DIYbanter

DIYbanter (https://www.diybanter.com/)
-   Home Repair (https://www.diybanter.com/home-repair/)
-   -   Circuit breaker does not deliver 240 volt (https://www.diybanter.com/home-repair/146358-circuit-breaker-does-not-deliver-240-volt.html)

[email protected] February 25th 06 03:30 PM

Circuit breaker does not deliver 240 volt
 
i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!


Doug Miller February 25th 06 03:36 PM

Circuit breaker does not deliver 240 volt
 
In article .com, wrote:
i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!


First question I have is: do you have a 240V breaker? (I.e. a double-pole
breaker)

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

Dr. Hardcrab February 25th 06 03:54 PM

Circuit breaker does not deliver 240 volt
 

"Doug Miller" wrote in message
et...
In article .com,
wrote:
i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!


First question I have is: do you have a 240V breaker? (I.e. a double-pole
breaker)



and how are you "testing" it to know it's only 120 volts???



Joseph Meehan February 25th 06 03:54 PM

Circuit breaker does not deliver 240 volt
 
wrote:
i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!


Scary question. If you don't know why a single breaker would only
supply 120V and do not understand about dual breakers using both legs, you
should not be that close to the breaker box.

At least find a good book on the subject and get an basic understanding
of how it all works before you do anything other than to rest a breaker (and
only do that once, it if needs it more often than that, it needs to be
fixed).

If on the other hand you do understand and you only forgot to note that
you were measuring voltage from a double breaker then I suggest that one
half of the breaker has tipped or the is a fault in the box.

--
Joseph Meehan

Dia duit



RBM February 25th 06 04:16 PM

Circuit breaker does not deliver 240 volt
 
Is it a double pole breaker that was giving you 240volt and then stopped, or
a newly installed breaker that should deliver 240 volt. If it is a new
installation , be sure you are using a double pole breaker, which is one
that connects to two different busses of your panel, as opposed to a split
breaker, which connects to one buss of the panel and has places for two
wires to attach to it


wrote in message
oups.com...
i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!




SQLit February 25th 06 04:44 PM

Circuit breaker does not deliver 240 volt
 

"Doug Miller" wrote in message
et...
In article .com,

wrote:
i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!


First question I have is: do you have a 240V breaker? (I.e. a double-pole
breaker)

--
Regards,
Doug Miller (alphageek at milmac dot com)


Intended as a clarification only
Check this there are twins out there that the uninformed might think that
are 2 pole breakers.
I am not so sure that the OP really knows what he is trying to say.



Toller February 25th 06 05:04 PM

Circuit breaker does not deliver 240 volt
 

"RBM" rbm2(remove wrote in message
...
Is it a double pole breaker that was giving you 240volt and then stopped,
or a newly installed breaker that should deliver 240 volt. If it is a new
installation , be sure you are using a double pole breaker, which is one
that connects to two different busses of your panel, as opposed to a split
breaker, which connects to one buss of the panel and has places for two
wires to attach to it

A split breaker gives 0v, hot-hot.

If I wanted to make a wild guess, the OP is probably measuring 120v H-G for
both hots, which is quite correct. OP, you have to measure H-H.



Toller February 25th 06 05:39 PM

Circuit breaker does not deliver 240 volt
 

"Al Moran" wrote in message
...
On 25 Feb 2006 07:30:36 -0800, wrote:

i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!



Install a circuit breaker booster.


A transformer?



Rich256 February 25th 06 06:05 PM

Circuit breaker does not deliver 240 volt
 
Toller wrote:
"RBM" rbm2(remove wrote in message
...
Is it a double pole breaker that was giving you 240volt and then stopped,
or a newly installed breaker that should deliver 240 volt. If it is a new
installation , be sure you are using a double pole breaker, which is one
that connects to two different busses of your panel, as opposed to a split
breaker, which connects to one buss of the panel and has places for two
wires to attach to it

A split breaker gives 0v, hot-hot.

If I wanted to make a wild guess, the OP is probably measuring 120v H-G for
both hots, which is quite correct. OP, you have to measure H-H.



Could also be that half the breaker is tripped.

Edwin Pawlowski February 25th 06 06:16 PM

Circuit breaker does not deliver 240 volt
 

wrote in message
oups.com...
i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!


That is supposed to be what you get on each leg. If you don't understand
it, get professional help before you get into trouble.

You don't give enough information for anything more than that as an answer.
New breaker? Old breaker that you tested in the past? Are you checking at
the breaker or at a down-line portion of the circuit?



unknown February 25th 06 06:29 PM

Circuit breaker does not deliver 240 volt
 
On 25 Feb 2006 07:30:36 -0800, wrote:

i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!


Make sure it's actually a double-pole breaker. That takes 2 slots in
your panel. Then measure hot to hot, not hot to neutral or ground.

Toller February 25th 06 06:49 PM

Circuit breaker does not deliver 240 volt
 

"Rich256" wrote in message
...
Toller wrote:
"RBM" rbm2(remove wrote in message
...
Is it a double pole breaker that was giving you 240volt and then
stopped, or a newly installed breaker that should deliver 240 volt. If
it is a new installation , be sure you are using a double pole breaker,
which is one that connects to two different busses of your panel, as
opposed to a split breaker, which connects to one buss of the panel and
has places for two wires to attach to it

A split breaker gives 0v, hot-hot.

If I wanted to make a wild guess, the OP is probably measuring 120v H-G
for both hots, which is quite correct. OP, you have to measure H-H.


Could also be that half the breaker is tripped.


No, it would then be an open circuit and measure zero.



Rich256 February 26th 06 12:27 AM

Circuit breaker does not deliver 240 volt
 
Toller wrote:
"Rich256" wrote in message
...
Toller wrote:
"RBM" rbm2(remove wrote in message
...
Is it a double pole breaker that was giving you 240volt and then
stopped, or a newly installed breaker that should deliver 240 volt. If
it is a new installation , be sure you are using a double pole breaker,
which is one that connects to two different busses of your panel, as
opposed to a split breaker, which connects to one buss of the panel and
has places for two wires to attach to it

A split breaker gives 0v, hot-hot.

If I wanted to make a wild guess, the OP is probably measuring 120v H-G
for both hots, which is quite correct. OP, you have to measure H-H.

Could also be that half the breaker is tripped.


No, it would then be an open circuit and measure zero.


You could measure 110 from one leg to return. I really don't understand
what he was saying. Is he getting 110 from hot to hot or from one hot
to return?

I have seen a breaker half tripped. Had to turn it all the way off and
back on again to set both sides.

Dave February 26th 06 12:55 AM

Circuit breaker does not deliver 240 volt
 
wrote:
i have a problem with the my circuit breaker it does not deliver 240
volts that i need instead only delivers 120 volts.
Need urgent answer!


Visit your local library and read a book on home wiring before you
electrocute yourself.


Rich256 February 26th 06 02:32 AM

Circuit breaker does not deliver 240 volt
 
Rich256 wrote:
Toller wrote:
"Rich256" wrote in message
...
Toller wrote:
"RBM" rbm2(remove wrote in message
...
Is it a double pole breaker that was giving you 240volt and then
stopped, or a newly installed breaker that should deliver 240
volt. If it is a new installation , be sure you are using a double
pole breaker, which is one that connects to two different busses of
your panel, as opposed to a split breaker, which connects to one
buss of the panel and has places for two wires to attach to it

A split breaker gives 0v, hot-hot.

If I wanted to make a wild guess, the OP is probably measuring 120v
H-G for both hots, which is quite correct. OP, you have to measure
H-H.
Could also be that half the breaker is tripped.


No, it would then be an open circuit and measure zero.

You could measure 110 from one leg to return. I really don't understand
what he was saying. Is he getting 110 from hot to hot or from one hot
to return?

I have seen a breaker half tripped. Had to turn it all the way off and
back on again to set both sides.


Thinking about it a bit more. If half of a breaker pair is tripped and
if there is any kind of a load, like a lamp or motor, between that line
and return he could measure 110 volts between the two hot lines.

For example in a dryer there are 110 volt timers and motors. Only the
heater is between the two hot lines.


All times are GMT +1. The time now is 03:17 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter