Default Electrical help needed

Hi,
I have recently purchased a new swimming pool heater, installed it next
to the shed in the backyard so naturally had to get electricity to it
from the main panel in the house.
I have a stab-lok panel in the house so I got a 50 amp NC0250cp bracer
that I installed in the house panel then connected the black wire and
the Red wire to each pole of the breaker the white wire to the neutral
of the panes and the Ground to the Ground I am using outdoor 6AWG wire.
I got the wire outside underground and to the shed where I installed a
new panel wired it up by connecting each Black and Reb to each main
connector of the new panel the white to the neutral bar and the ground
to the Ground bar I put in a 15amp single pole breaker for the pool
pump and a 30amp breaker for the pool heater.

with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't get
240vac I find that strange.

when 50amp breaker is on in the house and the 15amp breaker is on in
the shed the pomp works well but I would like to see if the 240 VAC is
ok before I connect up the pool heater.


Can you please help


  #2   Report Post  
Posted to alt.home.repair
Richard J Kinch
 
Posts: n/a
Default Electrical help needed

with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't get
240vac I find that strange.


Whaddya get? At both ends of the run?

If you need to ask this, maybe you shouldn't be doing it yourself?
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 479
Default Electrical help needed

Richard J Kinch wrote:
with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't
get 240vac I find that strange.


Whaddya get? At both ends of the run?


Also how are you measuring the voltage? Are you using a modern digital
meter?


If you need to ask this, maybe you shouldn't be doing it yourself?


--
Joseph Meehan

Dia duit


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 521
Default Electrical help needed

do you have 220 service in the house?
if you don't have 220 measurable at the main panel you won't get it in
the shed either.
for 220 you need two 110v hots out of phase, not just any 2 hots from a
110v main panel.
please read faq at:
http://www.faqs.org/faqs/electrical-wiring/part1/

wrote:
Hi,
I have recently purchased a new swimming pool heater, installed it next
to the shed in the backyard so naturally had to get electricity to it
from the main panel in the house.
I have a stab-lok panel in the house so I got a 50 amp NC0250cp bracer
that I installed in the house panel then connected the black wire and
the Red wire to each pole of the breaker the white wire to the neutral
of the panes and the Ground to the Ground I am using outdoor 6AWG wire.
I got the wire outside underground and to the shed where I installed a
new panel wired it up by connecting each Black and Reb to each main
connector of the new panel the white to the neutral bar and the ground
to the Ground bar I put in a 15amp single pole breaker for the pool
pump and a 30amp breaker for the pool heater.

with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't get
240vac I find that strange.

when 50amp breaker is on in the house and the 15amp breaker is on in
the shed the pomp works well but I would like to see if the 240 VAC is
ok before I connect up the pool heater.


Can you please help


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 28
Default Electrical help needed


wrote in message
oups.com...

with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't get
240vac I find that strange.


If you don't get 240v, what do you get?
If you get 0 v, it may mean your black and red are hooked up to the same
hot.



--
Posted via a free Usenet account from http://www.teranews.com



  #6   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default Electrical help needed


John wrote:
wrote in message
oups.com...

with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't get
240vac I find that strange.


If you don't get 240v, what do you get?
If you get 0 v, it may mean your black and red are hooked up to the same
hot.


That's my guess. Based on the "N" in the breaker number he gives, I'm
guessing it's a "narrow" style not designed for the particular panel he
has and isn't picking up but one side of the main buss bars...

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default Electrical help needed

wrote:

Hi,
I have recently purchased a new swimming pool heater, installed it next
to the shed in the backyard so naturally had to get electricity to it
from the main panel in the house.
I have a stab-lok panel in the house so I got a 50 amp NC0250cp bracer
that I installed in the house panel then connected the black wire and
the Red wire to each pole of the breaker the white wire to the neutral
of the panes and the Ground to the Ground I am using outdoor 6AWG wire.
I got the wire outside underground and to the shed where I installed a
new panel wired it up by connecting each Black and Reb to each main
connector of the new panel the white to the neutral bar and the ground
to the Ground bar I put in a 15amp single pole breaker for the pool
pump and a 30amp breaker for the pool heater.

with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't get
240vac I find that strange.

when 50amp breaker is on in the house and the 15amp breaker is on in
the shed the pomp works well but I would like to see if the 240 VAC is
ok before I connect up the pool heater.

Can you please help


Replace the Stab-Loc "incendiary device" a.k.a. panel before you burn
down your house. Then hook up the new heater to a proper two pole
breaker in a proper panel. My preference is for Square D QO panels, but
most anything current would be better that the Stab-Loc waiting to burn
the place down.

Pete C.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 41
Default Electrical help needed

Wiring is not a hobby, call a licensed electrical contractor. Sounds
like you have a real "cluster fu@k" going on, especially with the
Stab-lok panel. You are over you head and can easliy burn down your
house or kill yourself and others. The WORSE thing here is (and nobody
picked up on) is this is a swimming pool heater, and you did not
mention electrical bonding of pool related equipment. Trust me I
investigate this stuff for a living.






Pete C. wrote:
wrote:

Hi,
I have recently purchased a new swimming pool heater, installed it next
to the shed in the backyard so naturally had to get electricity to it
from the main panel in the house.
I have a stab-lok panel in the house so I got a 50 amp NC0250cp bracer
that I installed in the house panel then connected the black wire and
the Red wire to each pole of the breaker the white wire to the neutral
of the panes and the Ground to the Ground I am using outdoor 6AWG wire.
I got the wire outside underground and to the shed where I installed a
new panel wired it up by connecting each Black and Reb to each main
connector of the new panel the white to the neutral bar and the ground
to the Ground bar I put in a 15amp single pole breaker for the pool
pump and a 30amp breaker for the pool heater.

with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't get
240vac I find that strange.

when 50amp breaker is on in the house and the 15amp breaker is on in
the shed the pomp works well but I would like to see if the 240 VAC is
ok before I connect up the pool heater.

Can you please help


Replace the Stab-Loc "incendiary device" a.k.a. panel before you burn
down your house. Then hook up the new heater to a proper two pole
breaker in a proper panel. My preference is for Square D QO panels, but
most anything current would be better that the Stab-Loc waiting to burn
the place down.

Pete C.


  #13   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default Electrical help needed


dpb wrote:
....
...you don't get new ... the outer box itself.



But, there is a new cover plate and all to fit the new breakers so it
looks just like a new one from the outside as well when you're done...

  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Electrical help needed

Well older boxes were smaller when compared to today, and she appeared
to be using thin breakers too...

In my case my 100 amp box is JAMMED, for cost isues I have thought
about buying a 200 amp main box, with a extra 100 amp main breaker.

then replace the box but not the service line or meter can, and leave
it 100 amps. then when theres more $ go ahead and replace the remaining
components and install the 200 amp main breaker.

new service panels arent that expensive.

I do wonder with the OPs FPE if the grounding and bonding is current to
todays standards espically critical with that pool...........

  #16   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default Electrical help needed


wrote:
dpb wrote:
wrote:
...

new service panels arent that expensive.


I've already pointed out the cost savings aren't so much on the
hardware but in labor and OP in this thread certainly ain't gonna' be
doing this kind of upgrade him/herself...


please address my point...

assuming she has a 100 amp panel, is upgrading a FPE 100 amp a good
idea when adding a new major load of a electrical pool heater?

....

As I've pointed out repeatedly, assuming the physical size is adequate
(and OP has already indicated there was room available in the existing
panel) one can select a larger main w/ a larger ampacity main as part
of the retrofit kit. In essence, one no longer has an FPE panel at
all.

Whether it would be a fit in the particular application is
indeterminate from here, this asinine subthread started when I simply
pointed out there is a neat way to replace the trouble-prone FPE panels
besides a complete tearout which is potentially cheaper.

If the old box is surface mounted in an unfinished basement, there's no
purpose in a retrofit kit. Assuming it is embedded in a finished area
and does have physical capacity (and a lot of the FPE panels are plenty
large enough, dimensionally and that assumption is as equally
verifiable to be true in this case as that it isn't) the labor savings
in the associated replacement and repair of ancillary finished area can
save a sizable fraction of a replacement labor cost.

  #18   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default Electrical help needed


wrote:
dpb wrote:
wrote:
Good point, around here most panels are surface mount, in garages and
such.


Is OP around there??? Do you know what OP's mount is?

... replace the service drop, meter can ...


Those are external to the panel which is the item under discussion. If
those must be replaced, they have to be done irrespective of the panel
itself so no difference afaics.

As for the "guts" of the panel vis a vis replacing a panel, having the
wire already pulled and in place _is_ a sizable time-saver.

As for rust, if the box is in a place so wet that it's rusty enough to
need replacement, that's yet another problem that is totally unrelated
to subject question and needs to be addressed and selecting either a
new box or a retrofit kit doesn't address that problem/symptom (other
than masking it by putting a new box in a unsuitable location).


Geez I am having trouble explaining my position.

Someone suggested replacing the guts to save bucks

I asked does the current panel haver the AMP capacity? probably not
adding a 50 amp load

The response was you can use the existing box and upgrade the amp
capacity..

I asked about the service drop meter can and am told thats a seperate
issue.

Well NO ITS REALLY NOT, if the AMP capacity isnt enough upgrading will
require a new service drop meter can etc, at least around here the
panel capacity is matched to the service drop.


at that point using the old box wouldnt save much and a new one is
likely larger physically, my old FBE panel is on the small side, it
needs replaced and when that occurs I will have to remove some
shelving...

I wouldnt replace everything but the outer box, probably doesnt save
much and may cause irritating questions at home resale time, buyers are
very fussy.


  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Electrical help needed

Obviously you havent sold a home recently. I did nearly 2 years ago and
ended up getting middle group to reinspect my 8 year old panel. All
because the inspection stickers date and signature had faded. Middle
group inspector thought the home inspector was a idiot. The first buyer
backed out and the 2nd buyer and home inspector put me thru the
wringer a second time, for different issues Home inspector wrote me
up for no GFCI on sump pump in garage, so I installed one and was
rewarded by home inspector #2 writing it up too, saying it should be a
standard outlet. sometimes you cant win

My LAST post on this meaningless subject.............

If the service drop needs replaced I think a entire new panel is a
better choice, but to each his own!

My opinion is based on my own poor choice of upgrading to JUST a 100
amp, not only was FPE a bad choice but the cabinet is too small.....
along with a 100 amp limit.

Honestly if my main were physically larger and 200 AMP I would just
replace the guts.

I am hoping to upgrade this summer..

  #22   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Electrical help needed Haller Butt is unsafe

I have a lifetime of experience and some opinions too.

More importandly I am willing to learn.

A service tech by trade over 30 years repairing machines from copiers
to laminators and lots of other stuff in between, plus a ton of home
repairs and remodeling

  #23   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default Electrical help needed

On 3 Jul 2006 10:32:30 -0700, "dpb" wrote:


wrote:
Good point, around here most panels are surface mount, in garages and
such.


Is OP around there??? Do you know what OP's mount is?


He's explaining why he said what he did. No thread is just for the
OP. Now's a good time to take his explanation as it was intended.

... replace the service drop, meter can ...


Those are external to the panel which is the item under discussion. If
those must be replaced, they have to be done irrespective of the panel
itself so no difference afaics.

As for the "guts" of the panel vis a vis replacing a panel, having the
wire already pulled and in place _is_ a sizable time-saver.

As for rust, if the box is in a place so wet that it's rusty enough to
need replacement, that's yet another problem that is totally unrelated
to subject question and needs to be addressed and selecting either a
new box or a retrofit kit doesn't address that problem/symptom (other
than masking it by putting a new box in a unsuitable location).


He's still explaining why in many cases in his experience it's worth
replacing the whole box. That's all. The OP should be able to read
and decide if he has a lot of rust or not.
  #25   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 41
Default Electrical help needed Haller Butt is unsafe

NONE of you guys (including myself) are qualified to give advice on an
electrical problem you can not see and troubleshoot IN PERSON. Lets not
forget this guy is working on a pool. The best advice is to start
reading NEC art 680. Best advice is to call a licensed electrical
contractor.





wrote:
Tekkie® wrote:
posted for all of us...
I don't top post - see either inline or at bottom.

As my usual safety practice I then shrted this line to make certain it
was dead.

You are as big a dufus in electrical work as plumbing GO AWAY!!!!!
--
Tekkie


you think it dufus, did you know thats what linemen do, not only do
they check to make sure, they install intentional shorts so a bad
switch throw doesnt kill someone.

meters flake, lights dont work, a short is a short and very
reliable........!!!!!!!!!




  #26   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 856
Default Electrical help needed

According to :

I have a stab-lok panel in the house so I got a 50 amp NC0250cp bracer
that I installed in the house panel then connected the black wire and
the Red wire to each pole of the breaker the white wire to the neutral
of the panes and the Ground to the Ground I am using outdoor 6AWG wire.
I got the wire outside underground and to the shed where I installed a
new panel wired it up by connecting each Black and Reb to each main
connector of the new panel the white to the neutral bar and the ground
to the Ground bar I put in a 15amp single pole breaker for the pool
pump and a 30amp breaker for the pool heater.

with my voltmeter I cam measure 120vac when I go across neutral and
each Black and Red but when I measure across Black and Red I don't get
240vac I find that strange.


With at least _some_ STAB-LOK panels, it is possible to insert
a dual breaker so that the two halves of the breaker are on the
_same_ side of the main feed. [The backplane is wired AABBAABB...
instead of ABABAB...., and there are no interlocks to prevent
mis-registration]. If you have both halves of the breaker on the same
side, you'll have the precise symptoms you show.

Pull the breaker and move it _one_ slot (half the breaker width).
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
  #28   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Electrical help needed Haller Butt is unsafe & now STUUUPID


Heavy Butt wipe, that is not a short; that is a GROUND! Jesus, copier guy...
You are like Stormy - you think you learn but you don't.
--
Tekkie


I have a couple detractors here, so be it

While YOU depend on a meter or test light and might get zapped I try to
avoid that, its not the end of the world just unpleasant and possibly
dangerous.

Incidently MY test to make certain a line was dead, the one that fried
some wiring also alerted me to a bad breaker that would never trip
which lked to my finding out about the FPE panel hazards

The mention of copier guy! Thanks that explains you BAD attitude!

Your from the NASA or shuttle boards, I am NOT a supporter of the
current shuttle program, much has been made of my copier repairman job.
I moved on to other machines, its my own business the change was
definetely a improvement

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help needed with kitchen electrical issue HorneTD Home Repair 1 February 15th 05 04:27 PM
Part P: Date stamping accessories ? Mark Carver UK diy 20 December 30th 04 08:12 PM
DIY electrical work after 1st January 2005 Uno Hoo! UK diy 89 December 17th 04 05:11 PM
Installing Ceiling Fan with Red wire on electrical box. Josh Home Repair 20 July 31st 03 11:53 AM
Routeing Electrical FTE cable pickerel UK diy 3 July 24th 03 12:43 AM


All times are GMT +1. The time now is 09:02 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"