Posted to alt.home.repair
Carl
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

I want to be able to get power into my house from a portable generator
without the need of extension cords through open doors. I would like
to install an external box that can accept at NEMA-type plug from the
generator and then wire it to a couple of outlets inside the house that
are independent of the rest of the house's electrical system. I won't
need any transfer switch because the power from the generator will
never travel on the main wires in the house.

My question: The box that accepts a NEMA plug has two hot (red and
black) wires. Can I wire an outlet using the red wire and an another
outlet using the black wire (with the white and ground wires common to
both?)

Thanks.

  #2   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

yes you can, each red and black is 120v with white wire the common
neutral.

how are you planning on powering furnace etc?

  #3   Report Post  
Posted to alt.home.repair
Carl
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

Thanks. I was pretty sure that's how it worked, but I couldn't find
any website that talked about wiring it in this way.

The furnace will have to remain off during a power failure. If I want
to get that fancy, I will get an electrician to hook up a transfer
switch. I'm just trying to power the refrigerator, TV, some lights and
a fan without having an open door cluttered with extension cords.

Carl

  #4   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

Carl wrote:

Thanks. I was pretty sure that's how it worked, but I couldn't find
any website that talked about wiring it in this way.

The furnace will have to remain off during a power failure. If I want
to get that fancy, I will get an electrician to hook up a transfer
switch. I'm just trying to power the refrigerator, TV, some lights and
a fan without having an open door cluttered with extension cords.

Carl


There are better options than a true transfer switch available today for
small generators. A true transfer switch is needed for large loads, but
if you only have a small generator and have to do load management anyway
there is no need for a transfer switch.

There are a number of small generator sub panels in the ~$200 price
range that allow you to move 6-10 circuits that require backup to this
new sub panel and each one essentially has a little transfer switch.

An even cheaper option that can be used for large generators as well as
small ones is an interlock kit for your main panel. I just did a full
panel replacement with a Square D QO panel and I installed a ~$30
interlock kit from Square D that interlocks the main breaker (200A in
this case) with another 2 pole breaker (any size up to 125A) in panel
position 2/4.

I have a 20A breaker as the back feed breaker currently since I'm only
connecting a 5 kW generator, but if I switch to a larger generator I
just change that back feed breaker to a larger size. You could even use
an oversized breaker there if you wanted since it is really only doing
switching duty, the over current protection is provided by the breakers
on the generator itself.

This interlock kit is a much cheaper solution than a full transfer
switch or even one of the generator sub panels. Since it's produced by
the manufacturer of the panel it's a quality, approved option. Square D
makes the interlock kits for their Homeline panels as well and I expect
a few other manufacturers have similar options.

Pete C.
  #5   Report Post  
Posted to alt.home.repair
m Ransley
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

Price out your exterior box, socket plugs,, cable to the gen. Now look
at a Generac transfer switch kit, for 300$ you get everything , a pre
wired 6 circuit panel with 2 watt meters, exterior box, extra sockets,
plugs , cable. It is cheaper buying the kit, easy to install and you can
power everything you need.



  #6   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

m Ransley wrote:

Price out your exterior box, socket plugs,, cable to the gen. Now look
at a Generac transfer switch kit, for 300$ you get everything , a pre
wired 6 circuit panel with 2 watt meters, exterior box, extra sockets,
plugs , cable. It is cheaper buying the kit, easy to install and you can
power everything you need.


I think you miss the point of the Square D interlock kit. The little
generator sub panels only handle what circuits you relocate to that sub
panel, the $30 interlock kit takes the place of a full transfer switch
for generators supplying up to 125A. Since it provides power to the
entire panel it also lets you power any circuit you need and do load
management as required.

Pete C.
  #7   Report Post  
Posted to alt.home.repair
m Ransley
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

Does the sqare d have watt meters, he did say portable gen, it would be
to easy to overload the gen without a way to monitor it. I never looked
into square d, I just put in the Generac kit since it was complete and
pre wired .

  #8   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

m Ransley wrote:

Does the sqare d have watt meters, he did say portable gen, it would be
to easy to overload the gen without a way to monitor it. I never looked
into square d, I just put in the Generac kit since it was complete and
pre wired .


The Square D kit is nothing more than an approved interlock plate that
only allows one of the two (main or back feed) breaker to be on at the
same time, and a retainer bracket that prevents the back feed breaker
from being inadvertently removed from the panel. There are no meters,
inlet connectors, etc. The kit I used is a QOCGK2 if you want to see it
on the Square D site, it's very different from the little generator sub
panels.

As noted this is about a $30 kit that can take the place of a $200+ full
125A transfer switch. Even adding the cost of the back feed breaker and
inlet box for a small generator it would total perhaps $100.

Overloading a small generator isn't much of a concern since the
generator will have it's own circuit breakers and it will just pop them
or stall the engine if you switch in too big a load like a central A/C
compressor.

The interlock kit is a particularly good option for those who are
comfortable doing load management, or in cases where a generator large
enough to handle most everything is being installed.

Pete C.
  #9   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

This is actually a cheap, simple, safe,and approved method of transfer. I've
only seen it made by Square D for the QO series



"Pete C." wrote in message
...
m Ransley wrote:

Does the sqare d have watt meters, he did say portable gen, it would be
to easy to overload the gen without a way to monitor it. I never looked
into square d, I just put in the Generac kit since it was complete and
pre wired .


The Square D kit is nothing more than an approved interlock plate that
only allows one of the two (main or back feed) breaker to be on at the
same time, and a retainer bracket that prevents the back feed breaker
from being inadvertently removed from the panel. There are no meters,
inlet connectors, etc. The kit I used is a QOCGK2 if you want to see it
on the Square D site, it's very different from the little generator sub
panels.

As noted this is about a $30 kit that can take the place of a $200+ full
125A transfer switch. Even adding the cost of the back feed breaker and
inlet box for a small generator it would total perhaps $100.

Overloading a small generator isn't much of a concern since the
generator will have it's own circuit breakers and it will just pop them
or stall the engine if you switch in too big a load like a central A/C
compressor.

The interlock kit is a particularly good option for those who are
comfortable doing load management, or in cases where a generator large
enough to handle most everything is being installed.

Pete C.



  #10   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

RBM wrote:

This is actually a cheap, simple, safe,and approved method of transfer. I've
only seen it made by Square D for the QO series


They also make it for their Homeline series panels.

Pete C.








"Pete C." wrote in message
...
m Ransley wrote:

Does the sqare d have watt meters, he did say portable gen, it would be
to easy to overload the gen without a way to monitor it. I never looked
into square d, I just put in the Generac kit since it was complete and
pre wired .


The Square D kit is nothing more than an approved interlock plate that
only allows one of the two (main or back feed) breaker to be on at the
same time, and a retainer bracket that prevents the back feed breaker
from being inadvertently removed from the panel. There are no meters,
inlet connectors, etc. The kit I used is a QOCGK2 if you want to see it
on the Square D site, it's very different from the little generator sub
panels.

As noted this is about a $30 kit that can take the place of a $200+ full
125A transfer switch. Even adding the cost of the back feed breaker and
inlet box for a small generator it would total perhaps $100.

Overloading a small generator isn't much of a concern since the
generator will have it's own circuit breakers and it will just pop them
or stall the engine if you switch in too big a load like a central A/C
compressor.

The interlock kit is a particularly good option for those who are
comfortable doing load management, or in cases where a generator large
enough to handle most everything is being installed.

Pete C.



  #11   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

Pete C.

Any chance you could post the link to that on the Square D site? As an
electrician myself, I'd like more info. This sounds perfect for some
of my customers.

Thanks,

Glen

  #12   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

" wrote:

Pete C.

Any chance you could post the link to that on the Square D site? As an
electrician myself, I'd like more info. This sounds perfect for some
of my customers.

Thanks,

Glen


The link to the new product announcement that covers the four versions
of the interlock kit:

http://ecatalog.squared.com/techlib/...00892680126e4f

Pete C.
  #13   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring


Thanks Pete,

This is quite a system. Effective, Simple, Inexpensive and Safe.

Thanks Again.

Glen

  #14   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

AWESOME SYSTEM! Since we will replacing our main panel this decides the
one we want..........

simple cheap flexible and safe

  #15   Report Post  
Posted to alt.home.repair
swattsup
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

I've been Googling around looking for less expensive transfer
panels/switches/relays etc and also found this puppy. It's great to
see someone already using it. I hate to have to replace my entire load
center but even so it's still cheaper and more flexible than anything
else I've found.

The upside is it also gets me a main circuit cut-off inside the house
that the contractor crap doesn't have.

One question though, maybe two ;-), where did you get the interlock?
No one seems to have it and Square-D doesn't sell direct.

And a general question directed at anybody (who knows) - there wouldn't
be a problem installing another set of mains breakers in series with
the the main service breakers outside by the meter, would there?

Oh, and a third - does the inside breaker have to have the same rating
as the outside one (150Amp?) There is a great SquareD value pack I'd
like to use but it has a 200 Amp main breaker.

Thanks.

Pete C. wrote:
RBM wrote:

This is actually a cheap, simple, safe,and approved method of transfer. I've
only seen it made by Square D for the QO series


They also make it for their Homeline series panels.

Pete C.





  #16   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

The inside Main can be larger than the outside main as the conductors are
protected by the 150 amp . The inside would essentially just serve as a
disconnect. Call electrical supply houses that are Square D distributors for
the interlock


"swattsup" wrote in message
oups.com...
I've been Googling around looking for less expensive transfer
panels/switches/relays etc and also found this puppy. It's great to
see someone already using it. I hate to have to replace my entire load
center but even so it's still cheaper and more flexible than anything
else I've found.

The upside is it also gets me a main circuit cut-off inside the house
that the contractor crap doesn't have.

One question though, maybe two ;-), where did you get the interlock?
No one seems to have it and Square-D doesn't sell direct.

And a general question directed at anybody (who knows) - there wouldn't
be a problem installing another set of mains breakers in series with
the the main service breakers outside by the meter, would there?

Oh, and a third - does the inside breaker have to have the same rating
as the outside one (150Amp?) There is a great SquareD value pack I'd
like to use but it has a 200 Amp main breaker.

Thanks.

Pete C. wrote:
RBM wrote:

This is actually a cheap, simple, safe,and approved method of transfer.
I've
only seen it made by Square D for the QO series


They also make it for their Homeline series panels.

Pete C.





  #17   Report Post  
Posted to alt.home.repair
Tom Horne, Electrician
 
Posts: n/a
Default Wiring a Generator Independent of the house's wiring

swattsup wrote:
Pete C. wrote:
RBM wrote:
This is actually a cheap, simple, safe,and approved method of

transfer. I've
only seen it made by Square D for the QO series

They also make it for their Homeline series panels.

Pete C.


I've been Googling around looking for less expensive transfer
panels/switches/relays etc and also found this puppy. It's great to
see someone already using it. I hate to have to replace my entire load
center but even so it's still cheaper and more flexible than anything
else I've found.

The upside is it also gets me a main circuit cut-off inside the house
that the contractor crap doesn't have.

One question though, maybe two ;-), where did you get the interlock?
No one seems to have it and Square-D doesn't sell direct.

And a general question directed at anybody (who knows) - there wouldn't
be a problem installing another set of mains breakers in series with
the the main service breakers outside by the meter, would there?

Oh, and a third - does the inside breaker have to have the same rating
as the outside one (150Amp?) There is a great SquareD value pack I'd
like to use but it has a 200 Amp main breaker.

Thanks.


You can get the Interlock at any Square D stocking electrical supply
house. I've even seen them at the box stores.

The only issue with the series main breaker arrangement is that both
breakers must have an adequate withstand rating for the available fault
current. The 150 ampere breaker is undoubtedly sized for the service
entrance conductors so you can't eliminate it without changing out your
service entry conductors.

No the breakers don't have to be the same amperage rating as long as the
one at the meter is sized for the size of the service entry conductors.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous
for general use." Thomas Alva Edison
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PIR certificates - (Wiring regulations are complete & utter rubbish!!) Lightman UK diy 16 April 8th 06 12:59 AM
Instaling Outdoors Floodlight with ground wiring. xero Home Repair 0 February 7th 06 06:06 AM
Old houses, where to run wiring John Smith UK diy 15 August 10th 04 02:01 AM
peculiar wiring in residential switch box? David Jones Home Repair 6 July 20th 04 12:25 AM
connecting aluminum to copper wiring Mr. Bill Home Repair 12 May 5th 04 03:33 PM


All times are GMT +1. The time now is 07:42 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"