Unhappy Honeywell Thermostat Problem

I have three heat zones in my home, two upstairs and one in the basement. I recently upgraded my old mercury Honeywell thermostats upstairs to a digital type CT8775A. They are connected to Honeywell motorized valves at the boiler, type V8043E1012.

When I installed the thermostats I was careful to map the wiring and everything seemed fine, the digital display came up, the room temp was monitored and the backlight was working fine. However, now that I am starting to need the heat the problem occurs. When the room is above the temp of the thermostat setting everything is fine and the display works. When I raise the temp setting on the thermostat to turn the heating on, and after the furnace has fired up, the display goes blank, the backlight doesn't work but the furnace continues to burn. When the furnace switches off afet a couple of minutes the display reappears, only to disappear again.

I have tested the wiring connections at the boiler and behind the thermostat and they are all good. I have manually overridden the valve and tested the motor which appears to spin up OK. I don't know where to look next. Has anyone else had the same problem or can anyone suggest what the problem might be?
  #2   Report Post  
Posted to alt.home.repair
TURTLE
 
Posts: n/a
Default Honeywell Thermostat Problem

This is Turtle.

I can't see it from here but it sounds like a grounding of the
thermostat problem. Manual thermostats don't need these grounds but
digital does need these grounds to work properly. check out the
paperwork on the thermostat and see about the grounding of the
thermostat and which wire will do this.

TURTLE

  #3   Report Post  
Posted to alt.home.repair
CJT
 
Posts: n/a
Default Honeywell Thermostat Problem

TURTLE wrote:

This is Turtle.

I can't see it from here but it sounds like a grounding of the
thermostat problem. Manual thermostats don't need these grounds but
digital does need these grounds to work properly.


Doesn't that depend on whether or not they are battery operated?

check out the
paperwork on the thermostat and see about the grounding of the
thermostat and which wire will do this.

TURTLE



--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .
  #4   Report Post  
Posted to alt.home.repair
hvactech2
 
Posts: n/a
Default Honeywell Thermostat Problem

On Sat, 3 Dec 2005 18:04:09 +0000, Achattaway
wrote:


I have three heat zones in my home, two upstairs and one in the
basement. I recently upgraded my old mercury Honeywell thermostats
upstairs to a digital type CT8775A. They are connected to Honeywell
motorized valves at the boiler, type V8043E1012.

When I installed the thermostats I was careful to map the wiring and
everything seemed fine, the digital display came up, the room temp was
monitored and the backlight was working fine. However, now that I am
starting to need the heat the problem occurs. When the room is above
the temp of the thermostat setting everything is fine and the display
works. When I raise the temp setting on the thermostat to turn the
heating on, and after the furnace has fired up, the display goes blank,
the backlight doesn't work but the furnace continues to burn. When the
furnace switches off afet a couple of minutes the display reappears,
only to disappear again.

I have tested the wiring connections at the boiler and behind the
thermostat and they are all good. I have manually overridden the valve
and tested the motor which appears to spin up OK. I don't know where to
look next. Has anyone else had the same problem or can anyone suggest
what the problem might be?


Not being able to see what you have is a problem. what type of
controls do you have? how many transformers and what VA are they?
++++++++++++++++++++++++++++++++++++++++++++++++++ +++++++++++
spam protection measure, Please remove the 33 to send e-mail
  #5   Report Post  
Posted to alt.home.repair
CBHVAC
 
Posts: n/a
Default Honeywell Thermostat Problem


"CJT" wrote in message
...
TURTLE wrote:

This is Turtle.

I can't see it from here but it sounds like a grounding of the
thermostat problem. Manual thermostats don't need these grounds but
digital does need these grounds to work properly.


Doesn't that depend on whether or not they are battery operated?


SOME battery stats still need a COMMON...not a ground..there is not a ground
on a stat, unless its a line voltage stat..
Also, Honeywell has admitted problems with several stats...the VisionPro
series is one now...
Here lately, I just install Robertshaw 9800 series, and so far, no
problems....for heat pumps in particular, the 9865i is a champ...looks good
too.


check out the
paperwork on the thermostat and see about the grounding of the
thermostat and which wire will do this. TURTLE



--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .





  #6   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default Honeywell Thermostat Problem

This thermostat doesn't require a common, just the two wires. I would look
to the wattage of the transformer that's powering the three zone valves


"Achattaway" wrote in message
...

I have three heat zones in my home, two upstairs and one in the
basement. I recently upgraded my old mercury Honeywell thermostats
upstairs to a digital type CT8775A. They are connected to Honeywell
motorized valves at the boiler, type V8043E1012.

When I installed the thermostats I was careful to map the wiring and
everything seemed fine, the digital display came up, the room temp was
monitored and the backlight was working fine. However, now that I am
starting to need the heat the problem occurs. When the room is above
the temp of the thermostat setting everything is fine and the display
works. When I raise the temp setting on the thermostat to turn the
heating on, and after the furnace has fired up, the display goes blank,
the backlight doesn't work but the furnace continues to burn. When the
furnace switches off afet a couple of minutes the display reappears,
only to disappear again.

I have tested the wiring connections at the boiler and behind the
thermostat and they are all good. I have manually overridden the valve
and tested the motor which appears to spin up OK. I don't know where to
look next. Has anyone else had the same problem or can anyone suggest
what the problem might be?


--
Achattaway



  #7   Report Post  
Junior Member
 
Posts: 2
Default

Thanks for the replies so far. I have checked out the following as suggested: The wiring instructions for the thermostat do not show a requirement for a ground at the terminals, and it does not require a battery. An identical thermostat unit installed on the bedroom zone is working correctly. The transformer is rated at 24V so that rating should be fine with these thermostats. I have been monitoring excatly what seems to be happening: The display is on and showing the current room temperature. When I turn the dial to set the heat temp I want for the room the flame symbol appears and a few moments later the furnace fires up. After a short period of time the furnace cuts off, and after another short period the valve closes. When the valve closes, that is when the display shuts off. Several minutes later the display comes back on the valve has reopened, the room is not yet at the requested temperature, and the furnace may fire up again. After a short period of time again when the valve closes the display disappears again. This continues until either I switch the required setting to below the current room temperature, or when the room reaches the heat setting. I tried swapping the front panel from the bedroom zone, and the same thing happens. I am trying to determine whether the fault lies with the valve which is a few years old (not sure quite how old), or whether there is a fault with the thermostat before I go to the expense of replacing one or the other. Your suggestions are most welcome.



  #8   Report Post  
Posted to alt.home.repair
hvactech2
 
Posts: n/a
Default Honeywell Thermostat Problem

On Sun, 4 Dec 2005 16:51:09 +0000, Achattaway
wrote:


Thanks for the replies so far. I have checked out the following as
suggested: The wiring instructions for the thermostat do not show a
requirement for a ground at the terminals, and it does not require a
battery. An identical thermostat unit installed on the bedroom zone is
working correctly. The transformer is rated at 24V so that rating
should be fine with these thermostats. I have been monitoring excatly
what seems to be happening: The display is on and showing the current
room temperature. When I turn the dial to set the heat temp I want for
the room the flame symbol appears and a few moments later the furnace
fires up. After a short period of time the furnace cuts off, and after
another short period the valve closes. When the valve closes, that is
when the display shuts off. Several minutes later the display comes
back on the valve has reopened, the room is not yet at the requested
temperature, and the furnace may fire up again. After a short period
of time again when the valve closes the display disappears again. This
continues until either I switch the required setting to below the
current room temperature, or when the room reaches the heat setting. I
tried swapping the front panel from the bedroom zone, and the same thing
happens. I am trying to determine whether the fault lies with the valve
which is a few years old (not sure quite how old), or whether there is a
fault with the thermostat before I go to the expense of replacing one or
the other. Your suggestions are most welcome.


24 volts is normal but I really need to know how many transformers and
the VA rating of each before I can even take a guess.
++++++++++++++++++++++++++++++++++++++++++++++++++ +++++++++++
spam protection measure, Please remove the 33 to send e-mail
  #9   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default Honeywell Thermostat Problem

If you remove the stat and touch the two wires together, does the valve open
and circulator run?. The boiler won't necessarily start as it may already be
at high limit. If things run properly by touching the wires together, and
since you say you've already swapped the thermostat with another, I would be
looking for a weak transformer powering the zone valve(s). There may be one
or several. You need to find them and look for the wattage (VA) Standard
heating transformers are 40 VA, but sometimes zone valves are powered by the
transformer in a switching relay or aquastat relay.






"Achattaway" wrote in message
...

Thanks for the replies so far. I have checked out the following as
suggested: The wiring instructions for the thermostat do not show a
requirement for a ground at the terminals, and it does not require a
battery. An identical thermostat unit installed on the bedroom zone is
working correctly. The transformer is rated at 24V so that rating
should be fine with these thermostats. I have been monitoring excatly
what seems to be happening: The display is on and showing the current
room temperature. When I turn the dial to set the heat temp I want for
the room the flame symbol appears and a few moments later the furnace
fires up. After a short period of time the furnace cuts off, and after
another short period the valve closes. When the valve closes, that is
when the display shuts off. Several minutes later the display comes
back on the valve has reopened, the room is not yet at the requested
temperature, and the furnace may fire up again. After a short period
of time again when the valve closes the display disappears again. This
continues until either I switch the required setting to below the
current room temperature, or when the room reaches the heat setting. I
tried swapping the front panel from the bedroom zone, and the same thing
happens. I am trying to determine whether the fault lies with the valve
which is a few years old (not sure quite how old), or whether there is a
fault with the thermostat before I go to the expense of replacing one or
the other. Your suggestions are most welcome.



RBM Wrote:
This thermostat doesn't require a common, just the two wires. I would
look
to the wattage of the transformer that's powering the three zone
valves


"Achattaway" wrote in message
...

I have three heat zones in my home, two upstairs and one in the
basement. I recently upgraded my old mercury Honeywell thermostats
upstairs to a digital type CT8775A. They are connected to Honeywell
motorized valves at the boiler, type V8043E1012.

When I installed the thermostats I was careful to map the wiring and
everything seemed fine, the digital display came up, the room temp
was
monitored and the backlight was working fine. However, now that I am
starting to need the heat the problem occurs. When the room is above
the temp of the thermostat setting everything is fine and the display
works. When I raise the temp setting on the thermostat to turn the
heating on, and after the furnace has fired up, the display goes
blank,
the backlight doesn't work but the furnace continues to burn. When
the
furnace switches off afet a couple of minutes the display reappears,
only to disappear again.

I have tested the wiring connections at the boiler and behind the
thermostat and they are all good. I have manually overridden the
valve
and tested the motor which appears to spin up OK. I don't know where
to
look next. Has anyone else had the same problem or can anyone
suggest
what the problem might be?


--
Achattaway



--
Achattaway



  #10   Report Post  
Posted to alt.home.repair
TURTLE
 
Posts: n/a
Default Honeywell Thermostat Problem


CBHVAC wrote:
"CJT" wrote in message
...
TURTLE wrote:

This is Turtle.

I can't see it from here but it sounds like a grounding of the
thermostat problem. Manual thermostats don't need these grounds but
digital does need these grounds to work properly.


Doesn't that depend on whether or not they are battery operated?


SOME battery stats still need a COMMON...not a ground..there is not a ground
on a stat, unless its a line voltage stat..
Also, Honeywell has admitted problems with several stats...the VisionPro
series is one now...
Here lately, I just install Robertshaw 9800 series, and so far, no
problems....for heat pumps in particular, the 9865i is a champ...looks good
too.


This is Turtle.

I see you corrected me on the working of ground on the thermostat as a
common and not a ground. Well slick the wire that I called a Ground
leaves the thermostat and goes to the common side of the 24 volt
transformer and then RIGHT OVER TO THE FRAME OF THE FURENACE TO A
GROUND LUG. So now slick what is it a Ground or a Common.

Now after all this correcting of myself you did nothing for the poster
but tell him a bunch of bull**** to think about. He did not want to
hear all this bull**** from you but what was wrong with it to get it
right and you did not answer anything for him but corrected me out of a
flame war over at alt.hvac.

Leave the Flame CORRECTING back at alt.hvac !

TURTLE



  #11   Report Post  
Posted to alt.home.repair
CBHVAC
 
Posts: n/a
Default Honeywell Thermostat Problem


"TURTLE" wrote in message
oups.com...

CBHVAC wrote:
"CJT" wrote in message
...
TURTLE wrote:

This is Turtle.

I can't see it from here but it sounds like a grounding of the
thermostat problem. Manual thermostats don't need these grounds but
digital does need these grounds to work properly.

Doesn't that depend on whether or not they are battery operated?


SOME battery stats still need a COMMON...not a ground..there is not a
ground
on a stat, unless its a line voltage stat..
Also, Honeywell has admitted problems with several stats...the VisionPro
series is one now...
Here lately, I just install Robertshaw 9800 series, and so far, no
problems....for heat pumps in particular, the 9865i is a champ...looks
good
too.


This is Turtle.

I see you corrected me on the working of ground on the thermostat as a
common and not a ground. Well slick the wire that I called a Ground
leaves the thermostat and goes to the common side of the 24 volt
transformer and then RIGHT OVER TO THE FRAME OF THE FURENACE TO A
GROUND LUG. So now slick what is it a Ground or a Common.

Now after all this correcting of myself you did nothing for the poster
but tell him a bunch of bull**** to think about. He did not want to
hear all this bull**** from you but what was wrong with it to get it
right and you did not answer anything for him but corrected me out of a
flame war over at alt.hvac.

Leave the Flame CORRECTING back at alt.hvac !

TURTLE


Not a chance...So you gonna start calling a R line a hot?
Call it what it is, and act like what you claim to be...



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Baxi Solo Problem [email protected] UK diy 13 January 7th 05 11:08 AM
Honeywell CT3600 Thermostat Questions Shrek Home Repair 7 November 6th 04 06:43 PM
Please help diagnose water heater problem Peter Michelson Home Repair 16 March 8th 04 05:31 PM
FLA. Humidistat vs Thermostat operation? M.Burns Home Repair 4 August 2nd 03 03:13 PM


All times are GMT +1. The time now is 08:36 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"