Since I bought the house three years ago, the furnace has always operated as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I asked the
technician what his thoughts were, and he stated that this behaviour is due
to a faulty limit switch on the furnace. He quoted a price of $300 plus tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired, so I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default settings on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay


  #2   Report Post  
Art Todesco
 
Posts: n/a
Default

There is NO reason to get an answer as
you did on a forum like this!
This is a Q&A discussion board and
that's what you asked and here's
my personal experiences.

The numbers you quoted, "out of the box"
are probably fine. Usually
you can't adjust the upper limit .... is
that correct on your unit? On my
furnace, the limit switch and the fan
switch are 2 physical units. As for the
on/off temperature, you can adjust it up
or down. If you go down, you will
get more heat out of each furnace cycle,
however, at the risk of feeling a
cold draft from the now cooling down
heat exchanger. Even 90 degree
air moving can feel cold. My original
non adjustable switch in the furnace
was supposed to be something like
95/135, however, it, and a new replacement
unit from the factory, never even got
close to those numbers. I was more
like 120/155. I then put in an
adjustable unit and it works very well. I
adjusted it to allow the fan to run as
as low a temperature as possible and
still not feel too drafty. I think the
turn off temp is now something like 85
degrees. BTW, I asked a rep from the
furnace company about my experiences
and he said that he had done the same
thing on many units. I think the
manufacturer either had a bad batch of
fan switches or the placement on
the plenum was such that it didn't truly
represent the temp of the air flowing
out of the unit. The later was the
more probable. I hope this helps.

Jay Luke wrote:
Since I bought the house three years ago, the furnace has always operated as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I asked the
technician what his thoughts were, and he stated that this behaviour is due
to a faulty limit switch on the furnace. He quoted a price of $300 plus tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired, so I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default settings on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay


  #3   Report Post  
Amun
 
Posts: n/a
Default


"Jay Luke" wrote in message
news:7wISe.224715$HI.196868@edtnps84...
Since I bought the house three years ago, the furnace has always operated

as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the

heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I asked

the
technician what his thoughts were, and he stated that this behaviour is

due
to a faulty limit switch on the furnace. He quoted a price of $300 plus

tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new

replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired, so

I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default settings

on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay




Forgive me for asking.
But why would you trust a duct cleaner to work on your furnace ???

(avoiding the issue altogether that duct cleaning is often a waste of money)

From what you said the old fan limit switch was working fine but might have
simply needed a slight adjustment.

It would help to know if the blower ever worked differently, and just
"changed" recently.

Or if any work has been done to the heating system before this problem
occurred.


AMUN


  #4   Report Post  
Stretch
 
Posts: n/a
Default

Jay,

If your fan cycles and not the burner, it sounds like the air flow is
set too high. Not a limit problem at all. The duct cleaner is
clueless. It may be that the blower shutoff or turn on settings are
too low or out of wack. Try settint the On at 135 and Off at 90 to
100. If it still cycles, set the heating blower speed lower.

If it is 60 to 90 minutes between cycles, even when it is cold outside,
your furnace is oversized. It should run almost constantly when at
design conditions for your area.

Stretch

  #5   Report Post  
SQLit
 
Posts: n/a
Default


"Jay Luke" wrote in message
news:7wISe.224715$HI.196868@edtnps84...
Since I bought the house three years ago, the furnace has always operated

as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the

heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I asked

the
technician what his thoughts were, and he stated that this behaviour is

due
to a faulty limit switch on the furnace. He quoted a price of $300 plus

tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new

replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired, so

I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default settings

on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay


I recommend that you get a manual for the unit and see what the manufacture
says. Or hire a licensed pro to do the job. I am in a quandry as to why you
would wait 3 years to fix this problem.




  #6   Report Post  
Jay Luke
 
Posts: n/a
Default

Thanks for the advice Art. I'm going to install it with the factory
defaults and run the furnace through a few cycles. Basically, the blower
should kick in a minute or two after the furnace starts the heating process,
and should kick out a minute or two after the flames go out. If there's not
an uncomfortable cold-ish draft before and after the cycle, then we're in
the ball park. Sound about right?



"Art Todesco" wrote in message
.. .
There is NO reason to get an answer as you did on a forum like this!
This is a Q&A discussion board and that's what you asked and here's
my personal experiences.

The numbers you quoted, "out of the box" are probably fine. Usually
you can't adjust the upper limit .... is that correct on your unit? On my
furnace, the limit switch and the fan switch are 2 physical units. As for
the
on/off temperature, you can adjust it up or down. If you go down, you
will
get more heat out of each furnace cycle, however, at the risk of feeling a
cold draft from the now cooling down heat exchanger. Even 90 degree
air moving can feel cold. My original non adjustable switch in the
furnace
was supposed to be something like 95/135, however, it, and a new
replacement
unit from the factory, never even got close to those numbers. I was more
like 120/155. I then put in an adjustable unit and it works very well. I
adjusted it to allow the fan to run as as low a temperature as possible
and
still not feel too drafty. I think the turn off temp is now something
like 85
degrees. BTW, I asked a rep from the furnace company about my experiences
and he said that he had done the same thing on many units. I think the
manufacturer either had a bad batch of fan switches or the placement on
the plenum was such that it didn't truly represent the temp of the air
flowing
out of the unit. The later was the more probable. I hope this helps.

Jay Luke wrote:
Since I bought the house three years ago, the furnace has always operated
as follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the
heating stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I asked
the technician what his thoughts were, and he stated that this behaviour
is due to a faulty limit switch on the furnace. He quoted a price of
$300 plus tax to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new
replacement limiter switch for $40, so I purchased it. Installing should
be straightforward since the existing switch is exposed and already
wired, so I just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default settings
on the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay



  #7   Report Post  
Jay Luke
 
Posts: n/a
Default

The cleaner was also a technician, so he also did basic maintenance and a 21
point inspection on the motor; I just threw the question out there to get
his thoughts after he had finished.

And yes, after the ducts were "cleaned", I wondered if the whole procedure
was even necessary. (but agreed, lets avoid that issue for now)

I ran the furnace through a few cycles with the existing limit switch, and
it seems the limit switch is indeed faulty. When the burner begins the
heating (prior to the blower kicking in), the limit switch dial slowly
starts to rotate to reflect the increasing temperature in the plenum. But
the On/Off settings on the limit switch's dial don't rotate with the dial.
So the "Off" setting may be set to 90, but the dial turns past the setting.
Hard to explain, but the end result was that the furnace didn't stop running
when it hit 90.

No work had been done to the heating system before this behaviour started,
and as long as i've lived in the house (about three years) the furnace has
always run this way.

"Amun" wrote in message
.. .

"Jay Luke" wrote in message
news:7wISe.224715$HI.196868@edtnps84...
Since I bought the house three years ago, the furnace has always operated

as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the

heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I asked

the
technician what his thoughts were, and he stated that this behaviour is

due
to a faulty limit switch on the furnace. He quoted a price of $300 plus

tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new

replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired,
so

I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default settings

on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay




Forgive me for asking.
But why would you trust a duct cleaner to work on your furnace ???

(avoiding the issue altogether that duct cleaning is often a waste of
money)

From what you said the old fan limit switch was working fine but might
have
simply needed a slight adjustment.

It would help to know if the blower ever worked differently, and just
"changed" recently.

Or if any work has been done to the heating system before this problem
occurred.


AMUN




  #8   Report Post  
Jay Luke
 
Posts: n/a
Default

hah hah! you're such a dink!


"Anthony Berlin" wrote in message
. ..
Yea, I know what they should be, but you're not paying me to install and
set
it up, just as you chose to not pay the service company that told you what
the problem was to begin with either. Short story: Figure it out your
****in' self-thief.



"Jay Luke" wrote in message
news:7wISe.224715$HI.196868@edtnps84...
Since I bought the house three years ago, the furnace has always operated

as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the

heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I asked

the
technician what his thoughts were, and he stated that this behaviour is

due
to a faulty limit switch on the furnace. He quoted a price of $300 plus

tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new

replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired,
so

I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default settings

on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay






  #9   Report Post  
Anthony Berlin
 
Posts: n/a
Default

Is that english? Was there something regarding my response that you take
exception to? Are you even qualified to comment on the subject, other than
to inject incoherent non-sensical OT stupidity? Please enlighten me if you
have anything intelligent to add to the post that you don't have to Google
first............








"Jay Luke" wrote in message
news:5VmTe.165645$wr.140077@clgrps12...
hah hah! you're such a dink!


"Anthony Berlin" wrote in message
. ..
Yea, I know what they should be, but you're not paying me to install and
set
it up, just as you chose to not pay the service company that told you

what
the problem was to begin with either. Short story: Figure it out your
****in' self-thief.



"Jay Luke" wrote in message
news:7wISe.224715$HI.196868@edtnps84...
Since I bought the house three years ago, the furnace has always

operated
as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the

heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I

asked
the
technician what his thoughts were, and he stated that this behaviour is

due
to a faulty limit switch on the furnace. He quoted a price of $300

plus
tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new

replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired,
so

I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default

settings
on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because

the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay








  #10   Report Post  
Anthony Berlin
 
Posts: n/a
Default


"No work had been done to the heating system before this behaviour started,
and as long as i've lived in the house (about three years) the furnace has
always run this way."


That statement alone answers any question about competence that I may have
about you. You don't even deserve to benefit from forced air mechanical
heating. What kind of idiot let's a furnace, continue to operate.....for
three years, knowing something is failing with a safety component? Are you
just too ****ing tight to have it professionally serviced, if not for
yourself...for your family or are you really that ****ing ignorant?
Incidentally....failure to have your heating and cooling equipment
professionally serviced, is not saving you a dime it is costing you however.
People like you are the reason that E/O's with reasonable questions cannot
post a question and have it answered in the HVAC forums....you're too stupid
to take advice when it's given in your best interest.







"Jay Luke" wrote in message
news:JSmTe.165643$wr.37736@clgrps12...
The cleaner was also a technician, so he also did basic maintenance and a

21
point inspection on the motor; I just threw the question out there to get
his thoughts after he had finished.

And yes, after the ducts were "cleaned", I wondered if the whole procedure
was even necessary. (but agreed, lets avoid that issue for now)

I ran the furnace through a few cycles with the existing limit switch, and
it seems the limit switch is indeed faulty. When the burner begins the
heating (prior to the blower kicking in), the limit switch dial slowly
starts to rotate to reflect the increasing temperature in the plenum. But
the On/Off settings on the limit switch's dial don't rotate with the dial.
So the "Off" setting may be set to 90, but the dial turns past the

setting.
Hard to explain, but the end result was that the furnace didn't stop

running
when it hit 90.

No work had been done to the heating system before this behaviour started,
and as long as i've lived in the house (about three years) the furnace has
always run this way.

"Amun" wrote in message
.. .

"Jay Luke" wrote in message
news:7wISe.224715$HI.196868@edtnps84...
Since I bought the house three years ago, the furnace has always

operated
as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the

heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I

asked
the
technician what his thoughts were, and he stated that this behaviour is

due
to a faulty limit switch on the furnace. He quoted a price of $300

plus
tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new

replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired,
so

I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default

settings
on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because

the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay




Forgive me for asking.
But why would you trust a duct cleaner to work on your furnace ???

(avoiding the issue altogether that duct cleaning is often a waste of
money)

From what you said the old fan limit switch was working fine but might
have
simply needed a slight adjustment.

It would help to know if the blower ever worked differently, and just
"changed" recently.

Or if any work has been done to the heating system before this problem
occurred.


AMUN








  #11   Report Post  
Jay Luke
 
Posts: n/a
Default

"anything intelligent to add to the post?"

yes. beat it, dink.

"Anthony Berlin" wrote in message
. ..
Is that english? Was there something regarding my response that you take
exception to? Are you even qualified to comment on the subject, other than
to inject incoherent non-sensical OT stupidity? Please enlighten me if you
have anything intelligent to add to the post that you don't have to Google
first............








"Jay Luke" wrote in message
news:5VmTe.165645$wr.140077@clgrps12...
hah hah! you're such a dink!


"Anthony Berlin" wrote in message
. ..
Yea, I know what they should be, but you're not paying me to install
and
set
it up, just as you chose to not pay the service company that told you

what
the problem was to begin with either. Short story: Figure it out your
****in' self-thief.



"Jay Luke" wrote in message
news:7wISe.224715$HI.196868@edtnps84...
Since I bought the house three years ago, the furnace has always

operated
as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the
heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I

asked
the
technician what his thoughts were, and he stated that this behaviour
is
due
to a faulty limit switch on the furnace. He quoted a price of $300

plus
tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new
replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already
wired,
so
I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default

settings
on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because

the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay










  #12   Report Post  
Tekkie®
 
Posts: n/a
Default

Anthony Berlin posted for all of us...
I don't top post - see either inline or at bottom.

People like you are the reason that E/O's with reasonable questions cannot

Anthony what does E/O mean?
--

Tekkie
  #13   Report Post  
Amun
 
Posts: n/a
Default

"Amun" wrote in message
.. .

"Jay Luke" wrote in message
news:7wISe.224715$HI.196868@edtnps84...
Since I bought the house three years ago, the furnace has always

operated
as
follows:

- kicks in and blows heat for 30-45 seconds
- fan stops for 10-15 seconds
- repeats this cycle for 30 to 40 minutes, then the fan and the

heating
stop
- 60 to 90 minutes later, starts all over

When I had my furnace vents professionaly cleaned the other day, I

asked
the
technician what his thoughts were, and he stated that this behaviour is

due
to a faulty limit switch on the furnace. He quoted a price of $300

plus
tax
to install a new one.

After researching online and verifying for myself that this was rapid
cycling, I went down to the local hardware store and found a new

replacement
limiter switch for $40, so I purchased it. Installing should be
straightforward since the existing switch is exposed and already wired,
so

I
just need to set the start/stop limits on the switch.

How are the off/on temperature settings determined? The default

settings
on
the switch (out-of-box) a
Off: 95
On: 135
Limit 210

I can't refer to the current settings on the existing switch because

the
tech had moved them around before leaving.

Anyone have any knowledge or advice on this?

Cheers in advance - jay




Forgive me for asking.
But why would you trust a duct cleaner to work on your furnace ???

(avoiding the issue altogether that duct cleaning is often a waste of
money)

From what you said the old fan limit switch was working fine but might
have
simply needed a slight adjustment.

It would help to know if the blower ever worked differently, and just
"changed" recently.

Or if any work has been done to the heating system before this problem
occurred.


AMUN





"Jay Luke" wrote in message
news:JSmTe.165643$wr.37736@clgrps12...
The cleaner was also a technician, so he also did basic maintenance and a

21
point inspection on the motor; I just threw the question out there to get
his thoughts after he had finished.

And yes, after the ducts were "cleaned", I wondered if the whole procedure
was even necessary. (but agreed, lets avoid that issue for now)

I ran the furnace through a few cycles with the existing limit switch, and
it seems the limit switch is indeed faulty. When the burner begins the
heating (prior to the blower kicking in), the limit switch dial slowly
starts to rotate to reflect the increasing temperature in the plenum. But
the On/Off settings on the limit switch's dial don't rotate with the dial.
So the "Off" setting may be set to 90, but the dial turns past the

setting.
Hard to explain, but the end result was that the furnace didn't stop

running
when it hit 90.

No work had been done to the heating system before this behaviour started,
and as long as i've lived in the house (about three years) the furnace has
always run this way.



The whole post now is a bit pointless if you already replaced the fan
control.
As no one will take it back.

But the limits must be set in a certain order, or you will never get it to
work right.

Most have basic instructions in the cover, and that's the proper procedure
you need to use.
And if it came with any printed instructions, read them and do exactly what
it says.

From your original post I still think the original control was working fine,
but might have needed proper adjusting.

But there are also a lot of other things that have to be working right too,
If it was working right but broke/started acting up, at least we all have a
chance at offering a probable fix based on the symptoms.

But when you don't know if it ever was right, after 3 years, the problems
may be caused by countless things.

Bad parts, poor system installation, poor system design, wrong parts
installed, parts installed improperly/not adjusted properly etc.

Only someone there can check/test each part.
none of us can fix your furnace by email

Best we can offer is "reasonable guesses"
But even guesses have to be based on the system being put together right to
start with.


eg, the problem you originally described could just as easily be a
circulating fan turning too fast because of wrong motor or wrong drive belt
pulleys or a dual speed fan stuck on high

And the "technician" should have been able to test what the cause was before
he suggested "trying this" or fiddling with screws.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Re-Post for Wall Switch Harry Home Repair 1 July 27th 05 06:56 PM
Thermostat Wiring HvacTech2 Home Repair 31 July 13th 05 04:21 PM
3 way switch disaster (long but interesting) RB Home Repair 8 July 23rd 04 02:18 PM
Dimmer switch on ceiling barry martin Home Repair 1 December 21st 03 01:42 PM
help selecting a manual transfer switch wahzoo Home Repair 13 December 13th 03 01:50 AM


All times are GMT +1. The time now is 01:00 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"