#1
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
Hello. I have an Amana Air Command Hi Efficiency 90 Gas Furnace that just stopped working this afternoon. I noticed that cold air was blowing out the heat registers and the temperature in the house was 8 degrees below the thermostat setting. This furnace is a pilotless unit with a hair-dryer-shaped exhaust fan to vent the exhaust gases. Here is how the furnace normally operates (to the best of my memory): - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting, requesting heat - there is a short delay (for the igniter to heat up?) - the gas kicks in and ignites and the exhaust fan turns on - there is another short delay (for the heat exchanger to come up to temperature?) - the blower fan kicks in and voila, there's heat Here is the present abnormal operation: - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting - the blower fan *immediately* comes on and starts blowing unheated air throughout the house - the exhaust fan never comes on - there is no gas smell, and the burners never fire up - I cannot see any indication of an igniter heating up (not sure where to look, but I think if there was something glowing in there I would see it) Here is my working hypothesis: There is a thermal safety sensor/switch somewhere in there that thinks the heat exchanger is overheated. So even though the heat exchanger is dead cold, it wants to keep the blower motor on to cool it off. And it inhibits the ignition and the release of gas to the burners. So when I turn the thermostat up, requesting heat, all I get is the blower motor coming on. Does my reasoning make sense? And, is it pretty straightforward to replace the thermal safety switch? And, where is said switch/sensor? And finally, is there a quick and simple way to momentarily bypass the thermal safety switch to test my hypothesis... so I don't waste time and money buying the wrong part? Thanks. EJ |
#2
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
wrote in message oups.com... Hello. I have an Amana Air Command Hi Efficiency 90 Gas Furnace that just stopped working this afternoon. I noticed that cold air was blowing out the heat registers and the temperature in the house was 8 degrees below the thermostat setting. This furnace is a pilotless unit with a hair-dryer-shaped exhaust fan to vent the exhaust gases. Here is how the furnace normally operates (to the best of my memory): - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting, requesting heat - there is a short delay (for the igniter to heat up?) - the gas kicks in and ignites and the exhaust fan turns on - there is another short delay (for the heat exchanger to come up to temperature?) - the blower fan kicks in and voila, there's heat Here is the present abnormal operation: - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting - the blower fan *immediately* comes on and starts blowing unheated air throughout the house - the exhaust fan never comes on - there is no gas smell, and the burners never fire up - I cannot see any indication of an igniter heating up (not sure where to look, but I think if there was something glowing in there I would see it) Here is my working hypothesis: There is a thermal safety sensor/switch somewhere in there that thinks the heat exchanger is overheated. So even though the heat exchanger is dead cold, it wants to keep the blower motor on to cool it off. And it inhibits the ignition and the release of gas to the burners. So when I turn the thermostat up, requesting heat, all I get is the blower motor coming on. Does my reasoning make sense? And, is it pretty straightforward to replace the thermal safety switch? And, where is said switch/sensor? And finally, is there a quick and simple way to momentarily bypass the thermal safety switch to test my hypothesis... so I don't waste time and money buying the wrong part? Thanks. EJ Your reasoning makes sense, but I doubt that it's that simple. I have a similar furnace (different brand). The start-up sequence is the same. However, when I asked about DIY service should something go wrong, the installer said that I should read the book first and then look at the "error codes" that flash when the furnace doesn't operate. He pointed out a little bank of LEDs that blink the error codes. That tells me there's a computer in there someplace and just about anything could be going on. Before getting into the hardware, my suggestion is to read the installation/service manual to see if you can get any clues from the furnace itself. If you don't have the book, check on the web. Many can now be downloaded. I always check for the obvious -- tripped circuit breaker, loose wires, etc., and then try shutting off the power for a minute or so. That resets the computer. TKM |
#3
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
|
#4
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
|
#6
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
|
#7
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
My money is on a sticking relay, but I agree that he should hire a
professional. "Joey" wrote in message ... I would think you are on track. First, verify the gas is making it to the furnace. Make sure you hear the 'click' that opens the gas valve for the ignitors to fire. It's an electrical activated solonoid that you can hear or check with an ohm meter. Next, find that thermal protection fuse which should be located near the burners. Look on a site that sells them so you'll know what you're looking for. They have two leads and should read zero ohms if it's good. I would certainally hire a professional if the problem is beyond this. J wrote: Hello. I have an Amana Air Command Hi Efficiency 90 Gas Furnace that just stopped working this afternoon. I noticed that cold air was blowing out the heat registers and the temperature in the house was 8 degrees below the thermostat setting. This furnace is a pilotless unit with a hair-dryer-shaped exhaust fan to vent the exhaust gases. Here is how the furnace normally operates (to the best of my memory): - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting, requesting heat - there is a short delay (for the igniter to heat up?) - the gas kicks in and ignites and the exhaust fan turns on - there is another short delay (for the heat exchanger to come up to temperature?) - the blower fan kicks in and voila, there's heat Here is the present abnormal operation: - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting - the blower fan *immediately* comes on and starts blowing unheated air throughout the house - the exhaust fan never comes on - there is no gas smell, and the burners never fire up - I cannot see any indication of an igniter heating up (not sure where to look, but I think if there was something glowing in there I would see it) Here is my working hypothesis: There is a thermal safety sensor/switch somewhere in there that thinks the heat exchanger is overheated. So even though the heat exchanger is dead cold, it wants to keep the blower motor on to cool it off. And it inhibits the ignition and the release of gas to the burners. So when I turn the thermostat up, requesting heat, all I get is the blower motor coming on. Does my reasoning make sense? And, is it pretty straightforward to replace the thermal safety switch? And, where is said switch/sensor? And finally, is there a quick and simple way to momentarily bypass the thermal safety switch to test my hypothesis... so I don't waste time and money buying the wrong part? Thanks. EJ |
#8
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
Bob, that is a possibility, but I'm sitting here looking at a bag of 50
thermal fuses that I purchased just for this problem. My last job was a Trane unit with a bad thermal fuse. I cleaned around the burner entrance and replaced the fuse and problem solved. J Bob wrote: My money is on a sticking relay, but I agree that he should hire a professional. "Joey" wrote in message ... I would think you are on track. First, verify the gas is making it to the furnace. Make sure you hear the 'click' that opens the gas valve for the ignitors to fire. It's an electrical activated solonoid that you can hear or check with an ohm meter. Next, find that thermal protection fuse which should be located near the burners. Look on a site that sells them so you'll know what you're looking for. They have two leads and should read zero ohms if it's good. I would certainally hire a professional if the problem is beyond this. J wrote: Hello. I have an Amana Air Command Hi Efficiency 90 Gas Furnace that just stopped working this afternoon. I noticed that cold air was blowing out the heat registers and the temperature in the house was 8 degrees below the thermostat setting. This furnace is a pilotless unit with a hair-dryer-shaped exhaust fan to vent the exhaust gases. Here is how the furnace normally operates (to the best of my memory): - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting, requesting heat - there is a short delay (for the igniter to heat up?) - the gas kicks in and ignites and the exhaust fan turns on - there is another short delay (for the heat exchanger to come up to temperature?) - the blower fan kicks in and voila, there's heat Here is the present abnormal operation: - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting - the blower fan *immediately* comes on and starts blowing unheated air throughout the house - the exhaust fan never comes on - there is no gas smell, and the burners never fire up - I cannot see any indication of an igniter heating up (not sure where to look, but I think if there was something glowing in there I would see it) Here is my working hypothesis: There is a thermal safety sensor/switch somewhere in there that thinks the heat exchanger is overheated. So even though the heat exchanger is dead cold, it wants to keep the blower motor on to cool it off. And it inhibits the ignition and the release of gas to the burners. So when I turn the thermostat up, requesting heat, all I get is the blower motor coming on. Does my reasoning make sense? And, is it pretty straightforward to replace the thermal safety switch? And, where is said switch/sensor? And finally, is there a quick and simple way to momentarily bypass the thermal safety switch to test my hypothesis... so I don't waste time and money buying the wrong part? Thanks. EJ |
#9
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
I apologize profusely. In my haste, I gave wrong info in the previous post. I just spent the last hour with the panel off the furnace, looking for obvious problems (burnt wires etc) and re-checking what's happening. The blower motor is NOT coming on. The vent (exhaust) motor IS coming on. When I dial up the thermostat to request heat, all that happens is that the vent motor turns on. It stays that way for as long as I leave the thermostat turned up. The igniter never glows, the gas does not turn on (no gas smell), and there is no fire. When I dial the thermostat back down, the vent motor shuts off after about 30 seconds. This unit has a White-Rodgers model 50A50-206 control with the diagnostic LED. The LED does not indicate any problem (no flashes). Just to confirm that the control was not dead, I removed one wire from the vacuum sensor that monitors the vent motor's suction. Then I got 3 flashes on the control's diagnostic LED, indicating that the sensor was stuck open. So the control was healthy enough to detect that. What are the most likely culprits here? Does a failed igniter fit these symptoms? Is the igniter easy to test? How? I'm assuming that the White-Rodgers control does not monitor the igniter, because there is no error code listed for it. The error codes from the White-Rodgers are pretty limited. It's not like a modern auto computer which monitors just about everything. I'm not smelling any gas *at all*, so the control is apparently not opening the valve. Is it supposed to, even if the igniter is faulty? In other words, does the control monitor the health of the igniter, and refuse to open the gas valve if it's not glowing? Or does it just wait a short time, then open the gas valve, and if the temperature doesn't rise rapidly it turns the gas back off? |
#11
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
The reason I said a relay, and not a thermal link, is because the OP said
the blower motor was coming on. Now he said it's the inducer motor. "Joey" wrote in message ... Bob, that is a possibility, but I'm sitting here looking at a bag of 50 thermal fuses that I purchased just for this problem. My last job was a Trane unit with a bad thermal fuse. I cleaned around the burner entrance and replaced the fuse and problem solved. J Bob wrote: My money is on a sticking relay, but I agree that he should hire a professional. "Joey" wrote in message ... I would think you are on track. First, verify the gas is making it to the furnace. Make sure you hear the 'click' that opens the gas valve for the ignitors to fire. It's an electrical activated solonoid that you can hear or check with an ohm meter. Next, find that thermal protection fuse which should be located near the burners. Look on a site that sells them so you'll know what you're looking for. They have two leads and should read zero ohms if it's good. I would certainally hire a professional if the problem is beyond this. J wrote: Hello. I have an Amana Air Command Hi Efficiency 90 Gas Furnace that just stopped working this afternoon. I noticed that cold air was blowing out the heat registers and the temperature in the house was 8 degrees below the thermostat setting. This furnace is a pilotless unit with a hair-dryer-shaped exhaust fan to vent the exhaust gases. Here is how the furnace normally operates (to the best of my memory): - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting, requesting heat - there is a short delay (for the igniter to heat up?) - the gas kicks in and ignites and the exhaust fan turns on - there is another short delay (for the heat exchanger to come up to temperature?) - the blower fan kicks in and voila, there's heat Here is the present abnormal operation: - the thermostat "cool-off-heat" switch is on "heat" - the thermostat fan "on-auto" switch is on "auto" - I turn up the thermostat setting - the blower fan *immediately* comes on and starts blowing unheated air throughout the house - the exhaust fan never comes on - there is no gas smell, and the burners never fire up - I cannot see any indication of an igniter heating up (not sure where to look, but I think if there was something glowing in there I would see it) Here is my working hypothesis: There is a thermal safety sensor/switch somewhere in there that thinks the heat exchanger is overheated. So even though the heat exchanger is dead cold, it wants to keep the blower motor on to cool it off. And it inhibits the ignition and the release of gas to the burners. So when I turn the thermostat up, requesting heat, all I get is the blower motor coming on. Does my reasoning make sense? And, is it pretty straightforward to replace the thermal safety switch? And, where is said switch/sensor? And finally, is there a quick and simple way to momentarily bypass the thermal safety switch to test my hypothesis... so I don't waste time and money buying the wrong part? Thanks. EJ |
#12
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
Do you think it's time to call a professional?
"Ether Jones" wrote in message oups.com... I apologize profusely. In my haste, I gave wrong info in the previous post. I just spent the last hour with the panel off the furnace, looking for obvious problems (burnt wires etc) and re-checking what's happening. The blower motor is NOT coming on. The vent (exhaust) motor IS coming on. When I dial up the thermostat to request heat, all that happens is that the vent motor turns on. It stays that way for as long as I leave the thermostat turned up. The igniter never glows, the gas does not turn on (no gas smell), and there is no fire. When I dial the thermostat back down, the vent motor shuts off after about 30 seconds. This unit has a White-Rodgers model 50A50-206 control with the diagnostic LED. The LED does not indicate any problem (no flashes). Just to confirm that the control was not dead, I removed one wire from the vacuum sensor that monitors the vent motor's suction. Then I got 3 flashes on the control's diagnostic LED, indicating that the sensor was stuck open. So the control was healthy enough to detect that. What are the most likely culprits here? Does a failed igniter fit these symptoms? Is the igniter easy to test? How? I'm assuming that the White-Rodgers control does not monitor the igniter, because there is no error code listed for it. The error codes from the White-Rodgers are pretty limited. It's not like a modern auto computer which monitors just about everything. I'm not smelling any gas *at all*, so the control is apparently not opening the valve. Is it supposed to, even if the igniter is faulty? In other words, does the control monitor the health of the igniter, and refuse to open the gas valve if it's not glowing? Or does it just wait a short time, then open the gas valve, and if the temperature doesn't rise rapidly it turns the gas back off? |
#13
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
There is no way to troubleshoot a system over the internet I appreciate your concern, but that depends on the technical background of the person seeking help. I know enough about sensors and control systems and electronics; I just needed some info about how the system is supposed to work. I got the help I needed from another newsgroup. All I really needed was the sequence of operations. I'll post it here for the benefit of others: - control tests the vent prove switch (vacuum switch attached to vent motor). must be open. if not, flash error code and refuse to ignite - control powers up vent motor, delays for a moment, then tests vent prove switch again. must be closed. if not, flash error code and refuse to ignite. - control tests limit and rollout switches. if open, flash appropriate error code and refuse to ignite - control powers igniter, waits for it to heat up, then opens gas valve*. That's all I needed to find the problem. It was an open circuit in the ignitor heating element. I replaced the igniter (cost: $33) and everything is working fine. *I'm still a little unsure of this last step, and if a knowledgeable person could could shed some light on it that would be appreciated. Which of the following is the correct description of how the 50A50-206 actually works: a) control powers igniter, delays for a fixed time interval to allow igniter to glow, opens gas valve, then depowers igniter and uses it as a flame sensor b) control first tests the igniter and refuses to open the gas valve if an open circuit if found; then proceeds as in (a) above c) some other control approach ?? I tried the white-rodgers website, but the model 50A50-206 is discontinued, and they didn't have the charity to keep the info for it on their website. I was hoping someone had it, or knew of a website where it was archived. EJ |
#14
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
On Tue, 24 Jan 2006 21:00:19 -0500, Joey
wrote: Bob, that is a possibility, but I'm sitting here looking at a bag of 50 thermal fuses Golly. If you can't afford a computer monitor, at least get a television. that I purchased just for this problem. My last job was a Trane unit with a bad thermal fuse. I cleaned around the burner entrance and replaced the fuse and problem solved. Remove NOPSAM to email me. Please let me know if you have posted also. |
#15
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
On Wed, 25 Jan 2006 13:11:52 GMT, Al Moran
wrote: On 24 Jan 2006 18:43:21 -0800, "Ether Jones" wrote: I apologize profusely. In my haste, I gave wrong info in the previous post. I just spent the last hour with the panel off the furnace, looking for obvious problems (burnt wires etc) and re-checking what's happening. The blower motor is NOT coming on. The vent (exhaust) motor IS coming on. When I dial up the thermostat to request heat, all that happens is that the vent motor turns on. It stays that way for as long as I leave the thermostat turned up. The igniter never glows, the gas does not turn on (no gas smell), and there is no fire. When I dial the thermostat back down, the vent motor shuts off after about 30 seconds. This unit has a White-Rodgers model 50A50-206 control with the diagnostic LED. The LED does not indicate any problem (no flashes). Just to confirm that the control was not dead, I removed one wire from the vacuum sensor that monitors the vent motor's suction. Then I got 3 flashes on the control's diagnostic LED, indicating that the sensor was stuck open. So the control was healthy enough to detect that. What are the most likely culprits here? Does a failed igniter fit these symptoms? Is the igniter easy to test? How? I'm assuming that the White-Rodgers control does not monitor the igniter, because there is no error code listed for it. The error codes from the White-Rodgers are pretty limited. It's not like a modern auto computer which monitors just about everything. I'm not smelling any gas *at all*, so the control is apparently not opening the valve. Is it supposed to, even if the igniter is faulty? In other words, does the control monitor the health of the igniter, and refuse to open the gas valve if it's not glowing? Or does it just wait a short time, then open the gas valve, and if the temperature doesn't rise rapidly it turns the gas back off? Quite simple problem really. You need to replace the thermostat. Have you read the whole thread? Did you notice that some things did go on when he turned the thermostat to a higher temperature than that room was? If some things do happen, how do you reach the conclusion it is the thermostat? Remove NOPSAM to email me. Please let me know if you have posted also. |
#16
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
Just put him in your kill file like everyone else has done.
"mm" wrote in message ... On Wed, 25 Jan 2006 13:11:52 GMT, Al Moran wrote: On 24 Jan 2006 18:43:21 -0800, "Ether Jones" wrote: I apologize profusely. In my haste, I gave wrong info in the previous post. I just spent the last hour with the panel off the furnace, looking for obvious problems (burnt wires etc) and re-checking what's happening. The blower motor is NOT coming on. The vent (exhaust) motor IS coming on. When I dial up the thermostat to request heat, all that happens is that the vent motor turns on. It stays that way for as long as I leave the thermostat turned up. The igniter never glows, the gas does not turn on (no gas smell), and there is no fire. When I dial the thermostat back down, the vent motor shuts off after about 30 seconds. This unit has a White-Rodgers model 50A50-206 control with the diagnostic LED. The LED does not indicate any problem (no flashes). Just to confirm that the control was not dead, I removed one wire from the vacuum sensor that monitors the vent motor's suction. Then I got 3 flashes on the control's diagnostic LED, indicating that the sensor was stuck open. So the control was healthy enough to detect that. What are the most likely culprits here? Does a failed igniter fit these symptoms? Is the igniter easy to test? How? I'm assuming that the White-Rodgers control does not monitor the igniter, because there is no error code listed for it. The error codes from the White-Rodgers are pretty limited. It's not like a modern auto computer which monitors just about everything. I'm not smelling any gas *at all*, so the control is apparently not opening the valve. Is it supposed to, even if the igniter is faulty? In other words, does the control monitor the health of the igniter, and refuse to open the gas valve if it's not glowing? Or does it just wait a short time, then open the gas valve, and if the temperature doesn't rise rapidly it turns the gas back off? Quite simple problem really. You need to replace the thermostat. Have you read the whole thread? Did you notice that some things did go on when he turned the thermostat to a higher temperature than that room was? If some things do happen, how do you reach the conclusion it is the thermostat? Remove NOPSAM to email me. Please let me know if you have posted also. |
#17
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
The control powers the igniter, then senses that it is getting hot, then
opens the gas valve, then another sensor tells the control that there is a flame, then the igniter goes out. "Ether Jones" wrote in message ups.com... There is no way to troubleshoot a system over the internet I appreciate your concern, but that depends on the technical background of the person seeking help. I know enough about sensors and control systems and electronics; I just needed some info about how the system is supposed to work. I got the help I needed from another newsgroup. All I really needed was the sequence of operations. I'll post it here for the benefit of others: - control tests the vent prove switch (vacuum switch attached to vent motor). must be open. if not, flash error code and refuse to ignite - control powers up vent motor, delays for a moment, then tests vent prove switch again. must be closed. if not, flash error code and refuse to ignite. - control tests limit and rollout switches. if open, flash appropriate error code and refuse to ignite - control powers igniter, waits for it to heat up, then opens gas valve*. That's all I needed to find the problem. It was an open circuit in the ignitor heating element. I replaced the igniter (cost: $33) and everything is working fine. *I'm still a little unsure of this last step, and if a knowledgeable person could could shed some light on it that would be appreciated. Which of the following is the correct description of how the 50A50-206 actually works: a) control powers igniter, delays for a fixed time interval to allow igniter to glow, opens gas valve, then depowers igniter and uses it as a flame sensor b) control first tests the igniter and refuses to open the gas valve if an open circuit if found; then proceeds as in (a) above c) some other control approach ?? I tried the white-rodgers website, but the model 50A50-206 is discontinued, and they didn't have the charity to keep the info for it on their website. I was hoping someone had it, or knew of a website where it was archived. EJ |
#18
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
On Thu, 26 Jan 2006 02:37:05 GMT, Al Moran
wrote: On Wed, 25 Jan 2006 17:49:46 -0500, mm wrote: Have you read the whole thread? Did you notice that some things did go on when he turned the thermostat to a higher temperature than that room was? If some things do happen, how do you reach the conclusion it is the thermostat? Because it's always the thermostat. at least according to all the moronic homeowners/do it yorselfers I see every ****ing day. And besides, because I said so, that's why. Dumbass. Gosh, Bob, you're right! Remove NOPSAM to email me. Please let me know if you have posted also. |
#19
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
The control powers the igniter, then senses that it is getting hot, then opens the gas valve, then another sensor tells the control that there is a flame, then the igniter goes out Thanks Bob. I believe that for this particular control unit, the igniter doubles as a flame sensor. I'm thinking that once it's depowered, the control measures the igniter's resistance to detect flame. What I haven't been able to confirm yet are the following: - does the control (the white-rodgers 50A50-206) monitor the igniter to see if it's working before opening the gas valve (this would seem to be the safer approach), and if so, what method is used (I can think of two: 1) monitor the current while the igniter is being powered, or 2) wait a fixed time for the igniter to glow, then depower it and measure resistance (either by applying a lower fixed voltage and measuring current, or by driving a fixed current and measuring voltage) and - if the control does indeed monitor the igniter, it's odd that there is no LED fault code for that, as there is for the vent prove switch, the flame sensor, and the thermal overlimit sensor. If anyone reading the thread has documentation for the white-rodgers 50A50-206 and would be willing to share it, it would be appreciated. EJ |
#20
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
The control powers the igniter, then senses that it is getting hot, then opens the gas valve, then another sensor tells the control that there is a flame, then the igniter goes out. Thanks Bob. That certainly makes sense, and seems like a very safe control strategy for a unit with separate igniter and flame sensor. But I believe for this particular unit, the igniter doubles as a flame sensor. I was wondering what control strategy they use to achieve that (I can think of a couple, but was wondering how the 50A50-206 actually does it). EJ |
#21
Posted to alt.home.repair
|
|||
|
|||
furnace blows cold air
On Thu, 26 Jan 2006 02:37:05 GMT, Al Moran
wrote: On Wed, 25 Jan 2006 17:49:46 -0500, mm wrote: Have you read the whole thread? Did you notice that some things did go on when he turned the thermostat to a higher temperature than that room was? If some things do happen, how do you reach the conclusion it is the thermostat? Because it's always the thermostat. at least according to all the moronic homeowners/do it yorselfers I see every ****ing day. And I missed this. You repeat to others what people you don't respect say. Is this so others won't respect you too? besides, because I said so, that's why. Dumbass. Very angry! Remove NOPSAM to email me. Please let me know if you have posted also. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
power shower problems | UK diy | |||
Coleman furnace question | Home Repair | |||
How to deal with a furnace with a need to bleed | Home Repair | |||
Furnace Problem...HELP! | Home Repair | |||
how do I ensure there is a cold water path to the boilers return | UK diy |