the circuit. Both are being started and stopped at exactly the same time. My holiday light setup involved a GFI that was switched like that, I used if for about 40 days, and had not one trip that occurred when it was being switched. -- Mark Lloyd http://notstupid.laughingsquid.com "DISCLAIMER If you find a posting or message from me offensive, inappropriate, or disruptive, please ignore it. If you don't know how to ignore a posting, complain to me and I will demonstrate." |
#3
Posted to alt.home.repair
|
|||
|
|||
GFI question
Why should switching power to a GFI trip it? A GFI works on difference on current flowing in 2 parts of the circuit. Both are being started and stopped at exactly the same time. My holiday light setup involved a GFI that was switched like that, I used if for about 40 days, and had not one trip that occurred when it was being switched. Quite correct. BUT a un-powered GFCI can permit some safe hazards to continue. It is better to have the GFCI always powered and have the switch AFTER the GFCI. A powered GFCI will detect and "trip" a "fault" between neutral and ground. A GFCI will NOT detect incorrect wiring whereby neutral and HOT are switched. But a powered up GFCI will still trip when either of the two load wires have a 5ma path to ground. A further advantage of putting the GFCI before the switch is that it will be indoors and less subject to contamination from aerosols. Regardless, it's a GOOD idea to TEST the devices. They DO fail and outside units fail more often. And they don't necessarily fail "safe." |
#4
Posted to alt.home.repair
|
|||
|
|||
GFI question
Mark Lloyd wrote:
Why should switching power to a GFI trip it? A GFI works on difference on current flowing in 2 parts of the circuit. Both are being started and stopped at exactly the same time. I have two plug in GFI devices and they sometimes trip after a power outage. A friend of my had some GFI outlets in his garage do the same thing. I have NO idea why it happens but it does happen. -- I don't understand why they make gourmet cat foods. I have known many cats in my life and none of them were gourmets. They were all gourmands! |
#5
Posted to alt.home.repair
|
|||
|
|||
GFI question
gntry wrote:
I have a dedicated 20 amp line for my pool. I have a GFI outlet by the deck for the filter. I want to install a single pole switch in the house to turn the filter on and off from inside. If I install a switch, will the GFI trip everytime you turn the power off to the GFI? Not in my experience. I have a couple in the shop, one on the air compressor, plugged into the GFCI and then to the switch. Turning off the switch lets the GFI drop out. NBD since it's right next to the compressor, but it's not really "right". It should be the other way around; GFCI, then switch, then compressor. Same for the one on my workbench, though it's seldom without power unless I trip a breaker to work on something. I've heard others say no, they don't drop out before, but I haven't yet found one myself that didn't, nor anyone whose story about same seemed believable. From what I've seen of GFI designs on the 'net, they operate on a "latch" system and that "latch" drops when the ac goes away. You always have to press the button to let power thru a GFI when they're new also, according to those, so that seems to support my own experience. It might have been wikipedia; not sure. HTH Pop` |
#6
Posted to alt.home.repair
|
|||
|
|||
GFI question
I've heard others say no, they don't drop out before, but I haven't yet found one myself that didn't, nor anyone whose story about same seemed believable. From what I've seen of GFI designs on the 'net, they operate on a "latch" system and that "latch" drops when the ac goes away. I would like to see a URL to that design. The designs I have seen "on the net" and my own experience are that the GFCI contacts stay closed when the input power goes away. You always have to press the button to let power thru a GFI when they're new also, according to those, so that seems to support my own experience. It might have been wikipedia; not sure. It definitely would be a good idea to "ship" with the device already tripped. They will not reset without power being present. If it is wired backwards (load and line switched) and pre-tripped, it will never pass current (which is good.) |
#7
Posted to alt.home.repair
|
|||
|
|||
GFI question
John Gilmer wrote:
I've heard others say no, they don't drop out before, but I haven't yet found one myself that didn't, nor anyone whose story about same seemed believable. From what I've seen of GFI designs on the 'net, they operate on a "latch" system and that "latch" drops when the ac goes away. I would like to see a URL to that design. Well, you'll have to stop by here or go to one of our local places. They have the UL/CSA/EC MRUs and all that crap on them, along with the standard safety specs. Interesting ... Pop` The designs I have seen "on the net" and my own experience are that the GFCI contacts stay closed when the input power goes away. You always have to press the button to let power thru a GFI when they're new also, according to those, so that seems to support my own experience. It might have been wikipedia; not sure. It definitely would be a good idea to "ship" with the device already tripped. They will not reset without power being present. If it is wired backwards (load and line switched) and pre-tripped, it will never pass current (which is good.) |
#8
Posted to alt.home.repair
|
|||
|
|||
GFI question
John Gilmer wrote:
I've heard others say no, they don't drop out before, but I haven't yet found one myself that didn't, nor anyone whose story about same seemed believable. From what I've seen of GFI designs on the 'net, they operate on a "latch" system and that "latch" drops when the ac goes away. I would like to see a URL to that design. Oops, misread that. Try these: http://www.osha.gov/SLTC/smallbusiness/sec14.html Lots of other, better links too if you bother to try. Pop` The designs I have seen "on the net" and my own experience are that the GFCI contacts stay closed when the input power goes away. You always have to press the button to let power thru a GFI when they're new also, according to those, so that seems to support my own experience. It might have been wikipedia; not sure. It definitely would be a good idea to "ship" with the device already tripped. They will not reset without power being present. If it is wired backwards (load and line switched) and pre-tripped, it will never pass current (which is good.) |
#9
Posted to alt.home.repair
|
|||
|
|||
GFI question
On Wed, 9 May 2007 09:19:05 -0300, "John Gilmer"
wrote: Why should switching power to a GFI trip it? A GFI works on difference on current flowing in 2 parts of the circuit. Both are being started and stopped at exactly the same time. My holiday light setup involved a GFI that was switched like that, I used if for about 40 days, and had not one trip that occurred when it was being switched. Quite correct. BUT a un-powered GFCI can permit some safe hazards to continue. It is better to have the GFCI always powered and have the switch AFTER the GFCI. A powered GFCI will detect and "trip" a "fault" between neutral and ground. A GFCI will NOT detect incorrect wiring whereby neutral and HOT are switched. But a powered up GFCI will still trip when either of the two load wires have a 5ma path to ground. I wired them that way, so the GFCI would also be a switched receptacle. The other way (switch after GFCI) would require adding a second receptacle. A further advantage of putting the GFCI before the switch is that it will be indoors and less subject to contamination from aerosols. Regardless, it's a GOOD idea to TEST the devices. They DO fail and outside units fail more often. And they don't necessarily fail "safe." Why assume it's outside? My switch and GFCI were both inside. -- Mark Lloyd http://notstupid.laughingsquid.com "DISCLAIMER If you find a posting or message from me offensive, inappropriate, or disruptive, please ignore it. If you don't know how to ignore a posting, complain to me and I will demonstrate." |
#10
Posted to alt.home.repair
|
|||
|
|||
GFI question
Mark Lloyd writes:
Why should switching power to a GFI trip it? A GFI works on difference on current flowing in 2 parts of the circuit. Both are being started and stopped at exactly the same time. I have a portable GFI that's intended to be used with extension cords or portable tools. It's in the form of a 15 A extension cord (male plug on one end, female socket on the other) with a GFI in between. It drops out any time the input power is lost. You have to "reset" it initially whenever you plug it into a new power source. I assume this is a safety feature - you don't really want a power tool restarting on its own after it has stopped because the line power went away. So some GFIs do drop out on power loss, just like a magnetic starting switch for a large power tool. On the other hand, the wall-outlet type of GFI does not trip on power loss. It behaves more like a circuit breaker. Dave |
#11
Posted to alt.home.repair
|
|||
|
|||
GFI question
"John Gilmer" writes:
I've heard others say no, they don't drop out before, but I haven't yet found one myself that didn't, nor anyone whose story about same seemed believable. From what I've seen of GFI designs on the 'net, they operate on a "latch" system and that "latch" drops when the ac goes away. I would like to see a URL to that design. The designs I have seen "on the net" and my own experience are that the GFCI contacts stay closed when the input power goes away. I have both types. There's a portable GFI which is part of a short extension cord. It seems to use a relay to pass current; the relay drops out when input power goes away. The Reset button has to be pressed after the unit is plugged into a live outlet to get it to pass power. Then there are the wall-outlet GFIs. They work approximately like a breaker, mechanically latched in the ON state and electrically tripped when the monitoring circuit detects a ground fault. So both exist. Dave |
#12
Posted to alt.home.repair
|
|||
|
|||
GFI question
I have both types. There's a portable GFI which is part of a short extension cord. It seems to use a relay to pass current; the relay drops out when input power goes away. The Reset button has to be pressed after the unit is plugged into a live outlet to get it to pass power. I don't have a GFCI extension cord. But I do have some appliances (window A/C and hair dryer) that have GFCIs as part of the plug assembly. Neither of these needs to be reset when the power goes out. Then there are the wall-outlet GFIs. They work approximately like a breaker, mechanically latched in the ON state and electrically tripped when the monitoring circuit detects a ground fault. So both exist. Dave |
#13
Posted to alt.home.repair
|
|||
|
|||
GFI question
gntry wrote: I have a dedicated 20 amp line for my pool. I have a GFI outlet by the deck for the filter. I want to install a single pole switch in the house to turn the filter on and off from inside. If I install a switch, will the GFI trip everytime you turn the power off to the GFI? www.gfi.com |
#14
Posted to alt.home.repair
|
|||
|
|||
GFI question
Nguy n Thanh Tu n wrote:
gntry wrote: I have a dedicated 20 amp line for my pool. I have a GFI outlet by the deck for the filter. I want to install a single pole switch in the house to turn the filter on and off from inside. If I install a switch, will the GFI trip everytime you turn the power off to the GFI? www.gfi.com Hi, No. An exmple. Bathrooms are GFI protected. Turning lights on/off in the bathroom does not trip breaker. There are GFI outlet and GFI breaker. |
#15
Posted to alt.home.repair
|
|||
|
|||
GFI question
Tony Hwang wrote:
Nguy n Thanh Tu n wrote: gntry wrote: I have a dedicated 20 amp line for my pool. I have a GFI outlet by the deck for the filter. I want to install a single pole switch in the house to turn the filter on and off from inside. If I install a switch, will the GFI trip everytime you turn the power off to the GFI? www.gfi.com Hi, No. An exmple. Bathrooms are GFI protected. Turning lights on/off in the bathroom does not trip breaker. There are GFI outlet and GFI breaker. Note that in houses wired according to code, the GFI-protected outlets in the bathroom are on a different circuit from the bathroom lighting. Nevertheless, Tony is correct; the GFI will not trip if you wire the switch into the circuit. Make *very* sure you wire the switch in the hot line, not the neutral line. Yours aye, W. Underhill -- "Take sides! Always take sides! You may sometimes be wrong - but the man who refuses to take sides must *always* be wrong! Heaven save us from poltroons who fear to make a choice!" R.A. Heinlein, "Double Star" |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
GFI question | Home Repair | |||
GFI Receptacle Question | Home Repair | |||
GFI Receptacle Question | Home Repair | |||
GFI Outlet question | Home Repair | |||
Is it pointless to put GFI outlets on a on a curcuit that has gfi breaker??? | Home Repair |