Furnace losing 24v when heat requested
Hi. I have a Lenox furnace, about 15 years old I guess. It was working
fine, but then all of the sudden the thermostat seemed to just die. So I swapped thermostats. It worked again for a couple of days, and then failed again. So I debugged it a bit more carefully, and it turns out the thermostat "resets" whenever it tries to call for heat. The fan will come on for about a tenth of a second, and then the display acts like it does when you first plug it in. I'm not sure exactly what's happening, but it SEEMS that the furnace is shutting off 24v when heat is called. It's not the blower though, because if I just turn the fan on (from the thermostat) it works fine. It's also possible that the therm is somehow resetting itself, the only real test I did here was connecting 24v to the heat line directly, and the heat didn't come on, but I'm not sure if that's the proper "protocol" for requesting heat. Any thoughts before I call the techs? Thanks, --Max |
#2
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Max Metral wrote: but it SEEMS that the furnace is shutting off 24v when heat is called. Let me make a guess, You wired one of W, W2 to C? |
#3
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
No, not this time.
"Brian" wrote in message oups.com... Max Metral wrote: but it SEEMS that the furnace is shutting off 24v when heat is called. Let me make a guess, You wired one of W, W2 to C? |
#4
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
I guess you gave up on those pricks in alt.hvac, eh?
|
#5
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
They were indeed remarkably rude. At least most of them, a couple were
helpful. Anyhow, the main question has now become, if my digital (i.e. needs power) thermostat says it only requires the following leads connected: R - 24vac G - fan W - heat Y - cool Where does it get power when it demands heat, thus shorting (?) G and W to R? I would assume (standard decomposition of assume applies) that it gets it from Y staying at ground, and perhaps that's where the fault has occurred. If not, where else can it pull the power? wrote in message ps.com... I guess you gave up on those pricks in alt.hvac, eh? |
#6
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Where does a lighted doorbell button get its power from? It only has
two wires and it lights without ringing the doorbell. Mike |
#7
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Most digital thermostats require a ground (24V common) If you don't
have one the batteries will power it for a few days, then it will die. Get a mercury non programmable thermostat or run at least a 5-wire cable and hook up 24V common. You may be able to get your system to work with a power robbing thermostat. Those will work without a common. They use the Y & W as a ground (common) when heat or cool is off, using just a trickle of current to power the thermostat. Power robbing thermostats usually don't have back lit displays, as that requires more power than they can steal. Stretch |
#8
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
wrote in message oups.com... Where does a lighted doorbell button get its power from? It only has two wires and it lights without ringing the doorbell. Mike The light bulb is in series with the transformer and the door bell coil. The bulb does not draw enough current that would pull in the door bell coil. When you press the button, the bulb is shorted out and the only thing in the circuit with the transformer is the coil. |
#9
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
If the thermostat connects R to W when it calls for heat that's not the
same as shorting it to ground! A digital stat will still get power. If a call for heat is grounding out the 24V then presumably something is wired wrong, the stat is defective or something is wrong at the furnace end. |
#10
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
On Sun, 18 Dec 2005 19:14:23 -0500, Max Metral wrote:
They were indeed remarkably rude. At least most of them, a couple were helpful. Anyhow, the main question has now become, if my digital (i.e. needs power) thermostat says it only requires the following leads connected: R - 24vac G - fan W - heat Y - cool Where does it get power when it demands heat, thus shorting (?) G and W to R? I would assume (standard decomposition of assume applies) that it gets it from Y staying at ground, and perhaps that's where the fault has occurred. If not, where else can it pull the power? If the thermostat does not have batteries, you may need to connect the other side of the transformer to C (common). Some thermostats I got for our warehouse need that if you want to use them without the batteries (although I think that is just mentioned, not shown in wiring diagram). |
#11
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
On Sun, 18 Dec 2005 19:14:23 -0500, "Max Metral"
wrote: They were indeed remarkably rude. At least most of them, a couple were helpful. Anyhow, the main question has now become, if my digital (i.e. needs power) thermostat says it only requires the following leads connected: R - 24vac G - fan W - heat Y - cool Where does it get power when it demands heat, thus shorting (?) G and W to R? Is this a question with a built -in answer! The way you have your question, after the chart, makes me think you don't underwstand. First, I'm pretty sure the thermostat gets its power from the same source when it is "calling for heat" as any other time.** Assuming your colors, when you turn the fan to On, it's going to connect the R to the G, so the fan terminal back at the furnace gets 24 volts. But when you turn the thermostat switch to Heat, and it is cold enough to call for heat, it's going to connect the R to the W, so that the Heat terminal back at the furnace gets 24 volts. Unless the fan switch is on fan (and if that is the case, the fan is already running) it's not going to supply 24 volts to the G, because that would keep the fan running regardless of what the heating circuit wants, and the heating circuits in the last 30 years or more have wants. They want the fan OFF until the air in the furnace is hot, and they want the fan ON until the air in the furnace has cooled off a lot. The heat circuit is in charge of the entire heat functioning, including the fan. The Fan is directly controlled by the thermostat, only when the Fan/Auto switch is set on Fan. ** In my case, that is the furnace with battery backup. I know that because I haven't replaced the battery in more than a decade, and indeed when I turn off the power to the furnace, the thermostat forgets what time it is. So I know the furnace powers it, and I'm sure the battery would also if it weren't dead. But I get the impression that not all thermostats work the same way. (I only depend on the battery to keep the day and time. The temperature and setback times are set by mechanical multi-segment slide switches.) I would assume (standard decomposition of assume applies) that it gets it from Y staying at ground, and perhaps that's where the fault has occurred. If not, where else can it pull the power? wrote in message ups.com... I guess you gave up on those pricks in alt.hvac, eh? Remove NOPSAM to email me. Please let me know if you have posted also. |
#12
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
mm wrote:
On Sun, 18 Dec 2005 19:14:23 -0500, "Max Metral" wrote: They were indeed remarkably rude. At least most of them, a couple were helpful. Anyhow, the main question has now become, if my digital (i.e. needs power) thermostat says it only requires the following leads connected: R - 24vac G - fan W - heat Y - cool Where does it get power when it demands heat, thus shorting (?) G and W to R? Is this a question with a built -in answer! The way you have your question, after the chart, makes me think you don't underwstand. First, I'm pretty sure the thermostat gets its power from the same source when it is "calling for heat" as any other time.** Assuming your colors, when you turn the fan to On, it's going to connect the R to the G, so the fan terminal back at the furnace gets 24 volts. But when you turn the thermostat switch to Heat, and it is cold enough to call for heat, it's going to connect the R to the W, so that the Heat terminal back at the furnace gets 24 volts. Unless the fan switch is on fan (and if that is the case, the fan is already running) it's not going to supply 24 volts to the G, because that would keep the fan running regardless of what the heating circuit wants, and the heating circuits in the last 30 years or more have wants. They want the fan OFF until the air in the furnace is hot, and they want the fan ON until the air in the furnace has cooled off a lot. The heat circuit is in charge of the entire heat functioning, including the fan. The Fan is directly controlled by the thermostat, only when the Fan/Auto switch is set on Fan. ** In my case, that is the furnace with battery backup. I know that because I haven't replaced the battery in more than a decade, and indeed when I turn off the power to the furnace, the thermostat forgets what time it is. So I know the furnace powers it, and I'm sure the battery would also if it weren't dead. But I get the impression that not all thermostats work the same way. (I only depend on the battery to keep the day and time. The temperature and setback times are set by mechanical multi-segment slide switches.) I would assume (standard decomposition of assume applies) that it gets it from Y staying at ground, and perhaps that's where the fault has occurred. If not, where else can it pull the power? wrote in message oups.com... I guess you gave up on those pricks in alt.hvac, eh? Remove NOPSAM to email me. Please let me know if you have posted also. Hi, 24V is coming from a step down transformer. Battery back up for 'stat is to keep the program settings. As long as main power breaker to furnace is on, 24V should be present. It's called logic sequence control power. If it goes missing, something is shorting it out or the transformer is bad. Or sosmething is loose. Tony |
#13
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Max Metral wrote: Hi. I have a Lenox furnace, about 15 years old I guess. It was working fine, but then all of the sudden the thermostat seemed to just die. So I swapped thermostats. It worked again for a couple of days, and then failed again. So I debugged it a bit more carefully, and it turns out the thermostat "resets" whenever it tries to call for heat. The fan will come on for about a tenth of a second, and then the display acts like it does when you first plug it in. I'm not sure exactly what's happening, but it SEEMS that the furnace is shutting off 24v when heat is called. It's not the blower though, because if I just turn the fan on (from the thermostat) it works fine. It's also possible that the therm is somehow resetting itself, the only real test I did here was connecting 24v to the heat line directly, and the heat didn't come on, but I'm not sure if that's the proper "protocol" for requesting heat. Any thoughts before I call the techs? Thanks, --Max If your thermostat takes batteries then replace them. A battery powered t-stat with weak batteries will drop out when it attempts to bring in heating or cooling, having enough power for the display, but not enough for the internal relay circuits. If your thermostat doesn't take batteries then it is a power stealing stat, using Y to tap into common back through the compressor contactor. Depending upon model Y may or may not go directly to the compressor contactor--it may go instead through an electronic circuit on a main control board. This type of system may require that a resistor be wired across Y and C in the unit in order to provide a low resistance path from Y to C. This type of stat usually comes with a large ceramic resistor packaged with it. There are also power stealing stats that also use batteries for backup. The batteries in these are only provided to hold program and temp settings in the event of a power failure. Barring all of this it may be that your unit is shorted somewhere internally which could cause power to drop at the transformer, and thus from the t-stat when it calls for heat. hvacrmedic |
#14
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
So, it turns out the therm IS a power stealing therm. What's strange is
that when EVERYTHING is off, I still have 0V across Y and R**, so of course the therm has nowhere to steal power from when R and W are connected. The obvious fix is to connect C (I don't have a labeled C on the furnace board, will a screw terminal on the chassis do?) But the most confusing part is that this has worked for years, and now suddenly stopped. So I'm not sure if that means something has gone wrong with the unit and I should tread carefully. I'm also not sure whether this is just a little reminder that a 15 year old furnace should be scrapped. ** In truth, it's not 0, it's some barely readable amount. The meter moves, but hardly. "RP" wrote in message et... Max Metral wrote: Hi. I have a Lenox furnace, about 15 years old I guess. It was working fine, but then all of the sudden the thermostat seemed to just die. So I swapped thermostats. It worked again for a couple of days, and then failed again. So I debugged it a bit more carefully, and it turns out the thermostat "resets" whenever it tries to call for heat. The fan will come on for about a tenth of a second, and then the display acts like it does when you first plug it in. I'm not sure exactly what's happening, but it SEEMS that the furnace is shutting off 24v when heat is called. It's not the blower though, because if I just turn the fan on (from the thermostat) it works fine. It's also possible that the therm is somehow resetting itself, the only real test I did here was connecting 24v to the heat line directly, and the heat didn't come on, but I'm not sure if that's the proper "protocol" for requesting heat. Any thoughts before I call the techs? Thanks, --Max If your thermostat takes batteries then replace them. A battery powered t-stat with weak batteries will drop out when it attempts to bring in heating or cooling, having enough power for the display, but not enough for the internal relay circuits. If your thermostat doesn't take batteries then it is a power stealing stat, using Y to tap into common back through the compressor contactor. Depending upon model Y may or may not go directly to the compressor contactor--it may go instead through an electronic circuit on a main control board. This type of system may require that a resistor be wired across Y and C in the unit in order to provide a low resistance path from Y to C. This type of stat usually comes with a large ceramic resistor packaged with it. There are also power stealing stats that also use batteries for backup. The batteries in these are only provided to hold program and temp settings in the event of a power failure. Barring all of this it may be that your unit is shorted somewhere internally which could cause power to drop at the transformer, and thus from the t-stat when it calls for heat. hvacrmedic |
#15
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
It's my understanding that there is no C on most wiring, because there
isn't a need for one. (Ungrounded light switches don't have a common wire; they just connect the hot wire to the light.) All of the appliances are grounded so you only need the power wire and a wire for each device. Connecting R (24VAC) to a appliance's wire completes the circuit and allows the appliance to run. If it has worked for years then, yes, something has gone wrong. I would verify the wiring and then call the furnace guy to fix the problem. Mike |
#16
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Oh, and on a side note...
My mother's furnace behaved similarly years ago. The completely incompetent LICENSED HVAC guys that installed her furnace didn't ground it and it kept frying control boards. Fortunately, after their many stupid attempts to fix it and subsequent complaints to the manufacturer, Bryant sent their own techs out to fix it. And then Bryant stopped those lamebrains from using their products again. Mike |
#17
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
|
#18
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Max Metral wrote: So, it turns out the therm IS a power stealing therm. What's strange is that when EVERYTHING is off, I still have 0V across Y and R**, so of course the therm has nowhere to steal power from when R and W are connected. The obvious fix is to connect C (I don't have a labeled C on the furnace board, will a screw terminal on the chassis do?) But the most confusing part is that this has worked for years, and now suddenly stopped. So I'm not sure if that means something has gone wrong with the unit and I should tread carefully. I'm also not sure whether this is just a little reminder that a 15 year old furnace should be scrapped. Call a tech. hvacrmedic ** In truth, it's not 0, it's some barely readable amount. The meter moves, but hardly. "RP" wrote in message et... Max Metral wrote: Hi. I have a Lenox furnace, about 15 years old I guess. It was working fine, but then all of the sudden the thermostat seemed to just die. So I swapped thermostats. It worked again for a couple of days, and then failed again. So I debugged it a bit more carefully, and it turns out the thermostat "resets" whenever it tries to call for heat. The fan will come on for about a tenth of a second, and then the display acts like it does when you first plug it in. I'm not sure exactly what's happening, but it SEEMS that the furnace is shutting off 24v when heat is called. It's not the blower though, because if I just turn the fan on (from the thermostat) it works fine. It's also possible that the therm is somehow resetting itself, the only real test I did here was connecting 24v to the heat line directly, and the heat didn't come on, but I'm not sure if that's the proper "protocol" for requesting heat. Any thoughts before I call the techs? Thanks, --Max If your thermostat takes batteries then replace them. A battery powered t-stat with weak batteries will drop out when it attempts to bring in heating or cooling, having enough power for the display, but not enough for the internal relay circuits. If your thermostat doesn't take batteries then it is a power stealing stat, using Y to tap into common back through the compressor contactor. Depending upon model Y may or may not go directly to the compressor contactor--it may go instead through an electronic circuit on a main control board. This type of system may require that a resistor be wired across Y and C in the unit in order to provide a low resistance path from Y to C. This type of stat usually comes with a large ceramic resistor packaged with it. There are also power stealing stats that also use batteries for backup. The batteries in these are only provided to hold program and temp settings in the event of a power failure. Barring all of this it may be that your unit is shorted somewhere internally which could cause power to drop at the transformer, and thus from the t-stat when it calls for heat. hvacrmedic |
#19
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
In article .com,
wrote: Where does a lighted doorbell button get its power from? It only has two wires and it lights without ringing the doorbell. The transformer that supplies the doorbell supplies the light. The current drain for the light also flows thru the bell, but is much lower than the current needed to ring the bell. When you press the button, the light is shorted and the current rises to enough to ring the bell. -- Rich Greenberg Marietta, GA, USA richgr atsign panix.com + 1 770 321 6507 Eastern time. N6LRT I speak for myself & my dogs only. VM'er since CP-67 Canines:Val, Red & Shasta (RIP),Red, husky Owner:Chinook-L Atlanta Siberian Husky Rescue. www.panix.com/~richgr/ Asst Owner:Sibernet-L |
#20
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Yes, it was a dangerous mistake. I should have said common instead of
ground. My point was that you don't need both sides of a power supply, because you only switch one. Thanks. Mike |
#21
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
On Sun, 18 Dec 2005 19:14:23 -0500, "Max Metral"
wrote: They were indeed remarkably rude. At least most of them, a couple were helpful. Anyhow, the main question has now become, if my digital (i.e. needs power) thermostat says it only requires the following leads connected: R - 24vac G - fan W - heat Y - cool Where does it get power when it demands heat, thus shorting (?) G and W to R? Some furnaces switch the fan internally when heat is being used, and require only R & W to be shorted. I would assume (standard decomposition of assume applies) that it gets it from Y staying at ground, I would assume Y would be connected to a relay coil for the AC compressor, and would be open not ground. It may be possible to use it for a ground, as long as the current drain in very low. and perhaps that's where the fault has occurred. If not, where else can it pull the power? The first electronic thermostat I installed required an additional connection, which required running a 5th wire. The contact point wasn't hard to find, since I had a wiring diagram for that furnace. I think it was labeled "C" (24VAC common). The thermostat I have now (in a different house), uses a separate power supply (wall wart). wrote in message ups.com... I guess you gave up on those pricks in alt.hvac, eh? -- 6 days until the winter solstice celebration Mark Lloyd http://notstupid.laughingsquid.com "Democracy is two wolves and a lamb voting on what to have for lunch. Liberty is a well armed lamb contesting the vote." - Benjamin Franklin |
#23
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
On Mon, 19 Dec 2005 07:11:14 GMT, Tony Hwang wrote:
mm wrote: On Sun, 18 Dec 2005 19:14:23 -0500, "Max Metral" wrote: They were indeed remarkably rude. At least most of them, a couple were helpful. Anyhow, the main question has now become, if my digital (i.e. needs power) thermostat says it only requires the following leads connected: R - 24vac G - fan W - heat Y - cool Where does it get power when it demands heat, thus shorting (?) G and W to R? Is this a question with a built -in answer! The way you have your question, after the chart, makes me think you don't underwstand. First, I'm pretty sure the thermostat gets its power from the same source when it is "calling for heat" as any other time.** Assuming your colors, when you turn the fan to On, it's going to connect the R to the G, so the fan terminal back at the furnace gets 24 volts. But when you turn the thermostat switch to Heat, and it is cold enough to call for heat, it's going to connect the R to the W, so that the Heat terminal back at the furnace gets 24 volts. Unless the fan switch is on fan (and if that is the case, the fan is already running) it's not going to supply 24 volts to the G, because that would keep the fan running regardless of what the heating circuit wants, and the heating circuits in the last 30 years or more have wants. They want the fan OFF until the air in the furnace is hot, and they want the fan ON until the air in the furnace has cooled off a lot. The heat circuit is in charge of the entire heat functioning, including the fan. The Fan is directly controlled by the thermostat, only when the Fan/Auto switch is set on Fan. ** In my case, that is the furnace with battery backup. I know that because I haven't replaced the battery in more than a decade, and indeed when I turn off the power to the furnace, the thermostat forgets what time it is. So I know the furnace powers it, and I'm sure the battery would also if it weren't dead. But I get the impression that not all thermostats work the same way. (I only depend on the battery to keep the day and time. The temperature and setback times are set by mechanical multi-segment slide switches.) I would assume (standard decomposition of assume applies) that it gets it from Y staying at ground, and perhaps that's where the fault has occurred. If not, where else can it pull the power? wrote in message roups.com... I guess you gave up on those pricks in alt.hvac, eh? Remove NOPSAM to email me. Please let me know if you have posted also. Hi, 24V is coming from a step down transformer. Battery back up for 'stat is to keep the program settings. As long as main power breaker to furnace is on, 24V should be present. It's called logic sequence control power. If it goes missing, something is shorting it out or the transformer is bad. Or sosmething is loose. Tony On at least one furnace I've seen, the overheat switch would cut off the 24V. This disables the gas valve and fan relay. The fan relay (the one associated with heat, not "fan on" from thermostat) controls the fan through the NC (normally closed) contact, so the fan runs constantly in this case. -- 6 days until the winter solstice celebration Mark Lloyd http://notstupid.laughingsquid.com "Democracy is two wolves and a lamb voting on what to have for lunch. Liberty is a well armed lamb contesting the vote." - Benjamin Franklin |
#24
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
On Mon, 19 Dec 2005 09:37:45 -0500, "Max Metral"
wrote: So, it turns out the therm IS a power stealing therm. What's strange is that when EVERYTHING is off, I still have 0V across Y and R**, so of course the therm has nowhere to steal power from when R and W are connected. The obvious fix is to connect C (I don't have a labeled C on the furnace board, will a screw terminal on the chassis do?) Do you have a wiring diagram? It would show what the other side of the 24V transformer secondary is connected to. If this furnace is connected to (or can be connected to) air conditioning, there should be a C connection to go to the compressor. But the most confusing part is that this has worked for years, and now suddenly stopped. So I'm not sure if that means something has gone wrong with the unit and I should tread carefully. I'm also not sure whether this is just a little reminder that a 15 year old furnace should be scrapped. ** In truth, it's not 0, it's some barely readable amount. The meter moves, but hardly. "RP" wrote in message news:y_2dnSizw4KZ9TvenZ2dnUVZ_sGdnZ2d@centurytel. net... Max Metral wrote: Hi. I have a Lenox furnace, about 15 years old I guess. It was working fine, but then all of the sudden the thermostat seemed to just die. So I swapped thermostats. It worked again for a couple of days, and then failed again. So I debugged it a bit more carefully, and it turns out the thermostat "resets" whenever it tries to call for heat. The fan will come on for about a tenth of a second, and then the display acts like it does when you first plug it in. I'm not sure exactly what's happening, but it SEEMS that the furnace is shutting off 24v when heat is called. It's not the blower though, because if I just turn the fan on (from the thermostat) it works fine. It's also possible that the therm is somehow resetting itself, the only real test I did here was connecting 24v to the heat line directly, and the heat didn't come on, but I'm not sure if that's the proper "protocol" for requesting heat. Any thoughts before I call the techs? Thanks, --Max If your thermostat takes batteries then replace them. A battery powered t-stat with weak batteries will drop out when it attempts to bring in heating or cooling, having enough power for the display, but not enough for the internal relay circuits. If your thermostat doesn't take batteries then it is a power stealing stat, using Y to tap into common back through the compressor contactor. Depending upon model Y may or may not go directly to the compressor contactor--it may go instead through an electronic circuit on a main control board. This type of system may require that a resistor be wired across Y and C in the unit in order to provide a low resistance path from Y to C. This type of stat usually comes with a large ceramic resistor packaged with it. There are also power stealing stats that also use batteries for backup. The batteries in these are only provided to hold program and temp settings in the event of a power failure. Barring all of this it may be that your unit is shorted somewhere internally which could cause power to drop at the transformer, and thus from the t-stat when it calls for heat. hvacrmedic -- 6 days until the winter solstice celebration Mark Lloyd http://notstupid.laughingsquid.com "Democracy is two wolves and a lamb voting on what to have for lunch. Liberty is a well armed lamb contesting the vote." - Benjamin Franklin |
#25
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Well, the uncertainty about why this happened after two working heating
seasons will be a great unanswered question in my life. (ok, well, not that great) BUT, the problem is solved. So, as suspected, the digital therm was simply losing access to power when it routed R to W. The additional variable that I didn't realize is that there's a summer/winter hard switch on the furnace. I assumed that normally I had switched this to winter in the past. However, with meter in hand if the switch is on summer, I measure 24VAC across R and Y. If the switch is on summer, I measure 0VAC. I don't understand exactly what this switch does that other than I suppose forcibly disabling the compressor. But given this fact, there's no way for the therm to steal power when it requests heat, and it shuts off. My only explanation for previous success is that perhaps I forgot to switch that to winter in the past. I suppose maybe that switch does something more complex, which USED to leave Y at ground but doesn't anymore. It's also a remote possibility that the power stealing can work by stealing from the fan input, and that in my reconfiguring the therms, I reset it to request fan and heat simultaneously thus killing 24VAC on G. In any case, the solution was simple, run a dedicated C. That was sort of the obvious first fix, but it just concerned me why it was a problem now. I'll use the money I saved by not calling a tech for this to call them for my other problem, which is a radiant baseboard unit that spews water way too often. Now *that* I have no chance of fixing myself. "RP" wrote in message ... Max Metral wrote: So, it turns out the therm IS a power stealing therm. What's strange is that when EVERYTHING is off, I still have 0V across Y and R**, so of course the therm has nowhere to steal power from when R and W are connected. The obvious fix is to connect C (I don't have a labeled C on the furnace board, will a screw terminal on the chassis do?) But the most confusing part is that this has worked for years, and now suddenly stopped. So I'm not sure if that means something has gone wrong with the unit and I should tread carefully. I'm also not sure whether this is just a little reminder that a 15 year old furnace should be scrapped. Call a tech. hvacrmedic ** In truth, it's not 0, it's some barely readable amount. The meter moves, but hardly. "RP" wrote in message et... Max Metral wrote: Hi. I have a Lenox furnace, about 15 years old I guess. It was working fine, but then all of the sudden the thermostat seemed to just die. So I swapped thermostats. It worked again for a couple of days, and then failed again. So I debugged it a bit more carefully, and it turns out the thermostat "resets" whenever it tries to call for heat. The fan will come on for about a tenth of a second, and then the display acts like it does when you first plug it in. I'm not sure exactly what's happening, but it SEEMS that the furnace is shutting off 24v when heat is called. It's not the blower though, because if I just turn the fan on (from the thermostat) it works fine. It's also possible that the therm is somehow resetting itself, the only real test I did here was connecting 24v to the heat line directly, and the heat didn't come on, but I'm not sure if that's the proper "protocol" for requesting heat. Any thoughts before I call the techs? Thanks, --Max If your thermostat takes batteries then replace them. A battery powered t-stat with weak batteries will drop out when it attempts to bring in heating or cooling, having enough power for the display, but not enough for the internal relay circuits. If your thermostat doesn't take batteries then it is a power stealing stat, using Y to tap into common back through the compressor contactor. Depending upon model Y may or may not go directly to the compressor contactor--it may go instead through an electronic circuit on a main control board. This type of system may require that a resistor be wired across Y and C in the unit in order to provide a low resistance path from Y to C. This type of stat usually comes with a large ceramic resistor packaged with it. There are also power stealing stats that also use batteries for backup. The batteries in these are only provided to hold program and temp settings in the event of a power failure. Barring all of this it may be that your unit is shorted somewhere internally which could cause power to drop at the transformer, and thus from the t-stat when it calls for heat. hvacrmedic |
#26
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
On Sun, 18 Dec 2005 07:46:52 -0500, "Max Metral"
wrote: Hi. I have a Lenox furnace, about 15 years old I guess. It was working fine, but then all of the sudden the thermostat seemed to just die. So I swapped thermostats. It worked again for a couple of days, and then failed again. So I debugged it a bit more carefully, and it turns out the thermostat "resets" whenever it tries to call for heat. The fan will come on for about a tenth of a second, and then the display acts like it does when you first plug it in. I'm not sure exactly what's happening, but it SEEMS that the furnace is shutting off 24v when heat is called. It's not the blower though, because if I just turn the fan on (from the thermostat) it works fine. It's also possible that the therm is somehow resetting itself, the only real test I did here was connecting 24v to the heat line directly, and the heat didn't come on, but I'm not sure if that's the proper "protocol" for requesting heat. Any thoughts before I call the techs? Thanks, --Max You are on the right path. Just keep troubleshooting until you find the culprit. Look for a schematic on the furnace and you should find the controls in the circuit, one of which is malfunctioning. Wiring and/or connections could be the culprit too. |
#27
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Max Metral wrote:
Well, the uncertainty about why this happened after two working heating seasons will be a great unanswered question in my life. (ok, well, not that great) BUT, the problem is solved. So, as suspected, the digital therm was simply losing access to power when it routed R to W. The additional variable that I didn't realize is that there's a summer/winter hard switch on the furnace. I assumed that normally I had switched this to winter in the past. However, with meter in hand if the switch is on summer, I measure 24VAC across R and Y. If the switch is on summer, I measure 0VAC. I don't understand exactly what this switch does that other than I suppose forcibly disabling the compressor. But given this fact, there's no way for the therm to steal power when it requests heat, and it shuts off. snip So which is it when it's on summer -- 24VAC or 0VAC? (I think you mis-typed in the above quote.) If this is an attic-mount furnace, then my guess would be zero, which keeps the heat from coming on when, e.g., an attic exhaust fan might be running (which could lead to dangerous levels of CO). It sounds to me like whoever installed the digital thermostat didn't cover all the bases. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#28
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Yes, I mistyped, it should read:
....with meter in hand if the switch is on summer, I measure 24VAC across R and Y. If the switch is on winter, I measure 0VAC across R and Y. "CJT" wrote in message ... Max Metral wrote: Well, the uncertainty about why this happened after two working heating seasons will be a great unanswered question in my life. (ok, well, not that great) BUT, the problem is solved. So, as suspected, the digital therm was simply losing access to power when it routed R to W. The additional variable that I didn't realize is that there's a summer/winter hard switch on the furnace. I assumed that normally I had switched this to winter in the past. However, with meter in hand if the switch is on summer, I measure 24VAC across R and Y. If the switch is on summer, I measure 0VAC. I don't understand exactly what this switch does that other than I suppose forcibly disabling the compressor. But given this fact, there's no way for the therm to steal power when it requests heat, and it shuts off. snip So which is it when it's on summer -- 24VAC or 0VAC? (I think you mis-typed in the above quote.) If this is an attic-mount furnace, then my guess would be zero, which keeps the heat from coming on when, e.g., an attic exhaust fan might be running (which could lead to dangerous levels of CO). It sounds to me like whoever installed the digital thermostat didn't cover all the bases. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#29
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Max Metral wrote:
Yes, I mistyped, it should read: ...with meter in hand if the switch is on summer, I measure 24VAC across R and Y. If the switch is on winter, I measure 0VAC across R and Y. Well, I think now I'm the one who mis-spoke. :-) Having 24 VAC across R and Y in the summer is what you want, because then you can effectively call for cooling. In winter, you'd want it across R and W instead, to allow calling for heat. This could still be part of an interlock with an attic fan. "CJT" wrote in message ... Max Metral wrote: Well, the uncertainty about why this happened after two working heating seasons will be a great unanswered question in my life. (ok, well, not that great) BUT, the problem is solved. So, as suspected, the digital therm was simply losing access to power when it routed R to W. The additional variable that I didn't realize is that there's a summer/winter hard switch on the furnace. I assumed that normally I had switched this to winter in the past. However, with meter in hand if the switch is on summer, I measure 24VAC across R and Y. If the switch is on summer, I measure 0VAC. I don't understand exactly what this switch does that other than I suppose forcibly disabling the compressor. But given this fact, there's no way for the therm to steal power when it requests heat, and it shuts off. snip So which is it when it's on summer -- 24VAC or 0VAC? (I think you mis-typed in the above quote.) If this is an attic-mount furnace, then my guess would be zero, which keeps the heat from coming on when, e.g., an attic exhaust fan might be running (which could lead to dangerous levels of CO). It sounds to me like whoever installed the digital thermostat didn't cover all the bases. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#30
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
On Monday 19 December 2005 12:43, Mark Lloyd wrote:
BTW, considering strange electrical stuff, what if you had an old (Edison base) fuse box that you could screw a light bulb into instead of a fuse? When I was young (not too long ago) I read in some sort of "home emergencies" type of book something to the effect that you could screw in a light bulb in the fuse box to locate or diagnose a short. The bulb would glow brightly when there was too much current going through it. I'm guessing that if you screwed in a light bulb in a fuse box, the brightness or dimness of the glow would depend on how much current was being drawn on that circuit. -- Travis Evans [The email address on this post is valid, but may change from time to time. Make sure you use the latest email address; if you use an old one, I will not receive your message.] |
#31
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
"Travis Evans" wrote in message news:BmHpf.437$Cw5.54@fed1read05... On Monday 19 December 2005 12:43, Mark Lloyd wrote: BTW, considering strange electrical stuff, what if you had an old (Edison base) fuse box that you could screw a light bulb into instead of a fuse? When I was young (not too long ago) I read in some sort of "home emergencies" type of book something to the effect that you could screw in a light bulb in the fuse box to locate or diagnose a short. The bulb would glow brightly when there was too much current going through it. I'm guessing that if you screwed in a light bulb in a fuse box, the brightness or dimness of the glow would depend on how much current was being drawn on that circuit. That is true. While I don't recommend it to people that are not use to working with electricity, a trouble shooting practice is to subistute a lamp with for the fuse or breaker. If the circuit is suspose to be open the light will not burn. If you put in a 100 watt bulb in a 120 volt circuit and it lights up to full brightness then you have a short circuit or some device in the circuit that is drawing current. If you are sure there is nothing in the circuit you look around and disconnect things tuil the light goes out. If there could be a high current (more that an amp or two) device in the circuit, you will have to disconnect it. Anything in the circuit that uses less than a couple of amps will cause the light to burn dimmer. |
#32
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Ralph Mowery wrote: "Travis Evans" wrote in message news:BmHpf.437$Cw5.54@fed1read05... On Monday 19 December 2005 12:43, Mark Lloyd wrote: BTW, considering strange electrical stuff, what if you had an old (Edison base) fuse box that you could screw a light bulb into instead of a fuse? When I was young (not too long ago) I read in some sort of "home emergencies" type of book something to the effect that you could screw in a light bulb in the fuse box to locate or diagnose a short. The bulb would glow brightly when there was too much current going through it. I'm guessing that if you screwed in a light bulb in a fuse box, the brightness or dimness of the glow would depend on how much current was being drawn on that circuit. That is true. While I don't recommend it to people that are not use to working with electricity, a trouble shooting practice is to subistute a lamp with for the fuse or breaker. If the circuit is suspose to be open the light will not burn. If you put in a 100 watt bulb in a 120 volt circuit and it lights up to full brightness then you have a short circuit or some device in the circuit that is drawing current. If you are sure there is nothing in the circuit you look around and disconnect things tuil the light goes out. If there could be a high current (more that an amp or two) device in the circuit, you will have to disconnect it. Anything in the circuit that uses less than a couple of amps will cause the light to burn dimmer. Sounds like a good way to burn down a house or to smoke a few small appliances. For an encore you can slip a penny under the fuse. Dear readers, please don't try any of this at home! hvacrmedic |
#33
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
That is true. While I don't recommend it to people that are not use to working with electricity, a trouble shooting practice is to subistute a lamp with for the fuse or breaker. If the circuit is suspose to be open the light will not burn. If you put in a 100 watt bulb in a 120 volt circuit Of course, the sensible thing to do would be to shut off the breaker, and test continuity from the nuetral to the hot, but that requires a hunk of equipment that costs several thousand pennies. |
#34
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Goedjn wrote:
That is true. While I don't recommend it to people that are not use to working with electricity, a trouble shooting practice is to subistute a lamp with for the fuse or breaker. If the circuit is suspose to be open the light will not burn. If you put in a 100 watt bulb in a 120 volt circuit Of course, the sensible thing to do would be to shut off the breaker, and test continuity from the nuetral to the hot, but that requires a hunk of equipment that costs several thousand pennies. Before you do that, check the voltage between the two. You're presumably working on a troubled circuit. Don't assume shutting off the breaker eliminates all sources of electricity. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#35
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
On Mon, 19 Dec 2005 17:57:42 -0600, RP
wrote: Ralph Mowery wrote: "Travis Evans" wrote in message news:BmHpf.437$Cw5.54@fed1read05... On Monday 19 December 2005 12:43, Mark Lloyd wrote: BTW, considering strange electrical stuff, what if you had an old (Edison base) fuse box that you could screw a light bulb into instead of a fuse? When I was young (not too long ago) I read in some sort of "home emergencies" type of book something to the effect that you could screw in a light bulb in the fuse box to locate or diagnose a short. The bulb would glow brightly when there was too much current going through it. I'm guessing that if you screwed in a light bulb in a fuse box, the brightness or dimness of the glow would depend on how much current was being drawn on that circuit. That is true. While I don't recommend it to people that are not use to working with electricity, a trouble shooting practice is to subistute a lamp with for the fuse or breaker. If the circuit is suspose to be open the light will not burn. If you put in a 100 watt bulb in a 120 volt circuit and it lights up to full brightness then you have a short circuit or some device in the circuit that is drawing current. If you are sure there is nothing in the circuit you look around and disconnect things tuil the light goes out. If there could be a high current (more that an amp or two) device in the circuit, you will have to disconnect it. Anything in the circuit that uses less than a couple of amps will cause the light to burn dimmer. Sounds like a good way to burn down a house or to smoke a few small appliances. For an encore you can slip a penny under the fuse. Dear readers, please don't try any of this at home! Are you somehow equating a penny and a light bulb? A light bulb has a much higher resistance, and (unless it got shorted somehow) could never (on 120V) pass a current higher than 833mA (for a 100W bulb). It wouldn't even conduct that much unless it was into a shorted circuit. I used to work at Goodwill (for awhile), and they actually used light bulbs in series for testing appliances. hvacrmedic -- 5 days until the winter solstice celebration Mark Lloyd http://notstupid.laughingsquid.com "Democracy is two wolves and a lamb voting on what to have for lunch. Liberty is a well armed lamb contesting the vote." - Benjamin Franklin |
#36
Posted to alt.home.repair
|
|||
|
|||
Furnace losing 24v when heat requested
Mark Lloyd wrote: On Mon, 19 Dec 2005 17:57:42 -0600, RP wrote: Ralph Mowery wrote: "Travis Evans" wrote in message news:BmHpf.437$Cw5.54@fed1read05... On Monday 19 December 2005 12:43, Mark Lloyd wrote: BTW, considering strange electrical stuff, what if you had an old (Edison base) fuse box that you could screw a light bulb into instead of a fuse? When I was young (not too long ago) I read in some sort of "home emergencies" type of book something to the effect that you could screw in a light bulb in the fuse box to locate or diagnose a short. The bulb would glow brightly when there was too much current going through it. I'm guessing that if you screwed in a light bulb in a fuse box, the brightness or dimness of the glow would depend on how much current was being drawn on that circuit. That is true. While I don't recommend it to people that are not use to working with electricity, a trouble shooting practice is to subistute a lamp with for the fuse or breaker. If the circuit is suspose to be open the light will not burn. If you put in a 100 watt bulb in a 120 volt circuit and it lights up to full brightness then you have a short circuit or some device in the circuit that is drawing current. If you are sure there is nothing in the circuit you look around and disconnect things tuil the light goes out. If there could be a high current (more that an amp or two) device in the circuit, you will have to disconnect it. Anything in the circuit that uses less than a couple of amps will cause the light to burn dimmer. Sounds like a good way to burn down a house or to smoke a few small appliances. For an encore you can slip a penny under the fuse. Dear readers, please don't try any of this at home! Are you somehow equating a penny and a light bulb? A light bulb has a much higher resistance, and (unless it got shorted somehow) could never (on 120V) pass a current higher than 833mA (for a 100W bulb). It wouldn't even conduct that much unless it was into a shorted circuit. I used to work at Goodwill (for awhile), and they actually used light bulbs in series for testing appliances. Two reasons its a stupid idea: Suppose the ohmic resistance of the light bulb is 240ohms (60watt incandescent). Now suppose that the resistance at the short is 240ohms when you have the bulb in place in the fuse box. Each load drops 60 volts for a total of 15watts dissipated at the short. Now suppose the short is where a wire nut has fallen off. The wire junction has gotten next to the fart fan housing and is arcing to the paper thin sheet metal. There is a paper label inside the housing of the fart, opposite the short, and the arcing sets this paper on fire. How long to you think it will be before 15 watts continuously dissipating will get a junction hot enough to ignite any combustible materials adjacent to it? Arcing shorts can cause fires, and are in fact responsible for a large number of electrical fires every year in the real world. The odds may be against a fire starting in any one particular instance with this method of short detection, but I'd hate like hell to be that one in ten-thousand statistic on anything that I was diagnosing. Now let's suppose that there is a small appliance plugged into an outlet on that circuit. The voltage dropped across that appliance will vary from 0 to 120 depending upon its resistance and upon the nature of any upstream short which can vary from 0 to infinity ohms. Most appliance won't be harmed with continuous low voltage for 5 to 30 minutes, but some will. I also wouldn't want to be responsible for a smoked electronic or motorized appliance. A volt/ohmmeter can be obtained from any Walmart store for $10, (or 1,000 pennies even). hvacrmedic |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
AquaTherm Furnace - No Hot Water Issue | Home Repair | |||
prog. therm. and heat pump questions | Home Repair | |||
Desperate for advice on replacing dead 255K BTU furnace in 3200 sq foot house | Home Ownership | |||
Gas Furnace Air Flow problem | Home Ownership | |||
Furnace Blower Comes on but heat does not | Home Ownership |