Bond November 23rd 06 03:48 AM

Wiring Basement
 
I am just starting to finish part of my basement and just completed
the framing. I would like to install 5 receptacles and some recessed
lighting (6 of them), along with a dimmer switch for the light. My
plan is to create a new cicuit (there is room on the breaker). I am
having problems putting my head around how the wiring will work for the
circuit. Questions I have is can all this be put on 1 circuit? I am
running the wire from the breaker, to the receptacles (in series), to a
light switch, and then to each of the recessed lights ... is this right
method? Any help is greatly appreciated.


[email protected] November 23rd 06 04:07 AM

Wiring Basement
 
Can it be done??? Sure would I do it? Well, that depends on what you
plan on running in the room? 6 recessed lights at say 100 watts each
would be 600 watts right there in lighting.
15 amps x 110 volts = 1650 watts. So at 1650 - 600 = 1050 watts
avail.
What can run at 1050 watts? Lots of things, but again it all depends
on what you want to run in the room. Another idea is that you might
want to run a 20 amp circuit down there instead of a 15. That'll give
you a little extra power just in case. Now normally what people do is
run a seperate light circuit and a seperate circuit for outlets. If
you short out the outlet at least the lights above would still be on.
Another thing to consider is that if you have water nearby you should
run a gfci breaker or outlet. If the wiring is going to be left
exposed on the walls (opposite of the finished walls) you need to have
it use armored cable. Otherwise if all is closed up Romex should be
fine.

Tom


Bond wrote:
I am just starting to finish part of my basement and just completed
the framing. I would like to install 5 receptacles and some recessed
lighting (6 of them), along with a dimmer switch for the light. My
plan is to create a new cicuit (there is room on the breaker). I am
having problems putting my head around how the wiring will work for the
circuit. Questions I have is can all this be put on 1 circuit? I am
running the wire from the breaker, to the receptacles (in series), to a
light switch, and then to each of the recessed lights ... is this right
method? Any help is greatly appreciated.



Edwin Pawlowski November 23rd 06 04:53 AM

Wiring Basement
 

"Bond" wrote in message
oups.com...
I am just starting to finish part of my basement and just completed
the framing. I would like to install 5 receptacles and some recessed
lighting (6 of them), along with a dimmer switch for the light. My
plan is to create a new cicuit (there is room on the breaker). I am
having problems putting my head around how the wiring will work for the
circuit. Questions I have is can all this be put on 1 circuit? I am
running the wire from the breaker, to the receptacles (in series), to a
light switch, and then to each of the recessed lights ... is this right
method? Any help is greatly appreciated.


No, it is not right. Get a book. Really, it will have some simple diagrams
on how to properly do a layout. Fifteen dollars and a half hour will give
you a good basic education on home wiring.

You should not have the recepticals and light on only one circuit. Plug in
an appliance, trip the breaker, and you are sitting in the dark.






RBM November 23rd 06 12:29 PM

Wiring Basement
 
Depending upon what you plan to use in the space, it may make more sense to
run a few circuits


"Bond" wrote in message
oups.com...
I am just starting to finish part of my basement and just completed
the framing. I would like to install 5 receptacles and some recessed
lighting (6 of them), along with a dimmer switch for the light. My
plan is to create a new cicuit (there is room on the breaker). I am
having problems putting my head around how the wiring will work for the
circuit. Questions I have is can all this be put on 1 circuit? I am
running the wire from the breaker, to the receptacles (in series), to a
light switch, and then to each of the recessed lights ... is this right
method? Any help is greatly appreciated.




smcjensen November 23rd 06 03:28 PM

Wiring Basement
 
If the wiring is going to be left
exposed on the walls (opposite of the finished walls) you need to have
it use armored cable. Otherwise if all is closed up Romex should be
fine.

Tom

regarding armored cable, when I built an additionional stall in my
garage and wired it, no drywall, exposed studs, the inspector had me
run wooden blocking in front of the wiring. I'm not sure that even
armored cable would meet code if left exposed because stuff can still
bang into it or hang up on it and pull connections loose. Totally
agree on buying a simple book to get the basics. Rather than work in
the breaker box, I did all the wiring except the connection to the
breaker box and hired an electrician for that. $80 well spent to stay
out of there.


John Grabowski November 23rd 06 03:51 PM

Wiring Basement
 

"Bond" wrote in message
oups.com...
I am just starting to finish part of my basement and just completed
the framing. I would like to install 5 receptacles and some recessed
lighting (6 of them), along with a dimmer switch for the light. My
plan is to create a new cicuit (there is room on the breaker). I am
having problems putting my head around how the wiring will work for the
circuit. Questions I have is can all this be put on 1 circuit? I am
running the wire from the breaker, to the receptacles (in series), to a
light switch, and then to each of the recessed lights ... is this right
method? Any help is greatly appreciated.


You can do it that way, however I prefer to keep the lighting separate from
the receptacles by using two circuits. You never know what you will be
plugging in down the road and you don't want your lights dimming because of
a heater or refrigerator that's on the same circuit.

Make sure that you have permits and have this work inspected. More and more
I hear of home inspectors and attorneys bringing up the issue of finished
basements when a house is sold. I have had several customers have to pull
permits and get work inspected that was done two owners before. It is not
fun having to bring a basement up to code after it is finished and
especially for work that someone else did years before. In New Jersey it is
required to put firestops behind the basement walls every ten feet
horizontally and continuous vertically at the top. It is also a good idea
for insurance purposes to have had the work inspected.


Doug Miller November 23rd 06 04:01 PM

Wiring Basement
 
In article . com, "smcjensen" wrote:

regarding armored cable, when I built an additionional stall in my
garage and wired it, no drywall, exposed studs, the inspector had me
run wooden blocking in front of the wiring.


How close to the edges of the studs had you drilled the holes that you passed
the cable through? Code minimum is 1.25", and if you're closer than that, you
need *something* over it.

I'm not sure that even
armored cable would meet code if left exposed


Both BX ("armored cable") and MC (metal-clad cable) are explicitly approved
for exposed installation by the NEC

because stuff can still bang into it


Yeah, that's why you use BX or MC for exposed wiring -- so that the metal
covering protects the conductors when stuff bangs into it. That's kinda the
point in using the armored stuff for exposed wiring, you know -- stuff can
bang into it.

or hang up on it and pull connections loose.


If that's all it takes to pull a connection loose, the stuff wasn't properly
installed in the first place. Both BX and MC require cable clamps where
entering boxes, and if they're clamped properly with the proper type of clamp,
the connections can't be pulled loose accidentally.


--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

Chris Friesen November 23rd 06 05:23 PM

Wiring Basement
 
wrote:

Having receptacles and lights on the same circuit is poor practice.


I'd be interested to hear your reasoning for this. My simplified code
book suggests otherwise for general outlets (not appliance or special
purpose outlets):

"It is better to have the load consist of a mixture of lights and plugs.
This gives better load diversity on the circuit and less chance of a
complete blackout in case of circuit failure."


Chris

RBM November 23rd 06 06:58 PM

Wiring Basement
 
The NEC doesn't require "finished" areas to meet any particular outlet
spacing. It requires "habitable" rooms to meet these outlet requirements.
Regardless of how he may plan to use the room, if it doesn't meet the
criteria for "habitable" which sometimes requires specific ceiling heights,
and multiple methods of egress, this can just be a glorified storage space
with however many outlets he feels like installing


wrote in message
...
On 22 Nov 2006 19:48:38 -0800, "Bond" wrote:

I am just starting to finish part of my basement and just completed
the framing. I would like to install 5 receptacles and some recessed
lighting (6 of them), along with a dimmer switch for the light. My
plan is to create a new cicuit (there is room on the breaker). I am
having problems putting my head around how the wiring will work for the
circuit. Questions I have is can all this be put on 1 circuit? I am
running the wire from the breaker, to the receptacles (in series), to a
light switch, and then to each of the recessed lights ... is this right
method? Any help is greatly appreciated.


No.

Code requires a finished area to have a receptacle within six feet of
the doorway, and receptacles every twelve feet after that.

Having receptacles and lights on the same circuit is poor practice.

Get a book, get a permit, get an inspection.

Once you put drywall up, the wiring is not visible. If there is no
record of a permit and inspection, a buyer has no idea what is behind
the drywall.

Ken





Tom November 23rd 06 07:07 PM

Wiring Basement
 
Use the power formula to figure out how to load the circuits. If u use
14/2WG you need a 15 amp breaker. 12/2WG a 20 amp breaker. Add up the
potential wattage you could or may plug into your outlets, plus the wattage
of the lights and see what you come up with. P (power or total watts) over E
(volts) = Amps. If you use a 20 amp breaker you'll need a 20 amp duplex
receptacles.


"Chris Friesen" wrote in message
...
wrote:

Having receptacles and lights on the same circuit is poor practice.


I'd be interested to hear your reasoning for this. My simplified code
book suggests otherwise for general outlets (not appliance or special
purpose outlets):

"It is better to have the load consist of a mixture of lights and plugs.
This gives better load diversity on the circuit and less chance of a
complete blackout in case of circuit failure."


Chris




Bond November 23rd 06 09:24 PM

Wiring Basement
 
Thanks Everyone.... I did not expect such a quick response. I took the
advice ... got a book, and will separate the lights from the
receptacles.

thanks Again.


Tom wrote:
Use the power formula to figure out how to load the circuits. If u use
14/2WG you need a 15 amp breaker. 12/2WG a 20 amp breaker. Add up the
potential wattage you could or may plug into your outlets, plus the wattage
of the lights and see what you come up with. P (power or total watts) over E
(volts) = Amps. If you use a 20 amp breaker you'll need a 20 amp duplex
receptacles.


"Chris Friesen" wrote in message
...
wrote:

Having receptacles and lights on the same circuit is poor practice.


I'd be interested to hear your reasoning for this. My simplified code
book suggests otherwise for general outlets (not appliance or special
purpose outlets):

"It is better to have the load consist of a mixture of lights and plugs.
This gives better load diversity on the circuit and less chance of a
complete blackout in case of circuit failure."


Chris



Mark Lloyd November 24th 06 01:00 AM

Wiring Basement
 
On Thu, 23 Nov 2006 11:23:53 -0600, Chris Friesen
wrote:

wrote:

Having receptacles and lights on the same circuit is poor practice.


I'd be interested to hear your reasoning for this. My simplified code
book suggests otherwise for general outlets (not appliance or special
purpose outlets):

"It is better to have the load consist of a mixture of lights and plugs.
This gives better load diversity on the circuit and less chance of a
complete blackout in case of circuit failure."



Considering "less chance of a complete blackout in case of circuit
failure", don't put all the lights in the house on ONE lighting
circuit.

Chris

--
32 days until the winter solstice celebration

Mark Lloyd
http://notstupid.laughingsquid.com

"I have found Christian dogma unintelligable. Early
in life I absented myself from Christian assemblies."
-- Benjamin Franklin

RBM November 24th 06 01:01 AM

Wiring Basement
 
The NEC rules have nothing to do with my preferences, but they are pretty
specific about the requirements for various types of locations. People are
well within their rights to use those requirements to their advantage



wrote in message
...
On Thu, 23 Nov 2006 13:58:14 -0500, "RBM" rbm2(remove
wrote:

The NEC doesn't require "finished" areas to meet any particular outlet
spacing. It requires "habitable" rooms to meet these outlet requirements.
Regardless of how he may plan to use the room, if it doesn't meet the
criteria for "habitable" which sometimes requires specific ceiling
heights,
and multiple methods of egress, this can just be a glorified storage space
with however many outlets he feels like installing

Know a lot of people who put five receptacles and half a dozen pot
lights into a storage space??

Get a life, you nit-picking a***.

Ken




SAm E November 24th 06 01:01 AM

Wiring Basement
 
On Fri, 24 Nov 2006 00:13:44 GMT, wrote:

On Thu, 23 Nov 2006 13:58:14 -0500, "RBM" rbm2(remove
wrote:

The NEC doesn't require "finished" areas to meet any particular outlet
spacing. It requires "habitable" rooms to meet these outlet requirements.
Regardless of how he may plan to use the room, if it doesn't meet the
criteria for "habitable" which sometimes requires specific ceiling heights,
and multiple methods of egress, this can just be a glorified storage space
with however many outlets he feels like installing

Know a lot of people who put five receptacles and half a dozen pot
lights into a storage space??

Get a life, you nit-picking a***.


"nits don't grow on trees!". I'm not sure exactly what that means, but
it sure sounds relevant.

Ken