Just a quick question. New service...200a meter to 200a service panel
underground in sch 80 pvc conduit. What size and type of wire ( ie
4/0-4/0-2/0 )?

Thanks in advance.


SteveF January 23rd 07 03:40 PM

200amp service feed
 

"Dave Herron" wrote in message
ups.com...
Just a quick question. New service...200a meter to 200a service panel
underground in sch 80 pvc conduit. What size and type of wire ( ie
4/0-4/0-2/0 )?

Thanks in advance.


Since it's underground I'll assume the meter base isn't on the opposite side
of the wall from the panel so how long will this cable be?

Steve.



RBM January 23rd 07 03:41 PM

200amp service feed
 
That wire size if not to long a run is fine for aluminum, copper would be
2/0 with a reduced neutral


"Dave Herron" wrote in message
ups.com...
Just a quick question. New service...200a meter to 200a service panel
underground in sch 80 pvc conduit. What size and type of wire ( ie
4/0-4/0-2/0 )?

Thanks in advance.




Dave Herron January 23rd 07 03:42 PM

200amp service feed
 
150 feet

SteveF wrote:
"Dave Herron" wrote in message
ups.com...
Just a quick question. New service...200a meter to 200a service panel
underground in sch 80 pvc conduit. What size and type of wire ( ie
4/0-4/0-2/0 )?

Thanks in advance.


Since it's underground I'll assume the meter base isn't on the opposite side
of the wall from the panel so how long will this cable be?

Steve.



Joe January 23rd 07 04:12 PM

200amp service feed
 

Dave Herron wrote:
Just a quick question. New service...200a meter to 200a service panel
underground in sch 80 pvc conduit. What size and type of wire ( ie
4/0-4/0-2/0 )?

Thanks in advance.


Call your power company and ask them. They supply the power from the
pole to the meter base and you must follow their requirements. For
other than power company supplied connections, consult your local
building inspection department. Both will be very helpful.
For example, in our area the meter base to panel distance is held to 5'
or less. Underground service for residential must be in 2 1/2" conduit,
commercial is 3" conduit. Galvanized sweeps ( 90 dgree turns) are
required at the pole and meter base with adapters to the permitted PVC
conduit. For all the aggravation of dealing with stubborn cable between
the meter base and panel, consider hiring that part out.
Of course, if this is not a primary service, other rules may apply. HTH

Joe


Thomas Horne January 24th 07 12:51 AM

200amp service feed
 
Dave Herron wrote:
Just a quick question. New service...200a meter to 200a service panel
underground in sch 80 pvc conduit. What size and type of wire ( ie
4/0-4/0-2/0 )?

Thanks in advance.


Are you in North America? Well since your using American Wire gage
sizing I will guess yes.

Is the wire we are discussing before or after the meter?

Is the service single phase residential only?
--
Tom Horne

SteveF January 24th 07 02:06 AM

200amp service feed
 

"Dave Herron" wrote in message
ups.com...
Just a quick question. New service...200a meter to 200a service panel
underground in sch 80 pvc conduit. What size and type of wire ( ie
4/0-4/0-2/0 )?

Thanks in advance.


4/0-4/0-4/0 Aluminum will do. Not sure if the third cable needs to be a 4/0
but that is how the SER and SEU cables are bundled.

At 150 ft the voltage drop will be under 3% for 240v single phase service
which is fine.