Outlet wiring, does color matter?
 
When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


Doug Miller November 20th 06 05:22 PM

Outlet wiring, does color matter?
 
In article . com, " wrote:
When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

Yes, it does. Don't do it.

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.


You didn't hear that from anyone who knows what he's talking about. Polarity
*does* matter. Among other things, you could wind up making the housing of
whatever you plug in there, live.

Also, when wiring up lights, does it matter which color wire I run to
the switch?


Yes.

Most of the how-to articles show cutting the white
wire...does it make any difference?


No, they don't. You'd better look again. The switch should always go on the
hot side, which (in the US and Canada, anyway) is the black wire.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

CJT November 20th 06 05:27 PM

Outlet wiring, does color matter?
 
wrote:

When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?


It matters.

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?

It matters. And I doubt your last paragraph correctly describes those
articles.

The concern relates to safety and failure modes. Either way will appear
to work. But the wrong way will be unsafe and violate code.

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .

Bill November 20th 06 05:28 PM

Outlet wiring, does color matter?
 
Yes it matters that the white wire goes to the larger hole side of the
outlet and the black wire goes to the smaller hole side of the outlet.

Then when things are plugged in, they are safer if the outlet is wired
properly. For example a table lamp with one prong larger than the other. You
can only plug it in one way. The larger prong (white wire) goes to the
"ring" part of the light bulb. The smaller prong (black - hot) goes to the
switch and then to the contact down in the center of the socket.

You can get electrocuted if you touch the black hot wire. It is safer it
this is the wire going to the contact in the bottom of the light socket. It
is easy to accidentally touch the metal ring of a light bulb when changing a
light bulb. Best if it is connected to the white (neutral) wire and NOT to
the black hot wire!

So wire your outlets properly and wire lamps and appliances properly. Get a
book on wiring or call an electrician. These things are done to protect YOUR
life and the lives of YOUR family.


wrote in message
When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?




[email protected] November 20th 06 05:54 PM

Outlet wiring, does color matter?
 
In addition to what was written above, your nonstandard wiring would
pose a problem for anyone who worked on it inthe future.


Terry November 20th 06 06:22 PM

Outlet wiring, does color matter?
 
On 20 Nov 2006 09:15:50 -0800, "
wrote:

When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?


It matters. That is why they use different colors.

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?





Joseph Meehan November 20th 06 07:21 PM

Outlet wiring, does color matter?
 
wrote:
When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


Not only does it matter, it can be unsafe, it is against all known codes
and it can cause your home to fail inspections. You don't want to do it.

--
Joseph Meehan

Dia 's Muire duit




[email protected] November 20th 06 07:30 PM

Outlet wiring, does color matter?
 

wrote:
When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


kj:

The black wire (which can be any color, actually, except white) is the
'hot'.
The white or 'natural gray'-insulated wire is the 'neutral'. Think of
the 'hot'
as a permanently pressurized 'pipe', and the neutral as a 'drainpipe'
which
only carries electricity when the 'faucet' (switch, appliance, etc) is
using
it.

Now, lights and other plug-in appliances are designed so that the 'hot'

is less accessible than the 'neutral'. Ex.: the bulb 'shell' is
connected
to the white 'neutral', and the contact at the socket bottom is 'hot'.

This ensures that if somebody is removing a dead bulb with the light
switch
still on (for instance) and brushes against the shell, they are
unlikely
to get a shock (unless something else is wrong with the wiring). If
the
hot and neutral are reversed, this shell would be connected to the
'supply pipe' and not the 'drain pipe', and the user would be shocked.
(Note that it is still possible to get shocked by a neutral, but it is
less
likely).

Moral of the story: Safety dictates that hot and neutral must be
properly
connected. Follow the manufacturer's directions. If for some reason
it's
easier to do it the wrong way, that's too bad. Do the job right.

Now for switches. Switches must always control the 'hot' side of a
circuit,
cutting off the 'supply pipe'. That way, with the switch off, the only
unbroken
connections (if the light is properly wired) are to the 'drainpipe',
the neutral
side. When a switch is in the neutral it will still stop current from
flowing;
the light will turn on and off with no problems. However, even with
the
switch off, all terminals and wires in the lamp will be 'hot', part of
that
pressurized pipe of electricity, waiting for somebody to provide a path
to
ground. ZAP.

Moral of the story: Switches must be in the 'hot' wire, never the
neutral.
This is a common problem in old houses, where some damfool cut off
and reconnected an old K&T run (where the conductors may be hard
to tell apart) without bothering to check which was which.

There is one situation where you may find a white wire on a switch.
Power may go to a lamp or other switched outlet,then out to a switch
and back to the outlet on the two conductors of one cable. This is
known as a 'switch loop'. If you find a switch with only one
2-conductor cable coming into its box, and something goes on and
off when you flip it, you are definitely dealing with a switch loop.
In
a switch loop, all wires are considered 'hot'. If using cable, code
allows
the white wire to be used as part of a switch loop, but it is not a
neutral, is not connected to any other neutrals, and must be
permanently
reidentified some other color where the wire is exposed inside the
boxes.

Story time. My brother found an (overstuffed) j-box with a
questionable
receptacle in it, in a basement. Removing the receptacle, he proceeded
to wirenut all whites and all blacks together, then turned on the
power.
All well. Then he flipped the basement light switch. ZAP. One of
the
white wires was actually part of a hacked switch loop. He had
created a bolted short. Unfortunately, the circuit was also part of an
absurd multiwire circuit (which split 6' from the service panel) which
was
equally hacked, with overstuffed boxes, insecure connections, and
puny wire nuts, and one leg of this circuit was overfused. Both
breakers
tripped. My brother, being sensible, switched off the offending
light,
and turned the breakers back on. Well, some lights went poof, and
the phone, and some other electronic gadgets, now acted really
funny in a not-working way. Apparently the neutral of the multiwire
circuit had failed somewhere. Rather distressed by this, he shut off
both breakers (I told you he had sense) and we later straightened
everything out. This involved replacing one 4" octagon box with two
4S boxes and eliminating such idiocies as the elusive "switch threep"
- one wire to the switch, one wire from the switch to each of two
boxes,
using two pieces of 12-2 with one wire unused. Ugh.

Moral of the story: learn what you are doing before you do it. There
are
good books out there. Get a permit and get your work inspected.
It costs less than burning the place down. Finally, don't use USENET
as your sole source, and definitely don't use the home center.
House wiring is not as simple as some think.

Cordially yours:
G P


Tom The Great November 20th 06 08:27 PM

Outlet wiring, does color matter?
 
On 20 Nov 2006 09:15:50 -0800, "
wrote:

When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?



Hire a qualified electrician.


Mark Lloyd November 20th 06 08:31 PM

Outlet wiring, does color matter?
 
On 20 Nov 2006 09:15:50 -0800, "
wrote:

When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?


Yes. Correct it.

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.


It's not polarity (this is AC, where polarity is changing 120 times a
second), but connecting it right still matters.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


I guess I missed those articles. I always switched the hot (black)
wire, the obvious way to do it.
--
35 days until the winter solstice celebration

Mark Lloyd
http://notstupid.laughingsquid.com

"I have found Christian dogma unintelligable. Early
in life I absented myself from Christian assemblies."
-- Benjamin Franklin

Mark Lloyd November 20th 06 08:38 PM

Outlet wiring, does color matter?
 
On 20 Nov 2006 11:30:36 -0800, wrote:


wrote:
When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


kj:

The black wire (which can be any color, actually, except white)


or green?

is the
'hot'.
The white or 'natural gray'-insulated wire is the 'neutral'. Think of
the 'hot'
as a permanently pressurized 'pipe', and the neutral as a 'drainpipe'
which
only carries electricity when the 'faucet' (switch, appliance, etc) is
using
it.

Now, lights and other plug-in appliances are designed so that the 'hot'

is less accessible than the 'neutral'. Ex.: the bulb 'shell' is
connected
to the white 'neutral', and the contact at the socket bottom is 'hot'.

This ensures that if somebody is removing a dead bulb with the light
switch
still on (for instance) and brushes against the shell, they are
unlikely
to get a shock (unless something else is wrong with the wiring). If
the
hot and neutral are reversed, this shell would be connected to the
'supply pipe' and not the 'drain pipe', and the user would be shocked.
(Note that it is still possible to get shocked by a neutral, but it is
less
likely).


One time, while changing a switch, I held a hot wire and felt
absolutely nothing. I was careful not to touch anything else
electrical at the same time.

Moral of the story: Safety dictates that hot and neutral must be
properly
connected. Follow the manufacturer's directions. If for some reason
it's
easier to do it the wrong way, that's too bad. Do the job right.

Now for switches. Switches must always control the 'hot' side of a
circuit,
cutting off the 'supply pipe'. That way, with the switch off, the only
unbroken
connections (if the light is properly wired) are to the 'drainpipe',
the neutral
side. When a switch is in the neutral it will still stop current from
flowing;
the light will turn on and off with no problems. However, even with
the
switch off, all terminals and wires in the lamp will be 'hot', part of
that
pressurized pipe of electricity, waiting for somebody to provide a path
to
ground. ZAP.

Moral of the story: Switches must be in the 'hot' wire, never the
neutral.
This is a common problem in old houses, where some damfool cut off
and reconnected an old K&T run (where the conductors may be hard
to tell apart) without bothering to check which was which.

There is one situation where you may find a white wire on a switch.
Power may go to a lamp or other switched outlet,then out to a switch
and back to the outlet on the two conductors of one cable. This is
known as a 'switch loop'. If you find a switch with only one
2-conductor cable coming into its box, and something goes on and
off when you flip it, you are definitely dealing with a switch loop.
In
a switch loop, all wires are considered 'hot'. If using cable, code
allows
the white wire to be used as part of a switch loop, but it is not a
neutral, is not connected to any other neutrals, and must be
permanently
reidentified some other color where the wire is exposed inside the
boxes.

Story time. My brother found an (overstuffed) j-box with a
questionable
receptacle in it, in a basement. Removing the receptacle, he proceeded
to wirenut all whites and all blacks together, then turned on the
power.
All well. Then he flipped the basement light switch. ZAP. One of
the
white wires was actually part of a hacked switch loop. He had
created a bolted short. Unfortunately, the circuit was also part of an
absurd multiwire circuit (which split 6' from the service panel) which
was
equally hacked, with overstuffed boxes, insecure connections, and
puny wire nuts, and one leg of this circuit was overfused. Both
breakers
tripped. My brother, being sensible, switched off the offending
light,
and turned the breakers back on. Well, some lights went poof, and
the phone, and some other electronic gadgets, now acted really
funny in a not-working way. Apparently the neutral of the multiwire
circuit had failed somewhere. Rather distressed by this, he shut off
both breakers (I told you he had sense) and we later straightened
everything out. This involved replacing one 4" octagon box with two
4S boxes and eliminating such idiocies as the elusive "switch threep"
- one wire to the switch, one wire from the switch to each of two
boxes,
using two pieces of 12-2 with one wire unused. Ugh.

Moral of the story: learn what you are doing before you do it. There
are
good books out there. Get a permit and get your work inspected.
It costs less than burning the place down. Finally, don't use USENET
as your sole source, and definitely don't use the home center.


They do have a lot of people who don't know much.

House wiring is not as simple as some think.

Cordially yours:
G P

--
35 days until the winter solstice celebration

Mark Lloyd
http://notstupid.laughingsquid.com

"I have found Christian dogma unintelligable. Early
in life I absented myself from Christian assemblies."
-- Benjamin Franklin

Don Klipstein November 20th 06 09:35 PM

Outlet wiring, does color matter?
 
On 20 Nov 2006 09:15:50 -0800, "
wrote:

When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


Yes, it does make a difference.

As another poster mentioned, switch on the wrong wire allows switched
devices, such as lamp sockets, to be hot - you get shocked if you touch
such items and ground.

As for outlets - those have designated hot and neutral terminals that
should not be reversed. Many appliances have polarized plugs. If a lamp
has hot and neutral reversed, then the exposed part of the base of a
partially screwed-in lightbulb will be hot - even if the lamp's switch is
off!

Also keep in mind that in some fluorescent lamps, reversing hot and
neutral can adversely affect the electric field distribution within a bulb
that is trying to start, and that may impair starting.

- Don Klipstein )

Pop` November 20th 06 11:03 PM

Outlet wiring, does color matter?
 
wrote:
When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


KUDOS to you for checking and to all who responded with such good advice to
the OP.

It sounds like a trip to your local library or a related web site would do
you a world of good. The basics aren't that complicated and you might get
on well. Just don't get over-confident and assume you know things you don't
yet - always find out for sure, like you did here.
Electricity can be very deadly and can cause nearly instantaneious death
in some circumstances, so knowing the basics is essential.

And, the MOST BASIC RULE OF ALL, IMO at least: NEVER WORK ON A CIRCUIT WITH
THE POWER ON!!!!!!!!!!!!!!!!!!!!!!!!!!!!
Then after you kill the power, CHECK to be sure the wires you're going to
work on are actually dead! A switch is NOT the right way to turn off power;
it has to be done at the breaker box or fuse box, whichever you have.

Pop`



November 21st 06 08:40 AM

Outlet wiring, does color matter?
 
In article . com,
wrote:
When wiring up normal 3-prong outlets, does it matter if I switch the
black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm not
going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run to
the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


To be safe & meet code, all 120V outlets will be wired with
the neutral (white) connected to the neutral terminal on the outlet,
indicated by the silver screw; hot (almost always black, sometimes
red) connects to the brass colored screw; and ground, which is
bare or green insulated, connects to the green grounding screw on
the outlet. (or to the grounding screw of the outlet box, if box &
outlet are designed for this; usually the case when metal boxes are
used)

If by "switch the black and white wires" you mean connect
them opposite to above description, then doing so will create a
potentially unsafe condition. OTOH if you mean to install a switch to
control that outlet, then only the black or hot wire should be
switched. The neutral or white should always connect directly to the
outlet. In either case, there is only one correct way.

The term "polarity" has to do with positive & negative, and is
important in direct current systems, e.g. automotive. It really has no
bearing on a discussion of alternating current house wiring.

As far as connecting a light to a switch, there are a couple different
ways the wiring can be routed, that will make a difference as to which
color wire should go where; However, in all cases, the current
carrying neutral will connect to the neutral of the light fixture and
is never switched.

Why not get a good DIY book on house wiring? There are several that
do a good job of explaining both safe wiring and safe work practices.
Black and Decker sells a good one.
--
For every complicated, difficult problem, there is a simple, easy
solution that does not work.

Larry Wasserman - Baltimore Maryland -


dadiOH November 21st 06 01:04 PM

Outlet wiring, does color matter?
 
wrote:
When wiring up normal 3-prong outlets, does it matter if I switch
the black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm
not going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run
to the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


Please, hire an electrician.

--

dadiOH
____________________________

dadiOH's dandies v3.06...
....a help file of info about MP3s, recording from
LP/cassette and tips & tricks on this and that.
Get it at
http://mysite.verizon.net/xico




November 22nd 06 08:48 AM

Outlet wiring, does color matter?
 
In article RPC8h.4282$oP6.2508@trnddc03, dadiOH wrote:
wrote:
When wiring up normal 3-prong outlets, does it matter if I switch
the black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm
not going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run
to the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


Please, hire an electrician.

--


OP doesn't necessarily have to hire an electrician, but does need
more knowledge before attempting to DIY this job

Electricians aren't born with their knowledge. They have to learn it.
There's no reason a person of ordinary intelligence cannot learn, in a
reasonable length of time, how to safely perform simple, basic tasks
like wiring an outlet, switch, or light fixture.



--
Make it as simple as possible, but no simpler.

Larry Wasserman - Baltimore Maryland -

Bert Byfield November 22nd 06 04:00 PM

Outlet wiring, does color matter?
 
When wiring up normal 3-prong outlets, does it matter if I
switch the black and white wires on a single outlet in the run?


Please, hire an electrician.


OP doesn't necessarily have to hire an electrician, but does need
more knowledge before attempting to DIY this job
Electricians aren't born with their knowledge. They have to learn
it. There's no reason a person of ordinary intelligence cannot
learn, in a reasonable length of time, how to safely perform
simple, basic tasks like wiring an outlet, switch, or light
fixture.


In short, yes it matters, and you have to know why. Home Depot and
Loew's sell good books on home wiring.





barbarow November 23rd 06 01:22 AM

Outlet wiring, does color matter?
 
See http://www.doityourself.com/scat/basicelectric

--
Have a Great Week !

Check Winter Haven's Current Weather
http://www.wunderground.com/cgi-bin/...er+Haven+33881
wrote in message
...
In article RPC8h.4282$oP6.2508@trnddc03, dadiOH
wrote:
wrote:
When wiring up normal 3-prong outlets, does it matter if I switch
the black and white wires on a single outlet in the run?

I've heard the polarity doesn't matter...but want to make sure I'm
not going to short it out or something else horrible.

Also, when wiring up lights, does it matter which color wire I run
to the switch? Most of the how-to articles show cutting the white
wire...does it make any difference?


Please, hire an electrician.

--


OP doesn't necessarily have to hire an electrician, but does need
more knowledge before attempting to DIY this job

Electricians aren't born with their knowledge. They have to learn it.
There's no reason a person of ordinary intelligence cannot learn, in a
reasonable length of time, how to safely perform simple, basic tasks
like wiring an outlet, switch, or light fixture.



--
Make it as simple as possible, but no simpler.

Larry Wasserman - Baltimore Maryland -





All times are GMT +1. The time now is 10:58 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter