It is dangerous to have more than one surge protectors in you home I
have 3 surge protectors running in my home.

  #2   Report Post  
Posted to alt.home.repair
professorpaul
 
Posts: n/a
Default surge protectors


karsan wrote:
It is dangerous to have more than one surge protectors in you home I
have 3 surge protectors running in my home.


Not a problem. I assume that each is for a separate circuit, such as a
computer, hi-fi, misc. electronics, etc.

The only problem that I've had is knowing that they have been "hit," as
many of them are a "one shot" thing, and must be replace (varistor
type), if a real nasty surge hits them.

I have such devices, in the form of outlet strips, on both computers in
the house.

  #3   Report Post  
Posted to alt.home.repair
Ralph Mowery
 
Posts: n/a
Default surge protectors


"karsan" wrote in message
oups.com...
It is dangerous to have more than one surge protectors in you home I
have 3 surge protectors running in my home.


If you mean the kind that plug into the wall (may be called power strips)
and they are installed in seperate outlets, you can not have too many in
your house.
The only thing is if you have too many things using too much current plugged
in to them. Then a fuse or breaker should blow or trip.

I have 4 or 5 in use right now. One on each of the TV sets, computers and
my ham radio gear.

In a house I lived in before I moved , having 3 in use probably saved me a
bunch of equipment. A surge during a lightning storm took out 3 of the
protectors but did not get any of the electronic gear except an unprotected
telephone and an internal surge supressor saved most of the electronics in
the oven control.



  #4   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default surge protectors

Better to have UPS on critical or sensitive equiptement.

A WHOLE HOUSE surge protector is better, and probably more reliiable
and costs less than a bunch strewn all around the house

  #5   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default surge protectors

" wrote:

Better to have UPS on critical or sensitive equiptement.

A WHOLE HOUSE surge protector is better, and probably more reliiable
and costs less than a bunch strewn all around the house


The clamping capacity (Amps) of the surge suppressers will be additive
(no, not perfectly additive, but still increasing protection) so more
will be able to clamp bigger surges. A surge suppresser at the main
panel is best since it can clamp a surge before it gets further into the
homes wiring. Additional surge suppressers further down the line,
whether the little blocks or power strips with suppressers built in will
just add an additional line of defense.

The surge suppressers that install at the service entrance panel are
generally higher quality and capacity and more likely to use multiple
technologies like MOVs and gas discharge arrestors. Nearly all the small
plug in suppressers just use inexpensive MOVs.

A decent UPS is a must for computers and any other expensive items like
big plasma / LCD TVs, etc. UPSes used to be expensive, but they are now
quite reasonably priced for decent units. One thing to watch out for is
surge suppressers on the output of a UPS. Since suppressers work by
creating a short circuit across the line (briefly) they can damage a
UPSes inverter if a surge gets through and they clamp. Some cheaper
UPSes may generate small HV spikes that could trigger the suppresser as
well and again damage the UPS output.

Nothing will protect against a direct strike on the power line near your
house, so if that happens you'll have a big insurance claim no matter
what. The suppressers might help clamp things enough to lessen the
damage though.

Inductive pickup of nearby lightning strikes is also an issue and long
wires like phone, network and CATV lines can pickup significant surges
that way. Good suppressers on those lines along with good grounds will
help.

Pete C.


  #6   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

They are called shunt mode protectors. They work by earthing a
destructive transient such as a direct lighting strike and then remain
functional. If a 'whole house' protector could not earth that
transient, then what good willl a plug-in protector do trying to earth
to the same ground?

So instead some assume plug-in protectors sit between the surge and
an appliance to block or stop surges. Bull. Will that silly little
less than one inch component stop what 3 miles of sky could not?
Effective protection was never about stopping or absorbing surges.
Effective protection is about diverting - shunting - a destructive
transient to earth. Divert - not stop or absorb.

Protector amperage is additive IF all protectors have a same 'low
impedance' connection. And that is the problem. Things such as sharp
wire bends, long distances, splices, etc all increase that wire
impedance. Now a plug-in protector has too much impedance. Instead of
seeking earth via safety ground wire, that transient may seek earth
through an adjacent appliance and phone line. This is how modems are
so easily damaged. Incoming on AC electric. Through an adjacent
protector. Into comptuer motherboard and modem. Out to earth ground
via phone line. Notice where most modem destructive transients come
from.

Having learned this by tracing destructive surges, then what is a
most typically damaged component? The path through adjacent protector,
through modem (its DAA section), is often via a transistor that drives
an off-hook relay. The failure message is "No Dialtone Detected".
Incoming on AC. Through that transistor and off-hook relay. To earth,
destructively, via phone line and phone line surge protector.

Why did damage result? A transient was not earthed BEFORE it could
enter the building.

A surge protector basically shunts - connects all wires together
during a transient. If that wire makes a low impedance connection to
earth, then the transient is earthed. No damage. But plug-in
protectors don't have a good earthing connection. Above is one
example; demonstrated by tracing surges and replacing transistor. A
protector too close to transistors and too far from earth ground can
even contribute to damage of the adjacent (and powered off) appliance.
An effective protector makes a 'less than 10 foot' connection to the
building's earth ground.

Ineffective protectors (power strip and UPS) are easily identified.
1) No dedicated earthing wire. 2) Manufacturer does not even discuss
earthing. Look at your protector. Does it meet these criteria for
ineffective protector?

What does a telephone company do to protect their $multimillion
switching computer? Its computer connects to overhead wires everywhere
in town. Why do they not provide service for a whole week while
replacing that computer? Because the telco installs 'whole house' type
protectors on every single wire of every cable that enters the
building. Tehcnology even discussed in an Oct 1960 Bell System
Technical Journal article - because the technology is that old and that
well proven. An effective protector is ideally 50 meters from
transistors AND as close as possible to earth ground. That 50 meter
separation adds to protection. But most important is what makes that
'whole house' type protectors effective. A low impedance - meaning
short - connection to a building's single point *earth ground*. Not
only is the connection short. Every protector is earthed to a same
ground - the single point earth ground.

For residential protection, manufacturers with responsible brand
names provide effective 'whole house' protectors. Siemens,
Cutler-Hammer, Square D, Leviton, Intermatic, and GE all sell 'whole
house' protectors that are available in Home Depot, Lowes, and
electrical supply houses. These protectors have a dedicated earthing
wire. These protectors costs tens of times less money per protected
appliance. And these protectors are properly sized.

Why properly sized? Many plug-in protectors are so grossly
undersized (MOVs undersized; too few joules) as to vaporize during a
surge. Vaporized MOV provided ineffective protection. But its smoke
promotes more sales. Effective protectors, instead, earth direct
lightning strikes and remain functional. A human never knows that when
a properly sized protector is doing protection. Grossly undersized
plug-in protectors that vaporize and smoke will be recommended by the
naive. So many plug-in protectors are undersized - to promote sales
rather than provide effective protection.

Earthing - at minimum, the building must conform to post 1990
National Electrical Code earthing. Enhanced earthing means a protector
will be even more effective. And so we say, "a protector is only as
effective as its earth ground." What do those plug-in power strip and
UPS protectors manufacturers not even discuss? Earthing. Where is
that dedicated earthing wire? Did they just forget? Or do they hope
you never learn why earthing is so essential?

Some incoming wires are earthed using a protector. Telco provides a
'whole house' protector where their wire enters your building. But
again, that protector will only be as effective as its earth ground.
Did you (or your builder) provide that essential earthing connection?
Cable needs no protector. Its ground block must connect directly to
the same earth ground - a 'less than 10 foot' connection. Every
incoming wire must be earthed directly or through a 'whole house'
protectors to the single point earth ground.

Ineffective protector manufactures and those who promote them hope
you never learn what a shunt mode protector does: makes a low impedance
connection to earth. No earth ground means no effective protection.
So where is that earthing connection in a plug-in UPS? Notice that
their own numerical specifications don't even define protection? How's
that for a damning overlooked fact.

Appliances already contain internal protection. Protection that can
be overwhelmed if destructive transients are not earthed where wires
enter the building. Earthing is why 'whole house' protectors are so
effective. No earth ground (such as with plug-in protectors) means no
effective protection.

If you don't earth incoming transients such as the direct lighting
strike, then protection inside that appliance can be overwhelmed;
appliance damaged. Plug-in protectors can even provide more
destructive paths through an adjacent appliance.

Pete C. wrote:
" wrote:
...
A WHOLE HOUSE surge protector is better, and probably more reliiable
and costs less than a bunch strewn all around the house


The clamping capacity (Amps) of the surge suppressers will be additive
(no, not perfectly additive, but still increasing protection) so more
will be able to clamp bigger surges. A surge suppresser at the main
panel is best since it can clamp a surge before it gets further into the
homes wiring. Additional surge suppressers further down the line,
whether the little blocks or power strips with suppressers built in will
just add an additional line of defense.

The surge suppressers that install at the service entrance panel are
generally higher quality and capacity and more likely to use multiple
technologies like MOVs and gas discharge arrestors. Nearly all the small
plug in suppressers just use inexpensive MOVs.

A decent UPS is a must for computers and any other expensive items like
big plasma / LCD TVs, etc. UPSes used to be expensive, but they are now
quite reasonably priced for decent units. One thing to watch out for is
surge suppressers on the output of a UPS. Since suppressers work by
creating a short circuit across the line (briefly) they can damage a
UPSes inverter if a surge gets through and they clamp. Some cheaper
UPSes may generate small HV spikes that could trigger the suppresser as
well and again damage the UPS output.

Nothing will protect against a direct strike on the power line near your
house, so if that happens you'll have a big insurance claim no matter
what. The suppressers might help clamp things enough to lessen the
damage though.

Inductive pickup of nearby lightning strikes is also an issue and long
wires like phone, network and CATV lines can pickup significant surges
that way. Good suppressers on those lines along with good grounds will
help.

Pete C.


  #7   Report Post  
Posted to alt.home.repair
karsan
 
Posts: n/a
Default surge protectors


professorpaul wrote:
karsan wrote:
It is dangerous to have more than one surge protectors in you home I
have 3 surge protectors running in my home.


Not a problem. I assume that each is for a separate circuit, such as a
computer, hi-fi, misc. electronics, etc.

The only problem that I've had is knowing that they have been "hit," as
many of them are a "one shot" thing, and must be replace (varistor
type), if a real nasty surge hits them.

I have such devices, in the form of outlet strips, on both computers in
the house.


Yes. evertying is seperated. My computer is has surge protector I have
a telephone and a lamp on one surge protector and on the second one is
my computer and the third one I have water cooler running.

  #8   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

professorpaul wrote:
...
The only problem that I've had is knowing that they have been "hit," as
many of them are a "one shot" thing, and must be replace (varistor
type), if a real nasty surge hits them.

I have such devices, in the form of outlet strips, on both computers in
the house.


Any protector that was one shot protection was grossly undersized -
ineffective. When it vaporizes, then it promotes more sales to the
naive. Effective protectors do their job without vaporizing; human
never knows when it is working. But effective protectors are not
promoted by the naive.

Active component in a protector is the MOV. A datasheet from an MOV
manufacturer provides a ballpark idea how many times a properly sized
protector should work - without failing:
The change in Vb shall be measured after the impulse
listed below is applied 10,000 times continuously with
the interval of ten seconds at room temperature.


Does that sound like a one shot protector device? Of course not.
Ineffective protectors are also grossly undersize to be promoted by the
naive. Smoke rather than facts promote ineffetive plug-in protectors.

Effective 'whole house' protectors are manufactured by names
recognized as responsible: Square D, Cutler-Hammer, Leviton,
Intermatic, Square D, and GE. They are sold in Home Depot, Lowes, and
electrical supply houses. They are not sold in Radio Shack, Sears, and
grocery stores. Essential for any effective protector is earthing. A
protector is not protection. Protection is what the protector connects
'less than 10 feet' to: earthing.

Meanwhile, let's look at what some grossly undersized plug-in
protectors have done:
http://www.hanford.gov/rl/?page=556&parent=554
http://www.cob.org/fire/safety/surge.htm
http://www.ddxg.net/old/surge_protectors.htm
http://www.westwhitelandfire.com/Art...Protectors.pdf
http://www.rbs2.com/fire.htm

Think about it. Would you put a protector in dust balls behind a
table or atop a desk of papers? There are overhyped, so called 'one
shot' protectors. Properly earthed and sufficiently sized 'whole
house' protectors are available. And then we have this fact
demonstrated in commercial broadcasting stations and telephone
switching centers everywhere in the world. The protector is nothing
more than a connection to protection. That protection is a good earth
ground. An effective protector is only as effective as its earth
ground which is why effective protectors have a dedicated earthing
wire.

  #9   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default surge protectors

w_tom wrote:

They are called shunt mode protectors. They work by earthing a
destructive transient such as a direct lighting strike and then remain
functional. If a 'whole house' protector could not earth that
transient, then what good willl a plug-in protector do trying to earth
to the same ground?


The fact that they will operate in parallel. The transient will rise to
the trigger point of all the suppresser devices and all will clamp the
line. If there is sufficient clamping capacity the differential voltage
will be substantially reduced.


So instead some assume plug-in protectors sit between the surge and
an appliance to block or stop surges. Bull. Will that silly little
less than one inch component stop what 3 miles of sky could not?
Effective protection was never about stopping or absorbing surges.
Effective protection is about diverting - shunting - a destructive
transient to earth. Divert - not stop or absorb.


As I noted, nothing is going to stop a direct strike. Most strikes
aren't direct however and are primarily inductive pickup from a nearby
strike and therefore reduced to a much more manageable level.


Protector amperage is additive IF all protectors have a same 'low
impedance' connection. And that is the problem. Things such as sharp
wire bends, long distances, splices, etc all increase that wire
impedance. Now a plug-in protector has too much impedance. Instead of
seeking earth via safety ground wire, that transient may seek earth
through an adjacent appliance and phone line. This is how modems are
so easily damaged. Incoming on AC electric. Through an adjacent
protector. Into comptuer motherboard and modem. Out to earth ground
via phone line. Notice where most modem destructive transients come
from.


Again for a direct hit. For a surge of the level of the much more common
inductively coupled strike that does not apply.


Having learned this by tracing destructive surges, then what is a
most typically damaged component? The path through adjacent protector,
through modem (its DAA section), is often via a transistor that drives
an off-hook relay. The failure message is "No Dialtone Detected".
Incoming on AC. Through that transistor and off-hook relay. To earth,
destructively, via phone line and phone line surge protector.


The MOVs that are located adjacent to the phone line connector on a
quality modem should clamp the surge. The drive to the off hook relay is
also not electrically connected to the line, nor is most of the rest of
the modem. The DAA transformer, ring detect optoisolator and hook switch
relay are about all that is connected to the line.


Why did damage result? A transient was not earthed BEFORE it could
enter the building.


There is absolutely nothing magic about the building. The building wall
is no different than the wall of an electrical panel, or the case of a
computer.

One thing you do buy by clamping the surge as far out as possible is to
keep the current path of the clamped surge further away from other wires
which helps limit further inductive coupling.


A surge protector basically shunts - connects all wires together
during a transient. If that wire makes a low impedance connection to
earth, then the transient is earthed. No damage. But plug-in
protectors don't have a good earthing connection. Above is one
example; demonstrated by tracing surges and replacing transistor. A
protector too close to transistors and too far from earth ground can
even contribute to damage of the adjacent (and powered off) appliance.
An effective protector makes a 'less than 10 foot' connection to the
building's earth ground.


Again, reducing the current path and the potential for further inductive
coupling.


Ineffective protectors (power strip and UPS) are easily identified.
1) No dedicated earthing wire. 2) Manufacturer does not even discuss
earthing. Look at your protector. Does it meet these criteria for
ineffective protector?


As I noted, every suppresser on the line adds some level of protection.
Suppressers at the electric service entrance panel, the CATV and telco
demarcs all with short connections to a proper grounding electrode are
the first line of defense.

Any suppressers downstream provide further protection against
inductively coupled surges which don't have to come through the service
entrance conductors and residual surges past what the primary
suppressers were able to clamp. Also for #1, that third pin on the power
plug *is* a dedicated earthing wire.


What does a telephone company do to protect their $multimillion
switching computer? Its computer connects to overhead wires everywhere
in town. Why do they not provide service for a whole week while
replacing that computer? Because the telco installs 'whole house' type
protectors on every single wire of every cable that enters the
building. Tehcnology even discussed in an Oct 1960 Bell System
Technical Journal article - because the technology is that old and that
well proven. An effective protector is ideally 50 meters from
transistors AND as close as possible to earth ground. That 50 meter
separation adds to protection. But most important is what makes that
'whole house' type protectors effective. A low impedance - meaning
short - connection to a building's single point *earth ground*. Not
only is the connection short. Every protector is earthed to a same
ground - the single point earth ground.


Yes, the closer you can locate the suppressers to the grounding
electrode the more effective they can be. Those grounding electrodes are
also rarely a single point ground particularly in a utility application.
More commonly they will be a multipoint electrode array bonded together
with quite heavy conductors, often with exothermic welded connections.

The telco is also a good example since it employs multiple stages of
protection from the primary suppressers at the drop entrance to the
suppressers on the SLIC cards, the suppressers on the power system, etc.
More is better for the most part.


For residential protection, manufacturers with responsible brand
names provide effective 'whole house' protectors. Siemens,
Cutler-Hammer, Square D, Leviton, Intermatic, and GE all sell 'whole
house' protectors that are available in Home Depot, Lowes, and
electrical supply houses. These protectors have a dedicated earthing
wire. These protectors costs tens of times less money per protected
appliance. And these protectors are properly sized.


Again these should be the first line of defense along with quality
suppressers at the telco and CATV demarcs. This does not mean that
additional suppressers are of no value as lightning can induce surges in
the building wiring inside the house just as easily as outside.


Why properly sized? Many plug-in protectors are so grossly
undersized (MOVs undersized; too few joules) as to vaporize during a
surge. Vaporized MOV provided ineffective protection. But its smoke
promotes more sales. Effective protectors, instead, earth direct
lightning strikes and remain functional. A human never knows that when
a properly sized protector is doing protection. Grossly undersized
plug-in protectors that vaporize and smoke will be recommended by the
naive. So many plug-in protectors are undersized - to promote sales
rather than provide effective protection.


I've never seen a vaporized MOV of any size. I have seen a few that have
failed and cracked after being subjected to substantial surges. If you
review the joule ratings of the various MOVs and gas discharge arrestors
you find in typical small suppressers you'll see that their ratings are
not at all far behind those of the common whole house suppressers. Some
of the quite expensive service entrance suppressers intended for
commercial services have higher ratings, but not the common ones.

Earthing - at minimum, the building must conform to post 1990
National Electrical Code earthing. Enhanced earthing means a protector
will be even more effective. And so we say, "a protector is only as
effective as its earth ground." What do those plug-in power strip and
UPS protectors manufacturers not even discuss? Earthing. Where is
that dedicated earthing wire? Did they just forget? Or do they hope
you never learn why earthing is so essential?


Refer you to the dedicated grounding (earthing) conductor provided to
every electrical device in a residence. The dedicated third pin on a
NEMA 5-15 (or 5-20 or 5-xx, 6-xx, etc.) receptacle.


Some incoming wires are earthed using a protector. Telco provides a
'whole house' protector where their wire enters your building. But
again, that protector will only be as effective as its earth ground.
Did you (or your builder) provide that essential earthing connection?
Cable needs no protector. Its ground block must connect directly to
the same earth ground - a 'less than 10 foot' connection. Every
incoming wire must be earthed directly or through a 'whole house'
protectors to the single point earth ground.


Cable is not required by any code to have anything but the ground block
at the demarc, however this only grounds (earths) the shield of the
coax. The coax center conductor still can and often does convey
significant surges into the premises. A quality coax surge suppresser
will clamp surges on the center conductor to ground as well.


Ineffective protector manufactures and those who promote them hope
you never learn what a shunt mode protector does: makes a low impedance
connection to earth. No earth ground means no effective protection.


Again, every single one of those suppressers has an earth ground
connection. They wouldn't pass code and UL listing requirements if they
didn't.

So where is that earthing connection in a plug-in UPS?


The grounding pin of the NEMA 5-15 plug on the UPS.

Notice that
their own numerical specifications don't even define protection? How's
that for a damning overlooked fact.


The specifications for my UPS indicate the clamping voltage and joule
rating of the suppresser devices.


Appliances already contain internal protection.


Some appliances do, many do not. Don't recall the last time I saw any
suppression devices in a toaster or a blender.

Protection that can
be overwhelmed if destructive transients are not earthed where wires
enter the building. Earthing is why 'whole house' protectors are so
effective. No earth ground (such as with plug-in protectors) means no
effective protection.


Again you are 100% incorrect, any plug in suppresser with a three prong
plug *does* have an earth ground. What the heck do you think NEC article
250 is all about? NEC articles 280 and 285 relate to surge arrestors and
transient voltage surge suppressers BTW.


If you don't earth incoming transients such as the direct lighting
strike, then protection inside that appliance can be overwhelmed;
appliance damaged. Plug-in protectors can even provide more
destructive paths through an adjacent appliance.


If you have a direct lightning strike on your service entrance drop or
service feeder on the poles, your glorious whole house suppresser will
be in pieces along with your entire service panel.

Pete C.
  #10   Report Post  
Posted to alt.home.repair
Tom Horne, Electrician
 
Posts: n/a
Default surge protectors

Pete C. wrote:
w_tom wrote:
They are called shunt mode protectors. They work by earthing a
destructive transient such as a direct lighting strike and then remain
functional. If a 'whole house' protector could not earth that
transient, then what good willl a plug-in protector do trying to earth
to the same ground?


The fact that they will operate in parallel. The transient will rise to
the trigger point of all the suppresser devices and all will clamp the
line. If there is sufficient clamping capacity the differential voltage
will be substantially reduced.

So instead some assume plug-in protectors sit between the surge and
an appliance to block or stop surges. Bull. Will that silly little
less than one inch component stop what 3 miles of sky could not?
Effective protection was never about stopping or absorbing surges.
Effective protection is about diverting - shunting - a destructive
transient to earth. Divert - not stop or absorb.


As I noted, nothing is going to stop a direct strike. Most strikes
aren't direct however and are primarily inductive pickup from a nearby
strike and therefore reduced to a much more manageable level.

Protector amperage is additive IF all protectors have a same 'low
impedance' connection. And that is the problem. Things such as sharp
wire bends, long distances, splices, etc all increase that wire
impedance. Now a plug-in protector has too much impedance. Instead of
seeking earth via safety ground wire, that transient may seek earth
through an adjacent appliance and phone line. This is how modems are
so easily damaged. Incoming on AC electric. Through an adjacent
protector. Into comptuer motherboard and modem. Out to earth ground
via phone line. Notice where most modem destructive transients come
from.


Again for a direct hit. For a surge of the level of the much more common
inductively coupled strike that does not apply.

Having learned this by tracing destructive surges, then what is a
most typically damaged component? The path through adjacent protector,
through modem (its DAA section), is often via a transistor that drives
an off-hook relay. The failure message is "No Dialtone Detected".
Incoming on AC. Through that transistor and off-hook relay. To earth,
destructively, via phone line and phone line surge protector.


The MOVs that are located adjacent to the phone line connector on a
quality modem should clamp the surge. The drive to the off hook relay is
also not electrically connected to the line, nor is most of the rest of
the modem. The DAA transformer, ring detect optoisolator and hook switch
relay are about all that is connected to the line.

Why did damage result? A transient was not earthed BEFORE it could
enter the building.


There is absolutely nothing magic about the building. The building wall
is no different than the wall of an electrical panel, or the case of a
computer.

One thing you do buy by clamping the surge as far out as possible is to
keep the current path of the clamped surge further away from other wires
which helps limit further inductive coupling.

A surge protector basically shunts - connects all wires together
during a transient. If that wire makes a low impedance connection to
earth, then the transient is earthed. No damage. But plug-in
protectors don't have a good earthing connection. Above is one
example; demonstrated by tracing surges and replacing transistor. A
protector too close to transistors and too far from earth ground can
even contribute to damage of the adjacent (and powered off) appliance.
An effective protector makes a 'less than 10 foot' connection to the
building's earth ground.


Again, reducing the current path and the potential for further inductive
coupling.

Ineffective protectors (power strip and UPS) are easily identified.
1) No dedicated earthing wire. 2) Manufacturer does not even discuss
earthing. Look at your protector. Does it meet these criteria for
ineffective protector?


As I noted, every suppresser on the line adds some level of protection.
Suppressers at the electric service entrance panel, the CATV and telco
demarcs all with short connections to a proper grounding electrode are
the first line of defense.

Any suppressers downstream provide further protection against
inductively coupled surges which don't have to come through the service
entrance conductors and residual surges past what the primary
suppressers were able to clamp. Also for #1, that third pin on the power
plug *is* a dedicated earthing wire.

What does a telephone company do to protect their $multimillion
switching computer? Its computer connects to overhead wires everywhere
in town. Why do they not provide service for a whole week while
replacing that computer? Because the telco installs 'whole house' type
protectors on every single wire of every cable that enters the
building. Tehcnology even discussed in an Oct 1960 Bell System
Technical Journal article - because the technology is that old and that
well proven. An effective protector is ideally 50 meters from
transistors AND as close as possible to earth ground. That 50 meter
separation adds to protection. But most important is what makes that
'whole house' type protectors effective. A low impedance - meaning
short - connection to a building's single point *earth ground*. Not
only is the connection short. Every protector is earthed to a same
ground - the single point earth ground.


Yes, the closer you can locate the suppressers to the grounding
electrode the more effective they can be. Those grounding electrodes are
also rarely a single point ground particularly in a utility application.
More commonly they will be a multipoint electrode array bonded together
with quite heavy conductors, often with exothermic welded connections.

The telco is also a good example since it employs multiple stages of
protection from the primary suppressers at the drop entrance to the
suppressers on the SLIC cards, the suppressers on the power system, etc.
More is better for the most part.

For residential protection, manufacturers with responsible brand
names provide effective 'whole house' protectors. Siemens,
Cutler-Hammer, Square D, Leviton, Intermatic, and GE all sell 'whole
house' protectors that are available in Home Depot, Lowes, and
electrical supply houses. These protectors have a dedicated earthing
wire. These protectors costs tens of times less money per protected
appliance. And these protectors are properly sized.


Again these should be the first line of defense along with quality
suppressers at the telco and CATV demarcs. This does not mean that
additional suppressers are of no value as lightning can induce surges in
the building wiring inside the house just as easily as outside.

Why properly sized? Many plug-in protectors are so grossly
undersized (MOVs undersized; too few joules) as to vaporize during a
surge. Vaporized MOV provided ineffective protection. But its smoke
promotes more sales. Effective protectors, instead, earth direct
lightning strikes and remain functional. A human never knows that when
a properly sized protector is doing protection. Grossly undersized
plug-in protectors that vaporize and smoke will be recommended by the
naive. So many plug-in protectors are undersized - to promote sales
rather than provide effective protection.


I've never seen a vaporized MOV of any size. I have seen a few that have
failed and cracked after being subjected to substantial surges. If you
review the joule ratings of the various MOVs and gas discharge arrestors
you find in typical small suppressers you'll see that their ratings are
not at all far behind those of the common whole house suppressers. Some
of the quite expensive service entrance suppressers intended for
commercial services have higher ratings, but not the common ones.

Earthing - at minimum, the building must conform to post 1990
National Electrical Code earthing. Enhanced earthing means a protector
will be even more effective. And so we say, "a protector is only as
effective as its earth ground." What do those plug-in power strip and
UPS protectors manufacturers not even discuss? Earthing. Where is
that dedicated earthing wire? Did they just forget? Or do they hope
you never learn why earthing is so essential?


Refer you to the dedicated grounding (earthing) conductor provided to
every electrical device in a residence. The dedicated third pin on a
NEMA 5-15 (or 5-20 or 5-xx, 6-xx, etc.) receptacle.

Some incoming wires are earthed using a protector. Telco provides a
'whole house' protector where their wire enters your building. But
again, that protector will only be as effective as its earth ground.
Did you (or your builder) provide that essential earthing connection?
Cable needs no protector. Its ground block must connect directly to
the same earth ground - a 'less than 10 foot' connection. Every
incoming wire must be earthed directly or through a 'whole house'
protectors to the single point earth ground.


Cable is not required by any code to have anything but the ground block
at the demarc, however this only grounds (earths) the shield of the
coax. The coax center conductor still can and often does convey
significant surges into the premises. A quality coax surge suppresser
will clamp surges on the center conductor to ground as well.

Ineffective protector manufactures and those who promote them hope
you never learn what a shunt mode protector does: makes a low impedance
connection to earth. No earth ground means no effective protection.


Again, every single one of those suppressers has an earth ground
connection. They wouldn't pass code and UL listing requirements if they
didn't.

So where is that earthing connection in a plug-in UPS?


The grounding pin of the NEMA 5-15 plug on the UPS.

Notice that
their own numerical specifications don't even define protection? How's
that for a damning overlooked fact.


The specifications for my UPS indicate the clamping voltage and joule
rating of the suppresser devices.

Appliances already contain internal protection.


Some appliances do, many do not. Don't recall the last time I saw any
suppression devices in a toaster or a blender.

Protection that can
be overwhelmed if destructive transients are not earthed where wires
enter the building. Earthing is why 'whole house' protectors are so
effective. No earth ground (such as with plug-in protectors) means no
effective protection.


Again you are 100% incorrect, any plug in suppresser with a three prong
plug *does* have an earth ground. What the heck do you think NEC article
250 is all about? NEC articles 280 and 285 relate to surge arrestors and
transient voltage surge suppressers BTW.

If you don't earth incoming transients such as the direct lighting
strike, then protection inside that appliance can be overwhelmed;
appliance damaged. Plug-in protectors can even provide more
destructive paths through an adjacent appliance.


If you have a direct lightning strike on your service entrance drop or
service feeder on the poles, your glorious whole house suppresser will
be in pieces along with your entire service panel.

Pete C.


I work as a communications wireman whenever the electrical service
industry gets too slow. I have built alternative powered and utility
powered radio equipment shelters in remote places from Alaska to the
Argentine pampas. These room sized buildings are struck quite regularly
by lightning without loosing a single circuit. The inevitability of
damage secondary to a direct strike is a myth. If you are willing to
invest the necessary effort damage can be averted. Most home owners
will not find it cost effective to install fully effective lightning
protection.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous
for general use." Thomas Alva Edison


  #11   Report Post  
Posted to alt.home.repair
karsan
 
Posts: n/a
Default surge protectors


Ralph Mowery wrote:
"karsan" wrote in message
oups.com...
It is dangerous to have more than one surge protectors in you home I
have 3 surge protectors running in my home.


If you mean the kind that plug into the wall (may be called power strips)
and they are installed in seperate outlets, you can not have too many in
your house.
The only thing is if you have too many things using too much current plugged
in to them. Then a fuse or breaker should blow or trip.

I have 4 or 5 in use right now. One on each of the TV sets, computers and
my ham radio gear.

In a house I lived in before I moved , having 3 in use probably saved me a
bunch of equipment. A surge during a lightning storm took out 3 of the
protectors but did not get any of the electronic gear except an unprotected
telephone and an internal surge supressor saved most of the electronics in
the oven control.


I have a surge protector for my computer, the telephone, and our lamp.
We only have one televison.

  #12   Report Post  
Posted to alt.home.repair
Bud--
 
Posts: n/a
Default surge protectors

w_tom wrote:

They are called shunt mode protectors. They work by earthing a
destructive transient such as a direct lighting strike and then remain
functional. If a 'whole house' protector could not earth that
transient, then what good willl a plug-in protector do trying to earth
to the same ground?

So instead some assume plug-in protectors sit between the surge and
an appliance to block or stop surges. Bull. Will that silly little
less than one inch component stop what 3 miles of sky could not?
Effective protection was never about stopping or absorbing surges.
Effective protection is about diverting - shunting - a destructive
transient to earth. Divert - not stop or absorb.



The same old Bull.

The best information I have seen on surge protection is at
http://www.mikeholt.com/files/PDF/Li...ion_May051.pdf
It is a guide that was published by the Institute of Electrical and
Electronic Engineers in 2005. You provided the link to this guide.

Another good source is
http://www.nist.gov/public_affairs/p.../surgesfnl.pdf
published by the US government - National Institute of Standards and
Technology.

Both guides were intended for wide distribution to the general public to
explain where surges come from and how to protect against them. The IEEE
guide was targeted at people who have some (not much) technical
background. The NIST guide is intended for everyone.


Both the IEEE and the NIST say that plug-in surge suppressors ARE
EFFECTIVE. Perhaps you are smarter than they are.


Note that if equipment, like a computer, has connections in addition to
the power line, particularly phone but also possibly LAN or other, that
wiring also needs to go through the plug-in surge suppressor. That also
applies to equipment with power and cable TV connections. This is
described in both guides.

Plug-in surge suppressors work primarily by clamping the voltage on all
wires (power and signal) to the common ground at the surge suppressor.
That includes the cable TV coax center conductor, as described by Pete C.


bud--
  #13   Report Post  
Posted to alt.home.repair
Bob
 
Posts: n/a
Default surge protectors


karsan wrote:

It is dangerous to have more than one surge protectors in you home I
have 3 surge protectors running in my home.


I have a whole house "protector" at the electrical panel and several
smaller units scattered throught the house. I have had several
lightning hits in the near vicinity and have never had electrical
damage. But I have lost 4 TV's from lightning coming in on the cable -
all damaged in the tuner sections rather than power sections. And I
have had computer modems fry from surges on the telephone line. So
from that, I deduce the whole house unit is doing it's job, but the
others are questionable.
Bob

  #14   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

Was cable earthed before entering a building? If not, then yes,
cable may be an incoming source of electricity called a surge. Cable
must drop down and make a 'less than 10 foot' connection to a same
earth ground used by AC electric and telephone. If cable enters house
without dropping down and connecting to earth, then yes, cable can be
the incoming path of a surge that was seeking earth ground
destructively through tuners.

No protector is required to earth coax cable surges. But the most
important component of a protector - earth ground - must connect to
that cable. Connected so that a surge finds earth at the building
entrance instead of via TV tuners.

Actually we don't know that any protectors were doing their job. You
suffered damage. If, for example, the telephone line 'whole house'
protector and AC electric 'whole house' protector were not using a same
earth ground, then damage could still occur. Protection starts with
and is defined by earthing - not by some protector. The effective
protector makes a 'less than 10 foot' connection to same earth ground
used by all other protectors.

What makes problems more complex is that plug-in protectors have a
history of offering surges more destructive paths through household
appliances.

Forget that protectors are protection. What was the earth ground?
Earth ground is the protection. How were those protectors earthed?

Don't assume a modem was damaged by a surge from phone line. Don't
think of surges as a wave crashing on a beach. Surges just don't work
that way. First electricity flows in everything in a path through that
modem. Everything is conducting the same electricity. Long afterwards
(microseconds later), something in that path is destroyed. That path
could be incoming on phone line. Or a destructive path through modem
can be incoming on AC electric or cable; outgoing on phone line.
Notice - first there must be both an incoming and outgoing path.
Notice, the cable is not directly connected to computer. Since
numerous household items may be conductors, then even a cable surge
could have found a path to earth via that computer modem.

Any incoming utility could have been an incoming surge path into the
computer. However most modems are damaged by surges incoming on AC
electric; outgoing to earth via phone lines. No 'wave crashing on a
beach'. An incoming path and an outgoing path to earth must exist to
have damage.

You don't know if phone line was incoming or outgoing path based upon
what was posted. You only know a modem was in a destructive path from
cloud to earth. And that path existed because something was not
properly earthed where it enters the building. How do you learn from
and fix the problem? Start with earth ground. Is it the best earthing
on the property? Does every utility make a 'less than 10 foot'
connection to that one earthing electrode? IOW do all utilities enter
at a same location or is that earth ground expanded to connect to all
incoming utilities? We don't yet know whether cable or TV wire was the
incoming source or outgoing path to earth. Analysis must start by
identifying both incoming and outgoing path through that modem and
those TV tuners.

How did lightning from a cloud find earth ground through those tuners
and modem? Until we can answer that question, then it is only a guess
why something was damaged and no idea yet how to fix this human created
failure.

You cannot deduce the 'whole house' protector is doing anything
effective until the most essential part of a protection system - earth
ground - is verified. Did a surge enter on phone line if telco had
installed a 'whole house' protector -for free? Well again, what is
that protector earthed to. Protection is defined mostly by the quality
of earthing.

Meanwhile, what did those plug-in protectors have for a 'less than 10
foot' connection to earth? No less than 10 foot connection? Then of
course they were not effective.

Bob wrote:
I have a whole house "protector" at the electrical panel and several
smaller units scattered throught the house. I have had several
lightning hits in the near vicinity and have never had electrical
damage. But I have lost 4 TV's from lightning coming in on the cable -
all damaged in the tuner sections rather than power sections. And I
have had computer modems fry from surges on the telephone line. So
from that, I deduce the whole house unit is doing it's job, but the
others are questionable.
Bob


  #16   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

Numerous points that make assumptions based in a world where
impedance does not exist - where only resistance exists.

First, nothing will stop a direct strike. But direct strikes
routinely do no damage when they are diverted. Major difference
between stopping (which plug-in protectors hope you will assume) and
diverting which is standard where direct lightning strikes do not
damage. Again, 25 direct strikes annually to electronics atop the
Empire State Building; 40 annually to the WTC - and electronics not
damaged. It is routine to earth direct strikes without damage -
because we don't stop a direct strike. We divert it to earth.

Inductive transients? Well put some numbers to them. I assume
this is about a nearby lightning strike to a long wire antenna. Well
that nearby strike may induce a few thousand volts onto that antenna.
Then we connect an NE-2 (neon glow lamp) from that antenna to earth.
Because that neon glow lamp conducts only milliamps, then that
thousands volts on antenna is now less than 60 volts. IOW induced
transients are that trivial. So trivial as to be made irrelevant by
protection inside all appliances. And yet, even industry standards of
30+ years ago (i.e. CBEMA) defined protection that was inside all
electronic appliances even that long ago. It takes so little to make
induced transients irrelevant. But it is the direct strike that causes
damage.

You did not see protector devices inside the blender? You were not
looking like an engineer? Why do you think wire was heavier gauge than
necessary? You are making a classic mistake. You have assumed
protector is as specific device. Protection is not necessary achieved
by a protector. Protection is something in the engineering. You are
instead looking for a specific device rather than first learning the
design. Meanwhile, we were discussing electronics appliances - not
blenders that have no electronics.

Is "drive to the off hook relay ... also not electrically connected
to the line, nor is most of the rest of the modem"? First go to data
sheets. That coil inside a modem off hook relay does electrically
connect to its wiper as those datasheets demonstrate. Not at 100
volts. But then even floors and wall paints become conductive during
these transients. Datasheet for that off-hook relay even states what
voltage causes a coil to connect to relay wiper. That is how modems
are so often damaged - as we also demonstrated when constructing
massive relay switching drawers in test equipment to connect and
disconnect those voltages. How are modems damaged? Get those
datasheets. Even optocouplers have breakdown voltages. When that
off-hook relay coil breakdown voltage is exceeded, then a destructive
transient passes through PNP transistor, through relay, and to earth
ground via phone line. Everything has a breakdown voltage. What we
assume is not conductive at trivial low voltages become a perfect
conductor at higher voltage.

Defined was how a modem is damaged when an AC electric line surge
finds earth ground via modems DAA section, phone line, and earthed
'whole house' protector.

Try to make two ends of a fluorescent lamp conduct with an ohm meter.
No connection. Then why do so few volts conduct current across that
tube when tube is glowing? Same principle. That relay coil and relay
wiper are electrically connected during a surge which is why we so
routinely repaired modems by replacing a surge damaged PNP driver
transistor. Surge incoming on AC lines and outgoing on phone line. To
be damage, electronics must have both an incoming and outgoing path.
Surges do not enter on phone line, ignore phone line 'whole house'
protector, crash on a modem, and stop. Electricity just does not work
that way.

As described in another post is wire impedance. Using Bud's
citations that demonstrate how plug-in protectors can fail to provide
protection: two TVs sharing a plug-in protector are at 8000 volts.
How can this be when those plug-in protectors are grounded by three
prong electrical connection to breaker box? Because one end of that
safety ground wire is at near zero volts and the other end is at 8000
volts - wire impedance. How can one end of a wire be at 8000 volts and
the other end at near zero volts? Welcome to a basic electrical
principle that also explains why different parts of a transmitting
antenna wire are at different voltages.

A 50 foot AC electric ground wire is maybe 0.2 ohms resistance. But
that same ground wire is maybe 120 ohms impedance to a surge. A
trivial 100 amp surge enters wall receptacle. 120 ohms times 100 amps
is a voltage somewhere below 12,000 volts. Same reason why those two
TVs can be at 8000 volts during a surge. Same reason why earthing must
be 'less than 10 feet' to single point earth ground. But then this is
old and well proven concepts - wire impedance.

More reasons why that 50 foot AC electric wire has even higher
impedance and creates other surge related problems. Sharp bends.
Splices. Bundled with other wires thereby induced transients on those
other wires. Wall receptacle is not an earth ground. Wall receptacle
is a safety ground. Wire impedance is why that wall receptacle is not
sufficient for earthing.

Yes appliances do have internal protection as required by industry
standards. Once some appliances (ie Apple II) installed those
protectors. No longer. MOVs inside the computer were as not effective
as they would be on its power cord - for so many reasons - including
too far from earth ground.

You have not seen MOVs vaporize? Get 30+ years experience with this
technology to see it. Some vaporized MOVs looked ominously ghostly.
Only left were two leads. Nothing left of its carbon material or red
paint.

Meanwhile, learn what joules really mean in a plug-in protector.
1000 joules in a plug-in protector is maybe equivalent to a 333 joule
'whole house' protector. And that assumes none of those joules are
used on other ports such as telephone or cable. Furthermore, as
joules increase, then protector life expectancy increases
exponentially. To be equivalent to a minimal 1000 joule 'whole house'
protector, the plug-in protector must be at least 3000 joules. Too
often, UPSes and power strips were only 345 or 900 joules - grossly
undersized. Only recently have some plug-in protectors sold 'still
too small' 2000 joules products.

You have never seen a grossly undersized protector vaporize? View
what was too unacceptably common with so many plug-in protectors:
http://www.ehs.washington.edu/LabSaf/surge.htm
http://www.westwhitelandfire.com/Art...Protectors.pdf
http://www.hanford.gov/rl/?page=556&parent=554
Imagine what these would do in dust balls on a rug behind the table or
on a desktop covered in papers. Does not matter if your desktop does
not have papers. Other's do which is but another reason why plug-in
protectors can also cause human safety problems.

But again, some principles to grasp before understanding surge
protection. Ever touch a doorknob to cause a static discharge? What
was the electrical connection from that finger to charges below your
shoes? Notice how many of those items are normally not considered
conductive. And yet electricity flowed from that finger tip, through
door, through floor to bottom of your shoes. Welcome to surge
protection where concrete and linoleum become excellent conductors of
electricity. Where a coil and wiper inside a relay become electrically
connected. Just more examples of why surges cannot be stopped - and
therefore why effective protection has always been about diverting
before a surge can enter a building. Diverting via low impedance - not
just low resistance - connections to a single point electrode.

One final point. Single point need not be a single ground rod.
Single point can also be a halo or ufer ground completely enclosing a
building's perimeter. But single point earthing and low impedance
connections are essential to effective protection.

Pete C. wrote:
As I noted, nothing is going to stop a direct strike. Most strikes
aren't direct however and are primarily inductive pickup from a nearby
strike and therefore reduced to a much more manageable level.
...

Again for a direct hit. For a surge of the level of the much more common
inductively coupled strike that does not apply.
...

The MOVs that are located adjacent to the phone line connector on a
quality modem should clamp the surge. The drive to the off hook relay is
also not electrically connected to the line, nor is most of the rest of
the modem. The DAA transformer, ring detect optoisolator and hook switch
relay are about all that is connected to the line.
...

Again, reducing the current path and the potential for further inductive
coupling.
...

Any suppressers downstream provide further protection against
inductively coupled surges which don't have to come through the service
entrance conductors and residual surges past what the primary
suppressers were able to clamp. Also for #1, that third pin on the power
plug *is* a dedicated earthing wire.
...

I've never seen a vaporized MOV of any size. I have seen a few that have
failed and cracked after being subjected to substantial surges. If you
review the joule ratings of the various MOVs and gas discharge arrestors
you find in typical small suppressers you'll see that their ratings are
not at all far behind those of the common whole house suppressers. Some
of the quite expensive service entrance suppressers intended for
commercial services have higher ratings, but not the common ones.
...

Refer you to the dedicated grounding (earthing) conductor provided to
every electrical device in a residence. The dedicated third pin on a
NEMA 5-15 (or 5-20 or 5-xx, 6-xx, etc.) receptacle.
...

Appliances already contain internal protection.

Some appliances do, many do not. Don't recall the last time I saw any
suppression devices in a toaster or a blender.
...


  #17   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

Joshua Putnam wrote:
I've looked rather closely at my coax entrance -- only the outer
conductor is grounded. The center conductor is not. (Shouldn't be too
surprising, if you shorted them both to ground, it would attenuate the
signal a bit, no?)

What, other than a surge protector, stops transients on the center
conductor of cable TV?


Generally all protectors attentuate signals. In earlier days, I
always wondered why center core connection was not performed. Some
experienced professionals in the rec.radio.amateur.antenna newsgroup
confirmed what I had been told. Leakage from the center conductor to a
well earthed outer conductor provides sufficient protection. A
capacitive protector on center core would only attentuate signals;
provide little protection advantage. But then some legendary
manufacturers do make protectors that include that center core.

You are not earthing a 200,000 amp direct strike - which you probably
will never see in your lifetime. Using a ground block to earth the
outer braid is a massive protection improvement. If you still need
better, then visit some expensive and superior protector manufacturers
such as www.polyphaser.com .

Nothing 'stops transients on the ... conductor'. Anything that
stops or blocks such transients is not effective. Effective protection
is diverting. Destructive transients seek earth. Therefore the sooner
that transient is diverted / earthed (meaning a shorter connection to
earth and farther from transistors), then the better that protection.

  #18   Report Post  
Posted to alt.home.repair
Bud--
 
Posts: n/a
Default surge protectors

Bob wrote:

karsan wrote:


It is dangerous to have more than one surge protectors in you home I
have 3 surge protectors running in my home.



I have a whole house "protector" at the electrical panel and several
smaller units scattered throught the house. I have had several
lightning hits in the near vicinity and have never had electrical
damage. But I have lost 4 TV's from lightning coming in on the cable -
all damaged in the tuner sections rather than power sections. And I
have had computer modems fry from surges on the telephone line. So
from that, I deduce the whole house unit is doing it's job, but the
others are questionable.
Bob


Plug-in surge suppressors for cable TV need to have a port to include
both the power and cable TV. The multi-port surge suppressor will clamp
all voltages on power and signal wires to the common ground at the
suppressor. The IEEE guide at
http://www.mikeholt.com/files/PDF/Li...ion_May051.pdf
explains this quite well. It says the cable center conductor can be 4000
volts with respect to the shield. A plug-in suppressor will clamp this,
likely with a gas discharge tube. A bigger problem is if the cable
entrance ground block is not near, and connected with a short wire, to
the power service earthing conductor. That is also protected by a
multi-port plug-in surge suppressor and is illustrated in the IEEE guide.

Similarly, a plug-in suppressor for a computer with phone connection has
to have ports for both power and phone line.

bud--
  #19   Report Post  
Posted to alt.home.repair
Rob Mills
 
Posts: n/a
Default surge protectors


"karsan" wrote in message
oups.com...
It is dangerous to have more than one surge protectors in you home I

have 3 surge protectors running in my home.

I had a surge once (caused by nearby lightning strike) while I had 3 five
outlet strips connected together in one room. The surge protectors were
destroyed and the carpet they were sitting on was scorched/burned but
nothing that was connected to them was damaged which included a
computer a police scanner , shortwave radio and a couple of other small
items.
During the same incident in an adjacent room another surge protector
was destroyed along with a VCR but a TV that was connected to the
same protector was spared. RM~


PS, The surge protectors in use had well constructed metal housings. I
suspect we would have had a fire if they were of the plastic type.







  #21   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default surge protectors

w_tom wrote:

Numerous points that make assumptions based in a world where
impedance does not exist - where only resistance exists.

First, nothing will stop a direct strike. But direct strikes
routinely do no damage when they are diverted. Major difference
between stopping (which plug-in protectors hope you will assume) and
diverting which is standard where direct lightning strikes do not
damage. Again, 25 direct strikes annually to electronics atop the
Empire State Building; 40 annually to the WTC - and electronics not
damaged. It is routine to earth direct strikes without damage -
because we don't stop a direct strike. We divert it to earth.

Inductive transients? Well put some numbers to them. I assume
this is about a nearby lightning strike to a long wire antenna. Well
that nearby strike may induce a few thousand volts onto that antenna.
Then we connect an NE-2 (neon glow lamp) from that antenna to earth.
Because that neon glow lamp conducts only milliamps, then that
thousands volts on antenna is now less than 60 volts. IOW induced
transients are that trivial. So trivial as to be made irrelevant by
protection inside all appliances. And yet, even industry standards of
30+ years ago (i.e. CBEMA) defined protection that was inside all
electronic appliances even that long ago. It takes so little to make
induced transients irrelevant. But it is the direct strike that causes
damage.

You did not see protector devices inside the blender? You were not
looking like an engineer? Why do you think wire was heavier gauge than
necessary? You are making a classic mistake. You have assumed
protector is as specific device. Protection is not necessary achieved
by a protector. Protection is something in the engineering. You are
instead looking for a specific device rather than first learning the
design. Meanwhile, we were discussing electronics appliances - not
blenders that have no electronics.

Is "drive to the off hook relay ... also not electrically connected
to the line, nor is most of the rest of the modem"? First go to data
sheets. That coil inside a modem off hook relay does electrically
connect to its wiper as those datasheets demonstrate. Not at 100
volts. But then even floors and wall paints become conductive during
these transients. Datasheet for that off-hook relay even states what
voltage causes a coil to connect to relay wiper. That is how modems
are so often damaged - as we also demonstrated when constructing
massive relay switching drawers in test equipment to connect and
disconnect those voltages. How are modems damaged? Get those
datasheets. Even optocouplers have breakdown voltages. When that
off-hook relay coil breakdown voltage is exceeded, then a destructive
transient passes through PNP transistor, through relay, and to earth
ground via phone line. Everything has a breakdown voltage. What we
assume is not conductive at trivial low voltages become a perfect
conductor at higher voltage.

Defined was how a modem is damaged when an AC electric line surge
finds earth ground via modems DAA section, phone line, and earthed
'whole house' protector.

Try to make two ends of a fluorescent lamp conduct with an ohm meter.
No connection. Then why do so few volts conduct current across that
tube when tube is glowing? Same principle. That relay coil and relay
wiper are electrically connected during a surge which is why we so
routinely repaired modems by replacing a surge damaged PNP driver
transistor. Surge incoming on AC lines and outgoing on phone line. To
be damage, electronics must have both an incoming and outgoing path.
Surges do not enter on phone line, ignore phone line 'whole house'
protector, crash on a modem, and stop. Electricity just does not work
that way.

As described in another post is wire impedance. Using Bud's
citations that demonstrate how plug-in protectors can fail to provide
protection: two TVs sharing a plug-in protector are at 8000 volts.
How can this be when those plug-in protectors are grounded by three
prong electrical connection to breaker box? Because one end of that
safety ground wire is at near zero volts and the other end is at 8000
volts - wire impedance. How can one end of a wire be at 8000 volts and
the other end at near zero volts? Welcome to a basic electrical
principle that also explains why different parts of a transmitting
antenna wire are at different voltages.

A 50 foot AC electric ground wire is maybe 0.2 ohms resistance. But
that same ground wire is maybe 120 ohms impedance to a surge. A
trivial 100 amp surge enters wall receptacle. 120 ohms times 100 amps
is a voltage somewhere below 12,000 volts. Same reason why those two
TVs can be at 8000 volts during a surge. Same reason why earthing must
be 'less than 10 feet' to single point earth ground. But then this is
old and well proven concepts - wire impedance.

More reasons why that 50 foot AC electric wire has even higher
impedance and creates other surge related problems. Sharp bends.
Splices. Bundled with other wires thereby induced transients on those
other wires. Wall receptacle is not an earth ground. Wall receptacle
is a safety ground. Wire impedance is why that wall receptacle is not
sufficient for earthing.

Yes appliances do have internal protection as required by industry
standards. Once some appliances (ie Apple II) installed those
protectors. No longer. MOVs inside the computer were as not effective
as they would be on its power cord - for so many reasons - including
too far from earth ground.

You have not seen MOVs vaporize? Get 30+ years experience with this
technology to see it. Some vaporized MOVs looked ominously ghostly.
Only left were two leads. Nothing left of its carbon material or red
paint.

Meanwhile, learn what joules really mean in a plug-in protector.
1000 joules in a plug-in protector is maybe equivalent to a 333 joule
'whole house' protector. And that assumes none of those joules are
used on other ports such as telephone or cable. Furthermore, as
joules increase, then protector life expectancy increases
exponentially. To be equivalent to a minimal 1000 joule 'whole house'
protector, the plug-in protector must be at least 3000 joules. Too
often, UPSes and power strips were only 345 or 900 joules - grossly
undersized. Only recently have some plug-in protectors sold 'still
too small' 2000 joules products.

You have never seen a grossly undersized protector vaporize? View
what was too unacceptably common with so many plug-in protectors:
http://www.ehs.washington.edu/LabSaf/surge.htm
http://www.westwhitelandfire.com/Art...Protectors.pdf
http://www.hanford.gov/rl/?page=556&parent=554
Imagine what these would do in dust balls on a rug behind the table or
on a desktop covered in papers. Does not matter if your desktop does
not have papers. Other's do which is but another reason why plug-in
protectors can also cause human safety problems.

But again, some principles to grasp before understanding surge
protection. Ever touch a doorknob to cause a static discharge? What
was the electrical connection from that finger to charges below your
shoes? Notice how many of those items are normally not considered
conductive. And yet electricity flowed from that finger tip, through
door, through floor to bottom of your shoes. Welcome to surge
protection where concrete and linoleum become excellent conductors of
electricity. Where a coil and wiper inside a relay become electrically
connected. Just more examples of why surges cannot be stopped - and
therefore why effective protection has always been about diverting
before a surge can enter a building. Diverting via low impedance - not
just low resistance - connections to a single point electrode.

One final point. Single point need not be a single ground rod.
Single point can also be a halo or ufer ground completely enclosing a
building's perimeter. But single point earthing and low impedance
connections are essential to effective protection.


You sure do like to babble, too bad 99.9% of what you say is either
total nonsense, pseudo-science, or hopelessly misapplied scientific
principles. Your links to claimed "vaporized" MOVs show no such thing
either.

Pete C.
  #22   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

Plug-in protector has no effective earth ground. No earth ground
means no effective protection. Therefore Bud's article shows a plug-in
protector putting two TVs at 8000 volts. Will those TVs at 8000 volts
not be damaged - not leak currents in destructive paths? No. Those TVs
may be damaged because they are at 8000 volts. Bud's citation even
demonstrates why plug-in protectors can contribute to damage.

Other papers he forgets to cite note how plug-in protectors can even
contribute to damage of that adjacent appliance - TVs:
Martzloff and Key in 1994 wrote in "Surging the Upside-Down House:
Looking
into Upsetting Reference Voltages" :
1) Quantitative measurements in the Upside-Down house clearly
show objectionable difference in reference voltages. These occur
even when or perhaps because, surge protective devices are
present at the point of connection of appliances.


But then that is what the mikeholt.com paper also demonstrates on
page 33/34 in figures 8 and 9. TVs put at 8000 volts because a plug-in
protector is too far from earth ground; therefore is not properly
earthed. Earthing is essential to effective protection.

The paper on page 22 says:
An effective, low-impedance ground path is critical for the
successful operation of an SPD. ... Therefore, an evaluation
of the service entrance grounding system at the time of the
SPD installation is very important.


Of course. A protector is only as effective as its earth ground.
That protector adjacent to TVs put those TVs at 8000 volts -
ineffective protection. Effective protection must make a low impedance
connection to a good earth ground. That again means a protector
located 'less than 10 feet' from earth. Even Bud's paper demonstrates
how "objectionable ... voltages ... occur even when or perhaps because
surge protective devices are present at the point of connection of
appliances". The adjacent protector can even contribute to damage of
electronics.
..

Bud-- wrote:
Plug-in surge suppressors for cable TV need to have a port to include
both the power and cable TV. The multi-port surge suppressor will clamp
all voltages on power and signal wires to the common ground at the
suppressor. The IEEE guide at
http://www.mikeholt.com/files/PDF/Li...ion_May051.pdf
explains this quite well. It says the cable center conductor can be 4000
volts with respect to the shield. A plug-in suppressor will clamp this,
likely with a gas discharge tube. A bigger problem is if the cable
entrance ground block is not near, and connected with a short wire, to
the power service earthing conductor. That is also protected by a
multi-port plug-in surge suppressor and is illustrated in the IEEE guide.

Similarly, a plug-in suppressor for a computer with phone connection has
to have ports for both power and phone line.

bud--


  #23   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

Pete C. wrote:
You sure do like to babble, too bad 99.9% of what you say is either
total nonsense, pseudo-science, or hopelessly misapplied scientific
principles. Your links to claimed "vaporized" MOVs show no such thing
either.


You don't understand wire impedance. You insist that industry
professional papers are lies. Those burning power strip protectors due
to failing MOVs somehow are not fire threats? Meanwhile others who
want effective protection learn why properly earthed and properly sized
'whole house' protectors from responsible manufacturers such as Square
D, GE, Siemens, Polyphaser, Cuter-Hammer, Intermatic, and Leviton make
that short connection to earth; therefore provide effective
protection.

Reasons why such protectors sold in Home Depot and Lowes are long;
assume the reader understands basic electrical concepts such as wire
impedance. To make such problems such as wire impedance irrelevant, we
install an effective protector with a 'less than 10 foot' connection to
earth. Apparently concepts such as wire impedance and MOVs vaporizing
is completely new information to Pete C. Others are encouraged to learn
why above manufacturers of 'whole house' protectors are considered so
responsible; provide effective protection. In the case of Polyphaser,
that protection is considered legendary.

  #24   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default surge protectors

w_tom wrote:

Pete C. wrote:
You sure do like to babble, too bad 99.9% of what you say is either
total nonsense, pseudo-science, or hopelessly misapplied scientific
principles. Your links to claimed "vaporized" MOVs show no such thing
either.


You don't understand wire impedance. You insist that industry
professional papers are lies.


I understand wire impedance, you apparently do not and misapply the
concept. You haven't provided reference to any industry papers that
support your assertions.

Those burning power strip protectors due
to failing MOVs somehow are not fire threats?


Failing MOVs in an old poorly designed power strip / surge suppresser
combo that doesn't meet current standards could well be a fire threat,
however they have not been "vaporized" by a surge as you have claimed.

Meanwhile others who
want effective protection learn why properly earthed and properly sized
'whole house' protectors from responsible manufacturers such as Square
D, GE, Siemens, Polyphaser, Cuter-Hammer, Intermatic, and Leviton make
that short connection to earth; therefore provide effective
protection.


I have effective protection and it's multi level distributed protection
as good engineering practice dictates.

It starts with a Square D suppresser on the Square D QO series panel,
Leviton coax suppressers adjacent to the ground blocks at the CATV
demarc, the integral suppressers in the telco demarc and solid heavy
gauge ground leads to the adjacent 8' grounding electrode which is
solidly bonded to the secondary 8' electrode about 10' away.

It does not however end at this point in a "hope for the best" strategy,
the protection continues further with reasonable quality suppresser /
power strips (that have status indicators and thermal fuses), a large
quality UPS on the server rack, and additional suppressers on internal
phone / data / CATV lines.


Reasons why such protectors sold in Home Depot and Lowes are long;
assume the reader understands basic electrical concepts such as wire
impedance. To make such problems such as wire impedance irrelevant, we
install an effective protector with a 'less than 10 foot' connection to
earth. Apparently concepts such as wire impedance and MOVs vaporizing
is completely new information to Pete C. Others are encouraged to learn
why above manufacturers of 'whole house' protectors are considered so
responsible; provide effective protection. In the case of Polyphaser,
that protection is considered legendary.


Apparently folks like you latch onto technical terms like "wire
impedance" without bothering to get an understanding of what it really
means and how it is not the same as the wires DC resistance. You have
also not provided a single link to your claimed "vaporizing" MOVs.

The answer to the OP's original question "It is dangerous to have more
than one surge protectors in you home I
have 3 surge protectors running in my home." is clearly "no", it is not
dangerous.

And as myself and others have indicated a quality "whole house"
suppresser is very beneficial, but it does not obsolete secondary
suppressers further down the line, nor does it obsolete suppressers on
non power lines like CATV, phone and data.

Pete C.
  #25   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default surge protectors


w_tom wrote:
Joshua Putnam wrote:
I've looked rather closely at my coax entrance -- only the outer
conductor is grounded. The center conductor is not. (Shouldn't be too
surprising, if you shorted them both to ground, it would attenuate the
signal a bit, no?)

What, other than a surge protector, stops transients on the center
conductor of cable TV?


Generally all protectors attentuate signals. In earlier days, I
always wondered why center core connection was not performed. Some
experienced professionals in the rec.radio.amateur.antenna newsgroup
confirmed what I had been told. Leakage from the center conductor to a
well earthed outer conductor provides sufficient protection. A
capacitive protector on center core would only attentuate signals;
provide little protection advantage. But then some legendary
manufacturers do make protectors that include that center core.

You are not earthing a 200,000 amp direct strike - which you probably
will never see in your lifetime. Using a ground block to earth the
outer braid is a massive protection improvement. If you still need
better, then visit some expensive and superior protector manufacturers
such as www.polyphaser.com .

Nothing 'stops transients on the ... conductor'. Anything that
stops or blocks such transients is not effective. Effective protection
is diverting. Destructive transients seek earth. Therefore the sooner
that transient is diverted / earthed (meaning a shorter connection to
earth and farther from transistors), then the better that protection.



Tom like to make an argument out of everything, including symantics.
Most reasonable folks would agree that if a protective device shunts a
surge to ground, that it has in fact stopped the transient, because the
destructive transient does not make it to the protected equipment.



  #26   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default surge protectors


Rob Mills wrote:
"karsan" wrote in message
oups.com...
It is dangerous to have more than one surge protectors in you home I

have 3 surge protectors running in my home.

I had a surge once (caused by nearby lightning strike) while I had 3 five
outlet strips connected together in one room. The surge protectors were
destroyed and the carpet they were sitting on was scorched/burned but
nothing that was connected to them was damaged which included a
computer a police scanner , shortwave radio and a couple of other small
items.
During the same incident in an adjacent room another surge protector
was destroyed along with a VCR but a TV that was connected to the
same protector was spared. RM~


PS, The surge protectors in use had well constructed metal housings. I
suspect we would have had a fire if they were of the plastic type.



I had a similar experience, where my PC and Fax machine, which were
connected to the strip type surge protectors including phone line
protection were undamaged. During the same event my Tivo, which did
not have a surge protector on the phone line, had the telephone/modem
interface blown out. Of course, Tom has told me that this happened
by the surge coming in the AC line, getting through the AC surge
protector, going through the Tivo, and then blowing the modem on the
way out the phone line. I think the rest of us have a pretty good
idea of how it happened.

  #27   Report Post  
Posted to alt.home.repair
karsan
 
Posts: n/a
Default surge protectors


wrote:
Rob Mills wrote:
"karsan" wrote in message
oups.com...
It is dangerous to have more than one surge protectors in you home I

have 3 surge protectors running in my home.

I had a surge once (caused by nearby lightning strike) while I had 3 five
outlet strips connected together in one room. The surge protectors were
destroyed and the carpet they were sitting on was scorched/burned but
nothing that was connected to them was damaged which included a
computer a police scanner , shortwave radio and a couple of other small
items.
During the same incident in an adjacent room another surge protector
was destroyed along with a VCR but a TV that was connected to the
same protector was spared. RM~


PS, The surge protectors in use had well constructed metal housings. I
suspect we would have had a fire if they were of the plastic type.



I had a similar experience, where my PC and Fax machine, which were
connected to the strip type surge protectors including phone line
protection were undamaged. During the same event my Tivo, which did
not have a surge protector on the phone line, had the telephone/modem
interface blown out. Of course, Tom has told me that this happened
by the surge coming in the AC line, getting through the AC surge
protector, going through the Tivo, and then blowing the modem on the
way out the phone line. I think the rest of us have a pretty good
idea of how it happened.


I do not have lighting surges so I am pretty lucky.

  #28   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

They are all called shunt mode protectors. Typically destructive
transient seeks earth ground. Each layer of protection is defined by
its single point earthing. Primary protection is provided by a utility
and requires homeowner inspection:
http://www.tvtower.com/fpl.html

Secondary protection is the 'whole house' protector, et al - also
defined by its single point earth ground as demonstrated by:
http://www.erico.com/public/library/...es/tncr002.pdf

In each case, wire impedance must be kept low as repeatedly cited in
professional papers - which means short distance, no sharp bends, no
splices, not inside metallic conduit, etc.

When Orange County FL emergency response system suffered damage from
lightning, then reasons for system protector failure were repaired.
They fixed the earthing system:
http://www.psihq.com/AllCopper.htm

Why? Each protector is defined by what it connects to. Earth
ground. Those interior protectors claim to protect from what type of
surge? Well plug-in protectors don't even define protection for each
type of transient. Why let a consumer know it protects only from a
transient that is typically not destructive and that is made irrelevant
by protection already inside equipment.

Many plug-in protectors are undersized because that MOV vaporization
even promotes protectors to the naive. Meanwhile, if better protection
is required, did Orange County install plug-in protectors? Of course
not. They enhanced earth so that effective protectors would perform
even better.

What does that protector inside a plug-in UPS do? Where in numerical
specs does it even claim protection? Is dBs filtering considered
protection? No. Do standard numbers such as C62.xx or UL1449 define
protection? No. It does not list protection from every type of
transient because you might notice a glaring anomaly. With no low
impedance connection to earth ground, it does not claim to protection
from surges that cause damage. They forget to define protection from
each type of transient so that a consumer might assume it. And then we
have this layer of protection - forgetting to mention what defines each
layer: earth ground.

Pete C. has a problem with low impedance wiring requirement when
virtually every responsible installation requires 'a low impedance
connection'. His own Square D 'whole house' protector is reported
earthed by 10 feet. Of course that protector could be made better if
earthing wire was shorter, no sharp bends, separated from other wires,
etc. Each protector is defined by quality of and connection to its
single point earth ground. As one industry professional defined it
for every building owner and operator:
http://www.harvardrepeater.org/news/lightning.html
The keys to effective lightning protection are surprisingly simple, and
surprisingly less than obvious. Of course you *must* have a single
point ground system that eliminates all ground loops. And you must
present a low *impedance* path for the energy to go. That's most
generally a low *inductance* path rather than just a low ohm DC path.


They are called shunt mode protectors. They don't magically stop
surges. As wire impedance increases, then surges find other
(destructive) paths to earth. Wire impedance defined by an equation
where wire impedance increases proportional to wire length multiplied
by a factor that includes the Log of 4 times wire length divided by
wire diameter. Wire length increases wire impedance twice over which
is why low impedance means a shorter connection. A fact demonstrated as
relevant by Thottappillil in "Electromagnetic Pulse Environment of
Cloud to Ground Lightning for EMC Studies":
The most important properties of lightning current that produce
damage are peak current, maximum rate of change of current,
integral of current over time, and the integral of the square of
current over time. ... In objects that present essentially inductive
impedances such as wires ... the maximum overvoltage is
proportional to the maximum rate of change.


Of course, higher impedance means higher maximum overvoltage when we
want voltage to earth to be as low as possible. So we carefully lower
that wire impedance connection to earth.

As wire gets longer, impedance increases unacceptably. Polyphaser
notes in TD1023: Multiple I/O port protection, Single Point Ground
considerations at:
http://www.polyphaser.com/ppc_ptd_home.aspx
Another complication in this scenario is the inductance of the
conductor between the I/O protector and the ground system.
The inductance will determine how much of the strike energy
is conducted into the ground system and how much is left to
elevate the transmitter chassis. Since strike energy is a high
frequency pulse, a low inductance path to ground becomes a
critical factor. Copper strapping is preferred over large
diameter wire as an inter-connecting media. Copper strap has
a large circumference and low inductance per unit length. The
strike energy, like water, will follow the easiest (least inductive)
path to ground.


So what does that plug-in protector adjacent to two TVs do? Leaves
both TVs at 8000 volts. Why? Wire impedance to earth ground is too
large causing TVs to sit at 8000 volts during a surge. Where is the
protection? Demonstrates how a plug-in protector - without a low
impedance connection to earth - does nothing useful.

Some hype a myth about layered protection and forget to mention what
defines that layer - earth ground. Why would supplemental protectors
with excessively high impedance somehow earth to a point that the surge
ignored when entering a building? If that earthing was made superior,
then a surge is better earthed by the 'whole house' protector. And if
earthing is not sufficient, then why is a supplemental (plug-in)
protector going to earth to that same insufficient earth ground?

Rather than waste money on plug-in protectors, what did they do in
Orange County FL? They repaired reasons for lightning damage -
insufficient earthing. Plug-in protectors are in the same protection
layer as a 'whole house' protector. If 'whole house' protector's
earthing is not sufficient, then a plug-in protector - with excessive
wire impedance - will somehow earth to same ground? Nonsense. And yet
that is what plug-in shunt mode protectors must do.

BTW, another solution called series mode protectors; beyond scope of
this post.

As has been repeatedly demonstrated, even in a paper from Martzloff,
et al:
... objectionable difference in reference voltages ...occur
even when or perhaps because, surge protective devices are
present at the point of connection of appliances.


Each layer of protection is defined by the and most essential system
component - earth ground. Primary protection layer is earthed at the
utility pole. Secondary protection layer is properly earthed adjacent
to 'whole house' protector. Since plug-in protectors don't even claim
such protection in numerical specs, then such protectors neither have a
dedicated wire for earthing nor do they even discuss earthing. A shunt
mode protector earths. No earth ground - such as with plug-in
protectors - means no effective protection. Better is to put money
into enhancing the earthing system.

Lower wire impedance connection to earth. Enhance the earthing
electrodes. Establish a single point earth ground to be used by all
incoming utilities. Money wasted on plug-in protectors is better spent
here. Effective protection is defined by its most essential 'system'
component - single point earth ground.

Pete C. wrote:
I understand wire impedance, you apparently do not and misapply the
concept. You haven't provided reference to any industry papers that
support your assertions.

Those burning power strip protectors due
to failing MOVs somehow are not fire threats?


Failing MOVs in an old poorly designed power strip / surge suppresser
combo that doesn't meet current standards could well be a fire threat,
however they have not been "vaporized" by a surge as you have claimed.
...

Apparently folks like you latch onto technical terms like "wire
impedance" without bothering to get an understanding of what it really
means and how it is not the same as the wires DC resistance. You have
also not provided a single link to your claimed "vaporizing" MOVs.

The answer to the OP's original question "It is dangerous to have more
than one surge protectors in you home I
have 3 surge protectors running in my home." is clearly "no", it is not
dangerous.

And as myself and others have indicated a quality "whole house"
suppresser is very beneficial, but it does not obsolete secondary
suppressers further down the line, nor does it obsolete suppressers on
non power lines like CATV, phone and data.

Pete C.


  #30   Report Post  
Posted to alt.home.repair
Bob
 
Posts: n/a
Default surge protectors


w_tom wrote:

Was cable earthed before entering a building? If not, then yes,
cable may be an incoming source of electricity called a surge. Cable
must drop down and make a 'less than 10 foot' connection to a same
earth ground used by AC electric and telephone. If cable enters house
without dropping down and connecting to earth, then yes, cable can be
the incoming path of a surge that was seeking earth ground
destructively through tuners.



The cable shield was grounded via a grounding block, a 4' piece of #10
bare copper wire, and a separate grounding rod of unknown length, all
installed by the cable company. They have since rerouted the ground to
the service entrance ground.

Don't assume a modem was damaged by a surge from phone line. Don't
think of surges as a wave crashing on a beach. Surges just don't work
that way. First electricity flows in everything in a path through that
modem. Everything is conducting the same electricity. Long afterwards
(microseconds later), something in that path is destroyed. That path
could be incoming on phone line. Or a destructive path through modem
can be incoming on AC electric or cable; outgoing on phone line.


The modem was damaged from the incoming phone line. The computer was
switched off. The modem's impedance matching transformers were blown
along with the input/output stage. By the way, the phone line is all
underground for miles so it was a ground induced surge. But that is
not uncommon.

Bob



  #31   Report Post  
Posted to alt.home.repair
Bud--
 
Posts: n/a
Default surge protectors

w_tom wrote:

Plug-in protector has no effective earth ground. No earth ground
means no effective protection. Therefore Bud's article shows a plug-in
protector putting two TVs at 8000 volts. Will those TVs at 8000 volts
not be damaged - not leak currents in destructive paths? No. Those TVs
may be damaged because they are at 8000 volts. Bud's citation even
demonstrates why plug-in protectors can contribute to damage.


The IEEE guide clearly describes the action of a multi-port plug-in
surge suppressor as clamping all wires to the common ground at the surge
suppressor, with earthing being secondary. Why does chapter 6 of the
IEEE guide "SPECIFIC PROTECTION EXAMPLES" use multi-port plug-in surge
suppressors in both examples??

I agree with wfretwell. that a service panel surge suppressor and a
single point ground are both a very good ideas. The question is whether
plug-in surge suppressors are effective. To anyone who can read, the
IEEE and NIST guides clearly say they are.

You have proviced no reputable links saying plug-in surge suppressors
are not effective.
Where are your supporting links??

bud--
  #32   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default surge protectors


wrote:
On 13 Jun 2006 14:58:56 -0700, "w_tom" wrote:


Granted it is a minor point. But the point is made because many
assume a plug-in protectors sitting between a transistor and a surge
will somehow stop or block what three miles of sky could not.
Effective protectors 'shunt'. Those protectors that don't have earth
ground hope one assumes it will instead 'stop' or 'absorb' a surge to
promote a myth. Even shunt mode plug-in protectors only shunt - divert
- a transient. To be effective, it must shunt to earth and not divert
into the appliance. A 'semantic' that can otherwise create confusion
- promote an ineffective product.



This is the only place I dissagree with W-Tom.
He is 100% right about the importance of a single point ground,
bonding of all point of entry protection plus the importance of solid
grounding electrodes and connections. You should try to stop the
surge at the service entrance but where I dissagree is I still think a
plug in protector has value to catch the things his point of entry
system didn't stop. These will usually be a very low order tranient if
the POE system was working but still enough to hurt you. It is better
to heat up a shunt wired MOV than to let this into a MOSFET.
Good point of use protectors also have a large ferro resonant
componant that will eat some heat too.
It still needs a good ground path back to your grounding electrode
system, just to stabilize the reference levels. He is right that it
does little good to clamp the transient if the resulting "zero" is 40v
above the ground reference of the interface lines.
You can't have too many layers of protection if you live in a
lightning area. I just like to add another layer to his system.
When I was doing physical planning for a large corporation that sold
business machines internationally we had a lot of lightning experience
is South Florrida. Layers of protection works for people who can't
turn off their system and unplug it every afternoon in the summer.




I agree. Tom starts off with good advice, but then goes down the path
of "If the whole house surge protection didn't work, then you did
something wrong and point of use protectors are useless." I and many
others have had experiences where it was pretty clear that plug-in
surge protectors did work. He's right, that a short ground path with
a service protector is clearly better, but that doesn't mean the
plug-in protectors are totally useless. A lot, for example, depends on
the rise time of the surge. The slower the rise time, the less
impedance there will be.

Also, for many folks, eg, those living in apartments, a whole house AC
protector is just not possible.

  #33   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

For "have a pretty good idea of how it happened", than what also
protected those other undamaged electronic appliances? What protected
those kitchen and bathroom GFCIs? What protected the smoke detector?
What protected the dishwasher? How did those appliances without
plug-in protectors not suffer damage? Invisible surge protectors?

You are using same logic process that somehow proved childhood
leukemia from AC electric wires. Selectively ignoring other data such
as that undamaged microwave oven and furnace controls. Meanwhile,
demonstrated was how a plug-in protector simply provided lightning with
a destructive path through a network of computers. Shunt mode
protectors require earthing. No earth ground asks how does that surge
get shunted into earth? Via adjacent appliance. Or maybe another
appliance acts as a surge protector - shunts the surge to earth
destructively. IOW you only assume that protection works and
completely ignore that air conditioner control electronics that was not
damaged.

A method of making a kludge 'whole house' protector for apartment
dwellers was defined. Take a plug-in protector of maximum joules. Cut
its six foot power cord down to near zero feet. Plug it into the wall
receptacle that is closest to earth ground (and breaker box). It
becomes a 'poor mans' whole house protector. Best you can do if an
apartment owner will not install your 'whole house' protector.

But again, what makes that kludge solution into better protection?
Shorter power cord. Closer to earth ground. Increased distance from
appliance to be protected. What does a shunt mode protector do? It
shunts. Either it shunts a transient into earth (safely), or it shunts
a transient to earth, destructively, via the adjacent appliance. Or it
does nothing because the Tivo did that shunting.

Meanwhile: "getting through the AC surge protector" ? Do you think
some magical blocking device exists inside a shunt mode protector?
Incoming protector wire and outgoing receptacles are direct electrical
connections. Nothing 'blocks' inside that protector. Wall receptacle
connects directly to appliance plugged into that protector - a direct
wire connection. In fact, if a protector provides protection to its
receptacles, then protector also provides protection to anything
plugged into other side of same duplex wall receptacle and to other
wall receptacles on same circuit.

Nothing inside a shunt mode protector stops or blocks surges.
Protection is about diverting surges before surges gets to the
appliance. Protector is designed with transients "getting through the
AC surge protector". That direct connection is what wire inside the
protector does.

wrote:
I had a similar experience, where my PC and Fax machine, which were
connected to the strip type surge protectors including phone line
protection were undamaged. During the same event my Tivo, which did
not have a surge protector on the phone line, had the telephone/modem
interface blown out. Of course, Tom has told me that this happened
by the surge coming in the AC line, getting through the AC surge
protector, going through the Tivo, and then blowing the modem on the
way out the phone line. I think the rest of us have a pretty good
idea of how it happened.


  #34   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default surge protectors


w_tom wrote:
For "have a pretty good idea of how it happened", than what also
protected those other undamaged electronic appliances? What protected
those kitchen and bathroom GFCIs? What protected the smoke detector?
What protected the dishwasher? How did those appliances without
plug-in protectors not suffer damage? Invisible surge protectors?



Last time I checked, none of the devices on your list above gets
connected to the telephone line. The PC, FAX, and Tivo were connected
to the telephone line. The PC and FAX were connected through a strip
type surge protector and survived a surge caused by a thunderstorm.
The Tivo was not connected The Tivo had the modem section blown out,
while the rest of the Tivo was still functional.

Based on that, it seems very reasonable to conclude that the surge
likely came in on the phone line and that the surge protector for the
PC and Fax very likely saved them. However I know you will argue
otherwise.




You are using same logic process that somehow proved childhood
leukemia from AC electric wires. Selectively ignoring other data such
as that undamaged microwave oven and furnace controls.



Again, the furnace and microwave were not connected to the phone line.


Meanwhile,
demonstrated was how a plug-in protector simply provided lightning with
a destructive path through a network of computers. Shunt mode
protectors require earthing. No earth ground asks how does that surge
get shunted into earth? Via adjacent appliance. Or maybe another
appliance acts as a surge protector - shunts the surge to earth
destructively. IOW you only assume that protection works and
completely ignore that air conditioner control electronics that was not
damaged.



Hmmm, is your air conditioner connected to the phone line?



A method of making a kludge 'whole house' protector for apartment
dwellers was defined. Take a plug-in protector of maximum joules. Cut
its six foot power cord down to near zero feet. Plug it into the wall
receptacle that is closest to earth ground (and breaker box). It
becomes a 'poor mans' whole house protector. Best you can do if an
apartment owner will not install your 'whole house' protector.

But again, what makes that kludge solution into better protection?
Shorter power cord. Closer to earth ground. Increased distance from
appliance to be protected. What does a shunt mode protector do? It
shunts. Either it shunts a transient into earth (safely), or it shunts
a transient to earth, destructively, via the adjacent appliance. Or it
does nothing because the Tivo did that shunting.

Meanwhile: "getting through the AC surge protector" ? Do you think
some magical blocking device exists inside a shunt mode protector?
Incoming protector wire and outgoing receptacles are direct electrical
connections. Nothing 'blocks' inside that protector. Wall receptacle
connects directly to appliance plugged into that protector - a direct
wire connection. In fact, if a protector provides protection to its
receptacles, then protector also provides protection to anything
plugged into other side of same duplex wall receptacle and to other
wall receptacles on same circuit.

Nothing inside a shunt mode protector stops or blocks surges.
Protection is about diverting surges before surges gets to the
appliance. Protector is designed with transients "getting through the
AC surge protector". That direct connection is what wire inside the
protector does.



Rant on Tom. Others have provided links to credible sources, like the
IEEE, that clearly state that plug in surge protectors can be effective
and part of a tiered protection system. They even clearly show a
diagram in chapter 6 of exactly the settup that saved my PC and FAX,
while the unprotected Tivo got whacked. Now, who should we believe,
you or the IEEE?




happened.

  #35   Report Post  
Posted to alt.home.repair
w_tom
 
Posts: n/a
Default surge protectors

wrote:
Last time I checked, none of the devices on your list above gets
connected to the telephone line. The PC, FAX, and Tivo were connected
to the telephone line. The PC and FAX were connected through a strip
type surge protector and survived a surge caused by a thunderstorm.
The Tivo was not connected The Tivo had the modem section blown out,
while the rest of the Tivo was still functional.

Based on that, it seems very reasonable to conclude that the surge
likely came in on the phone line ...


So how did a surge enter on phone line, ignore the telephone line
'whole house' protector, destroy Tivo ... and then stop? What kind of
electricity does trader4 have that crashed on a Tivo like a wave on the
beach? That can decide to ignore a phone line protector but is somehow
miraculously stopped by a plug-in protector.

Trader4 knows how damaged happened only because he had damage and
then made assumptions. It must have been incoming on phone line
because only Tivo was damaged. What about other phones? What about
portable phone base station? He has no other phones - or just forgets
to mention that they too have no surge protector and yet were not
damaged.

A warning about how phone line items (Tivo. portable phone base
stations, modems, etc) are easily damaged when a 'whole house' AC
electric protector is not installed. Incoming on AC electric (that has
no protection) AND outgoing to earth via phone line is typically how
phone appliances are damaged. Phone line already has a 'whole house'
protector provided free by the telco. But somehow trader4 suffered
Tivo damage from a surge protected phone line. Somehow his surges
ignore earthed surge protectors - of they really enter on AC electric
that has no 'whole house' protector.

Somehow AC electric that even protects phone lines from lightning,
that is more often struck, then enters without any earthed protector,
and connects to most every household appliance including Tivo - somehow
AC electric did have any surge? Somehow lightning never struck AC
electric AND somehow a surge completely ignored the telephone line
protector? In reality, surge was on AC electric and other appliances
protected themselves. Lightning strikes AC electric wires - the most
exposed - most often. AC electric is the most common source of damage
even to phone line appliances. And then there is the telephone line
protector that somehow a surge will completely ignore to damage Tivo.
He must have treacherously smart surges.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Whole house surge protector? Patch Home Repair 56 April 1st 09 04:58 PM
Building Ground (long-...sorry) jakdedert Electronics Repair 32 May 19th 06 05:03 AM
Surge Protectors twfsa Home Repair 15 December 29th 05 07:27 PM
The Season for needing Surge Protectors and Interference Filters is upon us. American Technical Resources Electronics Repair 0 April 8th 05 08:11 PM
Are PC surge protectors needed in the UK? greywolf42 Electronics Repair 82 July 13th 04 11:37 AM


All times are GMT +1. The time now is 03:50 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"