james June 2nd 05 07:38 PM

hot tub electrical question
 
first: good group - i'm a lurker but learn a lot by reading!

i am purchasing a great hot tub from a co-worker for excellent price
(he's upgrading). i'm moving it saturday to the back patio of my
townhome, i'm sure everyone envys that job.

i have an electrician coming saturday evening, and am going to request
he use the 220 power in the laundry room to hardwire the hot tub to.
(my dryer is gas, so i don't use it), and the fuse box has two switches
strictly for the dryer.

the basement outlet is right next to the patio, so pretty close,

but a hot tub dealer mention the outlet might be 30amp, and the hot tub
is 50amp

should i be concerned about this? and is it a correctable problem, and
at approx. what price?

thanks in advance, i appreciate it!


JohnH June 2nd 05 07:47 PM


but a hot tub dealer mention the outlet might be 30amp, and the hot
tub is 50amp



You will need to run a 4 wire cable directly to the breaker box, connected
to a proper GFCI breaker, through a cutoff switch. Anything else will be an
unsafe rig.


http://www.spasupport.com/electrical...tallguide.html



RBM June 2nd 05 07:55 PM

Ditto JohnH, with the possible exception: Some units have an integral GFCI
device. The dryer circuit is definitely not useable
"JohnH" wrote in message
...

but a hot tub dealer mention the outlet might be 30amp, and the hot
tub is 50amp



You will need to run a 4 wire cable directly to the breaker box, connected
to a proper GFCI breaker, through a cutoff switch. Anything else will be
an unsafe rig.


http://www.spasupport.com/electrical...tallguide.html




[email protected] June 2nd 05 07:58 PM

"You will need to run a 4 wire cable directly to the breaker box,
connected
to a proper GFCI breaker, through a cutoff switch. Anything else will
be an
unsafe rig. "

Why does it have to be a direct run? I don't know of any code or
safety requirement that calls for this. As long as the wire is the
appropriate size and he gets a GFCI and disconnect installed, I don't
see anything wrong with eliminating the dryer outlet and starting the
run from there. Of course, it's very likely the existing wire gauge
isn't adequate anyway, but that's a different issue.


JohnH June 2nd 05 08:18 PM

wrote:
"You will need to run a 4 wire cable directly to the breaker box,
connected
to a proper GFCI breaker, through a cutoff switch. Anything else will
be an
unsafe rig. "

Why does it have to be a direct run? I don't know of any code or
safety requirement that calls for this. As long as the wire is the
appropriate size and he gets a GFCI and disconnect installed, I don't
see anything wrong with eliminating the dryer outlet and starting the
run from there. Of course, it's very likely the existing wire gauge
isn't adequate anyway, but that's a different issue.


You are correct; that will work IF the dryer outlet is removed and the wires
have the proper ampacity and separate neutral and grounds.

It seems to me it'd just be simpler and cleaner to run a whole new line,
unless he can save substantial money by starting the run from there.
Perhaps it will be cheaper as 4 conductor #6 isn't cheap! ;)



james June 2nd 05 09:47 PM

my dryer outlet doesn't work anyway. it came up bad in my home
inspection last year. (not sure if wiring is ok or not)

i'm mainly concerned about the 30/50 amp difference -- but if new
wiring needs to originate from breaker box it's no problem. it's on the
main floor of my townhome, and can drop the wires behind the wall into
the ceiling of laundry room, then out to patio. (see below side view)

i guess i'm more concerned if the two breakers can accept the load of a
hot tub - but it's 220, like a dryer, i'm guessing i'm ok?

thanks again for the responses! and don't worry i'm having an
electrician do it, just want to get some knowledge first.

HOT TUB________________ BREAKER BOX ------- - MAIN FLOOR



__________DRYER OUTLET__________ ------------------- BASEMENT


[email protected] June 2nd 05 10:00 PM



james wrote:
my dryer outlet doesn't work anyway. it came up bad in my home
inspection last year. (not sure if wiring is ok or not)

i'm mainly concerned about the 30/50 amp difference -- but if new
wiring needs to originate from breaker box it's no problem. it's on the
main floor of my townhome, and can drop the wires behind the wall into
the ceiling of laundry room, then out to patio. (see below side view)

i guess i'm more concerned if the two breakers can accept the load of a
hot tub - but it's 220, like a dryer, i'm guessing i'm ok?



What breakers are there won't matter. It sounds like what you will
need is a 240V 50 amp GFCI. This will either go in as

1 - A new location in the service panel

2 - Replacing the existing breaker for the dryer, which is very likely
not 50 Amp. The question for this method is whether it can even be
done, as the wire run for the dryer may not be of sufficient gauge.
Also, given that you have to take out the dryer outlet, put in some
kind of appropriate junction box, etc, it might be easier and about the
same cost to just make a new run.






thanks again for the responses! and don't worry i'm having an
electrician do it, just want to get some knowledge first.

HOT TUB________________ BREAKER BOX ------- - MAIN FLOOR



__________DRYER OUTLET__________ ------------------- BASEMENT



Doug Miller June 2nd 05 10:02 PM

In article .com, "james" wrote:

i guess i'm more concerned if the two breakers can accept the load of a
hot tub - but it's 220, like a dryer, i'm guessing i'm ok?


No, not if the dryer circuit is 30A at 220V and the hot tub draws 50A at 220V.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?

AutoTracer June 2nd 05 10:42 PM

The difference between a 30A and 50A is (usually) this:
1. wire gague
2. shape of plug on receptacle
3. rating of the circuit breaker in the panel.
4. the dryer wire may lack an integral ground conductor(4th wire)

You may need to upgrade one or all of these things


"james" wrote in message
oups.com...
my dryer outlet doesn't work anyway. it came up bad in my home
inspection last year. (not sure if wiring is ok or not)

i'm mainly concerned about the 30/50 amp difference -- but if new
wiring needs to originate from breaker box it's no problem. it's on the
main floor of my townhome, and can drop the wires behind the wall into
the ceiling of laundry room, then out to patio. (see below side view)

i guess i'm more concerned if the two breakers can accept the load of a
hot tub - but it's 220, like a dryer, i'm guessing i'm ok?

thanks again for the responses! and don't worry i'm having an
electrician do it, just want to get some knowledge first.

HOT TUB________________ BREAKER BOX ------- - MAIN FLOOR



__________DRYER OUTLET__________ ------------------- BASEMENT




tom June 2nd 05 11:08 PM

And national code requires that the disconnect be _within sight_ of the
pool/spa. If you wanna go by the NEC... Tom


HorneTD June 3rd 05 03:47 AM

JohnH wrote:
wrote:

"You will need to run a 4 wire cable directly to the breaker box,
connected
to a proper GFCI breaker, through a cutoff switch. Anything else will
be an
unsafe rig. "

Why does it have to be a direct run? I don't know of any code or
safety requirement that calls for this. As long as the wire is the
appropriate size and he gets a GFCI and disconnect installed, I don't
see anything wrong with eliminating the dryer outlet and starting the
run from there. Of course, it's very likely the existing wire gauge
isn't adequate anyway, but that's a different issue.



You are correct; that will work IF the dryer outlet is removed and the wires
have the proper ampacity and separate neutral and grounds.

It seems to me it'd just be simpler and cleaner to run a whole new line,
unless he can save substantial money by starting the run from there.
Perhaps it will be cheaper as 4 conductor #6 isn't cheap! ;)



Many hot tubs do not require a neutral in the circuit so the idea that
he must have a four wire circuit may be erroneous.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.

JohnH June 3rd 05 04:18 AM


Many hot tubs do not require a neutral in the circuit so the idea that
he must have a four wire circuit may be erroneous.


True enough!



Chris Lewis June 3rd 05 05:23 PM

According to JohnH :

Many hot tubs do not require a neutral in the circuit so the idea that
he must have a four wire circuit may be erroneous.


True enough!


We can tell him what he needs (roughly ;-) if he can give us the plate
amperage rating off the spa, the ampacity of the dryer breakers,
whether the dryer circuit is 3 or 4 wire, and whether the spa needs
3 or 4 wire.

Even if the dryer circuit is of adequate ampacity/wire count for the
spa, he'll probably need to install a GFCI breaker (unless there's
already one built into the spa).
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.

james June 3rd 05 05:37 PM

thanks for the responses. i'll know tomorrow evening when the
electrician comes, but this helps me get an idea!

he's a good electrician - friend and knowledgeable


james June 8th 05 03:30 PM

follow up - complete!

well we brought the enormous hot tub into my back patio, (through city
fence which i repaired. was 7.5 x 7.5 by about 4' high - a nice size
5-7 person spa. also had to rotate it 90, not only that but raining
steadily here in Denver all morning, but I didn't mind that, as the
park my place backs up to was empty and no cars around - made backing
in the trailer easier.

the electrical company, who i've used before, came saturday afternoon,
same day - and rain a new four wire connect straight from my breaker
box (see my above diagram), out to the patio. i have a disconnect box
next to the AC disconnect box. it's fully up to code, the disconnect
box is five feet from the tub, and the guy they sent has done spas
before, so he hardwired the line directly into the spa.

he did use my dryer breaker, so if i get an electric dryer i'll have to
get my breaker box expanded.

it was a few hundred bucks, but i don't mind as the used spa was a
great price and in great condition (seller getting a new one), and i
feel safe and the electrical is secure and won't damage the spa or
house wiring in the future

thanks for the above responses! it was heated up by Sunday, so made
the miserable task of moving it well worth it.


SteveB June 8th 05 05:53 PM


"james" wrote in message
ups.com...
follow up - complete!

well we brought the enormous hot tub into my back patio, (through city
fence which i repaired. was 7.5 x 7.5 by about 4' high - a nice size
5-7 person spa. also had to rotate it 90, not only that but raining
steadily here in Denver all morning, but I didn't mind that, as the
park my place backs up to was empty and no cars around - made backing
in the trailer easier.

the electrical company, who i've used before, came saturday afternoon,
same day - and rain a new four wire connect straight from my breaker
box (see my above diagram), out to the patio. i have a disconnect box
next to the AC disconnect box. it's fully up to code, the disconnect
box is five feet from the tub, and the guy they sent has done spas
before, so he hardwired the line directly into the spa.

he did use my dryer breaker, so if i get an electric dryer i'll have to
get my breaker box expanded.

it was a few hundred bucks, but i don't mind as the used spa was a
great price and in great condition (seller getting a new one), and i
feel safe and the electrical is secure and won't damage the spa or
house wiring in the future

thanks for the above responses! it was heated up by Sunday, so made
the miserable task of moving it well worth it.


We love ours. You will love yours, too.

Steve



SQLit June 8th 05 10:29 PM


"james" wrote in message
ups.com...
follow up - complete!

well we brought the enormous hot tub into my back patio, (through city
fence which i repaired. was 7.5 x 7.5 by about 4' high - a nice size
5-7 person spa. also had to rotate it 90, not only that but raining
steadily here in Denver all morning, but I didn't mind that, as the
park my place backs up to was empty and no cars around - made backing
in the trailer easier.

the electrical company, who i've used before, came saturday afternoon,
same day - and rain a new four wire connect straight from my breaker
box (see my above diagram), out to the patio. i have a disconnect box
next to the AC disconnect box. it's fully up to code, the disconnect
box is five feet from the tub, and the guy they sent has done spas
before, so he hardwired the line directly into the spa.

he did use my dryer breaker, so if i get an electric dryer i'll have to
get my breaker box expanded.

it was a few hundred bucks, but i don't mind as the used spa was a
great price and in great condition (seller getting a new one), and i
feel safe and the electrical is secure and won't damage the spa or
house wiring in the future

thanks for the above responses! it was heated up by Sunday, so made
the miserable task of moving it well worth it.



dryer breaker?? Not a GFCI? or does the spa provide that protection?