500 microns? - then you are a HACK!!
if you only pull 500 microns of vacuum for your customer, you are not
getting all of the water out and are going to be making hydrochloric acid for them, so they can buy a new unit from you, Mr. Con Artist. quit ripping off the customer and change your pump oil or buy a new pump and start pumping with good enough equipment, and for a long enough time, to get down to 50 - 75 microns for an hour. if you don't understand what the oil has to do with the final amount of vacuum, or don't understand what are "microns" or don't have a precision way to measure them, PLEASE RETIRE, because YOU SUCK, you INCOMPETENT HACK |
papaya wrote:
if you only pull 500 microns of vacuum for your customer, you are not getting all of the water out and are going to be making hydrochloric acid for them, so they can buy a new unit from you, Mr. Con Artist. Most manufacturers installation instructions say evacuate to 350 microns, then insure that the vacuum holds for at least a minute after closing off the vacuum pump. Their instructions (and their warranty) are good enough for me. |
In article ,
"papaya" wrote: if you only pull 500 microns of vacuum for your customer, you are not getting all of the water out and are going to be making hydrochloric acid for them, so they can buy a new unit from you, Mr. Con Artist. quit ripping off the customer and change your pump oil or buy a new pump and start pumping with good enough equipment, and for a long enough time, to get down to 50 - 75 microns for an hour. if you don't understand what the oil has to do with the final amount of vacuum, or don't understand what are "microns" or don't have a precision way to measure them, PLEASE RETIRE, because YOU SUCK, you INCOMPETENT HACK You're a uninformed dipstick who posts about things you don't know **** about. At 500 microns water boils at minus 12 degree's which is plenty to get the water out. At 50 microns you're boiling the oil out. -- Paul's cat got a furball and kept saying weasel's name. *Hack* *Hack* *hack* |
Gentlemen
I do not want blow you bobble however I think that you are depending far to much on micron gauge am I? nut no I am not I have been doing refrigeration work guess? for over 40 years and field work since 1969 first good mechanic must visualized ( presume lost of gas) how refrigerant was lost if is on high side or low side if is on high side take in consideration what it will take to fix the leak or problem and go from there on, it could need just half hour or couple hours that determine how long you will keep system open and to get it fix. Low side leak again examined problem was the unit running with no refrigerant in the system or did unit shut down on safety how long was it with out any refrigerant in it, all this things must be taken in consideration, only then you can decide how long you will need to have it on vacuum low side could be from hour to overnight and more if it happen that solid water got into system, first you must purge it with nitrogen (GN2) try to blow out all water as possible then and only then put it on vacuum. Now micron gauge With reading on the gauge of 100 MICRONS YOU CAN STILL HAVE WATER IN THE SYSTEM? impossible I have news for you It is possible! how? well while water boils at low pressures but it ALSO FREEZES and once it get frozen it does not boils any more. Procedure is to pump system down for couple hours then purge the system with GN2 let it sit for hour with GN2 in it then put on vacuum again this procedure you may have to do few times depend on size of the unit it self. I would also recommend changing of oil "filter drier must" open and clean oil separator if there is one plus add oil filter on return line On POE system oil change is must and do not put clean oil in until you have evacuated system first. and no you are not boiling oil out what you see is oil bubbling you are taken out residue of gas and moisture Good luck Dido say that "Travis Jordan" wrote in message .. . papaya wrote: if you only pull 500 microns of vacuum for your customer, you are not getting all of the water out and are going to be making hydrochloric acid for them, so they can buy a new unit from you, Mr. Con Artist. Most manufacturers installation instructions say evacuate to 350 microns, then insure that the vacuum holds for at least a minute after closing off the vacuum pump. Their instructions (and their warranty) are good enough for me. |
"DiDo" wrote in message news:BMrNe.128$IG2.84@trndny01... It is possible! how? well while water boils at low pressures but it ALSO FREEZES and once it get frozen it does not boils any more. Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. http://www.newton.dep.anl.gov/askasc.../chem03598.htm -- SVL |
-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1 On Fri, 19 Aug 2005 14:20:04 -0400, "papaya" wrote: if you only pull 500 microns of vacuum for your customer, you are not getting all of the water out and are going to be making hydrochloric acid for them, Bull feathers. If you are making acid, it's because you are a hack, but for different reasons: No nitrogen while brazing, no drier change, etc... no vacuum pump can purge all the acid without an oil change and flush, once contamination of "burnt freon" has taken place. Why do you think, back in the old days, some techs used to flush the lines with R11, R13 or dichloromethane, after a hermetic burnout? With a single-stage vacuum pump, a good idea is to triple evacuate, anyway. -----BEGIN PGP SIGNATURE----- Version: PGP 7.1 iQA/AwUBQwZeEAIk7T39FC4ZEQKCSwCeNrx4o/8DKt3InpXwjuExsB9IRUMAoPmF P+t1cifpZQANo5m/EmaVVsKL =O/jR -----END PGP SIGNATURE----- -- -john wide-open at throttle dot info |
-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1 On Fri, 19 Aug 2005 21:01:21 GMT, "DiDo" wrote: well while water boils at low pressures but it ALSO FREEZES and once it get frozen it does not boils any more. Poppycock. That far below its triple point, H2O sublimes readily. -----BEGIN PGP SIGNATURE----- Version: PGP 7.1 iQA/AwUBQwZfYQIk7T39FC4ZEQJ7EACeOmNs4gnLmcimQhI3wPlBD0 K5XuwAn1bl pLQeO00ydYhCzTRG6x+3TaBT =Rebz -----END PGP SIGNATURE----- -- -john wide-open at throttle dot info |
-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1 On Fri, 19 Aug 2005 15:32:50 -0700, ~^Johnny^~ wrote: some techs used to flush the lines with R11, R13 ^^^ Oops! Typo. That should be R113, of course. Stupid spell checker... -----BEGIN PGP SIGNATURE----- Version: PGP 7.1 iQA/AwUBQwZkFwIk7T39FC4ZEQI9kgCgmJfsZgZ9CCGlIYgokH0msl JSvVcAnRXk yZ/hJbbjn4Wg7TUt4HRgbS1A =oQGZ -----END PGP SIGNATURE----- -- -john wide-open at throttle dot info |
"PrecisionMachinisT" wrote in message ... "DiDo" wrote in message news:BMrNe.128$IG2.84@trndny01... It is possible! how? well while water boils at low pressures but it ALSO FREEZES and once it get frozen it does not boils any more. Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. keep on dreaming you will learn sooner or later From Dido http://www.newton.dep.anl.gov/askasc.../chem03598.htm -- SVL |
"bill" wrote in message ... In article , "papaya" wrote: if you only pull 500 microns of vacuum for your customer, you are not getting all of the water out and are going to be making hydrochloric acid for them, so they can buy a new unit from you, Mr. Con Artist. quit ripping off the customer and change your pump oil or buy a new pump and start pumping with good enough equipment, and for a long enough time, to get down to 50 - 75 microns for an hour. if you don't understand what the oil has to do with the final amount of vacuum, or don't understand what are "microns" or don't have a precision way to measure them, PLEASE RETIRE, because YOU SUCK, you INCOMPETENT HACK You're a uninformed dipstick who posts about things you don't know **** about. At 500 microns water boils at minus 12 degree's which is plenty to get the water out. At 50 microns you're boiling the oil out. My dear freinds who ever told you that, he or she better get little more knowlage and experience or is it what you saying that if I evacuate system to 10 microns I will pump all of the oil out of compressor you are so nerow mined I do not why I bother answering From Dido -- Paul's cat got a furball and kept saying weasel's name. *Hack* *Hack* *hack* |
What are these fabulous 'microns' you speak of, and where may I obtain
them? Are they expensive? I must have some. |
In article ,
~^Johnny^~ wrote: With a single-stage vacuum pump, a good idea is to triple evacuate, anyway. A single stage pump cannot pull a vacuum that can remove moisture. -- Paul's cat got a furball and kept saying weasel's name. *Hack* *Hack* *hack* |
In article 97uNe.1432$3%1.292@trndny08, "DiDo"
wrote: You're a uninformed dipstick who posts about things you don't know **** about. At 500 microns water boils at minus 12 degree's which is plenty to get the water out. At 50 microns you're boiling the oil out. My dear freinds who ever told you that, he or she better get little more knowlage and experience or is it what you saying that if I evacuate system to 10 microns I will pump all of the oil out of compressor you are so nerow mined I do not why I bother answering From Dido Dildo YOU need to do some reading. -- Paul's cat got a furball and kept saying weasel's name. *Hack* *Hack* *hack* |
In article IUtNe.29$rA2.28@trndny02, "DiDo"
wrote: Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. keep on dreaming you will learn sooner or later From Dido Cite your sources dildo. Or do you just pull **** out of your ass like weasel does? -- Paul's cat got a furball and kept saying weasel's name. *Hack* *Hack* *hack* |
Answer one question
on how many units did you work that do run at -85 degrees Fahrenheit and must make -100 yes you can use R-11, R-114 and few others but field person must use what is readily available and don't come telling people what is in book but from your own experience work done. ANYTHING I POST I HAVE ALREADY DONE IT I do not IMAGINE IT I did it I suggest not only to you but to any that read this get some books on ultra low temperature and start reading before you come back to me with some stupid answers that you have no idea of what the heck you are talking about it is bloody disgrace that some of you. servicing air conditioners and nothing ales as long as you being doing this and you think you are expert on refrigeration, with answers and posting you gave if I was to gave you to clean my bathroom I strongly believe that my bathroom would be insulted, and Johnny this does not only pretend to you. You have big company "~^Johnny^~" wrote in message ... -----BEGIN PGP SIGNED MESSAGE----- Hash: SHA1 On Fri, 19 Aug 2005 14:20:04 -0400, "papaya" wrote: if you only pull 500 microns of vacuum for your customer, you are not getting all of the water out and are going to be making hydrochloric acid for them, Bull feathers. If you are making acid, it's because you are a hack, but for different reasons: No nitrogen while brazing, no drier change, etc... no vacuum pump can purge all the acid without an oil change and flush, once contamination of "burnt freon" has taken place. Why do you think, back in the old days, some techs used to flush the lines with R11, R13 or dichloromethane, after a hermetic burnout? With a single-stage vacuum pump, a good idea is to triple evacuate, anyway. -----BEGIN PGP SIGNATURE----- Version: PGP 7.1 iQA/AwUBQwZeEAIk7T39FC4ZEQKCSwCeNrx4o/8DKt3InpXwjuExsB9IRUMAoPmF P+t1cifpZQANo5m/EmaVVsKL =O/jR -----END PGP SIGNATURE----- -- -john wide-open at throttle dot info |
"bill" wrote in message ... In article IUtNe.29$rA2.28@trndny02, "DiDo" wrote: Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. keep on dreaming you will learn sooner or later From Dido Cite your sources dildo. Or do you just pull **** out of your ass like weasel does? JEEBUS CHRIST ON A CRACKER!!!!!! This damn place is turning into alt.hvac........ |
On Sat, 20 Aug 2005 01:15:53 GMT, "Dr. Hardcrab"
wrote: "bill" wrote in message ... In article IUtNe.29$rA2.28@trndny02, "DiDo" wrote: Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. keep on dreaming you will learn sooner or later From Dido Cite your sources dildo. Or do you just pull **** out of your ass like weasel does? JEEBUS CHRIST ON A CRACKER!!!!!! This damn place is turning into alt.hvac........ Shee-it !!!! :-( Click here every day to feed an animal that needs you today !!! http://www.theanimalrescuesite.com/ Paul ( pjm @ pobox . com ) - remove spaces to email me 'Some days, it's just not worth chewing through the restraints.' 'With sufficient thrust, pigs fly just fine.' HVAC/R program for Palm PDA's Free demo now available online http://pmilligan.net/palm/ |
"Dr. Hardcrab" wrote in message
news:dvvNe.2316$137.1018@trnddc08... "bill" wrote in message ... In article IUtNe.29$rA2.28@trndny02, "DiDo" wrote: Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. keep on dreaming you will learn sooner or later From Dido Cite your sources dildo. Or do you just pull **** out of your ass like weasel does? JEEBUS CHRIST ON A CRACKER!!!!!! This damn place is turning into alt.hvac........ It is. Check the cross posting... |
In article D1vNe.131$Fq2.90@trndny03, "DiDo"
wrote: Answer one question on how many units did you work that do run at -85 degrees Fahrenheit and must make -100 yes you can use R-11, R-114 and few others but field person must use what is readily available and don't come telling people what is in book but from your own experience work done. ANYTHING I POST I HAVE ALREADY DONE IT I do not IMAGINE IT I did it I suggest not only to you but to any that read this get some books on ultra low temperature and start reading before you come back to me with some stupid answers that you have no idea of what the heck you are talking about it is bloody disgrace that some of you. servicing air conditioners and nothing ales as long as you being doing this and you think you are expert on refrigeration, with answers and posting you gave if I was to gave you to clean my bathroom I strongly believe that my bathroom would be insulted, and Johnny this does not only pretend to you. You have big company You aren't the only one who works on low temp refrigeration. You can't spew bull**** and not be called on it. Cite your sources dildo. Or STFU. There. You've been called on it. Pony up or pussy out. -- Paul's cat got a furball and kept saying weasel's name. *Hack* *Hack* *hack* |
PrecisionMachinisT wrote:
"DiDo" wrote in message news:BMrNe.128$IG2.84@trndny01... It is possible! how? well while water boils at low pressures but it ALSO FREEZES and once it get frozen it does not boils any more. Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. http://www.newton.dep.anl.gov/askasc.../chem03598.htm -- SVL Sam, I think Dido is talking about when you have a evap coil exposed to other cold temps within a running freezer.. a common occurence in the commercial world. This is what the man meant, I believe. Jake |
Dude, I got no idea what you are babbling on about.
reply below "papaya" wrote in message ... if you only pull 500 microns of vacuum for your customer, you are not getting all of the water out and are going to be making hydrochloric acid for them, so they can buy a new unit from you, Mr. Con Artist. Maybe if your pump is too big... quit ripping off the customer and change your pump oil or buy a new pump and start pumping with good enough equipment, and for a long enough time, to get down to 50 - 75 microns for an hour. Umm..... you better check the specs on *new* pumps... they are rated for and tested for a *maximum* of 50 microns if you don't understand what the oil has to do with the final amount of vacuum, or don't understand what are "microns" or don't have a precision way to measure them, PLEASE RETIRE, because YOU SUCK, you INCOMPETENT HACK Do it right with N2 purge while brazing, new filter dryer, and use a small vacuum pump(4 - 6 CFM) with new oil, and you won't have a problem drawing down to between 300 - 400 microns. Too big of a vacuum pump will cause too fast of a draw-down and cause any water in the system to turn to ice. OTOH, If you are really gonna be that anal and have the time to leave your vacuum pump on a resi system for 2 days while trying to draw it down to 50 microns, then by all means, knock yourself out. |
On 19 Aug 2005 16:59:55 -0700, "Matt" wrote:
What are these fabulous 'microns' you speak of, and where may I obtain them? Are they expensive? I must have some. don't new a/c installs have to be evacuated to 300 microns? in automotive we use 600 microns, but we also use 0-rings instead of sweated fittings. I'd really like to see the vaccuum pump that will pull it to 50 microns. Chip |
"DiDo" wrote in message news:IUtNe.29$rA2.28@trndny02... "PrecisionMachinisT" wrote in message ... "DiDo" wrote in message news:BMrNe.128$IG2.84@trndny01... It is possible! how? well while water boils at low pressures but it ALSO FREEZES and once it get frozen it does not boils any more. Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. keep on dreaming you will learn sooner or later From Dido Well, I spose it was rather unrealistic of me to expect an illiterate ****wit such as yourself to actually comprehend much if any of the information contained within the link I posted, and I guess I might be one of only a few that actually paid much attention in 9th grade science classes. Still, appreciate if you don't send me anymore email on the topic. -- SVL |
"JohnR66" wrote in message ... "Dr. Hardcrab" wrote in message news:dvvNe.2316$137.1018@trnddc08... "bill" wrote in message ... In article IUtNe.29$rA2.28@trndny02, "DiDo" wrote: Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. keep on dreaming you will learn sooner or later From Dido Cite your sources dildo. Or do you just pull **** out of your ass like weasel does? JEEBUS CHRIST ON A CRACKER!!!!!! This damn place is turning into alt.hvac........ It is. Check the cross posting... DUH! (I missed that) |
"Jake" wrote in message news:CDwNe.48754$084.28178@attbi_s22... PrecisionMachinisT wrote: "DiDo" wrote in message news:BMrNe.128$IG2.84@trndny01... It is possible! how? well while water boils at low pressures but it ALSO FREEZES and once it get frozen it does not boils any more. Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation'.....IOW, no "boiling" is needed. http://www.newton.dep.anl.gov/askasc.../chem03598.htm -- SVL Sam, I think Dido is talking about when you have a evap coil exposed to other cold temps within a running freezer.. a common occurence in the commercial world. This is what the man meant, I believe. Jake, Doesn't matter--next time it snows, watch your outside temp real close, and take note of any period over several days, or perhaps up to a week where the temp stays constantly below freezing....notice that the snow 'just kinda dissapears'....given enough time, it will eventually dissapear altogether, without ever reaching a temp above freezing, and without rain falling on it, etc.....now note that this process speeds up considerably at pressures below atmospheric. -- SVL |
Jake,
Doesn't matter--next time it snows, watch your outside temp real close, and take note of any period over several days, or perhaps up to a week where the temp stays constantly below freezing....notice that the snow 'just kinda dissapears'....given enough time, it will eventually dissapear altogether, without ever reaching a temp above freezing, and without rain falling on it, etc.....now note that this process speeds up considerably at pressures below atmospheric. -- SVL OK, I buy that! The info in your article also said "If you've got a week" or something similar. I don't think a tech in the field has that kind of time, so perhaps that's what Dido is addressing. I've seen ice develop in commercial Vacuum systems, and it does not dissipate easily... it takes a long and slow pull. (NO one please make a inference from this given my comments below)... I *do* understand the pressure relationship, believe it or not.... BTW, I think I was either drunk or high in 9th grade science class...or perhaps making passes at the lovely 'Tracey' that sat next to me, as I recall. Tracey ended up on crack or welfare, or both, I think... Oh, I got an A in Science... maybe it was Math, or English... or something (-;..... ahhhh... the '70's. DON'T TRY THIS NOW, KIDS! Jake |
WTF did you just say? Better leave that alcohol alone, ****'s burning the
cells faster than you're makin' 'em. "DiDo" wrote in message news:BMrNe.128$IG2.84@trndny01... Gentlemen I do not want blow you bobble however I think that you are depending far to much on micron gauge am I? nut no I am not I have been doing refrigeration work guess? for over 40 years and field work since 1969 first good mechanic must visualized ( presume lost of gas) how refrigerant was lost if is on high side or low side if is on high side take in consideration what it will take to fix the leak or problem and go from there on, it could need just half hour or couple hours that determine how long you will keep system open and to get it fix. Low side leak again examined problem was the unit running with no refrigerant in the system or did unit shut down on safety how long was it with out any refrigerant in it, all this things must be taken in consideration, only then you can decide how long you will need to have it on vacuum low side could be from hour to overnight and more if it happen that solid water got into system, first you must purge it with nitrogen (GN2) try to blow out all water as possible then and only then put it on vacuum. Now micron gauge With reading on the gauge of 100 MICRONS YOU CAN STILL HAVE WATER IN THE SYSTEM? impossible I have news for you It is possible! how? well while water boils at low pressures but it ALSO FREEZES and once it get frozen it does not boils any more. Procedure is to pump system down for couple hours then purge the system with GN2 let it sit for hour with GN2 in it then put on vacuum again this procedure you may have to do few times depend on size of the unit it self. I would also recommend changing of oil "filter drier must" open and clean oil separator if there is one plus add oil filter on return line On POE system oil change is must and do not put clean oil in until you have evacuated system first. and no you are not boiling oil out what you see is oil bubbling you are taken out residue of gas and moisture Good luck Dido say that "Travis Jordan" wrote in message .. . papaya wrote: if you only pull 500 microns of vacuum for your customer, you are not getting all of the water out and are going to be making hydrochloric acid for them, so they can buy a new unit from you, Mr. Con Artist. Most manufacturers installation instructions say evacuate to 350 microns, then insure that the vacuum holds for at least a minute after closing off the vacuum pump. Their instructions (and their warranty) are good enough for me. |
PrecisionMachinisT writes:
Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation' No, not without heat added. No, not when the water is hydrating another substance. |
bill writes:
At 500 microns water boils at minus 12 degree's which is plenty to get the water out. It will not vaporize without the addition of heat. It will not vaporize if it is bound to another substance. |
"Richard J Kinch" wrote in message . .. PrecisionMachinisT writes: Frozen water changes directly from the solid into the vapor phase under low pressure conditions, due to a phenomena known as 'sublimation' No, not without heat added. Dont be a ****wit. _Pressure_= heat..... No, not when the water is hydrating another substance. And so now pray tell just what the hell is this mysterious 'substance' youve added ( to the case in point) Hmmm....... Given a vacuum with some small amount of frozen water in it........will it ( eventually ) sublime or no ??? -- SVL |
On Sat, 20 Aug 2005 01:18:11 -0500, Richard J Kinch
wrote: bill writes: At 500 microns water boils at minus 12 degree's which is plenty to get the water out. It will not vaporize without the addition of heat. It will not vaporize if it is bound to another substance. What line of work are you in, exactly ? I know it ain't HVAC ..... Click here every day to feed an animal that needs you today !!! http://www.theanimalrescuesite.com/ Paul ( pjm @ pobox . com ) - remove spaces to email me 'Some days, it's just not worth chewing through the restraints.' 'With sufficient thrust, pigs fly just fine.' HVAC/R program for Palm PDA's Free demo now available online http://pmilligan.net/palm/ |
PrecisionMachinisT wrote:
_Pressure_= heat..... Learn something new every day around here. Nick |
On 20 Aug 2005 07:57:28 -0400, wrote:
PrecisionMachinisT wrote: _Pressure_= heat..... Learn something new every day around here. Nick Don't you have a big nasty program for that one ? :-) Click here every day to feed an animal that needs you today !!! http://www.theanimalrescuesite.com/ Paul ( pjm @ pobox . com ) - remove spaces to email me 'Some days, it's just not worth chewing through the restraints.' 'With sufficient thrust, pigs fly just fine.' HVAC/R program for Palm PDA's Free demo now available online http://pmilligan.net/palm/ |
don't new a/c installs have to be evacuated to 300 microns? in
automotive we use 600 microns, but we also use 0-rings instead of sweated fittings. I'd really like to see the vaccuum pump that will pull it to 50 microns. Chip " in automotive we use 600 microns" EXCUSE ME??? WHAT KIND OF BULL**** "MECHANIC" ARE YOU?? I am in automotive A/C, and we use 50-75 microns vacuum, if you use 600 then you are screwing your customers, and blaming O-rings for your insufficient vacuum is ridiculous, what the hell do you think the seals your manifold gauge set, hoses, and all other equipment are made up of? you need to be in the special olympics, rather than working on automotive A/C, you stupid retard hack |
"bill" wrote in message ... In article D1vNe.131$Fq2.90@trndny03, "DiDo" wrote: Answer one question on how many units did you work that do run at -85 degrees Fahrenheit and must make -100 yes you can use R-11, R-114 and few others but field person must use what is readily available and don't come telling people what is in book but from your own experience work done. ANYTHING I POST I HAVE ALREADY DONE IT I do not IMAGINE IT I did it I suggest not only to you but to any that read this get some books on ultra low temperature and start reading before you come back to me with some stupid answers that you have no idea of what the heck you are talking about it is bloody disgrace that some of you. servicing air conditioners and nothing ales as long as you being doing this and you think you are expert on refrigeration, with answers and posting you gave if I was to gave you to clean my bathroom I strongly believe that my bathroom would be insulted, and Johnny this does not only pretend to you. You have big company You aren't the only one who works on low temp refrigeration. No I am not you are absulutly right Good luck Dido You can't spew bull**** and not be called on it. Cite your sources dildo. Or STFU. There. You've been called on it. Pony up or pussy out. -- Paul's cat got a furball and kept saying weasel's name. *Hack* *Hack* *hack* |
In article pfGNe.132$p32.83@trndny06, "DiDo"
wrote: You aren't the only one who works on low temp refrigeration. No I am not you are absulutly right Good luck Dildo You can't spew bull**** and not be called on it. Cite your sources dildo. Or STFU. There. You've been called on it. Pony up or pussy out. So you're going to pussy out I take it? -- Paul's cat got a furball and kept saying weasel's name. *Hack* *Hack* *hack* |
Ah, an excellent question. A micron is a stone that is mined in South
Africa. -- Christopher A. Young Do good work. It's longer in the short run but shorter in the long run. .. .. "Matt" wrote in message oups.com... What are these fabulous 'microns' you speak of, and where may I obtain them? Are they expensive? I must have some. |
PrecisionMachinisT writes:
No, not when the water is hydrating another substance. And so now pray tell just what the hell is this mysterious 'substance' youve added ( to the case in point) Dessicants, lubricants, contaminants. They will not release water of hydration just because you apply a vacuum at ambient temperatures. Neither will slugs of free water trapped in lines, without either a lot of time or an external heating source. Given a vacuum with some small amount of frozen water in it........will it ( eventually ) sublime or no ??? Only in proportion to the heat added. It *will not* sublime at all if there is no heat added, even in a perfect vacuum. The universe is full of solid water in the near-perfect vacuum of space. Comets are an example. Commercial food freeze-drying apparatus provide a circulating heat medium on the trays. You can't just shove hunks of wet food in a vacuum chamber and pump it down to freeze-dry it, practically speaking. Neither can you dry out a wet HVAC system by leaving it on a vacuum. I know this is an article of faith in the HVAC trade, but it is a myth beacuse the tradesmen only learn a shallow smattering of chemistry and thermodynamics. And they just want to believe it. |
I am not sure where you live but it is about 600 degrees F warmer than
"space " on earth, even in the winter. There is plenty of available heat to sublimate water. Repeat after me: temperature is not heat. |
"Richard J Kinch" wrote in message .. . PrecisionMachinisT writes: Only in proportion to the heat added. It *will not* sublime at all if there is no heat added, even in a perfect vacuum. Ignore the entire concept of latent heat if its convenient to you then.... Point being is the heat was already added or subtrcated from the sytstem before or after the phase change took place........still, its pressure causing the actual change to occur. Im done, your a ****wit and my opinion still stands. The universe is full of solid water in the near-perfect vacuum of space. Comets are an example. And I've heard that it's ****ing hotter than hell out there, too... -- SVL |
All times are GMT +1. The time now is 09:34 AM. |
|
Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter