Posted to alt.home.repair
|
|||
|
|||
york furnace of woe
This is a York model G80C075120 Exterior forced air heater.
The blower, igniter and fan work, the main burners ignite but then shut off 5 seconds later; cycle three times and then shut down. There is no error code. Ive replaced the flame sensor Purged the gas valve, measured 9v from the control board on the two leads Re-inserted all the leads to the control board to insure good contact and bypassed the thermostat by leaving the ground attached and connecting the call for heat and blower wire twisted together with the same results. What am I missing ? |
#2
Posted to alt.home.repair
|
|||
|
|||
york furnace of woe
i do not have your furnace. here are some thoughts:
gas boiler burner problems i've has: i had to replace the pilot assembly and adjust the pilot flame to properly surround the flame sensor. different problem: replacing gas valve was required. you must refer to your service manual on this problem and the service pages of your furnace's components. owmytoe wrote: This is a York model G80C075120 Exterior forced air heater. The blower, igniter and fan work, the main burners ignite but then shut off 5 seconds later; cycle three times and then shut down. There is no error code. I've replaced the flame sensor Purged the gas valve, measured 9v from the control board on the two leads Re-inserted all the leads to the control board to insure good contact and bypassed the thermostat by leaving the ground attached and connecting the call for heat and blower wire twisted together with the same results. What am I missing ? |
#3
Posted to alt.home.repair
|
|||
|
|||
york furnace of woe
Reverse polarity will cause the problem you describe. Check and make
sure you have 120 volts from black to ground, and 0 from white to ground. Larry |
#4
Posted to alt.home.repair
|
|||
|
|||
york furnace of woe
lp13-30 wrote:
Reverse polarity will cause the problem you describe. Check and make sure you have 120 volts from black to ground, and 0 from white to ground. Larry Hmmm, Ground is ground. 120V is between black(hot) and white(neutral). Trying 3 times and quitting is sure sign of error condition. |
#5
Posted to alt.home.repair
|
|||
|
|||
york furnace of woe
buffalobill wrote:
i do not have your furnace. here are some thoughts: gas boiler burner problems i've has: i had to replace the pilot assembly and adjust the pilot flame to properly surround the flame sensor. different problem: replacing gas valve was required. you must refer to your service manual on this problem and the service pages of your furnace's components. owmytoe wrote: This is a York model G80C075120 Exterior forced air heater. The blower, igniter and fan work, the main burners ignite but then shut off 5 seconds later; cycle three times and then shut down. There is no error code. I've replaced the flame sensor Purged the gas valve, measured 9v from the control board on the two leads Re-inserted all the leads to the control board to insure good contact and bypassed the thermostat by leaving the ground attached and connecting the call for heat and blower wire twisted together with the same results. What am I missing ? Hi, It's funny he is talking about ignitor and flame sensor and you are talking about pilot flame? Different subject. |
#6
Posted to alt.home.repair
|
|||
|
|||
york furnace of woe
If the polarity of the incoming power is reversed you will still have
120 volts between black and white and the furnace will do exactly as the OP described. I have seen it happen before-- more than once. Make sure the black is hot and the white is neutral. Around here, about 99+% of furnaces are connected with a pigtail and receptacle, so the polarity can be accidentally switched easily if anything is done anywhere in the circuit. Most furnaces will run ok during a/c use that way-- it will not show up until the heat is fired up. Larry |
#7
Posted to alt.home.repair
|
|||
|
|||
york furnace of woe
"lp13-30" wrote in message ... If the polarity of the incoming power is reversed you will still have 120 volts between black and white and the furnace will do exactly as the OP described. I have seen it happen before-- more than once. Make sure the black is hot and the white is neutral. Around here, about 99+% of furnaces are connected with a pigtail and receptacle, so the polarity can be accidentally switched easily if anything is done anywhere in the circuit. Most furnaces will run ok during a/c use that way-- it will not show up until the heat is fired up. Larry My furnace installation manual specifically warns about this possibility. Larry's suggestion and method of testing are both valid. Don Young |
#8
Posted to alt.home.repair
|
|||
|
|||
york furnace of woe
thanks for the tips...flame sensor double checked, reading microamps under
use...i'm afraid ground ( white ) is indeed ground next step: a ball peen hammer Don Young wrote: If the polarity of the incoming power is reversed you will still have 120 volts between black and white and the furnace will do exactly as the [quoted text clipped - 4 lines] circuit. Most furnaces will run ok during a/c use that way-- it will not show up until the heat is fired up. Larry My furnace installation manual specifically warns about this possibility. Larry's suggestion and method of testing are both valid. Don Young -- Message posted via HomeKB.com http://www.homekb.com/Uwe/Forums.aspx/repair/200611/1 |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
York vs. Luxaire vs. Keeprite vs. ??? Furnace | Home Repair | |||
York Modulating Furnace | Home Repair | |||
York vs. Luxaire vs. Keeprite vs. ??? Furnace | Home Ownership | |||
York Furnace Problem | Home Repair | |||
York Furnace Filter (High velocity)? | Home Repair |