[email protected] March 5th 07 04:39 PM

8 gauge wire to 30 amp circuit
 
This is a great place for information thanks.

We are buying a dual fuel range that specifies a 30 amp 4 wire for
installation. I have 8 gauge wire and I'm wondering if it will be a
problem to use that for the 30 amp breaker or if i should get 10 gauge
instead--the run to the box is about 18 feet.

Thanks,
Gavin


Chris Friesen March 5th 07 04:50 PM

8 gauge wire to 30 amp circuit
 
wrote:

We are buying a dual fuel range that specifies a 30 amp 4 wire for
installation. I have 8 gauge wire and I'm wondering if it will be a
problem to use that for the 30 amp breaker or if i should get 10 gauge
instead--the run to the box is about 18 feet.


Using #8 is overkill but shouldn't be a problem as long as the breaker
and the range can handle the larger wire.

Chris

lp13-30 March 5th 07 04:51 PM

8 gauge wire to 30 amp circuit
 
Should be no problem at all. Larry


RBM March 5th 07 09:04 PM

8 gauge wire to 30 amp circuit
 
Nec requires an outlet and plug to connect your range, which is actually
good in your case as most of the wiring chambers on duel fuel units are
tight. Use the oversized cable, but connect it to a thirty amp four wire
outlet and use thirty amp cord set as well. Be real careful to note the
exact location where the outlets is to be installed. There's generally
little room for error



wrote in message
oups.com...
This is a great place for information thanks.

We are buying a dual fuel range that specifies a 30 amp 4 wire for
installation. I have 8 gauge wire and I'm wondering if it will be a
problem to use that for the 30 amp breaker or if i should get 10 gauge
instead--the run to the box is about 18 feet.

Thanks,
Gavin




Steve Barker March 5th 07 09:59 PM

8 gauge wire to 30 amp circuit
 
If it calls for 30A, then it would be a waste to use 8ga wire. Just get a
10/3 w/ground and be done.

--
Steve Barker




wrote in message
oups.com...
This is a great place for information thanks.

We are buying a dual fuel range that specifies a 30 amp 4 wire for
installation. I have 8 gauge wire and I'm wondering if it will be a
problem to use that for the 30 amp breaker or if i should get 10 gauge
instead--the run to the box is about 18 feet.

Thanks,
Gavin




Doug Miller March 5th 07 10:49 PM

8 gauge wire to 30 amp circuit
 
In article , "Steve Barker" wrote:
If it calls for 30A, then it would be a waste to use 8ga wire. Just get a
10/3 w/ground and be done.

He already has the 8. Using 10 will be more expensive, since he has to buy
that.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

Steve Barker March 6th 07 12:25 AM

8 gauge wire to 30 amp circuit
 
Boy! I'm just not reading well at all today, am I?

--
Steve Barker




"Doug Miller" wrote in message
.. .
In article , "Steve Barker"
wrote:
If it calls for 30A, then it would be a waste to use 8ga wire. Just get a
10/3 w/ground and be done.

He already has the 8. Using 10 will be more expensive, since he has to buy
that.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.




Don Klipstein March 6th 07 04:38 AM

8 gauge wire to 30 amp circuit
 
In article , Gerry Atrick wrote:

Bigger than needed never hurts a thing when it comes to wire, except
sometimes it's hard to connect to things. For example, one place I
worked in years ago, the owner built a rec-room in the basement and
ran a 10-2 cable to the unfinished side for a future outdoor outlet.
I ended up installing the box and outlet. What a pain in the butt to
connect #10 wire to a common outlet. I finally pigtailed some #12
with wirenuts. As long as you can attach the #8, use it. For a
Range, I doubt you'll have any problems attaching the wires. If by
chance you dont have enough of the #8, use a #10 for the ground.


I would like to add, should the branch circuit have any wire of maximum
allowable overcurrent protection less than that of any other wire in that
branch circuit likely to be seen: Put a note in the breaker box by the
breaker!

In fact, I have seen something saying that it is against code to have a
branch circuit with mixed wire sizes. Although I am not sure whether this
is NEC or a local building code - I saw this in a municipal government
website of some municipality.

Furthermore, if anything connected to that branch circuit has maximum
allowable overcurrent protection less than that typical of wiring likely
to be seen, even if other than these pigtails, I would see a yellow flag
in my head. I don't know whether or not code allows such. In any case I
would have a note in the breaker box saying maximum allowable overcurrent
protection for the branch circuit that both oversize wire and also
not-so-oversized items.

Things get easier when using common items with AWG 12 wire and 20 amp
breakers - this reduces chances of having the branch circuit
having/getting a breaker oversized for whatever. And I think especially
don't mix 14 and 12 AWG wire in a branch circuit, lest someone replace the
15 amp breaker with a 20 amp one in response to seeing the 12 AWG wire!

- Don Klipstein )